[HN Gopher] Solar panels + cold = A potential problem
       ___________________________________________________________________
        
       Solar panels + cold = A potential problem
        
       Author : behnamoh
       Score  : 159 points
       Date   : 2025-09-28 01:48 UTC (21 hours ago)
        
 (HTM) web link (www.linspyre.com)
 (TXT) w3m dump (www.linspyre.com)
        
       | BobbyTables2 wrote:
       | Why would lower temperatures lower the maximum voltage?
       | 
       | Sure, diode forward voltages change a little but seems like
       | something else is going on...
        
         | AgentK20 wrote:
         | It's not that it lowers the maximum voltage that the charge
         | controller/inverter can handle. It's actually that the panels
         | become MORE efficient in the cold temperatures, resulting in a
         | (potentially unconsidered by end-user) increase in voltage,
         | overwhelming the downstream BoS components.
        
         | mindslight wrote:
         | Solar panel voltage goes up as temperature decreases. The chart
         | is misleading, it's stating something like an equivalent max
         | voltage if you think of the solar cell voltage as staying the
         | same (and presuming your temperature coefficient matches)
        
         | bobjordan wrote:
         | Lower temperatures increase PV max voltage output, not lower
         | it. Conversely, when solar panel temperature increases, voltage
         | decreases. So the headline specs/outputs assume to be valid at
         | a particular temperature. As the temperature of the panels
         | change, the realized performance changes.
        
         | objectcode wrote:
         | I think it works this way but I could be wrong: 1. The forward
         | voltage across a diode depends on the current, and the graph is
         | r-shaped. For a certain diode, 0.01A might make the voltage
         | across it 0.4V, 0.1A might be 0.6V, 1A might be 0.65V. 2. The
         | forward voltage also depends on the temperature of the diode.
         | For a certain diode, per degC decrease there could be a 0.002V
         | increase.
         | 
         | Let's say with certain current there is 0.687V. If two diodes
         | are connected in series i.e. (point a) - diode 1 - diode 2 -
         | (point b), and each has a 0.687V voltage across, that's 0.687 +
         | 0.687 = 1.374 V between point b and point a.
         | 
         | For the solar diodes, the "current" depends on how "strong" the
         | sun is. If at a certain "current", across each diode is 0.687V,
         | you'll need 216 diodes in series (between two points) to get
         | 0.687x216[?]148.4 V.
         | 
         | If there is 0.002 V increase per diode per 1degC decrease, with
         | 216 diodes, that's a 0.002x216=0.432V increase per degC
         | decrease, so with a 4degC decrease it exceeds the MPPT's limit.
         | 
         | Another thing about solar that differs from how diodes are
         | "normally" used in circuits is that the "true" voltage depends
         | on the max current achievable with the how bright the sun is
         | right now, instead of the "true" current. When the "true"
         | current is 0 A, the voltage across each diode might be 0.687 V.
         | When the "true" current is 0.5 A, maybe 0.65 V. 1A, maybe 0.6V.
         | 2A, maybe 0.3V. Try to get more "true" current, the "true"
         | voltage drops. Try to get more "true" voltage, the "true"
         | current drops. Power is voltage x current so when full speed
         | charging, the MPPT uses an algorithm to find the (possibly)
         | best minimum (not maximum) input voltage based on the
         | temperature etc and trades voltage for current at the output.
         | If there is no minimum input voltage restriction, solar will
         | follow the battery's terminal voltage + cable drop instead, and
         | instead of something like 111V, there could for example be a
         | ~4x less powerful 25.5V (if the battery is a "24 V") with just
         | 10% more current.
         | 
         | At the MPPTed min input voltage for full speed charging, maybe
         | 111V, all might seem well even with low temperatures, but when
         | the battery is full and there is approximately nothing using
         | electricity from solar, the real input current will be ~0 A, so
         | there will no voltage "sag", so the solar will realize the full
         | voltage corresponding to the temperature and the illumination,
         | potentially >150 V...
        
         | namibj wrote:
         | It's not that little given these diodes run between sun baked
         | summer and cold soaked winter dawn.
        
       | mindslight wrote:
       | Why does the Delta Pro not have a fuse on the input, with the
       | MPPT limiting the max voltage to 150v (by upping the current
       | until the voltage sags and/or the fuse blows, or even a straight
       | crowbar circuit). This is a premium consumer brand selling a
       | mostly complete product, and protecting the input from
       | overvoltage would be straightforward. The frustration at the
       | warranty weaseling isn't surprising.
        
         | avidiax wrote:
         | You might think that the voltage rise could be too fast for
         | most protective technologies to save the downstream
         | electronics, but the general case is that the temperature
         | slowly drops and the sun slowly rises. So the voltage should
         | slowly approach the limit.
         | 
         | Adding a normally-open relay and a voltmeter and a
         | microcontroller should fix this. Relay won't close on startup
         | unless the voltage is safe. Microcontroller will open the relay
         | if the voltage gradually nears the limit. Should be solvable
         | for <$5 in parts.
         | 
         | Dark start (when the batteries are flat w/o grid power) will be
         | challenging. There will need to be a small battery to power the
         | voltmeter and relay, or a high-voltage tolerant supply to power
         | the microcontroller and relay temporarily. A 9V should likely
         | be sufficient.
        
           | mindslight wrote:
           | Common relays don't handle 150VDC, and I'd spec the voltage
           | even higher even though one would think the voltage rating
           | has more to do with arc interruption rather than creepage
           | while off. Also a microcontroller is complete overkill, draws
           | too much current to be easily powerable by the solar panel
           | side, and adds complexity for something to go wrong. A simple
           | analog comparator suffices.
           | 
           | The standard answer for overvoltage protection is a crowbar
           | circuit + fuse, and I think that's what I'd aim for rather
           | than a relay. The problem with DIYing that is knowing the
           | input capacitance of the Delta and finding out whether it has
           | any other problems with its input being abruptly shorted.
        
           | namibj wrote:
           | No the DC/DC converter could just turn it's transistors to
           | short out the panels and rely on the fuse you want anyways to
           | handle idiots paralleling more panels than allowed.
        
       | therein wrote:
       | I am sure many are familiar but I found it amusing when someone
       | explained to me why it is called magic smoke.
       | 
       | It is because electronics work through magic so when you let the
       | magic smoke out, they stop working.
        
         | setterle wrote:
         | It's the soul leaving the IC.
        
         | dgfitz wrote:
         | I've never heard it called magic smoke before, but a regular
         | saying at one of my old jobs was "ah yeah we let the smoke out"
         | in relation to 100% electric drive vehicles. Smoked many
         | inverters, shorted 96v bus to a 24v bus, etc.
         | 
         | It was almost a rite of passage to "let the smoke out" in that
         | org. That job was actually great because as a software engineer
         | I happily spent a lot of time with a fluke, a wrench, arm
         | buried in the bowels of a vehicle fishing out sockets, etc.
         | Writing the software was not the hardest part of those
         | programs, but being one of the handful of folks that knew the
         | entire electrical, cooling, mechanical, and software systems
         | made us the most valuable folks on the program. We had to know
         | all those things in order to write the software correctly.
        
           | ggm wrote:
           | In the early 80s we used to say electronics ran on magic
           | pixie dust, and when you let the pixie dust out as smoke, the
           | magic went away.
        
           | ramses0 wrote:
           | Hackers dictionary: http://www.catb.org/jargon/html/M/magic-
           | smoke.html
        
         | jonathanlydall wrote:
         | The presentation helps a lot too, the way I was told it was
         | something like:
         | 
         | "Did you know that computers actually run on magic smoke? Once
         | the magic smoke comes out though, it stops working."
        
         | hdgvhicv wrote:
         | Devices run on magic smoke. When something bad happens the
         | smoke escapes and thus the device no longer works.
         | 
         | This is proven by observation - the only thing you see charge
         | is the smoke escaping.
        
       | franciscop wrote:
       | I was going to comment on the manufacturer's safety margins, but
       | then I found a graph [1] on the variability of voltage vs
       | temperature and it seems to be a lot steeper than I
       | thought/expected, to the point that I'm wondering how these do
       | not require either training or a voltage regulator to install and
       | operate properly:
       | 
       | https://www.researchgate.net/figure/Module-voltage-current-v...
        
         | fake-name wrote:
         | They do!
         | 
         | Basically anything that consumes solar power incorporates
         | what's called a "MPPT", or maximum power point tracker.
         | 
         | Basically, it's a smart DC-DC converter that continually tracks
         | the voltage/current output of a solar panel and adjusts the
         | load to extract the maximum available power from the panel.
         | 
         | It's not uncommon to have issues with extremely high panel
         | voltages in snowy climates, when they're first illuminated in
         | the morning. If you are close to the maximum voltage your MPPT
         | charger can handle in normal circumstances, extreme cold can
         | even damage things during the initial morning transient. You
         | then have to do oddball things like use a crowbar system to
         | prevent blowing up your MPPT system.
         | 
         | (see https://en.wikipedia.org/wiki/Maximum_power_point_tracking
         | )
        
           | childintime wrote:
           | Note it would be sufficient to shut down (short-circuit) a
           | single panel, which is safe, to lower the overall voltage.
        
         | syntaxing wrote:
         | Another post commented but that's exactly the point of the
         | MPPT. Not only is it temperature dependent but solar incidence
         | angle matters too (how the sun angle is relative to the
         | surface). MPPT works by changing the internal impedance to
         | match the ideal charging voltage. But there's a limit to how
         | much it can regulate but I think it's very fair that a consumer
         | would expect nominal voltage times panels in series is less
         | than the marketed solar input to work.
        
           | namibj wrote:
           | There's a reason people don't install electric equipment
           | without training.
           | 
           | This is just like not upsizing wire gauge if you have a bunch
           | that are loaded simultaneously buried together in a somewhat
           | insulating wall. Without the burying under plaster,
           | everything would be fine. But combine that with simultaneous
           | loading during summer, and you fry/roast the PVC insulation.
        
             | syntaxing wrote:
             | > There's a reason people don't install electric equipment
             | without training.
             | 
             | I'm not sure if I follow that logic and if your analogy
             | follows. I would argue this is closer plugging in an
             | appliance rather than running wires. If I run a 15A
             | appliance on a 10A breaker, a normal person without
             | training would expect the breaker to trip. This is like
             | running a 10A appliance and the 15A breaker trips because
             | the appliance is sometimes 16A when it works in the cold.
        
               | shepherdjerred wrote:
               | > If I run a 15A appliance on a 10A breaker, a normal
               | person without training would expect the breaker to trip.
               | 
               | Would the breaker trip in this case? I thought in this
               | case it'd be more likely to start a fire.
               | 
               | Edit: thinking about this more, I think I'm wrong. A fire
               | would start if your wires were too thin for a given
               | amperage. Breakers detect current flowing.
        
         | marcosdumay wrote:
         | The part that they are warning about burning out is a voltage
         | regulator.
         | 
         | Those things are normally built to handle a nominal 115 V
         | assembly of panels. There's probably something on the manual
         | about this, but when you put a giant label saying your device
         | supports 150V, people are not going to read the manual.
        
       | Animats wrote:
       | Why doesn't this just produce a shutdown? Inverters have to track
       | voltage and current on the input and outputs sides, and can turn
       | themselves off. They shouldn't be that close to the absolute
       | maximum voltage ratings on the components.
       | 
       | Too much current is a heat dissipation problem, and you've got
       | some time to deal with that, at least tens of milliseconds.
       | 
       | Anyone have a teardown on these things? Are they using under-
       | rated MOSFETs? That's all too common in solid state relays from
       | China.
        
         | quailfarmer wrote:
         | High voltage, low RDSON FETs are (slightly) more expensive, and
         | these products are cheap. A better design would use a higher-
         | voltage rated input switch with poor (slow) switching
         | performance, like an IGBT. Don't design critical infrastructure
         | around EcoFlow hardware.
        
           | Animats wrote:
           | Fujitsu, which sells MOSFETs for this application, writes:
           | "Firstly devices should be rated at 600V or 650V, as this
           | will generally provide more than adequate protection against
           | the threat of high voltage transients."[1] That's a nice big
           | safety margin. It should hold until the voltage monitoring
           | shuts the whole thing off.
           | 
           | Not seeing UL certification on this thing.
           | 
           | If we're going to have US protectionism against China, a good
           | first step would be to require UL-type testing, carried out
           | in the US, on all imported electrical devices that run on
           | more than 12VDC or contain a battery chemistry capable of
           | thermal runaway. Electrical safety is a solved problem if you
           | can keep people from cheating.
           | 
           | [1] https://toshiba.semicon-
           | storage.com/eu/semiconductor/design-...
        
             | adrian_b wrote:
             | The voltage ratings of the MOSFETs used for 220/230/240 V
             | applications have been increased over the years.
             | 
             | Decades ago, when bipolar transistors were used, they were
             | rated for 350 V, which is barely enough for 220 V + 10%.
             | 
             | When everybody started to design universal converters
             | usable for 220/230/240 V, the ratings were increased to 400
             | V. The first power MOSFETs were also rated thus.
             | 
             | Then there were too many converters destroyed by random
             | voltage spikes, so the standard ratings were increased to
             | 500 V. That proved to still be not enough in many places
             | over the world, so the ratings were increased to 600 V or
             | 650 V, already many years ago, in order to make extremely
             | unlikely the destruction of the transistors by voltage
             | spikes much greater than the nominal mains voltage.
             | 
             | 600 V or 650 V is used for converter topologies where the
             | transistors see only the peak input voltage. For converter
             | topologies that use fewer transistors, but those see peak-
             | to-peak voltages, the rating of the transistors must be
             | 1200 V.
             | 
             | For 650 V, gallium nitride FETs are the best available
             | devices, while for 1200 V or higher voltages silicon
             | carbide transistors are the best. Silicon transistors are
             | the best only for ratings much lower than 100 V, but they
             | may be preferred also at high voltages for being much
             | cheaper.
        
             | _fizz_buzz_ wrote:
             | My understanding is that mosfets themselves are usually not
             | UL certified/listed. I recently did a UL certification of a
             | power supply and the IGBTs we used were themselves also not
             | UL certified. The UL certification was more about the
             | overall system design.
        
         | Aurornis wrote:
         | > They shouldn't be that close to the absolute maximum voltage
         | ratings on the components.
         | 
         | This appears to be a situation where the engineering team
         | determined the absolute maximum input voltage and the
         | marketing/product people put that number straight into the
         | documentation.
         | 
         | Standard practice with electronic parts is to determine the
         | absolute maximum rating, then to specify a recommended maximum
         | that allows for some safety margin and variation.
         | 
         | Instead, this company determined the absolute maximum and then
         | just shipped it.
        
           | jama211 wrote:
           | One way or another, many of us are in agreement the company
           | screwed up and it's on them to fix it - whether that's their
           | marketing, their manual, their lack of over voltage
           | protection, whatever it is it's their fault.
           | 
           | Yet so many people in this thread are so keen to blame the
           | customer, it's pure ego from them. "I'm too smart for that to
           | happen, so it's all their fault!" they sneer. Classic bad
           | faith forum behaviour...
        
             | privatelypublic wrote:
             | That's humanity in general. But yea- general guide says
             | "add up your open circuit voltage and don't exceed that."
             | If something fails because of the panel manages to get more
             | than 1000W of solar flux, and is cold... it's the mfgr's
             | problem.
             | 
             | I need to actually look up why the extra flux increases
             | voltage. Maybe it really doesn't but just moves the MPP to
             | a higher voltage by having more current.
        
       | dhosek wrote:
       | When I got solar panels for my (former) house 15 years ago, as I
       | recall, the best practice was to have panels in parallel (each
       | with its own microinverter) and not in serial as serial would
       | cause loss of efficiency when there was partial blockage of
       | panels. (I could be misremembering all of this).
        
         | NooneAtAll3 wrote:
         | you might be misremembering bypass diodes?
        
           | ianlevesque wrote:
           | No, microinverters are still a thing (Enphase is a popular
           | brand) and they do then get connected in parallel.
        
         | baq wrote:
         | There are also power optimizers which are DC-DC and connected
         | in series.
        
         | namibj wrote:
         | That's only relevant if you're so starved for panel area that
         | you can't put them into places that have each sub array
         | sufficiently homogeneous and only partially shaded during
         | sunrise/sunset.
        
       | syntaxing wrote:
       | > Plugging in four 400w solar panels in series is similar to
       | filling your gasoline powered car with diesel and wondering why
       | the car manufacturer isn't replacing your new car.
       | 
       | I don't think this analogy works. The solar input works like
       | Diesel or Gasoline in different temperature. It's pretty
       | unreasonable to assume the consumer knows when depending on
       | temperature unless the explicitly state in the manual (I'm
       | willing to bet good money majority of the people in US have never
       | read their car manual either)
        
         | saghm wrote:
         | Agreed. No one needs to change which type of gas they use
         | because it happens to be a warm sunny day.
        
           | dotancohen wrote:
           | In the Corvette community, using a higher octane fuel on
           | hotter days is well known to prevent ping.
        
             | jfengel wrote:
             | I'm surprised the Vette doesn't call for high octane all
             | the time. It's common for high compression engines.
        
               | dotancohen wrote:
               | The knock sensor on LT1 and later engines allows one to
               | get away with lower octane fuel for day to day driving.
        
           | myself248 wrote:
           | Straight Vegetable Oil (SVO) diesel conversions do. It'll gel
           | at low temperatures, so they blend or switch to a separate
           | tank of regular (or bio) diesel while the engine is cold,
           | wait until it generates enough heat, circulate that heat
           | along the SVO lines and into the tank, then switch over. Then
           | switch back a few minutes before shutdown so the lines are
           | full of regular diesel for the next cold start.
        
           | rcxdude wrote:
           | Because they run their engines well within the margins of
           | their design. If you were running at the edge of the envelope
           | you would find that the temperature does matter.
        
           | happosai wrote:
           | True for gas not for diesel. You have to switch to winter- or
           | arctic diesel if the temperature goes below -20c.
        
             | bryanlarsen wrote:
             | Gasoline is also blended differently for summer or winter.
             | It's not as crucial as for diesel, but it does make a
             | significant difference.
        
           | throw-qqqqq wrote:
           | Yeah car analogies suck.
           | 
           | Diesel is blended differently for winter and summer in many
           | countries. See this for instance
           | https://www.crownoil.co.uk/guides/winter-blend-vs-summer-
           | ble...
           | 
           | Around the skiing season, many automotive magazines will
           | remind diesel drivers to buy "winter diesel" or use additives
           | if e.g. driving up to the Alps or similar cold places.
           | 
           | It's not so black and white :)
        
         | Jgrubb wrote:
         | I love a good analogy. This is not a good analogy.
        
           | jfengel wrote:
           | I'm not sure I know what a good analogy looks like. If the
           | two things are identical, then the analogy is uninformative.
           | If they're at all different, you will zero in on the
           | differences rather than the similarities.
           | 
           | Sometimes they can be ok pedagogical tools, but they're
           | easily misused as tools of persuasion.
        
             | jama211 wrote:
             | You're not supposed to zero in on the ways in which an
             | analogy doesn't apply. You're simply supposed to read the
             | analogy in order to see what it's attempting to _highlight_
             | about the scenario.
             | 
             | This is a common pet peeve of mine, people not
             | understanding how analogies are supposed to work and
             | getting distracted by the differences. They're supposed to
             | work like a light filter placed over a lens, something will
             | be highlighted and focus on that, don't focus on the fact
             | that "but all the colours are different now!", the only
             | purpose of using the light filter was to highlight a
             | specific part of the image, the fact that it also coloured
             | everything wrong temporarily is supposed to be ignored.
             | 
             | You know, just to use an analogy to explain analogies.
             | Gotta be as meta as possible.
        
       | nenenejej wrote:
       | Why isn't there code/regulations for tbis. Why do you need blog
       | advice.
       | 
       | It is like using too thin wiring to your oven or something.
       | Because you based it off how you typically use the oven not is
       | max draw plus decent margin.
       | 
       | Which is why you get a qualified electrician who knows or get
       | qualified yourself.
        
         | unglaublich wrote:
         | Okay, but the oven tells you: use at least 8mm^2 wire, and then
         | it goes up in flames because hey sometime you actually need
         | 10mm^2...
        
         | maccard wrote:
         | > Why isn't there code/regulations for tbis. Why do you need
         | blog advice.
         | 
         | On pretty much every other device (domestic for sure, I don't
         | actually know abount commercial) there is.
         | 
         | > It is like using too thin wiring to your oven or something.
         | Because you based it off how you typically use the oven not is
         | max draw plus decent margin.
         | 
         | Sure, but with all other electrical labelling the numbers are
         | correct. Imagine if Neff said "you only need an 13A rated
         | socket" for their oven, and then when you want to bake bread it
         | draws more. That's very different to Neff saying "you need
         | 45A", and deciding to install it on a 13A socket yourself
         | because you don't need to make bread. The former is what's
         | happening in this case.
        
         | Aurornis wrote:
         | Most household solar systems do require permitting and
         | inspections before you can turn it on. There are some
         | exceptions in a few states for very small systems now. Ecoflow
         | provides equipment for these small legal unpermitted installs.
         | 
         | More importantly, equipment shouldn't self destruct in a
         | dangerous fashion when pushed over the limit.
        
       | sbierwagen wrote:
       | I am surprised that open circuit voltage is specified at 25degC
       | and increases dramatically as the temperature goes down. Seems
       | backwards! I'm looking at the Ecoflow spec sheet right now and
       | fair enough, it's got the open circuit voltage and then the
       | Temperature Coefficient of Open Circuit Voltage (-0.35%/degC)
       | right next to it.
       | 
       | Great, guys, how about you go ahead and multiply those two
       | numbers _for_ me, since you 're the ones writing the fucking spec
       | sheet? It's like if car battery manufacturers only specified a
       | cranking amps number, and told you to figure out cold cranking
       | amps yourself.
        
         | teiferer wrote:
         | > Great, guys, how about you go ahead and multiply those two
         | numbers for me, since you're the ones writing the fucking spec
         | sheet?
         | 
         | No time. Busy writing blog posts blaming customers.
        
         | BertoldVdb wrote:
         | A solar panel is like a normal silicon diode. The voltage over
         | the cell goes up drastically with lower temperatures. In cold
         | climates crowbars are usually added.
        
         | crote wrote:
         | > how about you go ahead and multiply those two numbers for me
         | 
         | What are you going to fill in for the _third_ number, though?
         | With an open-circuit voltage of 37.10V at 25degC and a
         | coefficient of -0.35% /degC it can _theoretically_ go up to 75V
         | at absolute zero. And that open-circuit voltage is with an
         | irradiance of 1000 W /m2, should we also account for the
         | possibility of someone building a heliostat around it?
         | 
         | There's no one-size-fits-all number they could _possibly_
         | quote. It 'll always depend on the environment, because that's
         | just how the physics work. The best you can do is provide a
         | figure for the standardized testing environment and the
         | relevant coefficients - which is _exactly_ what they are doing.
        
       | teiferer wrote:
       | Maybe they should just improve their product to make it more
       | resiliant, rather than blaming customers for thinking that 148 V
       | is below 150 V? Not everybody buying these has a Ph.D. in physics
       | and if it says 148 V on the label and 150 V on the other label
       | then it's your product that has a problem, not the customer.
       | 
       | And no matter what happens, customer support should help the
       | customer, not blame them.
        
         | leoedin wrote:
         | In both examples given you can have 2 panels in series.
         | 
         | So given that in almost all use cases, you can have 2 panels in
         | series, they should just say "max 2 panels in series". Simple.
         | 
         | A good product hides complexity from the user with sane
         | defaults and optional advanced configuration. This feels like
         | the same problem.
        
           | cornholio wrote:
           | Panels are not standardized and are themselves series-
           | parallel constructions with wildly diverse specs.
        
           | TeMPOraL wrote:
           | There's hiding complexity, and then there's creating fake
           | reality for people.
           | 
           | As it is, panels are gonna produce variable power depending
           | on the weather. Putting interoperability with third-party
           | panels aside, to get the simplicity of "max 2 panels in
           | series", they'd have to either cap the max power on the
           | panel/generator link and dump the excess, or set the limit
           | based on the worst case a customer is likely to encounter.
           | I.e. they're either gonna waste power, or gouge their
           | customers for extra hardware. Neither of that makes sense for
           | an ecological product sold to a price-conscious customer base
           | :).
        
             | namibj wrote:
             | The problem is that you run higher voltages with the same
             | hardware if your in Alaska than if you're in Florida.
             | Substantially so.
             | 
             | "Wasting" those 5~10% during severe winter conditions isn't
             | worth splurging on the voltage converter.
             | 
             | Though then selling units that suggest to not run a few
             | hundred volt strings before paralleling instead does sound
             | bad, as the string doesn't need separate fuses rated to
             | many volts DC.
        
         | geocar wrote:
         | > Not everybody buying these has a Ph.D. in physics and if it
         | says 148 V on the label and 150 V on the other label then it's
         | your product that has a problem, not the customer.
         | 
         | Idk. I don't have a PHD, but 220V sounds like 240V to me. I
         | wouldn't do this.
         | 
         | I feel like getting advice about how to wire up electronics
         | should not be so hard.
         | 
         | > Maybe they should just improve their product to make it more
         | resiliant
         | 
         | Adding "resilience" usually adds to the per-unit cost. I think
         | making a web page adds some cost too, but at least that can be
         | amortised.
         | 
         | > And no matter what happens, customer support should help the
         | customer, not blame them.
         | 
         | I think that's happening here: Making a web page to educate
         | future customers seems like a really good idea. I wouldn't have
         | thought that necessary until I saw it, but I'm always excited
         | to learn something new.
         | 
         | The existing customers who did dumb should consider this a
         | relatively cheap education in electronics; cheaper than a PHD
         | at least!
         | 
         | Also, whether the company also gave them rebates or credits we
         | don't know here, but telling "customer support" they "should
         | help the customer" is also telling them they're not helping the
         | customer, and _you don 't know that_.
        
           | delusional wrote:
           | > Making a web page to educate future customers seems like a
           | really good idea
           | 
           | I don't think this is an official website of ecoflow.
           | 
           | Other than that I agree. I don't think asking for a bit of
           | knowledge from the customers is a bad thing. A warning in the
           | manual about safety factors should be enough.
        
           | xenadu02 wrote:
           | They're just being cheap. If you're going to let customers
           | plug panels directly into your box you should have
           | overvoltage protection. It's that simple.
        
           | cornholio wrote:
           | > Adding "resilience" usually adds to the per-unit cost.
           | 
           | In this case, the cost is much less than a dollar (say, a
           | varistor that blows the existing fuse) and it prevents a
           | catastrophic failure.
        
             | immibis wrote:
             | But they want you to have to buy another one.
        
               | hyperhello wrote:
               | Why does this kind of comment get downvoted that
               | pinpoints the actual motivation? We just pretend that
               | planned obsolescence is history.
        
               | majorchord wrote:
               | At least in parent's case, probably because the vast
               | majority of their comments are black-and-white hot takes
               | that are always downvoted regardless. And they basically
               | never respond when asked for any sources.
        
               | jama211 wrote:
               | Because it's an extreme claim backed up with no evidence.
               | Hanlon's razor applies here.
        
               | ranger_danger wrote:
               | Also see Hitchens' razor and Russel's teapot.
        
           | saghm wrote:
           | To me, 220 sounds 20 like lower than 240. I have a hunch that
           | this might be a common perception.
        
             | geocar wrote:
             | Really?
             | 
             | I have all sorts of electronics that say everything from
             | 208V - 240V that all go in the wall, so I think all those
             | numbers are probably close to each other in whatever a volt
             | is.
             | 
             | I think if I'm worried about a limit of some kind, being
             | within 5% of that limit seems like I might as well be over-
             | limit if the _commonly seen_ distribution I see in my house
             | is greater than 15%
        
               | cjbgkagh wrote:
               | I have a lot of electronics that accept 100-240v doesn't
               | mean I think they're close together, just that they have
               | compensating mechanisms to handle such voltages.
               | 
               | The margins are generally lower for higher power devices
               | because the electronics are more expensive. Thankfully
               | these electronics in general are becoming cheaper which
               | is one reason why they're ending up in the hands of
               | people inexperienced with them.
               | 
               | Also try to tell someone they need an extra 30% in margin
               | and often they'll think they're being upsold.
        
               | geocar wrote:
               | > I have a lot of electronics that accept 100-240v
               | doesn't mean I think they're close together, just that
               | they have compensating mechanisms to handle such
               | voltages.
               | 
               | I bet you also have a lot of electronics that don't
               | though, and those that do probably say so.
               | 
               | My kitchen mixers, dishwasher, washing machine, driers,
               | rice cooker, refrigerators, sauna, and pool pump aren't
               | that tolerant by a long shot. I've got a few computers
               | with a switch on the back to choose between 220v and
               | 110v.
               | 
               | Plugging something that takes 110v into my house breaks
               | the thing, so I've learned to check.
               | 
               | But I don't have anything that's 208v that can't go into
               | the house. So I think whatever the situation is with
               | volts, within 15% is "basically the same", so coming
               | within 15% of the rated limit, is probably just like
               | exceeding the limit by 15%.
               | 
               | And so this is why I would not expect something at 146V
               | to be under the safety limit of 150V.
               | 
               | > Also try to tell someone they need an extra 30% in
               | margin and often they'll think they're being upsold.
               | 
               | Where do you get 30%?
        
               | cjbgkagh wrote:
               | You're listing things that are high powered and or old.
               | Modern PSUs don't have that switch. While it's in the
               | early stages I expect more white goods to switch to BLDC
               | motors which will likely use voltage transformers that'll
               | support the 110-240v.
               | 
               | People generally are not lugging white goods
               | internationally, the average persons experience with
               | different voltages is for laptop and phone chargers when
               | they travel.
               | 
               | But for the matter at hand, the margin mentioned is
               | needed on the solar systems, this is where the inverters
               | can get expensive, which is why it can look like an
               | unnecessary upsell to people who've never blown a device
               | before.
        
           | numpad0 wrote:
           | > Idk. I don't have a PHD, but 220V sounds like 240V to me. I
           | wouldn't do this.
           | 
           | 220[Vrms] * 1.414 = 311[Vp-p] btw. HOW!?
        
             | rzzzt wrote:
             | AC wiggles and wobbles.
        
             | mazurnification wrote:
             | So the issue is that 220V is nominal in China, 230V nominal
             | in UE and 240V is UK/part of Australia. So if anyone is
             | preparing product for global market (as most are doing now)
             | more likely then not will support all of this voltages.
             | Thus is kind of normal (but wrong) to assume 220V sounds
             | like 240V.
        
               | adrian_b wrote:
               | When the voltage was unified in UE, the nominal value was
               | set to the median of 230 V, but its tolerance was raised
               | from 10% to 15%, so that the new maximum peak value of
               | 230V + 15% will match the old value of 240 V + 10%.
               | 
               | So now for all 220/230/240 V standards you have the same
               | maximum voltage value that is used for electrical designs
               | (about 265 V effective), so they are equivalent,
               | regardless of the name.
        
               | gus_massa wrote:
               | Many charguers are now 100-240V, 50-60Hz, that is close
               | to pluggable anywhere on Earth. (I burned one or two a
               | long time ago, when I forgot to check and used a 120V
               | transformed here with 220V)
        
               | rzzzt wrote:
               | Same thing happened to PC PSUs. I don't think there is a
               | recent unit that still has the self-destruct voltage
               | selector switch which pops them if you are in 230V land
               | (and the switch is set to the smaller setting).
        
             | adrian_b wrote:
             | Besides the ratio between the peak and effective value, you
             | must also account for the standard tolerance of the nominal
             | value.
             | 
             | The actual maximum peak voltage for the European mains, is
             | 230 V * 1.15 * sqrt(2), because of a 15% tolerance. That is
             | about 375 V. With a small safety margin, the minimum
             | voltage rating for components connected to 230 V a.k.a. 220
             | V is of 400 volt.
        
         | Zanfa wrote:
         | This is 100% on the manufacturer if they intentionally chose to
         | highlight the "best case" 150V, rather than the 120V lower end.
         | Especially without any additional safety mechanisms.
        
           | rcxdude wrote:
           | The article presents it oddly, it's not that the converter
           | maximum input gets lower, it's the solar panel output that
           | gets higher from the nominal quoted value (which is _not_ a
           | maximum, and not really intended to be used as such).
           | Derating your converter is equivalent for the purposes of
           | ensuring margins, but it implies the issue is in the wrong
           | place.
        
             | lazide wrote:
             | The idea of safety margins has died under the more pressing
             | type - profit margins.
        
               | Pet_Ant wrote:
               | Your safety margin is my profit margin.
               | 
               | - Mr MBA
        
               | Workaccount2 wrote:
               | The failsafe circuit to protect against this (over
               | voltage condition) is maybe $3 and incredibly routine in
               | anything with power. I would bet everything that it is in
               | there.
               | 
               | What's most likely though is that the fuse is also
               | internal, and externally the unit will appear bricked.
        
             | namibj wrote:
             | Your converter doesn't need to like the voltage, it just
             | can't break from it. In fact, if it's the type that shorts
             | the panels for curtailing, it should be happy to just run
             | them at the highest voltage it's comfortable with, loosing
             | a few percent generation during exceptionally cold days.
        
               | jacquesm wrote:
               | > it just can't break from it
               | 
               | In fact, they can.
        
               | huxley wrote:
               | I think they meant "it just can't" in the sense of "it
               | shouldn't under any circumstances"
        
         | xg15 wrote:
         | This feels a bit like the logic behind "do not put hamster in
         | microwave" warning labels.
         | 
         | I think if you work with electrical or electronic systems in
         | practice, you learn pretty quickly to respect tolerances and
         | that data sheets are a map, not the territory.
         | 
         | Also, electrical installations are usually seen as a field that
         | should be done by trained personnel, not arbitrary laymen home
         | owners. So I think the appropriate reaction would be to remind
         | people that they should hire an electrician to do the
         | installation, if they don't have the necessary specialized
         | knowledge themselves.
        
           | harvey9 wrote:
           | I have the impression these are consumer products so I would
           | them to be designed to be installed by people who do not
           | normally work with electrical systems. If they are only sold
           | to tradesmen that would be different.
        
             | xg15 wrote:
             | Yeah, it would be important to understand who the company
             | is intending to sell to or do the installation.
             | 
             | Though the lines are often blurred, because I guess most
             | companies would like to _sell_ directly to end customers,
             | even if their product requires a professional to install.
             | 
             | Even IKEA does this. You can go in and buy an electric
             | stove and oven, grab them from the warehouse and take them
             | home with you right there. But it's a bit of an illusion:
             | You're still supposed to call an electrician to actually
             | connect the things.
        
               | krisoft wrote:
               | > Yeah, it would be important to understand who the
               | company is intending to sell to or do the installation
               | 
               | You can do that by just reading the product page[1]. The
               | delta pro, the equipment in question, looks like a plug-
               | in appliance. It visually communicates that it is
               | portable (by having a wheel and a handle) and by virtue
               | of having a power lead connect to it it communicates that
               | you can just plug it in. They further reinforce this by
               | writing this: "Plug & Play home backup solution". "Easy
               | installation with completely pre-wired Plug & play home
               | backup solution" "The solution provides a convenient home
               | battery system without rewiring or running dangerous
               | extension cables through your home." "Plug directly into
               | an AC wall outlet and make sure that the wall output
               | current is more than 15A."
               | 
               | And on top of that the manual[2] makes no mention of
               | needing an electrician.
               | 
               | In contrast an IKEA electric oven's product page[3]
               | states this: "No plug is included. Installation to be
               | carried out by a qualified installer." and then the
               | manual[4] states "Installation, including water supply
               | (if any) and electrical connections, and repairs must be
               | carried out by a qualified technician."
               | 
               | But of course nobody reads the manual. The big difference
               | is that one comes with a plug while the other doesn't.
               | 
               | 1: https://us.ecoflow.com/products/delta-pro-portable-
               | power-sta...
               | 
               | 2: https://websiteoss.ecoflow.com/cms/upload/2022/10/12/1
               | 312845...
               | 
               | 3: https://www.ikea.com/gb/en/p/mataelskare-forced-air-
               | oven-ike...
               | 
               | 4: https://www.ikea.com/in/en/manuals/matalskare-forced-
               | air-ove...
        
             | quickthrowman wrote:
             | If you can do a code compliant installation, then you're
             | the customer. If you can't, then I'd suggest hiring an
             | electrician.
        
           | beefnugs wrote:
           | Actually if "you work with electrical or electronic systems
           | in practice" you get pissed off at everything for how dumb it
           | all is: 12V DC batteries are more like 14 nominal? AC wall
           | plugs dip voltage when printers turn on, random equipment you
           | arent even sure in the building can trigger UPSes based on
           | unknown settings in the device? International standards and
           | communication protocols mean nothing as "a standard" because
           | each company has their own entire list of bugs/implementation
           | mistakes. All the international enforcement certifications
           | care way too much about inconsequential bullshit and miss all
           | the true showstopping problems in most industries?
           | 
           | This world is amazing anything runs at all. The slightest
           | addition of complexity is causing everything to fail now.
           | 
           | Modern computers are less reliable than ever, some companies
           | have decided to REMOVE the pinhole bios reset (that has been
           | around for 30 years) at the same time as things are buggier
           | now and dont boot again until you physically unplug the bios
           | battery deep inside and hard to get to.
        
             | xg15 wrote:
             | Spoken like a true professional!
        
             | amelius wrote:
             | The modern engineer:
             | 
             | It works! OK, stop touching it. We don't want to break it.
        
             | Workaccount2 wrote:
             | This is what makes software engineering so seductive,
             | everything works exactly as it was designed to (whether
             | intended or not). Imagine trying to program for computers
             | with memory that drifts values progressively more as it
             | wears down.
        
               | boothby wrote:
               | Software engineering _sucks_ compared to pure
               | mathematics. Back when I was in uni, everything always
               | did exactly what it said on the label.
        
           | emn13 wrote:
           | So on the one hand we have a product which isn't even
           | remotely designed for the use case (hamsters), and during
           | normal use shows obvious behaviour (cooking) that should
           | imply risk to said hamsters. On the other side, we have a
           | product designed to be installed in an electrical system, and
           | shows no signs during normal use that it's installed
           | unsafely, and where the advertised specs are not actually
           | safe for normal usage.
           | 
           | Whether or not the company in this case shares some or most
           | of the blame with novice users - the analogy is not a great
           | one.
        
             | nanomonkey wrote:
             | Microwaves were originally specifically invented to
             | microwave frozen hamsters:
             | 
             | https://interestingengineering.com/videos/1950s-reanimating
             | -...
        
               | adiabatichottub wrote:
               | As Doc Brown would say, "Great Scott!"
        
         | amelius wrote:
         | > make it more resiliant, rather than blaming customers
         | 
         | Yeah, this sounds very much like "you're holding it wrong".
        
           | bayindirh wrote:
           | They can add a relay, I guess? Voltage monitoring is cheap.
           | Relays might push price above a bit, but it's a worthy
           | premium to pay in my book.
        
         | abcd_f wrote:
         | I read it as a problem with _solar panel_ voltage going over
         | declared threshold of 37v in certain meteo conditions.
         | 
         | That is the issue is with the wrong labeling of things that are
         | being plugged into this vendor's device, not the vendor's own
         | labeling.
        
           | bayindirh wrote:
           | If something can go wrong, it _will_ go wrong. So both
           | parties should note that something can go wrong and point to
           | that something.
        
           | TeMPOraL wrote:
           | I believe the vendor here produces both the device and the
           | panels being plugged into it, and while they also supply
           | other vendors' panels, they seem concerned primarily with
           | customers who buy all components from them and then
           | experience this failure.
           | 
           | I agree the labeling is an issue here, but the solution must
           | come from the wider industry or regulatory bodies; the
           | alternative is for vendors to switch to their own pseudo-
           | units to internalize the math, which would not be good for
           | customers either - think "ACME Generator2000 accepts up to 4
           | Power Units of input; each ACME SuperEco Panel supplies 1
           | Power Unit, or 1.5 Power Units if you're in Canada...".
           | 
           | Saving users from having to do a little thinking to not brick
           | their device is a tried-and-true excuse for vendor lock-in in
           | our industry :).
        
             | ninalanyon wrote:
             | Why not label the panel with the maximum possible voltage
             | that it can produce? Or even have a little table showing
             | the maximum possible voltage at various ambient
             | temperatures. It's not as if there isn't room on the back
             | of the panel for a big enough label.
        
               | marcosdumay wrote:
               | The entire industry has standardized in having "typical"
               | and "maximum" values decades ago. That problem there is
               | completely self-imposed.
        
               | lostlogin wrote:
               | The flip side of this is also dumb labelling. 'Product
               | may contain traces of nuts'.
               | 
               | Completely unhelpful to those that need the info.
        
         | cowsandmilk wrote:
         | Considering the electric code has an 80% rule for loads, anyone
         | assuming they can use 100% of what is on a label probably
         | should not be doing electrical work.
        
           | immibis wrote:
           | Very true. My computer says 240V on it, so I should only use
           | it up to 192V.
        
             | rcxdude wrote:
             | No, you just shouldn't _assume_ that that 's the case. In
             | the case of a computer and mains, both of those are nominal
             | voltages and there will be a range of voltages which are
             | expected to function, and if you want to check for sure,
             | you should check those ranges.
        
             | lazide wrote:
             | Interestingly, the peak voltage of 240V AC (typical) is
             | 330ish+ volts.
             | 
             | Typical house wiring is required to handle 600v due to
             | voltage transients and wear and tear.
             | 
             | So any component rated to 240V dc will fail immediately on
             | AC, and even 400-500V DC is not a good idea.
             | 
             | I guess there is a reason there is a whole category of
             | engineers for this kind of thing.
        
           | stephen_g wrote:
           | Which electrical code? They vary from country to country and
           | even state/province in some countries!
        
           | quickthrowman wrote:
           | I agree with you, but. The NEC has an 80% rule for continuous
           | loads (over 3 hours) that use a typical circuit breaker as
           | overcurrent protection. If you use fuses or a 100% rated
           | breaker as your over current protection, then you can use all
           | of the available ampacity. Anyways, devices that use a 15A
           | receptacle (for example) will not draw more than 12A
           | continuous if they're meant to run continuously (3 hours or
           | longer).
           | 
           | https://www.se.com/us/en/faqs/FA104355/
        
         | cameronh90 wrote:
         | I don't know about the components they're selling, but with
         | electronic components, it's on the buyer to properly read the
         | data sheet and understand what the quoted nominal specs mean.
         | 
         | Unless it's safety critical, you usually _don't want_ a system
         | with a bunch of active electronics to prevent someone wiring it
         | up wrong, because those components will interfere with whatever
         | you're hooking it up to, such as the MPPT, the battery, or
         | whatever else.
         | 
         | This is like how AA batteries have a nominal voltage of 1.5V
         | but the actual open circuit voltage is 0.9V~1.65V depending on
         | charge level, temperature, etc. If you connect an AA to
         | something that'll explode at a voltage of 1.55V, that's on you.
         | 
         | Similarly if you buy a 470 ohm resistor, you will find in on
         | the data sheet that's usually at 20degC. To know what it'll be
         | at any other temperature, you'll need to use the temperature
         | coefficient to calculate it.
        
           | jama211 wrote:
           | This isn't electronic components, this is sold as a consumer
           | level gadget that anyone can use. No one expects a standard
           | consumer to understand data sheets like that.
           | 
           | You started off by saying you don't know about the components
           | they're selling - but that turns out to be absolutely
           | critical to understanding the context here.
           | 
           | Either way, I can't believe they just let it fry the main
           | board instead of having a sacrificial fuse or equivalent go
           | first in these scenarios, whether it was a product aimed at
           | professionals or not. It's just dumb.
        
         | mschuster91 wrote:
         | Maybe it would be a good idea to at least add a pair of MOSFETs
         | (one for each rail, + and -) and a voltage meter? Like, the
         | voltage doesn't rise to maximum instantaneously, there should
         | be ample of time to detect voltage rising to a critical amount.
         | 
         | So say, the input is rated for 150V, spec the components to
         | sustain 180V, and trigger the MOSFETs to disconnect the panels
         | at > 160V.
         | 
         | And maybe also add a big ass buffer capacitor, that can be used
         | to soak up a bit more energy in the case of an inrush spike
         | before the MOSFETs actually disconnect.
        
           | privatelypublic wrote:
           | MosFET's or IGBTs are likely what failed. And, capacitance is
           | something you do not want on a string of PV.
           | 
           | DC starts getting really nasty to deal with somewhere between
           | 36-52v, with 150v of panels not being something joe-blow
           | should be able to buy on amazon. Designing these systems to
           | be safe is difficult.
        
       | hathawsh wrote:
       | A few years ago, I plugged a single 100W solar panel into a
       | battery pack that advertised it accepts 18 volts. I left it
       | plugged in, on my deck, for hours. When I came back, there was a
       | foul smell and some parts of the battery pack had turned black,
       | apparently from getting charred. The battery pack no longer
       | worked at all. I was very fortunate that only the control circuit
       | had been destroyed and the battery cells (and my deck) had not
       | been touched.
       | 
       | Lesson learned: don't skimp on Li-ion battery packs!
       | 
       | Also, I have a question about this article. Don't EcoFlow battery
       | packs have a circuit that checks the incoming voltage and
       | automatically shuts off charging if the voltage is too high? I
       | would also expect a loud alert.
        
       | righthand wrote:
       | Current title is actually a subtitle. Actual title:
       | 
       | `Solar Panels + Cold = A Potential Problem`
        
         | marginalia_nu wrote:
         | To be honest I went into it half expecting it to be about papal
         | elections[1].
         | 
         | [1] https://theconversation.com/conclave-the-chemistry-behind-
         | th...
        
         | tgv wrote:
         | The subtitle is, though, and I do find a problem with it. There
         | might be someone out there (possibly not sober) who thinks
         | "Magic smoke? Let's see some!" It also somewhat distorts the
         | original. It should be more like "unless you want the magic
         | smoke to escape." The smoke's magic properties are gone once
         | that happens. At least, nobody has ever proven the escapee
         | smoke has any.
        
         | tomhow wrote:
         | Thanks, we've updated the HN title to the article's main title
         | now.
        
       | bob1029 wrote:
       | I never tried the solar charging on my ecoflow so this fragility
       | surprises me a bit.
       | 
       | I've been able to run laundry in a machine with a 1/2hp motor
       | using the inverter side on multiple occasions. No smoke or funny
       | smells. My 2200w generator would trip out the instant the spin
       | cycle tried to start.
        
         | dotancohen wrote:
         | Slightly OT, but how big of a capacitor would be needed to
         | smooth out those current spikes? Solar-friendly could be a
         | selling point for some appliances.
         | 
         | I wonder if such a capacitor could even be retrofitted.
        
           | namibj wrote:
           | Don't bother; at that point just plug them into 200~300 V DC
           | right to the battery (with just fuse and meter between, no
           | need for any conversion, the washer motor controller that'd
           | be needed to utilize a capacitor for smoothing these spikes
           | would do just fine on a reasonable battery charge/discharge
           | voltage spread.
        
             | dotancohen wrote:
             | Do any home battery systems, or home appliances, actually
             | support this?
        
           | bob1029 wrote:
           | A capacitor wouldn't help in this case. They're most useful
           | when you need to overcome transient situations like a locked
           | rotor, not when you have a heavy drum that needs to be spun
           | up from zero. During this phase the machine can consume well
           | over 2kW of power for a few seconds. The circuit is rated for
           | _continuous_ 15A, but it has no problem supplying 20 or 25
           | for a brief period of time.
        
             | dotancohen wrote:
             | I'm sure that home mains would have no problem, but a solar
             | installation might. Would a small li-ion help smooth over
             | those amperage hills?
        
               | jacquesm wrote:
               | It would help at noon, when usually inverters make so
               | much power they push the local grid to saturation which
               | causes them to disconnect from the grid for a while.
               | There are different rules for this for different
               | localities, typically the installer will pick the regime
               | appropriate for the local grid. Where I live (NL) the
               | voltage is allowed to hit 253V for up to a minute, if it
               | takes longer than that my inverters will switch off.
               | That's a requirement to pass inspection, if your inverter
               | can not do this then that's an automatic fail.
               | 
               | There are 'home batteries' that store power for practical
               | reasons up to a day, maybe two. They are useful for
               | sunny/cloudy conditions to maximize the amount of power
               | locally consumed. But battery storage and retrieval isn't
               | free and so far - at least, for my installation - this
               | does not make economic sense. But another factor of two
               | in price drop for my preferred chemistry and it
               | definitely would make sense and then I would probably
               | install about 20KWh worth of capacity. The trick then
               | becomes to balance power sent to the grid and sent to the
               | battery so that you maximize the utility of the grid in
               | order not to wear out the battery prematurely. That means
               | cycling the battery between 70 and 90% state-of-charge
               | for Lithium-Ion. I'd much rather have Lithium Titanate so
               | that is what I'll be holding out for, they are already
               | available, but still too expensive. But they're much
               | safer and have far better charge/discharge curves and
               | life-span.
        
               | dotancohen wrote:
               | I actually meant a small li-ion inside the appliance, to
               | smooth out the load. Do any batteries support 20C or 30C?
               | That seems like enough to smooth such a load.
        
               | jacquesm wrote:
               | That's a very complex and potentially dangerous device.
        
         | rini17 wrote:
         | The solar panel with inverter does not have any inertia so it
         | can survive power spikes more easily, can lower the voltage
         | till it's over. The generator on the other hand has physical
         | rotating parts that could be damaged by sudden torque asked by
         | increased load. Of course it could be mitigated with additional
         | "soft start" circuitry on the motor but that's usually not
         | included. Not capacitor alone please, you risk more damage.
        
       | uyzstvqs wrote:
       | Sounds to me like someone is misrepresenting their products. A
       | solar panel's VoC should be its maximum possible output in ideal
       | conditions (open circuit). If that's under your product's maximum
       | input voltage, it should be no problem. Ever.
       | 
       | Is EcoFlow advertising a higher input voltage than their products
       | can actually take, assuming most people won't actually reach it
       | due to temperature inefficiencies? That'd be false marketing, and
       | it'd make this article manipulative, false blaming of the
       | customer.
        
         | taneq wrote:
         | What does "maximum possible voltage" mean for a solar panel? Do
         | you include things like cloud edge effect (which increases
         | incident light beyond direct sunlight?) What about installs
         | with a nearby window reflecting light onto the panel? Do you
         | include ultra-cold environments (which will reduce the
         | resistance and therefore often increase voltage, although
         | admittedly not, I think, Voc)?
        
           | GLdRH wrote:
           | Obviously you include everything, otherwise it wouldn't be a
           | maximum. You can define a minimum temperature for this, of
           | course, but the customer should know about it.
        
             | numpad0 wrote:
             | There's no theoretical maximum voltages for solar panels
             | like there kind of is for batteries. They're just giant
             | array of photodiodes and they just generate whatever
             | voltage potentials proportionate to amount of lights
             | received.
             | 
             | You could produce a "max voltage flying low earth orbit
             | over Gobi with no shadows from Starlinks" value, but that's
             | just the value for circumstantial most absurd situation you
             | happened to have come up with, not a guaranteed theoretical
             | maximum.
        
               | jimnotgym wrote:
               | So it is doubly important that all equipment downstream
               | has overvoltage protection?
               | 
               | In fact considering there is no theoretical maximum, it
               | would be downright negligent not to have overvoltage
               | protection
        
               | numpad0 wrote:
               | Yeah, billowing magic smoke just sounds wrong. No
               | disagreement there.
        
               | mrob wrote:
               | There is a theoretical maximum: the open circuit voltage
               | of a single photovoltaic junction cannot exceed the
               | bandgap of the semiconductor used, no matter how much
               | light you apply. The manufacturer knows the semiconductor
               | used and the number of junctions in series.
        
               | adrian_b wrote:
               | The current is what varies proportionally with the amount
               | of light received.
               | 
               | The open-circuit voltage depends mostly on the structure
               | of the solar cells and on the temperature. It has only a
               | very weak (logarithmic) dependence on the amount of light
               | received.
               | 
               | The voltage that you measure at the output depends on the
               | open-circuit voltage, on the amount of light received and
               | on the amount of current that you draw from the panel.
               | 
               | The maximum open circuit voltage for a solar cell is easy
               | to estimate, because it happens at the minimum
               | temperature for which it is designed and the maximum
               | solar illumination. It can be exceeded only using a light
               | concentrator that projects on the panel light collected
               | from a much greater area.
        
               | namibj wrote:
               | They produce current until the diodes start conducting
               | given the forward voltage, as they'll take any current
               | you don't extract off of your hands.
               | 
               | Of course if you want to extract maximum power you have
               | to balance the higher worth of the current you take
               | against the loss of current to the diode forward
               | conduction.
        
           | uyzstvqs wrote:
           | VoC is the maximum potential voltage a cell is physically
           | capable of producing. It does not consider real-world
           | conditions. Rather, real-world conditions cause the solar
           | panel's output voltage to be somewhere between 0 and its VoC.
        
             | sunshinesnacks wrote:
             | Voc is just the open circuit voltage measured at the
             | terminals (plugs). "Nameplate" Voc is at standard test
             | conditions (STC) of 1000 W/m^2, 25 deg C cell temperature,
             | and a standard are mass/spectrum. The combo of 1000 W/m^2
             | and 25 C cell temp is not common in the real world in most
             | climates, but still happens. Even relatively hot climates
             | can have times in winter that exceed nameplate Voc if
             | inverters turn off (making the panels go to open circuit).
        
         | guerby wrote:
         | All solar panel datasheet have temp coefficient, eg for one
         | random ecoflow solar panel:                  Temperature
         | Coefficient Specifications        TKPower -(0.39+-0.02)%/k
         | TKVoltage -(0.33+-0.03)%/k        TKCurrent +(0.06+-0.015)%/k
         | 
         | source
         | https://websiteoss.ecoflow.com/cms/upload/2022/10/15/-139121...
         | 
         | STC ("standard testing conditions" for solar panels) is 25C so
         | if it's freezing 0C you have 25 multiplied by 0.33 Volt = 8.25
         | Volt more than STC in open circuit situation.
         | 
         | Unfortunately inverter manufacturers seldom document how many
         | Volt will destroy the MPPT and up to how many Volt the MPPT
         | will safely turn off by itself before breaking.
        
           | namibj wrote:
           | Not to mention a fail-safe MPPT would/should just crowbar the
           | input if there's any potential for overvoltage.
           | 
           | Solar panels are current sources that waste their power into
           | a long string of silicon PIN diodes that eventually reach
           | their forward voltage and begin to eat up all that juicy
           | current. You can just take the current and keep the voltage
           | as low as you want, just make sure to take all the current or
           | it's voltage will rise to let the diodes take the current you
           | aren't using.
        
       | taneq wrote:
       | What we're seeing here is the mismatch between component level
       | specs and end user ratings. A device which is rated to 24V input
       | power will probably tolerate up to 32V and it surviving 60V would
       | not be uncommon. A component with a Vmax of 24V probably explodes
       | if it sees 25V.
        
       | gsf_emergency_2 wrote:
       | To flip this into a potential _solution_ to a wider problem--
       | global thermal balance-- combine solar panels with radiative
       | cooling.
       | 
       | https://www.sciencedirect.com/science/article/pii/S258900422...
       | 
       | https://www.pv-magazine.com/2025/01/13/daytime-radiative-coo...
        
         | pfdietz wrote:
         | https://web.stanford.edu/group/fan/publication/Li_ACSPhotoni...
        
       | Faaak wrote:
       | Last year, I did yet another PV install at a friends house. While
       | plugging the SMA inverter to the solar field (600V), I fucked up
       | and inverted plus & minus.
       | 
       | Nothing happened. I read the manual and realised that SMA
       | inverters are protected against reverse polarity. Yeah, a bit
       | more expensive, but well worth it
        
         | namibj wrote:
         | I'm more surprised you managed to plug them in reversed; did
         | you have good reason to avoid the polarized semi-pwrmanently-
         | latching connects that most panels ship with?
        
       | phkahler wrote:
       | >> With mixed solar panels, lowest volts in parallel strands
       | prevails
       | 
       | If a panel can hold down the voltage of others, their device
       | should be able to do the same.
       | 
       | Sounds like a corner case their software can't handle. Even so,
       | the hardware should not go up in smoke.
        
       | myself248 wrote:
       | This is what happens when something goes mainstream. The
       | background knowledge that "everybody knows" when it's niche,
       | because only turbo-nerds are into it, simply isn't common sense
       | for everybody in the wider population.
       | 
       | Back when Home Power magazine started up, the panels were super
       | expensive, and squeezing out every watt was important. Since high
       | temperatures decrease voltage and output, keeping the panels cool
       | (while baking in the sun!) was top-of-mind for every
       | installation. And right along with learning that critical
       | consideration, everyone also learned the caveat that in the
       | bitter cold, that very same phenomenon means they can produce
       | significantly _more_. Temperature coefficient was simply
       | something  "everyone knew".
       | 
       | Now they're so cheap nobody cares. The magazine shut down because
       | "alternative power" and EVs aren't exactly alternative anymore,
       | you can buy one off the dealer's lot, it's nuts. And the panels
       | are crazy cheap now. If you lose 10% because the panels are hot,
       | it's likely cheaper to just buy 10% more panels, than to redesign
       | your support brackets to allow better airflow. But nobody
       | highlights the phenomenon behind the efficiency loss.
       | 
       | "Everybody knew" that the ratings on the panel are at Standard
       | Test Conditions: 25degC and 1000W/m2. That's almost never the
       | conditions in the real world, but it establishes a legal baseline
       | whereby panels can be compared apples-to-apples and advertising
       | kept honest (if anyone cared), but deviate from STC and output
       | will go down, or up. Again, ask _today 's_ consumer what the
       | ratings on the label mean, and most of 'em have never heard of
       | STC nor could define how the nameplate wattage is just one point
       | on a curve.
       | 
       | Is this the panel manufacturer's fault? They're labeling things
       | precisely the same as they've labeled them for 40-plus years.
       | (Perhaps there's even more data on the panel label now, as Vmp
       | and Imp are typically specified now, and they weren't always
       | universal.)
       | 
       | Edit to add: The label doesn't typically specify the temperature
       | coefficient, but for every panel I've checked, _it is in the
       | datasheet_. But who reads datasheets?
       | 
       | Is it the inverter manufacturer's fault? They're labeling things
       | precisely the same as they've labeled them for 40-plus years. The
       | input max is a hard limit where the silicon can take no more, and
       | there's a certain amount of headroom required between that and
       | the panels' max, _after_ compensating for temperature
       | coefficient. Of course you calculate your panel voltage for _your
       | local conditions_ before comparing it to the inverter input, duh!
       | 
       | Everyone knows that! Except now they don't.
        
         | jacquesm wrote:
         | The input max is for most inverters on the market now a
         | setpoint where they will simply disconnect, stop generating
         | power and go into an error state that you need to hard-reset if
         | you want to use the inverter again. It's pretty typical to have
         | a 1000V hard limit on a nominally 800V or 600V system. If
         | you're going to ride close to the limit then on some days you
         | will see overvoltage and disconnects. So it is something you
         | simply should not do. But people think that if the label says
         | 1000V then 990V total nominal panel voltage should be fine,
         | which it obviously is not. Panels are analog devices, they will
         | produce an open circuit voltage much higher than their nominal
         | use voltage and when you're on a switched mode inverter that
         | means that the average voltage may well be 'in spec' but the
         | voltage from one millisecond to another may well be outside of
         | that if the system was built 'on the edge'. And because
         | inverters have to take the grid side into account as well (they
         | are not allowed to exceed certain voltages) there is always the
         | risk of not being able to load the panels sufficiently to get
         | the voltage to drop. So you should side your system so that the
         | open loop voltage of your panels under ideal conditions is
         | still comfortably lower than the max input voltage of the
         | inverter. 800V nominal is pretty close to that limit, 700 is
         | better and 600 is playing it safe.
         | 
         | I think one of the main reasons why installers tend to
         | overprovision voltage wise is that they count on the inverters
         | switching off the whole string every now and then versus being
         | able to make more power without a lot of additional wiring
         | under normal conditions. The net effect of that is positive.
         | 
         | Low quality inverters (the ones without the ability to
         | disconnect the HV side autonomously) should be avoided like the
         | plague anyway, those are simply unsafe and as far as I am
         | concerned should not be allowed for re-sale at all.
         | 
         | My own system can make 17KW on a very good day in March at 1 pm
         | or so, but normally it is closer to 12KW even in the summer. So
         | those peaks are actually substantially over the normal output.
         | Over a given day the average is about 5 KW or so from sunrise
         | to sundown, and those first and last hours hardly contribute.
        
       | metalman wrote:
       | Where to start, eh! So most everything to do with off grid
       | specifications can be listed as "nominal", ish, depending on,
       | etc.Not knowing this means that persistance will provide the
       | circumstance to be educated. There are a number of ways to get
       | things wrong and melt stuff, or get hurt. Batteries should always
       | be treated as unpredictable dangerous beasts, happy as a clam if
       | they are treated just right, but capable of producing trouble and
       | disaster, or just del8vering a viscious bite to the unsuspecting
       | and surviving to do it again. A 48volt (nominal) battery bank
       | will happily turn the required 10mm wrench into single
       | demonstration of a wide range of metelurgical and other
       | phenomina. For fun on a cold morning take the leads from a 3 kw
       | solar array, off, and then strike the wires to produce a realy
       | big fat arc, h3y hey! The simple fact, that I tell enthused,nice,
       | but clearly unprepared people who express interest in "off grid",
       | is that I do it, but it's not for everybody, as there is a
       | significant technical learning curve, plus the required physical
       | skills to mount panels, run wireing, deal with battery banks,set
       | up the systems, and if costs are to be kept to a minimum then
       | source parts from distributors or import directly.
        
       | bryanlarsen wrote:
       | On the other hand, properly designed solar can do surprisingly
       | well surprisingly far north.
       | 
       | Here's one in Tromso Norway, well north of the Arctic Circle.
       | 
       | https://cleantechnica.com/2025/09/27/bifacial-rooftop-vertic...
        
       | sowbug wrote:
       | I can imagine future solar panels sending spec data to the MPPT
       | using Power Line Communication (PLC), allowing the system to shut
       | itself down gracefully rather than dying. Rapid-shutdown systems
       | already send keepalives using PLC today.
       | 
       | But then it goes all Black Mirror, with manufacturers restricting
       | solar-panel operation to approved devices only, and UIDs being
       | used to enhance shareholder value through recurring subscription
       | revenue.
        
         | namibj wrote:
         | The MPPT could just short them out and it'd be fine; solar
         | panels are a current source with a huge string of non-light-
         | emitting diodes wired in parallel with the output happy to soak
         | up any excess current around their forward voltage.
         | 
         | (Technically the current source in question is _within_ the
         | diode's junction capacitance.)
        
       | EcommerceFlow wrote:
       | Cool article. The real solution to this is have huge arrays in
       | the desert and move the energy north, which is 100% possible.
        
         | adrianN wrote:
         | There are a lot of possible things. The question is which is
         | the easiest to get financing for.
        
         | phyzome wrote:
         | I don't think that addresses the thing that the article is
         | actually about...
        
       | cornstalks wrote:
       | A lot of people here are saying things are mislabeled, but every
       | single solar panel comes with a datasheet that shows its Voc and
       | temperature coefficient.
       | 
       | Solar panel manufactures can't give you a hard maximum on voltage
       | because temperature will make that vary. Anyone who is buying
       | solar panels without understanding the temperature coefficient
       | shouldn't be buying solar panels. It's not hard to understand and
       | there are hundreds of guides out there explaining it if you just
       | search for terms on the datasheet.
        
       | 1970-01-01 wrote:
       | >Plugging in four 400w solar panels in series is similar to
       | filling your gasoline powered car with diesel and wondering why
       | the car manufacturer isn't replacing your new car.
       | 
       | Ok, that is a very bad answer. Diesel fuel contains more amounts
       | of energy per drop as gasoline, but that doesn't mean engine
       | damage will result. Diesel fuel will not damage an engine if you
       | were stupid enough to get it wrong at the pump. It will simply
       | refuse to cycle until the diesel fuel is pumped out and the
       | correct fuel is pumped in.
        
         | stockresearcher wrote:
         | Maybe it's different in the rest of the world (I doubt it), but
         | the fuel nozzles for gasoline and diesel are different. You
         | can't put a diesel nozzle into the opening on a gasoline car,
         | so it's rather difficult to fill a gasoline car with diesel
         | fuel.
         | 
         | The other way around is possible. You can fill a diesel tank
         | with gasoline. Whether it destroys the engine or not depends on
         | how much gasoline you put in. A gallon or two that is then
         | diluted by filling the rest of the tank with diesel is not
         | likely to cause any lasting damage. If you fill a tank 3/4 of
         | the way with gasoline and try running it in a diesel you are
         | probably going to need a new engine.
         | 
         | So yeah, the analogy is not good. Slightly exceeding the rated
         | voltage and breaking the whole thing is usually not the same as
         | putting a little gasoline in your diesel tank.
        
       | nerdralph wrote:
       | Calculating temperature correction is in both the NEC and CEC.
       | Here's the CEC version:
       | 
       | 64-202 Voltage of solar photovoltaic systems (see Appendix B)
       | 
       | 1) The maximum photovoltaic source and output circuit voltage
       | shall be the rated open-circuit voltage of the photovoltaic power
       | source multiplied by 125%.
       | 
       | 2) Notwithstanding Subrule 1), the maximum photovoltaic source
       | and output circuit voltage shall be permitted to be calculated
       | using a) the rated open-circuit voltage of the photovoltaic power
       | source; b) the difference between 25 degC and the lowest expected
       | daily minimum temperature; and c) the voltage temperature
       | coefficient as specified by the manufacturer.
        
       | PaulKeeble wrote:
       | The cause of this problem is the standards for Solar Panels, that
       | has the outputs measured at 25C so they are comparable with each
       | other. The specification sheets for panels do list their peak
       | voltage in other conditions but all the advertising is based on
       | the standard. Solar installers know about this and size
       | accordingly but your average consumer doesn't and is very quickly
       | going to get into trouble with this.
       | 
       | I think what Delta needs to do here is accept that the standards
       | mean all Solar will be sold this way and appropriately oversize
       | the inverter so that it can cope with -10C sunny days. Yes its
       | annoying for them but the reality is devices sold to people who
       | don't know how all this works need to compensate for lack of
       | expert knowledge in its user base.
        
       | jacquesm wrote:
       | This is not a problem in a properly dimensioned system at all.
       | 
       | It is still well within the 'engineering reserve'. Solar panels
       | produce the most power in mid March, when they are cooled very
       | well by the ambient air but the sun is already lining up nicely
       | with the panels at mid-day. But those conditions are pretty rare,
       | and most inverters will handle this gracefully by simply dumping
       | some of the excess power as heat - or in the better ones, by
       | simply chopping the input voltage at a high frequency. This
       | allows for very fine control over the average power and will help
       | to keep the voltage under the isolation break down voltage (which
       | usually is a very large factor over the voltages that you see in
       | practice).
       | 
       | My own system is 50 panels, 1000V maximum on panels that
       | nominally produce up to 100V, so I never have more than 8 of them
       | in series. That leaves 200V to play with and I've never seen it
       | get close to that 1000V. The inverters are easily capable of
       | dealing with this and if the strings were to ever exceed 1000V
       | then the inverters would simply disconnect those strings with
       | their internal disconnect relays.
       | 
       | So, in closing: don't run your system 'on the limit' or rare
       | conditions will push it over the limit. But even if you do:
       | inverters are fairly bullet proof nowadays and if you over-volt
       | the input the vast majority of the ones that you can normally buy
       | are going to just switch off and move to an error state that will
       | require you to power them down before they will be usable again.
        
       | mulle_nat wrote:
       | Can anyone comment on the "You can exceed the amperage specs" ? I
       | made myself a little case study using 4x1W panels and using them
       | in series and parallel. I got the distinct impression that
       | running panels in parallel is better in not so bright conditions
       | compared to a single panel. Whereas a serial configuration made
       | it worse. Since the sun doesn't shine here that much. Running in
       | parallel seems to be preferable, but it would slightly exceed the
       | amperage spec of a few converter i sampled.
        
         | jacquesm wrote:
         | The problem is usually shading, not so much the capacity of the
         | wiring, though, if you try hard enough you can exceed the
         | rating of the final stretch of wiring to the inverter (or the
         | little pigtail in the inverter if you connect all of the
         | strings at max voltage/amperage). Shading can really upset the
         | current flow in a set of parallel/series connected panels and
         | can cause local hotspots due to overcurrent. Usually inverters
         | are pretty smart about this and they'll detect that you are
         | pushing it further than is responsible and they will just
         | switch off. I've purposefully triggered such conditions to
         | ensure my installation is safe and I was pretty impressed with
         | how utterly painless fault detection, isolation and recovery
         | are in modern inverters. I also had an older one and there it
         | definitely wasn't all that friendly, to the point that the
         | whole thing had to be hard disconnected from the grid before it
         | would work again.
        
       | jama211 wrote:
       | Ecoflow fucked up, more news at 11.
        
       | jlundberg wrote:
       | Our installation from 2017 of 40 panels work great here in the
       | middle of Sweden.
       | 
       | Covered in snow over the winter and generate little power
       | November-February but rest of the year we have fine power output,
       | with peaks May-July (obviously).
        
       | londons_explore wrote:
       | Solar inverters could be designed smarter.
       | 
       | Today's inverters have a volt limit and an amp limit and you may
       | stay within both.
       | 
       | But physics doesn't require that - you could instead design a
       | solar inverter where you could stay within _either_!
       | 
       | It would work by detecting when one limit (volts or amps) was
       | about to be exceeded, and pushing the operational point away from
       | there. Remember that for solar there are _two_ zero power - ie
       | safe - points. I=0 is the usual one, but V=0 (ie short circuit)
       | is equally safe.
       | 
       | So this hypothetical inverter would operate between one of the
       | safe points and the max power point.
       | 
       | Obviously whilst installing the system and humans unplugging
       | wires, the V=0, huge current safe point is impractical. But
       | that's why you have breakers.
        
       ___________________________________________________________________
       (page generated 2025-09-28 23:01 UTC)