[HN Gopher] 2025 Iberia Blackout Report [pdf]
       ___________________________________________________________________
        
       2025 Iberia Blackout Report [pdf]
        
       Author : leymed
       Score  : 91 points
       Date   : 2025-06-23 18:34 UTC (4 hours ago)
        
 (HTM) web link (media.licdn.com)
 (TXT) w3m dump (media.licdn.com)
        
       | fuoqi wrote:
       | >Given the timing of this drop in solar generation, in the middle
       | of the production ramp-up and without any meteorological
       | phenomena to explain it, the most plausible explanation is that
       | it is due to market reasons (prices)
       | 
       | >These changes in production can be significant (if the price
       | signals from the markets are sufficiently strong) and affect the
       | energy flows in the networks and the stresses in the nodes
       | 
       | >Regarding the correlation between changes in generation and
       | voltage: if the generation operating at power factor falls (with
       | the existing regulation, the renewable generation), there is a
       | decrease in the reactive energy absorbed by these installations
       | (since it is reduced proportionally to the reduction in
       | generation). Additionally, as the energy transmitted by the
       | networks decreases due to this reduction in generation, the
       | capacitive effects of the electrical circuits increase as they
       | become more discharged, which causes an increase in reactive
       | energy. Both effects (higher reactive power production by the
       | circuits and lower reactive power absorption) push the voltages
       | upwards.
       | 
       | As expected, renewables played the leading role in
       | destabilization of the grid which led to the collapse. Of course,
       | these instabilities could be worked around on the grid level
       | using various (not cheap) measures, so you may argue that it's
       | not renewables' "fault", but the fact still stands: above the
       | certain threshold of renewable generation the current grid
       | architecture becomes increasingly unstable.
       | 
       | I wrote exactly about it in this comment
       | https://news.ycombinator.com/item?id=43831523 and its child
       | comment, but the fans of renewables just flagged it.
        
         | matsemann wrote:
         | But the quote literally spells out it was market forces, not
         | some instability in solar generation?
         | 
         | Your other comment probably got flagged because it started with
         | a huge straw man and had multiple unwarranted jabs in it.
        
           | fuoqi wrote:
           | Temporary negative prices have been caused by the renewable
           | generation which exceeded the grid demand at the time, which
           | then evolved into the nasty feedback loop caused by the
           | reaction of renewable generation to those conditions. You
           | simply do not get such situation with traditional generation,
           | it's the direct consequence of the intermittent nature of
           | renewables and its high ratio in the total generation.
           | 
           | Also, have you read after the market part? Please watch this
           | video https://www.youtube.com/watch?v=7G4ipM2qjfw if the last
           | quote is gibberish to you. It discusses somewhat different
           | issues, but the point still stands.
        
             | pkilgore wrote:
             | Where is the market for someone to get paid to pump water
             | into a reservoir and let it fall down later for $$$?
        
               | pdpi wrote:
               | That market exists, but the window of time here is like
               | twenty minutes. Pumps have inertia and take time to spin
               | up, you can't HFT load and generation.
        
           | shakow wrote:
           | True, but the market moves fast because renewables (or, more
           | precisely, wind & solar) move fast.
           | 
           | There is not much fast trading to be done on a
           | nuke/gas/coal/hydro powerplant ramping up or down, but there
           | is a lot of instability (and thus market volatility) to be
           | found in fast varying solar/wind conditions.
        
         | wavefunction wrote:
         | You quoted
         | 
         | >the most plausible explanation is that it is due to market
         | reasons (prices)
         | 
         | Seems to be market conditions or manipulations or
         | inefficiencies in the market.
        
         | pdpi wrote:
         | What I'm reading from that quote is that the issue wasn't
         | renewables as such, but an issue of power generation reacting
         | too quickly and too intensely to price fluctuations.
         | "Renewables" only matter insofar as they're the sort of
         | generation that, under the current regulatory regime, get to
         | react to those pricing changes.
        
           | baq wrote:
           | The report goes to great lengths to avoid certain words or
           | phrases. The market failed here, it didn't price in risk of
           | grid collapse correctly.
        
             | Yeask wrote:
             | That is a simple and great explanation.
        
           | fuoqi wrote:
           | See the sibling comment:
           | https://news.ycombinator.com/item?id=44360082
        
         | baq wrote:
         | Should've said 'not enough spinning mass' and it'd be perfectly
         | fine for the politically correct and mean the same thing. This
         | was highlighted as a risk for years and it finally
         | materialized.
        
           | philipkglass wrote:
           | According to the operator report linked in another comment by
           | leymed [1], the problem was not a lack of spinning mass
           | (inertia) but voltage instability. From page 16 of the PDF:
           | 
           |  _The incident was NOT caused by a lack of system inertia.
           | Rather, it was triggered by a voltage issue and the cascading
           | disconnection of renewable generation plants, as previously
           | indicated. Higher inertia would have only resulted in a
           | slightly slower frequency decline. However, due to the
           | massive generation loss caused by voltage instability, the
           | system would still have been unrecoverable._
           | 
           | [1] https://news.ycombinator.com/item?id=44360052
        
             | baq wrote:
             | Obviously I'm as good of a grid operator as I was a stealth
             | bomber expert on the weekend, but superficially that just
             | doesn't seem right. Maybe I'm underestimating how much
             | spinning mass would be required, but that still qualifies
             | as 'not enough was present'.
        
       | tofflos wrote:
       | It's a difficult read.
       | 
       | Cybersecurity and digital systems was not the issue but gets
       | thirteen pages of proposed measures. I feel this could have been
       | left out.
       | 
       | Electric System Operation was the issue and gets seven pages of
       | proposed measures.
        
         | leymed wrote:
         | Check this shorter report by the operator:
         | 
         | https://d1n1o4zeyfu21r.cloudfront.net/WEB_Incident_%2028A_Sp...
        
       | AnotherGoodName wrote:
       | Reads very similar to some blackouts we had in Australia. Weakly
       | connected grids with vast geographical distances leading to
       | oscillations that took down the grid.
       | 
       | https://en.wikipedia.org/wiki/2016_South_Australian_blackout
       | 
       | Completely solved with lithium based grid storage at key
       | locations btw. This grid storage has also been massively
       | profitable for it's owners
       | https://en.wikipedia.org/wiki/Hornsdale_Power_Reserve#Revenu...
       | 
       | Australia currently has 4 of the 5 largest battery storage
       | systems under construction as a result of this profit
       | opportunity;
       | https://en.wikipedia.org/wiki/Battery_energy_storage_system#...
       | 
       | You can also read numerous stories of how Australia's lithium ion
       | grid storage systems have prevented blackouts in many cases.
       | https://www.teslarati.com/tesla-big-battery-south-australia-...
       | The fact is that the batteries responsiveness is the fastest of
       | any system at correcting gaps like this. 50/60hz is nothing for a
       | lithium ion battery nor are brief periods of multi-gigawatt
       | draw/dumping as needed.
       | 
       | There's even articles that if Europe investing in battery storage
       | systems like Australia they'd have avoided this.
       | https://reneweconomy.com.au/no-batteries-no-flexibility-spai...
        
         | londons_explore wrote:
         | > nor are brief periods of multi-gigawatt draw/dumping as
         | needed.
         | 
         | Actually this is typically an issue for grid batteries.
         | 
         | Spinning generators can easily briefly go to 10x the rated
         | current for a second or so to smooth out big anomalies.
         | 
         | Stationary batteries inverters can't do 10x current spikes ever
         | - the max they can get to is more like 1.2x for a few seconds.
         | 
         | That means you end up needing a _lot_ of batteries to provide
         | the same spinning reserve as one regular power station.
        
           | AnotherGoodName wrote:
           | Collectively Australia's battery storage systems will be able
           | to beat any single power plant for peak output in Australia
           | once fully built out based on pure numbers. But for these
           | sorts of grid oscillations the more important thing is the
           | localization of generation. Which obviously favours the
           | batteries over large centralized power stations in any case.
        
           | giantg2 wrote:
           | Seems like pumped hydro offers a nice compromise.
        
             | AnotherGoodName wrote:
             | Fwiw the hornsdale battery linked above cost AUD$172
             | million and can provide 2000MW of equivalent inertia. Link:
             | https://www.energymagazine.com.au/sa-approves-world-first-
             | ba...
             | 
             | That equivalent inertia can only be done for short periods
             | but that's exactly what grids need in stability - there's
             | generally no lack of total generation, just a need to jump
             | in and smooth out spikes.
             | 
             | You can't build a dam for that price, nor could you do it
             | in under 100 days from contract signing as that battery was
             | built. Batteries are definitely the answer here. The 'more
             | spinning mass' answers don't make sense since Australia
             | literally solved the above problem in a much cheaper way
             | already.
        
               | giantg2 wrote:
               | You don't need to build a dam, you just need the pipes
               | and pumps for an existing dam (or elevated natural
               | basin).
        
           | ajross wrote:
           | That... doesn't sound correct. Inverters are the cheap part,
           | you can literally wire as many as you want in parallel.
           | Batteries have _immense_ power availability, with most
           | chemistries you can trivially deliver the entire capacity in
           | half an hour or so (more like 5 minutes with lithium cells).
           | 
           | Basically I'm dubious. I'm sure there are grids somewhere
           | that have misprovisioned their inverter capacity, but I don't
           | buy that battery facilities are inherently unable to buffer
           | spikes. Is there a cite I can read?
        
             | AnotherGoodName wrote:
             | Agreed. The relatively small battery substation linked
             | above can output 2GW of equivalent inertia generation (a
             | measure to align batteries to inertial power systems) when
             | needed. That's an entire power station they can match for
             | short periods of time. Link:
             | https://www.energymagazine.com.au/sa-approves-world-first-
             | ba...
             | 
             | Australia's largest power plant has 2.9GW of inertial
             | generation assuming all generators are running at 100%. As
             | in the small battery substation alone comes close to the
             | countries largest power station. I'm not sure where the
             | idea that lithium ion can't dump power quickly comes from.
             | They are absolutely phenomenal at it. Australia's building
             | dozens of these substations too since they are so cheap and
             | reduce overall power costs. It's a win from all points of
             | view.
        
             | probablypower wrote:
             | You can google "system inertia" as a starting point.
        
       | rcarmo wrote:
       | Page 130 is where the actual human readable summary is. Although
       | the previous pages were pretty detailed in explaining the
       | cumulative instabilities.
       | 
       | Sadly, some news outlets are probably only going to look at the
       | recommendations and read "cybersecurity" and (even though they
       | are common sense recommendations) assume there might be more to
       | say about the matter.
        
         | decimalenough wrote:
         | Don't worry, some news outlets will summarize this as
         | "renewables = bad" regardless of what the report actually says.
         | 
         | Oh wait, they already did:
         | https://www.telegraph.co.uk/business/2025/06/18/renewable-en...
         | 
         | Ed: Do I need a /s tag here or something? My point was that we
         | shouldn't worry too much about about the presentation of the
         | report, its actual contents will be spun to suit any narrative
         | regardless.
        
           | baq wrote:
           | Flame bait journalism is one of the things you can count on
           | in any circumstance. If you replace that 'renewables = bad'
           | with 'politicians = idiots' OTOH... sometimes the elected
           | representatives should listen to unelected physicists and
           | engineers. Grid stuff is one of those things.
        
       | decimalenough wrote:
       | > _Non-confidential version of the report of the committee for
       | the analysis of the circumstances surrounding the electricity
       | crisis of the April 28, 2025_
       | 
       | Now I'm curious about what's in the confidential version of the
       | report.
        
         | londons_explore wrote:
         | Based on the redacted bits, it is mostly company names and
         | locations.
        
       | londons_explore wrote:
       | It doesn't look like this report really identifies the root
       | causes...
       | 
       | I would like to see: "We have simulated the complete 200 and 400
       | kV grid of the iberian peninsula and western europe, and can
       | reproduce the situation that occurred. Any one of the following
       | changes would have prevented the issue, and we suggest
       | implementing them all for redundancy. This simulation will be re-
       | run every day from now on to identify future cases similar
       | incidents could occur"
        
         | baq wrote:
         | The engineers knew exactly what's going to happen, the report
         | is politically redacted. Very unfortunate, but completely
         | expected.
        
       | JanneVee wrote:
       | When skimming through the report I got to think of the
       | oscillation problem in RIP routing protocol. Although it isn't
       | the same thing, but it shows the complexity of the problem to
       | anyone who thinks there is a single solution to it.
        
       | gred wrote:
       | Why so many pages of "Recommendation: implement multi-factor
       | authentication" and other IT security irrelevancies? Did they
       | need to pad out the number of pages?
        
         | diggan wrote:
         | > In the systems with network traffic evaluation probes, no
         | records consistent with unauthorized activity have been
         | observed, such as lateral movements, network traces or file
         | movements for vulnerability exploitation or privilege
         | escalation, among others.
         | 
         | > However, as is common in networks and information systems in
         | any sector, other risks have been identified, such as
         | vulnerabilities, deficiencies or inadequate configurations of
         | security measures, which may expose networks and systems to
         | potential risks, for which a series of measures are proposed.
        
       | diggan wrote:
       | Seems the money shot starts at page 131:
       | 
       | > The ultimate cause of the peninsular electrical zero on April
       | 28th was a phenomenon of overvoltages in the form of a "chain
       | reaction" in which high voltages cause generation disconnections,
       | which in turn causes new increases in voltage and thus new
       | disconnections, and so on.
       | 
       | > 1. The system showed insufficient dynamic voltage control
       | capabilities sufficient to maintain stable voltage
       | 
       | > 2. A series of rhythmic oscillations significantly conditioned
       | the system, modifying its configuration and increasing the
       | difficulties for voltage stabilization.
       | 
       | If I understand it correctly (and like software, typical), it was
       | a positive feedback-loop. Since there wasn't enough voltage
       | control, some other station had to be added but got overloaded
       | instead, also turning off, and then on to the next station.
       | 
       | Late addition: It was very helpful for me to read through the
       | "ANNEX X. BRIEF BASICS OF THE ELECTRIC SYSTEM" (page 168) before
       | trying to read the report itself, as it explains a lot of things
       | that the rest of the report (rightly) assumes you already know.
        
         | leymed wrote:
         | I think your interpretation is correct. The voltage control is
         | done at the high level of the grid, meaning the control covers
         | bigger generation stations and major substations. Even if it's
         | small generator, rotating machinery, you won't have strict
         | voltage control other than its own AVR. The problem I see here
         | is that we embed smaller individual generations at the lower
         | level, where they pump the generated power to the grid at the
         | medium voltage level. When you have majority of your generation
         | at this level, you won't have strict control over voltage and
         | even frequency, I assume. I'm still digesting the report, but
         | what I am after is whether they really neglected it and if it
         | is not possible to do voltage control with 50% generation
         | coming from renewable and through medium voltage level, aka
         | lower level.
        