       | pdx_flyer wrote:
       | The article doesn't say much about it but I am sure there is
       | significant work being done at the transmission substations as
       | well to support the extra capacity.
        
         | ghouse wrote:
         | As the new conductors will have lower impedance, some breakers
         | may need to be replaced to interrupt higher fault current.
         | Otherwise, it's likely the only substation equipment needing to
         | upgrade would be series compensation stations which may have
         | lower normal and emergency ratings than the upgraded
         | conductors.
         | 
         | More likely is that lower impedance on the reconductored
         | circuit will cause increased flows on other, non-upgraded
         | circuits, either requiring those to be reconductored, or
         | installing phase-shifting tranformers or reactors to limit
         | current.
        
           | sitkack wrote:
           | If substations are being upgraded, they should also be
           | installing batteries and inverters at the substations at the
           | same time.
        
             | infecto wrote:
             | This sounds like moving the goal and a much more difficult
             | problem than just upgrading the substation.
        
           | pdx_flyer wrote:
           | Good points.
           | 
           | Have you seen a lot of phase-shifting transformers in the
           | U.S.? In my experience they've mostly been in Europe with a
           | few specialized applications in the States.
           | 
           | I would think a utility would want to reconductor the other
           | circuits otherwise they're leaving benefits on the table
           | right?
        
         | specialist wrote:
         | Spot on. David Roberts (Volts) also asked about that in one of
         | his interviews.
         | 
         | IIRC, the expert answer was: substations generally need a
         | retrofit (eg new transformer, breakers, smarts).
         | 
         | Even so, reconductoring is much faster and cheaper than
         | building new lines.
         | 
         | Because retro doesn't require a new permit, often reuse
         | existing footprint, and substations can be upgraded as needed
         | (eg only for sections pushing more power).
        
       | outside1234 wrote:
       | There is also a parallel technology that does a better job of
       | understanding line conditions with regards to heat, humidity,
       | etc. and enables higher utilization as well (versus having to
       | rate the lines to the worst 20 year scenario).
        
         | ghouse wrote:
         | You may be referring to either 1) the real-time line ratings
         | (directionally required by FERC order 881, or 2) technology
         | like the "SmartValve" from Smart Wires which dynamically
         | adjusts impedance to keep conductors within their operating
         | envelope.
         | 
         | Among risks that are managed is ground faults caused by sage
         | (as the line heats, it expands, getting closer to the ground),
         | or 2) annealing which is a permanent expansion of the conductor
         | due to operating too hot for too long. The advanced conductors
         | use composite cores allowing the conductor to carry more
         | current at a higher temperature with reduced risk for
         | annealing.
        
       | specialist wrote:
       | Good explainer, thanks for posting.
       | 
       | Volts recently interviewed Emilia Chojkiewicz of UC Berkeley
       | (quoted in article) and Jason Huang of TS Conductor.
       | 
       |  _" One easy way to boost the grid: upgrade the power lines"_
       | [Jan 31, 2024] https://www.volts.wtf/p/one-easy-way-to-boost-the-
       | grid-upgra...
       | 
       | Here's a prior episode about "grid enhancing technologies" in
       | general, including reconductoring.
       | 
       |  _" Getting more out of the grid we've already built"_ [Sep 13,
       | 2023] https://www.volts.wtf/p/getting-more-out-of-the-grid-weve
       | 
       | Grids are a common topic on Volts. Permitting, policy,
       | intransigent utilities, open data standards, biz models,
       | decentralization, virtual power plants, creating a national grid,
       | etc.
       | 
       | A handful of climate crisis / net-zero podcasts like Volts
       | connect and catalyze people, resulting in new startups,
       | legislation, and giving people hope & energy.
       | 
       | Highest recommendation.
       | 
       | Aside:
       | 
       | INTERGRID is my term for our future perfect grid-of-grids.
       | Inspired by the internet, of course. One such effort is
       | (Alphabet) X & AES' Tapestry project
       | https://x.company/projects/tapestry/ .
        
       | cool_dude85 wrote:
       | Strange not to mention wire weight which I gather is an extremely
       | important factor. If these are also heavier, they may sag more
       | for strictly physical reasons and that would cause problems. I
       | guess the modeling behind this article probably takes that into
       | account.
        
         | ghouse wrote:
         | Increased weight makes reconductoring much more difficult as
         | the structures are designed to carry specific weight. Increased
         | size can also impact structure loading from ice or wind. So,
         | generally, reconductoring does not materially increase weight.
         | 
         | The primary difference between the traditional conductors and
         | advanced conductors is temperature tolerance. Most transmission
         | lines are aluminum conductors with a steel core for strength
         | (ASCR). As current increases, so does temperature, causing
         | lines to sag (or the steel anneal if too hot).
         | 
         | Advanced conductors use a different composition to operate at
         | higher temperatures, or otherwise carry more current (one
         | example: aluminum conductor, composite reinforced, or ACCR) so
         | as to have similar weight (and profile) to the original,
         | traditional conductor.
        
         | elihu wrote:
         | > "Chojkiewicz and her colleagues at Berkeley's Energy and
         | Resources Group and Goldman School of Public Policy studied the
         | use of advanced conductors that wrap more aluminum around a
         | smaller, stronger composite core. These Aluminum Conductor
         | Composite Cores (ACCCs) are more conductive and can operate at
         | higher temperatures, resulting in roughly a doubling of
         | capacity for an equivalent diameter wire."
         | 
         | It isn't clear from the text, but the wires might not actually
         | be any heavier, given that they replace the steel core with a
         | composite.
         | 
         | Aluminum is about 2.7 g/cm^3, whereas steel is around 7.85.
         | 
         | I'd imagine they can switch to a slightly smaller cable size if
         | they have to keep to the original weight and a new cable
         | happens to be a little heavier at the same diameter.
         | 
         | I'm kind of surprised they don't lose the advantages of
         | stranded cable when switching to something that looks more like
         | a solid cable. As I understand it, for AC wiring you usually
         | want a lot of strands because most of the current tends to
         | travel on the surface. Maybe that's less of a thing for high
         | voltage. Or maybe the seams between the strands are enough to
         | cause the skin effect even if they're tight-fitting.
        
           | tuatoru wrote:
           | Skin effect is a high-frequency thing. From memory the down-
           | rating tables start at 100 kHz.
        
             | Kirby64 wrote:
             | Skin effect works at all frequencies besides DC. At 60 Hz
             | it's 8.5mm. So, solid conductors thicker than 17mm have
             | some skin loss. You can mitigate this by winding multi
             | strand wire in a particular way, though.
        
         | Animats wrote:
         | Composite-core cables are lighter. The core is carbon and
         | fiberglas fiber, rather than steel.[1]
         | 
         | [1] https://compow.com/blog/midal-accc
        
       | gok wrote:
       | previously https://news.ycombinator.com/item?id=39485940
        
       | wernerb wrote:
       | These cables can run much hotter and so have better capacity. BUT
       | there is a big downside. Because they run so hot (you can grill a
       | burger on them with ease), there will be a lot more resistance
       | resulting in net losses. Also fun, because they can run so hot
       | when rain hits it literally sizzles and cooks resulting in extra
       | noise.
        
         | SketchySeaBeast wrote:
         | Isn't that going to be a fire hazard as well?
        
           | aerostable_slug wrote:
           | They already need to be kept away from vegetation to prevent
           | faults.
        
       | bsder wrote:
       | It's not particularly cheap or effective. From the article:
       | 
       | > Chojkiewicz says her team's modeling neglected those
       | alternatives because their goal was simply to lay out the
       | "nationwide potential," of reconductoring.
       | 
       | They only compared it to buying new land and putting in
       | completely new lines.
       | 
       | They ignored simply increasing the voltage, switching to HVDC and
       | any solution other than "putting in whole new lines".
       | 
       | In particular, the fact that they just ignored HVDC is
       | problematic. HVDC gets you not just cheaper transmission but
       | _lower losses_ so makes better use of what you have even if you
       | don 't immediately boost capacity.
        
         | 7952 wrote:
         | HVDC converter stations are expensive though. And you would
         | need to have one every time you have a substation to directly
         | replace an AC cable. It makes sense for longer distances.
        
         | mastax wrote:
         | Wouldn't increasing the voltage require new towers in most
         | cases? The towers are sized to give sufficient isolation.
        
         | matt-p wrote:
         | HVDC is not a silver bullet.
         | 
         | Converter stations are very expensive and also take more space.
         | You need one every time you tap in/out of the transmission
         | line, great for point to point links say Offshore windfarm to
         | major IC, but general transmission gets tapped into and out of
         | much more frequently. Even if today you plan for this link to
         | be P2P from city A > city B today what happens tomorrow when
         | someone builds a generation plant, or a new town, datacentre
         | campus on that route?
         | 
         | The "efficiency" gain is debatable, you do lose less on
         | transmission but you now have this cost of getting from DC>AC
         | AC>DC which costs roughly 1.1-1.6% - in the grand scheme of
         | things for most schemes any overall efficiency gain is marginal
         | to nil.
         | 
         | Overall the most flexible thing to do is build AC at the
         | highest voltage your towers/interconnect points support (and
         | consider increasing that).
         | 
         | In the UK we are building more lines and converting more
         | substations from 275KV to 400KV.
        
         | quickthrowman wrote:
         | > They ignored simply increasing the voltage
         | 
         | For good reason, you can't do that.
         | 
         | Electrical distribution conductors are insulated by air (and
         | distance). If you crank up the voltage, you could have line-to-
         | line arc flashes if you don't increase the conductor spacing.
         | Increasing the conductor spacing requires new towers, so...
        
       ___________________________________________________________________