       | bad_alloc wrote:
       | I wish there was some standard way to add DC wiring in parallel
       | to AC. Seems like people who want to do this have to roll their
       | own systems for now.
        
         | amelius wrote:
         | You could use USB wall sockets :)
        
         | msandford wrote:
         | Same here. The problem is that there's no consensus on what
         | voltages. I might prefer 48v for lower losses but you might
         | want 24v since it's "safer" and my neighbor might want 192v
         | since he's already an electrician.
        
           | Szpadel wrote:
           | IMO just using the same voltage as in AC and multi voltage
           | DC/DC adapter would be sweet spot
        
         | PaulKeeble wrote:
         | There are multiple things that we really need to make it
         | viable. A standard for the plug that separates it from any AC
         | standard, a standard voltage and current and then standard DC
         | to DC convertors for adjusting the voltage. I guess also we
         | need a completely different light bulb fitting socket too that
         | only fits DC light bulbs. Lots of different commercial DC
         | convertors of varying sizes to replace the AC convertors in all
         | sorts of devices.
         | 
         | I do wonder how much in practice would be gained given the DC
         | to DC conversions are guaranteed for every device.
        
           | eternityforest wrote:
           | We do have a standard AC-DC converter, USB PPS, which can do
           | most of these use cases just fine. DC-DC versions can be done
           | too if one really wanted.
           | 
           | But running low voltage DC power wiring is still probably not
           | the best plan.
        
         | adrianN wrote:
         | Power over Ethernet perhaps?
        
         | cesarb wrote:
         | There's already a somewhat common standard for DC wiring in
         | homes and offices, though it's probably not exactly what you
         | had in mind: it's Power over Ethernet (PoE), which provides
         | around 48V over standard twisted pair Ethernet wiring, while
         | still allowing it to be used for data.
        
           | ianburrell wrote:
           | PoE is too low power to use for many things that would want
           | DC power. 802.3bt tops out at 71W. You couldn't run a 100W
           | USB-C adapter on it.
           | 
           | Also, PoE is pretty high losses running power over Ethernet
           | cable. The max power at source is 100W. PoE puts in higher
           | voltage for account for the losses which means it isn't a
           | straight 48V input to 48V output.
        
         | JKCalhoun wrote:
         | When I built out a van into an RV, I got to run a new
         | electrical system for it -- one based around the 12V automotive
         | battery.
         | 
         | It turns out that there is a small industry out there that
         | serves both RVs (and boats as well) that is 12V/DC based.
         | Lights, pumps, refrigerators, fans, all running straight off a
         | 12V power bank. "Cigarette lighter" outlets stand in for wall
         | outlets for USB-style chargers, etc.
         | 
         | The 12V/DC battery system in the van is of course charged from
         | both solar on the roof of the van and from the van's alternator
         | (when the van battery is topped off and the van is under power
         | of course).
         | 
         | I did add an inverter to supply 110V/AC for a pair of
         | traditional electrical outlets I installed in the kitchen area
         | of the van/RV. These are primarily used for plugging in wall-
         | wart style chargers for the laptops.
         | 
         | (My Kill-A-Watt suggests that my rice cooker and even the
         | electrical kettle would, just barely, function on the current
         | provided by the inverter but RV-life tends toward minimalism so
         | those extra appliances I've left behind.)
         | 
         | In any event, the whole experience did have me wondering if I
         | could run a parallel 12V/DC electrical system in a new home and
         | do away with a lot of the step-up/down of AC.
         | 
         | Definitely could do with some kind of modern outlet (USBC?)
         | rather than the cigarette lighter outlets, ha ha.
        
         | Gibbon1 wrote:
         | What would be nice is a residential power over Ethernet
         | standard. With standard crimp connections.
         | 
         | Some advantages power limited and low voltage means it's
         | safer[1]. Ethernet means you can control lights and other
         | devices. Smaller diameter wiring means it's cheaper. Not
         | needing a licensed electrician to install it saves $$$.
         | 
         | [1] Can imagine for a non North American not having to deal
         | with 230VAC would be a big bonus.
        
       | amelius wrote:
       | > Dutch researchers managed to reduce total cable length in a
       | house down from 40 metres to 12 metres. They did this by moving
       | the kitchen and the living room (where most electricity is used)
       | to the first floor, just below the roof (where the solar panels
       | are), while moving the bedrooms to the ground floor. They also
       | clustered most appliances in the central part of the building,
       | right below the solar panels
       | 
       | Now this is dedication ...
        
         | kabouseng wrote:
         | That's not great, since entertaining guests it is preferable to
         | have these rooms on the ground floor, and the bedrooms which
         | can be private on the upstairs floor.
        
           | Epa095 wrote:
           | While upstairs has a better view, more light coming in
           | through the windows, and heat rises up (so the bedrooms can
           | be kept comfortable cool). I guess it depends on the house
           | and it's surroundings:-)
        
         | brtkdotse wrote:
         | > 40 metres to 12 metres
         | 
         | So they sacrificed the freedom of design to save EUR100?
        
       | huppeldepup wrote:
       | Something I didn't find in the article is that in AC systems
       | sparks are self-extinguishing because of the zero-crossing.
       | 
       | There are a few domestic circuit breaker teardowns on youtube. I
       | suggest watching one and then asking the question: how can we
       | break a high current _DC_ surge?
        
         | weare138 wrote:
         | High voltage DC circuit breakers are a thing already.
        
           | adrian_b wrote:
           | Yes, but they are more complex, thus more expensive.
        
           | bluGill wrote:
           | They exist, but are much more complex. they do things like
           | pair with an air compressor to blow the arc out.
        
       | guenthert wrote:
       | "Because many modern devices operate internally on direct current
       | (DC)" But notably the high power consumers like electrical stove,
       | air conditioning, washing machines etc. do not. And it's not that
       | with DC throughout there are no conversions. Solar cells' output
       | varies greatly, hence it needs to be DC/DC converted to a fix
       | voltage to be of any use. The same, albeit to a much lesser
       | extend, applies to batteries. Further, there is no one single
       | voltage, AC or DC, which is optimal for all uses. Even for
       | devices which receive DC voltage, e.g. laptops, there are
       | internal DC/DC converters.
       | 
       | Removing the AC/DC conversion seems hardly worth the trouble.
       | High efficiency AC/DC converters can be constructed. It's rather
       | a question on how much one is willing to spend on such.
        
         | kzrdude wrote:
         | With more and more DC generation and consumption on the
         | network, I think the AC mains is becoming very noisy, i.e.
         | there are spikes, which we are not so used to handling.
        
           | Liftyee wrote:
           | That is true. There is a whole field of power factor
           | correction and filtering that tries to reduce the noise
           | injected into the mains (hello, EMC regulations) but some
           | devices do that better than others.
        
         | andix wrote:
         | Most of the high power consumers could run on DC power with
         | only slight modifications (in design, not aftermarket).
         | 
         | Heating elements can run on DC more or less unmodified. Also
         | electric motors can run on DC efficiently (see electric cars).
         | Back in the days 3-phase power was needed to run strong
         | electric motors (very common in Europe, but i think it exists
         | also in the US for factories and businesses). But there are
         | many easy solutions nowadays to just run them on DC.
        
           | Liftyee wrote:
           | > Heating elements can run on DC more or less unmodified.
           | 
           | ..but to get the same power (heat) output you need more
           | current in a low voltage DC system. And power loss in the
           | supply cables scales with the square of current, so you'll
           | need thick (expensive) wiring in the wall or you'll risk the
           | walls becoming an equally effective heating element.
           | 
           | Electric motors that run on DC are either brushed or have
           | extra driver/conversion circuitry to pulse their coils in the
           | right order. Both of these are not perfectly efficient.
        
           | eternityforest wrote:
           | High voltage DC is hard to switch with mechanical switches,
           | and you have to convert it back to AC to run motors(Unless
           | you're willing to accept brushed motors), so it wouldn't be
           | trivial.
        
           | cesarb wrote:
           | > Also electric motors can run on DC efficiently (see
           | electric cars).
           | 
           | It's quite likely that the motors on electric cars (and other
           | efficient electric motors) are actually using an inverter to
           | turn the DC into multi-phase AC and power an AC motor; this
           | allows varying both the voltage and frequency of the AC fed
           | into the motor.
        
         | deng wrote:
         | Yes, you cannot reasonably run these high-power devices on low-
         | voltage DC (12-48V), this is also said in the article. But the
         | reason is not that these devices cannot run on DC in principle,
         | the problem is cable loss. For running devices which need >1kW
         | on low-voltage DC, we are talking at least 20-80A, depending on
         | the voltage. So you need thick cables, which are expensive and
         | hard to deal with (amount of space needed, securing
         | connections, avoiding bending, everything becomes problematic
         | with these cables). Any little mistake done with cabling is
         | immediately a fire hazard.
         | 
         | So in the end, the article says: say good bye to your washing
         | machine, dish washer, electric kettle, electric stove, etc. I
         | mean, the site is called "low tech magazine" for a reason...
        
           | andix wrote:
           | I don't see any future in 12V systems, even in cars (with
           | rather short cable lengths) there are discussions to switch
           | to 48V, like Tesla is doing it in the Cybertruck.
           | 
           | I was thinking more like 200-400V DC systems, that could
           | power most devices, but comes with a lot of challenges.
        
             | deng wrote:
             | Yes, but this is not what this article is about, which is
             | to avoid the loss of efficiency by converting low-voltage
             | DC solar power to AC through an inverter, only to convert
             | it back to low-voltage DC again for most devices. If we are
             | talking high-voltage DC, you'd just replace the old DC-AC
             | conversion with low/high-voltage DC-DC conversion, which I
             | don't think is much more efficient. Also, I wouldn't want
             | to live in a house which runs on high-voltage DC, purely
             | because I don't want to instantly die if I accidentally
             | touch a life wire.
        
               | posterboy wrote:
               | I don't see how that would be any different from
               | unprotected "high" voltage lines, or preferably protected
               | ones for that matter. In house installations around 500V
               | count as Low Voltage in power engineering, by the way.
        
               | deng wrote:
               | That might very well be, but I have touched 240V AC
               | accidentally, and I'm fine. Don't think that would still
               | be the case for 400V DC, whether it counts as "low-
               | voltage" or not.
               | 
               | EDIT: After reading a bit, it seems that the "what is
               | more deadly" discussion regarding AC/DC is much more
               | complicated than I thought, so the above might very well
               | be false...
        
               | mc32 wrote:
               | Above 220/240 it's typically required a person be
               | certified and wear certain fabric types to minimize
               | hazards.
        
               | Dylan16807 wrote:
               | 240V AC peaks at 340V and most systems would rate 400V DC
               | as being pretty similar.
               | 
               | Significant risk of shock, not much risk of arcing.
        
               | andix wrote:
               | I think we need to talk about the definition of "low
               | voltage". In my understanding it's everything below
               | 1000V. Solar power systems often provide a voltage up to
               | 1000V, by serially chaining modules. Running them in
               | parallel with ~50V would require quite massive cables.
               | 
               | Edit: About the danger of DC wires: There are technical
               | solutions to mitigate risks. They may be too expensive
               | though. I think we can reuse some of the strategies
               | electric cars use. It's the only end-user application I
               | know that uses DC powered cables with up to 900V (Lucid
               | Air).
        
               | IndrekR wrote:
               | I (as someone who designs electric and electronic
               | equipment every day) agree. Low Voltage is a very
               | specific term and typically means <1kV AC and <1.5kV DC
               | in the industry:
               | https://en.wikipedia.org/wiki/Low_voltage
        
               | zamadatix wrote:
               | This is a great piece of data, thanks for posting it.
               | Without this comment I would never have realized low
               | voltage referring to ~50 volts or less was primarily a US
               | thing.
        
               | amelius wrote:
               | > I think we can reuse some of the strategies electric
               | cars use.
               | 
               | Sounds like it could be a patent minefield.
        
               | willis936 wrote:
               | Switching losses are less than ohmic losses. A few chips
               | cost less than a lot of copper. The crossover point
               | depends on the cable lengths, cable size, load, and
               | voltage in question.
               | 
               | Let's do a quick example. 16 AWG carrying 12V. 16 AWG is
               | 4 mOhm/ft. Let's say you have a 1200 W load (100 A, 0.12
               | ohm). Ohmic losses per foot of cable are 3%. So if you
               | have a 15 foot cable it will use as much power as the
               | load.
               | 
               | Edit: I think I responded to the wrong comment.
        
               | amelius wrote:
               | 100 amps through 16AWG? Man that's pushing it.
        
               | Dylan16807 wrote:
               | Especially for a 15 foot cable. I'd expect a cable >10x
               | the thickness with <1/10th the resistance.
        
             | tlb wrote:
             | 200-400V DC distribution systems are dangerous, both for
             | electrocution and fire. Though maybe modern GFCI and arc
             | detection breakers could make them adequately safe. Could
             | someone who knows the state of the art comment?
        
             | jbotdev wrote:
             | They've actually had 48V systems in production cars for
             | several years now. Tesla is late to the game on that one.
             | 
             | https://en.m.wikipedia.org/wiki/48-volt_electrical_system
        
           | amelius wrote:
           | > the problem is cable loss
           | 
           | One solution may be to make a cable with a step-up converter
           | at the beginning and a step-down converter at the end.
        
         | mananaysiempre wrote:
         | In-sync AC grids are an engineering marvel; high-voltage AC
         | lines are comparatively lossy due to the skin effect among
         | other things; a frequency of 50 or 60Hz yields what are, by
         | modern standards, comically huge step-down transformers; etc.
         | It's worth considering whether the relative ease of running AC
         | motors makes all the difficulties of AC supply worth it.
         | 
         | (It's worth remembering that the "modern", i.e. 1930s, three-
         | phase power grid is built primarily to power motors on factory
         | floors. I don't know if these are the highest load these days,
         | but wouldn't be surprised if not.)
        
           | VBprogrammer wrote:
           | > It's worth remembering that the "modern", i.e. 1930s,
           | three-phase power grid is built primarily to power motors on
           | factory floors.
           | 
           | Small nitpick, I don't believe 3 phase power was picked
           | primarily because it was convenient for powering 3 phase
           | motors - it was picked because it's convenient for generating
           | and transmission. There is no need for a neutral conductor in
           | a balanced AC transmission system for example and it can very
           | efficiently be converted to high voltage and stepped down
           | again. It also results in modest power pulses though the
           | generator compared to single phase etc.
        
             | tyingq wrote:
             | Feels like it's both to me. 3 phase, 3 wires is optimal for
             | the amount of conductor material needed to distribute it.
             | But it's also optimal for motors for a few reasons. Easy to
             | reverse direction of the motor, self starting without a
             | capacitor, and higher overall power and efficiency.
        
           | algo_trader wrote:
           | If you are building a custom mini grid from scratch, how do
           | you get from batteries/panels to distribution-level 11kv DC
           | without going through AC ?
        
           | quickthrowman wrote:
           | Motors consume around half of the world's electricity, and
           | nearly all of the power consumed by motors connected to the
           | grid is consumed by three-phase A/C induction motors. Motors
           | aren't just in factory equipment, HVAC systems have all sorts
           | of motor driven equipment.
           | 
           | VFDs have made A/C motors far more efficient than one driven
           | by an across-the-line starter.
        
           | tuatoru wrote:
           | The biggest point loads are aluminum smelters. Probably next
           | are electric arc furnaces for steelmaking, the so-called
           | mini-mills.
        
             | bob1029 wrote:
             | Semiconductor factories are not far down the list either.
             | Texas will probably see quite a few come online within the
             | next decade.
             | 
             | When I was working at SAS in ATX circa 2013, the 2
             | manufacturing lines were responsible for something like 10%
             | of the city's average power consumption. I can't imagine
             | the bleeding edge will have improved much - EUV light
             | sources aren't exactly Energy Star compliant.
        
         | coryrc wrote:
         | So all efficient (switching) voltage conversion involves AC.
         | Your stock plug-in DC power supply is actually a AC->DC->AC->DC
         | device yet it's trivial to get above 97% and miniscule
         | quiescent (minimum) load. High-frequency AC isn't a problem for
         | efficiency.
         | 
         | What's NOT easy is efficiently making 60 Hz AC at low quiescent
         | power. Most inverters always burn 2-5% of maximum power with no
         | load, while 1% would be considered far excessive if the output
         | was DC (maybe 0.1% would be generally okay?). Part of this is
         | lack of regulation; consumer devices have low-quiescent power
         | supplies originally because of government mandates and, now,
         | economies of scale. The government mandate didn't apply to
         | inverters so there isn't an initial push to shift to low-
         | quiescent topologies and prevent the first movers from being
         | undercut.
         | 
         | So just for that reason, lower-voltage DC distribution can
         | overall be more efficient if you are off-grid, even if some
         | other portions of the system have increased losses. 120Vdc
         | distribution would be superior from an efficiency standpoint in
         | every way, but you're going to spend a lot on switches and
         | protection equipment.
        
           | calamari4065 wrote:
           | > Your stock plug-in DC power supply is actually a
           | AC->DC->AC->DC device
           | 
           | That is actually not at all how switching converters work.
           | Pulsed DC is not AC. Those are two very different things.
        
         | amluto wrote:
         | > But notably the high power consumers like electrical stove,
         | air conditioning, washing machines etc. do not.
         | 
         | An electric resistance stove (radiant or exposed coil) would
         | work just fine on DC, although, if it's controlled using a
         | TRIAC, that would need to change.
         | 
         | An induction stove uses rather high frequency AC, and that
         | could be generated just fine from a DC supply.
         | 
         | Modern air conditioners use variable frequency drives, and
         | those generally work by first converting the AC supply to DC.
         | 
         | I imagine that many modern washing machines also use some sort
         | of variable frequency drive or DC-powered motor.
        
       | Physkal wrote:
       | Would this make DC appliances cheaper or smaller since there's no
       | need for rectification circuits?
        
         | andix wrote:
         | I don't think it would be significant.
        
           | _fizz_buzz_ wrote:
           | I think it could make a difference. A lot of devices have
           | power factor correction (pfc) now. To draw a current without
           | harmonics from the grid. You wouldn't need a pfc stage
           | anymore.
        
             | andix wrote:
             | Some kind of voltage conversion would be needed anyway.
             | Most electronic devices run at 5V, 3.3V or 1.8V. And that's
             | limiting cable lengths to a few meters (probably less than
             | 5m).
        
               | _fizz_buzz_ wrote:
               | Yeah of course, but the pfc stage boosts the voltage
               | first up above the ac peak voltage and then a second
               | stage steps it down to whatever voltage is needed. If one
               | has a dc grid one doesn't need the pfc stage (but of
               | course still the second stage).
        
       | limaoscarjuliet wrote:
       | All this requires the DC appliances to be the same voltage, as
       | transformers on DC is a tough task.
        
         | _fizz_buzz_ wrote:
         | Most stuff is switched mode nowadays anyway, so this becoming
         | less and less relevant. Not sure if there really are any
         | transformer based appliances in my house anymore.
        
         | Liftyee wrote:
         | Transformers on DC are already a solved problem with various
         | switched-mode converters that can boost or decrease voltages at
         | will. In fact, many AC-DC supplies (phone charger, etc.) are
         | already using such converters, first rectifying the incoming
         | AC. Not needing a bulky transformer makes them smaller and
         | lighter.
        
       | George2515 wrote:
       | That's a clever way to summarize it! The merge commit retains the
       | history of changes in the feature branch, while squashing
       | simplifies the history for the release branch, making it cleaner
       | and easier to follow. It's all about balancing clarity and detail
       | in version control.
        
       | jakedata wrote:
       | Just sitting here speculating, not even a web search yet...
       | 
       | In the USA we have both ground and neutral wires at every outlet
       | along with the hot (120VAC nominal) wire.
       | 
       | Why couldn't we raise the ground wire to +12VDC (or whatever)
       | with regard to the neutral? The ground would have a very
       | sensitive detector so that if electrical conditions exceeded some
       | preset threshold it would collapse to zero nearly instantly,
       | allowing the circuit protection to function as expected.
       | 
       | You could make a plug that only has a neutral and ground pin to
       | tap into the low voltage side, or use all three pins to provide
       | low power standby mode.
       | 
       | Now I'll do a search to find out that it is impossible because of
       | a, b or c reasons or that it has already been patented somewhere
       | and abandoned. Yay Internet...
        
         | tzs wrote:
         | Ground and neutral are tired together at the electrical panel.
        
           | jakedata wrote:
           | That's why this could work - the panel is the logical place
           | to insert the DC supply. If ground and neutral were bonded in
           | multiple places then it would just be a DC short.
        
             | sokoloff wrote:
             | They are bonded there for safety reasons and that bond
             | needs to be low impedance.
             | 
             | The reason is that you don't want to allow a fault which
             | puts a line voltage (120VAC) onto the chassis of a piece of
             | equipment waiting for a human to come along and complete
             | the circuit to ground. So, you use the protective earth to
             | connect to the chassis, such that if a power line ever did
             | contact it, it would be a dead short to ground, which would
             | trip the OCPD (over-current protection device, typically a
             | circuit breaker), clearing the fault.
             | 
             | If you replace this safety mechanism with something that's
             | high-enough impedance to maintain a 12VDC differential,
             | you've eliminated this important safety mechanism in your
             | AC distribution system.
        
               | tzs wrote:
               | I think this would also make another possible fault more
               | dangerous: a break in neutral somewhere between an AC
               | device and the panel.
               | 
               | If there was also a DC device on the same side of the
               | break as the AC device, then you'd have a possible return
               | path for the AC current that goes through the DC device,
               | the ground wire, and the DC power supply.
               | 
               | In addition to that, would it also cause problems with
               | GFCI?
               | 
               | The 12 VDC return current would be on the neutral. I'd
               | guess that a steady DC current on the neutral wouldn't
               | cause problems, but whenever a DC device is switched on
               | or off, or you use a DC device that has a fluctuating
               | instantaneous power need, that should induce current in
               | the GFCIs sensing coil that won't be canceled out by an
               | opposite current induced from the load wire.
               | 
               | I don't know if that mismatch would be long enough or
               | large enough to trip the GFCI.
        
               | sokoloff wrote:
               | GFCIs will trip at ~5mA of current imbalance, so your
               | point is an additional excellent one.
        
         | RetroTechie wrote:
         | Even if plug is polarized (plug goes in only in 1 orientation),
         | you can't assume _any_ of the high voltage wires to be touch-
         | safe. Wiring mistakes (swaps) can  & do happen.
         | 
         | In-house AC systems are designed to remain safe when that
         | occurs. But it prevents using any of those wires in ways like
         | what you suggested.
        
         | _fizz_buzz_ wrote:
         | The GND (or Earth/GND) is there for safety and equipotential
         | bonding. It's not meant to carry current and running current
         | through it will trigger your RCD, because that's how a ground
         | fault is detected. And detecting that is important so when you
         | trip with your hairdryer into the bathtub you won't kill
         | yourself.
        
         | ianburrell wrote:
         | One problem is that many older houses don't have grounding.
         | Half my outlets are ungrounded and I use GFCI to get three-
         | prong plugs. Or the grounding is done through pipes and conduit
         | which aren't suitable for running current.
         | 
         | The standards for grounding make them unsuitable for running
         | current. The ground wire in box are frequently bare. Metal
         | boxes are grounded. The center screw is grounded. If you run
         | current over the ground, those are live.
         | 
         | You have invented a way to electrocute lots of people.
        
       | RetroTechie wrote:
       | Not mentioned so far: AC->DC adapters also provide galvanic
       | isolation. In many power supplies, that electric isolation comes
       | 'for free', as you don't want device(s) connected to high voltage
       | wiring anyway. AC vs. DC as input isn't _that_ big a deal really.
       | 
       | In situations where power source (solar!), storage and most
       | consuming devices are low-voltage DC, just use a DC based setup
       | if more practical.
       | 
       | I'm on a boat & most everything electric here is low voltage DC.
       | But I do have a 12V->230V AC converter when needed.
       | 
       | In short: AC & low voltage DC can live happily side-by-side. The
       | DC vs. AC debate is kind of a moot point these days.
        
       | dang wrote:
       | Related:
       | 
       |  _Slow Electricity: The Return of DC Power? (2016)_ -
       | https://news.ycombinator.com/item?id=28216968 - Aug 2021 (230
       | comments)
        
         | Animats wrote:
         | Yeah, we did this already.
         | 
         | Few devices other than switching power supplies are designed to
         | work over a wide range of DC input voltages. There's an
         | electric pump which will run slowly on an low input voltage and
         | faster at a higher voltage.[1] Those are driven from windmills
         | and solar. It's not cheap. It has to be self-protecting against
         | too high and too low voltages.
         | 
         | [1] https://www.dankoffsolarpumps.com/product/solar-slowpump/
        
       | Johnny555 wrote:
       | If DC in houses became popular, it seems like they'd follow the
       | same model as RV's -- low power devices like lighting, water
       | pump, maybe refrigerator all run on 12VDC, high power devices
       | like air conditioning, microwave, etc run on 120VAC (sometimes
       | inverted from battery).
       | 
       | That limits the high gauge wire to the short run from battery to
       | inverter, otherwise you'd need very expensive and heavy large
       | gauge cable running to those high power devices.
        
         | amelius wrote:
         | Why not step up the DC voltage instead of inverting to AC?
        
           | Johnny555 wrote:
           | It's harder to step DC than AC, you'd probably end up using a
           | switching power supply, which gets you most of the way to an
           | AC inverter.
        
             | amelius wrote:
             | Yes, but once you have DC your losses will be less.
        
         | amluto wrote:
         | I think that, if DC appliances as used in RVs became genuinely
         | popular, they would move to reasonable voltages. 12VDC is
         | absurd. 48VDC would be much, much better.
        