       | 0wis wrote:
       | Interesting subject tackling two important home issues at the
       | same time : ventilation and heat exchange. It seems like a way to
       | get the best of both worlds. However, I do not know why this
       | forum is relevant or interesting. DIY solutions are easily doable
       | but is it really surprising ? I am sure people have done this
       | with old fridge parts, as someone suggest in the last post. Yes,
       | DIY can be cheaper but reliability is key for such systems. Size
       | can also be key.
        
         | notyoutube wrote:
         | Reacting to your first point: As far as I know (western
         | europe), heatpumps mostly are used to heat water to then heat
         | your house, and renovating generally means reducing
         | breathability of the house itself, which, combined with the
         | temp difference, means condensation/mold problems. You then
         | have to correct that by opening windows intelligently or
         | installing air ventilation, and then a heat exchanger to not
         | lose too much heat. Like you say, it seems to be a no-brainer
         | then to instead combine heat pump _and_ ventilation, so that
         | the ventilation itself works with a heat pump.
         | 
         | The only counter-argument I have is that if all the heating
         | were done using ventilation, you might have to live in a very
         | windy house, but I feel like entirely decoupling the two is not
         | the best solution to that problem...
        
           | rocqua wrote:
           | It makes a lot of sense to feed your ventilation output to a
           | heatpump input for energy recovery with an air-source
           | heatpump.
           | 
           | But otherwise I think there is a lot of value in other forms
           | of heating. Specifically in radiative heating. Floor heating
           | is great for that, but other water-based systems are also
           | possible.
        
           | geon wrote:
           | > if all the heating were done using ventilation, you might
           | have to live in a very windy house
           | 
           | Not an issue at all. A properly installed ceiling vent will
           | blow air along the ceiling, where Bernoulli's principle makes
           | the fast moving air stick to the ceiling until the speed
           | drops enough for the higher density to make it sink gently.
           | 
           | https://blog.swegon.com/hs-
           | fs/hubfs/Bild4-1.png?width=1100&n...
        
             | briHass wrote:
             | There's also significant engineering calculations and
             | guidelines/rules about the expected volume of air that is
             | expected to enter/exit vents vs their size and grille
             | restrictions. This is more to prevent loud airflow, but
             | there's also charts for air distribution for room sizes.
             | 
             | Now, most HVAC contractors go by gut feel/rules of thumb,
             | but if you want to pay for it, a well designed system would
             | never be 'windy' or noisy.
        
           | ClumsyPilot wrote:
           | > renovating generally means reducing breathability of the
           | house itself, which, combined with the temp difference, means
           | condensation/mold problems
           | 
           | Look up Passivehouse standard, modern construction can make
           | extremely effocient buildings, but it relies on the building
           | being nesrly airtight, so it must have ventillation.
           | 
           | 'Natural' ventillation naturally steals your heat, it's
           | incompatiable with efficiency
        
         | userbinator wrote:
         | _Yes, DIY can be cheaper but reliability is key for such
         | systems._
         | 
         | If you know what you're doing (not hard to these days with so
         | much information online), and depending on where you live, DIY
         | HVAC can be far more reliable than getting a "licensed
         | professional" who will attempt to overcharge for mediocre work
         | or even scam you.
        
         | Open_erv wrote:
         | There was a period where I considered DIY for such machines
         | impractical. I now think that to diy all the way through is
         | impractical, the design process is too laborious even for those
         | suitably skilled. However once the design is worked out it is
         | actually pretty practical, with a 3d printer. You definitely
         | have to own the printer, they charge way too much to have
         | things printed at cloud services for some reason.
         | 
         | I have pubished my STL files for an earlier version of the TW4
         | energy recovery ventilator. It's totally practical to make your
         | own with a printer, but it would take you a few days of labor
         | time for sure to get everything working nicely.
         | 
         | Reliability is very much on offer even with diy. In reality I
         | have looked at many commercial units and they have serious
         | reliability problems for long term like 5 years or more, and we
         | should be planning for 50 years wherever building tech is
         | concerned, imo.
        
       | mnw21cam wrote:
       | See also https://www.instructables.com/heat-recovery-ventilation/
        
         | schiffern wrote:
         | See also also https://youtu.be/w5sR-0oX1dg?t=184
         | 
         | In this one the heat exchanger construction is closer to OP,
         | with coroplast sheets glued together. However in a follow-up
         | video, he says this was a bad idea for his humid climate.
         | 
         | https://www.youtube.com/watch?v=LiptsaKmq80
        
       | kragen wrote:
       | heat exchangers are pretty important. does anyone have a summary
       | of the high points in this thread?
       | https://ecorenovator.org/forum/showpost.php?p=54888&postcoun...
       | seems to be kostas's summary of their completed build, documented
       | in more detail at https://diyvmc.wordpress.com/ and with an
       | overview video at https://youtu.be/phIWQD5LAcA
       | 
       | i have a couple of big unknowns about ventilation heat exchangers
       | for houses, and i'm wondering if anybody knows the answers to
       | these questions:
       | 
       | - why is everybody using recuperators when a regenerator would be
       | mechanically much simpler? i'd understand if preventing mass flow
       | was important, but in fact this thread says that in some cases
       | they build their recuperators with water-permeable heat exchange
       | membranes in order to _facilitate_ mass flow of water, which is
       | the main mass flow that a regenerator would introduce here. why
       | don 't people use regenerators?
       | 
       | - now that the price of solar energy has fallen so much, and in
       | particular solar panels cost half what they did even a year ago,
       | will house ventilation heat exchangers remain economical?
        
         | nine_k wrote:
         | I suppose that heat exchanger ventilation makes most sense at
         | winter time. Not everybody lives in San Diego, a lot of people
         | live in New York, Boston, Chicago, Seattle, etc, where a winter
         | is a thing.
        
           | genman wrote:
           | Also during hot summer when outside temperature is hotter
           | than inside - you don't want ventilation to bring in hot air.
        
           | kragen wrote:
           | i think heat exchanger ventilation makes roughly the same
           | amount of sense whenever you're spending costly energy to
           | change the temperature of your space, doesn't it? it works
           | just as well to keep summer heat out as to keep winter heat
           | in, and staying cool in summer can be just as critical as
           | staying warm in winter, depending on where you live
           | 
           | the main difference is that you can heat up a house
           | (inefficiently) with a nichrome wire or a gas burner, while
           | cooling it requires considerably more elaborate equipment
           | 
           | but if electricity costs 2C/ per kilowatt hour and daytime
           | electricity is free, will the savings of a heat exchanger be
           | enough to pay for the device?
        
             | spockz wrote:
             | Electricity here is EUR0,30-0,40/kWh after tax.
             | (Netherlands) (For fixed contact, dynamic contacts have
             | bigger variation). That makes it way more interesting to
             | save on energy. Although getting solar panels is still the
             | fastest investment. Heat pumps typically have 10-15years
             | payback time, especially now they are insanely overpriced
             | due to Ukrainian-Russian war and climate goals increasing
             | demand and lowering supply.
        
               | kragen wrote:
               | so when electricity costs drop by 15-20x the payback time
               | will be 150-300 years?
        
             | marcosdumay wrote:
             | The temperature difference most home heaters work on is
             | much higher than the one most home coolers work on.
             | 
             | Using a regenerator to get 5degC of cooling back with some
             | 30% of efficiency probably won't be cost-effectice. But if
             | you have to heat by some 30degC, the numbers change a lot.
        
             | nine_k wrote:
             | Winter has much less sunlight, so powering a heat pump via
             | solar panels + moderate battery becomes much harder. It's
             | no longer mostly free.
        
           | Open_erv wrote:
           | You can understand quantitatively how this goes for different
           | areas using Heating degree days and Cooling degree days,
           | factoring in latent heat in both cases, ideally. There are
           | calculators for this. I made a spreadsheet on my website
           | www.openerv.ca that shows some of how to reckon this, there
           | are links in there to get data.
           | 
           | In Austin, texas, I think you got quite a bit more energy and
           | money saved per year from avoiding cooling costs, but in
           | Ottawa, Canada, you save about 100x as much in winter as you
           | ever could in summer.
        
         | schiffern wrote:
         | >why is everybody using recuperators when a regenerator would
         | be mechanically much simpler?
         | 
         | They exist, search for "ductless HRV."
         | 
         | They're simply a small fan that reverses every few minutes and
         | a heat storage material. They also have wireless ones that
         | coordinate the fan direction between them.
        
           | kragen wrote:
           | thanks!
           | 
           | don't you need at least two fans and two chambers of heat
           | storage material?
        
             | schiffern wrote:
             | That's how the wireless kind works. One unit blows in while
             | a second identical unit (theoretically located across the
             | house) blows out, and they switch roughly every minute.
             | 
             | This balances the airflow, so you don't get non-regenerated
             | (or more accurately, _less_ regenerated) airflow
             | "somewhere else" like you do if you use a single unit.
             | "in thermal regenerators, the hot and cold fluids pass
             | through the same channels in the packing, alternately, both
             | fluids washing the same surface area. In recuperators, the
             | hot and cold fluids pass simultaneously through different
             | but adjacent channels."[0]
             | 
             | So these regenerative-type HRVs alternate the flow
             | direction of the air, using the packing material as a
             | thermal "battery" to warm the incoming fresh air from the
             | outgoing exhaust air.
             | 
             | While they are indeed simpler, my understanding is that
             | they don't really perform well. There's no humidity
             | recovery, the CFM is too low, the cheap units don't do any
             | active pressure balancing, you can't continuously exhaust
             | from bathrooms/kitchens, and the lack of net flow to
             | distribute air throughout the house means you're mostly
             | exhausting the fresh air you just brought in. Not great.
             | 
             | If you're going cheap, skip the regenerator-type and the
             | HRVs altogether and go straight to a jury-rig ERV.[1]
             | Though again, ideally you can run flex duct (or temporarily
             | on the interior, even just dryer hose) to pull exhaust air
             | from the opposite side of the house, and specifically from
             | bathroom/kitchen areas.
             | 
             | However, first you should test your CO2 levels and/or do a
             | blower-door test. Most buildings aren't tight enough to
             | need an ERV anyway!
             | 
             | [0] https://www.thermopedia.com/content/1087/
             | 
             | [1] https://www.youtube.com/watch?v=CnLwJxCbxfM
        
           | mrspuratic wrote:
           | I've just installed a pair of these standalone units on
           | opposite sides of a mostly open-plan 40m2 ground floor. They
           | can run in intake/exhaust/cycle modes, and be paired as
           | primary/secondary for contraflow.
           | 
           | Too early to see energy benefits yet, but one thing that
           | /really/ helps already is kicking both units into intake when
           | cooking on the hob with the hood fan extracting. I should
           | probably finish that hood sensor (looks at sensor sitting on
           | desk).
           | 
           | In trickle/night mode the rated performance is "up to 90%"
           | (at 1.2W and 15m3/h in unspecified test conditions). These
           | ones require a 165mm diameter hole, so the heat exchanger
           | cross section is ~2.7 times the 100mm version, and presumably
           | more efficient.
           | 
           | I also installed (refurb, old house) a recuperative MHVR
           | upstairs. This type has two fans for separated permanent
           | intake and exhaust channels. The alternative in my country is
           | knocking 7000mm2 holes in the walls (aka passive
           | ventilation). I have to meet various building requirements as
           | a refurb to qualify for energy upgrade grants.
        
             | schiffern wrote:
             | > one thing that /really/ helps already is kicking both
             | units into intake when cooking on the hob with the hood fan
             | extracting
             | 
             | Not sure how much good regeneration is doing[0], but it
             | sounds like it put a band-aid on your problem of inadequate
             | make-up air for the vent! :D
             | 
             | Do these standalone units recover heat only (HRV) or heat
             | and humidity (ERV)?
             | 
             | [0] https://news.ycombinator.com/item?id=38743885
        
               | mrspuratic wrote:
               | I have no external heat recovery system, so yes it's
               | exactly zero while I'm cooking - but a reasonable way to
               | maintain air quality in an open plan, one of my goals.
               | 
               | The house also has new external wall insulation and other
               | upgrades, so it's rather more airtight than before
               | (though not formally tested just yet). Otherwise they run
               | in synchronised cycle mode for heat recovery and air
               | movement.
               | 
               | I'm not well versed in all the subtleties of theory and
               | current technology, but I don't think regenerative and
               | true ERV go together. If condensation forms in the unit
               | on the exhaust cycle I'd guess does contribute a little
               | to the recovered heat?
               | 
               | These units are BSK Zephyrs, with one heat mass component
               | (ceramic honeycomb) and one fan inline in a telescopic
               | duct. To prevent condensation issues they are fitted with
               | a 2deg slope outwards, and a humidity sensor with
               | settable thresholds to purge high humidity internal air
               | at full rate (equivalent to about 1.2 air changes/h for
               | me).
        
               | Open_erv wrote:
               | They all are capable of doing so under some circumstances
               | with limited efficiency, because as the air exits the
               | house and cools down at some point water condenses out of
               | the air onto the regenerator media. Then it evaps again
               | when flow reverses.
               | 
               | However if you want maximal efficiency you want to add
               | some zeolite 3A adsorbent, which you can sort of do
               | yourself I am pretty sure. You just put some through a
               | coffee grinder, put the regenerator in a garbage bag with
               | it and shake it to get the powder inside the regenerator.
               | It's not idea but it'll certainly help. I tried this with
               | a thermal wheel of comparable size with silica gel and
               | measured the result with AHT10 sensors and it worked
               | pretty good actually.
               | 
               | Zeolite lasts longer but you need more. Obviously you
               | gotta try not to get the powder everywhere by getting
               | excess off etc.
        
               | mrspuratic wrote:
               | Interesting. With EWI and internal insulation the
               | telescopic duct is nearly maxed out as the total wall
               | thickness is close to 500mm, but 50% of that is empty
               | space. I though I might be able to get a secondary heat
               | mass into that in future.
        
         | andbberger wrote:
         | commercial systems often use rotary regenerators
        
       | jnsaff2 wrote:
       | This dude built their own and got bad mold problems
       | https://youtu.be/LiptsaKmq80?feature=shared
        
         | keep_reading wrote:
         | Exactly my concern... Just buy the Aprilaire 8100 and don't
         | risk mold...
        
         | zug_zug wrote:
         | Fascinating video. There was a comment on his video asking
         | "Wouldn't this introduce the same amount of humidity/mold as
         | opening a window?"
         | 
         | Curious if anybody has any more insight.
        
           | geon wrote:
           | There could be some issue with condensation. The moisture
           | from the indoor air could get trapped and leak.
        
           | aifooh7Keew6xoo wrote:
           | I think the issue is that when the heat exchange occurs one
           | way, the HRV is effectively a condenser.
           | 
           | Moisture builds on the heat exchange surfaces of the heat
           | exchanger, particulates, spores, etc. in the air deposit
           | nutrients and viable life in the crud, it thrives and
           | multiples right into the incoming airstream for your
           | residence.
           | 
           | When the window is opened the air mixes without a surface for
           | condensation and there's much less immediate deposition so
           | there's not an enriched medium to sustain accelerated growth
           | entirely in the air stream, but it still probably occurs to
           | some extent in a more diffuse manner that produces a
           | significantly lower ambient spore/toxin/particulate load
        
         | thadk wrote:
         | Wow, even just that bit about mold being able to colonize a
         | dehumidifier without its own MERV/HEPA filter is an important
         | and hard to realize insight.
        
         | schneems wrote:
         | Ive been deep down the HVAC rabbit hole. You really need 3
         | separate systems to do it right:
         | 
         | - ERV - Dehumidifier - HVAC
         | 
         | And basically no regular installer does it right. Lots of
         | efficiency nerds over at Green Home Builders, subscription
         | required.
        
           | samstave wrote:
           | Should throw in a UV bath as well - to kill any airborne
           | spores/other critters.
        
             | schneems wrote:
             | It's been a long time since I looked into it, but IIRC the
             | exposure time doesn't make sense in a duct. RealSexyCyborg
             | talked a lot about this during the pandemic. Though that
             | analysis was limited to the Covid virus.
             | 
             | Also to watch for: Some solutions produce irritants like
             | ozone. Not to say they aren't appropriate, just that they
             | don't come risk free.
             | 
             | It would be a good question for that forum for sure.
        
         | leoedin wrote:
         | It seems that the problems he had were in summer. There's many
         | climates where HRVs are only really needed in winter - in which
         | case those problems wouldn't happen.
         | 
         | Basically, as long as the outside air is drier than the inside
         | air, an HRV will work well. The moment the outside air contains
         | more moisture, ventilating will just drive up the humidity of
         | your space - causing many issues.
        
       | walterbell wrote:
       | For winter WFH in a rental, there aren't many commercial options
       | for energy efficient ventilation to keep CO2 at reasonable levels
       | for cognition. DIY HRV with coroplast can be customized for small
       | spaces.
       | 
       | For those with more room, an exhaust duct can transfer heat to
       | cold intake air, https://www.loudawson.com/17884/how-to-build-
       | air-cross-flow-.... Commercial units start around $1K+,
       | https://www.sylvane.com/search/results/?keywords=hrv.
       | 
       | One can also combine a DIY enclosure with commercial parts, e.g.
       | crossflow, https://www.aliexpress.us/item/3256801499168685.html
       | or ductless,
       | https://www.aliexpress.us/item/3256805773352155.html.
       | 
       | ERV pros/cons and review of $500 Panasonic FV-04VE1 ventilation
       | fan: https://doctorpapadopoulos.com/in-depth-advantages-and-
       | disad... & https://www.amazon.com/Panasonic-
       | FV-04VE1-WhisperComfortTM-V....
        
         | TheWoolRug wrote:
         | In a rental where you can't cut through the walls introduces
         | challenges. I wonder if anyone has created a DIY window unit
         | that incorporates a "ZEHNDER COMFOAIR 70" which is a small
         | contained HRV unit that has c02 detection and can ramp fan
         | speed to match co2.
         | 
         | https://www.smallplanetsupply.com/small-planet-blog/2020/6/6...
        
           | andbberger wrote:
           | you can hookup the panasonic unit to a window manifold for a
           | portable AC and put some insulation board over that. that is
           | the only reasonable solution I have found for the states
        
             | aifooh7Keew6xoo wrote:
             | I've had good success adding various utility and
             | ventilation feed throughs in rentals with sliding glass
             | door inserts, including large ducts for various HVAC
             | experiments.
             | 
             | I start with a board and cut/slot it so it fits neatly into
             | the top and bottom tracks, then I move the latch receiver
             | to the board, zip a few screws through the board where the
             | holes won't be noticed.
             | 
             | The glass door opening becomes a bit narrower, and I can
             | cut as many holes as I want in that little bit of wall.
             | 
             | If it's painted white it usually ends up looking better
             | than most of the corporate maintenance work on the
             | building.
        
           | walterbell wrote:
           | Bionaire Everfresh (circa 2005) $150 window HRV was
           | discontinued, https://www.youtube.com/watch?v=OcVowAsYVI4
           | 
           | $300 option from Alibaba,
           | http://mistersustainable.blogspot.com/2021/08/another-
           | mini-e...
           | 
           | $700+ options, https://old.reddit.com/r/hvacadvice/comments/w
           | dl0mn/do_windo...
           | 
           | OpenERV design (writeup pending), https://x.com/open_erv
        
         | sarchertech wrote:
         | The CO2 cognition studies are almost definitely wrong. The
         | military has done numerous studies over the decades with much
         | much higher CO2 levels with none of the reported cognitive
         | results reported more recently.
         | 
         | The CO2 cognition studies show huge results. It's virtual
         | impossible that none of the military CO2 studies would have
         | picked this up with much higher CO2 levels.
         | 
         | Also navies the world over have been running submarines for
         | decades with astronomically high CO2 levels with no reported
         | cognitive deficits.
         | 
         | Whatever these recent CO2 cognitive decline studies are
         | measuring it's not coming from CO2.
         | 
         | One of the commonly citied cognitive decline studies shows a
         | 50% reduction in cognitive ability at 1,400ppm. Submarines
         | routinely operate at much higher levels and there was a study
         | done where they exposed subjects to 40,000ppm for 2 weeks with
         | no measurable cognitive decline.
         | 
         | Here's a good summary from an old HN comment
         | https://news.ycombinator.com/item?id=19863319
        
           | JoshGG wrote:
           | Hi. It would be interesting to read these military studies
           | could you provide some citations or links?
           | 
           | Are they published in reputable journals?
        
             | sarchertech wrote:
             | If you read the comment thread I linked to, you can find
             | links to most of them.
             | 
             | The real kicker for me is how absurdly high the effect is
             | in the recent studies. You should basically see A students
             | failing tests when the teacher closes the window.
             | 
             | You should see huge swings in standardized test scores
             | based on building ventilation.
             | 
             | Companies with good ventilation, should absolutely dominate
             | their markets.
             | 
             | And nuclear submariners operating at 10,000 ppm should
             | basically be non functioning if there is any kind of dose
             | dependent effect (which the studies in question say there
             | is).
        
           | porkbeer wrote:
           | Reminder that the military held that 4 hours sleep was plenty
           | for a century, and had data to justify it.
        
             | jorvi wrote:
             | Yeah, I'm usually a very scientific man deferring to
             | studies over personal feelings, but I can literally feel
             | the mental fog clear up by the minute if I open a window on
             | the afternoon in my study/work room after forgetting to do
             | so in the morning.
             | 
             | Hell, if I have a day where I am quasi-forced to spend most
             | of it in musty rooms, I get a guaranteed headache.
        
               | sarchertech wrote:
               | There are so many things other than CO2 that can affect
               | your feeling of mental fog. In addition the placebo
               | effect is very very real.
               | 
               | ISS astronauts are routinely living in a 5000ppm
               | environment. If the size of the effects of these studies
               | were real, they'd be noticeable.
               | 
               | The most commonly cited study shows that 1400ppm cuts
               | basic decision making ability by 25% and complex decision
               | making ability by 50%. The study also shows a dose
               | dependent response.
               | 
               | So how are people routinely operating at nearly 5 times
               | that level for weeks at a time with no noticeable
               | decline?
               | 
               | Results this large should by very easy to detect by
               | simply measuring the CO2 levels at multiple SAT test
               | taking sites and comparing scores.
               | 
               | Even without looking, an effect this large is the kind of
               | thing that would jump out at the College Board or any
               | other standardized test creator anytime they're looking
               | through their data to normalize scores or detect
               | cheating.
        
               | jorvi wrote:
               | Here in The Netherlands for classrooms we have
               | regulations that aim for a classroom to stay below 950ppm
               | CO2. I think almost every high school kid can remember
               | how drowsy a full, poorly ventilated classroom would get.
               | 
               | Like I said I'm usually a scientific man but this is such
               | a basic thing that anyone with any daily life experience
               | would immediately recognize this 4000ppm (or whatever) as
               | wrong.
               | 
               | Humans are also quite sensitive to noticing when a room
               | is "stuffy", so, yeah.
        
               | maxerickson wrote:
               | What's the typical temperature change associated with
               | opening the window?
        
               | cameronh90 wrote:
               | Stuffiness is mostly a function of humidity.
               | 
               | The problem with these casual discussions about CO2
               | levels is they don't control for other factors. Opening a
               | window definitely wakes you up, but is it the cold breeze
               | or the CO2?
        
             | sarchertech wrote:
             | As far as I know the army said (and still says) 4 hours is
             | enough short term in the field not routinely.
             | 
             | If you're saying they suggested soldiers only need 4 hours
             | of sleep long term, do you have any citations for this?
             | Links to the studies they used to justify it.
             | 
             | Because you can read the studies on CO2 and judge the
             | methodology yourself.
        
       | a1o wrote:
       | Wtf are the Ads that replace the images attached to the forum
       | posts?
        
       | zug_zug wrote:
       | Love the idea. Curious if there's any maximal theoretical
       | efficiency. It seems to me that if you had a wide pipe with a
       | narrow pipe inside (each going different directions) that you
       | could theoretically have a system that transfers heat with no
       | loss.
        
         | upofadown wrote:
         | You can in theory extend the length of a counter flow heat
         | exchanger to get whatever efficiency you want. In practice,
         | such a long heat exchanger would transfer significant amounts
         | of heat to/from its environment. So then you are limited by how
         | well you can insulate things.
        
           | Open_erv wrote:
           | This is approximately correct, except for one big problem
           | with counterflow exchangers, which is frost. Even the
           | membrane types still frost up. What you really want is a
           | regenerator, either a thermal wheel or a fixed matrix
           | regenerator, if you really want maximal efficiency. And it
           | should be what they call the total sorption type, so it has
           | some adsorbent in it. Even then the latent efficiency could
           | be improved with a better adsorbent, the industry standard is
           | zeolite 3A. It's good because it lasts. Silica gel becomes
           | slowly inactive as it adsorbs other stuff that clogs the
           | adsorptions sites basically.
           | 
           | But the adsorbent only starts adsorbing at about 60% RH. So
           | in some cases that actually leads to efficiency loss,
           | compared to some kind of ideal adsorbent that adsorbed at any
           | differential.
        
       | doctorhandshake wrote:
       | Dang. Read a comment in this discussion pointing out that an
       | always-on ERV would work well in bathroom / laundry. I just
       | installed a Panasonic ERV for a whole (~500sq ft) space and a
       | Panasonic whisperquiet vent fan turned down to about the same CFM
       | as the ERV in the bathroom as well. Missed opportunity to
       | simplify, consolidate, and make more efficient the necessary
       | moisture control in the bath by solely having the ERV there.
       | 
       | GOLogic homes[1], IIRC, use a ducted ERV with return from bath,
       | laundry, and kitchen, and supply to bedrooms.
       | 
       | 1 https://www.gologic.us/
        
       | scotty79 wrote:
       | Shouldn't it also recapture moisture as well?
        
       | Open_erv wrote:
       | I'm the OpenERV guy. It's been a long road and it's not very open
       | source any more I'll admit, however I did publish a bit
       | Wikifactory article with all the cad etc. for a quite efficient
       | window mount unit. I now have the know how to boost the flow
       | through that thing by 2.5x or so so it could actually be a viable
       | product/machine. However it's not a good business proposition.
       | 
       | There is a whole class of energy recovery ventilators called
       | decentralized, ductless or sometimes push-pull which are quite
       | amenable to DIY. All you need is a good reversible fan and the
       | regenerator and a pipe.
       | 
       | I have shared elsewhere how to 3d print a regenerator. I use a
       | 0.3 mm nozzle and it takes about 24 hours to print a regenerator
       | that can do about 45 cfm at about 80 percent sensible efficiency.
       | Basically just take a cylinder in Cura of the desired diameter,
       | and use lines infill, no top layer, no bottom layer. That's
       | basically it. Make the lines as thin as you can and the line
       | spacing as small as you can while getting the desired airflow.
       | About 2.7 mm on center spacing was about right for me and a
       | typical fan with 6.5 mm stall pressure. The operating point was
       | about 3.5 mm h2o and 45 cfm at maximal fan power.
       | 
       | These devices do capture some water vapor during cold weather
       | because the water vapor condenses on the heat exchanger then re-
       | evaporates.
       | 
       | I have tried sprinkling zeolite and silica gel in there to get
       | good latent heat recover as well and it seems to work pretty
       | well. You don't need much, only about 5 grams of silica gel, more
       | for zeolite 3A molecular sieve.
       | 
       | I have built two window mount units. One for myself, the mega
       | sized one, which there are pics of on my twitter (@open_erv) and
       | also one for my friend Alex, whose landlord wouldn't let him use
       | it, so I sold it for the cost of the parts.
       | 
       | It took forever to sell that thing even at the cost of the parts,
       | so clearly window mount units are not a great business
       | proposition. Also for other reasons, mostly people don't think of
       | them as long term propositions so they aren't willing to amortize
       | the cost of manufacturing a good machine over long periods.
       | 
       | There is one called the purifresh, for windows too.
       | 
       | The ductless models for houses include the lunos e2 for about
       | $1800 CAD and only 25 cfm, and the blauberg Vento (there is
       | another related one called Twinfresh), however I don't believe
       | their noise or efficiency claims, and I have investigated.
       | 
       | There are many cheap chinese knockoffs and some of them aren't
       | too bad Holtop makes one. But mostly they are very poor.
       | 
       | Ultimately I would like to make a hackaday or something that
       | explains how to do all this, with a raspberry pi pico etc. Also
       | an anemometer based on thermistors and the hot wire technique is
       | useful to regulate flow, any extra flow in either direction hurts
       | efficiency.
        
       | aurizon wrote:
       | A number of youtubes pop up.
       | https://www.youtube.com/results?search_query=DIY+recuperator
       | 
       | and the goog has a few more.
       | https://www.google.com/search?q=DIY%2Brecuperator&rlz=1C1CHB...
        
       | symlinkk wrote:
       | Why is HN obsessed with air quality?
        
       | serpix wrote: