       | ethbr1 wrote:
       | >> _TL;DR: Despite otherwise seeming to work correctly, I can't
       | monitor a Back-UPS BX1600MI in Linux without seeing a constant
       | stream of spurious battery detach /reattach and power
       | fail/restore events that last less than 2 seconds each._
       | 
       | It sounds like the Windows software probably debounces the
       | incoming events, only bubbling up those that are sufficiently
       | time-stable, to account for bargain sensor false positives?
       | 
       |  _Edit:_ Looks like the apcupsd collection also has some EEPROM
       | programming utilities... (for supported devices)
       | http://www.apcupsd.org/manual/#configuration-directives-used...
        
         | bell-cot wrote:
         | I'd bet you're right. Experience at $Job is that certain cheapo
         | UPS's can be miserably twitchy about detecting power problems
         | and switching to their inverters. After a week of the clickity-
         | clicks of the cut-over relays - $Employee and his office mates
         | may ask for the UPS to be removed.
        
       | bell-cot wrote:
       | > Our power grid is very reliable. Looking at availability
       | information from "uptimed", my home file server has been powered
       | on for 99.97% of the time in the last 14 years. That includes
       | time spent moving house and a day when the house power was off
       | for several hours while the kitchen was refitted!
       | 
       | > However, in December 2023 a fault with our electric oven popped
       | the breaker for the sockets causing everything to be harshly
       | powered off. My fileserver took it badly and one drive died. That
       | wasn't a huge issue as it has a redundant filesystem, but I
       | didn't like it.
       | 
       | > I decided I could afford to treat myself to a relatively cheap
       | UPS.
       | 
       | Just from that, I'd say he for-sure should have avoided UPS's,
       | and gotten a "real" surge protector. The "shockwave" from that
       | high-amperage short is far more likely to have done the damage
       | than the mere loss of power. And the output of cheap UPS's is
       | often far worse than the input.
       | 
       | [Edit: And _good_ surge protection is never a feature of cheap
       | UPS 's.]
        
         | jeffbee wrote:
         | The quoted material sounds like a poor analysis. It doesn't
         | take into account all the times the UPS would have failed while
         | the grid was fine. UPSs are not pure goods with no downsides
         | that merely add to availability. Commercial UPS are very
         | unreliable, bordering on a scam.
        
           | Symbiote wrote:
           | It also doesn't account for the fire risk -- a cheap UPS is
           | much more likely to catch fire than a PC / NAS.
        
             | WWLink wrote:
             | Yea, a disturbing amount of reviews on amazon for the lower
             | end (still 1350/1500VA though!) UPSes contain words like
             | "smoke" and "fire".
             | 
             | My own experience with UPSes didn't involve smoke or fires,
             | but it did involve remote equipment going offline for
             | months until I had time to make a trip out to replace the
             | UPS with a surge protector.
        
         | gnuser wrote:
         | Sine-Wave UPSs are the only thing I allow in my DCs for a
         | reason! (don't forget the generators either!!!)
        
           | Night_Thastus wrote:
           | Pure Sine-wave UPSs are massive overkill and offer no
           | advantage for any normal consumer.
           | 
           | If you have incredibly power-sensitive $100k equipment that
           | needs protecting, _maybe_. But not for normal consumer
           | electronics. None of them are that picky about the power.
        
             | kcb wrote:
             | That's not my experience. Modern power supplies in desktop
             | PCs either don't work or trip up non Pure Sine wave UPSs. I
             | don't know the technical specifics but it has to do with
             | Active PFC on power supplies.
        
               | Night_Thastus wrote:
               | I've used square wave UPSs on my PCs for as long as I can
               | remember with power supplies from varying manufacturers,
               | I have never had a problem. I have heard this before but
               | I suspect it's either a myth or it only was ever a
               | problem with very rare combinations of poorly-made UPSs
               | and poorly-made power supplies.
        
               | wzdd wrote:
               | I was forced to change UPS relatively recently (a few
               | years ago) because the cheap but not bargain-basement PSU
               | on my computer didn't work with the non-sine-wave output
               | of my UPS. Call them poorly-made if you like, but either
               | I got unlucky or they're fairly common.
               | 
               | Power supplies tend not to advertise their compatibility
               | with non-sinewave power, but UPSes will certainly make it
               | clear if they produce sinewave output. So the safe option
               | is to get the UPS which gives the PSU what it's
               | expecting.
        
             | J_Shelby_J wrote:
             | I did a deep dive into this when buying a UPS last year,
             | and ended up with a sine wave ups. But just now I couldn't
             | find my sources for why I made that choice. I believe it
             | was something to do with the new ATX 3.0 PSU standard.
             | 
             | I did find this older thread[1], but the answer is more of
             | a "maybe if your PC or server is using an active PFC PSU."
             | However, this is out of date (2015), and may no longer be
             | correct.
             | 
             | Cyberpower's website says PSU with active PFC require pure
             | sine wave.[2] But that might be marketing. IDK, seems like
             | it something that may need to be tested to be sure.
             | 
             | [1] https://superuser.com/questions/912679/when-do-i-need-
             | a-pure... [2] https://www.cyberpower.com/global/en/product/
             | series/pfc_sine...
        
             | mcmcmc wrote:
             | Well they did specify it was for datacenter use.
        
         | criley2 wrote:
         | We recently upgraded to a whole house surge protector installed
         | at the panel. They're not that expensive ($100-$200 around me,
         | depending) and with the reduced quality of power we're seeing
         | lately here and the damage it has done to our circuit breakers,
         | it's become a necessity.
        
         | da768 wrote:
         | And after the UPS will inevitably fail to power on, he'll
         | probably want to add an automatic transfer switch to the mix.
        
         | ssl-3 wrote:
         | Can you be more precise about how a high-amperage short circuit
         | can produce a "shockwave" of a form that would be ameliorated
         | by a "real" surge protector?
        
           | bell-cot wrote:
           | > Can you be more precise...
           | 
           | Apologies - I know enough to do long-winded hand-waving on
           | the subject...but if you want precise and concise (and really
           | accurate), you'll need to ask a real electrical engineer.
        
           | javawizard wrote:
           | This Wikipedia article may point you in the right direction:
           | https://en.m.wikipedia.org/wiki/Voltage_spike
           | 
           | I'm not an electrician by any means so take everything I saw
           | with a grain of salt, but: in general, electricity flowing
           | through a system has some amount of "inertia" (the technical
           | term for this is inductance), and shutting off a circuit
           | breaker will cause a brief voltage spike upstream of the
           | breaker due to the flow of electrical current suddenly being
           | forced to stop.
           | 
           | Have you ever unplugged a running appliance from the wall and
           | noticed a brief spark at the plug? That's the same effect:
           | motors in general have high inductance and try quite hard to
           | fight changes in current.
           | 
           | It's bad enough that when designing circuits that switch
           | power to inductive loads like motors, you have to include a
           | flyback diode (read: one way valve) to allow a path for
           | electricity to continue to flow internal to the load when the
           | power is switched off, otherwise it will generate a voltage
           | spike high enough to damage the switching circuit.
           | 
           | Put another way: it's not the "high amperage short circuit"
           | that causes the voltage spike; it's the rapid stop to said
           | high current that happens when the circuit breaker realizes
           | what's going on and trips.
        
         | Saris wrote:
         | I'm curious how a voltage spike would have gotten through the
         | computer PSU conversion to DC, and then only damaged 1 drive
         | somehow?
        
           | dijit wrote:
           | it hit all the drives, but it'll affect things unevenly
        
         | tgsovlerkhgsel wrote:
         | I assume the drive failed due to the power cycle, not due to
         | electrical damage.
         | 
         | Especially if it was 14 years old.
        
       | justinclift wrote:
       | As a side note with UPS's, it can somewhat informative to look at
       | the pricing for their replacement batteries.
       | 
       | At least here in Australia, replacement batteries for some of the
       | common UPS's (for desktop usage) cost nearly as much as the UPS
       | itself.
        
         | alright2565 wrote:
         | From my own adventure in this area, the battery is very
         | standard and IMO reasonably priced. What gets expensive is
         | shipping it, since lead is so heavy. I remember having trouble
         | finding local sellers for them that would have avoided the
         | shipping cost.
        
           | twisteriffic wrote:
           | I've found home security companies to be a good source,
           | either of the batteries themselves or at least a local
           | supplier who can get what you need.
        
         | TMWNN wrote:
         | Also consider how the size of the UPS affects the battery
         | replacement cost. I purchased my most recent UPS, refurbished
         | by CyberPower, from its eBay store
         | <https://www.ebay.com/sch/i.html?_ssn=cyberpower>. For a few
         | dollars more I could have bought a larger size, but
         | 
         | * I didn't need more capacity (the one I bought will power the
         | server it serves for an hour, far more time than I need or
         | want) and, more to the point,
         | 
         | * The larger-size model has two batteries to replace,
         | significantly increasing the cost.
        
           | Libcat99 wrote:
           | I wish the battery layout/ amp hours was more obvious in UPS
           | sales listings. The watts/VA are always front and center, but
           | generally I want to know runtime which is harder to find and
           | compare.
        
         | Johnny555 wrote:
         | I never buy APC replacement batteries - third party batteries
         | are much cheaper, and seem to work just as well based on
         | testing by the UPS itself.
        
       | jonathantf2 wrote:
       | I own two Back-UPS 1400VA units, one monitored with apcupsd and
       | the other with a MikroTik router - so I guess it's just the newer
       | units that have this issue?
        
       | 1970-01-01 wrote:
       | >I then asked about this on the apcupsd mailing list. The first
       | response:
       | 
       | "Something's wrong with your..."
       | 
       | "Returning to my thread on the apcupsd mailing list, I asked
       | again if there was actually anyone out there who had one of these
       | working with non-Windows."
       | 
       | Linux's reputation in a nutshell. It just works after you spend
       | days checking if you have a bad device and another on the mailing
       | list. And then you are forced to find a working alternative.
        
         | ethbr1 wrote:
         | Hardware validation is time consuming, boring, and expensive.
         | 
         | Not surprising that given a mostly volunteer effort... it just
         | doesn't happen. Or vendors self-certify their own gear.
        
           | thayne wrote:
           | It's not like Microsoft or Apple do that either. But Vendors
           | are more thorough with testing on those OSes.
        
             | mynameisvlad wrote:
             | Uhhh... what? Both Apple and Microsoft have hardware
             | certification programs which require review.
             | 
             | https://mfi.apple.com/
             | 
             | https://learn.microsoft.com/en-us/windows-
             | hardware/design/co...
        
               | thayne wrote:
               | As far as I know, the actual testing is done by the
               | vendor. It might get reviewed by an MS or Apple imployee,
               | but that isn't the same thing as actively testing the
               | hardware themselves. Or providing software to work with
               | third party hardware.
               | 
               | It's a chicken and egg problem. Hardware vendors don't
               | worry about linux compatibility, at least for
               | consumer/desktop products because the market share is
               | low. But one reason lack of good hardware support hinders
               | adoption of linux on desktop.
        
         | gpderetta wrote:
         | typically you check for linux compatibility before buying the
         | actual hardware/software.
        
           | ziddoap wrote:
           | > _There's an entry in nut's hardware compatibility list for
           | "Back-UPS (USB)" of "supported, based on publicly available
           | protocol". I made the order._
        
             | gpderetta wrote:
             | Well, good point. In addition of wrong or incomplete
             | compatibility lists, sometimes internal details of products
             | change without even changing SKUs, breaking compatibility.
        
           | angry_moose wrote:
           | I probably spent 20 hours this week trying to get a not-that-
           | obscure piece of software that explicitly states "Debian 12"
           | support on their website working on a freshly-installed (as
           | in - install Debian 12, update system, install software); and
           | it still just doesn't work. After hammering my way through 4
           | different errors, and hopelessly out of date (and wrong)
           | documentation, I finally got them to issue a refund this
           | morning.
           | 
           | "Linux Compatibility" often means "someone got it working
           | once 6 years ago, on an extremely out of date version of the
           | OS, but its probably still fine".
        
             | graemep wrote:
             | Not often. I have nit rub into that problem, ever.
        
             | dingnuts wrote:
             | This is why you do an internet search instead of just
             | looking at what the vendor says, and/or look at what the
             | vendor actually ships for support. If you see something
             | like a binary blob, run away. If you see stuff shipped
             | upstream, go ahead.
             | 
             | As a counterpoint to your experience, I've had great luck
             | buying laptops off of Canonical's approved hardware list.
             | 
             | As a corollary, I've had worse luck buying computers that
             | come with Linux pre-installed, only to discover that the
             | pre-installed distribution is very specifically and
             | carefully configured and includes proprietary bits and it's
             | impossible to install any other Linux on the device or
             | upgrade it.
        
           | bravetraveler wrote:
           | Once you learn a few soft guidelines _(not rules, nothing is
           | perfect)_ , you don't really even need to research.
           | 
           | Intel/AMD: probably fine. Realtek: works, one driver codebase
           | for everything means weirdness is likely. Broadcom: don't
           | even bother. Nvidia/mobile: what kernel/stack are you
           | intending to use?
           | 
           | I haven't had to care about compatibility with _desktop_ or
           | _server_ components in over a decade.
           | 
           | It's fingerprint readers and dual-GPU laptops that really bum
           | a lot of people out.
        
           | justsomehnguy wrote:
           | Ah, yeah, the typical " _you_ should had checked for the
           | compatibility, it 's you who are the problem, not Linux".
           | 
           | And yes, I never check for Windows compatibility before
           | buying the actual hardware/software. Not even /s.
        
             | graemep wrote:
             | Lots of devices do not support Windows. I am typing this in
             | an ARM based tablet that does not,but does run Linux. Can
             | you install Windows on all Chrome books, or Apple Macs?
             | 
             | I do not usually check for hardware compatibility with
             | Linux either. The only things I have checked that I have
             | bought in the last few years have been graphics cards and
             | USB wifi, and the latter was just a matter of reading
             | product descriptions.
             | 
             | A lot of software I use either does not run on Windows, or
             | is harder to install or is less mature on Windows.
             | Obviously lots of server side stuff, but even some desktop
             | stuff I would be doubtful about because the bulk of users
             | are on Linux.
        
               | jrockway wrote:
               | The post you're replying to doesn't say that Windows runs
               | on everything. He's saying that every piece of commercial
               | software runs on Windows, and that every widget has a
               | Windows driver. I have found this to be quite true. If
               | you have Windows, you can impulse-buy pretty much
               | anything and end up OK.
        
               | justsomehnguy wrote:
               | And look how you immediately pivoted from the
               | compatibility _with Windows_ to the compatibility _with
               | running Windows_.
               | 
               | > The only things I have checked
               | 
               | That's great but nobody needs to check if it's compatible
               | with Windows. The whole step - it's just not needed.
               | 
               | So if the "everything just works in Linux!" people say
               | "oh you should had just checked" then the former was
               | clearly not in a good faith or outright delusional.
               | 
               | > A lot of software I use either does not run on Windows,
               | or is harder to install or is less mature on Windows.
               | Obviously lots of server side stuff, but even some
               | desktop stuff I would be doubtful about because the bulk
               | of users are on Linux.
               | 
               | And most of the people houses and people themselves can't
               | _run_ the welding equipment, so what? How from discussing
               | compatibility of widgets and gadgets of a regular Joe you
               | moved on to a highly specialized and a very narrow scope
               | of the server software?
        
             | HumblyTossed wrote:
             | Seriously? When buying a car, do you not look for features
             | you want?
        
         | lbotos wrote:
         | I mean -- I built a PC a few months ago and formatting the
         | windows disk from a non windows env was not trivial.
         | 
         | So yes, Linux is still not on par with Windows in many ways,
         | but boy oh boy was it weirder than it should have been to
         | format a USB drive to install windows.
         | 
         | I lost a solid 6 hours to that try, yay it work, wait I'm
         | getting a nonsensical error at a strange screen. Retry with
         | different flags, with different hardware, etc etc etc.
        
           | skirmish wrote:
           | Ditto, I was building a Windows desktop and spent hours
           | faffing around attempting to follow official Microsoft
           | instructions even with another Windows computer available; in
           | desperation tried Rufus Installer, worked on the first
           | attempt. Then months later was building another desktop and
           | went straight to Ventoy installed from Linux and just
           | dropping a downloaded ISO on the USB stick -- worked
           | immediately.
        
         | HumblyTossed wrote:
         | Or...
         | 
         | Don't buy a consumer grade UPS if you want to monitor it
         | properly.
        
           | nickt wrote:
           | Any suggestions?
           | 
           | Is there a power delivery equivalent of Ubiquti (I know we've
           | discussed their shortcomings here) that offer better than
           | consumer grade for less than enterprise prices?
        
             | HumblyTossed wrote:
             | Yeah, go with APC, just not their consumer grade stuff.
        
               | amluto wrote:
               | Or get something sold for off-grid use instead of as a
               | UPS. Ecoflow is one of many vendors.
        
             | monitron wrote:
             | I am having good luck with Eaton so far. Rock solid and
             | their network monitoring is noticeably less painful to use
             | than APC's!
        
               | schlauerfox wrote:
               | We have widely deployed the workstation devices and have
               | had no maintenance issues. we installed ~10 9PX models
               | and have had 2 fail suddenly and completely just out of
               | warranty and one with a failed battery charger, also just
               | out of warranty, and a gigabit management card that works
               | for a week or so then goes offline and requires local
               | reboot from console but we have about 10 deployed with no
               | issues too, so buy extended support because their support
               | team is good but useless if you don't pay the protection
               | money. We also had a rack PDU just die right out side
               | it's warranty phase and we only bought 6. Not great
               | quality it seems but it does the job. We had one install
               | of a full rack UPS and it's been running for more than 7
               | years, but you have to keep the maintenance up and
               | schedule battery swaps. They do make a really nice 1U
               | lithium-ION ups also which is neat. The IPM software is a
               | little janky but also works well.
        
         | NotYourLawyer wrote:
         | Not just that, but also "this is all your fault for buying
         | cheap trash!"
        
       | kayodelycaon wrote:
       | I have what was the cheapest APC UPS years ago and the macOS
       | software works fine.
       | 
       | Doesn't help anyone running Linux though. :/
        
         | e40 wrote:
         | I have an APC on macOS, too, and as of a couple of OS
         | iterations ago it recognizes it natively. I used to run apcupsd
         | on macOS, but it was quite tricky to keep it working, due to
         | the USB interface. This was on an older Mac than I'm using now
         | (the trashcan Mac Pro), but it mostly worked and I would always
         | have an indication when it stopped working as the icon in the
         | menubar would change. I think the usual issue was so lock file
         | was owned by root and couldn't be deleted.
        
       | dooglius wrote:
       | If the vendor gives a proprietary Windows application for
       | monitoring then... of course? What did you expect?
        
         | criddell wrote:
         | There's a USB standard for HID power devices. I would expect
         | basic functionality from any UPS with a USB port.
        
       | mrlonglong wrote:
       | I have one of these APC Back-UPS 900 (BR900GI) here, and they
       | work perfectly. Fully supported under apcupsd, that device has
       | saved my bacon quite a few times. The only thing is that you MUST
       | use the USB cable they provide.
        
         | throwawaaarrgh wrote:
         | Doesn't that kind of prove they're messed up, if no other USB
         | cable works?
        
           | rincebrain wrote:
           | APC doing horrible things with "standard" cables isn't new,
           | though - they used a nonstandard null modem serial cable back
           | in the day, such that if you tried to connect to the UPS
           | using a standard null modem cable, it'd trigger shutting off
           | the UPS.
           | 
           | This isn't to say it's good, just that it's not new.
        
             | extraduder_ire wrote:
             | Mine has a usb-A to rj45 cable with a ferrite bead on it,
             | as far as I can tell it just wires the four USB wires (no
             | ground) to the pins with spaces in between. I have never
             | understood why they do this.
             | 
             | It works perfectly with apcupsd though, even showing up in
             | my desktop power settings as a UPS.
        
               | mrlonglong wrote:
               | This, 100%.
        
               | mynameisvlad wrote:
               | They might be repurposing the same chassis for both USB
               | and Ethernet-based UPSes.
        
               | yanellena wrote:
               | Usually the APC UPS's with a network connection have a
               | separate slot in card which has a network connection and
               | an additional serial connection on it.
        
             | hackmiester wrote:
             | The pro series literally still has this exact connector
             | today, with the same behavior.
        
               | fuzzfactor wrote:
               | APC was the only UPS company to have their device drivers
               | natively included with Windows 95.
               | 
               | That was before USB was available so they used regular
               | COM port communication, I'm not surprised with that early
               | foothold there was no reason to change and sufficient
               | force to continue ever since.
               | 
               | At the time it seemed like the un-necessarily non-
               | standard RS-232 cable was just to create a "profit
               | center" from the cables themselves, along with the non-
               | standard replacement batteries. They sure would have been
               | a lot quicker to market and had lower up-front
               | engineering costs if they had used standard batteries
               | from the beginning.
               | 
               | It's good to recognize early when excessively high TCO is
               | the primary feature around which a product (or company)
               | is designed. There can be significant PR effort from the
               | beginning to divert any perception of anti-consumer
               | attitude.
               | 
               | Lots of stealth can be involved to muddy the comparison
               | with alternatives which offer normal TCO or well-
               | engineered low-target TCO.
        
             | ronniefalcon wrote:
             | sysadmin right of passage #4
        
               | unwind wrote:
               | It's _rite_ of passage [1], apologies if that was a typo
               | or auto-correct etc.
               | 
               | [1]: https://en.m.wikipedia.org/wiki/Rite_of_passage
        
               | ronniefalcon wrote:
               | are you a bot or do you do this in your spare time?
        
             | soneil wrote:
             | That's always drove me nuts because the underlying issue is
             | a great idea, frustrated by its implementation.
             | 
             | The serial port serves dual-purpose. Along-side the obvious
             | serial, you can also provide some inputs by grounding
             | certain pins, and some outputs by sinking current from
             | others. This has got me through some unorthodox
             | integrations by having the UPS signal that it's on battery
             | by having these "simple signals" close a contact/relay on
             | the load. It's not quite a full suite of dry contacts, but
             | it's pretty serviceable.
             | 
             | The problem is that 9 pins doesn't leave many spare, so to
             | achieve this they've repurposed some. I really wish they'd
             | implemented this as an alternate mode so you'd, for example
             | short tx to rx to change the behaviour - instead of having
             | the 'alternate behaviour' sitting on standard DTR/RTS pins.
             | 
             | Getting industrial interfaces at SOHO prices was awesome.
             | The unintended consequences .. less so.
        
             | csnover wrote:
             | It's baffling. When APC first added native USB support to
             | their Smart-UPS series, they chose a standard USB-B port.
             | When they introduced "SmartConnect" a few years ago, this
             | port was replaced by a USB-A port which requires a non-
             | compliant USB-A male-to-male cable for monitoring. The only
             | 'good' reason I can think of for this change is that
             | someone realised that these new cloud-connected UPSes would
             | be easily bricked by some bad firmware update (since
             | apparently that's a feature now), and wanted to use USB
             | thumb drives as a recovery mechanism, but I have no idea. I
             | think even though they have a built-in Ethernet port now,
             | one still needs to buy their network management card for
             | non-cloud remote management, so it could just as easily be
             | another attempt at some weird vendor lock-in.
        
           | rcxdude wrote:
           | The connector on the back is essentially a non-standard
           | serial connector, and the USB cable is a USB-serial adaptor.
           | You can probably make another work, but only by making an
           | adaptor cable yourself. They have some models where the USB-
           | serial adaptor is integrated into the unit, which is
           | generally a bit easier to use and a more typical approach.
           | 
           | (Generally, such a protocol is a better option from a
           | compatibility point of view: it's usually fairly easy to
           | reverse engineer. It would be interesting to sniff what the
           | windows software is doing to work out what protocol or
           | behaviour difference is responsible)
        
             | consp wrote:
             | The fun part is that there are at least two different, non
             | standard, DB9 serial configurations.
        
               | ssl-3 wrote:
               | The more-fun part is that using the wrong one can
               | instruct an APC UPS to shut down immediately.
               | 
               | (I'm not convinced that anyone has ever been behind the
               | wheel of the ship that is called APC.)
        
               | mr_person wrote:
               | I have lost 3 different usb-to-serial adapters to an old
               | server room APC, probably for this reason
        
         | tempest_ wrote:
         | I just bought batteries for a 20 year old UPS, still chugs
         | along, network interface is base 10!
        
           | StillBored wrote:
           | I had a 20 year old APC start misbehaving on me a few months
           | back, and new batteries didn't fix it. After messing up the
           | repair on the first one, a second one started doing the exact
           | same thing, and I immediately took it apart and, now an
           | expert on how not to fix them and what the root cause was, I
           | swapped every cap on the board that my ESR meter claimed was
           | bad. It's now back in operation, and while I was testing it,
           | I realized it's so inefficient that about 10% of its max
           | rating is just going up in heat. The replacement for the
           | first one, I assumed, would be much more efficient, and it
           | is, but it's still dumping about 7% of its energy into
           | heating the transformer.
           | 
           | OTOH, the older UPS behaves much better with apcupsd, going
           | so far as giving me the firmware versions, battery
           | replacement times, better power monitoring/etc. While the new
           | one works its missing most of what the older UPS could do
           | (although its not a APC).
           | 
           | So, i'm sorta on the fence about just using "backup
           | generators" from Amazon/etc because one of the ones I have
           | has about 5x the capacity of the new UPS and seems to be able
           | to switch without the computer plugging into it having an
           | issue. Plus, its power waste is less than 1%.
        
         | iforgotpassword wrote:
         | I've had an AMD based home server a decade ago. Connected an HP
         | printer, and it would frequently cause disconnect and reconnect
         | events in dmesg, sometimes ending up in some error state when
         | Linux would just give up trying to identify the device. After
         | trying different ports and cables I eventually, out of
         | desperation, threw in an unpowered old USB 2.0 hub and lo and
         | behold, the connection to the printer was rock solid.
        
       | spintin wrote:
       | It's better to just build your own with a 12v charger, a few 12v
       | lead acid deep discharge batteries in parallel and a 9-18v -> 12v
       | aligner.
       | 
       | If you live in EU go with 110-220v charger so your setup can
       | outlive a brownout.
        
         | alright2565 wrote:
         | How do you power a PC off this setup? Mine has a C14 inlet.
        
       | shrubble wrote:
       | Just a warning: there are differences in the output from UPSes
       | with the cheaper ones' output not working well with higher
       | efficiency power supplies. Better UPSes will output less 'jagged'
       | AC.
        
         | krunck wrote:
         | Yeah, I ran into this once. You want to find ones that state
         | they have true sine wave output.
        
         | folmar wrote:
         | If you do you shopping around getting clear sine output does
         | not increase the price usually, or maybe a few percent.
        
       | BlueTemplar wrote:
       | Is it me or going cheap on _anything_ power-related seems like a
       | _terrible_ idea ?
        
         | Borg3 wrote:
         | Yeah, it is. I own two good old APC SmartUPS 1000 (one for
         | desktop and second for server). They are absolutly reliable,
         | quiet and output Sine when on battery. Good old reliable tech,
         | easly monitored using apcupsd for example.
        
       | aaronmdjones wrote:
       | I have my APC Back-UPS CS650 (BK650EI) plugged into my router
       | (running OpenWrt) which works fine with Network-UPS Tools. The
       | router shares the UPS status with the whole LAN, and the machines
       | on the LAN that are powered by the UPS will shut down
       | automatically when the UPS battery goes critical.
        
       | zzzeek wrote:
       | I had some battery issues with my previous BackUPS 750 but once I
       | got a new battery, things were fine with apcupsd. Have been on a
       | BackUPS-Pro 1500 S for a couple of years now also using apcupsd
       | and zero problems. it legitimately records a low power event when
       | my Brother printer first starts up, switches to battery then
       | comes right back. Similar happens when it's stormy here and power
       | lines are going down and being re-routed.
        
       | simpaticoder wrote:
       | Can anyone recommend a good modern UPS? It seems like Lithium Ion
       | would have the best power density, but perhaps lead-acid is
       | actually better for this application? Good surge protection would
       | also be great. It would be nice if there existed a UPS brand that
       | is like Anker for USB cables and power adapters or Brother for
       | printers.
        
         | mplewis wrote:
         | I have had good luck with my refurbished APC BR line from
         | ExcessUPS.
        
         | slashink wrote:
         | The Cyberpower series sold at Costco is unironically good. No
         | frills or cool stuff, UI from 1995 but supports USB monitoring
         | out of the box and just... works. I was about to make the
         | brother comparison but after reading your entire comment
         | realize you already did it.
        
         | bongodongobob wrote:
         | In general, a UPS is just supposed to buy you time to assess
         | the situation and shut things down gracefully. Power density
         | doesn't come into the equation at all. It's just supposed to
         | give you an hour to figure out what you need to do. It's all
         | about the lifetime of the battery. I go with Cyberpower.
        
           | Johnny555 wrote:
           | I put an oversized UPS with extended battery pack on my
           | network gear (Cable modem, Router, ethernet switch and Wifi
           | nodes) to give me almost 8 hours of runtime in a power
           | outage. I've found, however, that the cable company's UPS
           | only lasts around 6 hours since that's how long it takes for
           | the internet to go out and the cable modem to lose carrier.
           | 
           | In the winter months (when we have most of our power
           | outages), I pay for a pre-paid cellular SIM for backup. The
           | cell tower(s) that serves my area must be on generator, it
           | doesn't seem to go down even in long power outages.
        
             | bongodongobob wrote:
             | That makes sense, network gear doesn't suck a lot of power.
             | For compute though, I always have to have the conversation
             | with clients that multiple hours of UPS backup for a server
             | rack is crazy expensive. They are usually better off with a
             | UPS that can take over while a generator spins up if they
             | really need that kind of reliability. I always ask, what
             | are the odds that your 8 hour power outage scenario isn't
             | from something catastrophic like a flood or a fire, eg, if
             | the power is out for that long, something is probably
             | literally on fire and you've got bigger problems.
        
         | Night_Thastus wrote:
         | APC's are good once you get to the 'PRO' line. I would not get
         | anything cheaper than that - those ones are poorly made.
        
         | folmar wrote:
         | Power density is not a problem usually as you don't care for
         | the size and weight, and lead-acid give best bang for buck.
        
         | radicality wrote:
         | Are Anker cables considered good? I have a few, but recently
         | one of my anker usb-c cables started to only go up to 15W,
         | making me think something broke with the usb pd chip.
        
           | yjftsjthsd-h wrote:
           | Yes AFAIK Anker generally has a good reputation, but what
           | does that have to do with uninterruptible power supplies?
        
           | ianburrell wrote:
           | Anker is good. The limit for USB-C cables is normal ones go
           | to 60W, marked ones go to 100W. The cables are passive except
           | for the marker chip. It is the charger that does USB-PD. Do
           | you have it plugged into regular charger that does 15W, or
           | USB-PD charger that does more?
           | 
           | I guess you could have a bad cable where the CC wire has
           | broken and can't do USB-PD.
        
           | ssl-3 wrote:
           | Anker products are generally good (and they were the first to
           | make consistently-good cables and chargers -- in the early
           | smartphone days, _everything_ non-OEM was junk), but things
           | still break eventually.
           | 
           | Their customer service is supposed to be legendary. If you
           | drop them a (polite) descriptive note, signed with your name
           | and address, I'll bet you a beer that you'll have a new cable
           | in your hands by the middle of next week.
        
         | dhd415 wrote:
         | I've found my moderately-priced Eaton 5S 1500 unit to perform
         | considerably better than any of the non-pro APC models I used
         | before it.
        
         | CamperBob2 wrote:
         | Look for used enterprise-grade or at least higher-end office
         | grade equipment on eBay and other surplus marketplaces, and
         | install new batteries. Cyberpower is a good brand in my
         | experience.
         | 
         | The only advantage to buying new is weight. Newer UPSes tend to
         | be a lot lighter, but that's often because they cut corners on
         | the magnetics and/or use expensive, hard-to-replace lithium
         | batteries. Weight is a high priority for the manufacturer to
         | optimize, but not for the consumer. When it comes to UPSes, old
         | school big-iron transformers and heavy-metal batteries are the
         | way to go IMO.
        
         | ianburrell wrote:
         | Lead acid is used for most UPSes. Lithium ion is bad battery
         | type for UPS since has lower cycles and safety, and power
         | density doesn't matter. LiFePO4 would be perfect, with good
         | cycles, current, and safety.
         | 
         | But manufacturers don't use it. Maybe they haven't redesigned
         | after the price dropped. Or maybe cause prices is still too
         | high. I think LiFePO4 would be most useful for rack mounts, or
         | small UPSes that aren't possible with lead acid.
        
           | soneil wrote:
           | Lithium in smaller UPS is mostly stuck in a marketing gap at
           | the moment.
           | 
           | Generally lithium UPS win in a 10-year TCO, but SLA wins in
           | up-front costing. Which leaves us with two issues - most
           | consumers look at the sticker price not the TCO, and no-one
           | wants to market their products as "Our lead acid offer only
           | /looks/ cheap, until you see what we charge you for
           | consumables!"
        
           | mardifoufs wrote:
           | Regular Li ion has more recharge cycles than most lead acid
           | batteries that come with UPS. Even high power density liion
           | still usually has 4-500 recharge cycles before reaching a
           | maximum of 80% SOC vs the original capacity. With smarter
           | power management you can get away with much more (for
           | example, if you don't fully cycle the battery)
        
           | ssl-3 wrote:
           | LiFePO4 can be had in the "portable solar generator" space,
           | and some of them have enough input/output capacity to
           | function as a usable UPS. All that they lack is comms for
           | status and automatic shutdown.
           | 
           | It seems like a fairly recent shift -- heck, the whole solar
           | generator concept is a fairly recent shift -- but maybe it's
           | an indication that LiFePO4 devices are becoming more common
           | in the consumer space.
        
         | annoyingnoob wrote:
         | After having tried several brands, I like CyberPower for the
         | combination of price/performance.
         | 
         | Things may have changed, the APC UPS systems I've used required
         | you to power off to replace the batteries. the CyberPower units
         | I've used allow for replacing the batteries hot.
         | 
         | I've had terrible results with Tripp Lite UPS systems - where
         | they fail for no reason at all, and will not auto power up
         | after a power failure.
         | 
         | At a very large size of 30KVA, I've used Eaton UPS systems and
         | they have been rock solid.
        
         | tadfisher wrote:
         | Eaton/Tripp-Lite have a few Li-ion models:
         | https://www.eaton.com/us/en-us/products/backup-power-ups-sur...
        
         | EvanAnderson wrote:
         | The Liebert / Vertiv lithium GTX series is nice but very
         | pricey. I was shocked at how light a 3000VA unit was.
        
       | SadWebDeveloper wrote:
       | I have a BR700G it works flawlessly with apcupsd, minimal to no
       | configuration... the cheap units of APC is for really really
       | desperate consumers, the battery didn't last more than a year
       | from my experience like the BR* ones that usually last 3 years,
       | these lines is the better of the both worlds cheap and
       | sophisticated enough to work "smart" but as expensive as the
       | SMT/SMC units.
       | 
       | Also like everyone say... remember to look for pure sine wave
       | output if you are going to "protect" servers, for network
       | equipment you could use the pwm based ones.
        
       | rpcope1 wrote:
       | Eaton makes much better UPSes at a close price point. I don't
       | know why anyone buys APC or things like Cyberpower anymore.
        
         | dhd415 wrote:
         | This. I finally switched from using various APC models to an
         | Eaton 5S 1500 unit for my desktop and a couple peripherals and
         | it's much better while still being comparably priced.
        
         | topspin wrote:
         | > Eaton makes much better UPSes
         | 
         | What makes Eaton products better? Sincerely want to know
         | anything you can tell me.
        
         | yjftsjthsd-h wrote:
         | I bought one because that's what I could get at Best Buy. This
         | was particularly important because being able because being
         | able to purchase it at a known physical store near me meant I
         | could get it the same day from a relatively trusted vendor, be
         | acceptably confident that I wasn't getting a counterfeit, and
         | that there was hopefully at least some minimum level of quality
         | (read: it probably isn't going to burn down my house).
        
           | macintux wrote:
           | I just looked at Eaton's website. They recommended two
           | companies near me that carry their products: one doesn't have
           | a website (it's not a retail address, maybe just some random
           | person's home), the other's website has lorem ipsum text on
           | their Eaton partnership page, and their shopping site has no
           | Eaton products at all.
           | 
           | So, yeah, it's understandable why people might not be buying
           | Eaton.
        
         | BenjiWiebe wrote:
         | Sorry, don't have the model numbers handy, but:
         | 
         | We have an Eaton and several APCs, all fairly cheap/lowend. One
         | recent power outage, the APCs flipped on but the Eaton just
         | turned off...
        
           | Toutouxc wrote:
           | I've had an ultra cheap Eaton 5E (900 VA) for a few weeks.
           | Because I still don't entirely trust it, I've tried cutting
           | the power to it several times (like 10x maybe) and it's been
           | fine every single time (it talks to a Debian box with NUT).
           | The whole thing was around $80, if it doesn't burn the house
           | down, there are no downsides.
        
       | rcarmo wrote:
       | I have a 550ES, works fine. Some models will require apcd instead
       | of nut, but I have configs for using Proxmox with both here:
       | https://github.com/rcarmo/ground-init/tree/main/samples
        
       | throw0101c wrote:
       | Note that APC has different lines (at various price points):
       | 
       | * Back-UPS: stand-by, Stepped approximation to a sinewave
       | 
       | * Back-UPS Pro: line interactive, Stepped approximation to a
       | sinewave
       | 
       | * Smart-UPS: line interactive, Sine wave
       | 
       | * Smart-UPS Online: double-conversion online, Sine wave
        
       | teddyh wrote:
       | I wonder what happened to Eric Raymond's UPSide project1.
       | 
       | 1. <https://gitlab.com/esr/upside>
        
       | liberix wrote:
       | I've been monitoring several dozen APC Back-UPS units for more
       | than 10 years using apcupsd on Debian without any issues.
       | 
       | There were only a few times (maybe 2 or 3 in all that time) when
       | I saw some messages indicating that something was wrong with the
       | battery (though they never were as frequent as in the author's
       | case). In each of those cases, the messages went away after
       | replacing the battery.
        
       | mmphosis wrote:
       | We get a lot of power failures. I use laptops, but for other non-
       | battery powered equipment, I have a BN1500M2-CA with a raspberry
       | pi running debian plugged into one of the USB charging ports and
       | the USB Data Port cable connected from the UPS to the raspberry
       | pi. It keeps my ISP's 185 watt router going for longer than the
       | ISP's switches will stay up when the power is out. I get more
       | than 3 hours with the router and a 4K monitor plugged into the
       | UPS. I remember seeing NUL characters in the text of an old log,
       | but otherwise apcupsd works well:                 2024-01-30
       | 08:15:13 -0800  Power failure.       2024-01-30 08:15:19 -0800
       | Running on UPS batteries.       2024-01-30 08:20:06 -0800  Mains
       | returned. No longer on UPS batteries.       2024-01-30 08:20:06
       | -0800  Power is back. UPS running on mains.       2024-02-04
       | 12:52:58 -0800  Power failure.       2024-02-04 12:53:04 -0800
       | Running on UPS batteries.       2024-02-04 12:54:04 -0800  Mains
       | returned. No longer on UPS batteries.       2024-02-04 12:54:04
       | -0800  Power is back. UPS running on mains.       2024-02-18
       | 12:10:13 -0800  UPS Self Test switch to battery.       2024-02-18
       | 12:10:21 -0800  UPS Self Test completed: Battery OK
        
         | xp84 wrote:
         | > ISP's 185 watt router
         | 
         | Wait, what?
         | 
         | Does it also heat your room? How can it be so power-hungry?
        
           | mmphosis wrote:
           | I call it "the chimney."
        
           | p1mrx wrote:
           | A Starlink terminal uses less than 185W, and that talks to
           | space while melting snow.
        
           | bongodongobob wrote:
           | I'd bet the power supply is just rated at 185W. No fucking
           | way is a router actually drawing that much power.
        
             | tenebrisalietum wrote:
             | Carrier grade routers do.
             | 
             | https://www.juniper.net/us/en/products/routers/mx-
             | series/mx3...
             | 
             | Random example from a search. According to a calculator I
             | plugged a few values in, it's 2880 watts, but not sure I
             | computed it correctly.
        
               | djbusby wrote:
               | P=I * E
               | 
               | 2880w = 60A * 48VDC
               | 
               | It checks out.
        
               | bongodongobob wrote:
               | I mean this is hacker news, but no one is talking about
               | that beast.
               | 
               | "My vehicle has 3000 horsepower."
               | 
               | "That doesn't sound right."
               | 
               | "Ackshually trains do. Maybe he drives a train."
               | 
               | "..."
        
             | deathanatos wrote:
             | My fairly beefy laptop's PSU is rated at 135 W. It includes
             | an entire GPU.
             | 
             | My own router's PSU is rated at 36 W, for comparison.
        
             | geerlingguy wrote:
             | I've seen people running routers on beefy machines that can
             | certainly pull down hundreds of watts. Even more if it's an
             | older machine.
        
             | mmphosis wrote:
             | You are correct. The input on the wall wart is 100-120vac
             | 1.5a (150watt to 180watt) but the output is _only_ 12.0vdc
             | 4.6a:                 55.2 watts
             | 
             | The "xFi Advanced Gateway (XB7)" router is definitely warm
             | to somewhat hot on the outside. The AC here varies from
             | 118vac to as high as 126vac (maximum rating.) Right now
             | it's at 122vac. I think my 185 watt number might have been
             | 123.3vac x 1.5a, or maybe it was the previous "xFi Advanced
             | Gateway (XB6)" which was also a chimney.
             | 
             | I am not an ISP. We work remotely -- there is no fiber here
             | yet.
        
               | blibble wrote:
               | for comparison my top of the range i9 gaming pc uses 62W
               | idle
        
               | bongodongobob wrote:
               | Yeah so that means _at most_ it can pull 1.5A. So
               | realistically it probably runs at like 20W or likely even
               | less.
        
           | tenebrisalietum wrote:
           | It sounds like OP works at or is an ISP.
        
       | tristor wrote:
       | I would never buy a cheap UPS. The one time I did so many years
       | ago, it ended up catching fire. UPS fires are the most common
       | cause of datacenter fires, and that's the "good" stuff. Adding a
       | UPS is not a zero-risk action that has only upsides. You need to
       | actually think about it.
       | 
       | At home, I have had a single rack w/ network and server gear for
       | more than a decade and I always run two good quality UPS, that I
       | run a test on annually, tied to two different circuits. My setup
       | now is a bit annoying because I'm renting currently, but when I
       | owned a home prior to my recent move I had an electrician run two
       | 20A Dual Function (AFCI+GFCI) circuits with hospital grade
       | outlets to power the two UPSes in the same room but on separate
       | circuits and breakers at the panel. I don't think that's
       | overkill, but I think anything more would be overkill at home.
       | When I buy a house again, I intend to do the same.
       | 
       | Since buying better quality UPS and testing them regularly so I
       | can replace batteries when needed I haven't had any fires, but
       | using batteries past their useful lifespan can greatly increase
       | risk of fire. Expect that you should replace the batteries every
       | 3-5 years, and that they will cost nearly as much as the UPS
       | itself. If you're not comfortable with that, invest in a quality
       | surge protector instead and figure out how to deal with failures.
       | UPS batteries are a big fire risk, so you need to understand it
       | and work to contain it. Also, keep a good dry fire extinguisher
       | near your rackmount equipment and get it tested annually.
        
         | turtlebits wrote:
         | Can't you buy a UPS with a LiFePO battery, or find an old lead
         | acid one and do a battery swap?
        
           | cptskippy wrote:
           | UPSes with dead lead acid batteries are a dime a dozen.
           | People don't realize or don't both servicing the batteries
           | and toss them out all the time.
        
             | russdill wrote:
             | I love hooking up large lead acid batteries to old UPSes,
             | there's no reason to be limited by the original battery
             | capacity.
             | 
             | However...I discovered why some APC UPSes are sealed and
             | the battery cannot be accessed. I was converting one such
             | UPS which had no monitor interface. Having already opened
             | it up to splice in an external battery, I noticed an empty
             | header for a serial port. Cool. Plugged that into my PC and
             | flash/bang/smoke. Fortunately my PC had a good path to
             | ground and was not damaged. But the UPS had some pretty
             | large burn marks at various points in the PCB and was
             | certainly dead.
             | 
             | It took me a bit to figure out what I did wrong. The reason
             | it went bang is directly related to why there's no user
             | access to the battery, and why there's no external
             | monitoring port. They went cheap on the electronics and did
             | not include an isolation transformer. Any points within the
             | UPS which are "ground", including the battery negative
             | terminal, are actually referenced to the full bridge
             | rectifier, which provides a direct path to live. Ahh...I'm
             | just very glad I didn't touch any of the battery terminals
             | while I had the thing plugged in.
        
         | bongodongobob wrote:
         | Nonsense. UPS's don't pose any sort of serious fire risk. UPSs
         | starting on fire are exceedingly rare. Sure, it's probably
         | happened. People get hit by lightning too.
        
           | silon42 wrote:
           | I'd guess they are certainly safer than a laptop, but it
           | depends on a manufacturer... (I've seen lots of "balooned"
           | laptops, including many Macs)
        
           | tristor wrote:
           | Not to be snarky, but UPS fires are one of the leading causes
           | of datacenter fires:
           | https://duckduckgo.com/?hps=1&q=UPS+Fire+datacenter&ia=web
        
             | bongodongobob wrote:
             | Right and data center fires are extremely rare. Think of
             | how many UPSs are in the wild. The failure by fire rate is
             | probably something like 0.000001%.
        
         | Grazester wrote:
         | After using hundreds, hundreds of very cheap to huge expensive
         | APC UPS' I can say I have never experienced a fire. They have
         | all used lead acid batteries, some as heavy as 50lbs. I have
         | even had to cut UPS' open to remove swollen batteries.
        
         | dheera wrote:
         | Is this specific to Lithium battery UPS units?
         | 
         | For home use I bought a lead acid UPS specifically to avoid a
         | fire. For a 5 hour power outage it makes no difference to me if
         | the UPS powers my machine for 5 minutes or 20 minutes; as long
         | as I can save my stuff and shut down it works for me.
        
         | wannacboatmovie wrote:
         | > I had an electrician run two 20A Dual Function (AFCI+GFCI)
         | circuits
         | 
         | Don't do this. This is a terrible idea if you intend to run a
         | UPS.
         | 
         | > with hospital grade outlets
         | 
         | Complete overkill and waste of money
         | 
         | > UPS batteries are a big fire risk
         | 
         | No they aren't.
         | 
         | Judging by all these incorrect assumptions about electrical,
         | I'd suggest stopping while you're ahead before you burn your
         | own house down.
        
           | bloopernova wrote:
           | > > I had an electrician run two 20A Dual Function
           | (AFCI+GFCI) circuits
           | 
           | > Don't do this. This is a terrible idea if you intend to run
           | a UPS.
           | 
           | Can you please elaborate why someone shouldn't do that? (not
           | who you responded to, I'm just curious about the reasoning
           | behind that statement)
        
             | wannacboatmovie wrote:
             | UPS's are notorious for nuisance tripping GFCI's due to the
             | extensive power filtering they usually have inside. It may
             | not happen right away but is dependent on how 'dirty' your
             | power is and on how sensitive your particular brand of GFCI
             | is. All it may take is a neighbour using his AC or power
             | saw and it could generate a spike large enough to knock
             | your system offline (UPS filters spike to ground, leakage
             | current trips GFCI which needs to be manually reset, UPS
             | runs out of battery because no one's home to restore
             | power).
             | 
             | This advice is specific to the US & Canada where GFCI's are
             | calibrated to trip at 5 mA. In the UK, their RCD's trip at
             | 30 mA so it's less likely.
             | 
             | If you read the fine print for your UPS and/or GFCI they
             | will say not to use them together.
             | 
             | What about AFCI's? Well they are basically nuisance devices
             | by design and most electricians hate them. Do not use
             | unless absolutely necessary by code.
             | 
             | The difficulty comes into play because UPS's, servers, etc
             | are essentially industrial equipment while the code is
             | written for such common residential usages as plugging in a
             | lamp (where a dog will chew on the cord, a good way to
             | start a fire hence a perceived need for AFCI protection.)
             | 
             | What if you're stuck because you want to locate your UPS
             | and equipment in an area where GFCI's are required (like a
             | residential basement)? Well I won't tell you what to do in
             | your own home but I'm sure you can devise a creative
             | solution. :)
        
             | tristor wrote:
             | The issues with UPS products tripping GFCI breakers is due
             | to leakage current that is out of spec for the GFCI
             | circuit, this is almost always caused by the load attached
             | to the UPS, not the UPS itself. While most UPS
             | manufacturers do recommend against connecting it to a GFCI
             | outlet, AFCI is required in all new construction for all
             | circuits and GFCI is required for many circuits, including
             | any circuits in basement areas which necessitates a dual
             | function circuit. Since the original thread is about APC,
             | even though I don't use their products, here's what they
             | have to say on the topic:
             | https://www.apc.com/us/en/faqs/FA369034/
             | 
             | FWIW, running my server and network equipment never caused
             | the breaker to trip erroneously while I was still living
             | there. I sold the house when I moved cross-country for
             | unrelated reasons so I can't say what happened afterwards,
             | but my setup was installed according to code and functioned
             | perfectly fine. I used quality UPS and decent quality
             | network and server equipment. Cheap stuff may be farther
             | out of spec and have more issues with leakage current.
        
               | wannacboatmovie wrote:
               | > AFCI is required in all new construction for all
               | circuits
               | 
               | This is absolutely false.
               | 
               | Though I'm sure you gave your electrician an earful and
               | he did whatever was needed to keep his customer satisfied
               | and happily took your money. Hope those $50 hospital-
               | grade outlets are working well.
        
               | tristor wrote:
               | From: https://www.nyeia.com/where-arc-fault-circuit-
               | interrupter-af...
               | 
               | "For new construction, Section 210.12 (A) of the National
               | Electrical Code states that all 120-volt, single-phase,
               | 15- and 20-ampere branch circuits supplying all outlets
               | must be Arc-Fault Circuit-Interrupter protected in the
               | following dwelling unit locations:
               | 
               | Kitchens, Family Rooms, Dining Rooms, Living Rooms,
               | Parlors, Libraries, Dens, Bedrooms, Sunrooms, Recreation
               | Rooms, Closets, Hallways, Laundry Areas, or Similar Rooms
               | or Areas.
               | 
               | Even though it is not listed, this includes finished
               | basements because once the basement is finished, the area
               | becomes one of the rooms listed above.
               | 
               | Adding to the confusion, most people assume that outlets
               | are only plugs or receptacles. However, outlets is
               | defined in Article 100 of the National Electrical Code as
               | "A point on the wiring system at which current is taken
               | to supply utilization equipment". That means that the
               | requirements for AFCI protection is required in the areas
               | stated above at all 120-volt, single-phase, 15- and
               | 20-amp receptacles, lighting fixtures, switches, smoke
               | alarms, dishwashers, refrigerators, and so on."
               | 
               | So, yes, /technically/ it's not /all/ circuits, however
               | please identify for me a room that's commonly found in a
               | residential property that's not a Kitchen, Family Room,
               | Living Room, Dining Room, Bedroom, Hallway, Laundry Area,
               | Closet or "similar rooms or areas"? Look at the floor
               | plan of most residential properties in the United States
               | and every room noted on that floor plan is on the list.
               | So /technically/ it's not /all/ circuits, so I was
               | /technically/ incorrect, in practice what I said is
               | absolutely true.
               | 
               | Maybe a bit less snark from you and a bit more reading
               | comprehension and you wouldn't come off as such a dick?
        
               | wannacboatmovie wrote:
               | You conveniently left out that few jurisdictions are on
               | the 2020 NEC code cycle when this provision was
               | introduced. New codes do not get adopted everywhere
               | immediately. Your town or city needs to adopt it and that
               | can take many years. So, no, not all new construction.
        
               | tristor wrote:
               | This provision I quoted above is from NEC 2017, not NEC
               | 2020, and NEC 2017 was adopted in my jurisdiction when I
               | had that house built. But, please, continue to tell me,
               | the almost electrician, that both myself and the master
               | electrician I hired to help during the construction of my
               | house are wrong and how you know better, Mr. Unqualified
               | Internet Commenter.
               | 
               | I reiterate to anyone reading this comment thread, hire a
               | certified electrician, get an inspection, don't get your
               | safety advice from random assholes on the Internet in the
               | comments section.
        
           | tristor wrote:
           | > Judging by all these incorrect assumptions about
           | electrical, I'd suggest stopping while you're ahead before
           | you burn your own house down.
           | 
           | For anyone reading this, this person has no idea what they're
           | talking about. Besides the fact that I once considered
           | becoming an electrician and completed my apprenticeship prior
           | to entering the tech industry, it is a published standard how
           | things should be installed in residential properties in the
           | US, called the National Electric Code or NEC.
           | 
           | The NEC 2020 states that GFCI is required (in additional to a
           | general AFCI requirement) for any 125V or 250V receptacles in
           | kitchens, bathrooms, laundry areas, finished or unfinished
           | basements, garages and anywhere within six feet of a sink.
           | Since my server rack was in a closet in a finished basement,
           | it is /REQUIRED/ by code to have a dual-function breaker.
           | 
           | Also, I once again refer you regarding fire risk to simply
           | search "UPS fire datacenter". UPS fires are the primary cause
           | of datacenter fires. But sure, I don't know what I'm talking
           | about, I've only been responsible for multiple datacenters
           | spanning the globe for one of the world's largest hosting
           | providers as part of my career after giving being an
           | electrician a go and deciding against it as a career in my
           | youth.
           | 
           | If anyone is ever in doubt about how to install something
           | that's electrical: 1. Hire a certified electrician and 2.
           | Read the applicable standard, which is the most recent
           | published version of the NEC. Don't listen to people who make
           | rude smart-ass comments on the Internet.
        
       | hedora wrote:
       | I have one of the nicer APC units (for use in offices, not
       | racks). Recently, when the power blipped, it went into backup
       | mode and got stuck there, draining the battery. I had to
       | physically unplug it and plug it back in to get it to turn back
       | on.
       | 
       | I'm not sure if there's a decent UPS brand any more. I get the
       | impression APC has been going downhill since the acquisition.
        
         | newsclues wrote:
         | Eaton
        
           | da768 wrote:
           | Vertiv Liebert
        
           | js2 wrote:
           | No one on this site has a large enough sample size to speak
           | authoritatively about the quality of consumer-oriented UPSes.
           | 
           | In my home right now, I have an APC (Schneider) Back-UPS Pro
           | 1000, Tripp Lite (Eaton) AVR550U, and CyberPower
           | CP1500PFCLCDa.
           | 
           | I purchased the APC in April 2017, the CyberPower in Nov
           | 2020, and the Tripp Lite in Sep 2021.
           | 
           | The APC was originally for all my IT gear but for some reason
           | that load caused it to cycle to battery at random times. I
           | replaced it with the CyberPower which works fine with my IT
           | gear. Meanwhile the APC works fine with my AV gear where I
           | re-purposed it.
           | 
           | Both of those are still on their original batteries which I
           | test every 6 months.
           | 
           | The Tripp Lite I use at my desk and I also test it every 6
           | months, but last month the power went out and the Tripp Lite
           | immediately shut down. The battery had failed w/o warning and
           | the Tripp Lite battery-monitoring is apparently useless since
           | it still thought the battery was good when power was
           | restored, but an actual load test proved otherwise.
           | 
           | When I replaced the battery, the Tripp Lite had a cheap
           | Chinese battery in it. I replaced it with a Duracell
           | (manufactured in Vietnam). I've had less trouble with non-
           | Chinese UPS batteries.
           | 
           | Another fun thing: Tripp Lite has reused the model "AVR550U"
           | for three different UPSes all which use a different battery.
           | Turns out my version uses the quite common APC RBC2 sized 7Ah
           | battery.
           | 
           | Which is all to say: I've had a lot of UPSes over the years
           | and you can't make any claims about any single manufacturer.
           | They all manufacture a range of models and none of us have
           | any actual data about failure rates. The best you can do if
           | you have the expertise is to take one apart and evaluate its
           | design and manufacturing quality.
        
             | da768 wrote:
             | Not necessarily, but reading online you'll quickly find
             | about certain manufacturers frying batteries faster using
             | out of spec charging voltages.
        
           | pastorhudson wrote:
           | Eaton is what I use and it is one of the only ones that
           | provide pure sine wave. It's good stuff.
        
           | tomek_ycomb wrote:
           | 100% agree, but have never had $1k to drop like that on a
           | backup dedicated to my PC ;p.
        
         | csnover wrote:
         | > I'm not sure if there's a decent UPS brand any more. I get
         | the impression APC has been going downhill since the
         | acquisition.
         | 
         | I've noticed a similar thing.
         | 
         | I had a 2005 Smart-UPS tower that never failed, but developed
         | some transformer buzz that was annoying in an office
         | environment--and hey, improved standby efficiency and an LCD
         | panel would be nice--so I replaced it in 2013 with its latest
         | equivalent. This one ran for about nine years and then started
         | rebooting itself randomly, dropping the load each time. (It had
         | no issues transferring and holding a load on battery, and self-
         | test passed.) Its 2022 replacement now uses a non-standard
         | USB-A male-to-male cable, is missing information that used to
         | exist in the LCD menu, seems to have a problem charging from
         | 98% to 100%, and has a broken event log (event 1 is always
         | "Site wiring" and every other event is always "None", even
         | though there have been multiple power events, and there is no
         | site wiring issue). It works, but QA issues are evident.
         | 
         | I'd previously tried a prosumer-grade CyberPower UPS
         | (CP1500PFCLCD) on some other less critical equipment. When its
         | battery failed after two years, it cut power to the load. When
         | the charger failed a few years later, it cut power to the load.
         | It died completely in about six years.
         | 
         | Tripp-Lite's consumer grade stuff seems to work well enough for
         | what it is, but their higher-end equipment seemed to all be
         | designed for environments where noise doesn't matter, which
         | makes it a non-starter for an office. Eaton (their parent)
         | seems the same.
         | 
         | So it would be great to know what is an actually good choice
         | these days. At the moment I'm not in the market for anything
         | and hopefully what I've got will run for another decade, but if
         | it doesn't, I have no good idea about what else to buy today.
        
           | aidenn0 wrote:
           | > I'd previously tried a prosumer-grade CyberPower UPS
           | (CP1500PFCLCD) on some other less critical equipment. When
           | its battery failed after two years, it cut power to the load.
           | When the charger failed a few years later, it cut power to
           | the load. It died completely in about six years.
           | 
           | I've never (n=4) had a stock CyberPower UPS battery last me 2
           | years. 3rd party replacement batteries have all lasted
           | significantly longer than what shipped in the box.
        
           | th3typh00n wrote:
           | > event 1 is always "Site wiring" and every other event is
           | always "None", even though there have been multiple power
           | events, and there is no site wiring issue
           | 
           | Some UPS:es are adamant about wanting live and neutral on
           | specific pins on the power plug and will throw that error
           | message if they're swapped.
           | 
           | If it's a reversible power plug, flip it around. If the power
           | plug can only be connected in one orientation the outlet is
           | likely incorrectly installed (which is not all that uncommon,
           | as 99.99% of stuff will work perfectly fine with live and
           | neutral swapped).
        
       | johnklos wrote:
       | First, it's extra work, but it's possible to configure apcupsd to
       | run a script on events, then use that script to ignore spurious
       | events.
       | 
       | Second, for people who can't necessarily afford either new UPSes
       | or something other than "consumer grade", a good option is to
       | find local sellers, perhaps on Craigslist or Facebook
       | Marketplace, who are selling or giving away old UPSes. Many
       | people and businesses don't bother replacing batteries, so they
       | just buy new devices when the batteries near or reach end of
       | life, and since they're heavy, they often just want to give the
       | hardware away.
       | 
       | New batteries are not expensive. A common 9AH battery for many /
       | most common smaller UPSes costs around $25 USD from Amazon
       | sellers that have 4.5 or more stars.
       | 
       | I've personally never bought a new UPS for myself, yet all of my
       | equipment and everywhere I've set up home Internet equipment for
       | others has UPSes. I've only ever bought batteries. Just a
       | thought.
        
       | underlogic wrote:
       | I have had maybe 10 UPS units over the years but I would never
       | buy another one. I was once severely poisoned by an APC unit with
       | a leaking battery. It released an odorless vapor, had me in the
       | hospital twice before I figured it out. Not a fan of APC quality
       | anymore either. I don't trust the product, don't want to plug it
       | into my equipment. Most everything I use now has a battery or
       | will just reset on power failure anyway.
       | 
       | The model he is referring to is the last UPS I owned and had some
       | very serious QA issues;
       | 
       | https://www.eevblog.com/forum/dodgy-technology/apc-ups-now-w...
        
         | e40 wrote:
         | Wow. What would you use?
         | 
         | We had a bunch of Cyberpowers and they were absolutely crap.
         | The failed at a high rate and had terrible software.
        
           | underlogic wrote:
           | A UPS is really just a car battery and a voltage regulator.
           | Actually the cheaper APC models have no voltage regulator
           | which is why you should avoid them. It's obsolete technology.
           | Modern regulated power adapters are enough just use a strip
           | with a surge protector. If you really need something to
           | protect your gear get a voltage regulator. But if the power
           | drops frequently then maybe you do need a UPS idk. If you
           | really do then the APC enterprise units. But I'd avoid if at
           | all possible
           | 
           | https://www.apc.com/us/en/product-
           | range/61877-liner/?parent-...
        
         | skottenborg wrote:
         | How did you figure out the UPS was the cause?
        
           | underlogic wrote:
           | When I came back from the ER I got sick again. The UPS only
           | had arrived a couple of days before
        
         | atesti wrote:
         | What was this odorless substance and where did it come from?
         | (just curious what to watch out for)
        
           | underlogic wrote:
           | It came from a leak in the battery during charging. Exactly
           | what the gas was is still unknown but it knocked me for six a
           | couple of days after I received the unit. I thought about
           | getting it tested and even suing but it took out my whole
           | apartment and I just had to get rid of it and cut my losses.
           | I was in the ER unable to stand and in quite a state, lost
           | balance and coordination and was incoherent for a while. CAT
           | scan w/contrast, it was a whole production on Thanksgiving at
           | 3am. They monitored me for a couple days and sent me back to
           | the apartment where all the symptoms immediately returned,
           | and then I put it together and looked closer at the UPS.
           | Underneath it was a couple of drops of black liquid that had
           | come from the battery compartment and after returning to the
           | ER again to go throw up some more I went back and took it
           | straight to the garbage. I think it was one of those types of
           | gas that can effect you in the PPM range. Totally odorless.
           | This was the enterprise APC UPS, the model was SUA1500
        
         | NotYourLawyer wrote:
         | > I was once severely poisoned by an APC unit with a leaking
         | battery. It released an odorless vapor, had me in the hospital
         | twice before I figured it out.
         | 
         | X doubt
        
       | NelsonMinar wrote:
       | I once installed apcupsd only to be so appalled by its lack of
       | security design I ripped it out PDQ. It demands to run as root so
       | it can run shutdown (and maybe access the USB?!) and goes
       | downhill from there.
        
       | rubatuga wrote:
       | Seems like your best bet is to use an industrial battery
       | inverter/charger system (Victron Multiplus) for slow-switching
       | (>20ms) and then layer a secondary industrial grade UPS to
       | provide fast switching (<15ms) and shutdown process through
       | USB/serial/network etc. Is it cheap? No, but you shouldn't be
       | using cheap power supplies to protect your more expensive server
       | equipment.
        
       | shmerl wrote:
       | I have no issues with Back-UPS RS 1500MS2 on Linux.
       | 
       | I had to configure an udev rule though for it to set up a static
       | USB device name since that wasn't happening out of the box, but
       | other than that - no problems.
       | 
       | See http://apcupsd.org/manual/manual.html#usb-configuration
        
       | ek750 wrote:
       | I'm kinda sick of buying these cheap lead-acid based UPS units
       | (only tried APC and Cyberpower so far) to have the batteries die
       | in just a couple of years.
       | 
       | Are the lithium-based batteries more durable (probably more
       | dangerous)? Anyone have experience with these?
       | https://www.amazon.com/Xtreme-Power-Conversion-J60-600-Lithi...
        
       | alright2565 wrote:
       | What's interesting is that APS's Windows-only software,
       | Powerchute Serial Shutdown, is actually Java-based, accessed
       | through the browser, and trivially de-compilable and readable.
        
       | secabeen wrote:
       | In my experience, all modern operating systems and widely-used
       | databases handle power interruption well. I can't recall an time
       | where a filesystem or database was corrupted by power loss in
       | decades. Adding a monitoring/shutdown system for basic UPSes is
       | not worth the risk/hassle. I'd just monitor the power directly
       | and let the system fall over when the UPS runs out of battery.
        
         | nayuki wrote:
         | Some SSDs brick themselves in an abrupt shutdown.
        
       | neilv wrote:
       | After many UPSes at home over the years, I currently have only 1
       | (a business-grade rackmount Cyberpower), and once it needs a new
       | battery pack, I'll probably just switch to a surge protector.
       | 
       | My local electric is pretty stable, I no longer run servers at
       | home that need to be up 24/7, most of my work at home is on a
       | laptop with integrated battery backup, I can use my phone WiFI AP
       | mode for backup Internet, UPSes are a pain to move between
       | apartments, and UPSes have a small risk of dangerous battery
       | leakage.
        
       | 1letterunixname wrote:
       | Don't even bother buying used enterprise APC units because
       | firmware updates now require $$$.
       | 
       | NMC2 and NMC3 can't even install proper SSL certs without some
       | shitty Windows-only tool.
        
       | mastax wrote:
       | I'm having exactly the same issue with apcupsd and my APC Smart-
       | UPS X 1500, so it's not just an issue with the cheapo units.
        
       | binkHN wrote:
       | I refused to go down this route; the hours lost in frustration
       | are not worth it.
       | 
       | I purchased a UPS that supports a network management card,
       | basically an overpriced SNMP daemon with an Ethernet interface,
       | and have been happy ever since, since every system can query the
       | status of the UPS.
        
       | Animats wrote:
       | Have low-end UPS units gone lithium iron phosphate yet? That's
       | the battery technology of choice now for non-portable
       | applications. Cheaper and longer-lived than lithium-ion, no
       | thermal runaway risk, about the same energy density per cubic
       | meter, but twice the weight.
       | 
       | Such UPSs are available in small rackmount units.[1] The usual
       | serious players, such as Tripp-Lite, have LiFeP04 battery powered
       | units. Searching for consumer-grade LiFePo4 UPSs turns up many
       | articles on how to replace crappy batteries in UPS units with
       | newer battery technology. The batteries themselves are cheap now.
       | APC doesn't seem to have caught up yet.
       | 
       | This looks like an APC corporate problem.
       | 
       | [1] https://www.falconups.com/ups/lifepo4-ups-sl.htm
        
       | neilv wrote:
       | For most home use, you don't need UPS monitoring.
       | 
       | If you're home when it switches to battery power, the equipment
       | will probably have been protected from any surge, and you'll hear
       | the beeps from the UPS, and can manually shut down equipment.
       | 
       | If you're not home, and the power doesn't come on soon enough,
       | power will be cut to protected equipment, without a surge, and at
       | most the equipment probably only needs the auto-`fsck`.
       | 
       | And because no monitor means that you can have the UPS airgapped
       | for data, there's less theoretical risk of a remote firmware hack
       | causing a fire/explosion or toxic leak.
        