[HN Gopher] Data centers are transitioning from AC to DC
       ___________________________________________________________________
        
       Data centers are transitioning from AC to DC
        
       Author : jnord
       Score  : 295 points
       Date   : 2026-03-25 00:44 UTC (22 hours ago)
        
 (HTM) web link (spectrum.ieee.org)
 (TXT) w3m dump (spectrum.ieee.org)
        
       | shdudns wrote:
       | How is DC better than a three phase delta 800Vrms, at 400Hz?
       | 
       | - Three conductors vs two, but they can be the next gauge up
       | since the current flows on three conductors
       | 
       | - no significant skin effect at 400Hz -> use speaker wire, lol.
       | 
       | - large voltage/current DC brakers are.. gnarly, and expensive.
       | DC does not like to stop flowing
       | 
       | - The 400Hz distribution industry is massive; the entire
       | aerospace industry runs on it. No need for niche or custom parts.
       | 
       | - 3 phase @ 400Hz is x6 = 2.4kHz. Six diodes will rectify it with
       | almost no relevant amount of ripple (Vmin is 87% of Vmax) and
       | very small caps will smooth it.
       | 
       | As an aside, with three (or more) phase you can use multi-tap
       | transformers and get an arbitrary number of poles. 7 phases at
       | 400Hz -> 5.6kHz. Your PSU is now 14 diodes and a ceramic cap.
       | 
       | - you still get to use step up/down transformers, but at 400Hz
       | they're very small.
       | 
       | - merging power sources is a lot easier (but for the phase angle)
       | 
       | - DC-DC converters are great, but you're not going to beat a
       | transformer in efficiency or reliability
        
         | shiroiuma wrote:
         | >- no significant skin effect at 400Hz -> use speaker wire,
         | lol.
         | 
         | What are you talking about? There's a very significant skin
         | effect at 400Hz. Skin effect goes up with frequency. These
         | datacenters use copper busbars, not cable, so skin effect is an
         | important consideration.
        
           | shdudns wrote:
           | At 100 000 A for a 100 MW data center at 1000 V, speaker wire
           | is a joke.
           | 
           | You obviously need at least a dozen stands in parallel!!
           | 
           | Clearly skin effect scales with frequency but, 400 Hz is
           | still low, only 2.5x lines frequency (the scale is by the
           | root); so the skin depth is 3mm. 3mm on each side makes for a
           | pretty hefty rectangular cross-section.
        
             | bigiain wrote:
             | If you could get that 100,000Amps flowing through your
             | speaker wire, the vaporised copper and the plasma channel
             | would probably keep your 100MW flowing, at least until your
             | building caught fire.
        
               | jacquesm wrote:
               | Even your monster cable? ;)
        
               | bigiain wrote:
               | Well, it'd still vaporise, but it'd sound smoother and
               | more musical as it did it, and the soundstage from the
               | plasma arc would be _stunning!_
        
               | jacquesm wrote:
               | It's almost worth the experiment and your cables are a
               | sacrifice I'm willing to make. For science, of course.
        
               | bigiain wrote:
               | You're _so_ right!
               | 
               | I'm pretty sure you have my delivery address from when I
               | bought sorted Lego from you about 10 years back.
               | 
               | Let me know when to expect the 100,000Amp test equipment!
               | 
               | I shall make sure I wear better PPE than just my reading
               | glasses.
               | 
               | :-)
        
               | jacquesm wrote:
               | This would be the funniest thing to do. 100K Amps is
               | doable, the question is for how long. That would be one
               | very impressive bank of capacitors. And to turn a 00 into
               | plasma would have some spectacular side effects, such as
               | raining molten copper across a sizeable area. Just your
               | reading glasses would indeed not be enough, there
               | probably isn't any PPE that I would consider entirely
               | safe other than sufficient distance from ground zero. But
               | now I'm really curious. I have a spot welder that will do
               | bursts of 5KA and that will happily throw the breaker
               | every so many welds. 100KA sustained will be a fair
               | engineering challenge.
               | 
               | Ah, that lego project... that was one I always wondered
               | if I should have industrialized it but sourcing enough
               | lego was a real problem.
        
               | adiabatichottub wrote:
               | Ho ho ho, you asked for it:
               | 
               | https://www.youtube.com/watch?v=OC7sNfNuTNU
        
               | bigiain wrote:
               | See also (as posted elsethread):
               | https://www.youtube.com/watch?v=RoGbrgOhPes
        
               | jacquesm wrote:
               | Holy crap. That's a whole series of bad ideas extremely
               | well executed. That guy probably has never seen what a
               | lead acid battery can do when it explodes. He keeps
               | hiding away from the hot metal but in the path of ~half
               | of those batteries. Ignorance is bliss.
               | 
               | That's low voltage lightning :)
        
               | adiabatichottub wrote:
               | He was gifted an arch flash suit by the guys from
               | Lightening on Demand :D
        
               | jacquesm wrote:
               | "The gift of life". Complete madness.
        
         | adamking wrote:
         | > no significant skin effect at 400Hz -> use speaker wire, lol
         | 
         | now run that unshielded wire 50 meters past racks of GPUs and
         | enjoy your EMI
         | 
         | > The 400Hz distribution industry is massive; the entire
         | aerospace industry runs on it
         | 
         | nothing in that catalog is rated for 100kW-1MW rack loads at
         | 800Vrms
         | 
         | > 3 phase @ 400Hz is x6 = 2.4kHz... Your PSU is now 14 diodes
         | and a ceramic cap
         | 
         | you still need an inverter-based UPS upstream, which is the
         | exact conversion stage DC eliminates
         | 
         | > large voltage/current DC breakers are.. gnarly, and
         | expensive. DC does not like to stop flowing
         | 
         | SiC solid-state DC breakers are shipping today from every major
         | vendor
         | 
         | > DC-DC converters are great, but you're not going to beat a
         | transformer in efficiency or reliability
         | 
         | wide-bandgap converters are at 95%+ with no moving parts
        
           | shdudns wrote:
           | "now run that unshielded wire 50 meters past racks of GPUs
           | and enjoy your EMI"
           | 
           | Multipole expansion scales faster than r^2.
           | 
           | Also, im not in the field (clearly) but GPUs cant handle 2.4
           | kHz? The quarter wavelength is 30km.
           | 
           | "nothing in that catalog is rated for 100kW-1MW rack loads at
           | 800Vrms"
           | 
           | Current wise, the catalog covers this track just fine. As to
           | the voltages, well that's the whole point of AC! The voltage
           | you need is but a few loops of wire away.
           | 
           | "you still need an inverter-based UPS upstream, which is the
           | exact conversion stage DC eliminates"
           | 
           | So keep it? To clarify, this is the "we're too good for
           | plebeian power, so we'll transform it AC->DC->AC", right?
           | 
           | "SiC solid-state DC breakers are shipping today from every
           | major vendor"
           | 
           | Of course they do. They're also pricey, have limited current
           | capability (both capital costs and therefore irrelevant when
           | the industry is awash with GCC money) and lower conduction,
           | and therefore higher heat.
           | 
           | They're really nice though.
           | 
           | "wide-bandgap converters are at 95%+ with no moving parts"
           | 
           | transformers have no moving parts. Loaded they can do 97%+
           | efficiency, or 2MW of heat eliminated on a 100MW center.
        
         | prezk wrote:
         | An advanced AI rack might use 100kW = 800V 125A, requiring
         | gauge 2, quarter inch diameter---this isn't your lol speaker
         | wire. Actually, I apologize, I realized I may be talking to a
         | serious audiophile, didn't mean to disrespect your Monster
         | cables.
         | 
         | The skin depth by the way is sqrt(2 1.7e-8 ohm m / (2 pi 400Hz
         | mu0))=~3mm for copper---OK for single rack, but starts to be
         | significant for the type of bus bars that an aisle of racks
         | might want.
         | 
         | As for efficiency, both 400Hz transformers AND fancy DC-DC
         | converters are around 95% efficient, except that AC requires
         | electronics to rectify it to DC, losing another few percent, so
         | the slight advantage goes to DC, actually.
         | 
         | As for merging power, remember that DC DC converter uses an
         | internal AC stage, so it's the same---you can have multiple
         | primary windings, just like for plain AC.
        
           | bigiain wrote:
           | > I realized I may be talking to a serious audiophile, didn't
           | mean to disrespect your Monster cables.
           | 
           | I am a recovering audiophool.
           | 
           | I do own a pair of 2m long Monster Cable speaker cables (with
           | locking gold plated banana plugs). I am fairly certain I've
           | used welders with smaller cables.
           | 
           | (In my defence, I bought those as a teenager in the late 80s.
           | I am not so easily marketed to with snake oil these days. I
           | hope.)
           | 
           | (On the other hand, I really like the idea of a reliably
           | stable plus and minus 70V or maybe 100V DC power supply to my
           | house. That'd make audio power amplifiers much easier and
           | lighter...)
        
         | hrmtst93837 wrote:
         | 400Hz is an aircraft hack. In a data center, where batteries
         | and most of the stuff behind the PSU already want DC, cutting
         | conversion stages and a bunch of UPS weirdness is a boring win
         | even if DC breakers are nastier and pricier. If you want
         | switchgear with aerospace pricing in a building full of racks,
         | AC at boutique frequencies is one way to get there.
        
       | bandrami wrote:
       | I stg if I see the kids talk about Westinghouse being
       | batterymogged I'm leaving the Internet
        
       | otterley wrote:
       | DC power has been an option for datacenter equipment since I was
       | a young lad racking and stacking hardware. Cisco, Dell, HPE, IBM,
       | and countless others all had DC supply options. Same with PDUs.
       | What's old is new again.
       | 
       | See e.g. https://www.dell.com/support/kbdoc/en-
       | us/000221234/wiring-in...
        
         | bluGill wrote:
         | 48vdc was common in phone exchanges. They filled the basement
         | with lead-acid batteries and to could run without the grid for
         | a couple weeks. In turn the phone was 99.999% reliable for
         | decades.
        
           | mjuarez wrote:
           | Not to be _that_ guy, but it was technically -48V DC.
           | 
           | Honestly, that was pretty surprising to me when I had to work
           | with some telco equipment a couple of decades ago. To this
           | day, I don't think I've encountered anything else that
           | requires negative voltage relative to ground.
        
             | yostrovs wrote:
             | Check out older English cars.
        
             | bluGill wrote:
             | positive ground used to be in all cars. When they went from
             | 6 volts to 12 the disadvantages became appearant fast and
             | so everyone went negative ground then (mid 1950s). I am not
             | clear why positive ground was bad (maybe corrosion?)
        
             | servo_sausage wrote:
             | Is that something other than a labelling convention? Is
             | ground actually connected to a earth stake?
        
               | CamperBob2 wrote:
               | Cathodic protection against corrosion was the goal of
               | using -48V, in the telcos' case.
        
               | myself248 wrote:
               | And the telegraph lines before that.
        
             | jacquesm wrote:
             | Yes, and that tiny little difference can cost you a lot of
             | expensive gear if you run it off the battery and plug in a
             | serial port or something like that. You'll also learn first
             | hand what arc welding looks like without welding glass.
        
             | SAI_Peregrinus wrote:
             | Lots of amplifier circuits need a bipolar supply: both
             | positive and negative voltages with respect to ground.
        
             | aidenn0 wrote:
             | RTL and DTL both needed negative-voltage relative to
             | ground, as do many analog circuits.
        
             | em3rgent0rdr wrote:
             | Some old guitar effects used -9V DC.[1] And the convention
             | with guitar effects power adapter is the barrel is center
             | negative (which is motivated with facilitating easy wiring
             | of the socket's switch to connect to a 9V battery inside).
             | 
             | [1] https://www.analogisnotdead.com/article26/what-is-
             | going-on-w...
        
             | HWR_14 wrote:
             | Can you explain why it's -48 VDC as opposed to 48 VDC with
             | the + and - inputs mislabeled?
        
               | jojobas wrote:
               | In short, ground.
        
               | crote wrote:
               | Because the chassis is connected to ground (as in, a
               | literal grounding rod hammered into the soil) and by
               | definition your 0V reference point.
               | 
               | The crucial difference is the direction in which the
               | current is flowing: is it going "in to", or "out of" a
               | hot wire? This becomes rather important when those wires
               | are leaving the building and are buried underground for
               | miles, where they will _inevitably_ develop minor faults.
               | 
               | With +48V corrosion will attack all those individual
               | telephone wires, which will rapidly become a huge
               | maintenance nightmare as you have to chase the precise
               | location of each, dig it up, and patch it.
               | 
               | With -48V corrosion will attack the grounding rod at your
               | exchange. Still not ideal, but monitoring it isn't too
               | bad and replacing a corroded grounding rod isn't that
               | difficult. Telephone wires will still develop minor
               | faults, but it'll just cause some additional load rather
               | than inevitably corroding away.
        
               | tinyhitman wrote:
               | Do you also happen to why this is not more common? Must
               | be useful for more than just telephone wires.
        
               | bluGill wrote:
               | Most large scale systems are AC because transformers are
               | relatively cheap, low maintenance, and efficient. When
               | the system is AC ground makes no difference.
               | 
               | With DC systems you generally think about the issues -
               | which is why modern cars are negative ground. However
               | other than cars most people never encounter power systems
               | of any size - inside a computer the voltages and
               | distances are usually small enough that it doesn't matter
               | what ground is. Not to mention most computers don't even
               | have a chassis ground plane (there are circuit board
               | ground planes but they conceptually different), and with
               | non-conductive (plastic) cases ground doesn't even make
               | sense.
        
               | jcalvinowens wrote:
               | > When the system is AC ground makes no difference.
               | 
               | With AC it's about where the ground is attached along the
               | length of the transformer secondary. In the EU they
               | ground one of the ends of the secondary, in the US we
               | ground the center point.
               | 
               | I don't get to say this very often ... but the US way is
               | objectively safer with no downside: 99% of human shocks
               | are via ground, and it halves the voltage to ground (120V
               | vs 240V). A neutral isn't required if there aren't 120V
               | loads.
        
               | Liftyee wrote:
               | I agree that the US _voltage_ is safer (with the tradeoff
               | of lower output powers available at your outlets).
               | However, I suspect this is more than negated by the US
               | plug design, which carries a much larger risk of shocks
               | than almost all EU plug designs (Schuko, British /Type G,
               | etc...)
               | 
               | - uninsulated metal pins make contact with supply while
               | partially exposed - much smaller distance between metal
               | pins and the edge of the plug
        
               | jcalvinowens wrote:
               | 100% agree the US plug designs are terrible.
               | 
               | But there's no inherent power tradeoff: you can have 240V
               | outlets in the US, with the two prongs both 120V to
               | ground. They're just really uncommon in residences.
        
               | bluGill wrote:
               | Dryers and Stoves/range outlets are very common in US
               | houses. Of course they are generally hidden behind the
               | device and so most people are not sure if they have them
               | at not. They are also reasonably common in garages
               | (welders, air compressors, table saws... - if your hobby
               | needs them you install them, otherwise you won't have
               | them).
        
               | crote wrote:
               | In the EU it is quite common for houses to have three-
               | phase power. If you squint a bit, the grounded neutral of
               | the Y transformer isn't entirely unlike the grounded
               | center tap in the US. The voltage is a lot higher, of
               | course!
        
               | Dylan16807 wrote:
               | > If you squint a bit, the grounded neutral of the Y
               | transformer isn't entirely unlike the grounded center tap
               | in the US.
               | 
               | Yes, but you only get the safety benefit on three phase
               | equipment.
               | 
               | In the US there aren't a lot of 240V plugs, but if you
               | get some installed you can get the safety benefits with
               | plain old consumer goods.
        
               | crote wrote:
               | It is! Look up "impressed current cathodic protection":
               | you apply a small DC voltage to, say, pipelines to
               | prevent corrosion.
        
               | nhecker wrote:
               | I ran into a guy at a hardware store who ran just such a
               | power supply attached our city's water (or was it natural
               | gas?) infrastructure. I was incredulous, but the idea
               | that it helped prevent corrosion did make sense.
        
               | HWR_14 wrote:
               | So, there is a true value for 0?
               | 
               | Does that mean when you have electronics and use multiple
               | dc-dc converters all the inputs and outputs share the
               | same ground, it's not just the values for that pair of
               | wires?
               | 
               | And if I want to use a telephone on an incorrectly wired
               | 48dc circuit, I could switch the positive and negative
               | wires, as long as the circuit in the telephone is
               | isolated and never touches ground?
               | 
               | Thanks. Somehow I got in my head that all circuits were
               | just about the delta from neutral and therefore nothing
               | outside them mattered.
        
               | wat10000 wrote:
               | There is a true zero potential. You can detect this
               | because two charged objects with zero delta between them
               | will still repel each other.
               | 
               | I think a circuit should mostly care about the deltas,
               | but when you're talking about things like phone lines,
               | the earth becomes part of your circuit. You can't
               | influence its potential (it's almost exactly neutral
               | because any charge imbalance gets removed by interaction
               | with the interplanetary medium) so everything else is
               | going to end up being determined by what you need for
               | their relative potential to that.
        
               | bonzini wrote:
               | > all the inputs and outputs share the same ground, it's
               | not just the values for that pair of wires?
               | 
               | No, it depends on the converter. There are converters
               | that leave 160V on the DC power rail for a 110V AC input,
               | and 155V on the DC "ground" rail.
               | 
               | They are economic and you could find then when galvanic
               | isolation is at least in theory not important, but
               | they're terribly unsafe when used on PCBs that people
               | might muck with.
               | 
               | If you have some "normal" converters and some of this
               | kind, sharing the ground would be quite dangerous.
        
             | fecal_henge wrote:
             | I am STILL designing hardware for -48v telco standard. The
             | first thing we do is convert -48 -> 48v. That's 4 square
             | inches of PCB space we waste.
        
               | eqvinox wrote:
               | What do you need +48V for?
        
               | pluies wrote:
               | Well if it's negative 48V the electricty flows out of
               | your circuit and back to the grid, so you need to make it
               | positive to have the electricity come in.
        
               | djmips wrote:
               | Likely as a basis for converting to other useful DC
               | voltages.
        
               | fecal_henge wrote:
               | We go -48 -> 48 -> 12 -> 3v3,1v8 etc etc. If you went 48
               | straight to POL voltages then you would have horrific
               | converter performance.
        
               | eqvinox wrote:
               | > If you went 48 straight to POL voltages then you would
               | have horrific converter performance.
               | 
               | What's horrific converter performance in numbers?
               | 
               | An isolated flyback (to 12V) should be able to hit >92%
               | and doesn't care if it's fed -48V or +48V or +-24V. TI
               | webench gives me 95% though I'd only believe that if I'd
               | built and measured it. What's the performance of your
               | -48V - +48V?
               | 
               | [with the caveat that these frequently require custom
               | transformers... not an issue with large runs, but finding
               | something that can be done with an existing part for
               | smaller runs is... meh]
        
               | fecal_henge wrote:
               | -48 to 48 claims something like 97% (load dependent of
               | course). It also needs to arbitrate between two input
               | supplies for glitchless redundancy, plus have PM bus and
               | other spec mandated stuff. There is no technical reason
               | why you cant go -48 -> 12 as you state with good
               | efficiceny, but we cant get hold of a part that ticks all
               | the boxes.
               | 
               | Horrific performance by my definition would be 48v to say
               | 1v. We only realistically use buck topologies for POL
               | supplies. Such a ratio is really bad for current
               | transients, not to mention issues like minimum on times
               | for the controller.
        
               | eqvinox wrote:
               | I'm just surprised that either input isolation isn't on
               | your spec, or it still somehow works out better with
               | isolated to +48V than straight to 12V... but I guess if
               | your spec requires other things, it makes sense.
               | 
               | (Thanks for the info!)
        
             | swed420 wrote:
             | > I don't think I've encountered anything else that
             | requires negative voltage relative to ground
             | 
             | Automotive collectors can probably still relate to cars
             | from the 1920s-50s having a "positive ground."
        
               | fuzzfactor wrote:
               | With positive ground the traditional more-sacrificial
               | spark plugs lasted longer.
        
           | divbzero wrote:
           | Interesting, so this is why the phone line still worked when
           | power was out across the whole town.
        
             | eqvinox wrote:
             | Yeah, it used to be that you could still make calls
             | (particularly to emergency services) even in complete power
             | outages, for as long as your local exchange has batteries
             | for. (AFAIR that tended to be on the order of hours, but
             | probably differs quite a bit across locations and
             | regulatory domains/countries.)
             | 
             | Another thing we lost in the age of VoIP landlines, but
             | then again mobile towers also have batteries. Just don't be
             | unlucky and have a power outage with 3% battery on your
             | phone...
        
           | MathMonkeyMan wrote:
           | Yeah I always heard that the phone lines carried their own
           | power, and in Florida the phones did keep working when the
           | power went out, but I never knew why.
           | 
           | So the grid was always charging up the lead acid batteries,
           | and the phone lines were always draining them? Or was there
           | some kind of power switching going on where when the grid was
           | available the batteries would just get "topped off"
           | occasionally and were only drained when the power went out?
        
             | bluGill wrote:
             | Grid charging batteries, phone draining them as I
             | understand. Of course there were switches all over the us
             | so I can't make blanket claims but from what I hear that
             | was normal.
        
             | pocksuppet wrote:
             | The phone grid predated the electrical grid. There was no
             | other choice for power.
             | 
             | Actually, there was one. Even earlier phones had their own
             | power. A dry-cell battery in each phone, and every 6
             | months, the phone company would come around with a cart and
             | replace everyone's battery. Central battery was found to be
             | more convenient, since phone company employees didn't have
             | to go around to everyone's site. Central offices could
             | economize scale and have actual generators feeding
             | rechargeable batteries.
        
             | qingcharles wrote:
             | It's a pretty decent chunk of power down a POTS cable too,
             | as it was designed to ring multiple big chunky metal bells
             | in the days of yore.
             | 
             | I was wiring in a phone extension for my grandma once as a
             | boy and grabbed the live cable instead of the extension and
             | stripped the wire with my teeth (as you do). I've been
             | electrocuted a great number of times by the mains AC, but
             | getting hit by that juicy DC was the best one yet. Jumped
             | me 6ft across the room :D
        
               | rdtsc wrote:
               | The teeth. Yikes! But yeah, I remember having the rotary
               | phone disassembled and touching the wires adjusting
               | something when a ring came. Gave me enough of a jolt to
               | remember.
        
               | elcritch wrote:
               | I discovered the same exact thing wiring a second phone
               | line to my bedroom as a teenager. I jumped into a pile of
               | fiberglass insulation! :/
        
             | SigmundA wrote:
             | The batteries and phone lines were one system at -48v with
             | power supplies converting AC power to DC while grid /
             | generator is up.
             | 
             | The batteries are floated at the line voltage nothing was
             | really charging or discharging and there was no switchover.
             | 
             | This is similar to your cars 12v dc power system such the
             | when the car is running the alternator is providing DC
             | power and the batteries float doing nothing except
             | buffering large fluctuations stabilizing voltage.
        
           | idiotsecant wrote:
           | I still have a bunch of 48vdc comms gear in my powerplant.
        
             | beAbU wrote:
             | Why do you have a powerplant?
        
               | bluGill wrote:
               | Power plant is the convention for any large company that
               | has backup power. A few UPSes for the server room - they
               | are the power plant. A backup generator - power plant.
               | Sometimes even just the room with all the break boxes
               | from where the grid comes in is called the power plant
               | (though normally power plant is reserved for backup
               | power). It is extremely common for commercial buildings
               | to have their own power plant. Most of their power comes
               | from the grid in all cases, but they have a power plant.
               | At commercial scale you can often save money by buying a
               | backup generator powerful enough for your whole building
               | so you disconnect from the grid when grid power is in
               | highest demand (see your utility, then your accountant:
               | for details if you can afford a generator this large)
        
           | tverbeure wrote:
           | -48V! :-)
        
           | boricj wrote:
           | I'm working on stuff in that market, it's still largely is.
           | _DC Power System Design For Telecommunications_ is still a
           | must read and it doesn 't even cover the last 15 years or so
           | of development, notably lithium batteries and high efficiency
           | rectifiers.
           | 
           | I will say that this is a surprisingly deep and complex
           | domain. The amount of flexibility, variety and scalability
           | you see in DC architectures is mind-boogling. They can span
           | from a 3kW system that fits in 2U all the way to multiples of
           | 100kWs that span entire buildings and be powered through any
           | combination of grid, solar and/or gas.
        
           | amelius wrote:
           | You need thick cables if you want to power a rack with 48V.
        
           | superxpro12 wrote:
           | This reminds me of the early google data centers that
           | directly soldered those massive duracell lantern batteries
           | directly to the motherboards as a primitive battery backup.
           | I'm struggling to google examples of it, this would have been
           | back around 2008, but i have a vivid memory of it.
           | 
           | edit: found it https://www.cnet.com/tech/tech-
           | industry/google-uncloaks-once...
        
         | _fizz_buzz_ wrote:
         | Obviously 48VDC has been around and internally they will
         | probably still step down to 48V. But these 48V islands are
         | nowadays inter connected by regular AC grid. They want to
         | replace that interconnection with a 800VDc bus. I kind of
         | assume they chose 800vdc because there are already bunch of
         | stuff available from EVs which also have 800vdc battery packs
         | now.
        
           | 15155 wrote:
           | They chose 800VDC because it's a convenient multiple that is
           | the peak possible with a two-level 650V (probably GaN) FET
           | arrangement.
        
             | eternauta3k wrote:
             | And why is 650V special?
        
               | 15155 wrote:
               | Historical, physical, engineering reasons.
               | 
               | Much of the world's mains-voltage electronics run at 240V
               | (historical) and have PFC circuits (which are essentially
               | just boost converters) that run at ~400V DC link
               | voltages. 650V gives you enough headroom to tolerate
               | overshoots and still have an 80% safety margin with a
               | single level topology.
               | 
               | This voltage also coincidentally is a convenient
               | crossover point where silicon MOSFETs start to become
               | inefficient and GaN FETs have recently become feasible
               | and mass-produced.
        
         | _zoltan_ wrote:
         | 800V DC is definitely not "old".
        
       | stego-tech wrote:
       | I've been hearing this line for over a decade, now. "Immersion
       | cooling will make data centers scale!" "Converting to DC at the
       | perimeter increases density!"
       | 
       | Yes, of course both of those things are true, and yes, some data
       | centers do engage in those processes for their unique advantages.
       | The issue is that aside from specialty kit designed for that use
       | (like the AWS Outposts with their DC conversion), the rank-and-
       | file kit is still predominantly AC-driven, and that doesn't seem
       | to be changing just yet.
       | 
       | While I'd love to see more DC-flavored kit accessible to the
       | mainstream, it's a chicken-and-egg problem that neither the power
       | vendors (APC, Eaton, etc) or the kit makers (Dell, Cisco, HP,
       | Supermicro, etc) seem to want to take the plunge on first. Until
       | then, this remains a niche-feature for niche-users deal, I wager.
        
         | otterley wrote:
         | Those vendors all have DC power supply options, to my
         | knowledge. It's hardly new; early telco datacenters had DC
         | power rails, since Western Electric switching equipment ran on
         | 48VDC.
         | 
         | https://www.nokia.com/bell-labs/publications-and-media/publi...
        
           | stego-tech wrote:
           | That's just it though, telco DCs != Compute DCs. Telcos had a
           | vested interest in DC adoption because their wireline
           | networks used it anyway, and the fewer conversions being done
           | the more efficient their deployments were.
           | 
           | Every single DC I've worked in, from two racks to hundreds,
           | has been AC-driven. It's just cheaper to go after
           | inefficiencies in consumption first with standard kit than to
           | optimize for AC-DC conversion loss. I'm not saying DC isn't
           | the future so much as I've been hearing it's the future for
           | about as long as Elmo's promised FSD is coming "next year".
        
             | jacquesm wrote:
             | I think the real reason is because battery power didn't
             | have to be converted twice to be able to run the gear in
             | case of an outage, so you'd get longer runtime in case of a
             | power failure, and it saves a bunch of money on supplies
             | and inverters because you effectively only need a single
             | giant supply for all of the gear and those tend to be more
             | efficient (and easier to keep cool) than a whole raft of
             | smaller ones.
        
         | arijun wrote:
         | Surely if it makes sense for the big players, they will do it,
         | and then the benefits will trickle down to the rest? Like how
         | Formula 1 technology will end up in consumer vehicles.
        
         | gizmo686 wrote:
         | At least for servers, power supplies are highly modular. It
         | just takes 1 moderately sized customer to commit to buying
         | them, and a DC module will appear.
         | 
         | Looking at the manual for the first server line that came to
         | mind, you can buy a Dell PowerEdge R730 today with a first
         | party support DC power supply.
        
         | dist-epoch wrote:
         | These are GigaWatt data centers. For a single one they buy
         | equipment by the container ship. Nothing is niche about it.
        
         | crote wrote:
         | As seen on HN a few days ago, immersion cooling is dead: turns
         | out the risks of getting sued to oblivion due to widespread
         | PFAS contamination isn't worth it. [0]
         | 
         | DC doesn't have such a killer. There are a decent bunch of
         | benefits, and the main drawback is gear availability. However,
         | the chicken-and-egg problem is being solved by hyperscalers.
         | Like it or not, the rank-and-file of small & medium businesses
         | is _dying_ , and massive deployments like AWS/GCP/Azure/Meta
         | are becoming the norm. Those four already account for 44% of
         | data center capacity! If they switch to DC can you still call
         | it "specialty kit", or would it perhaps be more accurate to
         | call it "industry norm"?
         | 
         | It is becoming increasingly obvious that the rest of the
         | industry is essentially getting Big Tech's leftovers. I
         | wouldn't be surprised if DC became the norm for colocation over
         | the next few decades.
         | 
         | [0]: https://thecoolingreport.com/intel/pfas-two-phase-
         | immersion-...
        
           | mrguyorama wrote:
           | They poison water supplies, knowingly, for decades, and it
           | only takes $12 billion dollars to finally get them to stop?
           | 
           | Fucks sake.
        
         | KaiserPro wrote:
         | Immersion cooling was/is so fucking impractical it is only
         | useful for very specific issues. If you talk to any engineer
         | who worked on CRAY machines that were full of liquid freon,
         | they'll tell how hard it is to do quick swaps of anything.
         | 
         | Its much cheaper, quicker and easier to use cooling blocks with
         | leak proof quick connectors to do liquid cooling. It means you
         | can use normal equipment, and don't need to re-re-enforce the
         | floor.
         | 
         | A lot of "edge" stuff has 12/48v screw terminals, which I
         | suspect is because they are designed to be telco compatible.
         | 
         | For megawatt racks though, I'm still not really sure.
        
           | kjs3 wrote:
           | We had a cluster of liquid cooled CDC Cyber mainframes. One
           | of them developed a bad leak and managed to drain itself into
           | the raised floor. This was a Very Bad Day for many folks in
           | the computer center.
           | 
           | Edit: s/have/had/
        
         | jeffbee wrote:
         | It is weird to me how far from the state of the art mainstream
         | server equipment is. I can't imagine anything worse than AC-AC
         | UPS, active PDUs, and redundant AC-DC supplies in each rack
         | unit, but that's still how people are doing it.
        
         | _zoltan_ wrote:
         | I recommend reading these two:
         | 
         | https://developer.nvidia.com/blog/nvidia-800-v-hvdc-architec...
         | 
         | https://blogs.nvidia.com/blog/gigawatt-ai-factories-ocp-vera...
         | 
         | almost everybody in the industry is embracing 800V DC mostly
         | because of Vera Rubin and the increased electricity
         | requirements.
        
       | hristov wrote:
       | It is absolutely stupid to talk about this as edisons revenge. If
       | Tesla had the modern high power transistors needed to get high
       | voltage dc out of the ac produced from a spinning turbine he
       | would be all for high voltage dc too. Tesla understood that high
       | voltage was needed for efficient long range transmission. He also
       | understood that transformers were the inly remotely efficient way
       | to climb up to and down from these high voltages. And
       | transformers only work with ac. So he designed an ac system and
       | even designed some better transformers for it.
       | 
       | If there was anything like a high power transistor back then he
       | would have used that. High power transistors that are robust
       | enough to handle the grid were designed inly recently over 100
       | years after the tesla/edison ac/dc argument.
        
         | arijun wrote:
         | Also, if anything would have been Edison's revenge it would
         | have been HVDC, where they're sending power long distances with
         | DC. (But as you said, even there it wouldn't make a ton of
         | sense, since they were arguing in a different era).
        
           | themafia wrote:
           | The two primary reasons to do that are to allow the intertie
           | of two AC grids that are not otherwise synchronized, and to
           | take advantage of "earth return" paths when necessary to
           | double the capacity of the line. The latter you may need to
           | consider just to make the line cost effective over an
           | equivalent AC span.
        
         | bluGill wrote:
         | Tesla also design the modern induction motor which needs ac.
         | Though these days we often run them on a phase generator which
         | has a dc step.
        
         | jacquesm wrote:
         | Agreed, for the IEEE to go down this route is more than a
         | little weird.
        
         | Georgelemental wrote:
         | It's just a fun title, you are overthinking it
        
         | chrneu wrote:
         | the internet really needs to stfu about tesla and get over that
         | oatmeal comic that spawned a billion internet myths. dude was a
         | decent inventor but suffered from chronic mental health issues
         | and, in his lifetime, wasted so much time/energy/money and
         | burned so many bridges with his horrible attitude. there's a
         | reason most people didnt like him in his day, he was a
         | depressed asshole who alienated everyone around him, and yes I
         | know he was likely gay in a time when that wasn't cool. the
         | fact still remains; his inventions are massively overblown by
         | internet nerds.
         | 
         | the podcaster Sebastian Major from "Our Fake History" did a
         | looonnngg patreon episode on tesla and debunked most of the
         | weird myths around tesla. Sebastian doesn't have a vendetta or
         | anything, it's just amazing how much of the Tesla stuff is just
         | nonsense or is viewed through a very weird bias nowadays. Major
         | also briefly touches on the weird Edison stuff and how the
         | internet has twisted Edison into a villain.
        
           | anonymousiam wrote:
           | Tesla was an outstanding technologist, but a poor
           | businessman. He had a "vision" (actually more than one) about
           | how his ideas could transform the world. Some of his ideas
           | were amazing, but he was swindled out of his patents because
           | the investors knew he had a passion and wanted to see them in
           | use. The polyphase AC motor or fluorescent light bulb could
           | have made him millions.
           | 
           | IMHO, the vision he had about universal free electricity
           | (transmitted wirelessly) was the dumbest. It was a novel
           | idea, and he invested a lot (his time and other people's
           | money) in it. The problem with his idea is that there was no
           | way to monetize it (and profit from it). (There were also the
           | technical issues of the power loss over distance (1/R^2), the
           | harm to the environment, and the interference with radio
           | communications.)
           | 
           | Edison was quite a villain. He stole many of his
           | "inventions", and orchestrated a PR campaign against Tesla
           | touting the "evils" of AC power. AFAIK, the electric chair
           | was either invented or inspired by him.
           | 
           | I know these things because I've read many books on various
           | topics related to Tesla, and all of this knowledge predates
           | the Internet.
        
             | HWR_14 wrote:
             | Edison did not invent the electric chair. When the
             | inventors were trying to choose between using AC or DC he
             | helped them decide on AC as part of his PR campaign.
        
             | fsh wrote:
             | Essentially none of this is true. The war of the currents
             | was between Edison and Westinghouse, not Tesla. Tesla's
             | downfall was that he turned into a crackpot who rejected
             | modern science, such as Maxwell's equations, and started
             | defrauding investors. Edison was an outspoken opponent of
             | the death penalty, and the electric chair used AC simply
             | because it is much more deadly.
        
               | chipster_f00 wrote:
               | > The war of the currents was between Edison and
               | Westinghouse [...]
               | 
               | Thank you for quashing the gross misinformation. I was
               | going to post this, but searched and found your comment.
               | `\m/`
               | 
               | (I learned of the "Current War" in the 70's, since the
               | Edison Museum was in my "backyard" -- and was a common
               | destination of local school field trips.)
        
           | aaronbrethorst wrote:
           | We're talking about Nikola Tesla, not Elon Musk, and I don't
           | think Musk is gay.
        
             | beAbU wrote:
             | I think you need to read the post you are responding to
             | again.
        
           | elar_verole wrote:
           | People need heroes. It's like the Keanu Reeves or Musk era,
           | all the ""badass"" stories about this or that soldier / local
           | hero / w/e that are very often overblown and get further and
           | further away from the initial facts every time they
           | resurface. No hate here, just noticing there is a weird
           | visceral need to distill stories to their most essential,
           | good vs evil, and the Tesla v Edison thing embodies this
           | perfectly I think.
        
             | Imustaskforhelp wrote:
             | Keanu Reeves and Nikola Tesla to a degree as well, are
             | decent figures.
             | 
             | Aside from all the cult classics Keanu is part of like john
             | wick and the matrix, even discounting that, he is a good
             | person in it of itself who is genuinely humble and might be
             | one of the best persons within hollywood.
             | 
             | What I feel pissed about is that people like Andrew Tate
             | and others like them took the concept of Matrix and the
             | contributions Keanu did within that movie and tried to
             | capitalize on that cult classic decades after in the most
             | toxic form that might be the issue if we are talking about
             | an era
             | 
             | To be honest, Nikola tesla is also a great person within
             | the context of his time. GGP's comment is still true but
             | Tesla's contributions can hardly be reinstated and I'd much
             | rather people believe these to be the heros (Keanu/Tesla)
             | rather than Tate/Musk etc.
             | 
             | If I take anything from Keanu, I would like to take his
             | humility/humbleness.
        
               | giancarlostoro wrote:
               | Tate is just attention hungry. It's pretty obvious. If
               | you feed no attention to him, he will go back to where he
               | crawled from.
        
               | ndsipa_pomu wrote:
               | Whilst I agree that Keanu is a most excellent human, he
               | was hardly responsible for the concept of the Matrix. In
               | my opinion, Philip K Dick was a major influence (I'm a
               | fan and consider him the prophet of the modern age),
               | though Gibson's Neuromancer was likely a big influence
               | too. (Also, there's the old Doctor Who episode "The
               | Deadly Assassin" which features the Matrix).
               | 
               | It always seems to me that the far right are bereft of
               | original ideas and always co-opt other pre-existing
               | concepts. There's exceptions, but I always find that
               | right wing works are always lacking humour or irony (c.f.
               | Ayn Rand's works).
        
               | something765478 wrote:
               | > the far right are bereft of original ideas and always
               | co-opt other pre-existing concepts.
               | 
               | That's not unique to them: Good artists copy; great
               | artists steal.
        
               | ndsipa_pomu wrote:
               | Yes, but I'd have difficulty in pronouncing Andrew Tate
               | as a good or great artist. Maybe con-artist would be the
               | highest that I'd go.
        
               | tomtomtom777 wrote:
               | "It is only the unimaginative who ever invents. The true
               | artist is known by the use he makes of what he annexes.
               | And he annexes everything."
               | 
               | - Oscar Wilde
        
             | ngvrnd wrote:
             | Except for Keith Moon. All the stories about him are true
             | and if anything underplay the truth. :-)
        
           | boomskats wrote:
           | I mean yeah, but it's not like the guy's 'horrible attitude'
           | came from nowhere. He naiively romanticised migrating to the
           | US thinking the game was about scientific progress rather
           | than capital, and so he got repeatedly screwed over by almost
           | everyone around him for decades.
           | 
           | If I was in his position I'm not sure I'd have taken it as
           | well as he did.
        
             | wil421 wrote:
             | There's no way he suddenly developed autism or whatever
             | mental illness plagued him upon arrival to American. Like
             | most absolute geniuses he struggled in other areas. He said
             | he had visions as a child.
        
               | balamatom wrote:
               | But there is: his neurotype _suddenly_ became
               | _considered_ "whatever mental illness" upon arrival in
               | Eugenicsland.
        
           | KaiserPro wrote:
           | > he was a depressed asshole who alienated everyone around
           | him,
           | 
           | enough Edison bashing!
           | 
           | Look, Tesla was a weirdo, but, he was a very good inventor
           | who actually invented shit.
           | 
           | Edison was an industrialist, who knew the price of
           | everything, and wasn't above spending a lot of money to
           | destroy a rival.
           | 
           | Do I idolise Tesla? no, but I respect his understanding of
           | high frequency electronics with _really_ primitive tooling.
           | 
           | Do I despise Edison? also no, but he is a massive prick.
           | Excellent buisness man, but an abrasive prick never the less.
        
           | throw4847285 wrote:
           | Software engineers idolize Tesla because they see themselves
           | as the Tesla (a selfless devotee of the abstract idea of
           | technology) against evil Edisons (businessmen who only care
           | about money and steal other people's ideas). They've
           | basically projected the Jobs/Woz divide back onto two
           | historical figures who, in reality, barely interacted.
           | 
           | The funniest part is that The Oatmeal comic didn't invent
           | this concept, but drew on pre-Internet narratives put forward
           | by The Tesla Society, who were mailing busts of Tesla to
           | universities around the country since the 70s at least. And
           | that organization is explicitly nationalistic and religious,
           | tied to other Serbian-American heritage organizations, and
           | doing events with the Orthodox church.
        
             | balamatom wrote:
             | > And that organization is explicitly nationalistic and
             | religious
             | 
             | So are many Serbs (more so if emigrants from atheist-
             | socialist Yugoslavia, or descendants of folks who moved
             | before WW2) as well as many other nations and organizations
             | (America itself lol). So are many Something-Or-Other-
             | American individuals and communities.
             | 
             | I presume that the organization(s) sending Tesla busts,
             | being American-rooted, have had no illusions about which
             | matters will forever remain impossible to communicate to
             | Americans. (Such as anything not reducible to paperclip
             | optimization.)
             | 
             | Instead, I consider it more likely that the point of
             | promoting Tesla was not to impress anyone in America, but
             | to uplift Serbia and generally the South Slavs of the
             | Balkans _who 'd only gained national sovereignty in Tesla's
             | day_: "look, our heritage has already produced an honest-
             | to-god American inventor half a jebani vek ago, so you guys
             | have zero excuse to act as if you're stuck in the middle
             | ages - do join the cargo cult of mordorn civilization
             | instead, will ya - we got value to extract from ya!"
             | 
             | >They've basically projected the Jobs/Woz divide back onto
             | two historical figures who, in reality, barely interacted.
             | 
             | I'd rather say this has been projected _for_ them, but by
             | whom is anyone 's guess; not like there's a shadowy cabal
             | operating. Besides said Serbian-American heritage promoters
             | and whatever their game is, I guess - but here we're not
             | talking mid-XX century Serbian diaspora any more, but a
             | "culturally nonspecific" audience.
             | 
             | Much safer to call it "a hivemind situation" when nobody
             | knows where some idea comes from, and nobody is accountable
             | for rebroadcasting it either, since it comes pre-tagged as
             | Good and True and Useful and it is wrongthink to doubt
             | those. Especially when the idea is so obviously Useful for
             | excusing nonaction. ("I can't be bothered to learn the
             | first thing about electricity, even the history of why I
             | have access to it in the first place - but now that Tesla
             | guy I've vaguely heard of, he was the great genius of the
             | people! What better reason to Experience a Positive
             | Emotion!")
        
           | tibbydudeza wrote:
           | Did he also not fall in love with a pigeon ?.
        
         | teleforce wrote:
         | >It is absolutely stupid to talk about this as edisons revenge.
         | If Tesla had the modern high power transistors needed to get
         | high voltage dc out of the ac produced from a spinning turbine
         | he would be all for high voltage dc too.
         | 
         | This!
         | 
         | The soon people realized these facts the better. The pervasive
         | high rise buildings did not happen before the invention of
         | modern cranes.
         | 
         | Exactly twenty years ago I was doing a novel research on GaN
         | characterization, and my supervisors made a lot money with
         | consulations around the world, and succesfully founded govt
         | funded start-up company around the technology. Together with
         | SiC, these are the two game changing power devices with
         | wideband semiconductor technology that only maturing recently.
         | 
         | Heck, even the Nobel price winning blue LED discovery was only
         | made feasible by GaN. Watch the excellent video made by
         | Veritasium for this back story [1].
         | 
         | [1] Why It Was Almost Impossible to Make the Blue LED:
         | 
         | https://youtu.be/AF8d72mA41M
        
           | mcbishop wrote:
           | I've heard the EV charging has played a big role in the
           | maturation of GaN / SiC.
        
             | teleforce wrote:
             | Yes, EV and high frequency electronics (microwave, mmWave,
             | photonics) that require very fast switching capability.
        
               | UltraSane wrote:
               | And military radars love GaN
        
           | jibal wrote:
           | https://shrunk.ai/research-journals/f/cranes-skyhooks-and-
           | it...
        
           | ta9000 wrote:
           | Does that mean when we run out of Ga there are no more LED
           | TVs?
        
             | AndrewDucker wrote:
             | Why would we run out of Ga?
        
               | mikkupikku wrote:
               | There's a component of modern culture that trains and
               | expects people to be extremely pessimistic about long
               | term human development. It results in situations above,
               | where without any further information people just assume
               | by default that were going to run out of a thing and are
               | on some collision course with not just a disaster, but
               | every single conceivable one.
               | 
               | (Gallium is a byproduct of aluminum production. We aren't
               | going to run out.)
        
               | threetonesun wrote:
               | My understanding of most elements is if we want more it's
               | either pretty easy to make from something else we have a
               | lot of, or we need to redo the Big Bang, the latter
               | being, in my opinion, a bit of a disaster scenario.
        
               | nkrisc wrote:
               | Even synthesizing helium is prohibitively expensive.
               | Unless you want whatever heavy decay products we have
               | from nuclear waste, synthesizing elements at industrial
               | scale probably isn't happening.
               | 
               | Unless by "make from something" else you mean extract the
               | element from existing chemical compounds found in Earth,
               | in which case we're still just using existing deposits on
               | Earth.
        
               | bananaflag wrote:
               | On the other hand, it is possible to run out of a metal
               | when all of it is either somewhere in some device or
               | scattered among landfills (i.e. not concentrated in a
               | place like a mine).
        
               | nkrisc wrote:
               | That's still not running out. It's still there, just more
               | effort to get.
        
               | card_zero wrote:
               | "At 10 parts per quadrillion, the Earth's oceans would
               | hold 15,000 tonnes of gold", says the Wikipedia page on
               | gold.
               | 
               | I'm inclined to think we've lost that gold.
        
               | nkrisc wrote:
               | Practically speaking, sure. It's obviously not cost-
               | effective to extract it. But it's there if someone can
               | get it. I don't expect anyone to be extracting gold from
               | ocean water, but there are other source of other elements
               | that may not be cost-effective now but could be in the
               | future or may simply become necessary despite the cost.
        
               | PowerElectronix wrote:
               | Effort high enough to consider that material lost to any
               | practical purpose like a tv.
        
               | swiftcoder wrote:
               | Cost scales with refinement effort, so it just results in
               | more expensive TVs. That said, pretty sure we'll have
               | drowned the planet in landfilled TVs long before this
               | becomes a serious issue
        
               | nkrisc wrote:
               | If prices of certain metals were high enough I bet people
               | would stop throwing out TVs and dig up old ones from the
               | dump.
        
               | margalabargala wrote:
               | It's a byproduct of aluminum production.
               | 
               | The earth's crust is 8% aluminum.
               | 
               | We will have bigger problems before hitting this one.
        
               | adrian_b wrote:
               | That is true, but gallium is present in the aluminum and
               | zinc ores only in minute quantities.
               | 
               | We will not remain without gallium, but it is impossible
               | to scale up the gallium production to a higher level than
               | provided by the current productions of aluminum and zinc.
               | 
               | So there is a maximum level of gallium that can be used
               | per year and it would not be possible to increase the
               | production of blue and white LEDs and of power
               | transistors above that level.
               | 
               | Fortunately, the amount of gallium used per device is
               | very small, so it is not likely that we will hit that
               | level soon. A much more serious problem is the associated
               | consumption of indium, for which the resources are much
               | less.
        
               | ta9000 wrote:
               | Thanks for providing a real answer.
        
               | pwndByDeath wrote:
               | Its concentrated in a place like a landfill that already
               | has access for large vehicles.
        
               | pyrale wrote:
               | > On the other hand, it is possible to run out of a metal
               | when all of it is either somewhere in some device or
               | scattered among landfills
               | 
               | The metal isn't going to disappear, but it won't be
               | concentrated enough to be as easily retrievable.
        
             | myrmidon wrote:
             | Sidenote: Whenever someone tells you that (vital) reserves
             | of some ressource are going to run out soonish (implying
             | drastic consequences), you should be _extremely_ skeptical:
             | 
             | Such predictions have an abysmal historic track record,
             | because we tend to find workarounds both on the supply side
             | (=> previously undiscovered reserves) as well as
             | flexibility on the demand side (using substitutes).
             | 
             | This applies historically for oil, lithium, rare earth
             | metals and basically everything else.
             | 
             | edit: I'm not saying we're never gonna run out of
             | anything-- I'm just saying to not expect sudden,
             | cataclysmic shortages in general, but instead steadily
             | rising prices and a somewhat smoothish transition to
             | alternatives.
        
               | mschuster91 wrote:
               | > Such predictions have an abysmal historic track record,
               | because we tend to find workarounds both on the supply
               | side (=> previously undiscovered reserves) as well as
               | flexibility on the demand side (using substitutes).
               | 
               | That's a classic example of the "preparedness paradox"
               | [1]. When no one raises the alarm in time or it is being
               | ignored, resources can go (effectively) exhausted before
               | alternatives can be found, or countries either need to
               | pay extraordinary amounts of money or go to war outright
               | - this has happened in the past with guano [2], which was
               | used for fertilizer and gunpowder production for well
               | over a century until the Haber-Bosch ammonia process was
               | developed at the start of the 20th century.
               | 
               | And we're actually seeing a repeat of that as well
               | happening right now. Economists and scientists have
               | sounded the alarm _for decades_ that oil and gas are
               | finite resources and that geopolitical tensions may
               | impact everyone... no one gave too much of a fuck because
               | one could always  "drill baby drill", and now look where
               | we are - Iran has blasted about 20% of Qatar's LNG
               | capacity alone to pieces and blocked off the Strait of
               | Hormuz, sending oil prices skyrocketing.
               | 
               | [1] https://en.wikipedia.org/wiki/Preparedness_paradox
               | 
               | [2] https://en.wikipedia.org/wiki/Guano
        
               | myrmidon wrote:
               | I don't see the Guano industry as a straight counter-
               | example, it even illustrates my point:
               | 
               | If you had made predictions/scenarios in 1850 based on
               | Guano deposits running out within a decade or two, you
               | would have mispredicted completely, because a lot of the
               | industry just transitioned to sodium nitrate (before
               | synthetic fertilisers took over). Nowadays media
               | landscape would've gladly made such doom-and-gloom
               | predictions for global agriculture back then.
               | 
               | I completely agree that quickly depleting reserves often
               | indicate non-sustainable pricing for ressources (which is
               | obviously bad long term), but that is very different from
               | sudden collapse.
        
               | bluGill wrote:
               | I've seen articles from the 1880s claiming oil will run
               | out by 1890. 140 years latter...
               | 
               | Yes we can run out of oil, but nobody really knows if or
               | even when that will happen. Right now I'm guessing we
               | won't run out because wind and solar is so much cheaper
               | for most purposes everyone is shifting anyway - this will
               | take decades to play out.
        
               | reylas wrote:
               | I always add "cheap" to the sentence. It seems they are
               | always talking about the cheap version of anything. Going
               | to run out of water? Or are we running out of the "cheap"
               | version of water that does not have to be processed?
        
               | myrmidon wrote:
               | This is a valid point: quickly depleting reserves often
               | indicate that pricing is not sustainable. Which is bad.
               | 
               | But non-sustainable pricing is very different from
               | "cataclysmic collapse", and too many people expect the
               | latter for too many things, which is just not realistic
               | in my view (and historical precendent makes a strong case
               | against that assumption, too).
               | 
               | A society where water prices gradually increases to
               | "reverse-osmosis only" (instead of "pump-from-the-ground-
               | everywhere") levels is very different from a society
               | where water suddenly runs out.
        
             | nancyminusone wrote:
             | Except for gaseous hydrogen and helium, and some
             | spacecraft, all other atoms remain on the earth and are
             | recoverable with enough energy and effort.
        
               | philipkglass wrote:
               | One more exception: uranium. It actually splits into
               | smaller atoms when it's used as fuel.
        
             | adrian_b wrote:
             | Gallium is expensive to extract because it is extremely
             | diluted in the environment.
             | 
             | It accompanies in very low quantities aluminum and zinc, so
             | it is extracted only in the mines of aluminum or of zinc,
             | as a byproduct.
             | 
             | However, the abundance of gallium is similar to that of
             | lithium, while gallium is used in smaller amounts, so there
             | is no risk to not have enough gallium in the near future.
             | 
             | On the other hand, all semiconductor devices with gallium
             | also use some indium. Indium is used in even greater
             | quantities in all LCD or OLED displays, to make transparent
             | electrodes.
             | 
             | Indium is an extremely rare element in the entire universe,
             | comparable with gold, so for indium there is a much greater
             | risk that its reserves will become insufficient.
             | 
             | This could be mitigated by extracting such critical
             | elements from the dumped electronic devices, but this is
             | very expensive, because only small amounts of indium are
             | used per device, so very large amounts of garbage would
             | have to be processed in order to extract a sizable amount
             | of it.
        
           | da02 wrote:
           | What are some novel processes or technologies you see
           | becoming more important in the next 5-10 years?
        
           | asah wrote:
           | > The pervasive high rise buildings did not happen before the
           | invention of modern cranes.
           | 
           | yyy! if we're going to wander off-topic :-) then I should
           | mention elevators, water pumps, fire suppression including
           | fire truck ladders and more! :-)
        
         | bryanrasmussen wrote:
         | sure, and also Montezuma didn't actually plan on diarrhea
         | ruining people's vacations, but vernacular usage being what it
         | is we have the phrase Montezuma's revenge.
         | 
         | I only found Edison in the headline, I didn't find it anywhere
         | in the body, nor did I find Tesla. Glancing through the article
         | it almost seems like someone tried to make a catchy headline to
         | get clicks.
        
         | fsh wrote:
         | It was Westinghouse who pushed the AC grid against his rival
         | Edison's DC approach. Tesla was a minor figure working for both
         | of them for a bit.
        
         | mr_toad wrote:
         | > If there was anything like a high power transistor back then
         | he would have used that.
         | 
         | Mercury arc rectifiers were used long before his death.
        
           | crote wrote:
           | Yes, but a rectifier only _rectifies_. That 's not going to
           | give you DC-DC conversion - let alone converting it to a
           | _higher_ voltage for long-distance transmission.
        
             | wildzzz wrote:
             | DC-DC before the transistor was difficult to do at scale.
             | Vibrators and relays existed but were not reliable long
             | term.
        
         | amelius wrote:
         | But there was an equivalent: a mechanical switch. Or an
         | electromechanical relay. Or a spinning wheel with electrical
         | contacts.
        
         | ghighi7878 wrote:
         | Title is clickbait. Edison is not mentioned anywhere else in
         | article. I am okay with it.
        
         | superxpro12 wrote:
         | Yeah this isnt an argument. It was far simpler to wrap some
         | copper wire around a chunk of metal than it was to fire up a
         | mosfet fabrication plant in the 1800's.
         | 
         | You can have the best idea in the world, but if you cant
         | manufacture it you're SOL.
        
         | crimshawz wrote:
         | Agree, clickbait.
        
         | metalliqaz wrote:
         | yes, this! thank you good post
        
         | altairprime wrote:
         | Note that one could email the mods to de-clickbait/enrage the
         | title, especially with such a concrete point as this comment's.
         | (I haven't done so as TIL is a poor basis for such an
         | argument.)
        
         | dang wrote:
         | Ok, we've deposed Edison from the title above.
        
       | sghiassy wrote:
       | I've always wondered about these new High-Voltage DC (HVDC)
       | transmission lines.
       | 
       | I always thought AC's primary benefit was its transmission
       | efficiency??
       | 
       | Would love to learn if anyone knows more about this
        
         | cjbgkagh wrote:
         | https://en.wikipedia.org/wiki/High-voltage_direct_current
        
         | adgjlsfhk1 wrote:
         | AC is less efficient than DC at a given voltage. The advantage
         | of AC is that voltage switching is cheap, easy and efficient.
         | Switching DC voltage is way harder, more expensive, and less
         | efficient. However the switching costs are O(1) and the
         | transmission losses are O(n) so for some distance (currently
         | somewhere around 500 km) it's worth paying the switching cost
         | to get super high voltage DC. The big thing that's changed in
         | the last ~30 years is a ton of research into high voltage
         | transistors, and fast enough computers to do computer
         | controlled mhz switching of giant high power transistors. These
         | new super fancy switching technologies brought the switching
         | costs down from ludicrous to annoyingly high.
        
           | arijun wrote:
           | > AC is less efficient than DC at a given voltage
           | 
           | To expand on this, a given power line can only take a set
           | maximum current and voltage before it becomes a problem. DC
           | can stay at this maximum voltage constantly, while AC spends
           | time going to zero voltage and back, so it's delivering less
           | power on the same line.
        
             | adgjlsfhk1 wrote:
             | this iirc is the smallest of 3 problems. the other 2 are
             | skin effect (AC wires only store power on the outside of
             | the wire) and capacitive effects (a write running parallel
             | to the ground is a capacitor and AC current is equivalent
             | to constantly charging and discharging the capacitor)
        
             | manwe150 wrote:
             | That's true, but my understanding is the main contributor
             | is skin effect, since AC travels only on the surface of the
             | wire, while DC uses the whole area, resulting in lower
             | resistance loss (https://en.wikipedia.org/wiki/Skin_effect)
        
             | adiabatichottub wrote:
             | Maybe if by "same voltage" we mean DC voltage the same as
             | AC peak voltage. When we talk about AC voltage we are
             | referring to root-mean-square (RMS) voltage. It's kind of
             | like saying the average, though for math reasons the
             | average of an unbiased sine wave is 0. Anyhooo, 1 VRMS into
             | a load will produce the same power as 1VDC. If AC delivered
             | less power than DC at the same voltage then life would be
             | very confusing.
        
         | cogman10 wrote:
         | The primary benefit of AC is it's really easy to change the
         | voltage of AC up or down.
         | 
         | The transmission efficiency of AC comes from the fact that you
         | can pretty trivially make a 1 megavolt AC line. The higher the
         | voltage, the lower the current has to be to provide the same
         | amount of power. And lower current means less power in line
         | loss due to how electricity be.
         | 
         | But that really is the only advantage of AC. DC at the same
         | voltage as AC will ultimately be more efficient, especially if
         | it's humid or the line is underwater. Due to how electricy be,
         | a change in the current of a line will induce a current into
         | conductive materials. A portion of AC power is being drained
         | simply by the fact that the current on the line is constantly
         | alternating. DC doesn't alternate, so it doesn't ever lose
         | power from that alternation.
         | 
         | Another key benefit of DC is can work to bridge grids. The
         | thing causing a problem with grids being interconnected is
         | entirely due to the nature of AC power. AC has a frequency and
         | a phase. If two grids don't share a frequency (happens in the
         | EU) or a phase (happens everywhere, particularly the grids in
         | the US) they cannot be connected. Otherwise the power
         | generators end up fighting each other rather than providing
         | power to a load.
         | 
         | In short, AC won because it it was cheap and easy to make high
         | voltage AC. DC is comming back because it's only somewhat
         | recently been affordable to make similar transformations on DC
         | from High to low and low to high voltages. DC carries further
         | benefits that AC does not.
        
         | prezk wrote:
         | Important factor is that AC at given nominal voltage V swings
         | between 1.41V and -1.41V, so it requires let's say 40%
         | better/thicker insulation than the equivalent V volts DC line.
         | This is OK for overhead lines (just space the wires more) but
         | is a pain for buried or undersea transmission lines; for that
         | reason, they tend to use DC nowadays.
         | 
         | BTW, megavolt DC DC converters are a sign to behold:
         | https://en.wikipedia.org/wiki/File:Pole_2_Thyristor_Valve.jp...
        
         | topspin wrote:
         | > I always thought AC's primary benefit was its transmission
         | efficiency??
         | 
         | There are many factors involved, and "efficiency" is only one.
         | Cost is the real driver, as with everything.
         | 
         | AC is effective when you need to step down frequently. Think
         | transformers on poles everywhere. Stepping down AC using
         | transformers means you can use smaller, cheaper conductors to
         | get from high voltage transmission, lower voltage distribution
         | and, finally lower voltage consumers. Without this, you need
         | massive conductors and/or high voltages and all the costs that
         | go with them.
         | 
         | AC is less effective, for instance, when transmitting high
         | power over long, uninterrupted distances or feeding high
         | density DC loads. Here, the reactive[1] power penalty of AC
         | begins to dominate. This is a far less common problem, and so
         | "Tesla won" is the widely held mental shortcut. Physics doesn't
         | care, however; the DC case remains and is applied when
         | necessary to reduce cost.
         | 
         | [1] https://en.wikipedia.org/wiki/Electrical_reactance
        
       | umvi wrote:
       | I don't understand why new houses don't just have one high
       | quality AC/DC converter so you can just use LED lighting without
       | every bulb needing its own AC/DC converter. I imagine the light
       | bulb cartel wouldn't really like that.
        
         | bluGill wrote:
         | It wouldn't work. leds need low voltages, meaning massive
         | wires. you can run the voltage change on ac or dc. Ac just
         | needs a few capacters to smooth the wave out.
        
         | throw0101d wrote:
         | > _I don 't understand why new houses don't just have one high
         | quality AC/DC converter so you can just use LED lighting
         | without every bulb needing its own AC/DC converter._
         | 
         | IEEE 802.3bt can deliver up to 71W at the destination: just
         | pull Cat 5/6 everywhere.
         | 
         | *
         | https://en.wikipedia.org/wiki/Power_over_Ethernet#Standard_i...
         | 
         | * https://www.usailighting.com/poe-lighting
        
           | elcritch wrote:
           | And pay $60 per Ethernet POE+ light bulb.
        
             | throw0101d wrote:
             | > _And pay $60 per Ethernet POE+ light bulb._
             | 
             | In the commercial/industrial space this may be worth it:
             | how long do these bulbs last? how much (per hour
             | (equivalent)) do you pay your facilities folks? how much
             | time does it take for employees or tenants to report an
             | outage and for your folks to get a ladder (or scissor lift)
             | to change the bulb?
        
         | fortran77 wrote:
         | Do you want your house to burn down? Lower voltages for LED
         | lights mean higher current.
        
           | bigiain wrote:
           | That's traded off against the increase efficiency of LED
           | lighting, at least compared to incandescent lighting. An LED
           | "equivalent replacement" for a typical incandescent globe is
           | down around 1/10th of the power. A 7Watt LED bulb is
           | typically marketed as "60W equivalent". If that configured as
           | a bunch of LEDs in series (or series/parallel) that need
           | 12VDC, it's right about the same current draw as the 120V 60W
           | incandescent equivalent. (Or perhaps double the current for
           | those of us who get 220VAC out of our walls.)
           | 
           | (Am I just showing my age here? How many of you have ever
           | bought incandescent globes for house lighting? I vaguely
           | recall it may be illegal to sell them here in .au these days.
           | I really like quartz halogen globes, and use them in 4 or 5
           | desk lamps I have, but these days I need to get globes for em
           | out of China instead of being able to pick them up from the
           | supermarket like I could 10 or 20 years ago.)
        
         | Majromax wrote:
         | With modern technologies, that's power over ethernet or USB-C.
         | Other comments in this thread point out that the telephone
         | service also routinely used 48V for the ring signal.
         | 
         | However, higher DC voltage is riskier, and it's not at all
         | standard for electrical and building code reasons. In
         | particular, breaking DC circuits is more difficult because
         | there's no zero-crossing point to naturally extinguish an arc,
         | and 170V (US/120VAC) or 340V (Europe/240VAC) is enough to start
         | a substantial arc under the right circumstances.
         | 
         | Unfortunately for your lighting, it's also both simple and
         | efficient to stack enough LEDs together such that their forward
         | voltage drop is approximately the rectified peak (i.e.
         | targeting that 170/340V peak). That means that the bulb needs
         | only one serial string of LEDs without parallel balancing,
         | making the rest of the circuitry (including voltage regulation,
         | which would still be necessary in DC world) simpler.
        
         | fragmede wrote:
         | because shorts and voltage loss are a real issue at that scale.
        
         | gizmo686 wrote:
         | LED light bulbs exist exclusively for compatibility with Edison
         | sockets. Every LED fixture I have seen had a single transformer
         | for the entire fixture; and that transformer was reasonably
         | separate from the LEDs themselves.
        
         | ianburrell wrote:
         | What voltage do you use? Most DC stuff wants low voltage
         | (5-48V), but appliances need higher voltage like AC-level to
         | get enough power over existing wiring. The result is DC-DC
         | converters every place that have transformers now.
         | 
         | The gain from DC-DC converters is small and DC devices are
         | small part of usage compared appliances. There is no way will
         | pay back costs of replacing all the appliances.
        
         | amluto wrote:
         | Every decent LED would then need ... a switching power supply.
         | LEDs are _current_ -driven devices, and you get the best
         | efficiency if you use an actual current-controlled supply. And
         | those ICs are very, very cheap now.
         | 
         | The part that would genuinely be cheaper is avoiding
         | problematic flicker. It takes a reasonably high quality LED
         | driver to avoid 120Hz flicker, but a DC-supplied driver could
         | be simpler and cheaper.
        
       | adrr wrote:
       | Our houses should be DC. So wasteful to have all these bricks to
       | change to AC to DC.
        
         | bandrami wrote:
         | I've worked overseas a lot and one thing that's really
         | different from 2 decades ago is that I simply don't need a
         | step-down transformer anymore because every single thing I plug
         | in converts to DC (or otherwise accepts dual-voltage) anyways.
         | So I have a giant collection of physical plug adapters because
         | every device I use just needs to fit into the socket and takes
         | care of it from there.
         | 
         | (My stand mixer is the lone sad exception)
        
           | 747fulloftapes wrote:
           | Agreed!
           | 
           | I spent a few years getting flown out around the world to
           | service gear at different datacenters. I learned to pack an
           | IEC 60320 C14 to NEMA 5-15R adapter cable and a dumb, un-
           | protected* NEMA 5-15R power strip. While on-site at the
           | datacenters, an empty PDU receptacle was often easy to find.
           | At hotels, I'd bring home a native cable borrowed from or
           | given to me by the native datacenter staff or I'd ask the
           | hotel front desk to borrow a "computer power cable," (more
           | often, I'd just show them a photo) and they generally were
           | able to lend me one. It worked great. I never found a power
           | supply that wasn't content with 208 or 240V.
           | 
           | Example adapters: https://www.amazon.com/dp/B0FD7PHB7Y or
           | https://www.amazon.com/dp/B01IBIC1XG
           | 
           | *: Some fancier power strips with surge suppression have a
           | MOV over-voltage varistor that may burn up if given 200V+,
           | rendering the power strip useless. Hence, unprotected strips
           | are necessary.
        
         | ericd wrote:
         | Something to consider, and something I got a vivid
         | demonstration of while playing with solar panels, DC arcs
         | aren't self-extinguishing, unlike AC arcs. At one point I stuck
         | a voltage probe in, and the arc stuck with it as I pulled the
         | probe away. It also vaporized the metal tip of the probe.
         | 
         | My understanding is that DC breakers are somewhat prone to
         | fires for this reason, too.
        
           | bigiain wrote:
           | Heh - I vaporised a fairly large soldering iron tip (probably
           | 4mm copper cylindrical bar?), when I fucked up soldering a
           | connector to a big 7 cell ~6000mAHr LiPo battery and shorted
           | the terminals. Quite how I didn't end up blind or in hospital
           | I don't know. It reinforced just how much respect you need to
           | pay to even low-ish voltage DC when the available current was
           | likely able to exceed 700A by a fair margin momentarily. I
           | think those cells were rated at 60C continuous and 120C for 5
           | seconds.
        
             | ericd wrote:
             | heh man, I'm glad you got out of that easy, I definitely
             | wore safety glasses 100% of the time after my experience. I
             | think a lifetime of experience with dangerous wall outlets
             | and harmless little 1.5V/9V DC cells teaches us the wrong
             | lessons about DC safety. I've since heard stories of
             | wrenches _exploding_ when they fall across EV high voltage
             | battery terminals. Wrenches aren 't supposed to be
             | explosive.
             | 
             | The electricians I was working with also told me stories
             | about how with the really big breakers, you don't stand in
             | front of it when you throw it, because sometimes it can
             | turn into a cloud of molten metal vapor. And that's just
             | using them as intended.
        
               | bluGill wrote:
               | Amps - the old 48vdc telco data centers vaporized wrenchs
               | once in a while.
        
               | jacquesm wrote:
               | Those harmless 9V DC cells can do a lot of damage if you
               | use them right.
        
               | sobjornstad wrote:
               | This reminds me of the sailor who [decided](https://darwi
               | nawards.com/darwin/darwin1999-50.html) to measure his
               | internal resistance by pushing probes through the skin on
               | his thumbs and electrocuted himself with the 9V
               | multimeter battery.
        
               | jacquesm wrote:
               | Mythbusters time. Salty fluids can be remarkably
               | conductive. Blood qualifies. What's interesting though is
               | that you have to wonder if there isn't some contributing
               | factor here, as a kid I did this quite a few times, so
               | that's one more for that list of stuff that could have
               | killed me. At the same time: I didn't have nice
               | insulation piercing tips back then (I _do_ now) and that
               | may be what saved me. I will definitely not try this
               | again.
               | 
               | Another story in the same line is that I heard that a
               | horse got killed by contact with a lantern battery, but I
               | don't have any reference for that, just a story by a
               | family member that collected coaches.
        
               | scheme271 wrote:
               | A bunch of those big breakers require two people. One
               | person in a flash suit and another with a 2m long pole
               | around the first person. That way if an arc flash
               | happens, the second person can yank the first person to
               | safety without also getting hurt.
        
               | pocksuppet wrote:
               | Why don't they use the pole to flip the breaker from 2m
               | away?
        
               | defrost wrote:
               | Ruins the fun and interrupts instilling respect deep into
               | the bones of interns.
               | 
               |  _Allegedly_
               | 
               | While on "work experience" from high school I was put on
               | washing power lines coming straight out of the local
               | power station near the ocean - lots of salt buildups to
               | clear.
               | 
               | Same deal, flashover suits and occasional arcs .. and
               | much laughter from the ground operators who drifted the
               | work bucket close.
        
             | jacquesm wrote:
             | You got super lucky.
        
               | bigiain wrote:
               | Yep. Super super lucky. I suspect my reading glasses are
               | the only reason I can still see anything.
        
               | jacquesm wrote:
               | I have a couple of those narrow escapes one of which led
               | me to put a significant chunk of Eastern Amsterdam out of
               | power. Another involved Beryllium oxide. 9 lives are
               | barely enough.
        
               | bigiain wrote:
               | I would read that book...
        
               | jacquesm wrote:
               | 'Stupid stuff I've done and survived'...
        
               | swamp_donkey wrote:
               | Ah! Perhaps you are a member of the gigawatt club?
               | Eligible for entry once you have accidentally tripped off
               | 1000 MW of load or generation! No sweeping that under the
               | table
        
               | jacquesm wrote:
               | I'm the idiot that sent a fairly high voltage spike into
               | the grid setting off a cascade. Even years later I do not
               | fully understand how it could happen, you'd think the
               | grid would be low impedance enough to absorb a spike like
               | that. But it set off a cascade on a part of the local
               | grid that was known to be weak.
        
               | bigiain wrote:
               | Somehow I simultaneously desperately want to be in that
               | club, and never want to be responsible for an event that
               | would let me join that club...
        
           | toast0 wrote:
           | > DC arcs aren't self-extinguishing, unlike AC arcs. At one
           | point I stuck a voltage probe in, and the arc stuck with it
           | as I pulled the probe away. It also vaporized the metal tip
           | of the probe.
           | 
           | It would have self-extinguished if you waited long enough for
           | the probe to vaporize.
        
           | KaiserPro wrote:
           | > My understanding is that DC breakers are somewhat prone to
           | fires for this reason, too.
           | 
           | I think its that DC breakers are more expensive, so people
           | use AC rated breakers instead. They are both rated for 400v
           | @10 amps, its the same thing right?
           | 
           | It turns out they are not, and most people, even electronics
           | types rarely play with 200v+ of DC.
        
             | ericd wrote:
             | Yeah, I think this array was pushing 350-400V
        
         | kccqzy wrote:
         | That's actually a recent phenomenon. Before the age of
         | electronics most household appliances either worked with AC or
         | DC equally well (like incandescent bulbs) or worked well with
         | AC only given the technology at the time (think anything with a
         | motor, fans, HVAC compressors etc).
        
           | analog31 wrote:
           | Taking it to an extreme, the house I lived in while in grad
           | school had wall lamp fixtures that doubled as electric and
           | gas lamps. At some point I imagine it would have been
           | possible to choose between using electric or gas by either
           | flipping the switch or turning a valve. They said "Edison
           | Patent" on them. We could have lit the house on AC, DC, or
           | gas.
           | 
           | Thinking about the failure modes gave me the heebie jeebies,
           | but the gas had been disconnected ages prior.
        
             | jazzyjackson wrote:
             | It's kind of fun that light switches predate electricity. I
             | think you used to turn a key, I guess you were turning a
             | valve? Now that I think of it using a key to operate a
             | valve makes a lot of sense but you don't see it too often,
             | well, I guess you want to turn things off without needing
             | to find a key...
        
             | eszed wrote:
             | I lived in a 19th century house in San Francisco that had
             | gorgeous plaster work medallions on the ceilings - think
             | cherubs and fruits - in the middle of which were the light
             | fixtures. One day my dumb-ass flatmate made an ill-advised
             | attempt to DIY his light fixture and cracked the still-
             | active gas line embedded in the ceiling. Sometime in the
             | 1920s - the date was printed on a sticker in the electrical
             | panel - when they electrified the house, they'd wrapped the
             | electrical wires around the gas pipes, and left them
             | otherwise in situ. Crazy stuff.
        
         | torginus wrote:
         | I've had discussed with people familiar with the matter, and
         | they convinced me its really not worth it for many reasons, the
         | main one being safety - DC arcs are self sustaining - AC
         | voltage constantly goes to zero, so if an arc were to form, it
         | gets auto extinguished when the voltage drops. With DC this
         | never happens, meaing every switch or plug socket can create
         | this nice long arcs and is a potential fire hazard.
        
           | adiabatichottub wrote:
           | Really depends on what we're talking about. A lot of
           | electrical safety equipment has a DC rating, usually
           | something like 90VDC/300VAC. Also, most DC equipment just
           | isn't going to have the stored energy to generate a big arc.
           | Well, except batteries, and we're already piling them all
           | around us.
        
             | torginus wrote:
             | I mean it depends, but for dual rated stuff has both a
             | voltage and current limit, both of which are way lower.
             | Like typically a 230V/20A AC switch can switch 24VDC/2A.
             | And the energy is not in the equipment, its in the mains
             | (or batteries like you said, or PV panels)
        
               | adiabatichottub wrote:
               | Right, but that's why I mentioned safety equipment. Your
               | common DIN-mount UL-489 branch circuit breaker will be
               | rated for the same trip current, same short circuit
               | current rating (SCCR), but lower voltage. So you can use
               | the same wiring and breakers as you might have with AC
               | and your 48V battery bank won't vaporize the $5 hardware
               | store toggle switch that somehow became a shunt.
        
               | torginus wrote:
               | I mean, most AC circuit breakers use electromagnets to
               | trip on overcurrent (as well as bimetallic strips using
               | thermal methods for sustained high current).
               | 
               | Electromagnets dont work for DC, so your breaker will
               | never trip. For thermal protection, you need current, so
               | that checks out, and it would make sense for it to be
               | rated under 50V as thats considered the highest voltage
               | thats not life threatening on touch.
               | 
               | PV Batteries in general have a very high current (100s of
               | A) at ~50Vish volts, so I dont think there's a major
               | usecase for using household breakers for them.
               | 
               | Im still not getting your point BTW, switches and
               | breakers are two separate things, with different
               | workings, and household (and datacenter) DC would be I
               | think around 400ish V, which is a bit higher than the
               | peak voltage of AC, but still within the arc limits of
               | household wiring (at least in 230V countries).
               | 
               | The advantage of DC is that you use your wiring more
               | efficiently as the mean and peak wattage is the same at
               | all times. Going with 48V would mean high resistive
               | losses.
        
               | adiabatichottub wrote:
               | > Electromagnets dont work for DC, so your breaker will
               | never trip.
               | 
               | If electromagnets don't work for DC then what am I
               | supposed to do with this pile of DC solenoids and relays?
               | ;)
               | 
               | > PV Batteries in general have a very high current (100s
               | of A) at ~50Vish volts, so I dont think there's a major
               | usecase for using household breakers for them.
               | 
               | That's what the SCCR rating is for. When there's a fault
               | you're going to have a LOT of current flowing until your
               | safety kicks in. Something like the grid or a battery
               | bank will happily provide thousands of amps almost
               | instantaneously. Breakers designed for protecting
               | building wiring are rated for this. Now, most household
               | breakers aren't dual DC/AC rated, but you can actually
               | buy DC rated breakers that fit in a home panel (Square D
               | QO series).
               | 
               | > Im still not getting your point BTW, switches and
               | breakers are two separate things, with different
               | workings, and household (and datacenter) DC would be I
               | think around 400ish V, which is a bit higher than the
               | peak voltage of AC, but still within the arc limits of
               | household wiring (at least in 230V countries).
               | 
               | My point is that there isn't any material reason why DC
               | can't be as safe as AC, all the proper safety equipment
               | already exists. Extinguishing a DC arc during a fault is
               | a solved problem for equipment at household scale.
               | 
               | > The advantage of DC is that you use your wiring more
               | efficiently as the mean and peak wattage is the same at
               | all times. Going with 48V would mean high resistive
               | losses.
               | 
               | I just mentioned 48V because it's a common equipment
               | voltage for household DC systems. 400V would be good for
               | big motors and resistive heating loads.
               | 
               | Regarding DC vs AC and wiring efficiency, talking about
               | mean vs peak wattage just confuses the issue. 1 volt DC
               | is 1 volt RMS. It is an apples-to-apples comparison. If
               | you want to say "we can use 170VDC or 120VAC with the
               | same insulation withstand rating, and at lower current
               | for the same power", then that is absolutely true. But
               | your common 600V THHN building wire won't care if you're
               | using 400V AC or DC, so it's mostly immaterial.
        
           | jacquesm wrote:
           | The 'what is safer' question for DC and AC at the same
           | effective current and power has a mixed set of answers
           | depending on conditions. For instance, DC is more likely to
           | cause your muscles to contact and not let go (bad), but AC is
           | more likely to send your heart into ventricular fibrillation
           | (sp?, also bad).
           | 
           | AC arcs are easier to extinguish than DC arcs, but DC will
           | creep much easier than AC and so on.
           | 
           | From a personal point of view: I've worked enough with both
           | up to about 1KV at appreciable power levels and much higher
           | than that at reduced power. Up to 50V or so I'd rather work
           | with DC than AC but they're not much different. Up to 400V or
           | so above that I'd much rather have AC and above 400V the
           | answer is 'neither' because you're in some kind of gray zone
           | where creep is still low so you won't know something is amiss
           | until it is too late. And above 1KV in normal settings (say,
           | picture tubes in old small b&w tvs and higher up when they're
           | color and larger) and it will throw you right across the room
           | but you'll likely live because the currents are low.
           | 
           | HF HV... now that's a different matter and I'm very
           | respectful of anything in that domain, and still have a burn
           | from a Tronser trimmer more than 45 years after it happened.
           | Note to self: keep eye on SWR meter/Spectrum analyzer _and_
           | finger position while trimming large end stages.
        
             | Tempest1981 wrote:
             | > DC will creep much easier than AC
             | 
             | Can you say more about "creep"? Is the resistance changing?
             | Or is material actually migrating?
             | 
             | Also curious why it's worse using DC.
        
               | jacquesm wrote:
               | https://www.eevblog.com/forum/beginners/understanding-
               | high-v...
        
               | Tempest1981 wrote:
               | Thanks Jacques. So creepage is when current flows/arcs
               | across the surface of an insulator, vs through the air.
               | And it's worse with DC due to its unidirectional nature.
               | Worsens when pollution builds up, or the surface
               | degrades.
        
               | jacquesm wrote:
               | Indeed. And it's a really nasty thing to properly protect
               | against because that pollution, especially with stuff
               | that is unattended for a long time has a habit of ending
               | up much worse than your worst fantasies. I've taken more
               | than one electrocuted mouse out of the HV section of
               | older color TVs for instance. Up to 250V or so it is
               | manageable, above that you can get the weirdest problems
               | including completely invisible arcing where the only
               | giveaway is the ozone smell and the occasional click.
               | Looking at HV circuitry in the dark or by putting a flame
               | near a suspect spot is a great way to spot these kind of
               | issues.
        
         | bigiain wrote:
         | Sure, maybe?
         | 
         | If your house gets 800V DC you're still gonna need "bricks" to
         | convert that to 5VDC of 12VDC (or maybe 19VDC) that most of the
         | things that currently have "bricks" need.
         | 
         | And if your house gets lower voltage DC, you're gonna have the
         | problem of worth-stealing sized wiring to run your stove, water
         | heater, or car charger.
         | 
         | I reckon it'd be nice to have USB C PD ports everywhere I have
         | a 220VAC power point, but 5 years ago that'd have been a USB
         | type A port - and even now those'd be getting close to useless.
         | We use a Type I (AS/NZS 2112) power point plug here - and that
         | hasn't needed to change in probably a century. I doubt there's
         | ever been a low voltage DC plug/socket standard that's lasted
         | in use for anything like that long - probably the old "car
         | cigarette lighter" 12DC thing? I'm glad I don't have a house
         | full of those.
        
         | jwilliams wrote:
         | There are niches where DC makes sense - low-voltage lighting,
         | USB/LED ecosystems.
         | 
         | Once you get into higher power (laptops and up), switching and
         | distribution get harder, so the advantages fade.
         | 
         | For bigger appliances (fridge, etc), AC is fine + practical.
        
           | adiabatichottub wrote:
           | Your modern fridge is probably going to have an inverter-
           | driven motor, so you're right back to using DC.
        
             | adrr wrote:
             | All modern appliances and HVACs are using inverter drive
             | motors for efficiency. Brushless DC motors are more
             | efficient though.
        
               | userbinator wrote:
               | "Brushless DC motors" are actually just AC synchronous
               | motors.
        
         | epx wrote:
         | Having a single big DC converter at a home would help a lot
         | with power factor (LED lamps connected directly to AC have
         | terrible power factor).
        
         | Mistletoe wrote:
         | Modern bricks really aren't that inefficient though. An Apple
         | charger is like 90% efficient. A DC to DC converter is about
         | that efficient or worse.
        
           | catlikesshrimp wrote:
           | The power adapters became so efficient that we have to
           | transition to wireless charging to keep it down
           | 
           | The irony...
        
         | flowerthoughts wrote:
         | I'm renovating a house, and have been considering 24V or 48V DC
         | outlets in a few rooms. Semiconductors become more expensive
         | above ~32V, so 24V might be the sweetspot.
         | 
         | However, there's also PoE (24 or 48V!), so maybe that's the
         | right approach. It's not like each outlet is going to run a
         | heater anyway.
        
           | fc417fc802 wrote:
           | Lower voltage makes voltage drop across the line
           | proportionally worse. Depending on the purpose PoE is
           | probably the way to go since the wiring and hardware is all
           | standardized and safety certified.
           | 
           | Unless you mean running AC and installing inverters in the
           | wall? What is this even for? All my electronics are DC but
           | critically they all require different voltages. The only
           | thing I might benefit from would be higher voltage service
           | because there are times that 15 A at 120 V doesn't cut it.
        
       | Aloisius wrote:
       | This article seems to imply that 800V DC is high-voltage DC, but
       | that seems quite low.
        
         | MathMonkeyMan wrote:
         | Quite low compared to a power utility's HVDC, but quite high
         | compared to the 5/12/24 V output of most AC/DC converters used
         | for electronics.
        
         | bigiain wrote:
         | I think there'a a regulatory "Low Voltage" definition of "below
         | 50V", which has implications around whether you need to be a
         | licensed electrician to install it or not. Anything above that
         | is - for at least some purposes - considered "High Voltage".
         | 
         | Other people, of course, have other definitions of high
         | voltage:
         | 
         | "This resonant tower is known as a Tesla coil. This particular
         | one is just over 17 feet tall and it can generate about a
         | million volts at 60,000 cycles per second."
         | 
         | and:
         | 
         | "This pulse forming network can deliver a shaped pulse of over
         | 50,000 amps with a total energy of about 1,057 times the tower
         | primary energy"
         | 
         | https://www.youtube.com/watch?v=RoGbrgOhPes
        
       | KnuthIsGod wrote:
       | Waiting for home DC.
       | 
       | It is silly to have AC to DC converters in all of my wall
       | connected electronics ( LED bulbs, home controller, computer
       | equipment etc )
        
         | jacquesm wrote:
         | Not going to happen. For the same reason that the US never
         | converted to a higher domestic voltage even though there are
         | many practical advantages. The transition from one system to
         | another at the consumer level would be terrible, even if there
         | would be some advantage (and I'm not sure the one you list is
         | even valid, you'd get DC-DC converters instead because your
         | consumers typically use a lower voltage than the house
         | distribution network powering your sockets) it would be offset
         | by the cost of maintaining two systems side by side for
         | decades.
         | 
         | You could wire your house for 12, 24 or 48V DC tomorrow and
         | some off-grid dwellers have done just that. But since inverters
         | have become cheap enough such installations are becoming more
         | and more rare. The only place where you still see that is in
         | cars, trucks and vessels.
         | 
         | And if you thought cooking water in a camper on an inverter is
         | tricky wait until you start running things like washing
         | machines and other large appliances off low voltage DC. You'll
         | be using massive cables the cost of which will outweigh any
         | savings.
        
           | manwe150 wrote:
           | I suppose that still begs the question somewhat, since the US
           | does have 240V (2 phase) already driving many appliances. Why
           | hasn't it ever become standard for luxury kitchens to have a
           | European-style outlet for use with a European kettle? I know
           | the US already has a different 240V plug shape, so it might
           | have to be an unlicensed installation, but surely someone
           | wanted hot tea faster and did that calculus before?
        
             | jacquesm wrote:
             | Well, as you say, it would not be according to code and the
             | insurance company might have something to say about it.
             | It's also single phase but not quite the way you do it in
             | the USA, it would be a neutral and a phase whereas in the
             | USA I think it is 2x110. Finally, it's 50 Hz rather than 60
             | which would work fine for resistive loads but not so well
             | for inductive ones such as transformers and motors.
             | 
             | In all likely not worth the trouble. When I moved to Canada
             | I gave away most of my power tools for that reason and when
             | I moved back I had to do that all over again.
        
               | aidenn0 wrote:
               | > In all likely not worth the trouble. When I moved to
               | Canada I gave away most of my power tools for that reason
               | and when I moved back I had to do that all over again.
               | 
               | If you ever have to do it again, you can probably get a
               | transformer rated high enough for power-tools for cheaper
               | than replacing all of your power tools.
        
               | jacquesm wrote:
               | Of course you can. That's kind of obvious. It is also
               | highly impractical. Besides the frequency delta you end
               | up having to lug a heavy transformer along and then you
               | have to alternate it across your tools so you don't end
               | up frying the transformer.
        
               | mauvehaus wrote:
               | The line frequency tends to screw with things with motors
               | too. Moved from the US to Belgium back when compact
               | cassette was a common format for music.
               | 
               | Killed a few tapes with a transformer on a US tape deck
               | before buying a 220V 50Hz unit. No, I don't remember if
               | the pitch was grossly off, but I'm guessing it wasn't.
        
             | ianburrell wrote:
             | You can run 240V circuit to kitchen for kettle and put in
             | NEMA 6 outlet. But few people care about fast boil and
             | importing European kettle. Most people use the microwave or
             | stovetop, and 120V kettles are fine in most cases. It will
             | never become a standard thing.
        
             | tbrownaw wrote:
             | > _I know the US already has a different 240V plug shape,
             | so it might have to be an unlicensed installation, but
             | surely someone wanted hot tea faster and did that calculus
             | before?_
             | 
             | How expensive would a proper AC->DC->AC brick for that
             | power level be?
        
               | jacquesm wrote:
               | Not so simple, you'd have to use a 'drier' or 'welder'
               | socket for that otherwise you won't have enough power. A
               | single circuit in Europe is 240V 16A or 3840W!
               | 
               | A pure sinewave inverter for that kind of power is maybe
               | 600 to 1000 bucks or so, then you'd still need the other
               | side and maybe a smallish battery in the middle t
               | stabilize the whole thing. Or you could use one of those
               | single phase inverters they use for motors.
        
             | jcalvinowens wrote:
             | I wired a UK kettle to an unused 240V range outlet in the
             | US once. It was amazing, boiled a liter of water in just
             | under a minute. Obviously kinda sketchy.
        
               | jacquesm wrote:
               | That's more like it :)
        
               | zahlman wrote:
               | "Wired"?
               | 
               | ...There was some kind of switch involved, I hope?
        
             | vessenes wrote:
             | Most important comment here!! I would love to buy like a
             | 6kw battery induction kettle for the states. As far as I
             | can tell, they don't exist.
        
             | fc417fc802 wrote:
             | Ahckhually US residential is split single phase, not two
             | phase. https://en.wikipedia.org/wiki/Split-
             | phase_electric_power
             | 
             | I think the answer to your question is that it mostly
             | doesn't matter for personal mug size quantities of hot
             | water and if it does matter to you there are readily
             | available competing options such as dedicated taps for your
             | kitchen sink.
             | 
             | Perhaps the biggest reason is that a traditional kettle on
             | any half decent electric range will match if not exceed the
             | power output of any imported electric kettle. Many even go
             | well beyond that with one burner marked "quick boil" or
             | similar.
        
               | lostlogin wrote:
               | I use an induction stove on maximum to boil water as I
               | get irritated at the time it takes to boil water with
               | 240v.
               | 
               | I'm surprised that American exceptionalism can tolerate
               | half powered sockets.
        
             | bregma wrote:
             | > but surely someone wanted hot tea faster
             | 
             | No one in the USA drinks hat tea. The choices (and it tends
             | to be regionally-based) is sweet or unsweet tea. No need to
             | boil a kettle quickly for that.
        
               | margalabargala wrote:
               | What? Plenty of people in the US drink hot tea.
        
               | mauvehaus wrote:
               | > No one in the USA drinks h[o]t tea.
               | 
               | There are dozens of us.
               | 
               | Perplexingly I was traveling in one of the iced tea
               | regions of the country in need of a cup of hot tea, and
               | they had no way to make it. Like, you have a commercial
               | coffee maker and hot cups, the coffee maker has a
               | hot(ish) water tap. All you need is a $4 box of teabags
               | that'll last until the heat death of the universe. Nope.
        
               | vel0city wrote:
               | As a counter argument, things like pour over coffee is
               | getting to be more popular in the US and older drip
               | coffee makers seem to be getting slightly less popular.
               | 
               | Still though, I don't seem to see most of those people
               | seriously clamoring for the electric kettle to go a bit
               | faster. The cost for the wiring difference and dealing
               | with odd imported kettles just isn't worth it generally.
        
               | zahlman wrote:
               | > The choices (and it tends to be regionally-based) is
               | sweet or unsweet tea.
               | 
               | ... Unless you're buying it pre-made, does this not still
               | start with making hot tea the regular way? Or what
               | exactly are you doing with the tea bags and loose tea
               | from the supermarket?
        
             | xoxxala wrote:
             | Technology Connections did this with an EV battery charger:
             | 
             | https://youtu.be/INZybkX8tLI
        
           | SoftTalker wrote:
           | I'm not sure it's likely, but I could see DC lighting start
           | to happen in new construction. Have a single AC-to-DC
           | converter off the main service entrance that powers hard-
           | wired LED lighting fixtures in the house. Would probably be
           | better than running the individual (and usually very low
           | quality) converters in dozens of standard LED light bulbs.
           | Would need to be standardized, codified, etc. so probably not
           | happening soon.
        
             | ansgri wrote:
             | Would be more practical to have a single 50-300W AC-DC 24V
             | PSU per room or group of rooms, then pull relatively short
             | DC cables to each light. A multichannel light controller
             | could also be placed nearby, and then if you need fully-
             | featured brightness and color control, only a small PWM
             | amplifier could be placed at each light if distance from
             | controller to each light is too long to transmit PWM power
             | directly.
        
           | wincy wrote:
           | I just wish I could run my air conditioner and my desktop
           | computer at the same time without flipping the breaker. The
           | RTX 5090 is a space heater and will easily peg at the 600W
           | it's rated for, and so with that and an air conditioner
           | window unit, I have to run a long cable from another unused
           | room if I want to do anything that stresses the video card.
        
             | jacquesm wrote:
             | You can use nvidia-smi to reduce the powerdraw of the card
             | to just below what will trip the breaker.
        
             | zahlman wrote:
             | If you're running an air conditioner and a "space heater"
             | at the same time it might be worth reconsidering your
             | priorities.
             | 
             | I can watch 1080p video on YouTube and it runs in an up-to-
             | date web browser using less than 50% CPU on 12-year-old
             | hardware with 8GB of RAM and a graphics card that was a
             | budget option at the time (my searches indicate it draws at
             | most 80W, though it expects a 500W PSU for some reason).
        
           | throw0101c wrote:
           | > _Not going to happen. For the same reason that the US never
           | converted to a higher domestic voltage even though there are
           | many practical advantages._
           | 
           | It would be relatively easy for the US to go to 240V: swap
           | out single-pole breakers for double-pole, and change your
           | NEMA 5 plugs for NEMA 6.
           | 
           | For a transition period you could easily have 240V and 120V
           | plugs right next to each other (because of split phase you
           | can 'splice in' 120V easily: just run cable like you would
           | for a NEMA 14 plug: L1/L2/N/G).
           | 
           | What would be the real challenge would be going from 50 to
           | 60Hz.
        
             | rkomorn wrote:
             | > What would be the real challenge would be going from 50
             | to 60Hz.
             | 
             | Other way around, no? The US is already 60Hz.
             | 
             | Edit: I mostly remember this because the SNES games I used
             | to buy in the US and brought back to Europe ran noticeably
             | slower.
        
           | zahlman wrote:
           | ... or we could have _both_ sets of wiring, and use what 's
           | appropriate for the task/appliance?
        
         | ternus wrote:
         | The lesser-known instance of this is RV power. When you're
         | running off small batteries and solar, you want to make the
         | best use of the watt-hours you have, and that means avoiding
         | the DC-to-AC-to-DC loop wherever possible. So you run 12V (or
         | in newer models, higher voltage) versions of everything,
         | upconverting as necessary.
        
           | amluto wrote:
           | I am really skeptical that 12VDC power distribution in RVs
           | actually saves power compared to a high-quality (hah!) higher
           | voltage AC or DC system. 12V is absurdly low and you can't
           | easily lose quite a few percent in resistive losses even with
           | fairly large cables, and those large cables are quite
           | unpleasant to work with and rather dangerous.
        
             | saltyoldman wrote:
             | I tried using a microwave off the RV batteries, your
             | inverter needs 4/0 cable. Very "fun".
        
         | scarecrowbob wrote:
         | Well, having spent some time operating a 12VDC system last year
         | when I moved into some shacks, I will say that I find it a lot
         | more convenient to run 120VAC.
         | 
         | I end up converting stuff anyhow, because all my loads run at
         | different voltages- even though I had my lights, vent fan, and
         | heater fans running on 12V I still ended up having to change
         | voltages for most of the loads I wanted to run, or generate a
         | AC to to charge my computer and run a rice cooker.
         | 
         | Not to mention that running anything that draws any real power
         | quickly needs a much thicker wire at 12V. So you're either
         | needing to run higher voltage DC than all your loads for
         | distribution and then lowering the voltage when it gets to the
         | device, or you simply can't draw much power.
         | 
         | Not that you can't have higher voltage DC; with my newer system
         | the line from my solar panels to my charger controller is
         | around 350VDC and I can use 10awg for that... but none of the
         | loads I own that draw much power (saws, instapot, rice cooker,
         | hammond organ, tube guitar amp) take DC :D
        
           | jazzyjackson wrote:
           | Catch me wiring my house with 20V USBC ;)
        
           | mauvehaus wrote:
           | Do you have a website with your system on it? I have an off-
           | grid building I need to add solar to in the next year or so.
           | After I fix the foundation and roof, of course. Naturally I'm
           | exploring options for item 387 on the todo list instead of
           | think about how I'm going to jack the building up.
        
             | scarecrowbob wrote:
             | It's a pretty simple system:
             | 
             | 4KW of panels, 400W 48V EG4 6000XP charge controller/
             | inverter 3x EG4 LifePower4 48V batteries a raspberry pi
             | running solar assistant
             | 
             | I feels like a bit overkill, and there is still a whole
             | mppt unused on the 6000xp so I could still double my panel
             | input. Also solar assistant tells me that I rarly go below
             | 75% battery storage. If I just wanted to run my fridge and
             | assorted convenience loads (and ran things like table saws
             | off a generator) then I could get away with a lot less of a
             | system.
             | 
             | But I'm operating a recording studio, and there were a
             | couple days this winter where I had a full-band session and
             | a couple days of storms and got down to below 50%.
        
         | est wrote:
         | home appliances have lower voltage, like 12V or 5V. The wire
         | loss and heat would be a problem.
        
         | hahn-kev wrote:
         | It's called USB power delivery
        
         | gwbas1c wrote:
         | Assuming you live in a "large" western home, it's impractical.
         | Remember, Edison's first power grid operated at 110/220v DC to
         | the home. If there was lower voltage (IE, 12 volts) going from
         | the street to your walls, the line loss would be _significant._
         | It only works in RVs and shacks because the wires are short.
         | 
         | Thus, even if you had DC in the walls, it would be 100+ volts,
         | and you'd still have conversion down to the lower voltages that
         | electronics use. If you look at the comments in this thread
         | from people who work in telco, they talk about how voltage
         | enters equipment at -48V and is then further lowered.
        
       | skullone wrote:
       | Transitioning? It already happened decades ago. Only smaller
       | scale/generic or less proficient "we bought all Dell and HP" use
       | AC. At large scale it's been a ton of DC for literally decades.
       | And for 70 years in telco and network gear.
        
       | b00ty4breakfast wrote:
       | They're still converting from AC to DC at the datacenter, it just
       | isn't being stepped down at the perimeter. There is no
       | transmission of HVDC going on. This isn't really Edison's
       | revenge, more like his consolation price, ha!
        
       | neoCrimeLabs wrote:
       | The datacenter I built in 2007 was DC.
       | 
       | Many datacenters I'd been to at that point were already DC.
       | 
       | Didn't think this was that new of a trend in 2026, but also
       | acknowledge I did not visit more than a handful of datacenters
       | since 2007.
       | 
       | It just seemed like a undenyably logical thing to do.
        
         | jeffbee wrote:
         | It's obviously not new. +-400VDC architecture was presented at
         | Open Compute last year, which is a fair indicator that the
         | presenter had put it into practice at least 5 years prior to
         | disclosing it. 48VDC distribution within a rack, and 48-to-1V
         | direct regulators for CPUs, were both contributed to OCP 7
         | years ago, at which point they were both old hat. And 48VDC
         | telco junk is, of course, totally ancient.
        
       | Animats wrote:
       | 800V to each rackmount unit, with hot plugging of rack units?
       | That's scary. The usual setup at this voltage is that you throw a
       | hulking big switch to cut the power, and that mechanically
       | unlocks the cabinet. But that's not what these people have in
       | mind. They want hot-plugging of individual rackmount units.
       | 
       | GE has a paper about the power conversion design, but it doesn't
       | mention the unit to rack electrical and mechanical interface.
       | Liteon is working on that, but the animation is rather vague.[2]
       | They hint at hot plugging but hand-wave how the disconnects work.
       | Delta offers a few more hints.[3] There's a complex hot-plugging
       | control unit to avoid inrush currents on plug-in and arcing on
       | disconnect. This requires active management of the switching
       | silicon carbide MOSFETs.
       | 
       | There ought to be a mechanical disconnect behind this, so that
       | when someone pulls out a rackmount unit, a shutter drops behind
       | it to protect people from 800V. All these papers are kind of
       | hand-wavey about how the electrical safety works.
       | 
       | Plus, all this is liquid-cooled, and that has to hot-plug, too.
       | 
       | [1] https://library.grid.gevernova.com/white-papers-case-
       | studies...
       | 
       | [2] https://www.youtube.com/watch?v=CQOreYMhe-M&
       | 
       | [3]
       | https://filecenter.deltaww.com/Products/download/2510/202510...
        
         | rdtsc wrote:
         | It is a pretty clever design
         | 
         | > When it is detected that the PDB starts to detach from the
         | interface, the hot-swap controller quickly turns off the MOSFET
         | to block the discharge path from Cin to the system. After the
         | main power path is completely disconnected, the interface is
         | physically detached, and no current flows at this time
         | 
         | > For insertion, long pins (typically for ground and control
         | signals) make contact first to establish a stable reference and
         | enable pre-insertion checks, while short pins (for power or
         | sensitive signals) connect later once conditions are safe;
         | during removal, the sequence is reversed, with short pins
         | disconnecting first to minimize interference.
        
           | Animats wrote:
           | Yes, I read that. There had better be a backup system.
           | MOSFETs tend to fail ON, and there's a megawatt going into
           | each rack.
           | 
           | Somehow this seems the wrong approach to AI.
        
             | superxpro12 wrote:
             | Fail _spectacularly_
             | 
             | Data center workers are gonna need those big yoink sticks
             | and those thick arc-fault bibs that furnace operators wear.
        
               | Animats wrote:
               | McMaster-Carr has the personal protective equipment
               | required for 800V: Flash protection face shields [1] and
               | Class 0 electrical protection gloves.[2]
               | 
               | It's not that bad. It's just ordinary industrial
               | protective gear.
               | 
               | [1] https://www.mcmaster.com/products/arc-flash-
               | protection-face-...
               | 
               | [2] https://www.mcmaster.com/products/electrical-
               | protection-glov...
        
         | dist-epoch wrote:
         | Or maybe you can require technicians to be in full-protection
         | electrical suits.
        
         | elif wrote:
         | As long as you can control for fire, electrical safety seems
         | like a temporary condition as robots and intelligent machines
         | are cheaper and more available long term solution to hot swap
         | blades in datacenter racks.
        
           | QuantumGood wrote:
           | I think you're being downvoted for speaking of a complex
           | future possibility ("robots and intelligent machines ...
           | solution") as if it was a proven commodity. There will be
           | many twists and turns in the path to the possible
           | reliability, scalability, and cost effectiveness of robots
           | and intelligent machines.
        
             | elif wrote:
             | Yea I literally said long term but HN voters have such a
             | hate boner for anything adjacent to AI
        
             | elif wrote:
             | It is a proven commodity already. Just not in our behind-
             | the-curve country.
             | 
             | Look at NTT Data or SoftBank.
             | 
             | https://www.softbank.jp/en/sbnews/entry/20250917_01
        
           | elif wrote:
           | Dear downvoters: softbank has been optimizing their
           | datacenters for robotic technicians since 2020.
           | 
           | They are about to have fully human free datacenters by the
           | end of this year.
           | 
           | When you are designing _long term_ goals with datacenters, as
           | I explicitly mentioned talking about, you can 't ignore
           | automation.
        
         | riedel wrote:
         | An EV fast charger can do 1000V, so with a bit of logic that
         | sounds doable.
        
           | t0mas88 wrote:
           | EV chargers take a different approach. There is no power on
           | the connector while you're plugging it in. It then locks in
           | place before the contactor closes and power is delivered.
           | Unplugging is the same, power is removed before the plug is
           | unlocked for release.
        
         | hinkley wrote:
         | The power connectors will be on the far side of the rack from
         | the service side so shouldn't be a problem for humans touching
         | the third rail so to speak.
         | 
         | With that sort of voltage you should be able to use a
         | capacitive or inductive sensor to activate a relay.
        
           | mikewarot wrote:
           | With a power rail that could supply kiloamps of fault
           | current, thus megajoules of energy into an arc, I wouldn't be
           | so sure of that.
           | 
           | Copper vapor inhalation is a definite possibility and a
           | horrible way to die.
        
       | amluto wrote:
       | I wonder how much of the benefit is simpler redundant power
       | equipment. For AC, you have standby UPSes and line-interactive
       | UPSes and frequency and phase synchronization. And everything
       | needs a bit more hold-up time because, in case of failure, your
       | new power supply might be at a zero crossing.
       | 
       | For 800V DC, a simple UPS could interface with the main supply
       | using just a pair of (large) diodes, and a more complex and more
       | efficient one could use some fancy solid state switches, but
       | there's no need for anything as complex as a line-interactive AC
       | UPS.
        
       | saltyoldman wrote:
       | The large brick you have on all your tech when you plug it in is
       | the converter. AC works great for some applications, none of them
       | really technical in nature.
        
       | fredgrott wrote:
       | That is about like aying the band AC DC had its revenge.....
       | 
       | can we stop vibe generating headlines?
        
       | flossly wrote:
       | AC is also waaaay safer for households: since the power drop to
       | to zero 100x (50Hz) per second switches are cheaper and safer,
       | and electrocution is less likely to happen.
        
       | pjdesno wrote:
       | 90% of the power in our academic data center goes 13.8kV 3-phase
       | -> 400v 3-phase, and then the machines run directly from one leg
       | to neutral (230v). One transformer step, no UPS losses, and the
       | server power supplies are more efficient at EU voltages.
       | 
       | But what about availability? If you ask most of our users whether
       | they'd prefer 4 9s of availability or 10% more money to spend on
       | CPUs, they choose the CPUs. We asked them.
       | 
       | There are a lot of availability-insensitive workloads in the
       | commercial world, as well, like AI training. What matters in
       | those cases is how much computing you get done by the end of the
       | month, and for a fixed budget a UPS reduces this number.
        
         | chromacity wrote:
         | > and then the machines run directly from one leg to neutral
         | (230v)
         | 
         | And then every machine has a switching power supply to convert
         | this to low-voltage DC, and then probably random point-of-load
         | converters in various places (DC -> AC -> DC again) for stuff
         | like the CPU / GPU core, RAM, etc. Each of these stages may be
         | ~95% efficient with optimal load, but the losses add up, and
         | get a lot worse outside a narrow envelope.
        
           | Dylan16807 wrote:
           | Yes, but it's not like any other layouts avoid those issues.
           | 
           | You could feed your servers off fat 12/24/48 volt supplies
           | but with how much power a modern server can pull you're
           | already converting in bulk even if you don't do that,
           | limiting the potential advantages. For running CPU/GPU/RAM,
           | there is no other option. When you need hundreds of amps at
           | 1-2 volts, you convert that centimeters away if at all
           | possible.
           | 
           | A datacenter using DC distribution is still using high
           | voltages and stepping them down in layers. The hassle it
           | avoids is in other aspects of power delivery.
        
         | poemxo wrote:
         | Really you're down for over an hour a year? Unscheduled?
        
       | gwbas1c wrote:
       | Anyone notice that 400V and 800V are also used in EV battery
       | architecture? I wonder if there's any sharing of technology?
        
       | notorandit wrote:
       | It does make a whole lot is sense. The amount of energy you loose
       | to convert AC to DC can be humongous . And useless if you produce
       | your own power (normally already in DC).
        
       | sholladay wrote:
       | Is there anything left in a modern home that really needs or is
       | better on AC?
       | 
       | We have some old ceiling and exhaust fans, but I know those can
       | be replaced. Our refrigerator is AC, but extended family with an
       | off-grid home has a DC refrigerator that cycles way less,
       | probably due to multiple design factors but I'm sure the lack of
       | transformer heat is part of it. I'm not as sure about laundry
       | machine or oven/cooktop options but I believe those are also
       | running on DC in the off-grid home without inverters.
       | 
       | Most of these AC appliances also have transformers in them anyway
       | for the control boards. It seems kind of insane to me that we are
       | still doing things this way.
        
         | Retric wrote:
         | Of grid homes are vastly more concerned with the energy
         | efficiency of their appliances and thus DC refrigerators
         | generally have more insulation. Most AC customers prefer more
         | internal volume for food over slightly increased efficiency.
         | 
         | AC motors are using way more power than the puddly control
         | boards in most home appliances. So you lose a little efficiency
         | on conversion but being 80% efficient doesn't matter much when
         | it's 1-5% of the devices energy budget. You generally gain way
         | more than that from similarly priced AC motors being more
         | efficient.
        
           | sholladay wrote:
           | I agree with everything you said, except it seems like a
           | false dichotomy. We can clearly build DC refrigerators with
           | more or less insulation. We can clearly build them large or
           | small. If you want to prioritize volume, then surely you
           | could do that with DC. Right?
           | 
           | I know that a long time ago DC-to-DC voltage converters were
           | very large in size, which meant AC would win on space
           | efficiency. But unless I'm mistaken, that's no longer the
           | case. Wouldn't a DC refrigerator with equivalent insulation
           | and interior volume have nearly identical exterior dimensions
           | as an AC refrigerator?
        
             | Retric wrote:
             | > Wouldn't a DC refrigerator with equivalent insulation and
             | interior volume have nearly identical exterior dimensions
             | as an AC refrigerator?
             | 
             | Sure, but it's important to separate what could be built
             | from what is being built based on consumer preferences and
             | buying habits. The average refrigerator could be
             | significantly quieter, but how often do people actually
             | listen to what they are buying? People buying Tesla's
             | didn't test drive the actual car they were buying so the
             | company deprioritized panel gaps. And so forth, companies
             | optimize in ways that maximize their profits not arbitrary
             | metrics.
        
         | samus wrote:
         | Any appliance with strong motors should be more efficient with
         | AC supply. But almost anything else can be regarded as a heater
         | that doesn't care much as long as it is fed with the correct
         | voltage. Which is actually the core issue.
         | 
         | A DC household would have to choose a trade-off between
         | multiple lines with different voltages or fewer voltages that
         | need to be adapted to the appliances. And we're right back at
         | the AC situation, but worse since DC voltages are more
         | difficult to change.
         | 
         | But consumers like datacenters can very well plan ahead and
         | standardize on a single DC voltage. They already need beefy
         | equipment to deal with interruptions, power sourges, non-sinus
         | components, and brownouts, which already involves transformers,
         | condensators, and DC conversion for battery storage. Therefore
         | almost no additional equipment is required.
        
           | sholladay wrote:
           | What qualifies as a strong motor here? Are you comparing to a
           | brushed DC motor? Do you think a washer/dryer would have
           | worse overall efficiency with a BLDC in a DC home compared to
           | what we have today? If so, that's news to me. Where can I
           | learn more about that?
           | 
           | The trade-off between, say, one (relatively) high voltage DC
           | bus throughout the home vs many branches with lower discrete
           | voltages is indeed a problem. With AC, we took the bus
           | approach, running 120v everywhere (in the U.S., higher
           | elsewhere). I'm inclined to say we should keep doing that for
           | flexibility and predictability. But it's a trade off, like
           | you said. It would obviously help if regulatory and standards
           | bodies came out with official recommendations.
        
             | zarzavat wrote:
             | Probably 90% of my devices run 5V DC or similar, but you
             | can't run that through a home so you're back to needing AC.
             | If you're going to have AC and DC then you might as well
             | just have AC.
        
               | sholladay wrote:
               | > Probably 90% of my devices run 5V DC or similar,
               | 
               | Indeed. And that's quite normal. Our electrical system
               | should serve our modern needs.
               | 
               | > but you can't run that through a home
               | 
               | 5V might be too low for that length of wire. But you
               | could most definitely have a low voltage line in your
               | house that we could design around, maybe 12V. Electric
               | vehicles are moving towards 48V for accessories. It seems
               | like lack of a standard is holding us back more than
               | anything else.
               | 
               | Or we could just keep doing 120V in the walls, with a DC
               | supply. Modern DC-to-DC voltage converters are very
               | efficient and small. But maybe I'm wrong. A lot of people
               | seem to believe they are still not good enough yet for
               | such a change to make sense.
               | 
               | > If you're going to have AC and DC then you might as
               | well just have AC.
               | 
               | I arrive at the opposite conclusion. Most things are
               | natively DC. So therefore, power in the walls should be
               | DC and we should covert it to AC near the endpoint where
               | necessary.
        
             | samus wrote:
             | Things like washing machines, dryers, dishwashers, air
             | conditioners, or fridges spend a lot of energy by running
             | powerful electrical motors, which should benefit from AC.
             | 
             | Everything else I can think of in a typical household is
             | basically a mere heater that in principle works equally
             | well with AC and DC of the correct voltage. Even computers
             | can be said to mostly care about the correct voltage since
             | AC->DC conversion is vastly easier than voltage conversion.
        
       | tibbydudeza wrote:
       | Have a solar system at home and from the panels it is DC into the
       | batteries but then the inverter needs to convert it to 220V/50Hz
       | AC for home use.
        
       | everdrive wrote:
       | "How can we turn this technical story into a story about people
       | and their conflicts?"
        
       | BorisMelnik wrote:
       | its really wild at all the AC to DC changes. for those non
       | electric engineers / hardware hackers (like myself) one of the
       | biggest "examples" I've seen of this has been ceiling fans.
       | 
       | Installing a ceiling fan used to be treacherous and so heavy.
       | Also loud and buzzy after installed. Now the fans in these things
       | are so lightweight and easy.
       | 
       | seeing the same in many more areas (lighting, etc)
        
         | hamdingers wrote:
         | Would love to see more mainstream DC lighting options and an
         | updated code to match. I just finished a remodel of my workshop
         | and blew over a hundred bucks on 14/2 for a 15 amp lighting
         | circuit that is unlikely to ever see more than a 1 amps load.
         | 
         | The irony is all the recessed lights I picked out _are_ DC,
         | they all have little AC-DC boxes hanging off them using a
         | proprietary connector. If I hadn 't needed to pass a rough-in
         | inspection going all DC would've been trivial.
        
       | p0w3n3d wrote:
       | Hard as a rock!       Well it's harder than a rock!
        
       | Xcelerate wrote:
       | I set up my own home network with a Vertiv Liebert Li-ion UPS a
       | few years ago and was thinking about how inefficient the whole
       | process is regarding power. The current goes from AC to DC back
       | to AC back to DC. Straight from the UPS as DC would work much
       | better, and as I was teaching myself more about networking
       | equipment, I was surprised to learn that most of it _isn 't_ DC
       | input by default (i.e., each piece of equipment tends to come
       | with built-in AC-DC conversion).
       | 
       | Then I started routing ethernet with PoE throughout my house and
       | observed that other than a few large appliances, the majority of
       | powered devices in a typical home in 2026 could be supplied via
       | PoE DC current as well! Lighting, laptops, small/medium
       | televisions. The current PoE spec allows up to 100 W, which
       | covers like 80% of the powered devices in most homes. I think it
       | would make more sense to have fewer AC outlets around the modern
       | house and many more terminals for PoE instead (maybe with a more
       | robust connector than RJ45). I wonder what sort of energy
       | efficiency improvements this would yield. No more power bricks
       | all over the place either.
        
         | estimator7292 wrote:
         | I think we're slowly, slowly coming around to the idea of
         | domestic DC distribution. The vast majority of consumer
         | electronics would be perfectly happy to consume 12v. It's
         | cheaper, safer, more efficient. Less design work and
         | certification on inbuilt AC adapters.
         | 
         | I think it's highly unlikely we'll see mass scale retrofits,
         | but if enough momentum builds up, I can see it as a great bonus
         | feature for new builds.
         | 
         | I got lucky with my house and every room has a dedicated phone
         | line meeting at a distribution panel (a couple of 2x4s with
         | screw terminals) built in the 50s. I'm in the process of
         | converting it to light duty DC power. The wiring is only good
         | for an amp or two, but at 48v that's still significant power
         | transmission.
        
           | zahlman wrote:
           | > I think it's highly unlikely we'll see mass scale
           | retrofits, but if enough momentum builds up, I can see it as
           | a great bonus feature for new builds.
           | 
           | I imagine rooftop solar could also source DC for the house
           | directly (or via a battery), before hitting the inverter... ?
           | 
           | The main problem I see is educating consumers. Maybe that
           | starts with a standard for DC outlets and plugs that can't be
           | confused with AC... ?
           | 
           | (Now I'm imagining desktop computers with much simpler power
           | supplies; but you'd presumably have to wire for dozens of
           | amps incoming...)
        
           | matt-p wrote:
           | 48v is what most home battery/solar systems run off. Also
           | coincidentally POE, IMO it makes a much more sensible
           | candidate as it is still 'safe' while carrying 4x as much
           | power for a given cable gauge. Consider laptops are 19 or 20v
           | so you would essentially /need/ a minimum of 24v.
        
         | rsync wrote:
         | "... throughout my house and observed that other than a few
         | large appliances, the majority of powered devices in a typical
         | home in 2026 could be supplied via PoE DC current as well!"
         | 
         | We installed 120 LED ceiling lights in our home circa 2020, all
         | of which were run with high voltage (romex) and accompanied by
         | 120 little transformer boxes that mount inside the ceiling next
         | to them.
         | 
         | Later ...
         | 
         | We installed outdoor lighting with low voltage, outdoor rated
         | wiring and powered by a 12V transformer[1] and I felt the same
         | way you did: why did we use a mile of romex and install all of
         | those little mini transformers when we could have powered the
         | same lights with 12V and low voltage wire ?
         | 
         | I then learned that the energy draw of running the low-volt
         | transformer all the time - especially one large enough to
         | supply an entire house of lighting - would more than cancel out
         | energy savings from powering lower voltage fixtures.
         | 
         | You don't have this problem with outdoor lighting because the
         | entire transformer is on a switch leg and is off most of the
         | time.
         | 
         | So ... I like the idea of removing a lot of unnecessary high
         | voltage wire but it's not as simple as "just put all of your
         | lights behind a transformer".
         | 
         | [1] https://residential.vistapro.com/lex-
         | cms/product/262396-es-s...
        
           | eqvinox wrote:
           | > I then learned that the energy draw of running the low-volt
           | transformer all the time - especially one large enough to
           | supply an entire house of lighting - would more than cancel
           | out energy savings from powering lower voltage fixtures.
           | 
           | That's not a constraint of physics, you can absolutely build
           | a DC power supply that is efficient in a wide load range.
           | (Worst case it might involve paralleling and switching
           | between multiple PSUs that target different load ranges.) But
           | of course something like that is more expensive...
        
             | Dylan16807 wrote:
             | > But of course something like that is more expensive...
             | 
             | More expensive than an inefficient unit, but it should
             | still be a lot cheaper than 120 separate units, right?
             | 
             | And I expect one big fat unit to do a better job of
             | smoothing out voltage and avoiding flicker than a bunch of
             | single-light units. Especially because the output
             | capacitors are sized for the entire system, but you'll
             | rarely have all the lights on at the same time.
             | 
             | Though for efficiency I'd think you'd want 48v and not 12v.
        
         | throw0101d wrote:
         | > _I set up my own home network with a Vertiv Liebert Li-ion
         | UPS a few years ago and was thinking about how inefficient the
         | whole process is regarding power. The current goes from AC to
         | DC back to AC back to DC._
         | 
         | With double-conversion, generally yes.
         | 
         | I recently ran across the (patented?) concept of a delta
         | conversion/transformer UPS that seems to eliminate/reduce the
         | inefficiencies:
         | 
         | * https://dc.mynetworkinsights.com/what-are-the-different-
         | type...
         | 
         | * a bit technical: https://www.youtube.com/watch?v=nn_ydJemqCk
         | 
         | * Figures 6 to 8 [pdf]: https://www.totalpowersolutions.ie/wp-
         | content/uploads/WP1-Di...
         | 
         | The double-conversion only occurs when there's a 'hiccup' from
         | utility power, otherwise if power is clean the double-
         | conversion is not done at all so the inefficiencies don't kick
         | in.
        
         | zahlman wrote:
         | > Lighting, laptops, small/medium televisions. The current PoE
         | spec allows up to 100 W, which covers like 80% of the powered
         | devices in most homes.
         | 
         | I find it a little hard to imagine that those devices outnumber
         | things like stoves, dishwashers, washers/dryers, kettles, hair
         | dryers... by 4:1.
         | 
         | Unsure why PoE would be better for LED lighting than the
         | standard approach of screwing a bulb directly into AC, either.
         | How many lumens do you get out of strip lights these days? And
         | you still have AC-DC conversion for whatever's sourcing power
         | onto the Ethernet link.
        
           | formerly_proven wrote:
           | PoE is also fairly bulky, requires large connectors, and
           | either requires a wholly isolated PD or what's basically a
           | class 2 DC/DC converter. That's why PoE-powered stuff usually
           | has that big transformer cube in it with a lot of clearance,
           | slotted PCB, 2-4 kV capacitors etc.
           | 
           | In practice PoE will have lower efficiency than mains
           | powered, since it'll usually be at least double conversion,
           | often three converters in series, plus the losses of the thin
           | network wires, and the relatively high idle losses / poor
           | low-load efficiency of the necessarily over-dimensioned PSE.
        
         | sneak wrote:
         | I think Ubiquiti (makers of the UniFi wifi products, as well as
         | some of the most popular managed PoE switches) also make a ton
         | of other PoE products such as the usual stuff like cameras, ip
         | phones, network switches, access card readers, door locks, and,
         | now, ceiling lights (presumably due to the latest PoE standards
         | delivering significant wattage).
         | 
         | It's super nice because you only need to put the UPS/ATS at the
         | PoE switch and then you get power redundancy everywhere you
         | have ethernet running (i.e. the phones don't go down).
        
         | pdpi wrote:
         | > maybe with a more robust connector than RJ45
         | 
         | USB-C could be that connector, using USB-PD instead of PoE.
         | Though I'm not sure I'd want to need that much smarts for every
         | single power outlet.
        
           | kjs3 wrote:
           | Considering the number of times I've sheared off a USB-C
           | connector vs ethernet, I wouldn't consider USB-C to be more
           | robust than RJ45. YMMV.
        
             | pdpi wrote:
             | How often do you unplug RJ45s versus USB-C, though?
        
               | kjs3 wrote:
               | I'm not talking about unplugging. Normal use.
        
         | crote wrote:
         | The problem is that all of those DC devices don't operate on
         | 48V either. The _vast_ majority of chips require a 5V or lower
         | input, so with a 48V DC supply you 're still going to need a
         | per-device PSU to do DC-DC conversion. In other words: no
         | getting rid of power bricks.
         | 
         | Efficiency isn't as straightforward either. You're still being
         | fed by 120V/230V AC, so you're going to need some kind of
         | centralized rectifier and down converter. It'll need to be
         | specced for peak use, but in practice it'll usually operate at
         | a fraction of that load - which means it'll have a pretty poor
         | efficiency. A per-device PSU can be designed exactly for the
         | expected load, which means it'll operate at its peak
         | efficiency.
         | 
         | We also don't use 5V DC grids because the wire losses would be
         | _horrible_ , so a domestic DC grid should probably operate at
         | pretty close to regular AC voltage as well. In practice this
         | means the most sensible option would be to have a centralized
         | rectifier and a grid operating at whatever voltage it outputs -
         | but what would be the point?
         | 
         | As to PoE: I personally really like the idea, but I don't
         | believe it'll have a bright future. For its traditional use the
         | main issue is that there doesn't seem to be a future for
         | twisted-pair beyond 10Gbps. 25GBASE-T might exist as a standard
         | on paper, but the hardware never took off due to complete
         | disinterest from the datacenter market, and it is too limited
         | to be of use in offices and homes. I fully expect that 25G will
         | arrive in the home and office as some form of fiber-optic
         | interconnect - with fiber+copper hybrid for things like access
         | points.
         | 
         | On the other hand, for a lot of IoT applications PoE seems to
         | be too complicated and too expensive. It makes sense for things
         | like cameras, but individual lights, or things like smoke
         | sensors are probably better served in office/industrial
         | applications by either a regular AC supply or a local DC one,
         | plus something like KNX, X10, CAN, or Modbus for comms: just
         | being able to be wired as a bus rather than a star topology is
         | already a massive advantage. And for domestic use the whole
         | "has a wire" thing is of course a massive drawback - most
         | consumers _strongly_ prefer using Wifi over running a dedicated
         | wire to every single little doodad.
        
           | matt-p wrote:
           | What if all homes had battery storage and or solar? You could
           | then simply use it's rectifier as needed or direct 48v from
           | the solar panels. That would be even more efficient than
           | 230v.
        
             | lillecarl wrote:
             | We live on societies, switching from AC to DC because your
             | low-power home appliances doesn't need AC makes no sense.
             | Home power usage is dominated by heating and cooling not by
             | your 45w laptop charger.
             | 
             | DC infrastucture makes sense in highly specialised
             | environments.... Like new gigawatt AI farms
        
             | ssl-3 wrote:
             | That'd be neat. But there's no standard for voltage for
             | home solar: The batteries might be 12, 24, 48v, 60v, or
             | even much more. Meanwhile, the panel arrays commonly output
             | anything as low as 0V and up to ~600V. There's not much for
             | rules and norms here.
             | 
             | Even if we were to standardize a low (<50V) voltage for DC
             | distribution within homes, we'd still need ~120/240VAC to
             | power big stuff, or we'd instead need even-larger
             | conductors (more copper) than we use today to do the same
             | work with low voltage.
             | 
             | But, sure -- we can play it out. So let's say we have an
             | in-home 48VDC distribution standard and decide that this is
             | the path forward and we enshrine it in law.
             | 
             | We need to convert whatever the solar system has available
             | to 48VDC. Then, we need to distribute that 48VDC using a
             | completely separate network of cabling. Finally, we still
             | need to convert 48VDC to whatever it is that devices can
             | actually use.
             | 
             | That's not representative of a reduction in steps, or an
             | increase in efficiency.
             | 
             | That is instead just an increase in installed
             | infrastructure expense, and a decrease in device
             | compatibility. It takes what we have, which is simply
             | universal (at least within any given geographical area) and
             | adds complexity.
             | 
             | And for what? What's the perceived benefit?
        
         | matt-p wrote:
         | One of the main problems is conductor size. I wish we could
         | access 22AWG copper in cheap and cheerful cat5e/cat6 format
         | cable. 24AWG cat5e, sometimes CCA is not great for doing large
         | amounts of POE.
        
           | Xcelerate wrote:
           | 22AWG Cat6A is actually what I used (cheap it was not
           | however).
        
         | ssl-3 wrote:
         | It's fun to think about. There's advantages both ways, but I
         | think it leans most-heavily towards keeping AC.
         | 
         | 1. One of these is simplicity. With AC, one single home run of
         | cabling (eg, Romex) can feed a whole room full of stuff, like a
         | bedroom or a living room. At one end of the run is a circuit
         | breaker (a fairly simple electromechanical device) and at the
         | other end is a series of outlets (which are physically daisy-
         | chained, but are functionally just wired in parallel with
         | eachother).
         | 
         | Since one single run of cable can feed many devices, it is easy
         | to accomplish.
         | 
         | 2. Another advantage is that it is universal. Anything can plug
         | into these outlets. Whatever a person brings into the home to
         | use, they can plug it into an outlet and it works. It works
         | this same way in every home.
         | 
         | 3. And there's quite a lot of power available: A common 20A
         | 120v branch circuit cabled up with 12AWG Romex is stated to
         | supply up to 16A continuously, or 1920W. For intermittent
         | loads, it can supply 20A -- or 2400W. That's tiny by European
         | standards, but it's still quite a lot of power. It's plenty to
         | run a space heater when Grandma visits and she complains about
         | the guest room being cold (even as you start to sweat when you
         | cross the threshold to investigate) and a big TV and a whole
         | world of table lamps, all at once. And you can plug this stuff
         | into any outlets in a room, and it Just Works.
         | 
         | 4. But, sure: Lots of devices want DC, not AC. So there's a
         | necessary conversion step that is either integral to the device
         | being plugged in, or in the form of the external wall warts we
         | all know very well.
         | 
         | So let's compare to power-over-ethernet.
         | 
         | 1. It's also simple, but only tangentially-so. One home-run
         | cable per outlet, whether that outlet is used or not, is
         | something that can be rationalized as being a simple topology.
         | A PoE switch at the head-end instead of a central box with
         | circuit breakers is a simple-enough thing to transition to. And
         | a lot more individual cables are required, but they're
         | relatively small and are generally easier to install.
         | 
         | 2. It's standardized, but it's not universal at all. I've got a
         | few PoE widgets around the house, but I'm pretty friggin' weird
         | when it comes to what I do with electricity. I can't go to Wal-
         | Mart and buy more PoE widgets to use at home, and when people
         | visit they aren't bringing PoE adapters to charge their phones
         | and other electronics. My computer monitor doesn't have a PoE
         | input. I can easily imagine a table lamp or a fan that connects
         | to PoE, and also uses it as a network connection for
         | automation, and that sounds pretty sweet in ways that tickle my
         | automation bones in the most filthy of fashions... but that's
         | getting even further into the weeds compared to how regular
         | people expect to do regular things.
         | 
         | 3. There isn't a lot of power available. 802.3bt Type 4 is the
         | highest spec. And within that spec: While switch ports can
         | output up to 100W, a device being powered is limited drawing no
         | more than 71.3W. Now, sure, that's 71.3W _per port_ , but in a
         | room with 10 ports that's still only ~700W -- at most -- in
         | that room. And Grandma's space heater won't run on 71.3W, nor
         | her electric blanket. My laptop wants more than this. The list
         | of useful, portable things that we casually plug into a wall
         | that only draw less than 71.3W is pretty short and most don't
         | benefit from the main advantage of PoE, which is a
         | _combination_ of [some] power alongside high-speed Ethernet
         | data.
         | 
         | 4. We still need wall warts since PoE is nominally ~48VDC. For
         | example: Phones use less than 71.3W while charging, but they
         | don't run on 48V. That means 120V AC comes in from the grid,
         | gets shifted to 48VDC for distribution within the dwelling, and
         | then gets shifted yet again to the produce the power (5, 9, 15,
         | and 20V are common-enough in USB PD world) that devices
         | actually want. That's _more_ lossy conversion steps, not fewer
         | -- and we still get to keep the extra conversion (wall warts)
         | as punishment for our great ideas. This is not the path towards
         | increased energy efficiency.
         | 
         | ---
         | 
         | PoE is great for the things we use it for today. A camera, a
         | wireless access point -- you know, fixed-location stuff that
         | uses networked data as its _primary function_ and also requires
         | power.
         | 
         | Installed PoE light fixtures (like, say, task lights in a
         | kitchen) also sounds neat -- unless they die prematurely and no
         | PoE replacements are to be found. (Now, you have not just one
         | or two problems, but many: The lights aren't working in that
         | space and they can't be replaced with a trip to Lowes because
         | the Romex that would normally have been installed was
         | deliberately deleted from the plan. It could have been a
         | 20-minute DIY fix that costs less than $100, but now it
         | involves drywall and paint and retrofitting new cabling. Or
         | maybe PoE replacements do exist, but it's now 2035 and the new
         | ones don't talk the same network protocols as the old ones
         | did.)
         | 
         | But there are other upsides: I've got an 8-port PoE-powered
         | network switch that works a treat. It's a dandy little thing.
         | And it sure would be neat to plug my streaming box in with PoE
         | and kill two birds with one cable; I would like that very much.
         | 
         | But most people? Most people don't give a damn about ethernet
         | (PoE, or not!) these days, or streaming boxes, and that trend
         | is increasing. They just plug their lamp into the regular
         | outlet on the wall like they always have, and deal with
         | whatever terrible UI is built into their smart TV, and use wifi
         | for anything that needs data.
         | 
         | And when they buy a home that is filled with someone else's
         | smart infrastucture, their first task (more often than not) is
         | to figure out who to call to erase those parts completely and
         | put it back to being normal and boring.
        
       | wolvoleo wrote:
       | Well they're kinda transitioning back. When I grew up most DCs
       | (and telecom facilities) were running on 48V DC. Easy to back up
       | with a big room full of lead acid batteries (just keep an eye on
       | that hydrogen gas lol)
        
       | tezza wrote:
       | They were Thunderstruck?
        
       | Rapzid wrote:
       | I somehow made it to middle age without making the connection
       | from AC/DC to electricity. Or I never thought about it till now.
        
       | redm wrote:
       | I guess we've come full circle. It was just 20 years ago that my
       | datacenters gutted DC in favor of AC.
        
       ___________________________________________________________________
       (page generated 2026-03-25 23:01 UTC)