[HN Gopher] How the electricity markets respond to a nuclear trip
       ___________________________________________________________________
        
       How the electricity markets respond to a nuclear trip
        
       Author : kmax12
       Score  : 71 points
       Date   : 2024-07-30 17:56 UTC (5 hours ago)
        
 (HTM) web link (blog.gridstatus.io)
 (TXT) w3m dump (blog.gridstatus.io)
        
       | toomuchtodo wrote:
       | Something interesting is that with substantial solar and
       | batteries being deployed in the ERCOT market (in scope grid
       | operator for this piece), solar generation in excess of what the
       | grid can consume with load combined with grid forming inverters
       | (vs traditional grid following) can step in when called upon if a
       | traditionally firmer generator (coal or nuclear) trips out. The
       | potential is already there (photons hitting panels), simply
       | turned down to align with grid demand (curtailment), but if the
       | sun is shining and PV is called upon, curtailment can quickly
       | turn into emergency grid support as long as the sun is shining (I
       | am not familiar how long it takes from ISO signal to inverter
       | command).
       | 
       | It would be cool if individual generators shared this curtailment
       | status/reserve in realtime publicly similar to how ERCOT reports
       | real time generation mix data.
       | 
       | Citations:
       | 
       | https://news.ycombinator.com/item?id=40908526
       | 
       | https://news.ycombinator.com/item?id=38848989
        
         | kccqzy wrote:
         | Most curtailment IIRC is due to insufficient transmission
         | capacity. I doubt curtailed solar can be called upon in an
         | emergency unless the emergency is located very close to the
         | curtailed solar.
        
           | toomuchtodo wrote:
           | It's a fair point (why curtailment is in effect), and I think
           | speaks to the fact that more granular and timely data is
           | needed wrt all nodes and transmission segment within the
           | system. Also a call for more batteries everywhere between
           | generation and load.
           | 
           | With regards to transmission congestion, that is easily fixed
           | with installing batteries at currently storageless renewable
           | generation facilities (the batteries then charge with excess
           | solar, and can continue to discharge after the sun sets or
           | the wind dies down, maximizing transmission utilization
           | temporally). The Inflation Reduction Act also enables those
           | batteries to charge from utility side if needed, whereas
           | before they could only charge from the renewable generation
           | (AC vs DC coupling).
        
             | gunapologist99 wrote:
             | Batteries are extremely expensive per megawatt, not very
             | durable, require carefully controlled temperatures, and
             | their manufacturer and recycling extract a tremendous cost
             | from the environment. For non-mobile usage, batteries
             | shouldn't be seen as any kind of viable solution at scale.
             | 
             | However, there are other ways to store energy;
             | unfortunately, most involve converting electricity to
             | another form of energy such as potential (gravitational)
             | energy, like pumping water uphill or lifting heavy weights.
             | These also have relatively little long-term environmental
             | cost. Unfortunately, they're a bit more inefficient (but so
             | are batteries, relative to some other forms of stored
             | energy such as fossil fuels).
             | 
             | It'd be interesting if we could find some ways to convert
             | landfills or other urban blight issues into a durable
             | energy store without poisoning the environment.
        
               | toomuchtodo wrote:
               | > Batteries are extremely expensive per megawatt, not
               | very durable, require carefully controlled temperatures,
               | and their manufacturer and recycling extract a tremendous
               | cost from the environment. For non-mobile usage,
               | batteries shouldn't be seen as any kind of viable
               | solution at scale.
               | 
               | None of this is accurate. I encourage you to update your
               | mental model with recent data. Citations below for your
               | convenience. AMA, global energy transition is my passion.
               | 
               | https://www.utilitydive.com/news/batteries-texas-
               | consumers-6... ("Utility Dive: Batteries saved Texas
               | consumers $683M during 2-day January freeze: Aurora
               | Energy Research")
               | 
               | https://news.ycombinator.com/item?id=40919052 ("HN:
               | China's Batteries Are Now Cheap Enough to Power Huge
               | Shifts")
               | 
               | https://news.ycombinator.com/item?id=40601878 ("Lazard:
               | IRA brings LCOS of 100MW, 4hr standalone BESS down as low
               | as US$124/MWh"
               | 
               | https://news.ycombinator.com/item?id=35513612 ("HN: The
               | biggest EV battery recycling plant in the US is open for
               | business")
               | 
               | https://www.bloomberg.com/news/articles/2024-04-24/batter
               | y-r... | https://archive.today/OjA91 ("Bloomberg: Battery
               | Recycling Shatters the Myth of Electric Vehicle Waste")
               | 
               | https://www.lazard.com/research-insights/2023-levelized-
               | cost... ("Lazard: 2023 Levelized Cost Of Energy+")
               | 
               | https://raokonidena.substack.com/p/history-
               | of-10000-cycles-o... ("History of 10,000 cycles or 10
               | year warranty for Battery Energy Storage System (BESS)")
               | 
               | https://www.nrel.gov/docs/fy23osti/85332.pdf ("NREL data
               | shows BESS asset life is 15-20 years.")
               | 
               | https://web.archive.org/web/20240728011101/https://www.ei
               | a.g... (US EIA; gray installations are new battery
               | storage planned for deployment over the next 12 months,
               | June 2024 through May 2025)
               | 
               | https://www.eia.gov/todayinenergy/detail.php?id=61202
               | ("US EIA: U.S. battery storage capacity expected to
               | nearly double in 2024")
               | 
               | https://www.eia.gov/todayinenergy/detail.php?id=61424
               | ("US EIA: Solar and battery storage to make up 81% of new
               | U.S. electric-generating capacity in 2024")
               | 
               | https://www.woodmac.com/blogs/energy-pulse/battery-
               | storage-b... ("Wood Mackenzie: Battery storage begins to
               | play a key role for US grids")
               | 
               | https://www.nytimes.com/interactive/2024/05/07/climate/ba
               | tte... ("NY Times: Giant Batteries Are Transforming the
               | Way the U.S. Uses Electricity")
        
               | floatrock wrote:
               | > For non-mobile usage, batteries shouldn't be seen as
               | any kind of viable solution at scale.
               | 
               | Lithium-ion, sure, but aren't there a whole host of other
               | battery chemistries that are basically too big / too
               | heavy to put on vehicles but a lot cheaper so well suited
               | for stationary storage?
               | 
               | Are they _all_ still at the research phase and so
               | currently more expensive than the decades-of-learning-
               | curve lithium-ion?
        
               | shagie wrote:
               | The vanadium redox flow battery.
               | https://en.wikipedia.org/wiki/Vanadium_redox_battery
               | 
               | > For several reasons, including their relative
               | bulkiness, vanadium batteries are typically used for grid
               | energy storage, i.e., attached to power plants/electrical
               | grids.                   VRFBs' main advantages over
               | other types of battery:              no limit on energy
               | capacity         can remain discharged indefinitely
               | without damage         ...         wide operating
               | temperature range including passive cooling         long
               | charge/discharge cycle lives: 15,000-20,000 cycles and
               | 10-20 years.         low levelized cost: (a few tens of
               | cents), approaching the 2016 $0.05 target stated by the
               | United States Department of Energy and the European
               | Commission Strategic Energy Technology Plan EUR0.05
               | target
               | 
               | (and yes, there are disadvantages too)
               | 
               | See also NPR's story: The U.S. made a breakthrough
               | battery discovery -- then gave the technology to China
               | https://www.npr.org/2022/08/03/1114964240/new-battery-
               | techno...
        
               | bboygravity wrote:
               | How is 10 - 20 years "sustainable"?
        
               | toomuchtodo wrote:
               | We're currently experiencing a Cambrian explosion in
               | battery tech. As the technology matures, and we establish
               | a closed loop ecosystem to build and then recycle these
               | systems, longevity can improve over time. To get better
               | at something, you must first suck at it, and 10-20 years
               | is not an immaterial service life for an asset that just
               | sits and hums with no moving parts.
        
               | gunapologist99 wrote:
               | I agree if we were talking about a motor or a pump, but
               | it seems like batteries basically devastate the
               | environment every time we make one, and doing that
               | millions of times every ten years is probably not great.
               | (But I don't know anything about that specific battery
               | technology.. perhaps it's just saltwater and two
               | dissimilar metals.)
        
               | toomuchtodo wrote:
               | https://sustainability.stackexchange.com/questions/9866/i
               | s-l...
        
               | energy123 wrote:
               | Lithium-ion is the cheapest form of stationary storage
               | for the sub-8 hour duration niche. The vast majority of
               | battery storage being deployed is lithium-ion.
               | 
               | Sodium-ion is the second largest contender, with a few
               | pilot facilities opening in China recently, but it will
               | be a few years before it eclipses lithium-ion.
        
               | megaman821 wrote:
               | Not a single thing you said about batteries is true.
               | Pumped hydro is in no way competitive with batteries for
               | most locations. In the future it is likely they won't be
               | competitive in any location.
        
               | jillesvangurp wrote:
               | Better still; the amount of deployed batteries world wide
               | is projected to overtake the amount of deployed hydro
               | this year. Pumped hydro is barely growing. Battery
               | capacity is growing exponentially to eclipse it this
               | year. That's driven by pure economics. Cheaper, better,
               | faster, etc.
        
               | ZeroGravitas wrote:
               | A recent article asks:
               | 
               | "Why did the U.S. miss the battery revolution?"
               | 
               | https://www.noahpinion.blog/p/why-did-the-us-miss-the-
               | batter...
               | 
               | About half the comments on the article were Americans
               | saying very similar things to your comment and denying
               | there was a revolution to have missed, which kind of
               | answers the question posed.
        
               | energy123 wrote:
               | They're the cheapest form of storage after recent price
               | declines, even cheaper than pumped hydro and compressed
               | air.
        
             | galangalalgol wrote:
             | The secure authentication of all those nodes concerns me.
             | Are these old scada systems coommunicating over plaintext
             | rs232 or similar? Is it something running crowdstrike?
        
           | rtkwe wrote:
           | The transmission lines run to solar farms should be able to
           | take 100% of the output of the farm and then some otherwise
           | the farm was over built and wasted money.
        
             | kccqzy wrote:
             | I agree with your use of the word "should" here. But that
             | unfortunately is not what happens in reality.
        
             | adrianmonk wrote:
             | At short distances from the solar farm, yes. But it's not
             | 100% in every direction for arbitrarily long distance. At
             | some point, you assume the energy will be tend to be used
             | sort of near where it's generated.
             | 
             | To put it another way, if you build solar between city A
             | and city B, would you build it so it can still be fully
             | utilized even if city A stops using any power and city B
             | wants all of it? No, you assume city A is always going to
             | need some power.
        
             | callalex wrote:
             | By this definition all reserve capacity is wasted money.
             | That is clearly false, as demonstrated by the event in this
             | article _not_ leading to failure and harm.
        
               | rtkwe wrote:
               | I'm not talking about reserve capacity at the grid level.
               | I'm talking about excess capacity at the individual
               | generation plant level that exceeds the grids capacity to
               | take in. If you can't output the energy onto the grid the
               | only benefit is for local maintenance and you don't need
               | huge amounts of excess capacity to solve that and that
               | excess doesn't help in the event of a large base producer
               | like a nuclear plant going offline because it can't get
               | onto the grid!
        
             | energy123 wrote:
             | That's not necessarily optimal. For home installs, you can
             | overbuild panels because they're cheap compared to the
             | inverter. Then you curtail sometimes at midday and have
             | extra energy on cloudy days and in the morning/afternoon.
             | Turns out that's more cost effective than sizing the panels
             | perfectly. The same logic could apply to utility farms,
             | because transmission lines can be expensive. I don't really
             | know myself since I don't work in the industry, but I would
             | not be surprised if this were the case.
        
         | huijzer wrote:
         | An individual inverter can usually switch in about 4 ms. A
         | Tesla Megapack can go from 0% output to max output in 100 ms.
         | Conversely, gas turbines (the fastest type of traditional power
         | plant) takes about a minute to go from say 40% to 60%. Even in
         | the fastest possible design, there is a mechanical rotor
         | (kinetic energy) that has to change speed.
         | 
         | What I mean to say is that solar and batteries are likely an
         | order of magnitude faster to respond to sudden demand changes.
         | So I would expect a more reliable system when more solar and
         | especially batteries are being added.
        
           | bell-cot wrote:
           | IANAEE (not an electrical engineer), but doesn't a gas
           | turbine spin at a constant speed to drive a 60Hz generator,
           | regardless of whether it's running at 20%, 60%, or 100% of
           | capacity?
        
             | markus92 wrote:
             | When there's a load imbalance on the grid (more load than
             | capacity), the turbines physically slow down as inertial
             | energy is extracted from them. This causes the grid
             | frequency to drop. It takes some time to ramp up production
             | and speed up the turbine etc.
        
               | bell-cot wrote:
               | The maximum slow-down of the turbines (before the
               | generator trips off-line, removing the load on it) is far
               | less than you seem to assume. The article's graph shows
               | the 60.00Hz grid frequency dropping...all the way to
               | 59.92Hz. That's 0.1333%.
               | 
               | For an on-line gas turbine, the time to ramp up
               | production is the second or few needed for the automated
               | controls to open the throttle on the "Gas IN" pipe. It's
               | basically a natural gas-burning turboprop jet engine,
               | with the propeller replaced by a generator. (Yes, this
               | can be less efficient in a combined cycle plant.)
        
               | jeffbee wrote:
               | The more interesting thing about rotating power plants is
               | that they are routinely destroyed by transmission
               | outages, because when a rotating generator is suddenly
               | disconnected from its load, there are infinity terms in
               | the equations that govern its motion and infinity isn't a
               | thing you can resist. For steam turbines the control
               | system has to slam the valve shut on the steam, otherwise
               | the machine would overspeed, and closing that valve
               | destroys some sacrificial part of the steam plumbing
               | (hopefully). Steam power plants have to be inspected and
               | repaired after disconnects and this is one of the
               | numerous reasons why fission kinda sucks on the
               | reliability front.
        
           | leymed wrote:
           | I think you're missing the point how turbine-generator works.
           | The rpm speed has to stay the same, meaning the rotor speed
           | doesn't change. As long as you don't have closed circuit
           | you'll waste that mechanical energy. If you meant starting
           | from stand still position, then you're right it takes couple
           | minutes to pick up the load.
           | 
           | With that said, turbines responding in couple minutes are
           | more reliable as a baseline when you're planning load flow of
           | as big as country or wider area. The basic reason is that you
           | have source of energy under your control such as nuclear,
           | water, gas, coal. You cannot have solar, wind as your
           | baseline, I don't want sound dramatic, but it's kind of
           | suicidal to do that. Solar's ramping is not a win when you
           | consider greater scale.
        
             | ViewTrick1002 wrote:
             | Reliable until it isn't.
             | 
             | The entire grid is a statistical system where we define the
             | acceptable uptime.
             | 
             | Renewables are as good as any other energy source bringing
             | its own fuel, just need to take the variability into
             | account.
             | 
             | https://www.nytimes.com/2022/11/15/business/nuclear-power-
             | fr...
        
               | leymed wrote:
               | You're correct that the system is statistical, and it's
               | planned accordingly. However, we cannot omit the fact
               | that it's the running turbine that responds faster to the
               | unpredictable nature of the grid. The backbone of the
               | grid, aka the baseline plants, are extremely responsive
               | to unpredictable nature of the grid at a greater scale,
               | with enough amount of safety margins to bring into
               | service under unusual circumstances. I really don't see,
               | at least what we have in hand rn, that happening with
               | solar or wind. Without strong baseline you'd experience
               | supply demand imbalance, in engineering terms frequency
               | decay, voltage collapse.
        
           | quickthrowman wrote:
           | > An individual inverter can usually switch in about 4 ms.
           | 
           | A quarter of a 60 hz cycle or a fifth of a 50 hz cycle is
           | _really_ fast. For comparison, it takes a current limiting
           | fuse around a half cycle to clear a short circuit current and
           | a GFCI takes around two cycles to clear a ground fault.
        
         | Reason077 wrote:
         | > _" (I am not familiar how long it takes from ISO signal to
         | inverter command)."_
         | 
         | The grid frequency itself functions as a signal: a deviation
         | below 50/60 Hz indicates support is needed, and a deviation
         | above means curtailment is needed (or load added).
         | 
         | Instant frequency-response assets such as batteries typically
         | monitor the frequency independently and respond as required.
         | They don't need to wait for explicit signals from the ISO.
        
           | toomuchtodo wrote:
           | True! But this signal is typically locally monitored and
           | responded to by individual assets ("frequency response"
           | ancillary services). That is distinct from a grid operator,
           | ISO, whomever is orchestrating grid health to call on
           | generating units due to a supply crunch. Tesla Megapacks can
           | respond within milliseconds to frequency and voltage sags
           | (when configured to provide these services), but Autobidder
           | is what orchestrates and pushes out overarching power control
           | strategy to individual assets (for example) [1] [2] [3].
           | 
           | [1] https://www.tesla.com/support/energy/tesla-
           | software/autobidd...
           | 
           | [2] https://www.tesla.com/support/energy/tesla-software
           | 
           | [3] https://electrek.co/2023/09/15/tesla-autobidder-
           | product-330-...
        
         | sunshinesnacks wrote:
         | Grid following inverters can do something similar, although
         | their response time is usually limited to the grid operator's
         | automatic generation control (AGC) communication cycle, which
         | is typically on the order of 4 to 6 seconds. And this requires
         | plant controllers, and markets/contracts, to be setup for it.
         | 
         | See https://www.nrel.gov/docs/fy24osti/86932.pdf. It deals with
         | estimating reserves from these types of resources, but also
         | talks a bit about general considerations, and references other
         | good papers and demonstrations.
        
       | Symbiote wrote:
       | Where does the 1500MW of heat the reactor is producing go,
       | immediately after the generators are isolated from the grid?
        
         | csours wrote:
         | Water? Same place it was going
        
           | Scoundreller wrote:
           | I mean, at least some percentage was going down the wire.
           | That's why we do it, right?
        
             | csours wrote:
             | It would be funny if we were doing the whole song and dance
             | just to amuse the electrons.
             | 
             | If the turbines are 50% efficient, then the heat load on
             | the cooling towers would double, which I have to assume is
             | WELL within design limits.
             | 
             | You have made me wonder about turbine overspeed and steam
             | bypass.
        
         | rtkwe wrote:
         | The reactor is turned down and rapidly stops producing that
         | much heat. On site backups keep the pumps running to continue
         | cooling the residual heat. There's a long slow tail as lower
         | energy fusion chains tail off towards lead but the vast
         | majority of the power comes down quickly.
        
         | pstrateman wrote:
         | Enthalpy of vaporization for water is very very large.
         | 
         | The amount of heat that can be dissipated by evaporating water
         | is kind of incredible.
        
         | theideaofcoffee wrote:
         | Instead of that energy being directed to the turbines to
         | convert the thermal energy into rotational energy (and thus it
         | to electricity), the reactor begins cooling from the primary
         | reactions (but not completely since secondary reactions/decay
         | still are going) since there is no reaction heat (reactor
         | idled). All of that excess residual heat contained in the mass
         | of the fuel and reactor water is carried away by the cooling
         | water loop, and either out to the cooling tower where it
         | evaporates and releases its energy, or through the next stages
         | of the loop into the cooling supply, most likely a neighboring
         | river or lake.
        
         | gunapologist99 wrote:
         | It seems like you might really be asking about a meltdown
         | scenario.
         | 
         | The reaction can be slowed with control rods, which
         | stops/minimizes the heat from being generated. The previously
         | generated heat still needs to be handled, however (by
         | evaporation).
         | 
         | https://en.wikipedia.org/wiki/Nuclear_reactor
         | 
         | A meltdown occurs when the reaction can't be slowed down
         | through normal means because the safety systems fail.
         | 
         | For example, Fukushima and Chernobyl:
         | 
         | https://en.wikipedia.org/wiki/Fukushima_nuclear_accident
         | 
         | https://en.wikipedia.org/wiki/Chernobyl_disaster
         | 
         | However, those safety systems are obviously designed expressly
         | to prevent such a disaster. For example, control rod systems
         | are often designed to be fall (via gravity) into the reactor in
         | the event power fails. These failsafe systems are typically
         | very reliable, in the absence of other external events (such as
         | the flooding and earthquake that took place in Fukashima.)
        
           | thijson wrote:
           | The control rods don't stop decay heat from being produced.
           | That's what happened with Fukushima.
           | 
           | Also, nuclear poisons (neutron absorbers) build up after the
           | reactor is shut down. After the control rods are withdrawn it
           | takes a few days for the poisons to be burned up and the
           | reactor can resume power production. I think they call that
           | poisoning out the reactor.
           | 
           | https://en.wikipedia.org/wiki/Neutron_poison
        
             | thijson wrote:
             | When the Northeast power grid went down down in 2003, the
             | Bruce Nuclear Power Development was almost entirely kicked
             | off the grid. It was able to keep ticking over at a few
             | percent of power output though because of a feeder line
             | that went North. This prevented the reactors from poisoning
             | out, and allowed them to come back faster than if they had
             | poisoned out.
        
         | bell-cot wrote:
         | In general, any sort of "boil water to steam, use steam to
         | drive turbines" system can vent the hot steam from the boilers
         | to the atmosphere. There's a big reserve tank of cold boiler
         | feed water, to replace the water you're no longer getting back
         | from the steam condensers (attached to the "OUT" steam pipe on
         | the turbine). So the boilers will keep soaking up just as much
         | heat, while the engineers scramble to reduce the heat coming in
         | from the burning wood, or burning coal, or burning oil, or
         | fissioning atoms, or whatever.
        
         | quickthrowman wrote:
         | I would assume the cooling loop is still running, so the heat
         | from the reactor would go into the water of the cooling loop,
         | and then the heat would be rejected into the atmosphere when
         | the cooling loop water evaporates in the cooling towers, just
         | like it does when its generating power.
        
       | konschubert wrote:
       | I think the nodal pricing structure in the Texas grid is
       | extremely conductive to an efficient electricity market.
       | 
       | It incentivises the grid-stabilizing deployment of batteries.
       | 
       | Texas is really the market to watch and learn from.
        