       Is it okay to daisy chain a UPS?
        
       Author : nuker
       Score  : 108 points
       Date   : 2024-04-28 08:17 UTC (14 hours ago)
        
 (HTM) web link (www.eaton.com)
 (TXT) w3m dump (www.eaton.com)
        
       | delichon wrote:
       | I've never found a straight answer on whether it's ok to daisy
       | chain surge protectors. Anyone know? I've been trying to avoid it
       | based on a warning I don't understand, but it can be tough to
       | find power bars without surge protection.
        
         | 4gotunameagain wrote:
         | yes, as they are passive device unless in the case of a surge,
         | which would be shorted to ground by the first one in the row
         | (technically, the first one whose limits are lower than the
         | surge)
        
           | kosma wrote:
           | The nature of surges is not simple like that - a lightning
           | strike can easily blow MOVs and inrush limiting resistors in
           | multiple devices. I come from a rural area and coming to
           | someone's house with a bag of fresh MOVs and resistors is not
           | an uncommon thing after a big storm.
        
             | 4gotunameagain wrote:
             | I believe that it highly depends on the type of the surge
             | protector, their ratings and the cable network involved. I
             | do not think that it would cause issues in two surge
             | protectors from power outlets connected in series, and
             | depending on their rating and switching characteristics
             | maybe both could trigger, I agree.
        
             | numpad0 wrote:
             | I believe the question is if it's safe at all to do so
             | rather than whether the protection works or not, though I'd
             | have to be all ears about interactions between multiple
             | parallel surge arrestors.
        
         | kosma wrote:
         | It's not very different from daisy chaining normal extension
         | cords - safe if you know what you're doing (not exceeding the
         | current rating on any of them). Most surge protectors are
         | fused, making them safer to daisy-chain than normal extension
         | cords.
        
           | sgarland wrote:
           | As an aside, increasing the length of extension cords can
           | cause premature failure of some devices (mostly motorized
           | tools, especially cheaply-made ones) if the wire gauge is
           | inadequate, due to voltage drop.
           | 
           | As a general rule, I wouldn't run tools past 50 feet on
           | anything smaller than 12 AWG (and really, 14 AWG is the
           | smallest I'd go for any length; anything smaller isn't safe
           | for most loads).
        
           | quickthrowman wrote:
           | > It's not very different from daisy chaining normal
           | extension cords - safe if you know what you're doing
           | 
           | It's not safe, and it's expressly forbidden by the NEC, see
           | 11.1.5 below:
           | 
           |  _> 11.1.5 Extension Cords
           | 
           | > 11.1.5.1
           | 
           | > Extension cords shall be plugged directly into an approved
           | receptacle, power tap, or multiplug adapter and shall, except
           | for approved multiplug extension cords, serve only one
           | portable appliance._
           | 
           | Daisy chaining extension cords is unsafe and not recommended.
           | Only use extension cords that you've inspected and are
           | properly rated for the environment (don't use indoor cords
           | outside, don't use an outdoor extension cord outdoors unless
           | it's GFCI protected) and power usage of the device you are
           | powering.
           | 
           | Any time electricity has to flow through a splice or
           | mechanical connection, the possibility of a loose connection
           | causing an arc and subsequent fire exists.
           | 
           | It's unlikely to happen to you specifically, but it does
           | happen and avoiding electrical fires is a good thing if it
           | can be avoided.
           | 
           | Daisy chaining power strips is also forbidden by the NEC:
           | 
           | > 11.1.4.2
           | 
           | > The relocatable power taps shall be directly connected to a
           | _permanently installed receptacle._
        
             | dvdkon wrote:
             | Yes, there is a risk of failure involved with _anything_
             | electrical, but I don 't see why anyone would consider
             | chaining extension cords inherently dangerous enough to
             | ban. It increases the number of connections, but that's a
             | miniscule risk compared to the 5+ connections an extension
             | cord might have on its own. The only significant risk I
             | know is people disregarding the max amperage rating of
             | everything in that chain.
             | 
             | For anecdotal experience, I've had both extension cords and
             | wall plugs fail (nothing serious thankfully, but they did
             | get a bit melted), but in those cases it had nothing to do
             | with my extension cord chains, but rather an internal
             | connection failure.
        
               | fbdab103 wrote:
               | It is probably one of those little process changes to
               | minimize chance of catastrophic failure. Sure, the risk
               | of the daisy chained system going poof is low, but not
               | zero. Instead, you should try to re-work your plans so
               | you do not need to daisy chain.
        
               | marcosdumay wrote:
               | AFAIk, the rationale for extension chords is that they
               | are sized to cause a controlled amount of voltage drop
               | within their lenght. If you keep adding them, you will
               | increase the drop, and many devices will react by
               | increasing the current.
        
               | quickthrowman wrote:
               | This is correct. For a 120v 12FLA load at a distance of
               | 50', you're fine using a #14 cord. If you double that to
               | 100', you need to use #10 cord to account for the voltage
               | drop. As voltage drop increases, the amount of current
               | flowing through the cord increases, which can potentially
               | heat up the insulation beyond its rated temperature.
        
         | AstroJetson wrote:
         | You need to know what the cable size is of the power strip and
         | the current you are going to draw. If you have bar A with 14 ga
         | cable plugged into the wall, and bar C With 18 gauge plugged
         | into that, then with devices that don't exceed C current rating
         | (12 amps) and devices in A ( including the devices in C ) that
         | don't exceed A's rating, you will be fine. The other way wall -
         | C - A is the problem, C isn't able to manage the full load.
         | 
         | Only buy known surge suppressor, there have been tear downs
         | where the surge components were missing / fake.
         | 
         | Since surge comments are passive, chaining the surge components
         | is not a problem.
        
           | xprn wrote:
           | Today I learned. I always thought it was some "electricity
           | magic thing" like additional heat generated within the power
           | strips causing issues between the connected devices, but this
           | makes a lot more sense than whatever I was thinking of.
           | 
           | Although I do think I might have mixed some things up between
           | regular power strips and those outdoors/industrial ones with
           | a long (double/triple digit meter) rollable cable which my
           | dad was a big user of back when he used to work in
           | construction. Basically back when I was little he used to
           | tell me never to plug power tools into a rolled-up "power
           | wheel", and I think that when I was later heard you shouldn't
           | daisy chain power strips I must have made that (wrong)
           | connection.
        
             | vbezhenar wrote:
             | It's about heat. Cable has some resistance and emits heat.
             | This heat has to dissipate somewhere. If cable is rolled
             | out, it'll dissipate heat to the air. If "power wheel" is
             | not rolled out, cable will heat cables around. Outer cables
             | will dissipate heat to the air, but inner cables will not.
             | So with enough current and enough time, this thing will
             | melt.
             | 
             | You probably won't have issues charging iPhone from this
             | thing or powering something for few seconds, so no need to
             | go crazy about it, just something to keep in mind.
        
             | willis936 wrote:
             | Surge protectors do have one magical electrical thingy in
             | them: metal oxide varistors (MOVs). They're what shunt
             | current in an overvoltage transient and they do age with
             | usage.
        
               | aceazzameen wrote:
               | I've always known surge protectors age and eventually
               | stop protecting from surges. But what I always wanted to
               | know is how can you tell when it expires? I'm assumings
               | it's based on how good/bad/stable the electricity is in
               | your area. But still, is there any way to know when it's
               | time to replace?
        
               | malfist wrote:
               | Typically surge protectors have a little light to let you
               | know if the surge circuitry is still good. Others will
               | fail safe, meaning the won't power on if the circuitry is
               | bad. Cheap ones may do neither.
               | 
               | Either way, if your house has had a surge and other
               | equipment has died that wasn't surge protected, probably
               | a good time to replace all surge protectors in the house,
               | they're not really meant to survive multiple large
               | surges. They shunt the power destructively, just
               | somewhere you don't care.
        
               | neilv wrote:
               | > _they 're not really meant to survive multiple large
               | surges. They shunt the power destructively, just
               | somewhere you don't care._
               | 
               | Is this a concern when buying _used_ rackmount power
               | conditioners (like used for live music setups?), to
               | protect home IT gear? Can they be worn out without a sign
               | that they are?
        
               | cesarb wrote:
               | What I've read is that their main failure mode is that,
               | as they age, their trigger voltage gets lower and lower,
               | and at some point the normal line voltage is enough to
               | trigger them all the time. And when they overheat, either
               | due to being triggered all the time or due to diverting a
               | large surge, they fail open and no longer have any
               | protective effect on the circuit. High quality surge
               | suppressors would have fuses physically touching the
               | MOVs, so that when a MOV overheats and fails, the fuse
               | opens and cuts power to the now unprotected output.
        
         | willis936 wrote:
         | You are not supposed to. The upstream device is sized for a
         | maximum current and daisy chaining can lead to a scenario where
         | downstream devices are sized for larger current than upstream
         | devices, which is avoided everywhere else in electrical
         | distribution.
         | 
         | So it's fine as long as you control the strip and keep track of
         | loads (e.g. you know your spouse will never plug a vacuum into
         | that handy receptacle you have there), but at work your EHS
         | team will mark you down for it.
        
           | vasco wrote:
           | In your example there's a first undersized UPS A, then
           | another UPS B, then whatever combination of electrical
           | devices which power usage exceeds UPS A. You say this is
           | problem.
           | 
           | If you have said combination of electrical devices, and if
           | you're assuming we're using an undersized UPS A + the combo
           | of devices, why does the UPS B matter?
           | 
           | If you're going to overload the UPS A you're going to
           | overload the UPS A regardless of UPS B, no? Daisy chaining or
           | not, that doesn't seem like the actual problem to a knee-jerk
           | thinking.
        
           | 4gotunameagain wrote:
           | This is not specific to surge protection, but extension cords
           | in general.
        
           | xtqv wrote:
           | Daisy chaining is irrelevant to the problem that you can buy
           | 18ga "lighting-only" extensions that bear a 15A rated NEMA
           | 15R but are limited to 8A.
           | 
           | Daisy chaining a power bar with it's own circuit breaker can
           | be ideal if it prevents someone from making the mistake of
           | using a circuit in a way that trips a panel breaker, ie
           | preventing your spouse from plugging a vacuum into a circuit
           | shared by several rooms.
        
           | ta1243 wrote:
           | In the UK, if I have a 6 way strip sized for 10A, which thus
           | has a 10A plug in, I could then plug in a 4 way strip
           | downstream with a 5A fuse, then a lamp with a 3A fuse, and
           | that's fine. I could even connect it the other way.
           | 
           | If I plug in a heater pulling 10A then sure, the 5A fuse will
           | blow.
           | 
           | Daisy chaining multiways will increase the resistance in the
           | earth wire which could mean you end up with a class 1 device
           | with a fault connecting live to earth which would only
           | punting say 8A to earth due to a high resistance (but then
           | your circuit's RCD would trip with that), but is it a major
           | problem?
           | 
           | With the US system, do you not have wires capable of 3A (say
           | 24 AWG) which you can connect to a normal socket which also
           | takes a 10A vacuum?
           | 
           | If that lamp has a fault where it pulls 6A, what protects the
           | 3A wire -- i.e. there's a fault with your lamp which is
           | plugged into a 15A circuit breaker, and the lamp draws 10A,
           | it wouldn't trip the breaker, and that nice thin 3A lamp cord
           | would melt.
        
             | t0mas88 wrote:
             | That lamp example happens nearly everywhere except the UK,
             | due to the UK having fuses in plugs. We don't have that in
             | the rest of Europe for example.
        
         | vbezhenar wrote:
         | As long as you keep load below threshold, I don't see any
         | potential issues.
        
         | quickthrowman wrote:
         | It's not OK, it's a violation of the NEC:
         | 
         | > 11.1.4.2
         | 
         | > The relocatable power taps shall be directly connected to a
         | _permanently installed receptacle._
         | 
         | A surge protector is a 'relocatable power tap' and _must_ be
         | plugged into a permanent receptacle.
        
         | immibis wrote:
         | "surge protector" is what Americans call a passive device that
         | splits one outlet into several, yeah?
         | 
         | The danger is overloading. Back in the days when the main
         | things you plugged in were incandescent lights and space
         | heaters, this was probably a big issue. With computer equipment
         | and LED lights you have to have a lot more stuff - many
         | outlets' worth - to reach the circuit's maximum capacity.
         | 
         | If the circuit and "surge protectors" are rated for 1800W (15
         | amps x 120V), officially you should limit yourself to 80% of
         | that for continuous loads which is 1440W, so you can supply 14
         | laptops or small small desktops that use 100W each, or over 200
         | raspberry pis on USB chargers that use 5W each, and either way
         | you're going to need a lot of outlets before you come anywhere
         | close to that limit.
         | 
         | At least that's a rough estimate. Power factor could decrease
         | that number by up to 50% and you can use the full rating for
         | intermittent loads; I'm not certified to know the fine print.
         | Point is that 10 computers can easily use less power than a
         | single space heater.
        
           | jcalvinowens wrote:
           | > or over 200 raspberry pis on USB chargers that use 5W each
           | 
           | Those little switcher bricks are horribly inefficient: the
           | 15W one I just pulled out of a drawer draws 0.8A on the
           | primary. Realistically you're going to max out a 15A circuit
           | around 20-30 of those, not 96 (1440/15).
        
           | wnoise wrote:
           | > "surge protector" is what Americans call a passive device
           | that splits one outlet into several, yeah?
           | 
           | Technically different, but often combined functions. The
           | splitting bit is a "power strip", or sometimes a "power bar".
           | The surge protection is switching off when there's a short or
           | overvoltage in the supply, or other larger than expected
           | power draw.
        
           | callalex wrote:
           | >surge protector" is what Americans call a passive device
           | that splits one outlet into several, yeah?
           | 
           | Not necessarily. There are "power strips" which turn one
           | receptacle into several. Then there are sure protectors which
           | are typically built into power strips. So not all power
           | strips are surge protectors but almost all surge protectors
           | are also power strips.
        
             | cesarb wrote:
             | > So not all power strips are surge protectors but almost
             | all surge protectors are also power strips.
             | 
             | There are panel-mounted surge suppressors (which can
             | protect all circuits coming from the panel), and also
             | inline surge suppressors with a single output like this
             | one: https://www.lojaclamper.com.br/dps-iclamper-
             | pocket-2pinos-10...
        
         | GuB-42 wrote:
         | I don't see the problem, provided that you are within the
         | current draw limits.
         | 
         | Surge protectors are usually made of components that cause a
         | short when a surge happens, protecting the equipment
         | downstream. It usually pairs with some kind of overcurrent
         | protection (breaker, fuse, sometimes GFCI) to protect against
         | the short the surge protector itself caused.
         | 
         | Having chained surge protectors it actually quite common. You
         | may have a surge protector in your breaker panel, then in your
         | powerstrip, then in the power supply of the device you have
         | plugged in. Most good quality ATX power supplies have built-in
         | surge protection for instance. They also all tend to have
         | overcurrent protection too. The breaker panel has breakers
         | (duh), the power strip may have a simple breaker too, and the
         | device may have a fuse. In the UK, the plug itself may have a
         | fuse, plus the breaker from the utility company.
         | 
         | The risk from chaining surge protectors is that it increases
         | the risk of false triggers if one of them is defective. But it
         | may also provide better protection. All in all, I wouldn't
         | worry too much about it. Just don't overload that power bar and
         | whatever it is plugged in.
        
           | WarOnPrivacy wrote:
           | > it may also provide better protection.
           | 
           | This has been my experience. There was a corridor between 2
           | FL counties known for heavy lightning strikes. I serviced
           | small sites that had their IT equip fried (exploded, melted)
           | once or twice a year.
           | 
           | Putting it behind 4-6 decent, consumer-grade surge protectors
           | turned out to be really effective. I was a bit surprised
           | given how lightning can jump over protection during a strike.
           | 
           | To illustrate the area: An XO's home was hit. Char marks
           | lined the walls wherever wiring ran. Pipes burst all over.
           | Nothing plugged in or wired survived. The front door was blow
           | into the street.
           | 
           | His grade school kids were home at the time; they were
           | physically fine.
        
             | LorenPechtel wrote:
             | There's also the fact that consumer surge protectors are
             | incapable of determining if they're any good or not.
             | There's a small component in there that eats the surge--a
             | severe surge and it's destroyed, it's obvious. However,
             | there's a range in which it no longer functions but is not
             | destroyed. The next surge goes on down the wire.
             | 
             | I really wish someone would come up with some surge
             | suppressors that have a string of field-replaceable
             | suppressors. Periodic maintenance, replace the suppressors.
        
         | orblivion wrote:
         | This is funny, I actually am wondering about plugging a surge
         | protector into a UPS. I have some equipment (probably not very
         | high power draw but I can confirm) conveniently zip tied to a
         | peg board along with a power strip that I assume has a basic
         | surge protector on it. One power cord leaves the whole thing,
         | which is very clean, but power goes out a surprising amount
         | here. Can I plug this whole thing into a UPS or should I find a
         | replacement strip without a surge protector?
        
           | Eisenstein wrote:
           | You can plug it in. The problems with the UPS being plugged
           | into another UPS are related to the internal batteries and
           | the inverters, not to the surge protection. Just don't plug
           | in too many things and overload the UPS.
        
           | radicality wrote:
           | From what I remember reading, you should not do that. Only
           | plug in PDUs or directly connect equipment to a UPS. You're
           | meant to put the surge protection before the UPS. I think
           | it's because the circuitry in surge protectors can mess with
           | what the UPS thinks the actual load is.
           | 
           | I believe some UPS brands might also void parts of your
           | warranty if you use them with a surge protector plugged in.
           | 
           | https://www.apc.com/us/en/faqs/FA158852/
        
         | rinron wrote:
         | probably because it Depends, If you dont know its safer not to.
         | long answer (keep in mind i live in canada, im not a
         | professional, this is just what i learned and trust, keep in
         | mind above) - As long as no wire/bar exceeds its max Amp your
         | safe no matter how many things are plugged in or how long of a
         | daisy chain, the max amp is usually listed. - all devices
         | should list the max amp they use, add up the amp's of all the
         | devices connected to that wire and if its below your safe. - if
         | your breaker is 15 amp, virtually all normal extensions/power
         | bars are rated for at least 15 amps which means doesnt matter
         | what you do the breaker should* flip before any damage is done
         | - if breaker is above 15 amp most surge protectors have
         | protection that will trigger if they exceed their max, most
         | basic "splitters" and extension cords dont, eg if they dont
         | have a switch or reset button they are pretty much guaranteed
         | to not have this protection, be extra carful how much you load
         | on those. some good rules of thumb to keep in mind, look for
         | imprints or labels that list amps, smaller wires can handle
         | less, damaged wires can handle less then they did before and
         | shouldn't be used, if a wire or connector warms when its in use
         | its overloaded reduce the load on it, especially if it warms
         | quickly. here is a video that i liked that talks about it as
         | well https://www.youtube.com/watch?v=K_q-xnYRugQ
        
         | dreamcompiler wrote:
         | The reason it's a "bad idea" is that most surge protectors are
         | power strips and you must be cautious when you daisy chain
         | power strips. Likewise extension cords.
         | 
         | Why? Two reasons: You have to ensure the wire gauge on every
         | link can handle the current, and at every junction (plug) the
         | resistance is higher than in the wire itself. When electrical
         | fires start they usually start at these plug junctions because
         | they overheat.
         | 
         | The surge protectors themselves don't mind being daisy chained.
        
       | madaxe_again wrote:
       | I mean, it _is_ ok, as long as everything is appropriately sized
       | - I live entirely off grid, with several battery banks and
       | inverters, which are essentially giant UPSs - and have regular
       | UPSs for various equipment so that when I shut the power down for
       | whatever reason the network and servers stay up.
        
         | lambdaone wrote:
         | There are a vast number of problems that all can be summarized
         | as "this is a really stupid thing to do, unless you really know
         | what you are doing". This is one of them.
        
         | dgacmu wrote:
         | Not really. In your case, you probably have a very high quality
         | pure sine wave inverter that's much larger than the individual
         | UPSes, which will make the downstream UPSes mostly happy as
         | long as you don't approach max load.
         | 
         | Many cheap inverters are not pure sine, and a UPS seeing this
         | waveform may decide it needs to go to battery also.
         | 
         | Practically, a UPS also adds to the current draw, and many
         | people may accidentally exceed the circuit limit because they
         | only look at the useful load but not also the UPS charging load
         | after a power failure ends.
        
         | K0balt wrote:
         | Same here, I run a lot of different equipment on grden variety
         | UPS's on our solar grid - but that is fed by redundant 18KW
         | three-phase inverters and 72KWH of batteries... so that
         | probably looks a lot like utility power from the perspective of
         | the UPS's.
         | 
         | Overall, the discussion tangentially reminds me of a common
         | theme in aviation - twin vs single engine aircraft. With two
         | engines, the chance of having an engine failure at a critical
         | time is doubled.
        
           | immibis wrote:
           | But you also have a good chance to get through the failure
           | with one working engine. A two engine plane with one working
           | engine climbs slowly, and a one engine plane with zero
           | working engines doesn't climb at all.
        
         | geor9e wrote:
         | This article is about daisy chaining UPSs into each other's AC
         | outputs. I hope you're not doing that off grid. Daisy chained
         | UPS means the energy takes the path of DC battery > AC inverter
         | > DC rectifier > different DC battery > AC inverter > DC
         | rectifier to whatever device you're powering. You could be
         | losing up to 20% of the energy (server uptime) at each step of
         | the daisy chain. And since there's only one path for power to
         | take, if anything fails, it all goes down. The article's
         | solution is super simple, just use them in parallel instead.
        
           | madaxe_again wrote:
           | UPSs typically operate in passthrough mode unless a deviation
           | in supply occurs - so no efficiency loss day to day - and no,
           | I don't chain UPSs, but as I said, the house batteries are
           | essentially big damn UPSs.
           | 
           | Also, not particularly caring about efficiency currently as
           | we always have more energy than we can use, and I'm currently
           | looking at filling a shipping container with sand as a dump.
        
             | geor9e wrote:
             | >UPSs typically operate in passthrough mode
             | 
             | Oh, that makes a lot of sense. In that case, daisy chaining
             | two sounds like no big deal.
             | 
             | >filling a shipping container with sand as a dump
             | 
             | That's pretty cool. I didn't know private folks were doing
             | that.
        
       | chx wrote:
       | Note the last image of the article is not correct, if you want
       | full redundancy you need two independent power feeds. How
       | independent depends on your needs of course. You might just want
       | to run it from a different circuit but the same utility power. If
       | you've got insane needs and megabucks you can talk to the utility
       | about being fed from two substations or at the extreme end you
       | can get one feed from the utility and you can make your own
       | second feed. Traditionally we did this with water turbine working
       | from a river but today I might look into solar and perhaps molten
       | salt.
       | 
       | As an example, way back then when this was a very lucrative
       | business, we placed the servers for a premium number erotic call
       | in an industrial park on the border of two districts in Budapest
       | because that's where we could get two independent power feeds
       | without running our own lines. Internet connection wise, one was
       | a simple leased line the other was a microwave connection to very
       | far away. Short of bombing the entire site it was fair impossible
       | for the installation to go offline and -- for the six years I
       | knew about it, it never did. Note the site served German callers,
       | that's where the big bucks came from.
        
         | mcfedr wrote:
         | Presumably that's what they are showing with two wires with
         | different shape connectors
        
           | adrianmonk wrote:
           | And/or the box labeled "Utility Power" is not intended to
           | convey any specific notion of single circuits or multiple
           | circuits nor of single substations or multiple substations.
           | It just depicts power that in some way comes from a utility
           | and no more.
           | 
           | In that sense, it is not incorrect about the configuration of
           | utility power because it doesn't say anything about that
           | subject.
        
         | willis936 wrote:
         | I'm working on a facility with redundant power and my
         | impression is that it's not insanely expensive if you have
         | expensive machinery to protect and that diesel generators are
         | far and away the most common and inexpensive second feed.
        
           | michaelt wrote:
           | Diesel generators are great if you need a few hours of backup
           | (assuming the generator actually starts when you call on it).
           | 
           | But if you need enough backup capacity to survive something a
           | multi-state, multi-day blackout [1] that probably gets
           | expensive.
           | 
           | You wouldn't need that for a premium erotic call processor,
           | but a 911 call exchange might, for the portion of their
           | workload they can't pass off to another exchange.
           | 
           | [1] https://en.wikipedia.org/wiki/Northeast_blackout_of_2003
        
             | segmondy wrote:
             | Natural gas generators.
        
             | j45 wrote:
             | Looking at multi fuel generators is worth it too depending
             | on your setup.
             | 
             | For example some can run gas/propane/natural gas
        
             | willis936 wrote:
             | You can store about a day's worth of diesel on-site and
             | have agreements in place to have daily refills in cases of
             | emergencies.
             | 
             | If you can't get gasoline within a day's drive then there's
             | bigger problems in the world.
        
               | progbits wrote:
               | In many places going over what you can store might put
               | you over emission quotas and you would have to shut down
               | anyway. I'm familiar with one incident at large DC which
               | had fuel left and could easily get more, but only had few
               | hours before they were required to shut down by EPA.
        
             | s0rce wrote:
             | I worked at a site where we powered a bunch of stuff
             | consistently from diesel generators until the grid hookup
             | was finished, much longer than a few days. Probably was
             | expensive.
        
           | xen2xen1 wrote:
           | Worked at a place with a natural gas genny as the second
           | source. You don't have to feed it, it just keeps working.
        
             | ocdtrekkie wrote:
             | Technically you are just feeding it power from a different
             | utility company than the electric company.
        
               | hedora wrote:
               | I wonder if natural gas is actually redundant at this
               | point. Around here, phone company decided to take a
               | dependency on the power grid, so phone + internet go down
               | if the power is down.
               | 
               | It wouldn't surprise me at all if some utilities have
               | started installing smart meter upgrades or inline
               | compressors or computer-controlled valves that don't have
               | generators attached to them.
        
               | wongarsu wrote:
               | > phone company decided to take a dependency on the power
               | grid, so phone + internet go down if the power is down
               | 
               | I hope it goes down a couple hours later?
               | 
               | Around here (Germany) your phone and internet is also
               | dependent on a junction box with routers somewhere within
               | half a mile or so of your home having power. But they
               | have four hours of battery backup, and on normal-sized
               | outages they send people out with diesel generators when
               | the batteries start running low (prioritizing business
               | customers). Having it go down from power loss is a
               | decision made in triage, not something that just happens
        
               | tharkun__ wrote:
               | How common are power outages? Historically and in the
               | coming years given nuclear power I hear is dead in
               | Germany and France's reactors are old or need to shut
               | down because of rivers being too hot in summer. Is the 4
               | hours a 1980s decision that needs revising?
               | 
               | Asking, coz Canada here. Power outages aren't uncommon
               | (when I say that I mean: expect at least one that makes
               | you get out the generator in 'shoulder season' per year),
               | coz power lines (not talking transmission lines) are
               | mostly above ground, except in large cities of course.
               | But as soon as you get out of the "center" (which
               | depending on city is larger or smaller too) it's good old
               | wooden poles that carry power on the top and cable /
               | phone on the lower level.
               | 
               | Bucket transformer[1] on a pole near you blows up is a
               | favourite but the lines are actually fine, including your
               | cable / DSL. Last time we also lost internet it took
               | about 24 hours after power went out that internet went
               | down as well. Cell phone service from the same company
               | was still fine. The entire metro area was out of power
               | for days and I guess they prioritized topping up the
               | diesel/LP for those.
               | 
               | [1] These guys
               | https://en.wikipedia.org/wiki/Distribution_transformer
        
               | 20after4 wrote:
               | In small town USA, my cable internet goes offline
               | immediately even if the power outage is just a 1 second
               | flicker. Then takes some equipment to reboot at the cable
               | office before it comes back online. Very annoying. Phone
               | companies typically have a good battery backup though.
        
               | wongarsu wrote:
               | Large-scale power outages are exceedingly uncommon in
               | Germany, or really all of Europe. The last big one was in
               | 2006 because of some mistakes when taking down a major
               | transmission line [1]. I don't remember reactors being
               | offline ever causing a power outage. When France has to
               | shut down its nuclear reactors Germany just fires up more
               | coal plants, that's the beauty of a large interconnected
               | grid.
               | 
               | What does happen are smaller scale outages. Power lines
               | are mostly buried along streets and under the sidewalk,
               | just like telephone lines. That doesn't stop the
               | occasional excavator digging too deep and taking a street
               | off the grid. At an individual level it's extremely
               | uncommon, maybe once a decade. But deploy thousands of
               | boxes with networking equipment all around the country
               | and it happens to your equipment all the time.
               | 
               | 1: https://en.wikipedia.org/wiki/2006_European_blackout
        
               | tharkun__ wrote:
               | Yeah historically that makes a lot of sense to me.
               | Reactors going offline directly would usually be planned
               | and thus not cause instability.
               | 
               | The 2006 one I had read about before. I love reading
               | timelines of such disasters. Shows how hard this actually
               | is and how much work it is to keep it all running.
               | 
               | Here's another one: https://en.wikipedia.org/wiki/Northea
               | st_blackout_of_2003#Tim... And speaking of Canada and
               | power lines (this time it does include transmission
               | lines) https://en.wikipedia.org/wiki/January_1998_North_A
               | merican_ic... While not so severe this is basically the
               | kind of thing I was referring to us happening in
               | "shoulder season". There's usually at least one ice storm
               | or very wet snow event at the start and/or end of winter
               | now and it's very likely that in our wooded area we get
               | trees into power lines and boom the buckets go. When
               | we're lucky it's localized and crews are available to
               | come out and fix it in a few hours. If it's all over the
               | place then it's gonna take a while and they'll have crews
               | from other provinces and the US come in to help as well.
               | 
               | I'd be interested in your outlook on the future of the
               | grid in Germany and Europe though. Of course when France
               | takes a nuke offline, that's usually planned, even when
               | done for a "river water temperature emergency" it's gonna
               | take a while and you can bring that coal plant online
               | like you mention. But doesn't Germany want to reach the
               | climate goals it set itself? How does coal make sense
               | there? And how is shutting down their own nukes a thing
               | when it's OK to use French nuke power?
               | 
               | Or some natural gas, which is quicker. If you have the
               | gas. Re: Russia.
               | 
               | In all of the European (NATO) countries together, is
               | there enough generation capacity if you assume zero
               | Russian inputs (save for say untraceable third party
               | transit or resources) and half of France's nukes going
               | offline? Especially when the sun doesn't shine because
               | bad weather and thus the winds are so high that you have
               | to shut down your wind turbines?
        
               | bobthepanda wrote:
               | At least during the Texas grid failures during their
               | freeze the other year, gas ended up not being a backup
               | because the lines froze over.
               | 
               | Something is only really a backup if the actual fuel is
               | on site, at this point
        
         | znpy wrote:
         | > for the six years I knew about it, it never did.
         | 
         | my dude i cannot tell you how much i love these stories of non-
         | faang, real world engineering for extreme reliability.
         | 
         | thank you for posting that.
        
           | chx wrote:
           | my fav real world engineering story is of the first
           | commercial ISP in Hungary
           | 
           | back then running leased lines would've been _way_ too
           | expensive. So what did the kids running the show did? They
           | got wind of a central office in an older part of Budapest
           | have excess capacity so they rented an apartment in the next
           | building and _drilled the wall_ :D no expensive trenching, no
           | expensive equipment to demultiplex landlines, nothing, just a
           | bunch of wires running straight from the CO equipment into
           | retail modems... We had no idea what we were doing, mind you.
           | I was already doing Linux at the time so among the few
           | installers I was the lucky guy who got to install the
           | Internet at a small business who wanted it to be done on a
           | Solaris workstation. That was a fun challenge... Other
           | installs were Trumpet Winsock. The ISP itself ran a custom
           | linux app, you dialed in and landed on a text app or maybe it
           | was Lynx? can 't quite remember, it's been 30 years...
        
         | linsomniac wrote:
         | >run it from a different circuit but the same utility power.
         | 
         | If you're going to come from a different circuit, see if you
         | can at least pull it from a different phase, if we're talking a
         | 120v circuit on 240v service (typical US home service). It's a
         | small improvement, but I'd say 10%+ of the power outages I've
         | seen have been just a single phase going out.
        
           | DrPhish wrote:
           | I have also seen a single phase go out (bird poop into a
           | transformer) and having redundant PSUs on different phases
           | saved our bacon
        
             | dylan604 wrote:
             | The house I grew up in lost transformers multiple times a
             | year from squirrels.
        
           | hunter2_ wrote:
           | The center tapped transformer that provides residential split
           | phase 120/240 on its secondary winding connects to just 1 of
           | the 3 grid phases on its primary winding. If that one phase
           | goes out on the grid, both sides of the split phase service
           | go out together. There would need to be a fault on just one
           | side of the split, downstream of that transformer, for your
           | suggestion to hold up. Certainly not impossible, but far less
           | common than a "losing one phase" scenario which would
           | typically originate upstream on the high voltage side.
           | 
           | On a commercial 3 phase service, yes, connect redundant PSUs
           | to separate phases, since each phase on the panel actually
           | corresponds to each phase of the grid.
        
             | kurthr wrote:
             | But if the issue is a local breaker flip, then being on a
             | different phase is very effective!
             | 
             | I don't have a power outage more than once a year, but we
             | manage to blow a breaker more than a few times a decade
             | (vacuum + water boiler was one).
        
               | anamexis wrote:
               | If the issue is a breaker flip, then you only need to be
               | on different breakers, right? Phase is irrelevant in that
               | case
        
               | hunter2_ wrote:
               | Right, because the main breaker would be 2 pole (or at
               | the very least handle tied).
        
             | cesarb wrote:
             | > The center tapped transformer that provides residential
             | split phase 120/240 on its secondary winding connects to
             | just 1 of the 3 grid phases on its primary winding.
             | 
             | I believe that's a USA peculiarity. Where I live, the usual
             | residential and commercial wiring is from 13.8 kV to
             | 127V/220V through a three-phase delta-wye transformer, in
             | which the primary connects between each pair of phases, and
             | the secondary connects between one phase and the neutral
             | (the high-voltage primary side does not have a neutral).
             | When one phase of the high voltage side is lost (very
             | common, since each high-voltage phase is a separate wire
             | and has an independent fuse upstream of the transformer),
             | what happens is that one phase of the low voltage side
             | stays normal (the one between the two intact high voltage
             | phases), and the other two have a lower voltage which
             | varies depending on their relative load.
        
               | kelnos wrote:
               | > _I believe that 's a USA peculiarity._
               | 
               | Yep. Sounds like you have true 3-phase service, whereas
               | most places in the US just get split-phase.
        
             | Maskawanian wrote:
             | You can definitely loose one phase of a split phase
             | transformer. I've seen it 3 times in my life. Sometimes it
             | is completely out, other times I've seen only getting 80v
             | rather than the full 120.
             | 
             | All depends on how it failed.
        
         | j45 wrote:
         | I read the graphic differently and it reads ok to me.
         | 
         | The two different power sources are different shapes.
         | 
         | To someone who's setup things in datacentres, it seems pretty
         | reasonable to see that could be 2 different circuits.
         | 
         | Of course it should be 2 separate plugs with the 2 different
         | shapes in them.
         | 
         | As for batteries you can just get a UPS system that supports
         | adding extra batteries to it.
        
       | nuker wrote:
       | The main point against seems to be that downstream UPS will not
       | like "simulated or modified sine wave" if upstream UPS is not
       | producing "Pure sine wave". To be tested :)
        
         | dgacmu wrote:
         | I've tested it before. TFA is correct, at least with the APC
         | UPS I tried it with once. The apc ups went to battery and then
         | turned off when out of battery.
        
           | nuker wrote:
           | Thanks! But why they don't like it? UPS, as a black box,
           | should harvest whatever energy is in the source, regardless
           | is it sine wave or freaking square mess. Even DC or RF is
           | present :) Why so picky?
        
             | boricj wrote:
             | That's true to an extent for online UPSes, which converts
             | from AC to DC and then from DC to AC, completely isolating
             | the input current from the output, but these are the most
             | expensive types of UPSes.
             | 
             | Your run-of-the-mill UPS is likely to either be offline,
             | which forwards the input to the output, or line-
             | interactive, which can compensate to an extent under or
             | over voltage conditions with a regulator. If the input
             | current characteristics are outside allowable tolerances,
             | they can't compensate and must switch the load to battery
             | to continue powering it.
        
               | nuker wrote:
               | > If the input current characteristics are outside
               | allowable tolerances
               | 
               | This is the key to this whole discussion. I guess it
               | boils down to existing line-interactive designs, why they
               | can't work with simulated sine as a source.
        
               | dgacmu wrote:
               | A transfer-switch based UPS still needs to protect
               | against brownouts, so it too has line behavior parameters
               | outside of which it will switch to battery. It's an
               | interesting question if/why a modified sine wave input
               | would trigger that or not. Probably one of those "it
               | depends on the design" things. (modified sine ->
               | approximately an oscillating square wave.)
               | 
               | A dual-conversion (online) UPS is almost certainly more
               | robust as far as what kinds of inputs it can accept
               | (though as GP noted, they're more expensive, and they're
               | also less efficient due to the additional
               | rectification->inverter).
        
               | nuker wrote:
               | > Your run-of-the-mill UPS is likely to either be
               | offline, which forwards the input to the output,
               | 
               | This one surely should "like" simulated sine wave as a
               | source and don't drop to battery?
        
               | boricj wrote:
               | An offline UPS will switch to battery if it doesn't like
               | the input. What qualifies as acceptable input depends on
               | the design and specifications of the UPS. If it expects a
               | real grid-like sine wave and doesn't see one it will
               | reject it, regardless if the load would like it or not.
        
               | nuker wrote:
               | > If it expects a real grid-like sine wave and doesn't
               | see one it will reject it, regardless if the load would
               | like it or not.
               | 
               | But why would it require grid-like sine wave and not go
               | along with whatever is the source, provided source can
               | still be used to charge its batteries? I saw no answers
               | yet, and this "why" is the very key to the discussion.
        
               | soneil wrote:
               | There's a lot of compromise in UPS design.
               | 
               | For example, a common topology in offline UPS is that the
               | inverter and the charger are the same circuit driven
               | differently[0] - so you can't charge the battery while
               | the inverter is carrying load. This is popular at the
               | low-end because you have literally half as much UPS, but
               | makes what you're describing impossible.
               | 
               | Another common issue at the low end is that the inverter
               | isn't thermally sized to run non-stop, they know they can
               | cut a corner because your battery presents a finite and
               | known duty cycle.
               | 
               | There are ways around this, but at some point you end up
               | fixing the wrong problem - eg, it's cheaper, safer, and
               | more resilient to buy a transfer switch instead of
               | uprating two UPS to be capable of daisy-chaining.
               | 
               | [0] https://patents.google.com/patent/US5302858A/en
        
               | numpad0 wrote:
               | I think you're being gatekept. It's inconceivable that
               | just no one knows why square and triangular waves don't
               | pass as AC.
        
               | nuker wrote:
               | In other words. I asked if A should lead to B. You
               | answered "A leads to Not B" :)
        
         | boricj wrote:
         | Another important point is that an UPS can produce huge surge
         | currents, for example when switching from battery to utility.
         | The upstream load goes from zero to the sum of both the
         | protected load _and_ the UPS charging its battery.
         | 
         | When daisy-chaining an UPS to another, the downstream UPS can
         | easily overload and trip the upstream UPS because of that.
        
           | lucumo wrote:
           | Wow. Your post is much more informative and clearer than the
           | article. And it's only three sentences.
        
             | nuker wrote:
             | > Another important point is that an UPS can produce huge
             | surge currents, for example when switching from battery to
             | utility.
             | 
             | It has not happened yet. If downstream UPS likes the
             | source, it is not going to switch to battery, and battery
             | charging will Not be happening because downstream UPS had
             | it charged already long time ago.
        
           | effluvium wrote:
           | An easy fix for that would be to put a surge protector
           | between the UPSs. (Joke)
           | 
           | ------------
           | 
           | I bought three UPSs, all them used independently; but I had
           | to stop using all of them. They all had a capacitor whine
           | that was driving me crazy.
        
       | myself248 wrote:
       | Another thing they don't mention is that when utility AC returns,
       | each UPS in the chain tries to recharge, which can be a
       | significant chunk of power. Any given UPS is sized so that its
       | downstream load plus its own recharging power doesn't overdraw
       | the circuit, but add two recharging powers and it's much more
       | likely.
       | 
       | I don't think this is an issue with double-conversion UPSs, since
       | their input power is fixed by their rectifier size and they'll
       | simply charge more slowly instead, but with standby type, it's
       | very much a concern.
        
       | lucumo wrote:
       | What a stupid article. It doesn't tell you anything beyond "no,
       | buy our products instead". WHY is it bad? HOW does it fail?
       | 
       | I mean, it's possible that I don't know enough about UPSes to
       | understand the finer details and all this would be obvious to
       | someone who does. But presumably they already know why it's a bad
       | idea, and don't need this particular article to explain them.
       | 
       | The amount of scare words and the lack of detail honestly make me
       | believe it probably IS okay to do, and Eaton just wants to scam
       | some extra money out of people. It's just the posts in this
       | thread that make me take it slightly more seriously.
        
         | tssge wrote:
         | >Eaton just wants to scam some extra money out of people
         | 
         | Seems quite improbable that would be the purpose of the
         | article. The article is basically saying "buy a single UPS
         | instead of buying two to daisy chain them expecting to get
         | better results". If anything, such advice would lead to people
         | buying less devices.
         | 
         | Of course if one had two UPSes laying around for nothing, then
         | I guess daisy chaining might come to mind to get better
         | capacity or something for no extra price. However, generally
         | people don't randomly have UPSs laying around for no reason, so
         | it would make sense to buy higher capacity UPS than two lower
         | capacity UPSs to daisy chain them anyways (and for probably
         | quite similar total cost of ownership).
        
           | nixpulvis wrote:
           | Let's say I do have two UPSs lying around though, and a
           | soldering iron.
        
         | pixl97 wrote:
         | >make me believe it probably IS okay to do
         | 
         | Yea, as someone that ran their own micro ISP for a while, and
         | worked for larger ISPs, no it's not ok to do at all. APC brand
         | was the absolute worst about immediately tripping when plugged
         | into another UPS. Eaton online UPS' actually handled it ok in
         | comparison, but they are typically pretty expensive units.
         | 
         | This is definitely a case of the vendor attempting to save you
         | money. Get an ATS on anything that doesn't accept dual power.
        
           | tssge wrote:
           | >APC brand was the absolute worst about immediately tripping
           | when plugged into another UPS.
           | 
           | At least from my experience of owning multiple APC UPS
           | devices, they have a customizable acceptable power quality
           | setting. In such cases setting them to accept the absolute
           | worst quality of power could probably stop them from tripping
           | on bad power input.
           | 
           | No idea if this affects the end devices, however there's
           | probably a reason other than simply extra profit for the
           | default power quality tolerance setting on those devices.
           | Generally they are set to rather low tolerance threshold as
           | the expected usage scenario is servers and other relatively
           | sensitive equipment.
           | 
           | The models I own aren't really the most expensive either,
           | some of the lower end tower models and they still have
           | configurable acceptable power input settings available.
           | Regarding them tripping on bad input and being "absolute
           | worst", I consider this tripping a feature more than an anti-
           | feature, especially as it is user configurable.
           | 
           | EDIT: Also wanted to add that it is actually _preferable_ for
           | UPS to trip as immediately as possible on bad power input.
           | That is the only purpose of such product after all: to
           | protect the devices attached to it from bad or otherwise
           | inadequate power input.
        
       | Waterluvian wrote:
       | I'm guessing the sine waves wouldn't line up?
       | 
       | Edit: derp. Wouldn't matter. I was thinking putting them in
       | parallel.
        
       | CapitalistCartr wrote:
       | The places I've worked on used multiple generators, more than was
       | required to keep running. Home Shopping Network had 8, 5 of which
       | would keep them on air. That's an extremely reliable backup.
        
         | toxic72 wrote:
         | Can you share more about the Home Shopping Network's broadcast
         | infrastructure - that's such an explored little nugget of the
         | world I've never given any thought to before
        
           | CapitalistCartr wrote:
           | This is 30+ years ago, they had a halon system. They had
           | calculated the volume of the rooms, including the contents so
           | as to not kill people while supressing fire. So making a hole
           | in a wall, or adding/subtracting _anything_ was a huge
           | production.
        
       | NelsonMinar wrote:
       | This page is SEO crap. A thin article with little technical
       | content peppered with links to the company's own products.
        
       | rietta wrote:
       | I know from experience that plugging an old school digital alarm
       | clock into a UPS does not work. The clock drifts badly. Turns out
       | those use the AC cycle rate as their clock.
        
         | kadoban wrote:
         | It should depend on the UPS, some I believe are
         | indistinguishable from wall power, especially without actually
         | trying.
         | 
         | Even for the cheaper UPSes I wonder if the issue isn't the
         | cycle rate, but the cycle shape? My understanding is that they
         | tend to be able to hit 60Hz pretty easily, but the cheaper ones
         | are a ~square wave instead of a ~sine wave. Maybe the digital
         | clock just glitches on that more.
        
           | yafosuda wrote:
           | To clarify this comment: there are two primary types of UPS,
           | double conversion and line interactive.
           | 
           | Double conversion takes power from AC, converts it to DC to
           | charge batteries, takes battery output, and inverts it back
           | to AC. All power drawn from the UPS goes through the battery
           | and inverter stack, and there is no transient/power loss when
           | AC mains are lost. They tend to be more expensive, louder,
           | run hotter, etc.
           | 
           | Line interactive UPSs, on the other hand, tend to be cheaper
           | and are in most cheap consumer products. They take AC mains,
           | convert it to DC, and charge batteries. But AC mains is also
           | connected directly to the output device through switch
           | circuitry that will quickly switch the power source from AC
           | mains to batteries/inverter if power loss is detected.
           | 
           | Reputable UPSs will use pure sine wave inverters for
           | converting DC battery back to AC. Modified sine waves are
           | indeed a lot cheaper but are not suitable for some sensitive
           | equipment.
        
         | LorenPechtel wrote:
         | Yup, made a variation of this mistake once long ago. Ordinary
         | clock, plugged into a transformer connected to Chinese (220/50)
         | power. It ran 20% slow.
        
       | digitalsushi wrote:
       | I had an underpowered battery backup for my desk, and was using
       | it for my gaming PC, two laptops, and two external monitors, and
       | all my peripherals. (It didnt occur to me I was overrunning it,
       | otherwise my rant here is nonsensical)
       | 
       | The monitors both had the same general issue - they would fail to
       | find a signal every few weeks, and I'd find that waiting a few
       | hours with them turned off would help.
       | 
       | I have pages of notes here. Another way to get them to work would
       | be booting up the windows computer, which would seem to 'trick'
       | the monitor into getting a signal on hdmi, and then I could
       | switch to display port for the mac laptops to be used.
       | 
       | Anyways it's all crazy rambling notes, with copious timestamps,
       | looking for patterns. I have an IR heat thermometer from the
       | kitchen and my monitor vents would regularly have air over 160F
       | coming out the tops when the monitors would not even post the
       | vendor logo after a hard power reset.
       | 
       | I removed the battery backup and it's been months now with zero
       | blips. So the only obvious takeaway I have is that overrunning a
       | battery is a completely worthless endeavor.
        
         | lmpdev wrote:
         | What I find insane is the peak current discharge those little
         | 12V 7-9ah backup batteries can push out
         | 
         | Well over 100A for a few seconds
         | 
         | Lithium can't even do that in a single cell (but in turn is
         | infinitely better for continuous current)
         | 
         | It sort of baffles me intuitively that an extremely simple lead
         | battery can for a short while compete with the _grid_
        
           | jpgvm wrote:
           | Yeah this is why lead acid was hard to replace in cars with
           | lithium chemistries.
           | 
           | The Cold Cranking Amps (pretty much the peak startup current)
           | that they can provide is rather insane. Even my small
           | motorcycle battery provides over 250 CCA.
        
             | elintknower wrote:
             | Super capacitors / just large capacitors in general might
             | eventually save the day here. The only issue is super
             | capacitors can't generally bake in the heat all day and
             | still work for 3-5 years like lead acid batteries can.
             | 
             | Supercaps is how "fast" charging in most smartphones works
             | as well since they can soak current faster than the battery
             | itself and also mitigate cycling batteries too hard.
        
           | jnsaff2 wrote:
           | It won't be anywhere near 12V while supplying those 100A.
        
           | p1mrx wrote:
           | 12V x 100A = 1.2 kW. A typical grid connection for a house is
           | 240V x 200A = 48 kW.
        
           | somehnguy wrote:
           | Lithium polymer pouch cells can easily push out well over
           | 100A, even relatively small cells hit this mark no problem.
        
         | russdill wrote:
         | Are they Asus monitors by any chance?
        
         | j45 wrote:
         | It might also be helpful to ensure you have a battery backup
         | that provides pure-sine wave electricity when plugged in, and
         | ideally as close to it as possible when on battery backup and
         | the power is out.
        
           | jjeaff wrote:
           | most electronics don't need pure sine waves as they are
           | converting the ac to DC anyway. but perhaps a square wave
           | could throw off some PSUs.
        
       | danjl wrote:
       | Do kids these days actually make Daisy chains anymore? You know,
       | with real Daisy flowers.
        
         | AzzyHN wrote:
         | I was unaware that was the origin of the term, so probably not
        
       | elintknower wrote:
       | Is anyone else here using Ecoflow batteries as a UPS backup? I
       | really wish Eeaton would produce a similar consumer facing
       | function that is intended to be used long-term 24/7 not just on
       | weekend trips etc.
        
       | necovek wrote:
       | This is the type of article I find useless.
       | 
       | It would be great if Eaton went to the trouble to explain what
       | exact conditions the two UPSes need to fulfill to be successfully
       | daisy chained, which would probably put people away from doing it
       | anyway.
       | 
       | But it would also be a much more informative article, and also
       | positively framed, which is always a much better read.
        
         | deadbunny wrote:
         | That just leads to "I followed your instructions on your
         | website and my house burned down". No company is going to open
         | themselves up to that.
        
         | zootboy wrote:
         | They don't explain it because it basically never makes sense to
         | daisy-chain a UPS. If you want redundancy in your power supply
         | chain, use a dual-PSU computer. If you want longer backup
         | times, get a UPS with a bigger battery.
        
           | BuildTheRobots wrote:
           | The only time I think it makes sense if if you're doing a
           | belt+braces with colo'd stuff in a datacentre.
           | 
           | The DC will have its own UPS system, but in the event it all
           | goes wrong (which happens more often than I'd like) you
           | probably want something in your cab that can give your
           | equipment notification and time to shut down safely, and
           | provide surge suppression and maybe some level of isolation
           | from the inevitable back-emf caused by the rest of the hall
           | going dark.
        