[HN Gopher] Why does the USA use 110V and UK use 230-240V? (2014)
       ___________________________________________________________________
        
       Why does the USA use 110V and UK use 230-240V? (2014)
        
       Author : dilawar
       Score  : 159 points
       Date   : 2023-08-29 09:48 UTC (13 hours ago)
        
 (HTM) web link (electronics.stackexchange.com)
 (TXT) w3m dump (electronics.stackexchange.com)
        
       | mhandley wrote:
       | As a Brit, the best thing about 230v is being able to run a 3kW
       | kettle to make my tea. I took this for granted until I moved to
       | the US.
        
         | kccqzy wrote:
         | It's possible to ask an electrician to install a 240V outlet in
         | the US and then get a UK-spec kettle. You just need to make
         | sure the kettle doesn't care about the frequency difference
         | (probably not), and the hot-hot vs hot-neutral difference (also
         | probably not).
        
           | bluGill wrote:
           | Possible, but the outlet will have a different plug. Most
           | window air conditioners use that type of outlet, and some
           | garages will have it for hobby equipment. I don't think you
           | can legally install a UK (or EU) outlet in the US even though
           | everything that plugs into it would be just fine on our 240V
           | power (a few clocks won't work right, but they won't be
           | harmed or harm anything)
        
             | Kirby64 wrote:
             | Presumably, you would chop off the plug on the UK/EU
             | kettle, and replace it with your own NEMA 6-20 plug. No
             | need to install a UK/EU plug in your house. Also works good
             | in case you need to use some sort of weird industrial
             | equipment that needs 240V.
        
               | teamonkey wrote:
               | Or just use a travel adapter
        
         | TrueGeek wrote:
         | The difference really is night and day between a US and UK
         | kettle.
         | 
         | The worst part of the British system though (although I don't
         | think this has anything to do with voltage, IDK) is there is
         | nowhere to plug-in your razor, hair clippers, hair dryer,
         | toothbrush, curling iron, etc. etc.
        
           | pmlnr wrote:
           | That's building regulations, sadly. Sockets need to be
           | multiple meters from splash zones, but there's an exception
           | for shaver sockets, which have their own transformer, limited
           | amps, and have a plug that looks very similar to the non-
           | grounded EU plugs.
        
             | tialaramex wrote:
             | Yeah, both bathrooms in my (UK) home have such sockets, I
             | don't actually use them, the electric toothbrush gets
             | charged by this desk instead, but they exist.
             | 
             | Regulations change over time, this home's bathrooms are all
             | interior, with fans to evacuate moisture, and the toilets
             | accordingly have internal overflow+, both these features
             | were not legal when my parents home was built.
             | 
             | + Historically for a residential toilet in the UK if the
             | water rises above the intended maximum level in the tank,
             | it just runs into a pipe to the outside of the building, in
             | principle you can now see what's wrong and it's not
             | dangerous... but, if you don't fix it promptly this results
             | in a stain on the building exterior, as well as potentially
             | wider water damage, plus it can freeze in mid-winter which
             | isn't good. But wait, a toilet has a very obvious place to
             | dump unwanted water, it's connected to the sewer and if
             | _that_ is broken you 've got much more serious problems. So
             | a modern toilet tank just re-uses the flush mechanism to
             | dump excess water the same place as everything else. This
             | elegant solution, already needed in some commercial
             | applications, was I believe made legal in newer residential
             | building regulations maybe in the 1980s.
        
               | allendoerfer wrote:
               | Thank you, now I have even more highly specific but
               | useless information about British homes. It will sit next
               | to my knowledge about why you guys (used to) have two
               | faucets.
        
               | Symbiote wrote:
               | They still mostly choose to have two taps in the
               | bathroom.
               | 
               | Part of the reason I emigrated.
        
             | rdsnsca wrote:
             | You don't use GFCI's in the UK?
             | 
             | https://www.canadianhomeinspection.com/home-reference-
             | librar...
        
               | blue_cookeh wrote:
               | Yes - though we call them RCDs and they're typically
               | located in the consumer unit. Up until recently they'd be
               | shared across several circuits (a "split" or "dual" RCD
               | consumer unit). Nowadays regs are pushing for each
               | cicruit in the consumer unit to be protected individually
               | by their own RCBO (almost the same thing as an RCD/GFCI)
        
           | bemusedthrow75 wrote:
           | No, we can still do that -- I have a dual-voltage shaver
           | point next to my bathroom sink with my electric toothbrush
           | plugged in.
           | 
           | There's a famous, common 20VA fixture by Legrand with a
           | distinctive symbol. I asked an electrician about this last
           | year. Most electricians will still fit them.
           | 
           | It won't supply a hairdryer or a pair of curling tongs,
           | probably. Not that you really want such things in a bathroom
           | or without an earth pin.
        
             | TrueGeek wrote:
             | Yeah, it's fine for me as all my stuff is rechargeable and
             | cordless anyway. But my wife needs her hairdryer. In the US
             | any plugs that could get wet are GFCI [1] so you just wait
             | for it to dry out and then push the reset button.
             | 
             | I've rarely had it happen in the bathroom, even with
             | outlets right next to a sink. But I had an outlet at ground
             | level outdoors that would trip during heavy storms
             | sometimes. We fixed it by putting a physical cover over it.
             | 
             | 1: https://en.wikipedia.org/wiki/Residual-current_device
        
               | bemusedthrow75 wrote:
               | Yes. New houses and rented properties in the UK have to
               | have an RCD now as well. But we have the additional EU
               | building codes.
        
         | [deleted]
        
         | the_mitsuhiko wrote:
         | With induction stoves getting more popular that's less of an
         | issue nowadays.
        
           | swarnie wrote:
           | Still, putting the stove on to make a cup of tea seems wrong.
        
             | ikekkdcjkfke wrote:
             | Nobody heard of Quooker?
        
             | ThatMedicIsASpy wrote:
             | yeah but it is 5 times faster than a kettle
        
             | the_mitsuhiko wrote:
             | That seems purely emotional. An induction stove heats
             | faster than a kettle at almost the same efficiency.
        
               | Tuna-Fish wrote:
               | No, it really does not. A typical induction stove has
               | ~2kW of power on each element, and is ~20% less efficient
               | at heating water than the resistive kettle.
               | 
               | This makes it about half as fast at boiling water.
        
               | oblio wrote:
               | You made me check and adjust my other comment:
               | 
               | https://www.aeg.co.uk/kitchen/cooking/hobs/induction-
               | hob/ikb...
               | 
               | 3.7kW for the main element.
               | 
               | Also, why would it be less efficient? Due to the
               | distance?
        
               | Tuna-Fish wrote:
               | Note that the 3.7kW element can only provide all that to
               | a single vessel if it covers the entire area of the
               | element.
               | 
               | The resistive element submerged in the water dumps very
               | nearly 100% of energy into the water. The stove heating
               | the kettle has many more sources of loss, but mostly that
               | it first heats a piece of metal, which is not fully
               | submerged in water.
        
               | the_mitsuhiko wrote:
               | In theory, in practice the induction heating on a regular
               | pan is faster than my kettle by almost three times. YMMV
               | on type of kettle and induction hob used. But it
               | generally means that if you live in the US and you have
               | an induction hob, there is absolutely no reason to buy a
               | kettle.
        
               | rightbyte wrote:
               | You might want to decalcify your kettle.
               | 
               | Edit: Wait. Are you using a frying pan to heat tee water
               | to make it faster?
        
               | the_mitsuhiko wrote:
               | My experience with US induction stoves is limited but I
               | believe it can also deliver 3.5kW on boost. My induction
               | stove boosts to 3.8kW for heating which beats my kettle
               | significantly. I also measures the efficiency and it's
               | quite comparable.
        
               | Tuna-Fish wrote:
               | What is the power of your kettle?
        
               | the_mitsuhiko wrote:
               | 2200 Watts.
        
               | londons_explore wrote:
               | A British kettle on 230 volts boils enough water for a
               | cup of tea in about 45 seconds. (3 kilowatt heater, 300
               | ml of water, theoretically takes 33 seconds, but slightly
               | longer because it has to heat the body of the kettle too)
        
               | bloopernova wrote:
               | I wonder if it's possible to replicate that circuit in a
               | USA house but still stay within code. I'd love to make my
               | tea faster!
        
               | dboreham wrote:
               | Pretty much. My office building was formerly a
               | woodworking shop and has wiring for 220V. Long ago I
               | bought a laser printer on eBay. The seller omitted to
               | mention it was a 220/240V model (probably why it was
               | cheap). Laser printers unlike most appliances are not
               | dual voltage because the fuser is run directly off the ac
               | supply line. So I wired in a 6-20 outlet and changed the
               | plug. Worked fine for many years. I also have a table saw
               | running from a 6-20 outlet. There is a 6-15 NEMA type
               | that presumably would provide a UK compatible supply. I
               | think the problem might be how to provide in-wall cabling
               | that's to code for 220V. In my case I already had conduit
               | with THHN wire.
               | 
               | Not necessarily to code, consult your electrical engineer
               | and lawyer before doing your own wiring, etc.
        
               | rootusrootus wrote:
               | > I think the problem might be how to provide in-wall
               | cabling that's to code for 220V
               | 
               | That's no problem, standard romex nm-b is rated up to
               | 600V. The only real difficulty in doing that in most US
               | homes is that it's all or nothing. You'd have to upgrade
               | all receptacles on the circuit to 240V. Depending on when
               | your home was built, the kitchen might well have several
               | circuits for the wall receptacles (even just one circuit
               | per receptacle, not terribly uncommon in my area), which
               | makes converting one of the circuits to 240V pretty
               | trivial.
               | 
               | Given how many appliances these days use switching power
               | supplies capable of a wide range of voltage, I wouldn't
               | be totally surprised if it was possible to wire an entire
               | house with nothing but 6-15 or 6-20 receptacles and not
               | have too much difficulty sourcing compatible appliances.
        
               | londons_explore wrote:
               | Most _kitchen_ appliances require the right voltage. They
               | normally have a heater or motor driven direct from the AC
               | voltage.
               | 
               | Most devices you'd use outside the kitchen usually will
               | work on any voltage - with notable exceptions being
               | vacuum cleaners, washing machines and fan heaters.
        
               | rootusrootus wrote:
               | For sure you'd want to be careful. My Kitchenaid stand
               | mixer would certainly be unhappy if it were plugged into
               | a 240V outlet, but Kitchenaid makes a 240V version that I
               | could replace it with. A lot of work, but technically
               | doable.
               | 
               | Probably about as likely as wiring up DC receptacles
               | throughout the house. Zero.
        
               | bluGill wrote:
               | I believe that US code requires a dedicated circuit for
               | all 240v outlets. Only 120V outlets can be chained. The
               | only people who use 240v outlets are planing on using all
               | the power it can provide, if they want a second outlet
               | they want a second circuit as well.
               | 
               | Check with your local codes of course. Even if the local
               | codes allow it, your building inspector may not.
        
               | mindslight wrote:
               | 12-2 NM/Romex is fine for 240V (120V+120V), and is
               | commonly used for things like large ACs, heaters, etc.
               | Mark the white wire with red electrical tape at both ends
               | (or really any color besides white/grey/green, but avoid
               | black because while technically correct it just blends in
               | as regular electrical tape).
        
               | TheSpiceIsLife wrote:
               | I use a Panasonic flatbed microwave to heat precisely the
               | volume of water I want by filling the tea cup(s) I want.
               | 
               | Two minutes on high (1100 watt microwave output from,
               | IIRC 1800 watt input) per cup. So usually two minutes for
               | the one cup of I intend to drink.
               | 
               | Every electric kettle I've ever owned has a minimum
               | volume of at least two cups. Who bother heating two cups
               | if I'm only going to drink one at a time.
               | 
               | Tasmania (AU), 240v / 100amp supply to residential is
               | standard.
        
               | londons_explore wrote:
               | Any kettle with a flat bottom (no exposed heating
               | element) can be used with far less water than the 'min'
               | line - and some models don't have a min line at all.
               | 
               | All new kettles have boil-dry protection as well, so they
               | won't be damaged with no water at all.
        
               | londons_explore wrote:
               | Install an A/C socket in your kitchen. Then buy a British
               | 240 volt 3 kilowatt kettle from eBay and wire on a US A/C
               | plug (NEMA 6-15) - hooking the brown and blue wires from
               | the kettle to the two line pins, and the green/yellow
               | wire to ground.
               | 
               | This would be both code legal, safe and functional.
               | 
               | It would also be possible to use a clothes dryer socket
               | (NEMA 14-30), but you should install a smaller than usual
               | breaker for the circuit (15 amps), since the british
               | kettle normally has a 13 amp fuse in it's plug, but a
               | NEMA plug does not contain that.
        
               | bloopernova wrote:
               | Sweet, I had no idea it would be that straightforward.
               | Thank you for the information!
        
               | zoomablemind wrote:
               | I wonder how does this compare to boiling water in a
               | regular coffee mug in microwave oven?
        
             | CalRobert wrote:
             | To be honest for the many years I lacked a proper stovetop
             | kettle it felt wrong to not have the whistle. Though I also
             | missed the auto-shutoff.
        
             | googlryas wrote:
             | Huh? That's how people did it for all of eternity until
             | about 75 years ago.
        
               | bemusedthrow75 wrote:
               | We drink an unbelievable amount of tea. Firing up the hob
               | each time would be silly, when you can fill a kettle to
               | the minimum and have boiling water in an incredibly short
               | time. Not much more than half a minute with a good modern
               | kettle.
        
               | rootusrootus wrote:
               | That sounds like a good use case for an insta-hot tap. No
               | filing anything, always ready to go.
        
             | wil421 wrote:
             | Isn't that the traditional method with a kettle that
             | whistles?
        
           | mhandley wrote:
           | We have an induction stove too and it's great. But the kettle
           | is still significantly faster at boiling water.
        
             | oblio wrote:
             | I'm kind of surprised by this. An induction stove turns the
             | entire kettle into a resistive element so water boils super
             | quickly.
             | 
             | At least with EU induction stoves, so 230V.
        
               | rootusrootus wrote:
               | > At least with EU induction stoves, so 230V.
               | 
               | US induction cooktops/stoves are almost always 240V,
               | unless you get a little countertop burner.
               | 
               | > I'm kind of surprised by this.
               | 
               | As am I. The first time I put a small pot of water on my
               | induction cooktop and turned it on maximum power, I
               | laughed out loud. If I'm only doing enough for a cup of
               | coffee or tea, it starts boiling so fast you don't want
               | to step away.
        
               | [deleted]
        
               | mhandley wrote:
               | Ours is a Smeg model. The two large rings are 2.3kW, with
               | a outer booster ring to 3kW. The problem is if I'm just
               | boiling water for my tea with a saucepan, only the inner
               | ring is triggered. I can put a large pan on there and get
               | 3kW to match the 3kW kettle, but then I've got to warm a
               | large metal pan too, whereas the kettle has very little
               | thermal mass and is lightweight and easy to fill too.
        
           | Tuna-Fish wrote:
           | An induction stove is still really inefficient at heating
           | water, compared to an electric kettle with the resistive
           | element in the water and 3kW of power.
        
             | the_mitsuhiko wrote:
             | There is a small difference but not much. I compared my
             | 230V Kettle with my 400V induction stove and it's within 5%
             | or so. Obviously it depends a bit on what pot you use. I'm
             | guessing most losses come from the lack of insulation on
             | the metal pot.
        
             | oblio wrote:
             | Why? I'm not sure I understand the logic.
             | 
             | For example this: https://www.emag.ro/plita-cu-inductie-
             | aeg-hob-hood-60-cm-ikb... (in the EU), at max power can
             | supposedly reach 7.3kW.
             | 
             | Edit: Checked per element, max 3.7k, more than enough
             | anyway.
        
               | vel0city wrote:
               | For the induction cooktop, there's circuitry to drive the
               | induction system, which then creates magnetic fields,
               | which then interacts with the metal pot, which gets hot
               | and heats the water on one side while radiating heat into
               | the air on the other. There's a lot of stages for losses
               | here.
               | 
               | On an electric kettle, there's just a heating element,
               | often directly bathed in the hot water.
               | 
               | There's absolutely less losses with the electric kettle,
               | so for a 3kW kettle and a 3kW induction cooktop the
               | kettle is _slightly_ more efficient. _Slightly_.
        
             | beeforpork wrote:
             | Hmm, I measured it once (temp increase over time, computed
             | back into watts, compared to a watt meter on the induction
             | cooker), and I found that of the 3,5kW I put in, 80%
             | actually convert to temperature increase in the water. That
             | is not too bad, is it? Are electric kettles more efficient?
        
             | andersa wrote:
             | They should make turbo kettles that hook up to 3 phase
             | power like a stove. That seems like it would be fun. Why
             | stop at 3kW, when you can have 11?
        
           | doublesocket wrote:
           | My in-laws have fried three different induction hobs boiling
           | a kettle on them. Good quality brands too, they just can't
           | seem to cope with frequently being set to max.
        
           | myrmidon wrote:
           | Are people actually using induction stoves for tea, though?
           | 
           | For me, a big selling point of the kettle is that you don't
           | have to clean it and stow it after every use, so I would
           | still use the kettle even if it was slower (maybe no longer
           | for pasta or when cooking in general though)...
           | 
           | edit: I guess you could just get a teapot that is induction-
           | compatible, didn't think of that.
        
             | PrimeMcFly wrote:
             | You don't really have to clean a pot either if you just
             | used it to boil water.
        
               | fireflash38 wrote:
               | Mostly just descaling, but cleaning it with soap and
               | water isn't going to do much about that - you need an
               | acid like vinegar or citric acid.
        
           | bowsamic wrote:
           | There's no chance I'm bothering with getting out a stovetop
           | kettle every time I want a tea. Far easier to just have a
           | separate kettle
        
             | teamonkey wrote:
             | You don't put the kettle away, it lives on the stove!
        
         | CalRobert wrote:
         | If you use an induction hob, a classic stovetop kettle (the
         | kind that whistles!) will allow you to boil water quickly. The
         | large ring on my last hob was 3kw.
        
           | iso1631 wrote:
           | How 1950s!
        
             | CalRobert wrote:
             | I'm not in my seventies but I do have fond memories of the
             | kettle whistling as a kid.
        
           | xavdid wrote:
           | TIL about the word "hob". Americans call it a "cooktop" or
           | "stovetop" or "range"
        
             | rootusrootus wrote:
             | Nitpick: a cooktop is just the burners, a range is an
             | appliance with burners and an oven. It's relatively common
             | on newer houses to separate them. E.g. I have a 36 inch
             | induction cooktop and a completely separate double wall
             | oven in another area of the kitchen.
             | 
             | AFAIK stovetop is also sometimes used when people mean
             | cooktop, though in my area it's more often a casual
             | reference to the burners of a range. I'm sure that
             | convention varies wildly across the country.
        
               | CalRobert wrote:
               | I always just called it the stove.
        
             | lol768 wrote:
             | I still find it very odd they call the central heating
             | boiler/heat pump a "furnace".
             | 
             | A furnace is what you use to make clay set into a pot!
        
               | sib wrote:
               | "Kiln"?
        
             | [deleted]
        
           | BaseballPhysics wrote:
           | Not worth it. A temperature controllable kettle that shuts
           | itself off and can keep water warm is both incredibly
           | convenient and far more safe.
        
             | shawabawa3 wrote:
             | lots of new induction hobs have "boil detection" and auto
             | shut off, fwiw
        
               | BaseballPhysics wrote:
               | So I just need to upgrade my current induction stove to a
               | newer model? That seems reasonable... ;)
        
             | rootusrootus wrote:
             | I have a temperature controllable "kettle" (tank) under my
             | sink connected to a tap and I get water at 195F. I agree on
             | the convenience. They are pretty common.
        
             | CalRobert wrote:
             | But no whistle! Good point on safety though
        
         | zeroonetwothree wrote:
         | Now that I have a 5kw induction cooktop I can boil water
         | incredibly fast. However I'm not sure it's that useful since
         | it's not like I'm standing there watching it, so whether it's 1
         | min or 5 min doesn't matter.
        
           | laurencerowe wrote:
           | I definitely notice the difference in speed between a Uk and
           | US kettle.
           | 
           | In the UK I put the water on then while it's boiling get a
           | mug and tea bag and then the kettle is boiled very soon
           | after.
           | 
           | In the US I generally wonder off as the kettle takes a couple
           | of minutes longer.
        
           | secondcoming wrote:
           | Sometimes you need an emergency cup of tea
        
           | fragmede wrote:
           | If it took 15 seconds, you'd stand there and watch it.
        
           | bluGill wrote:
           | I have a really old infrared range that takes 20+ minutes to
           | boil a pot of water. Believe me when it takes that long it
           | does matter. (it is on the list to replace, but there are
           | higher priorities in this house to fix first, and only
           | limited budget)
        
         | 1vuio0pswjnm7 wrote:
         | Those electric kettles in the US boil water _really slow_ when
         | one is used to 230v.
        
           | vehemenz wrote:
           | As an American, I find the boiling speed of 1L in an electric
           | kettle to be remarkably fast compared to drip coffee or
           | boiling on the stove. Granted, that says more about my
           | expectations than the actual speed.
           | 
           | Generally I use an insulated 4L kettle that stays warm all
           | day, so it heats up very quickly when needed and somewhat
           | negates the issue.
        
             | ianburrell wrote:
             | I find with electric kettle that I use the right amount of
             | water since there are markings for volume. It also heats up
             | to the right temp for coffee instead of to boiling. Both
             | mean that electric kettle is faster than on stove. I like
             | that it will maintain right temp for the second pour for
             | coffee.
        
         | amelius wrote:
         | From the article:
         | 
         | > USA uses 230-240 VAC, too. The only difference is that we
         | ground it in the center, creating "split" phases, reducing the
         | peak voltage relative to ground and making it easier to
         | interface low-power loads. But high-power loads (stoves, water
         | heaters, clothes dryers, etc.) operate across the full voltage,
         | reducing the current required.
        
         | greggsy wrote:
         | The power companies know this, and time their cutovers from
         | Europe with the end of Eastendets, which is when people turn on
         | their kettle for a cup of tea before making dinner. (I'm not
         | sure if that's still a good hint, but it certainly was ten or
         | so years ago.)
        
           | seanw444 wrote:
           | Tom Scott's video on this is interesting, as a side note.
        
             | nickt wrote:
             | Guy Martin did a good 3 part TV show earlier in the year
             | 
             | https://www.channel4.com/programmes/guy-martins-great-
             | britis...
        
           | nickt wrote:
           | It's called "TV pickup", and Wikipedia has a good article
           | explaining it, especially the bit about using pumped storage
           | to meet demand in seconds.
           | 
           | https://en.wikipedia.org/wiki/TV_pickup
        
             | iso1631 wrote:
             | Less important now. Back when 17 million would tune in to
             | watch Coronation Street 3 times a week it was a much bigger
             | thing. It's rare to get half that for legacy live TV
             | outside of specific major broadcasts (The Euro 2020 final
             | pulled in 30 million) -- the 10th most watched show of 2022
             | only got 8 million and the soaps are lucky to get 6 -
             | inlcuding those watching time-shifted.
        
         | rootusrootus wrote:
         | As an American, I have a faucet at my kitchen sink that will
         | give me water at 195F. That takes care of nearly all my needs
         | for truly hot water. When I do need the last few degrees to get
         | a roiling boil, my induction cooktop has a 3700W burner that
         | will do it in a hurry.
        
           | sib wrote:
           | We have the same. The system has a high-end water filter
           | which then exits into a split, one outlet of which goes to a
           | room-temp tap and the other into the heater, so we have both
           | filtered "cold" and hot water.
        
           | wffurr wrote:
           | That sounds really dangerous. My hot water is set to 120degF.
        
             | oaktowner wrote:
             | We put one in 15 years ago and use it every single day.
             | Sorry for the commercial link, but
             | https://insinkerator.emerson.com/en-us/insinkerator-
             | products... is an example. It's great to have near-boiling
             | water on demand.
        
             | rootusrootus wrote:
             | It's just one tap at that sink, clearly identified, in
             | addition to the regular hot & cold water taps. I don't run
             | my main hot water tank at 195F, that would be dumb.
        
               | hughes wrote:
               | So you have an auxiliary heater at the tap? How is energy
               | delivered to this system?
        
               | rootusrootus wrote:
               | Yep, I have a separate tap at the kitchen sink which is
               | connected to a small (about 3 liters IIRC) tank
               | underneath. I have it set to 195F, though it can be set
               | as high as 210F. There is a receptacle in the cupboard
               | under the sink where it plugs in.
        
               | LUmBULtERA wrote:
               | I'm curious, do you know how many kwh that uses in a day?
        
           | throw0101b wrote:
           | > _As an American, I have a faucet at my kitchen sink that
           | will give me water at 195F._
           | 
           | The building code for the province of Ontario (Canada) states
           | that delivered water cannot be higher than 49C (120F);
           | SS7.6.5.1. Maximum Temperature of Hot Water:
           | 
           | * https://www.ontario.ca/laws/regulation/r04023
           | 
           | An exception is given for dish-- and clothes washer outlets.
        
             | buildsjets wrote:
             | No. The law you quoted limits the maximum temperature of
             | hot water supplied by fittings to fixtures.
             | 
             | It says nothing about fixtures that increase the
             | temperature of water and dispense it, and does not limit
             | the temperature of dispensed water. Instant hot taps are
             | both legal and commonplace in Canada.
             | 
             | https://ca.zipwater.com/
        
           | nullc wrote:
           | Best appliance I've ever owned.
        
           | hot_gril wrote:
           | 195@ tap water coming from a dedicated tank is not a common
           | American thing, in case someone is wondering.
        
           | tiborsaas wrote:
           | How many accidental burn injuries you or your guests have?
        
             | rootusrootus wrote:
             | Zero. The 195F tap is not the same one you use for normal
             | hot & cold water. The normal hot water in our house is set
             | to 140F (we do not have any small children or elderly, if
             | we did I might dial it down to 120F).
        
             | pimlottc wrote:
             | To be clear, in the US the "instant hot" tap (when present)
             | is separate from the main adjustable-temperature faucet.
             | It's normally off to the side and visually distinct. It's
             | usually much smaller and provides a limited amount of water
             | from a pre-heated tank under the sink.
        
         | kccqzy wrote:
         | And yet people have 36kW water heaters and they can't boil the
         | water!
         | 
         | https://www.homedepot.com/p/Rheem-Performance-36-kw-Self-Mod...
         | 
         | /s
        
         | wongarsu wrote:
         | It's probably the most remarkable difference. It's interesting
         | how houses are wired for 10-20A of current everywhere,
         | regardless of voltage. You'd assume that since European houses
         | are mostly wired for 16A then US houses would be wired for 32A
         | (or the other way around, if you know US houses wired for 15A,
         | you would assume the European wires for 8A). But curiously
         | that's not the case.
         | 
         | Ignoring the UK with their 13A/30A rings for a moment, since
         | their wiring is unique.
        
           | eutectic wrote:
           | Resistive losses are related to current (I^2 R), so you need
           | thicker wires to deliver the same power at a lower voltage. I
           | guess it was decided that it wasn't worth the expense.
        
             | wongarsu wrote:
             | Sure, obviously. But you'd expect power requirements to be
             | more or less the same, and the ideal wire diameter to be
             | dependent on voltage. But instead what happened is that the
             | wire diameter is more or less constant, and Europe just
             | uses more powerful electrical devices.
        
               | rootusrootus wrote:
               | > Europe just uses more powerful electrical devices
               | 
               | Aside from kettles? I guess maybe some people have
               | electric heaters? What else pulls enough power that the
               | extra voltage will matter? Vacuums maybe, but no, those
               | are limited to 1600W.
        
               | wongarsu wrote:
               | Just looking up my local (German) retailer:
               | 
               | - Irons are commonly 2000-3200W (3200W is 14.5A at 220V)
               | 
               | - Portable Induction Stovetops are 3000W
               | 
               | - Deep Fryers are 2000-3000W
               | 
               | - Hair Dryers are 2000-2500W
               | 
               | And of course some things are connected via 3-phase 400V
               | (3 220V phases, because of the 120deg phase offset that's
               | 400V between any two phases)
               | 
               | - actual oven + stovetop combinations, about 7000W for
               | the stovetop, plus 1000W for the oven
               | 
               | - many tankless water heaters, 5000W-24000W seems common
               | 
               | The most impactful in day-to-day use are probably kettles
               | and hair dryers, but with stovetops and water heaters
               | there's probably a big difference in the prevalence in
               | gas vs electrical, and tankless vs boiler simply due to
               | wiring.
        
               | rootusrootus wrote:
               | That's a good list, thanks. I'd be interested to know
               | what the experience is like between a 120V hair dryer and
               | a 240V model. I don't have enough hair to worry about
               | such things, but my wife does, and it seems like her hair
               | dryer gets hot enough that she usually turns it down a
               | bit anyway.
               | 
               | The 'industrial' level appliances are probably less of an
               | issue, because the wiring run is limited and you can
               | customize it however you need to. I could go down and buy
               | a 36kW electric tankless water heater today and wire it
               | up without any difficulty. Though it would probably be
               | worth upgrading my 200A panel in that case.
               | 
               | Ranges sound like they're probably pretty similar.
               | Typical modern electric ranges in the US are about 10kW.
               | 
               | Three phases would be handy for reducing the cost of
               | wiring, though. Cost me $1500 USD _just for the wire_
               | when I ran four new circuits last year. Couple of them
               | were 50A, which is partly why it was so expensive, but
               | mostly it 's just that copper is $$$. Any bigger than 60A
               | and I'd switch to aluminum.
        
               | wongarsu wrote:
               | I don't have first-hand experience with the difference in
               | hair dryers either, but I imagine it's mostly air
               | velocity? With more power you can turn more air scalding
               | hot, meaning you can offer higher fan speeds without
               | compromising temperature.
        
               | fragmede wrote:
               | Also consider: your wife might not be the kind of woman
               | who would use one on high. Pain tolerances among women,
               | like men, vary.
        
           | rspoerri wrote:
           | If you increase Ampere you must increase the width of the
           | cable, or it will overheat. If you increase Voltage you must
           | increase the insulation around the cable.
        
           | sbradford26 wrote:
           | Largely this is resolved by US houses having a lot more
           | circuits. My bathroom has a dedicated 20 amp (2.4 kW) circuit
           | for the outlets and a separate 15 amp (1.8 kW) circuit for
           | the lights. Every bedroom in my house has its own 15 amp
           | breaker. The kitchen has 3 20 amp breakers for different wall
           | outlets, a 15 amp breaker for the lights, then a 30 amp 240v
           | (7.2 kW) breaker for the cooktop, and a 20 amp 240v (4.8 kW)
           | breaker for the oven.
           | 
           | For the a typical US house the standard feed into the house
           | is 200 amps at 240v. So 48kW of power coming in we just
           | segment it down a lot more.
        
             | bialpio wrote:
             | It starts to become annoying when you have a home office
             | for 2 people though. 2 PCs + 4 monitors and some random
             | things in a room can start approaching the wattage limit.
             | Especially given that I think it's not too common to have
             | one circuit per room (anecdata: my house has one circuit
             | for all outlets per story; not counting bathroom and
             | kitchen which I believe are mandated by building code to be
             | separate).
        
               | hajile wrote:
               | Lots of smaller (kw) circuits is safer than a few very
               | large circuits. The NEC in the US actually stipulates
               | that you must use different receptacle styles for higher
               | ampacities specifically because it is less dangerous. If
               | you run a small appliance on a 30-40amp circuit, you run
               | the risk of that seemingly safe appliance pulling the
               | full 40+ amps required to trip the breaker
        
               | Symbiote wrote:
               | Britain solves this with fuses inside appliance plugs.
               | 
               | The continental European system doesn't really solve it,
               | as far as I know, so you have thicker wires on low power
               | appliances than you would in the USA.
        
               | sbradford26 wrote:
               | The US also has fused plugs but their are not widely used
               | for some reason. I see them mostly on Christmas lights,
               | but I have also seen it on some small home electronics
               | like a window fan and air purifier.
        
               | bialpio wrote:
               | Not sure if I understand - can you clarify? Did you mean
               | that a normally safe 1.5kW appliance runs the risk of
               | cooking itself if it's connected to a 40amp circuit? If
               | yes, then sure, that makes sense.
               | 
               | > Lots of smaller (kw) circuits is safer than a few very
               | large circuits.
               | 
               | Not fully convinced about the safety aspect but it
               | definitely feels more convenient (can selectively turn
               | rooms off if you need to work on something) - if I'm ever
               | opening the walls, I'm going to switch to that approach.
               | At the very least, I want to have a dedicated 20amp
               | circuit in the home office...
        
               | sbradford26 wrote:
               | Largely yes a 1.5 kW device (a 12.5 amp space heater for
               | example) is less safe on a 40 amp circuit. Since if it
               | fail pulling more load than designed but not truly
               | shorted the breaker may not trip. But if you put that
               | space heater on a 15 amp circuit it would most likely
               | trip the breaker. As other commenters have said the UK
               | addresses that risk with fuses in the plug.
               | 
               | Also I recently redid my kitchen and I added an
               | additional 20 amp circuit just for the kitchen island
               | outlets and it has been super nice.
        
               | bialpio wrote:
               | Are safety concerns alleviated here by GFCI breakers? In
               | what cases could this appliance pull more amps than it
               | was designed for? I know it's not required for circuits
               | outside kitchen and bathroom, but I was thinking about
               | just replacing all the breakers with combined GFCI/AFCI
               | ones (especially given that my circuits are so old that
               | there's no ground on them, in which case code I believe
               | mandates that the outlets are GFCI-protected and labeled
               | as "no ground").
        
               | sbradford26 wrote:
               | So the risk would be reduced. Since if the failure causes
               | a electricity to travel anywhere other than the neutral
               | it will cause the gfci to trip. A scenario where a device
               | would pull more power would be a short developing in a
               | heating element reducing its resistance. So it would just
               | pull more power but all of the power is still going to
               | the neutral and wouldn't trip the GFCI.
               | 
               | Also with replacing all your breakers it can increase
               | safety. But first the breakers are not cheap. Second it
               | can lead to a lot of nuisance trips, albeit that is
               | better than it used to be with modern breakers.
        
               | bialpio wrote:
               | Gotcha, so I guess it'll only protect from electrical
               | hazard but fire hazard is still going to be there...
               | 
               | Breakers are probably going to be a bit cheaper and
               | easier than opening all the walls to redo the circuits
               | though...
        
               | sbradford26 wrote:
               | Yeah your AFCI in theory is supposed to help reduce fire
               | risk. Since failures like that cause arcing. But yeah it
               | will be around $60-$80 per breaker, but there is
               | definitely cheaper than ripping open walls to re-run
               | wires.
        
               | sbradford26 wrote:
               | Yeah sadly having separate circuits for each room is not
               | required by the NEC to the best of my knowledge (and
               | might be overkill depending on the situation). Usually
               | though best practice is to have a separate circuit though
               | for each bedroom. Depending on how your outlets are wired
               | it might be possible to split them off onto separate
               | breakers relatively easily though.
        
           | rootusrootus wrote:
           | 32A capable wiring is much more expensive. And if we are
           | being honest, the number of modern appliances that need more
           | than 1800W is very small outside of the kitchen. If it were a
           | common problem people would be installing 6-20 receptacles,
           | but that's pretty rare. I have exactly one, and it's in the
           | garage.
        
         | sph wrote:
         | I'm struggling to understand how the British grid works, as an
         | Italian transplated to UK. IIRC in Italy most residential
         | circuit breakers have a limit of 3.3 kW, so it's pretty easy to
         | trip it with a few appliances running, and we don't even use
         | electric kettles that much.
         | 
         | Yet in Britain, with a 3 kW kettle, I've never managed to trip
         | it, with a combination of laundry machine, electric oven,
         | microwave, dishwasher. Is there no circuit breaker limit?
        
           | laurencerowe wrote:
           | That sounds almost as bad as what we have to deal with in the
           | US!
           | 
           | I live in an early 20th century apartment in San Francisco
           | and I quickly learned not to run my 1.8kW kettle at the same
           | time as my 1.2kW microwave as it would consistently trip the
           | power.
           | 
           | More annoying is when the fridge compressor motor starts up
           | while running either as that also trips the power.
        
             | unethical_ban wrote:
             | I just moved from a place where, if I ground my beans and
             | then turned on the kettle or toaster, I could hear the
             | motor slow down.
        
           | rickboyce wrote:
           | If you want a deep dive this video made by a British
           | electrician is worth a watch https://youtu.be/hZN6hiGLtrE
           | 
           | In a perfect world a ring circuit is a clever invention - it
           | offers a circuit that can safely deliver about 7.3kW with
           | hardly any more copper than normally could deliver about
           | 4.6kW.
           | 
           | However in practice they have a hidden failure mode - if you
           | break the ring they will carry on working apparently without
           | problem except it's quite possible that you now have
           | overheating cables in a wall somewhere. In the real world
           | houses are full of changes (both DIY and professional) that
           | inadvertently break the ring and it's not at all uncommon to
           | see in a house with even modest refurb works having been
           | done.
        
           | MisterTea wrote:
           | Going from memory but this is an artifact of WW2. There was a
           | copper shortage so they decided to save on wiring costs by
           | running only a few high current circuits through the whole
           | house. The appliance plugs are instead fused as any fault in
           | the appliance would happen after the plug. This is why UK
           | plugs are all fused - they are the final branch circuit over
           | current protection device. I actually like the idea.
        
           | jonatron wrote:
           | We have ring circuits, which are typically on 32A breakers.
        
             | iso1631 wrote:
             | And it's great, until the ring is broken. If a ring becomes
             | disconnected, you then have a single 4mm circuit rated at
             | 18A carrying 30A.
        
             | sph wrote:
             | 3000 W / 230 V = ~13A, does this mean I could run two 3kW
             | kettles and still have 1.3kW spare before everything shuts
             | down?
             | 
             | That's massive.
        
           | sbuk wrote:
           | When when the UK was rebuilding the housing stock post WW2,
           | ring mains (or circuits) were designed to both increase
           | consumer safety and to combat the anticipated post-war copper
           | shortage. This design allows for high integrity earthing and
           | greater power per unit of floor area for a given cable size
           | than a radial circuit. Most white goods (Dishwashers, washing
           | machines, etc.) are locally fused and often ovens are on a
           | separate ring with their own fuses in the distribution board.
           | This is why you rarely trip the circuit. It can be done
           | though.
        
           | dotancohen wrote:
           | > I'm struggling to understand how the British grid works
           | 
           | Like most things, understanding the history helps. The ring
           | circuit was designed because it uses less copper than other
           | methods - and copper was scarce after WWII. Almost all other
           | design decisions either come directly from the idea of saving
           | copper, or the idea that there are not enough Legos to step
           | on so the electric plug must substitute.
        
           | dfawcus wrote:
           | Post WW2 for newly built small flats, ring mains were
           | designed to save on copper (as it was in shortage). The
           | intention was to allow for 3-bar electric fires to be
           | operated as 13A loads, and be moveable between rooms.
           | 
           | Rings are more complex to test, and have nasty failure modes.
           | I'd argue that they should only be used in said small flats,
           | and that 20A bus/radial runs should be used in larger builds.
           | i.e. any modern house, rather than a flat. Said run the
           | supplying all of the sockets in any given room, it does
           | though require a larger "consumer unit".
           | 
           | The rings have a 30A (or now 32A) at the "consumer unit"
           | (distribution fuse box) with two cables running in a loop
           | around all sockets in the circuit. The cables have
           | traditionally been 2.5mm, and open clipped, so rated at
           | around 27A (based upon preventing overheating).
           | 
           | Hence when operating properly, the wiring in the circuit can
           | carry 54A, the circuit is fused at 30A (or 32A) to protect
           | the cable, and an individual load is limited to 13A (being
           | the highest cartridge fuse commonly available).
           | 
           | Have a look here:
           | https://www.diydoctor.org.uk/projects/cablesizes.htm
        
           | mytailorisrich wrote:
           | There may be several circuits, and they all have independent
           | breakers. Certainly, an electric cooker/oven will be on its
           | own circuit as it has higher requirements.
           | 
           | Then, standard ring circuit is 32A, and individual sockets
           | are limited to 13A (via fuse in plug). So you will need to
           | have 2 kettles on on the same circuit and then add a third
           | device pulling not an insignificant amount of power (32 -
           | 2x13 = 6A) before the breaker trips. This will be safe if the
           | ring circuit is not faulty as they are usually wired with two
           | 2.5mm2 cables (two because it's a ring) that have a standard
           | rating of 24A each...
        
             | housemusicfan wrote:
             | UK electrics are mad - with the ring main and what not
             | requiring fuses in the enormous plugs. All vestiges of
             | post-WWII design. By code a modern American kitchen must
             | have:
             | 
             | - dedicated 50A 240V for an electric stove or oven (unless
             | gas service is present)
             | 
             | - dedicated 20A 120V each for the fridge, microwave,
             | dishwasher, disposal (the latter being uncommon outside the
             | US and Canada). The last two often share a circuit.
             | 
             | - two 20A countertop circuits with GFCI protection (what
             | the Brits call 'RCD' - the difference being ours trip at
             | 5mA vs 30mA and won't knock out half the house.)
        
               | laurencerowe wrote:
               | My apartment in San Francisco which I pay an absurd
               | amount of money for has just two or three 20A circuits in
               | total going by the breaker. I regularly trip the power.
        
               | bluGill wrote:
               | How old. What you describe sounds like it was built
               | before 1970 and never updated to modern standards. Since
               | the wire is often in okay shape few consider it worth the
               | cost to replace it even though it really can't supply
               | enough power for modern uses. (often you have to replace
               | it all as if you touch it the insulation will break and
               | then it isn't okay)
        
               | laurencerowe wrote:
               | Built around 1910 I think but the wiring is definitely a
               | lot newer than that, 70s or 80s at a guess. They just
               | didn't put many circuits in.
               | 
               | Has never been an issue anywhere I lived in the UK. As I
               | understand it they have been putting in 30A/230V ring
               | circuits as standard for 75 years now.
        
               | iso1631 wrote:
               | You assert that it's mad but then describe a mad
               | situation in the US.
               | 
               | A typical British kitchen will have a ton of sockets
               | (although never enough), to plug in a fridge (or two, or
               | three), a microwave (or several - they rarely goes about
               | 1kW anyway), a dishwasher, a washing machine, a tumble
               | dryer (UK kitchens tend to have washers and dryers,
               | rather than bathrooms. Larger houses have separate
               | utility rooms)
               | 
               | The only thing on a dedicated circuit would be a hard-
               | wired oven.
        
               | housemusicfan wrote:
               | Thinking that having dedicated independent circuits is
               | madness sounds like Stockholm syndrome. The point being a
               | single faulty appliance won't knock out the lights and
               | sockets to half the house simultaneously (a common
               | occurrence during a fault in the UK, especially the RCD).
               | It's also quite convenient to switch off a single
               | appliance for service. Yes British sockets are all
               | switched but not necessarily in a convenient location.
               | 
               | A software analogy would be running all your services on
               | separate VMs, as opposed to running them all on a single
               | server which could go down at once.
               | 
               | Brits don't even put outlets in the bathroom, minus a
               | current-limited transformer-isolated one for an electric
               | razor.
        
               | mytailorisrich wrote:
               | Ah, the regs have changed and we can now have a full
               | socket in the bathroom as long as it's far enough from
               | the bath (.6 + 2.5 = 3.1m from edge of bath), which rules
               | out most bathrooms...
        
               | housemusicfan wrote:
               | I assume the temptation to use the electric tea kettle
               | whilst having a bath is too great...
        
             | sph wrote:
             | Thanks, that's incredible. I won't have to worry about
             | tripping the circuit breaker anymore.
        
           | mananaysiempre wrote:
           | > in Italy most residential circuit breakers have a limit of
           | 3.3 kW
           | 
           | Wait, really? That's seriously underpowered, though I guess
           | if you never need electric stoves or heating it could be
           | somewhat usable. An ex-Soviet big-city apartment building
           | will usually support 40A (~9kW) per apartment, and in France
           | I had the impression that the values were similar--except for
           | student dorms, which are supplied and wired like apartment
           | buildings despite the density of occupants being 3x that or
           | more, because apparently the builders could not into
           | engineering and the uni authorities find it easier to blame
           | the occupants (yes, I'm still a bit salty about that).
        
             | sph wrote:
             | I haven't lived in Italy for 10+ years, so I don't know if
             | anything has changed since, but that was the limit for all
             | houses I've lived in, and from a quick Google search, it
             | depends on your contract -- the lowest is a 2 kW limit, 3.3
             | kW is the most common, and you can ask for an increase for
             | an additional monthly fee. Heating and stoves are usually
             | gas-powered, we don't do electric except for water boilers.
             | 
             | I have always wondered if those limits and the high
             | electricity costs are because Italy abolished nuclear
             | energy post-Chernobyl, doesn't have a massive oil and gas
             | operation, so most of it is imported at a premium.
        
             | gulikoza wrote:
             | That ~9kW is probably split over 3 phases. Here you have
             | 3x20A main breakers and then each circuit has a 10A or 16A
             | breaker. So about 3.7kW limit for larger appliances (16A *
             | 230V) on a single circuit, but should not exceed 20A on one
             | phase. Stoves can be connected to 2 phases, 400V and get
             | 7.2kW.
        
               | mananaysiempre wrote:
               | > That ~9kW is probably split over 3 phases.
               | 
               | In the Soviet system, usually not. There are often
               | several downstream circuits with their own 20A or so
               | breakers and wiring (e.g.: kitchen stove, normal kitchen
               | sockets, bathroom sockets and lighting, other rooms'
               | sockets, everything non-wet lighting), but each apartment
               | is normally supplied from a single phase. On the other
               | hand, different apartments on the same floor (or
               | different single-family homes on the same street, etc.)
               | might indeed be supplied from different phases. Normal
               | (Schuko) wall sockets are most frequently 16A (so yes,
               | 3kW kettles max), stove sockets (and circuits) might be
               | up to 32A, still single-phase.
               | 
               | (That's not to say the system is ideal, of course. E.g.
               | GFCIs have become common only in the past fifteen years
               | or so, and in a country-home setting I've actually
               | encountered disposable screw-socket [IEC 60269] fuses.)
        
             | N19PEDL2 wrote:
             | > Wait, really?
             | 
             | We should thank whoever came up with the idea of abolishing
             | nuclear power in Italy. What a big mistake!
             | 
             | > if you never need electric stoves or heating it could be
             | somewhat usable
             | 
             | Heating and stoves in Italy are usually gas-powered. Ovens
             | and kettles are electric but normally do not exceed 3.3 kW,
             | however, we need to be careful not to use too many high-
             | consumption appliances together (e.g., oven and washing
             | machine).
             | 
             | The introduction of increasingly restrictive energy classes
             | for electric appliances in recent years has mitigated the
             | problem to some extent anyway.
        
               | pjc50 wrote:
               | Italy has almost the same per-capita electricity
               | consumption as the UK. I suspect any residential
               | limitations are made up by industrial and transport
               | usages.
               | 
               | You guys really need to get on the solar panels, though.
        
         | jedberg wrote:
         | I have a question for you as a Brit. I live in an Asian
         | household (my wife is Asian). We have a hot water boiler, as
         | most Asian households do. It keeps 4L of water at "tea"
         | temperature at all times (after boiling it).
         | 
         | When we want tea, we just fill up the cup with the already
         | boiled and ready water. It's super efficient because it's super
         | insulated so it barely takes any energy to keep it hot after
         | it's been boiled.
         | 
         | Why don't Brits (and other tea drinking cultures in Europe) do
         | this?
        
           | laurencerowe wrote:
           | What is tea temperature for you? As I understand it black tea
           | which Brits drink should be made with water at close to
           | boiling (100 C) while green tea should be made with water at
           | 80 C.
           | 
           | My pet peeve in the US is ordering a cup of tea and getting a
           | cup of cooling water and a teabag by the side. Fine for
           | herbal or green tea but terrible for black tea.
        
             | jedberg wrote:
             | My boiler lets me set the hold temp at 208f(97.8C),
             | 195F(90.5C), and 175F(79.4C). So basically you can do all
             | the different "ideal" temps depending on which tea you make
             | the most.
             | 
             | We keep it at 195 since we don't make black teas, and then
             | we can let it cool down to whichever tea we want or just
             | mix it with some filtered cold to get it to temp.
        
             | hot_gril wrote:
             | My pet peeve is ordering hot tea and finding out they only
             | have coffee or iced tea. I've also gotten hot tea in a
             | plastic melting cup a few times.
        
           | bjornasm wrote:
           | >Why don't Brits (and other tea drinking cultures in Europe)
           | do this?
           | 
           | Because it is better to boil the right amount of water to the
           | precise temperature when you need it, as it takes virtually
           | no time.
        
           | davnn wrote:
           | At least in the German-speaking market there exist said
           | solutions, but they are not very common (yet?). I believe
           | keeping 4L at near boiling temperature is still less
           | efficient than individually heating and it takes less than a
           | minute with 3kW.
        
             | L_226 wrote:
             | Now all the German speaking market needs is tea that
             | actually tastes good.
        
           | walthamstow wrote:
           | Some do. It's become a popular addition to a middle class
           | kitchen. All offices have them.
           | 
           | As to why Asian households have it and we don't, I think it's
           | simply that we have been boiling water in kettles since the
           | stoves ran on coal, and the electric kettle is just an
           | upgrade of that same old system
           | 
           | Not to mention the age of our housing stock. The Asian
           | households you refer to, when were their homes built? I'm
           | guessing much more recently, comparatively speaking.
        
             | fragmede wrote:
             | Why is the age of the housing stock relevant here? An
             | Japanese-style water boiler is an add-on kitchen appliance,
             | like the Instapot or an air-fryer, so, cultural differences
             | aside, you'd expect similar adoption rates. Given that we
             | haven't, there must be some cultural component as to why.
        
               | desas wrote:
               | Some people have instant boiling water taps with tanks,
               | they're not unknown but rare and becoming increasingly
               | less so. I think this is because a) they're relatively
               | new here and b) last time I looked they cost about PS1k
               | plus fitting.
               | 
               | The Japanese water boilers look like they cost PS200ish
               | (vs PS15 for a kettle) and are bulkier than a kettle.
               | They will save practically no time - kettles boil fast
               | here and while they're boiling it gives you time to put
               | the tea in and any other preparations.
        
               | jedberg wrote:
               | It just occurred to me that Japan also uses 120V
               | (actually I think they use 100V), so it may be just a
               | matter of speed. You can boil water a lot quicker with
               | your 240V outlets than we can with our 100-120V.
        
               | bluGill wrote:
               | Age matters because in many cases the house was built
               | with some expectations, and something else won't work at
               | all. In the 1950s your house got a total of 4 circuits,
               | which was enough for clocks and lights, one fridge, and a
               | kitchen mixer (an electric range was an option and added
               | circuits). Of course TVs arrived in the 1950s (they
               | existed before then but were not common) and started
               | blowing power budgets. As people started using more
               | electric new houses got upgraded to handle those loads,
               | but many older houses have not been updated as it is
               | expensive (major remodel as you need to tear down walls).
               | 
               | Of course the above is standard, not everyone takes the
               | standard. However it is unusual to take something else.
               | 
               | Builders (read electric codes) build for what is common
               | uses. If everyone wants an something that uses a lot of
               | power the wires will be made to handle that in new
               | houses. However if you want that same thing in an older
               | house you may discover that the rewiring needed makes it
               | not worth it and so you look for an alternate.
        
               | desas wrote:
               | I'm not sure that's exactly true in this context. At
               | least, I've never been in the house in the UK where the
               | electrics in the kitchen couldn't handle a kettle, and a
               | water boiler for hot drinks isn't likely to use more.
        
           | mhandley wrote:
           | According to Twinings tea:
           | 
           |  _Always use freshly drawn (filtered if possible) cold water
           | in the kettle. Tea loves oxygen as it helps the flavour
           | develop._
           | 
           |  _Most of us are guilty of the following... looking at the
           | kettle seeing there is some old, used water in there and
           | simply re-boiling._
           | 
           |  _If you keep re-boiling the water in the kettle, it loses
           | all of its oxygen and you'll be left with a really flat cup
           | of tea._
           | 
           |  _If you boil the kettle with fresh water, you'll have a
           | delicious cup of oxygenated tea that tastes divine._
           | 
           | https://twinings.co.uk/blogs/news/how-to-make-a-cup-of-
           | tea-p...
           | 
           | I'm not sure how much difference this makes, but when I use
           | the hot water boiler at work, the tea definitely tastes
           | slightly off compared to using a kettle at home. But it's
           | also possible the hot water boiler at work is not producing
           | hot enough water.
        
             | benhurmarcel wrote:
             | Honestly if it's to put Twinings in it, it doesn't really
             | matter.
        
             | housemusicfan wrote:
             | They do make such a thing as an instant hot water
             | dispenser, though they are considered a luxury and not very
             | common:
             | 
             | https://insinkerator.emerson.com/en-
             | us/shop/insinkerator/ins...
        
             | ReptileMan wrote:
             | Just put it in the blender for a while.
        
             | Astronaut3315 wrote:
             | An Asian style water boiler maintains the temp just below
             | boiling, so there isn't any reboiling throughout the day.
             | Think of it as a water boiling thermos.
             | 
             | You're meant to replace the water daily. Not sure how many
             | follow that guideline.
             | 
             | ETA: Only the so-called "hybrid" models have vacuum
             | insulation. It's worth the extra charge.
        
               | scotty79 wrote:
               | Warmer water loses dissolved gasses faster.
        
               | jedberg wrote:
               | But as it cools the gasses reintegrate. So I'm not sure
               | the science backs this up. Water at the same temp should
               | have the same amount of dissolved gas regardless of how
               | it got to that temp (given enough time for the gas to
               | reintegrate).
        
               | mindslight wrote:
               | I think you're incorrectly discounting that time aspect.
               | If you leave a glass of tap water sitting out, eventually
               | there will be a bunch of bubbles clinging to the sides of
               | the glass. This doesn't happen immediately, but rather
               | over many hours. Similarly, I would think that boiling
               | water won't reach its gas equilibrium during the course
               | of making tea, but hot water sitting around waiting to be
               | used will.
        
               | jrockway wrote:
               | I agree with this. I develop my own film and the way I
               | manage water is to boil it, put it into sealed bottles,
               | and store those in the fridge. This avoids bubbles more
               | readily than just using tap water (which is over 20C in
               | the summer anyway, which is why I do the refrigeration
               | thing). No, I don't have an aerator on my tap either.
               | Obviously that introduces a lot of bubbles.
        
             | jedberg wrote:
             | It's true that boiling water reduces dissolved oxygen, but
             | cooling water takes on dissolved oxygen.
             | 
             | So I don't think the science backs this up.
        
               | mrguyorama wrote:
               | Nearly all tea advice is ideology and superstition,
               | explicitly because most people like different things
               | about tea. There cannot be a right answer for such a
               | personal preference.
               | 
               | Make tea such that you enjoy it. Same as coffee.
        
               | markdown wrote:
               | Agreed. You can't beat good old Nescafe instant coffee.
               | Starbucks just can't compare.
        
               | eep_social wrote:
               | Hmm, I don't seem to be able to go back and delete this
               | comment.
        
           | psd1 wrote:
           | The hot urn cannot be more efficient than boiling the correct
           | amount of water each time.
           | 
           | The limiting factor is the specific heat capacity of water.
           | If daily consumption is 2l, you have to put in the joules to
           | raise 2l to boiling, either way. If you have heat losses
           | during the day, there's your inefficiency.
        
             | jedberg wrote:
             | It is of course less efficient. I never said it was more
             | efficient. But it's more convenient.
        
               | bialpio wrote:
               | Your comment literally says "It's super efficient"
               | though.
        
               | jedberg wrote:
               | Sure, but that doesn't imply it's more efficient than the
               | other options. Just that it's also very efficient.
        
             | HDThoreaun wrote:
             | How many people are boiling the correct amount each time
             | though? I fill my jug up all the way and then keep
             | reboiling which seems less efficient as the boiled water
             | keeps cooling down.
        
               | shrx wrote:
               | Why wouldn't you boil just the amount that's needed?
               | Boiling the whole container is unnecessarily wasteful.
        
               | zbrozek wrote:
               | I use my target cup to measure out how much water to
               | boil.
        
               | hot_gril wrote:
               | I fill it to a certain mark every time. Not that I'm
               | trying to conserve energy, I just don't want to leave
               | extra water sitting.
        
           | porbelm wrote:
           | Legionella
           | 
           | I kid, but there's something about "fresh" water probably?
        
             | jedberg wrote:
             | The water stays way above the temp for legionella. And the
             | water is still pretty fresh, it ends up getting replaced
             | every other day or so in winter. And in summer we just
             | replace it once in a while anyway.
             | 
             | Also it will reboil after a certain amount of time.
        
           | Astronaut3315 wrote:
           | I've had a 4L Zojirushi boiler in the US for about 15 years
           | now. This is the best solution for those who complain about
           | 120V kettles.
        
         | awalach wrote:
         | Obligatory TechnologyConnections reference -
         | https://www.youtube.com/watch?v=_yMMTVVJI4c TLDR: in US it
         | takes 2 minutes more :). Is that difference that noticeable
         | IRL?
        
           | bemusedthrow75 wrote:
           | If you were British, you would not need to ask this.
           | 
           | Being compelled to wait two minutes more to boil a kettle for
           | a cuppa would be enough to provoke an armed rebellion.
           | 
           | Not even sure I'm kidding.
        
             | creole_wither wrote:
             | Why not just keep the water warm in an electric samovar?
        
               | bemusedthrow75 wrote:
               | Typical British teabag tea -- the stuff we consume in
               | quantity -- is brewed with water just off the boil, and
               | consumed often pretty quickly afterwards because cold
               | milk gets added.
               | 
               | (Or it goes into a teapot for brewing, and again needs to
               | be just off the boil for that)
               | 
               | Given that we can boil a kettle for a mug's worth of tea
               | in not much more than half a minute, there's no reason to
               | use them, I think.
        
             | mrguyorama wrote:
             | Most Americans drink substantially more coffee than tea,
             | which is why we have a purpose built appliances for making
             | coffee, and have had those for decades.
             | 
             | The reason Americans don't have a super fast boiling kettle
             | is that very few Americans WANT a very fast boiling kettle
             | for large portions of water. If an American wants a cup of
             | tea, two minutes or less in the microwave is sufficient. I
             | don't care if you think that's bad, because I want a cup of
             | tea, not some elitist purity contest.
        
           | zoenolan wrote:
           | Well you have to remember the UK is the nation that fit
           | kettles in Tanks
           | 
           | https://en.wikipedia.org/wiki/Boiling_vessel
        
             | mrguyorama wrote:
             | People like to joke about this but the reason it's called a
             | "boiling vessel" and not a "Tea maker" is because it's
             | incredibly useful other than just making tea, to the point
             | that the US has also added them to many modern vehicles.
             | 
             | On demand hot water, from the safety of your combat
             | vehicle, is a genuine war innovation on the same level as
             | canned food. Especially now that combat vehicles are aiming
             | towards having more robust electrical systems makes it
             | trivial to implement. Hot water means hot food, means
             | warmth on a cold day, means sterilizing sketchy water
             | sources without chemical tablets, means you don't have to
             | light a visible fire to make your coffee, means you keep
             | morale way higher. Your troops are now cleaner, better fed,
             | happier, more motivated.
        
         | dfxm12 wrote:
         | On the hot beverage topic, I'm jealous that the espresso gear
         | in Europe is a little cheaper/faster. The motors that drive
         | coffee grinders and the heaters that heat up water in the
         | boilers work a lot easier/faster.
        
         | HALtheWise wrote:
         | Has anyone ever made a battery-powered kettle with
         | significantly higher power than can be pulled from a wall
         | outlet? Modern lithium batteries can deliver many kilowatts of
         | power, and given that the total _energy_ needed to boil the
         | water is basically fixed, the battery size requirements might
         | be pretty reasonable. I wouldn 't be surprised if boiling water
         | in 15s is possible even on a 120v American outlet.
        
           | mhandley wrote:
           | Now I realize that what I really want to build is a kettle
           | with two 3kW heating elements. On a UK ring main, I can plug
           | the two elements into two neighbouring sockets and still have
           | headroom before I blow the breaker. I can cut my time-to-tea
           | from 45 seconds to 22 seconds!
        
           | kccqzy wrote:
           | I think it's certainly possible. FWIW car batteries can often
           | support 1000A especially those for large diesel engines. They
           | aren't meant for continuously loads or deep cycles though.
           | Marine batteries may be able to overcome this.
        
           | jaywee wrote:
           | Impulse Labs, a startup, is doing lithium-backed kitchen
           | stoves. Claims to heat-up 1L of water in ~40secs. That's at
           | least 8.6kW.
           | 
           | https://twitter.com/sdamico/status/1592553611879673856?s=20
        
           | adrianmonk wrote:
           | It does seem feasible to equal the performance of a 3
           | kilowatt kettle with batteries!
           | 
           | =-=-=
           | 
           | Question #1: Can we get 3 kilowatts of power out of some
           | lithium ion batteries?
           | 
           | There are high-current versions of lithium batteries.
           | Conveniently, they're widely available because they're used
           | for vaping.
           | 
           | I found a battery that looks reasonable
           | (https://www.18650batterystore.com/products/molicel-p42a).
           | Its stats: 4200 mAh capacity, 3.6V nominal, 45A continuous
           | discharge, and retail cost $4.99.
           | 
           | At 3.6V and 45A, each battery should output 162 watts.
           | Rounding to 150 watts, we'd need 20 of them to make 3
           | kilowatts. So $100 worth of batteries.
           | 
           | =-=-=
           | 
           | Question #2: How long will they last? Long enough to boil
           | water?
           | 
           | At the 45-amp discharge rate and with 4.2 amp-hour capacity,
           | it should take 4.2/45 hours = 6 or 7 minutes to discharge
           | them.
           | 
           | By my math, it takes 335 kilojoules to heat a liter of water
           | from 20degC to 100degC. A 3 kilowatt kettle should be able to
           | do it in 335/3 = 112 seconds.
           | 
           | So the batteries should be able to boil water around 3 times
           | before discharged.
           | 
           | =-=-=
           | 
           | Those calculations are for running on battery alone. Since
           | you can get 1500W out of an American 120V outlet, you could
           | make a kettle that draws 1500W from the wall and boosts it
           | with 1500W of battery power. (I'd use two heating elements.)
           | Then you only need $50 of batteries.
           | 
           | The kettle is going to be a bit heavy, though. The batteries
           | are 70g each, so 20 of them is 1.4 kg. Also, I don't know
           | much batteries heat up when cranking out 45 amps, but I bet
           | the answer is a lot, and you may need active cooling and/or
           | thermal shutoff.
        
         | p1mrx wrote:
         | I would like to see a US electric range with Schuko outlets and
         | 16A GFCI breakers on the side, but that probably violates too
         | many electrical codes.
         | 
         | Schuko makes the most sense because it's unpolarized, so
         | appliances don't expect a neutral leg. You still have the 50/60
         | Hz problem, but something like a kettle probably won't care.
         | 
         | Or there could be a countertop "Schuko dongle" that attaches to
         | the screw terminals on the back of an existing range, if it
         | weren't for those meddling codes...
         | 
         | Though in practice, the key to boiling fast is to use less
         | water. A 1500W kettle with 500 mL minimum fill is totally
         | reasonable for cup of coffee/tea.
        
         | dfawcus wrote:
         | It's not 230, it is 240!
         | 
         | 3000 / 230 = 13.04
         | 
         | 3000 / 240 = 12.5
         | 
         | We fit 13A fuses to the plugs of kettles. At 230V the tolerance
         | would be too close.
         | 
         | Whereas in reality, a kettle designed to be 3kW at 240V would
         | only be 2.755kW at 230V, or 2.520kW at 220V.
         | 
         | You'll often find the latter pair of number printed on the base
         | of the kettle. i.e. 2520-3000W at 220-240V.
        
           | djaychela wrote:
           | They generally don't blow at the rated current. I've reliably
           | used a 13A fuse on something that draws 16A for a while when
           | starting up and never had a problem. Obviously RCDs etc are
           | more accurate, but wired / cartridge fuses are always under-
           | rated, in my experience.
        
             | bluGill wrote:
             | Most fuses are slow blow - they will allow somewhat over
             | the rates power draw for a while before blowing. Many
             | things (motors) take a lot more than rated current for a
             | few seconds and this is perfectly safe so the fuse
             | shouldn't blow. The purpose of the fuse is to prevent a
             | house fire, if your wires are good for 13 amps that means
             | at 100% duty cycle, you can draw 16 amps for "a while"
             | before the wires get hot enough to burn the house down, so
             | long as you drop under 13 amps for "a while" so the wires
             | cool down and never get hot enough to start a fire the fuse
             | is working.
             | 
             | Note that the above is about safety. If you are going to
             | draw 16 amps you should stick to a circuit rates for that,
             | as it will have less resistance and thus waste less energy.
        
         | myrandomcomment wrote:
         | https://www.youtube.com/watch?v=_yMMTVVJI4c
         | 
         | The difference is 2 minutes on the boil time of 1L.
        
         | lbourdages wrote:
         | I have 20 amp sockets in my kitchen (as all newly built housing
         | has, really) but there are no 20 amp kettles on the market. I
         | wish I could get that extra 600 watts or power :(
        
           | Astronaut3315 wrote:
           | _In theory_ you could use one of those Leviton British-style
           | receptacles designed for US-style boxes on a dedicated 240V
           | circuit.
           | 
           | In practice, NEC code likely prohibits you from doing this.
        
             | bombela wrote:
             | I would install an US 240V@20A receptacle and replace the
             | plug on the kettle.
             | 
             | You can also wire a duplex 120V with the two phases (you
             | might find this in some kitchens, and in my workshop). Then
             | you can make a dangerous extension cord adapter combining
             | the split phase 120V into one 240V female plug.
        
           | brocklobsta wrote:
           | In the US it is against code to have any regular appliance
           | use more than 15 amps continuously I believe
        
             | lbourdages wrote:
             | My hair dryer is rated for 1875W - a bit over 15 amps at
             | 120V.
        
             | pjc50 wrote:
             | The standard British kettle is 13A .. at 240V.
        
             | mindslight wrote:
             | If you're referring to the standard 80% continuous load
             | rule, it's 16 amps. But I wouldn't think a kettle would be
             | considered a continuous load.
             | 
             | If I wanted a British kettle in the US I'd wire up a 6-20R,
             | buy a British kettle, and swap the plug.
        
             | bitbckt wrote:
             | The circuit rating is 80% of nominal for continuous loads -
             | runtimes of 3 hours or more - according to NEC in the US.
             | Not sure what you mean by "regular appliance"; there is no
             | such definition by code.
             | 
             | A kettle is fine at a full circuit load for under 3 hours.
        
             | macrolime wrote:
             | Your run your kettle for hours on end?
        
             | AlgorithmicTime wrote:
             | [dead]
        
             | vel0city wrote:
             | A kettle is not a continuous load.
        
               | SkyPuncher wrote:
               | Continuous is anything outside of a small "startup
               | window". Appliances with motors will often have an
               | initial surge amperage that's higher than peak.
               | 
               | Fuses/breakers are ultimately about heat control. They
               | can run "indefinitely" at their rated amperage, but can
               | support short, higher loads.
        
               | rootusrootus wrote:
               | There are regional differences that are probably causing
               | some confusion. In the US, breakers have a nameplate
               | rating 25% higher than their continuous load capacity. Go
               | to Australia, for example, and the identical breaker will
               | have a nameplate rating 80% of what it would in the US.
               | 
               | So you can run indefinitely at the nameplate rating in
               | Australia, but only 3 hours in the US. And the startup
               | current (inrush) can be _much_ higher than the rating.
               | Most breakers are thermo-magnetic. The magnetic part has
               | a much higher tripping point and allows for inrush
               | current. The thermo part trips when it gets too hot, and
               | that 'll be the current printed on the breaker.
        
               | bitbckt wrote:
               | No, continuous is very specifically defined in the NEC as
               | 3 hours or more of runtime.
        
               | SkyPuncher wrote:
               | This article does a good job of explaining how failure
               | modes/alternative usages can make that definition fuzzy:
               | https://www.csemag.com/articles/understanding-
               | overcurrent-pr...
               | 
               | Practically speaking, any intermittent device that _can_
               | run continuously or can fail to a continuous needs to be
               | considered as such for safety purposes.
               | 
               | For example, a fridge should only run the compressor
               | intermittently, but it has two obvious cases where the
               | compressor could run indefinitely:
               | 
               | * An influx of heat, like filling an empty fridge with
               | room temperature cans.
               | 
               | * A door being left open.
               | 
               | In the case of the kettle, it will likely be evaluated
               | against it's "nominal" draw after the initial startup. If
               | the auto-off sensor were to fail, it could run
               | continuously at the tempurature.
        
               | bitbckt wrote:
               | I probably can't speak to your jurisdiction, but no
               | electrical inspector I've ever met would consider those
               | loads continuous - in its precise, non-colloquial meaning
               | - for the purpose of rating the circuit.
               | 
               | An appliance manufacturer may be under different UL
               | regulations for failure modes of a device on a specific
               | rated circuit. I don't know anything about that.
        
               | fragmede wrote:
               | Yes, laymen and non-experts are going to use words to
               | mean the wrong thing. NEC defines continuous load as 3 or
               | more hours of uninterrupted demand. If you want to use
               | the amateur definition, go right ahead, but understand
               | there's an accepted industry definition of that term,
               | even though it looks just like normal words. :)
        
               | vel0city wrote:
               | If this is the standard then everything is a continuous
               | load. A soldering iron or a hair dryer or a blender might
               | get left on forever, who knows. Maybe I want the
               | microwave to run 24 hours a day. If everything is a
               | continuous load, why would the NEC make a difference at
               | all?
        
               | mindslight wrote:
               | Even in the context of your refrigerator example (which I
               | don't necessarily agree with), a kettle should have two
               | thermostats - a primary one that keeps the temperature
               | setpoint, and a safety cutoff in case the primary stops
               | working. In both fail and the kettle is somehow drawing
               | its nominal power for hours at a time, the main safety
               | hazard is going to be the kettle itself trying to
               | dissipate >1Kw.
        
               | dfawcus wrote:
               | Well they can be, until they boil dry, and the thermal
               | cut out kicks in.
               | 
               | Prior to the late 70s / early 80s so called "automatic
               | kettles" were not necessarily all that common in the UK,
               | and one had to manually switch them off.
               | 
               | I certainly recall a time or two with a kitchen full of
               | steam due to forgetting about putting the kettle on.
        
             | Kirby64 wrote:
             | No it's not. It's just against code if they use a NEMA 5-15
             | outlet. If GP used NEMA 5-20 outlets and the appliance used
             | a 5-20 plug, then there's no issue.
             | 
             | Many commercial appliances use 5-20 plugs. Also, lots of
             | commercial cleaning equipment seems to use 5-20, which is
             | why you see businesses tend to only use 5-20 outlets.
             | 
             | I'm not aware of any kettles that use 5-20 plugs but I bet
             | they exist somewhere.
        
               | lbourdages wrote:
               | Yep my kitchen outlets are all the 20-amp specific ones,
               | with the T slot.
        
             | fragmede wrote:
             | It's not, and for laymen "continuous load" has a specific
             | meaning in this context. It means something that runs for
             | 3+ hours continuously, without a break.
        
           | fragmede wrote:
           | Just get a Japanese-style hot water boiler. They're way
           | faster.
        
         | izolate wrote:
         | I used to sympathize with this take until I bought a Zojirushi
         | water boiler, which provides instantaneous hot water. Now even
         | a faster kettle is a downgrade in experience.
        
         | hot_gril wrote:
         | Somehow I've never considered my home kettle too slow in the
         | US, even though I have tea probably 2-3 times a day. And
         | there's an instant hot water machine at our office, so it's not
         | like I've gotten used to slowness.
        
       | perfectstorm wrote:
       | i wish 240V was more common. i can't charge my EV at a reasonable
       | rate and it would cost me $15k+ to install a 240V in my detached
       | garage (requires trenching).
        
         | tzs wrote:
         | Could you do the trenching yourself?
         | 
         | I don't know where you are, but in the US a walk-behind
         | trencher rents for under $500 per day [1] [2] [3] [4].
         | 
         | [1] https://www.sunbeltrentals.com/equipment-rental/earth-
         | moving...
         | 
         | [2] https://www.compactpowerrents.com/rental-
         | equipment/trencher/...
         | 
         | [3] https://www.compactpowerrents.com/rental-
         | equipment/trencher/...
         | 
         | [4] https://www.compactpowerrents.com/rental-
         | equipment/trencher/...
        
         | [deleted]
        
         | Anon_Forever wrote:
         | >i wish 240V was more common
         | 
         | More common where? Your main service panel is 240V. Do you only
         | have a single 120V circuit feeding your garage?
        
       | somat wrote:
       | Really all residential connections in the US are 220V split
       | phase. The nice thing about split phase is that it is easy to
       | well... split and run two linked 110V circuits, so most houses
       | will have a few 220V items(ovens, airconditioner) and the rest
       | wired half with phase A the other half with phase B. all of our
       | consumer items expect this 110V
       | 
       | As to why split phase.... I am not really sure. Really, I wish a
       | three phase residential had become normal instead. All the
       | advantages of split phase but now your motors don't have to suck.
       | I have heard a three phase residential connection is common in
       | some parts of Germany, lucky bastards.
       | 
       | One interesting side note is how the US last mile distribution
       | layout is different than germany. The US uses a lot more smaller
       | transformers, really one per street. while germany uses fewer
       | larger transformers, one per neighborhood. not sure which one is
       | better I bet the german layout is more efficient. but I will note
       | it is a lot easier to keep spares and change out a small
       | transformer.
        
         | linsomniac wrote:
         | I thought residential US service was 240V split phase with two
         | 120V legs.
         | 
         | I've heard for some wet construction locations they'll set up
         | 120V split phase with two 60V legs, to keep the potential to
         | ground smaller.
        
           | bootlooped wrote:
           | When talking about the voltage of US residential service, and
           | the devices that use it, 240 and 220, and 120 and 110 are
           | functionally the same. The house theoretically has 240v and
           | 120v power, but voltage may sag throughout the home's wiring,
           | and some outlets will a real voltage reading lower than
           | 240/120.
        
         | pacaro wrote:
         | > but I will note it is a lot easier to keep spares and change
         | out a small transformer.
         | 
         | In my neighborhood, about once a year there's a loud pop, or
         | quiet bang, and a bunch of houses lose power. The electric
         | company will fix it pretty quickly.
         | 
         | I think that it's performing selection pressure on the
         | unlicensed squirrel electrician population.
        
           | dylan604 wrote:
           | Growing up in the sticks, I'm pretty sure there was an
           | unlicensed trade school for squirrels in the area. Pretty
           | much once a year, we'd need a replaced transformer from one
           | of these unlicensed squirrel electricians. I never charted
           | the timing of the year this would happen, but now I wonder if
           | aligned with the start of a new class.
        
             | kefabean wrote:
             | Here in the UK I think some of those unlicensed squirrel
             | electricians are beginning to retain in fibre broadband
             | installations. My neighbour was 'disconnected' last week.
        
               | dylan604 wrote:
               | The next time a friendly representative from the
               | international brotherhood squirrel electrical (IBSE)
               | union stops by to discuss joining their service
               | protection plan, they should reconsider. "This a real
               | nice connection you have here. It'd be shame if something
               | were to happen to it"
               | 
               | Edit: or would that be the Free Mesons
        
           | Spooky23 wrote:
           | Depending on where you live, they age out too. The one behind
           | my house exploded a year or two ago.
           | 
           | It was manufactured in 1959!
        
           | kelnos wrote:
           | I was a little surprised that my neighborhood must have some
           | redundancy. A year or so ago a transformer on a pole two
           | doors down from us popped, and our power actually didn't go
           | out.
        
         | user2342 wrote:
         | > I have heard a three phase residential connection is common
         | in some parts of Germany, lucky bastards.
         | 
         | Not some parts. It's common in all parts of Germany - and I
         | think even common on the whole EU.
        
         | mschuster91 wrote:
         | > I have heard a three phase residential connection is common
         | in some parts of Germany, lucky bastards.
         | 
         | German here. Virtually all houses built after the 60s will have
         | _at least_ 3x63A @ 230V (L-N)  / 400V (L1-L2/L2-L3/L3-L1) AC.
         | Individual flats/apartments/studios from before the 90s will
         | usually have a single phase 32-40A uplink, so in a 12-unit
         | house you'll have four flats wired to L1, four to L2, and the
         | last four to L3 to ensure even load across the phases. More
         | recent builds that don't have gas stoves any more will have a
         | 3x40 connection to allow for powerful electric stoves and
         | ovens.
        
           | askvictor wrote:
           | Nice over-provisioning; I doubt the gas shortage or electric
           | cars were on the radar when 3 phase became the norm...
           | 
           | How are loads balanced to phases in a standalone house?
        
         | mjan22640 wrote:
         | > I have heard a three phase residential connection is common
         | in some parts of Germany, lucky bastards.
         | 
         | Czech Republic switched to 3 phase 380V in 1919. I guess the
         | transition DC -> 110V AC -> 3 phase ~400V went quick everywhere
         | in the world, just in US they did not do the last step.
        
         | melenaboija wrote:
         | > The US uses a lot more smaller transformers, really one per
         | street. while germany uses fewer larger transformers
         | 
         | I am from Spain and living in the US and something that was
         | shocking to me about it is that here, at least where I lived,
         | these last transformers are hanging from poles and every now
         | and then I can hear an explosion and it is one of them blowing
         | up.
         | 
         | I have no idea but, maybe being exposed like they are here in
         | the US makes them more vulnerable to weather conditions and
         | that makes them explode? Or maybe it simply is that in Spain
         | they also explode but the fact of not being that close to
         | residences makes it harder to hear it.
        
           | bluGill wrote:
           | Transformer explosions are rare. Unless you can produce
           | statistics saying otherwise it is safe to assume they happen
           | as often in both countries (per something, the US obvious has
           | far more transformers given larger population and area, and
           | thus should have more total)
        
             | TheCleric wrote:
             | Yeah near me they rarely ever pop, and when they do it's
             | almost always lightning related.
        
               | Symbiote wrote:
               | "Rarely ever" and "when they do" suggests this happens
               | more often than "I've never heard of this as a thing"
               | here in Europe.
               | 
               | With higher voltages, fewer transformers are needed.
               | Power lines are buried, and transformers are generally
               | larger and not exposed to weather.
        
               | melenaboija wrote:
               | That was exactly my point, I have never heard that in
               | Europe and I would say at least a dozen of them in US in
               | a decade. Probably because there are more of them and
               | exposed.
               | 
               | I am not criticizing the infrastructure but as European
               | (and this is something others told me) it feels weird to
               | see transformers hanging from poles and every now and
               | then blowing up.
               | 
               | And I mentioned the weather because my experience is that
               | it usually happens during storms, it might be lightnings
               | or tree branches but that is what I have seen.
        
             | Symbiote wrote:
             | For some statistics, "U.S. electricity customers averaged
             | seven hours of power interruptions in 2021." [1].
             | 
             | At first I couldn't find equivalent European statistics,
             | until I changed my search to "minutes", which is how Europe
             | measures outages. The EU average in 2010-2014 was just over
             | 2 hours, and as low as 29 minutes in Germany, or 20 here in
             | Denmark.
             | 
             | [1] https://www.eia.gov/todayinenergy/detail.php?id=54639
             | 
             | [2] https://neon.energy/Neon_Data-quality_European-
             | Commission.pd... (22nd page, figure 5)
        
           | [deleted]
        
         | _trampeltier wrote:
         | The cool thing is in Switzerland with the T15 / T25 plug you
         | can use from a small 230V LN plug, 230V LNPE plug or a 3x400V
         | 3LNPE plug. You see this often in workshops. I think this is
         | unique in the world.[1]
         | 
         | Also the 3xT13, 3 plugs where everywhere else in the world is
         | just one plug. [2]
         | 
         | [1] https://de.m.wikipedia.org/wiki/SN_441011
         | 
         | [2] https://hager.com/de-ch/katalog/produkt/wh22730700k-ka-eb-
         | st...
        
         | jhoechtl wrote:
         | > Really all residential connections in the US are 220V split
         | phase
         | 
         | Really all modern residential connections in Europe are 400V
         | three phase electric power, capable to immediately power an
         | electric motor without the need of capacitors.
         | 
         | No matter how you put it, the US residential power grid is
         | conceptionally lagging.
        
           | gumby wrote:
           | > No matter how you put it, the US residential power grid is
           | conceptionally lagging.
           | 
           | Not just conceptually == reliability is lower than that of
           | its peers:
           | https://www.statista.com/statistics/268155/ranking-of-
           | the-20... (if you don't have a statista account, US is at the
           | bottom of this list at 98.6)
           | 
           | State level data:
           | https://www.eia.gov/electricity/data/eia861/
        
           | dghlsakjg wrote:
           | You do realize that the grid runs at a completely different
           | voltage than what is actually delivered to standard
           | residential service, right?
           | 
           | It is entirely possible to get three phase, high-voltage
           | power in North America, it just isn't run to individual
           | houses unless specifically requested.
        
             | sokoloff wrote:
             | Far more common for 3-phase motor loads in residential
             | areas (already an unusual requirement) is the point use of
             | a rotary phase convertor or (more commonly now) variable
             | frequency drive to run the 3-phase motor from the existing
             | split-phase supply.
        
             | kukkamario wrote:
             | 400V three phase is wired to all houses at least here in
             | Finland. All 3 phases are wired to the electric box and
             | then that splits phases to normal sockets and for lighting
             | etc. Ovens use three phases and detached houses usually
             | have separate 3-phase plugs outside for running eg. heavy
             | construction tools, like cement mixer and such. Oh right
             | and sauna stove also needs all 3 phases obviously.
             | 
             | Even apartments have that full 3-phases, but just for
             | plugging in the oven and the sauna stove.
        
               | chris_va wrote:
               | There really isn't a huge advantage for 3 phase unless
               | you are doing high-power DC rectification or trying to
               | run a motor.
               | 
               | The US grid is basically 3-phase everywhere, but it's
               | neither needed nor cost-effective to run it into the
               | home.
               | 
               | Now, the 400V part is different. That would require less
               | copper (but with a safety cost).
        
               | pangolinja wrote:
               | [flagged]
        
               | robswc wrote:
               | No idea if you're from the US but this "weak
               | infrastructure" has/is hosted/hosting nearly every
               | important infrastructure that makes the online world go
               | round and has been doing perfectly fine for decades.
               | 
               | What are you doing that you need 400v?
        
               | hot_gril wrote:
               | > What are you doing that you need 400v?
               | 
               | Complaining about Americans on the internet, obviously.
        
               | FLT8 wrote:
               | I am in Australia and am in the process of having our
               | home supply wired for three-phase 415v. Everything is
               | heading down the path of electrification. Where
               | previously we had gas central heating, cooking, and hot
               | water, we are replacing those with electric HVAC (30amp
               | circuit @ 240v, admittedly rarely driven that hard),
               | electric instantaneous hot water (40 amp @ 240v),
               | induction cooktop (32 amp), oven (15 amp), and also
               | introducing a car charger (total approx 45 amps across
               | the three phases).. it's likely at least the HVAC,
               | cooktop/oven, car charger, and hot water could be on at
               | or around the same time, which would result in more power
               | draw than a standard single phase connection here (80a)
               | could supply. It's not that it's needed _all_ the time,
               | but it 's helpful to have the headroom a 3-phase supply
               | can provide.
        
               | deaddodo wrote:
               | [flagged]
        
               | pavlov wrote:
               | The Nazi genocide in the East was explicitly modeled on
               | the treatment of Native Americans in the 19th century.
               | 
               | So, like voltage, it's another case where Americans
               | invented something and Europeans doubled down.
        
               | catchnear4321 wrote:
               | yes, but who invented the americans
        
               | hot_gril wrote:
               | Interesting thing I learned, horses actually originated
               | in the Americas. Some of them migrated to Asia, then the
               | ones in the Americas died out before human civilization,
               | so only the Old World civs had them. When Europeans
               | brought horses to the Americas, they were bringing them
               | _back_.
        
               | deaddodo wrote:
               | Yes, _Americans_ invented populace relocation (and the
               | abuses that come with it). Nice to know the Roman Empire
               | had a time machine to pull a major component of their
               | imperial edict from.
               | 
               | But let's pretend your warped view of history is
               | reality...that happened 100 years earlier. If Europeans
               | are so enlightened atop those tall horses, maybe don't do
               | it again and 10x worse?
               | 
               | In addition, I wasn't referring to the Holocaust...but
               | the entire continent's shared sick desire to kill
               | themselves off for 10km of border movement or literal
               | dreams of world conquest.
        
               | hot_gril wrote:
               | This wouldn't surprise me, but I can't find it. I'm
               | seeing some authors drawing comparisons, but haven't
               | found Hitler or his party actually mentioning Native
               | Americans. There are explicit references to Turkey, with
               | Hitler mentioning the Armenian Genocide (as justification
               | for invading Poland) and calling Ataturk a "shining
               | star," along with the Nazi papers obsessing over his
               | nationalist policies.
        
               | hot_gril wrote:
               | Ok I'm going to make this even darker: The metric system
               | sucks for non-scientific usage, especially using Celsius
               | for room or weather temps. Idk why Europeans (and other
               | continents) insist on using something with such low
               | granularity and weird usable ranges. 0F = prob not going
               | outside, 100F = close to highest temp you'll see all
               | year, 56C = highest outdoor temperature ever on Earth. In
               | the 70s (F) = warmish weather, in the 60s = coolish
               | weather, in the 20s (C) = either cool or hot. Digital
               | thermostats add 0.5 increments if you set them to C mode,
               | lol. Meanwhile KPH is too granular, while 0-100MPH is all
               | you need for cars outside of racing. Divisibility into
               | meters etc is pointless, cause it's not like I need to
               | compare a road trip length to the height of a person.
               | 
               | No surprise that basing your units on the physical
               | properties of water doesn't give you very human-friendly
               | results. Their only good unit is kilograms/grams. Edit:
               | actually not even that.
        
               | riversflow wrote:
               | Meh, I don't even thing grams are very good.
               | 
               | Pounds have a nice granularity for every day stuff: a 3
               | pound laptop and a 2 pound laptop are significantly
               | different, but both are "about a kilo".
               | 
               | On the other end, a gram is such a small amount that I
               | can only perceive it in multiples, whereas I have a
               | pretty good idea of how much an ounce is.
        
               | hot_gril wrote:
               | Actually yeah, I remember realizing the same thing a
               | while back. 1 pound difference is about what I can
               | perceive. Same with 1@F difference.
        
               | Dylan16807 wrote:
               | A laptop that's a pound and a half is also very
               | different.
               | 
               | But oh, if you're willing to say "and a half" you might
               | as well be willing to say .7 kilo.
               | 
               | There's no real overall advantage, you just picked a
               | couple very specific numbers. You can always pick very
               | specific numbers to make any system look better/worse.
        
               | mulmen wrote:
               | Inventor syndrome. Same thing with our cell phone
               | networks and space ships. When you invent something you
               | end up with the most "archaic" version, by definition.
               | But it seems to still be working. American pragmatism
               | says there's better places to allocate resources.
        
               | [deleted]
        
               | chris_va wrote:
               | ... the infrastructure is high voltage 3-phase, same as
               | EU.
               | 
               | Also, stone tools are easier to replace :P
        
               | saiya-jin wrote:
               | Its everywhere in Europe. I haven't seen nor heard about
               | say a single oven not plugged into 400V. I've lived in 4
               | different countries in east & west, all the same. Even
               | when traveling around a bit, I see those special plugs in
               | convenient places, where you may expect to plug something
               | powerful for some heavier work.
               | 
               | Anything high power, you go for this plug. I'd imagine
               | car charging would also benefit from this but not
               | personally in that market yet.
        
               | pmontra wrote:
               | This HN thread is the first time I learned about 400 V to
               | homes in Europe. My oven is 220 V. I just checked the
               | manual. All my house is 220 V. I live in Italy.
               | 
               | Plugs are usually Shuko for high power appliances
               | (washing machine) and two smaller pins for low power
               | (phone chargers.)
               | 
               | By the way, Italy traditionally had a three pin in a line
               | high power plug but more and more appliances are coming
               | with Shuko plugs so wall socket are either bi-standard or
               | just Shuko now.
        
               | jaywee wrote:
               | The 400V is between phases. 230V is between a phase and
               | ground. Ie, you get 3 wires (phases) of 230V from the
               | 400V connection.
               | 
               | Btw, Europe standardized at 230/400V in the nineties. In
               | Czechia we switched from 220V to 230V in 1993. Not sure
               | when Italy did, but probably around the same time.
        
               | kelnos wrote:
               | > _detached houses usually have separate 3-phase plugs
               | outside for running eg. heavy construction tools, like
               | cement mixer and such._
               | 
               | Is this sort of use common in Finland? It seems like
               | kinda a waste of money and materials to install the
               | infrastructure to allow everyone to run heavy
               | construction equipment off their home's electrical
               | supply.
        
               | Gravityloss wrote:
               | Since you need three phase 380V for the sauna and the
               | kitchen anyway, and probably for the ground or air heat
               | pump too... it doesn't cost almost anything to run a
               | cable from the electrical box and installing a three
               | phase socket.
               | 
               | This shows a 32A 400V socket costs under 10 euros:
               | https://www.taloon.com/voimapistorasia-pinta-
               | bals-101-3pne-3...
        
               | malermeister wrote:
               | I can't talk about Finland, but in Central Europe it's
               | pretty common as there is a culture of house building.
               | 
               | In the US, a developer typically buys an entire
               | neighborhood's worth of land and builds a bunch of houses
               | there to sell to individuals.
               | 
               | Over here, the individuals will typically buy their own
               | small plot of land and then have a house built there
               | according to their specifications. You need to be able to
               | run heavy construction equipment to do so.
        
               | djhn wrote:
               | How esle is the home going to get renovation work and
               | upkeep done?
        
               | hinkley wrote:
               | The last transformer between houses and the grid is 440v
               | three phase. As I understand it the distribution networks
               | all look pretty much the same, it's only the last mile
               | that differs. And thus consumer electronics.
               | 
               | If you want to run a machine shop, it's a pain but not
               | impossible to get 440 three phase wired straight through
               | to your business. But consumer "heavy" motors and
               | induction stoves run on two phase 230V.
        
             | cptcobalt wrote:
             | In the US, the amount of three phase electricians that will
             | work at a Residential home and not charge you an arm and a
             | leg for it is _vanishingly low_ , almost certainly not
             | worth it.
        
               | mitthrowaway2 wrote:
               | That's sort of a chicken-and-egg problem. If residential
               | three-phase electricity were commonplace, electricians
               | would all happily handle it at their standard rates, your
               | air conditioners and refrigerators would all be running
               | on it.
        
               | MichaelZuo wrote:
               | No? It clearly takes more training and has more liability
               | since the consequences of a mistake are more serious. The
               | average billable rate would inevitably be higher
               | regardless.
        
               | jrockway wrote:
               | What kinds of mistakes are harmless at 120V @ 100A vs
               | 400V @ 30A?
        
               | rootusrootus wrote:
               | Touching 120V with dry skin is nearly always harmless.
               | 240V is considerably more exciting.
        
               | b3orn wrote:
               | Wait, there are special electricians for three-phase in
               | the US, is this like an additional certification or are
               | the normal ones scared of three phases?
        
               | kelnos wrote:
               | Not sure if there's an additional certification, but it
               | would not surprise me at all that an electrician here
               | would not want to work on a home with an unusual setup
               | that they're not particularly familiar with.
        
               | chinchilla2020 wrote:
               | There isn't. But residential electricians are
               | specialists. Then there are commercial and industrial
               | ones, etc, etc.
        
               | CapitalistCartr wrote:
               | Electricians specialize. Resi guys do residential and
               | rarely to never handle 3 phase. I do commercial and light
               | industrial because heavy industry isn't around here and I
               | despise doing resi work. Three phase is usually run
               | everywhere by the power co and a transformer (pole pig)
               | converts to single phase near the residence.
        
               | Blackthorn wrote:
               | Maybe it's a little different for just a converter, but
               | mine didn't have a problem installing a Phase Perfect and
               | running a few three-phase outlets for it.
        
             | RedShift1 wrote:
             | In Europe the wiring in the ground is always 3 phase, they
             | just connect only 1 phase. You can upgrade to 3 phase for a
             | fee and then a guy comes and switches it over. They don't
             | need to open up the streets or anything like that to get
             | you 3 phase power.
        
               | justincormack wrote:
               | Not always - I live in the countryside in the UK and we
               | seem to have single phase sadly.
        
               | youngtaff wrote:
               | Tends we live in a row of cottages and the phase is split
               | between us so every third house is on the same phase
               | 
               | Pretty sure that's standard for the UK
        
               | gambiting wrote:
               | Nearly everywhere in UK has only a single phase supply,
               | it's how the grid in this country is designed.
        
             | Blackthorn wrote:
             | You can request it all you want in North America, but you
             | probably won't get it. A three phase converter is way more
             | likely.
        
               | mcpackieh wrote:
               | You can get it if you're willing to pay for it, but you
               | may not like the quoted price.
        
               | coding123 wrote:
               | In CA it's just a matter of checking a box, then they put
               | a transformer on the PG&E pole to match your voltage reqs
               | - the wire to your pole is $90. The transformer can run
               | in the thousands probably up to 10k. Of course, if your
               | area can't handle the voltage * amperage requested, they
               | may deny it or ask for about 10k per new pole to install
               | in the ground.
               | 
               | That said you just pay that once, after that you have
               | your rate.
               | 
               | A lot of people have odd power requirements - but usually
               | not residences. Farms typically get 400V for greenhouse
               | fans, for example.
        
               | bob1029 wrote:
               | If I had a periodic need for three phase power on-site, I
               | would just purchase (or rent) a generator that can
               | provide this style of output.
        
               | mcpackieh wrote:
               | I think most home shops use phase converters, either
               | rotary phase converters or variable frequency drives.
               | With those you can create a third phase to run machines
               | that need it, although obviously you won't have as much
               | power available to you.
        
               | coding123 wrote:
               | And of course, an alternatives is to have a battery bank
               | as well with inverters - which means you can get your
               | amps - but only if you're not running 24/7. You'd have to
               | let the grid (or solar) charge you up.
        
               | Blackthorn wrote:
               | My own shop uses:
               | https://www.phasetechnologies.com/products/phase-
               | converters/...
               | 
               | It's nice because there's no motor to worry about
               | maintaining and the machines can run at full power.
        
               | Blackthorn wrote:
               | Haha, I can't get it at all here. It's not a matter of
               | paying an absurd price that will get you a PhasePerfect
               | for 10% of it. It's a matter of it just not being
               | available at all.
        
               | bluGill wrote:
               | Have you really asked? Generally it is possible if you
               | pay, but expect to pay $100,000+ to get it. Most
               | neighborhoods don't have the right wires to you pay
               | paying for all new poles and wires to your neighborhood.
               | 
               | That said, a few cities/states don't allow 3 phase to
               | residences in their building code. However most do allow
               | it, and so it is just a matter of convincing the power
               | company to run it.
        
           | hajile wrote:
           | 400v 3-phase in a house is crazy to me. I was hit with 480v
           | once (someone cut my lockout and turned the power on). That
           | stuff will outright kill you unless someone else is around to
           | help.
           | 
           | One of my favorite things about US residential power is that
           | 120v is far less dangerous when homeowners (or worse, kids)
           | accidentally do something they shouldn't.
        
             | atonse wrote:
             | I read it as 400v coming into the house, not coming out of
             | outlets... Like 220v is coming into the house in the US.
        
               | [deleted]
        
             | ohgodplsno wrote:
             | You forget to take something crucial into account: the US's
             | safety standards are laughable when it comes to
             | electricity. The standard US plug is _begging_ for people
             | to stuff things in it like say, knives, rarely if ever has
             | an earth pin, has no shutters, is massively unsafe, the
             | cable gauge is laughable, GFCI outlets are a miracle to
             | find, and the building rules are... let's just say they're
             | an invitation for house fires.
             | 
             | Most european houses have a single 400v outlet: right in
             | your kitchen, for the oven (which means the oven is going
             | to be right in front of it.) The likelihood of a child
             | playing with it is close to nil. As for adults, the vast
             | majority of people are taught to just flip the breaker and
             | work on it if needed.
             | 
             | I promise you more people died of sticking metal into US
             | outlets than from 400 volts.
        
               | lazide wrote:
               | EU countries have their own history of terrible plugs and
               | outlets, not that far back either. The 2 pin continental
               | plug (when not shuttered, which old outlets aren't) has
               | all the same issues as the old US two prong plug - but
               | twice the voltage!
               | 
               | Modern US outlets are usually shuttered, and 3 prong
               | grounded outlets have been the required standard since
               | about 1969. Which is over 50 years ago.
        
               | z2 wrote:
               | The Swiss and UK plugs and receptacles are awesome
               | because they have plastic buffers in the plug's prongs
               | and/or receptacle that make it hard to ever be able to
               | touch live metal prongs in a plug that's between 0 and
               | 100% plugged in. Schuko looks pretty safe too and that
               | standard is from almost 100 years ago! I consider myself
               | careful, but have had a metallic cover and a pen fall
               | onto North American plugs that were partially exposed
               | (thus shorting hot with neutral). Both times the outlet
               | had tamper resistant shutters which did nothing to
               | prevent ensuing fireworks.
        
               | tails4e wrote:
               | Yes the UK plug design is the best I've seen. Mandatory
               | 3rd pin to open the shutters, insulated prongs until they
               | are well disconnected, and very solid fit. More often
               | than not I see plugs half falling out of US sockets, with
               | live and exposed terminals. Thankfully it is only 110v,
               | but still a fire hazard
        
               | rodgerd wrote:
               | The UK plug is the gold standard, and for me it's one of
               | those things that would have been great if they concepts
               | had become the norm.
        
               | lazide wrote:
               | Too bad it weighs so much :s
               | 
               | Also, stepping on one in the dark is a... life changing
               | experience! Definitely pretty solid though.
        
               | codedokode wrote:
               | Will you get an electric shock from sticking a fork
               | across pins? I thought that the fork would short the
               | curcuit. More probable scenario is that one can easy
               | stick a finger between pins when plugging or unplugging a
               | device.
               | 
               | That is why the voltage should be lowered to 70 Volts.
        
               | housemusicfan wrote:
               | > _The standard US plug is _begging_ for people to stuff
               | things in it like say, knives, rarely if ever has an
               | earth pin, has no shutters, is massively unsafe, the
               | cable gauge is laughable, GFCI outlets are a miracle to
               | find, and the building rules are... let 's just say
               | they're an invitation for house fires. _
               | 
               | Literally _every single thing_ you 've asserted is
               | categorically false.
               | 
               | Earth pins have been required on outlets for nearly 50
               | years at this point. US outlets are also polarized, which
               | Europlugs are not.
               | 
               | Shutters on outlets have been mandatory in residences and
               | medical facilities for well over a decade.
               | 
               | The cable gauge is sized for the current and ambient
               | temperature.
               | 
               | GFCI outlets are required nearly everywhere there is
               | water, damp conditions (such as basements), and power
               | tools used (such as garages and outdoors) because tools
               | are most likely to have frayed and poorly repaired cords.
               | Additionally all bedrooms and living spaces now require
               | arc fault protection as a leading cause of fires is due
               | to frayed lamp cords.
               | 
               | Europe still leads the world when it comes to smoking in
               | bed as being a leading cause of house fires so I would
               | not cast stones in glass houses.
        
               | crooked-v wrote:
               | > Shutters on outlets have been mandatory in residences
               | 
               | The only shutters on outlets in any US homes I've ever
               | lived in have been... ones I put in myself.
        
               | chinchilla2020 wrote:
               | > rarely if ever had an earth pin
               | 
               | False
               | 
               | > GFCI outlets are a miracle to find
               | 
               | False
               | 
               | I don't know where some of these people come from on
               | hackernews.
        
               | jumpkick wrote:
               | Are you saying that US homes "rarely, if ever" have
               | grounded receptacles? That's not correct. All
               | construction since the late 50s or early 60s require
               | grounded receptacles.
        
             | WheatMillington wrote:
             | And it's a good thing that 110v is safer because American
             | electrical safety standards are appallingly bad.
        
             | tails4e wrote:
             | And given the US outlet design, I imagine people do come
             | into contact with 110v quite frequently!
        
           | kelnos wrote:
           | The answers and comments on [0] would seem to suggest that's
           | not true.
           | 
           | Seems the power grid has the capability of delivering three
           | phase power, but many (most?) homes in quite a few European
           | countries don't actually have all three phases delivered.
           | 
           | > _No matter how you put it, the US residential power grid is
           | conceptionally lagging._
           | 
           | That's only the case if you believe the US is "missing out"
           | on all that much with our split-phase setup. I don't think
           | that's the case, really. Even for EV charging, using the 240V
           | across the -120V and 120V lines is more or less fine. We've
           | been doing the same thing with our electric stoves, water
           | heaters, etc. for quite some time now.
           | 
           | Certainly there are some things you can do with 3-phase that
           | aren't really feasible with split-phase, but I don't think
           | most people living in the US care too much. It's true that
           | those who do are probably upset about it, though!
           | 
           | Also consider that the US power system _is_ trivially
           | 3-phase! We just don 't wire all those phases to homes, as we
           | a) don't generally see the need to, b) chicken-and-egg
           | problem suggests that most people wouldn't be able to use it
           | anyway, since appliances made for the US wouldn't be able to
           | take advantage of it.
           | 
           | [0] https://electronics.stackexchange.com/questions/625353/is
           | -3-...
        
             | SSLy wrote:
             | I live in a house built somwhere between 1900 and 1930, and
             | it's powered by 3 phases. Since deep commie era.
        
             | danieldk wrote:
             | We definitely had the wires for three phases coming into
             | the house (Europe, NL) when we got a heat pump and
             | induction cooking plate, the electricity company connected
             | two additional phases in our utilities closet. I asked
             | them, and the only thing they did was actually hooking it
             | up.
             | 
             | It was also free (there was a small cost, but the
             | government subsidizes it to encourage that people switch to
             | heat pumps).
        
             | lazide wrote:
             | Long haul power transmission is almost always 3 phase AC in
             | the US - it can be done using either 3 or 4 wires. It tends
             | to better distribute loads and requires smaller conductors
             | for the same power transmission level.
             | 
             | Split phase is almost always the last mile to residential
             | customers as it's simpler and easier to reason about (less
             | likely to have severely unbalanced phases too) and requires
             | fewer conductors.
        
           | quickthrowman wrote:
           | Here are the motor loads for a typical residence:
           | 
           | -1/2 to 3/4 HP furnace fan - 3 to 5 ton AC unit
           | 
           | Neither of these benefit from a 3-phase motor aside from not
           | having to swap out $10 start/run capacitors, the conductors
           | would be #8 for 3p and #6 for split phase.
           | 
           | You can easily power a three-phase motor on a split-phase
           | service with a VFD.
           | 
           | You _can_ get three-phase power in certain locations at a
           | residence, but you pay a monthly connection charge and
           | commercial rates.
        
             | nvy wrote:
             | Why are AC units measured in weight?
        
               | kens wrote:
               | It's actually an interesting unit: a ton of air
               | conditioning is equal to the cooling that you get from
               | melting a ton of ice per day. It has nothing to do with
               | the weight of the air conditioner. Presumably this was
               | useful in the olden days when businesses used ice for
               | cooling and wanted to know what size of refrigeration
               | unit they would need.
               | 
               | One ton of cooling is defined as 12,000 BTU/hour. The
               | "real" value is 11966; apparently it's coincidental that
               | it is so close to a round number. (One ton of
               | refrigeration is 3517 watts in metric.)
        
               | sokoloff wrote:
               | I thought the conversion was exact.
               | 
               | The latent heat of fusion of 1 pound of water at 0degC is
               | 144 BTU. 144 BTU/lb * 2000 lb/ton / 24 hr is 12000 BTU/hr
               | per ton exactly.
        
               | kens wrote:
               | No, the latent heat of fusion is 143.6 BTU/pound, not
               | 144. It's just a coincidence that the energy to raise
               | water one degF / the energy to melt ice is almost 144.
        
               | nvy wrote:
               | Good grief what an obtuse system of units.
        
               | gottorf wrote:
               | Like many customary units, the ton (of cooling) is tied
               | to historical accidents and I dare say is easier to
               | imagine for a layperson; one could visualize the coolness
               | rushing off a cubic-meter block of ice in a room, and how
               | quickly it would melt depending on the temperature. 12000
               | BTUs, in the other hand, is not as intuitive (and the BTU
               | itself is a customary unit, which is the amount of energy
               | required to raise the temperature of one pound of water
               | by one degree Fahrenheit).
               | 
               | And further, I guess there's just not much to be gained
               | by going metric and saying "14 kilowatt AC unit" vs.
               | "4-ton AC unit".
        
               | Symbiote wrote:
               | Since electricity is metered in kilowatt hours, it's much
               | easier to see the running costs of a device with a power
               | given in that unit.
        
               | Kirby64 wrote:
               | When picking an AC unit, running cost is not the primary
               | concern: sizing is the primary concern. If you pick too
               | large or small of a unit you will have issues. Too small
               | won't be able to cool, too large generally won't be able
               | to bring humidity down (outside of the newer inverter
               | units that can run slower for longer).
               | 
               | Tons (or, BTUs of cooling) makes more sense, because the
               | efficiency for a given cooling amount is variable.
               | 
               | For efficiency, we have efficiency ratings in the
               | SEER/SEER2 ratings.
        
               | Dylan16807 wrote:
               | Kilowatts are ambiguous between amount of cooling and
               | amount of electricity used.
        
           | sammorrowdrums wrote:
           | Good induction cookers and electric car chargers, heat pumps
           | and things really do often require the high voltage for best
           | function so this high voltage three-phase is also becoming
           | standard for the energy transition.
           | 
           | I had to upgrade my electricity meter and switch box (even
           | though as mentioned three-phase to the house is already
           | standard) recently in order to accommodate planned
           | environmental upgrades.
        
           | lol768 wrote:
           | > Really all modern residential connections in Europe are
           | 400V three phase electric power
           | 
           | Not the case in the UK.
        
           | gambiting wrote:
           | UK is in Europe and yet this isn't true here. Nearly all
           | residential properties in this country are wired for single
           | phase 220V. It's true on the continent though.
        
             | chartpath wrote:
             | UK scored a massive own goal and are no longer part of
             | Europe ;)
        
               | gambiting wrote:
               | I assume that's tongue in cheek, but EU and Europe are
               | two different entities - UK is still very much in Europe.
        
           | Kirby64 wrote:
           | How many residential appliances benefit from three phase, and
           | is the benefit outweighed by the additional cost of more
           | copper for the additional wires?
           | 
           | For example, a common big motor that needs a starter
           | capacitor is a HVAC unit. Usually the copper to run those is
           | extremely expensive, on the order of hundreds of dollars.
           | Adding an additional wire may add an additional hundred
           | dollars or more. By comparison, starter caps are quite cheap.
           | $20 for a HVAC sized one. That also isn't counting any of the
           | costs of three phase infrastructure for breakers etc.
           | 
           | That also isn't even counting that many appliances are moving
           | to inverter based technologies that don't utilize induction
           | motors at all, such as induction hobs. Or, many appliances
           | with no benefit from extra phases (resistive heating devices
           | such as ovens, dryers, toasters, etc).
           | 
           | Seems to me that the tradeoff is worth it.
        
             | bell-cot wrote:
             | > ...the copper to run those is extremely expensive, on the
             | order of hundreds of dollars. Adding an additional wire may
             | add an additional hundred dollars or more...
             | 
             | Vs. checking a couple commodity pricing web sites - copper
             | is currently ~$3.85 per pound.
             | 
             | I really doubt the motor of any "residential" HVAC unit is
             | heavy enough for that "hundreds of dollars" to actually pan
             | out...
        
               | Kirby64 wrote:
               | I'm referring to the cost of the wiring, not raw copper
               | stock price. Also, I mean the cost of the wire from the
               | breaker panel to the HVAC unit. On average, I'd assume
               | that the wire run is at least 50 feet. 100 feet wouldn't
               | be unusual. 100 feet of single-wire 10 gauge THHN (enough
               | to run most HVAC units here) would be ~$60. That also
               | doesn't include any additional cost by upsizing certain
               | things (conduit) that may add.
               | 
               | To note, as mentioned, copper is not the only cost here.
               | You also need another pole to your breaker, which adds
               | cost. Plus busbar upgrades. And more.
        
               | timc3 wrote:
               | 3 phases is cheaper than single line for delivering a
               | houses power. You can get away with 3 smaller cables than
               | the larger cables needed for 110V or 230V low voltage
               | single phase at a particular amperage.
               | 
               | The cost of termination of 3 phases is insignificant
               | compared to the cost of the rest of an electrical system
               | in a modern home.
               | 
               | It's the better system.
        
               | [deleted]
        
             | dijit wrote:
             | > How many residential appliances benefit from three phase
             | 
             | I know of at least one, but I am ignorant of many other
             | things and this just comes from my understanding of AC
             | motors but: Any directly connected AC fan will have
             | enormous benefits in terms of performance and efficiency
             | with three phase.
        
               | Kirby64 wrote:
               | Low current devices such as AC ceiling fans use so little
               | current that the wire gauge is largely based on the
               | minimum sizing for code standards. At least in the US,
               | you can't put anything smaller than 14 gauge (AWG) in
               | walls. Maybe in Europe they allow much smaller gauge, in
               | which case maybe it makes sense... but usually there are
               | minimum requirements for wiring since it becomes a
               | structural issue (i.e., too thin of wire will break
               | easily when pulled).
        
               | quickthrowman wrote:
               | There is no benefit to performance or efficiency with a
               | single-phase motor vs a three-phase motor.
               | 
               | Controlling the motor with a VFD is how you increase the
               | efficiency and performance of a three-phase motor, simply
               | being a three-phase motor provides no efficiency benefit
               | other than you can use slightly smaller conductors to
               | power the motor.
        
               | brianwawok wrote:
               | Why are large industrial motors three-phase? I almost
               | always see large industry getting three-phase, which I
               | assumed either gave more power or more efficiency.
        
               | thsksbd wrote:
               | It has nothing to do with efficiency (do the math on the
               | conductor gauge and it all mostly cancels out) or power
               | (idem) but the types of motors used (squirrel cage I
               | believe).
               | 
               | The problem is getting the motor to start spinning. You
               | cant start all motors on just one or two phases. And if a
               | motor isn't spinning, it's essentially a short.
        
               | quickthrowman wrote:
               | Basically what the sibling comment said, it's easier to
               | start a three-phase motor, and a three-phase motor will
               | also run more smoothly as it is powered by 3 sine waves
               | 120 degrees out of phase with each other which provides
               | constant power; versus a single-phase motor being powered
               | by a single sine wave that outputs no power at the middle
               | of the sine wave with two power peaks, which doesn't run
               | as smoothly as three-phase power with no points of zero
               | power output.
        
               | [deleted]
        
             | japanuspus wrote:
             | I read this comment as implicitly assuming two phases to
             | require less copper than three. In reality, the total
             | copper cross-section needed to transfer power in a multi-
             | phase system _decreases_ with increased number of
             | independently wired phases (all else being equal).
        
               | [deleted]
        
             | loandbehold wrote:
             | Transmitting same amount of power at higher voltage
             | requires LESS copper.
        
               | kelnos wrote:
               | But you need an extra conductor, no? Doesn't that make up
               | for the reduced amount of copper in each one?
        
               | nullc wrote:
               | For three phase vs single face, the amount of copper
               | doesn't go up since the current is shared across the
               | additional conductors-- generally the amount of copper
               | required is actually lower due to power factor
               | improvements.
               | 
               | However, for low capacity hops the cost of additional
               | insulation and extra copper needed to achieve ampacity
               | (for worst case fault currents-- the cable must have
               | higher capacity than the breaker so the breaker trips
               | first and with 3ph you have three over-provisioned
               | conductors instead of two) may make it worse off.
        
               | [deleted]
        
             | user2342 wrote:
             | > How many residential appliances benefit from three phase,
             | and is the benefit outweighed by the additional cost of
             | more copper for the additional wires?
             | 
             | Three phase wiring is so ubiquitous here, there is nearly
             | no additional cost.
        
               | Kirby64 wrote:
               | You can't just say there's no cost because you don't see
               | it. You don't have the option, so of course there's no
               | way to tell price differentiation. I'm talking purely of
               | raw material cost though. By adding a 3rd load conductor,
               | you inherently add wiring cost and complexity, which
               | should result in cost to the consumer.
               | 
               | It may be offset, as others point out, by power delivered
               | being higher (and thus, wire gauge can go down) when
               | running 3 phase... however that will largely depend on
               | the load.
        
               | bluGill wrote:
               | Most people have so few things in their house that would
               | benefit from 3 phase that the cost isn't worth it. That
               | extra wire isn't cheap, even if you downsize them all you
               | still pay more. And as others have pointed out modern
               | motors are (slowly) switching to using a VFD to generate
               | 3 phase so there is even less need (in fact in industry a
               | lot of equipment is switching to a VFD even though 3
               | phase is wired to the machine)
        
               | timc3 wrote:
               | The cost is insignificant.
               | 
               | I have monitoring on all the phases on my house (in
               | Sweden) and I can charge two electric cars, run the
               | heating in winter, run the washer and drier and cook with
               | two ovens a microwave and the induction hob at the same
               | time and everything just works.
               | 
               | Things on three phase in my home: swimming pool, sauna,
               | induction hob, electric car chargers, heating system and
               | I have sockets to plug-in welding and other power hungry
               | equipment. The rest is split on the phases. I can't
               | remember whether my solar system supplies on three phases
               | or not but I think it does.
        
             | jonhohle wrote:
             | Others have made the comment about lower current
             | requirements at high voltage, but from a maintenance
             | perspective, that $20 capacitor is a common failure part.
             | Calling an HVAC repair company to diagnosis, parts, and
             | labor it costs around $200 for anyone not electrically
             | minded. Over the life of an AC unit, starter/run caps might
             | have to replaced twice.
             | 
             | Even if an extra conductor in the line was a few hundred
             | dollars, I'd rather have one less common failure point. In
             | AZ AC is effectively required in the summer. AC outages are
             | similar to winter furnace outages in northern areas. I have
             | extra caps ready to deploy (we lose a cap about every 3
             | years across multiple units) but have never needed to
             | unexpectedly replace copper.
        
               | jrockway wrote:
               | Don't more modern AC units use VFDs that can run the
               | compressor at arbitrary speeds, which is an improvement
               | over both fixed 3 phase power and a starter capacitor?
               | Maybe this tech hasn't made it into the house-sized units
               | yet, though.
        
               | lfowles wrote:
               | It was only present on the high end when we were
               | replacing our system in 2021.
        
               | kelnos wrote:
               | Unfortunately these more modern units are still stupid
               | expensive (in the US) compared to the older style.
               | Unclear why; probably some sort of shenanigans with the
               | HVAC manufacturing companies.
        
               | amluto wrote:
               | Little variable-speed units sold as ductless minisplits
               | are fairly inexpensive in the US. They're especially
               | reasonable if you actually use them in a ductless
               | configuration, because you don't have to install ducts.
               | 
               | The fact that they might have a higher list price than a
               | conventional single-speed outdoor unit and indoor
               | evaporator coil is a red herring, as the conventional
               | units can't do anything on their own, and they need a
               | furnace and a fan added to be useful.
        
               | mindslight wrote:
               | VFDs / "inverters" are happier on 3 phase as well,
               | because the input rectifier caps can be much smaller.
               | Whereas with single phase they have to be large enough to
               | store energy for riding out the zero crossings of low
               | power delivery.
               | 
               | This whole thread is like that Dewey Cox bit. "But three
               | phase surely must use more copper, no?" "Actually it uses
               | less". Split phase is really just a great demonstration
               | of institutional momentum.
        
               | lizknope wrote:
               | I just replaced one of my two HVAC units with a variable
               | speed compressor. It cost a lot more than the single or 2
               | stage units but it is more comfortable, uses less
               | electricity, and runs at "low" to dehumidify longer.
        
               | Kirby64 wrote:
               | My point isn't that the single individual wire to your
               | HVAC is $100 vs. a $20 cap, though. There is likely
               | hundreds or thousands of dollars of additional
               | infrastructure needed to handle 3-phase input to a house.
               | You have breakers, busbars, the transformer into the
               | house is different, and on and on.
               | 
               | I agree that less failure points is nice, however you
               | have to consider the tradeoff. Is it worth $100?
               | Probably. What about $1000? $2000? If it's $2000, why not
               | just get a more efficient inverter based one, which
               | doesn't have a starter cap in the first place?
        
               | hnuser123456 wrote:
               | Just had to have my apartment's AC capacitor replaced
               | last week.
        
             | rekoil wrote:
             | > How many residential appliances benefit from three phase
             | 
             | Induction hobs, saunas, EV chargers, to name some.
             | 
             | > and is the benefit outweighed by the additional cost of
             | more copper for the additional wires?
             | 
             | Additional cost? You don't run that many 3-phase circuits,
             | so the cost is negligible, and your 110V circuits require
             | substantially higher current than ours (meaning thicker
             | wires) so if anything I'd guess the cost for wiring a US
             | home is on average higher than a European home.
        
             | Mvandenbergh wrote:
             | In many places (but not the US because of thermostat
             | standards) HVAC systems are now typically inverter driven
             | as well so that does remove some of the advantages of
             | three-phase since any individual load is single-phase
             | anyway.
        
               | briHass wrote:
               | Many HVAC systems in the US also use inverter compressors
               | now. The efficient units (which includes most minisplits)
               | are inverter. The efficiency requirements of the recent
               | government subsidy program pretty much requires an
               | inverter.
        
             | gambiting wrote:
             | Well, here in UK nearly all residential properties have
             | only a single phase supply - it can actually be really
             | limiting nowadays. Some older properties are only wired for
             | 60amp draw at 220V, meaning you can really only have an
             | electric shower and an oven on at the same time and that's
             | it, you've gone over the limit. People are finding it more
             | and more as electric cars are getting popular and turns out
             | fitting a 32amp(7.2kW) charger on a single phase 60 or even
             | 80amp supply is sometimes not feasible depending on what
             | else you have in your house already. Continental setup is
             | far superior to what we have here for this reason.
        
               | rekoil wrote:
               | > meaning you can really only have an electric shower and
               | an oven on at the same time and that's it, you've gone
               | over the limit
               | 
               | What's the deal with your electric showers anyway? Surely
               | it's more efficient to heat in a central location and
               | distribute both a cold and a hot water circuit through
               | the building...
               | 
               | Probably talking out of my ass, it's just so weird and I
               | haven't seen it anywhere other than in the UK.
        
               | muxator wrote:
               | > 60amp draw at 220V
               | 
               | You are very luky! The standard installed power for
               | residential use in Italy is 220 V, 3.3 kW.
               | 
               | My apartment runs on it. I have a small heat pump
               | reservoir for hot water, AC, induction coils for cooking.
               | I think having to cope with this objective limitation in
               | installed power really pushed me to look for maximum
               | efficiency, to the point that I could have gone to 4.5
               | kW, but it ended up being not needed.
               | 
               | Nowadays, the idea of heating water to >50 degC via Joule
               | effect in real time seems a bit inefficient to me.
        
             | Faaak wrote:
             | On the contrary, more phases = less copper.
             | 
             | Example of appliances: HVAC, induction heaters, boilers,
             | car chargers, solar panels inverters, ...
        
             | wyager wrote:
             | Three phase and high voltage are both more copper-
             | efficient.
        
             | sidewndr46 wrote:
             | inverter technology is always an induction motor. No one
             | runs an inverter to run a universal motor.
        
               | dreamcompiler wrote:
               | Brushless DC motors are always driven by inverters. They
               | aren't usually _sinusoidal_ inverters, and these things
               | are more accurately called digital electronic pulse
               | modulators, but they 're often advertised as "inverter-
               | controlled."
        
           | webmobdev wrote:
           | Three-phase power supply for residential use is common even
           | in India.
        
         | dusted wrote:
         | In Denmark, most homes have 3 phases of 240 volts, along with
         | neutral. (and protective ground, of course)
         | 
         | More power in less copper. Most items do fine with 240 volts,
         | but high-power items like ovens and electric cars can use two
         | or three. Also, we have the CEE 5P plugs, which look awesome
         | and allow you to draw a lot of juice from a single point.
        
         | Mvandenbergh wrote:
         | The US also uses a different primary network configuration,
         | typically running a three-phase network as main primary with
         | single phase primary laterals. The pole-mount single-phase
         | transformers then turn this single-phase into split-phase LV
         | for consumer use. One consequence of this is that adding three-
         | phase to a property that doesn't have it already is really hard
         | - you need to upgrade the LV service connection, the
         | transformer, and the MV lateral (since the MV lateral is only a
         | single phase). Compare that to the European system which has
         | three-phase distribution transformers and then runs three-phase
         | LV past every property. In some places like Germany, the
         | standard is to provide three-phase to every property, in others
         | like the UK, standard is single phase service connection but...
         | it's easy to add three phase since the other two phases are
         | only a few metres away, I understand the Dutch standard is to
         | run all three phases to the property but only connect as a
         | standard (you have to pay for the upgrade).
         | 
         | I think in both cases, for urban and suburban areas it is
         | standard to run the MV feeder as a normally open ring so that
         | in case of a fault in the primary, parts of the system can be
         | run from the other end of the ring by remotely operated
         | automatic breakers. What I don't know is whether US systems do
         | that at the level of the main primary only or also on the
         | laterals.
        
         | dehrmann wrote:
         | Could I run a standard computer PSU of 220V split-phase?
        
           | zeroonetwothree wrote:
           | At current rates of ballooning power requirements we will
           | soon have to
        
             | mrguyorama wrote:
             | American circuits are designed to support a constant 15amp
             | load, meaning you get 1500 ish watts. One 4090 overclocked
             | and one high end Intel CPU overclocked, plus the cooling
             | for all that, plus other parts, gets you uncomfortably
             | close to that.
             | 
             | My hope is that this limit forces the computer industry to
             | put at least one cycle into actual efficiency instead of
             | just promising a node shrink will magically fix things,
             | since we only have a few of those left really.
             | 
             | I shouldn't need to run a damn space heater to play a
             | stupid video game. At this rate, you have to think about
             | how much video game you plan to play in your electricity
             | budget!
        
               | hot_gril wrote:
               | Most video games don't require high-end gaming PCs,
               | though.
        
               | hajile wrote:
               | You can increase wire size a little and run 20 amps
               | without much trouble.
        
               | sleepybrett wrote:
               | Yes but most of your house's power outlets are sitting
               | behind a 15amp fuse.
        
           | TylerE wrote:
           | Every computer power supply I've seen in the last 10 years or
           | so is basically rated for input as something like '100-250v,
           | 50-60hz. That way they work on virtually any power grid
           | anywhere in the world, it's just a matter of having the right
           | female IEC to male <local whatever> power cable.
        
             | Gibbon1 wrote:
             | White paper I read 20-25 years ago described how those tend
             | to work. Larger power supplies are required to be power
             | factor corrected. They need to draw sinusoidal power in
             | phase with the voltage. To do that they need a power factor
             | correction front end. In the design the paper described
             | what happens is 120VC gets rectified and stepped up to
             | 240DC. Which then feeds a main DC/DC step down inverter.
             | 
             | I think the advantage of stepping up is the filter
             | capacitors are cheaper for the higher voltage. I think
             | because they handle half the current.
        
             | mrguyorama wrote:
             | Cheaper and older power supplies typically have a switch to
             | change the input voltage. DO NOT attempt to plug in and
             | turn on a power supply set to 110v to a 240 volt socket.
        
           | nullc wrote:
           | Yep, most of them are a few percent more efficient at 240v
           | too and have higher maximum power output... I run all my
           | always-on computers that way.
           | 
           |  _Generally_ anything that has an IEC power connector will
           | support running at 240v (but beware, you may need to flip a
           | switch).
        
           | ianburrell wrote:
           | Most power supplies do 100-240V so they can be used in
           | multiple countries. You might be able to find cable to
           | connect it to 240V plug, or could wire one up. But there
           | would be no advantage to using 240V.
           | 
           | The only advantage for 240V is higher power. All desktop PSUs
           | top out at 1800W because of the 120V 15A limit. There are
           | server PSU that have higher power limits that would need to
           | use 240V to reach the higher limit.
        
           | lokar wrote:
           | Most switching power supplies won't care
        
         | 2143 wrote:
         | > I have heard a three phase residential connection is common
         | in some parts of Germany
         | 
         | Over here (large country in South Asia) it's three phase by
         | default.
         | 
         | You can get single phase upon request, provided it's a really
         | really small house, shop etc.
        
         | elzbardico wrote:
         | EDIT: I stand corrected by the comments below. Readers Ignore
         | most of what I said on this comment. I was mistaken.
         | 
         | --------------------------------------
         | 
         | You have some misunderstandings in your comment.
         | 
         | Unless it is a very old construction or a smaller home, houses
         | in the US as well as most of americas are provided with one or
         | more phases derived from the secondary of a step-down
         | transformer in Y configuration (3-phase, 1-neutral => 4 wires).
         | 
         | So, for a small apartment, maybe you'll get a single phase wire
         | plus the neutral, or more commonly 2-phase wires plus neutral,
         | up to the full 3 phase wires plus neutral.
         | 
         | The phases are usually 220V between then and 120 between any
         | individual phase and the neutral connector.
         | 
         | Europeans don't have this convenience because the step-down
         | transformers give homes 3 phases in a delta configuration (so,
         | 3 phase wires, no neutral wire), so, they only have the 220V
         | between any two-phases.
         | 
         | Also, split and wall ar-conditioning systems are almost
         | universally bi-polar with a capacitor, in Europe, Asia, or the
         | Americas. As well as most refrigerators, freezers and other
         | similar appliances. In the past we used to have driers that
         | would be multi-polar, but it was never very common.
         | 
         | It is more usual to have tri-phase motors in bigger motors,
         | like those used in central AC units. And HVAC systems in the US
         | accordingly will usually require an upgrade if your home is not
         | wired with 3-phase plus neutral, unless it is a small HVAC.
         | Electrical vehicle charges also usually require 3-phase.
         | 
         | People are confusing what they have the electric outlets inside
         | their homes with what gets from the street into the
         | distribution panel in the house. Most power outlets inside a
         | house are bi-polar connectors (so, in europe, they can only be
         | 220 phase-to-phase, and in the US and most of the American
         | continent, they can be either 220 phase-to-phase or 110 V
         | phase-to-neutral. The third connector in a domestic outlet is
         | usually the ground, not another phase or the neutral.
         | 
         | The three-phases are usually split between different circuits
         | at home, trying to ensure that the load is somewhat evenly
         | split, but at the outlets, you'll have either phase-phase, or
         | phase-neutral, and this is the same in Europe or America, but
         | the americans have the flexibility to have phase-neutral dipole
         | with half the voltage that europeans don't have.
         | 
         | Regarding having smaller step down transformers close to homes
         | instead of a single giant unit, we need to remember that
         | keeping the low-tension wires short is more efficient, and this
         | is achieved by having the transformers closer to consumers,
         | instead of having a giant transformer distant from the
         | consumers.
         | 
         | I am not an American, and I know that a lot of things in
         | America could be more efficient, but power distribution to
         | residences is probably not something were europe have an edge
         | over the US.
        
           | [deleted]
        
           | sbradford26 wrote:
           | So your first statement is correct for apartments and condos.
           | Typically 3 phase comes into the building then each unit gets
           | 2 phases and a neutral ran to them. This actually works out
           | to 208V phase to phase but phase to neutral is still 120v.
           | Appliances like cooktops and ovens are definitely less power
           | when ran off of 208v. For single family homes you only get a
           | single phase, a center tapped transformer steps down the
           | voltage to 240V leg to leg so coming into the house is two
           | legs from the transformer and the center tap which is your
           | neutral. Some really large houses sometimes get 3 phase but
           | that is very rare. Usually large houses will just bump to 400
           | amp service.
        
           | LeifCarrotson wrote:
           | > Unless it is a very old construction or a smaller home,
           | houses in the US as well as most of americas are provided
           | with multiple phases in Y configuration (3-phase, 4 wires,
           | one neutral).
           | 
           | > So, for a small apartment, maybe you'll get a single phase
           | wire plus the neutral, or more commonly 2-phase wires plus
           | neutral, up to the full 3 phase wires plus neutral.
           | 
           | > The phases are usually 220V between then and 120 between
           | any individual phase and the neutral connector.
           | 
           | I am an American - an electrical engineer in the Midwest -
           | and I was on roofs last week after a tornado came through our
           | town, working with the distribution panels. What you said is
           | not correct. Homes get 240/120 nominal line voltage, or
           | 220/110V at the load, 180 degrees out of phase, plus a
           | neutral.
           | 
           | That is not the same as two phases plus the center conductor
           | of 3-phase Y.
           | 
           | In industrial facilities, it's reasonably common 208V 3-phase
           | in a Y configuration, with three wires each 120 degrees out
           | of phase with each other. This is typically used for lighting
           | circuits, because it's 120 phase to ground and can use
           | commodity bulbs and ballasts. More commonly, machines will
           | run off 480V 3-phase, which is 277 phase-to-ground.
        
             | elzbardico wrote:
             | I stand corrected and added a disclaimer in my original
             | comment. Thanks for teaching me something I assumed
             | incorrectly.
        
               | coding123 wrote:
               | Just for knowledge sake: you are correct that there are 4
               | wires:                   1 - hot 1 120 v         2 - hot
               | 2 120 v         3 - neutral         4 - ground
               | 
               | The hot 1 and 2 are 180 degrees out of phase with each
               | other which is why 240v appliances can consider having
               | those 2 wires (and at least the neutral) to be a 240v
               | appliance.
               | 
               | And to be more pedantic about it, the ground is not
               | provided not by the power company but the ground. I have
               | 3 lines coming from the grid to my pole, line 1, 2 and
               | the neutral that is created by the transformer. The
               | ground comes from my ground - a long copper wire that
               | goes a few feet down and back up. All ground connections
               | in the (future) house will go there. Ground is also
               | bonded with neutral at the box on my pole.
        
             | MichaelZuo wrote:
             | Same in Canada, though with 600V 3-phase instead of 480V,
             | mostly.
        
         | no-reply wrote:
         | Three phase residential connection is also common in India (at
         | least some bigger cities).
        
         | amluto wrote:
         | How many residential devices actually ought to contain a three-
         | phase motor running at fixed frequency? (And I mean now, in
         | 2023, not in 1990.)
         | 
         | I can think of three, sort of:
         | 
         | 1. A well pump, pumping from a high-producing well, into a tank
         | or pond at the surface, where the pump is sized to efficiently
         | pump somewhat less than the well's production.
         | 
         | 2. A pool or pond pump which, by some miracle, has been
         | correctly sized for the system, and which, by some other
         | miracle, is more appropriate in the application in question
         | than an Intelliflo VSF or similar pump.
         | 
         | 3. HVAC fans. But these are usually pretty small, and better
         | systems usually use ECM motors.
        
           | Corrado wrote:
           | There are tons of people who have garages with table saws,
           | air compressors, etc. that would benefit from 3 phase power.
        
             | ajross wrote:
             | I think that's overselling. I mean, sure, 3 phase is better
             | for motors and you can get more power a little more
             | efficiently and with less vibration to deal with in the
             | mechanical design. And that's valuable. But come on, US
             | workshop afficionados are doing just fine. No one is crying
             | in their shop wishing for the blissful experience of a
             | Danish band saw or whatever. It's better. It's not _that
             | much_ better.
             | 
             | What actually wins this fight is on the other side. A two-
             | connector polarized NEMA 1-15 plug is a tiny, convenient,
             | easy to use form factor that will still deliver 1400W. The
             | experience of a normal consumer plugging in their normal
             | junk in the US is just plain superior to the poor folks
             | across the oceans charging their devices with BS1363
             | connectors that are _almost bigger than the phones_. And
             | don 't even get me started on Europlug.
        
               | housemusicfan wrote:
               | BS1363 are comically oversized because they contain
               | internal fuses, due in part to the strange ring main
               | design, itself a vestige of WWII copper shortages.
        
               | pmyteh wrote:
               | BS1363 plugs are joyfully oversized, yes (and make
               | excellent caltrops if dropped) but they are in other ways
               | _excellently_ engineered. Inherently polarised, fuses to
               | protect the appliance wiring[0], socket shutters that
               | open on the earth pin only to prevent vigorous insertion
               | of metal by children, sleeved conductors to avoid shock
               | when partially inserted, essentially unbendable...
               | 
               | Plus, I will fight anyone who suggests that 1400W is
               | enough for a decent kettle ;-)
               | 
               | [0] Admittedly this was mostly included to offset the
               | idiosyncrasies of final ring circuit wiring, but it's
               | still better than just a big breaker.
        
               | shrx wrote:
               | Every time I try to charge something from a US socket the
               | charger cable will frequently fall out of the socket due
               | to poor design tolerances. Never an issue with EU
               | sockets.
        
           | liquidgecka wrote:
           | I have all three of these and absolutely none of them contain
           | (or will contain at any point) a three phase motor. All three
           | of these use variable speed motors in my house. I suspect
           | even more will moving forward as well. So honestly three
           | phase is pointless as I just need "power" to drive the
           | variable speed controller system. My hottub has fixed speed
           | 220 pumps but its old. I suspect newer systems would be
           | moving to variable speed as well.
           | 
           | I think your pretty spot on that most people do not need 3
           | phase, even in the limited cases you mentioned. =)
        
         | dfox wrote:
         | The split phase arrangement comes from Edison's DC systems. For
         | large installations they found out that the losses were
         | unacceptable and solved thet by running the lighting on 220V
         | with sets of two 110V bulbs in series, usually combined with
         | some somewhat funky wiring scheme in order to even more reduce
         | the required wiring cross-section (it is somewhat reminiscent
         | of later British ring mains construction and strikingly similar
         | to various arrangements for powering long LED strips). This is
         | also the reason why it is somewhat common for the US commercial
         | lighting to use 220V.
         | 
         | Three phase for residental connection is pretty much a standard
         | everywhere with 230/400V system. Only small flats and really
         | small houses get single phase. This is because the 230/400V
         | output of the larger distribution transformer is inherently
         | threephase and this gets distributed to essentially all the
         | points of connection and the only reason why there are single
         | phase residental connection is that they are slightly cheaper
         | (both in terms of fixed monthly payment for capacity and in
         | terms of initial installation costs). While in US the input to
         | the typical residental pole/pedestal mounted local distribution
         | transformer is already single phase, so you cannot really get
         | three phases without running additional wires to the substation
         | (and probably also having you own dedicated distribution
         | transformer) and thus in a residantal area you are simply stuck
         | with split-phase.
        
           | sokoloff wrote:
           | > solved thet by running the lighting on 220V with sets of
           | two 110V bulbs in series
           | 
           | A related tip is to build a "dim bulb tester" to help you
           | diagnose short circuits on mains-powered equipment. I have a
           | traditional incandescent lightbulb in a porcelain socket
           | wired in series with an outlet (and a switch). A non-shorted
           | load will tend to work pretty well as the cold/cool
           | incandescent bulb is fairly low resistance in series with the
           | load. A shorted load will light up the light bulb brightly
           | but not trip any breakers, allowing the opportunity to do
           | some troubleshooting on the bench.
           | 
           | I've also used this concept several times to find short
           | circuits in house wiring. Put the dim bulb tester in series
           | with the circuit that's shorted and then, using a non-contact
           | voltage tester, find where the measurement on the NCVT
           | changes. That's likely where your short is.
           | 
           | In building such a device, you're on your own liability-wise;
           | please don't be dumb.
        
             | mindslight wrote:
             | When I was a kid, I (ab)used this trick by wiring around a
             | dozen 100 watt bulbs in parallel, between the line and a
             | "probe". It was great fun for zapping whatever I wanted,
             | writing stuff on metal, etc. In retrospect the biggest
             | safety issue I missed was the light from the arc.
        
           | MrBuddyCasino wrote:
           | Another thing Americans miss out on - the "boost" function on
           | modern induction stoves. Since the oven usually gets one
           | phase and the cooking fields get two dedicated phases of the
           | 400V lines, you can use "boost" to steal power from the other
           | phase. Water boils even faster than in a tea kettle!
        
             | Kirby64 wrote:
             | What do you mean? Comparing a UK Bosch induction hob with a
             | US one, they both seem to offer roughly 2.5kW of power in
             | normal mode, and both offers a "boost" functionality that
             | boosts the output temporarily to 3.6kW.
             | 
             | Stove outlets can handle 12kW in the US... So there's
             | plenty of power to go around. Built in outlets can go even
             | higher, with 240V/60A being somewhat common for larger
             | appliances.
        
               | MrBuddyCasino wrote:
               | It is hard to find numbers, but combining phases is
               | definitely how it works for some models, eg Miele
               | PowerFlex uses "booster output of up to 7.4 kW" [0]. This
               | is why you can only use it for one field.
               | 
               | > Stove outlets can handle 12kW
               | 
               | wasn't aware, in that case I was wrong, good for them
               | 
               | [0] https://www.miele.co.th/domestic/1512.htm?&&&info=200
               | 004302-...
        
             | andersa wrote:
             | Sure would be nice to have some kind of hyper boost
             | setting. There's a 3 phase connection, so why don't they
             | use it? Time to heat that one pot of water with 11 kW.
        
               | [deleted]
        
               | Ekaros wrote:
               | Having 3 different inducting circuits would be hard to
               | fit and make less even heating distribution. Also I think
               | they would induct to each other. Also 11 kW could be
               | dangerous with empty containers that is quite a bit of
               | power. Like resistive heaters get red hot at lower power.
        
               | andersa wrote:
               | There are actually some stoves out there that can use two
               | phases for one large pot, reaching 7.2kW. For example,
               | Miele stoves with the "PowerFlex" feature do this (that
               | is quite the big brain name given the context).
               | 
               | Since it is possible to do for two phases, why wouldn't
               | it also work for 3? More power!
        
               | dtgriscom wrote:
               | More power! https://www.youtube.com/watch?v=kBNPAJLhKZ4
        
             | sbradford26 wrote:
             | American induction cooktops also have boost functionality.
             | All boost does is temporarily increases the power output
             | usually at the expense of other elements. Power isn't
             | "stolen" from other phases. Usually the reason why the
             | cooktop cannot be in boost mode the entire time is cooling
             | related.
             | 
             | https://www.subzero-
             | wolf.com/assistance/answers/wolf/common/...
        
             | chinchilla2020 wrote:
             | It's just increasing the power draw. There is no concept of
             | 'stealing power from another phase'
        
           | bruckie wrote:
           | > solved thet by running the lighting on 220V with sets of
           | two 110V bulbs in series
           | 
           | Sounds like an exciting day when one of your bulbs burns out!
        
             | bitdivision wrote:
             | Bulbs normally burn out open, breaking the circuit. And in
             | the unusual case that they don't, I would imagine the thin
             | wires leading to the filament will melt, also breaking the
             | circuit.
             | 
             | And if all else fails you your circuit breaker should flip.
             | 
             | If bulbs normally failed short, then you'd have circuit
             | breaker's flipping a lot more often.
        
             | jefftk wrote:
             | Why? A burned-out bulb fails open not closed.
             | 
             | If it failed closed then a bulb burning out would trip the
             | circuit breaker.
        
               | sokoloff wrote:
               | > Why? A burned-out bulb fails closed not open.
               | 
               | In electrical circuit terminology, "open" means "not
               | connected" while "closed" means "connected/shorted".
               | 
               | That's different from direct translation of Chinese (and
               | I think several European languages) where "open the
               | light" means to turn it on (by closing the circuit,
               | naturally).
               | 
               | I think it's most common English engineering usage (by
               | far) to say that a burned out lamp fails open [circuit].
        
               | jefftk wrote:
               | Whoops, sorry, I had them reversed!
        
               | sokoloff wrote:
               | Interesting/random side note: modern mini Christmas light
               | bulbs do burn out (mostly) closed:
               | https://www.youtube.com/watch?v=0MOpfT0f7bQ&t=179s
        
               | unethical_ban wrote:
               | To close a circuit is to connect it, correct? So when the
               | filament burns out, the circuit breaks, which is an open
               | circuit, correct?
        
       | jraph wrote:
       | (edit: this comment is quite useless, I need to leave it to keep
       | the discussion understandable)
       | 
       | Interested in the answer which I don't have.
       | 
       | That said, UK is wired to the continent, which runs at 230V, 50
       | Hz.
       | 
       | Everyone runs at the exact same frequency (same fluctuations) at
       | any moment across the whole continent for technical reasons.
       | (edit: UK is actually not synchronized with the continent, I
       | didn't know that either).
       | 
       | I guess having the about the same voltage as the rest of the
       | continent is at least convenient (edit: apparently it's not
       | exactly the same?).
       | 
       | So I guess the question is US vs the European continent.
       | 
       | Curious about the rest of America (North and South).
        
         | projektfu wrote:
         | North America is generally on 220-240V split phase with NEMA
         | compatible plugs. In Mexico, the plugs are often ungrounded and
         | only compatible, not identical to NEMA. In my house in the US I
         | have mostly 120V circuits with a few 240V for appliances.
         | 
         | Brazil is a bizarre mess of 127V single phase in most of the
         | south and 220V single phase in the rest. They are supposed to
         | use euro-style grounded receptacles but often have installed
         | euro and NEMA bi-compatible plugs at 220V or 127V. A lot of 220
         | circuits only carry 8-10A.
         | 
         | Argentina uses the Australian style receptacle with 220V 50Hz.
         | 
         | I'm not sure about the rest of South America but I think
         | Uruguay and Paraguay are compatible with Argentina and the rest
         | are on 60Hz and generally 220V.
         | 
         | I'm surprised nobody mentioned Japan, and its varied system.
        
         | mytailorisrich wrote:
         | It's almost North America (and some friends) vs rest of the
         | world, really:
         | 
         | https://en.wikipedia.org/wiki/Mains_electricity_by_country
        
           | [deleted]
        
         | HPsquared wrote:
         | UK interconnections to the continent are via HVDC links; the UK
         | grid is not synchronous with the continental grid.
        
         | ourlordcaffeine wrote:
         | The uk grid is not synchronized with the european grid, it is
         | just HVDC interconnected.
         | 
         | You are right about the european grid, it is synchronized
        
         | baz00 wrote:
         | Picking a small point from your comment I find interesting, the
         | voltages vary considerably across Europe depending on all sorts
         | of factors.
         | 
         | In the UK at least it's from around 216 to 253 volts. Mine is
         | sitting at 249 now.
        
         | [deleted]
        
       | thrdbndndn wrote:
       | TIL UK (or EU) uses 230V, not 220V like my country.
        
         | oblio wrote:
         | Po-ta-toe - po-ta-toh. You can use 220V stuff with 230V plugs.
         | There are fluctuations for each network, anyway.
         | 
         | Which country are you talking about?
        
           | thrdbndndn wrote:
           | China.
        
         | alex3305 wrote:
         | In The Netherlands the allowed voltage tolerance is 10% by law.
         | So everything between 207V and 253V should be fine. And we also
         | had 220V until 1989.
        
         | jonatron wrote:
         | UK actually uses 240V, which happens to be within +10% of 230V.
        
           | soneil wrote:
           | This is my favourite story about standardization.
           | 
           | It used to be the continent used 220V, and the UK used 240V,
           | until we standardized on 230V.
           | 
           | The UK defines this as 230V -6% +10% (i.e. 216.2V - 253.0V),
           | and nominal supply is 240V
           | 
           | The continent defines this as 230V -10% +6% (i.e. 207.0V -
           | 243.8V), and nominal supply is 220 or 230 by region.
           | 
           | We called this harmonisation - in reality it's more like
           | agreeing to disagree. We just fudged the tolerances until
           | everyone was happy.
           | 
           | (To put some context around this - most sites don't receive
           | nominal supply. The actual voltage delivered depends on your
           | distance to the local substation. Typically they over-deliver
           | such that sites closest are a little over, sites furthest are
           | a little under. If they actually delivered +-0%, sites at the
           | edge of their network would be further from nominal. So end-
           | user equipment should be built to expect variation.)
        
             | thrdbndndn wrote:
             | 230V+-6% should be enough for both though, right?
        
               | soneil wrote:
               | That'd give an upper bound of 243.8, which is far too
               | close to 240 to be practical. As I tried to add, there is
               | some necessary and natural deviation from nominal to
               | account for path loss etc. 230+-6% only allows 240 to
               | deviate by 1.5%, which isn't much scope at all.
               | 
               | I believe +-10% was the traditional definition, so they
               | just trimmed a little off the top end so it strayed less
               | from Europe's definition - but not enough to actually
               | affect nominal distribution.
        
         | [deleted]
        
         | jdietrich wrote:
         | The UK used to be nominally 240V and a lot of EU countries used
         | to be 220V, but we harmonised on 230V because it's comfortably
         | within the tolerance bands for both. Nothing really changed in
         | practice - UK installations still deliver about 240V and most
         | EU installations deliver about 220V - but it was convenient to
         | have a common standard.
        
           | PaulKeeble wrote:
           | My solar inverter consistently finds the UK grid at 243-245V.
        
           | gulikoza wrote:
           | My UPS is showing 236V at the moment (continental EU). We
           | also used to have 220V IIRC, but are now closer to 240V it
           | seems.
        
       | rinron wrote:
       | Here is a really great video that goes over the history
       | https://www.youtube.com/watch?v=7yRGvMgieEU Sometimes we think
       | about the technical reasons and forget of the human and the
       | developmental process that can sometimes have an effect on how
       | things are today. spoiler for the video - its because too many
       | 110v light bulbs were already in place by the time 220v ones were
       | made and it was too expensive/difficult to change. kind of
       | reminds me of why the US never switched to metric.
        
       | chociej wrote:
       | Nobody's pointed it out yet, so I'll mention it:
       | 
       | US voltage is 120 V (240 V phase to phase), not 110 V. And while
       | 115 V is within service tolerances specified by ANSI C84.1 (114 V
       | to 126 V), that's not the nominal value.
        
         | c-linkage wrote:
         | 110V is the Room Mean Squared (RMS) voltage.
         | 
         | https://www.electrical4u.com/rms-or-root-mean-square-value-o...
        
           | p1mrx wrote:
           | No, 120V is the nominal RMS voltage; the peak is
           | 120V*sqrt(2)[?]170V.
        
           | andromaton wrote:
           | The *root mean square is 120V.
        
         | version_five wrote:
         | Thanks, I'm in canada and I know we're 120, I was wondering if
         | there was some reason the US was different and I'd just never
         | heard about it. Iirc Japan, at least part of it, may actually
         | be 110.
        
           | _whiteCaps_ wrote:
           | https://electronics.stackexchange.com/questions/614270/why-d.
           | ..
           | 
           | Japan uses 100V and 50/60 Hz depending on where you are in
           | the country.
        
             | hot_gril wrote:
             | Speaking of Japan and frequency differences, one funny
             | indirect consequence of the power differences is the video
             | game Super Smash Bros Melee having separate NTSC and PAL
             | versions, one at 60Hz and another at 50Hz, and consequently
             | running at 60fps or 50fps (unless you override this at
             | start). For good players, 50fps changed the game a lot, so
             | they'd always use NTSC or override to 60. But PAL Melee
             | also had other gameplay changes.
        
               | aeyes wrote:
               | A lot of games on the Mega Drive / Genesis didn't
               | properly adjust their speed for PAL/NTSC, for example
               | Sonic 1. They'd just run slower/faster according to VDP
               | clock.
        
             | w0mbat wrote:
             | It's really annoying as Japan has lots of wonderful vintage
             | secondhand synthesizers for sale, but being domestic market
             | models they often have non-switching power supplies that
             | require 100 V.
        
               | _whiteCaps_ wrote:
               | Yup! I've got a 120->100V step down transformer for my
               | Minidisc player.
        
         | ezfe wrote:
         | While it's true, the US does supply 120V+-5%, appliances and
         | equipment are operable on a much wider range.
         | 
         | For example, my laptop charger is rated for 100-240V, which is
         | not uncommon.
        
           | version_five wrote:
           | Laptops and other electronics are often the same between
           | North America and europe, just with a different plug, thus
           | the wide tolerance. For anything with a motor or coil this
           | probably won't work
        
           | doikor wrote:
           | The 100V low end is there due to Japan.
        
           | p1mrx wrote:
           | 120V-5% is still greater than 110V.
           | 
           | Power supplies are rated for 100V because that's the voltage
           | in Japan. Though the tolerance would probably be useful for
           | running a _really long_ US extension cord.
        
             | MichaelZuo wrote:
             | Technically they function fine as low as 95V for the worst
             | case scenario, if they're well built.
        
               | Moru wrote:
               | My old computer started burning in some internal cabling
               | about 30 years ago. Turns out our power wasn't 230 V when
               | the power company came and set up a machine to make a
               | graph. Some times of the day it could be much lower and
               | that made my ancient atari converted to a towerbox to
               | burn the cable to the harddrive on booting.
        
               | Kirby64 wrote:
               | Nothing to do with well built usually, just designed to
               | work in all regions (specifically, Japan, which has 100V
               | power for because of... reasons).
        
           | analog31 wrote:
           | That's a fairly recent development, mainly limited to
           | switchmode power supplies.
        
         | tragiclos wrote:
         | It's about looking at supply vs demand. Electrical devices are
         | often labeled by the minimum voltage they require to operate.
         | 110 V is commonly used because the device can operate reliably
         | on a 120 V distribution system.
        
           | darknavi wrote:
           | I learned recently that Japan is often on 100V power so I'd
           | think a lot of international components would support
           | 100-240V.
        
         | rootusrootus wrote:
         | It's a bit of a pet peeve of mine. We've been standardized on
         | 240/120 since 1967, and still many people insist on saying 110
         | and 220. It hasn't been 110V since well before 1967, either --
         | it was increasing over time before they locked it at 120.
        
           | TheCleric wrote:
           | 220, 221, whatever it takes.
        
         | hajile wrote:
         | This is partially done to compensate for terrible wiring. Lots
         | of people are fond of using small wires and going long
         | distances leading to a lot of voltage drop. They often send
         | 125v or so from the transformer which is 123-124 at the panel,
         | 120 v or so at the receptacle, and >100v after someone decides
         | to run something on a few hundred feet of #18 extension cord.
        
       | codedokode wrote:
       | I would like the voltage to be lowered even more, to 70 Volts.
       | The reason is that 240V is very dangerous and can easily kill a
       | human. But it seems governments care only about saving aluminium
       | in wires rather than lives.
        
         | mcpackieh wrote:
         | > _But it seems governments care only about saving aluminium in
         | wires rather than lives._
         | 
         | That's needlessly inflammatory. Both the US and UK governments
         | have numerous electrical standards and regulations designed to
         | keep people safe despite unsafe power levels in residential
         | wiring. You might argue that they aren't doing enough in this
         | regard, but to say they _only_ care about saving metal just isn
         | 't true.
        
         | mdekkers wrote:
         | Death by electrocution is incredibly rare in the EU, what are
         | you talking about? Data, or hold your peace.
        
           | codedokode wrote:
           | Here is a recent case, for example [1]
           | 
           | [1]
           | https://www.dailymail.co.uk/news/article-12042495/Italian-
           | gi...
        
         | vel0city wrote:
         | > But it seems governments care only about saving aluminium in
         | wires rather than lives.
         | 
         | I go even further on trying to save aluminum in my wires by not
         | using any aluminum wires. Aluminum wiring is pretty rare in the
         | US and largely considered a nightmare to work with.
        
       | 1970-01-01 wrote:
       | >Why do they use different frequencies like 50Hz, 60Hz?
       | 
       | I've never found a technical answer for the 50Hz vs 60Hz
       | question. It does seem to be an arbitrary standard.
        
         | michaelrpeskin wrote:
         | My guess: in the old days when electricity was new, power
         | conversion was done with Rotary converters which were basically
         | a fused motor-generator. To change voltage you had different
         | winding and number of poles. So if you were at 60 Hz, you have
         | the magic of being divisible by a lot of numbers and you could
         | easily go up down by common integer values.
         | 
         | Then when Europe was standardizing, they wanted to be all
         | metric, and 50 was close enough to 60 and still could become
         | 100 by doubling.
         | 
         | I don't know, those are just pure guesses.
         | 
         | I think when you come from the engineering/tinkering side of
         | things, you like units with easy integer fractions (12 inches
         | in a foot is really easy to work with at human scale). When you
         | come from the science side of things, you like easy decimals
         | and that's why metric wins there.
        
       | nzach wrote:
       | My understanding is that this choice is a balancing act between
       | having good efficiency for long distances transmissions (230v)
       | and having a lower peak load in the grid (110v) for desely
       | populated areas. But I'm no expert in this matter.
       | 
       | Where I live (Brazil) is commom to have both. In the big cities
       | you will find 110v and outside that you are more likely to find
       | 220v. And yes, it is a pain if you move from a 220v city to a
       | 110v one. But besides that most people don't care about having 2
       | standards.
       | 
       | For anyone interested there is a semi-relevant
       | TechnologyConnections video[0] where he discusses the popularity
       | of kettles as way to heat water in the US.
       | 
       | [0] - https://www.youtube.com/watch?v=_yMMTVVJI4c
        
         | johann8384 wrote:
         | The lines in your neighborhood that feed your house are 7200v,
         | that goes into a transformer in the yard or on the pole which
         | provides 240v to your house. Larger transmission lines are
         | 38000 volts. There are other voltages in place as well.
        
       | throw0101b wrote:
       | _Kathy Loves Physics & History_ did a video on this, and the
       | reason is basically legacy:
       | 
       | * https://www.youtube.com/watch?v=7yRGvMgieEU
       | 
       | Edison originally purchased others' dynamos, especially Wallace-
       | Farmer, which was 110V (DC):
       | 
       | * https://americanhistory.si.edu/collections/search/object/nma...
       | 
       | * https://en.wikipedia.org/wiki/Moses_G._Farmer
       | 
       | So Edison's long-legged Mary-Ann was also 110V:
       | 
       | * https://www.collectorsweekly.com/stories/82967-thomas-edison...
       | 
       | * https://edison.rutgers.edu/life-of-edison/inventions?view=ar...
       | 
       | * https://americanhistory.si.edu/collections/search/object/nma...
       | 
       | Light bulbs in the early 1900s were first designed for lower
       | voltages, and the grid slowly raised things over time, but at
       | some point they couldn't go any higher because it would start
       | blowing things, so they were 'stuck' in the 110-120V range.
        
       | tomohawk wrote:
       | In the US, you can have electric receptacles in bathrooms. In
       | fact, code requires it. You can plug in 120V electronics and
       | appliances no big deal.
       | 
       | In the UK, this is not allowed because 240V is not a good idea in
       | bathrooms.
        
         | kypro wrote:
         | Most bathrooms in UK hotels will have two pin 115v & 230v
         | outlets for shavers. You can get them installed in homes too I
         | believe, but most residential properties don't have them.
         | 
         | They really are just for shavers though. You can't run anything
         | high power without blowing the fuse. I believe Americans often
         | use hairdryers in bathrooms. We definitely can't do that.
         | 
         | That said, we do have electric showers in UK bathrooms but
         | legally those need to have a kill switch installed.
        
         | tzs wrote:
         | But it is allowed in most of the rest of Europe. I believe they
         | do require those to have GFCI (as does the US since 1975). Does
         | the UK disallow them even with GFCI?
        
       | kelnos wrote:
       | I found it somewhat funny that the question included:
       | 
       | > _Explain me with calculation._
       | 
       | As with many things related to technology, decisions are very
       | often made for seemingly arbitrary (or political, or economic, or
       | competitive-advantage) reasons, not because of some calculation
       | that was done that proved a decision optimal.
        
       | lprd wrote:
       | I spent about a decade in Europe and really enjoyed learning
       | about how their electrical grid works. The ability to directly
       | plug most appliances without needing to buy extra adapters was
       | amazing. Boiling water also took half the amount of time.
       | 
       | If memory serves, Thomas Edison used a 110v DC power supply to
       | create a system of electricity for people. Meanwhile, Nikola
       | Tesla invented the three-phase 240v Alternating Current (AC).
       | Tesla was clearly a man ahead of his time (even by today's
       | standards).
       | 
       | tldr; Europe's grid is vastly superior to America's.
        
         | mixmastamyk wrote:
         | There's a special plug for the oven, no adapter needed.
        
         | gattilorenz wrote:
         | "The ability to directly plug most appliances without needing
         | to buy extra adapters was amazing" unless you live in Italy,
         | Switzerland, France (they have a socket with the ground
         | sticking out I think), Poland, the UK, Denmark... it's getting
         | better and better due to the use of DC and the reduced need for
         | grounding, though
        
       | Egoist wrote:
       | Some devices can also be more efficient when using 230V. Eg: PSUs
       | 
       | https://electronics.stackexchange.com/questions/469913/compu...
        
       | getarofilter wrote:
       | [dead]
        
       | vonwoodson wrote:
       | Because, Freedom. And, because America. **===
       | 
       | Now, I'm going to go talk to My Fellow 'Mericans about continuing
       | to not use the metric system.
        
         | otherme123 wrote:
         | I am european. Regarding to the metric system, IMO americans
         | are wrong. But regarding to electricity, americans have it
         | better than Europe: France, UK, Italy, Switzerland, Denmark and
         | Germany have their own sockets, and that after a recent spread
         | of the german Schuko. We shouldn't lecture americans about
         | changing things to use a standard.
        
           | vonwoodson wrote:
           | There's nothing "wrong" about being The Best! #FREEDOM
           | #TheseColorsDontRun #Merica
        
       | HPsquared wrote:
       | The 50Hz and 60Hz is quite noticeable. I'm used to hearing mains
       | hum at 50 Hz, so hearing it at 60 Hz sounds a little different.
       | (You can sometimes hear it in audio recordings etc).
       | 
       | 50 Hz is about a G, and 60 Hz is about a B-flat. Video
       | comparison: https://youtu.be/pMtn-loUrg8
        
         | dvh wrote:
         | There was a video recently where YouTuber diodegonewild was
         | fixing old power supply, he turned it on, listened to it and
         | said "the transformer has DC offset on it, because it's humming
         | at 50Hz, the magnetostriction doesn't care about polarity,
         | healthy transformer hums at 100Hz, I think one of the diodes in
         | bridge rectifier is bad" and he was right.
         | 
         | https://www.youtube.com/watch?v=bWxS2njU-JI&t=355s
        
       | ChrisArchitect wrote:
       | (2014)
        
       | consp wrote:
       | It's not all that weird though. Until the 1970's we had (in NL)
       | 127 in some and 220v in other places which could either be 127v
       | to ground, 220v to ground or 220v line-to-line. By around mid
       | 2000's everything was switched to 230/400v for standardization in
       | Europe, so it's not that long ago we still had some lower
       | voltages.
        
       | sph wrote:
       | Relevant Technology Connections video: "The US electrical system
       | is not 120V" https://www.youtube.com/watch?v=jMmUoZh3Hq4
        
       | PrimeMcFly wrote:
       | Better yet why does the UK use those ridiculous cumbersome over-
       | designed plugs?
       | 
       | Or, even more curious, why are so many British authorities so
       | bizarrely (to the point it's funny) protective over electricity,
       | fining people and threatening to call police on people who try to
       | charge their phones in train stations, for example?
        
         | tgbugs wrote:
         | The tradition answer to this question is surely this wonderful
         | Tom Scott video: https://www.youtube.com/watch?v=UEfP1OKKz_Q.
        
         | dwb wrote:
         | Granted I grew up with them, but I like them. They can be
         | annoying to travel with, and accidentally stepping on them
         | barefoot is very painful, but apart from that the size is
         | handy. I've never had them slip out of the socket, for
         | instance, like US or EU plugs.
        
           | PrimeMcFly wrote:
           | > They can be annoying to travel with
           | 
           | That's my main problem since I travel a lot, or used to at
           | least.
        
           | vladvasiliu wrote:
           | > I've never had them slip out of the socket, for instance,
           | like US or EU plugs.
           | 
           | Aside from old-style type-C plugs (two prongs) in old
           | sockets, I've never seen an EU plug work itself loose in a
           | socket, let alone slip out of it. Usually, there's the
           | reverse problem: they're difficult to unplug, even when you
           | want to.
        
           | JoeAltmaier wrote:
           | That always seemed to me, to be a fabulous danger. Reach for
           | your towel on the counter, tangled with the hair dryer cord
           | and the hair-dryer is pulled into the bathtub. Yow!
           | 
           | In the US, the cord would likely pull out of the wall,
           | safely.
        
             | pjc50 wrote:
             | > hair-dryer is pulled into the bathtub
             | 
             | What hairdryer? British building regs restrict you to an
             | isolated "shaver" socket in the bathroom which takes
             | different plugs. You can't drop a hairdryer in the bath
             | unless you play silly games with extension cables.
        
               | OkayPhysicist wrote:
               | The British paranoia about bathroom electrical devices
               | has always amused me. Stick a GFCI on every outlet in the
               | bathroom, then it doesn't matter if you're swimming with
               | a toaster or an electric shaver. Heck, it was uncommon to
               | even find a light switch inside the restroom.
        
         | jraph wrote:
         | > cumbersome over-designed
         | 
         | It's a pain they are not the same as the rest of Europe, but
         | what is cumbersome and over-designed about UK plugs?
         | 
         | Follow up question, why Swiss plug needed to be so close to the
         | rest of Europe, but different anyway? (same distance between
         | the 2 pins, but the pins are a bit thinner and the ground is in
         | the opposite way).
        
           | mytailorisrich wrote:
           | British plugs are big but they are flat (cable runs parallel
           | to wall), which actually makes them less cumbersome than EU
           | ones because you only need a small gap between wall and
           | furniture/whatever.
        
             | crote wrote:
             | A very significant fraction of Schuko plugs is also
             | 90-degree angled, though. Angled is neat for furniture, but
             | straight-out is better for unplugging and high-density
             | power strips.
        
           | PrimeMcFly wrote:
           | > It's a pain they are not the same as the rest of Europe,
           | but what is cumbersome and over-designed about UK plugs?
           | 
           | The size is definitely cumbersome. Look how much bigger they
           | are than US/EU/AU plugs, basically any other countries plugs.
           | 
           | I'd call having a fuse in the plug itself over-designed.
           | 
           | > Follow up question, why Swiss plug needed to be so close to
           | the rest of Europe, but different anyway?
           | 
           | I have the same question about AU plugs. Literally the same
           | as the US plugs (newer ones that don't have one side larger
           | at least), just at an angle.
        
             | jonatron wrote:
             | The fuse in the plug is necessary to protect the wiring on
             | ring circuits.
        
               | PrimeMcFly wrote:
               | Other countries get by just fine without it.
        
               | wongarsu wrote:
               | Other countries don't use ring circuits to the extend the
               | British do. We just rate every outlet to the specs of the
               | wire in the wall, but the British have a 30A ring that
               | serves multiple 13A outlets. As a consequence they need
               | to protect the outlets (and device wires) from
               | overcurrent somewhere in the circuit.
        
               | mixmastamyk wrote:
               | Believe it has to with lowering the cost of rebuilding
               | after the war.
        
               | wongarsu wrote:
               | The fuse in the plug was _chosen_ to protect wiring on
               | ring circuits. They could also have put the fuse in the
               | wall socket. After all, they already put switches on
               | them. Of course then you would have to go with the screw-
               | in fuse design that was used in circuit breakers back
               | then, instead of the fuse design in UK plugs.
        
             | mhandley wrote:
             | > I'd call having a fuse in the plug itself over-designed.
             | 
             | Personally, I'm quite happy that all my lower power devices
             | with relatively thin power cables are protected by a 3A
             | fuse. There's no risk of causing those cables to catch fire
             | if there's a fault that draws 20A, which isn't enough to
             | blow the 32A breaker on that ring.
             | 
             | How much difference it makes in practice though? Pretty
             | sure that if I short the power at the device end of a 5A
             | cable, the 32A breaker would blow before the cable caught
             | fire. But I'm happy not to depend on that.
        
               | PrimeMcFly wrote:
               | I've never had issues in the US/AU/EU, so I really
               | question how useful it is compared to the amount of
               | incidents it is actually offering protection against.
               | 
               | Seems to me it's somewhat like having an additional
               | seatbelt for your head, which might protect against
               | whiplash but isn't justified by the inconvenience.
        
             | jdietrich wrote:
             | The size is cumbersome, but folding plugs are available for
             | devices like phone chargers - the dummy earth pin is
             | retractable, so the overall size of the charger is
             | essentially the same as a US or EU charger.
             | 
             |  _> I'd call having a fuse in the plug itself over-
             | designed._
             | 
             | I wouldn't. A UK mains circuit typically has a 32A breaker.
             | Pulling that much current through an appliance that's
             | designed for a fraction of an amp or a cable that's
             | designed for 3A is obviously a very hazardous fault
             | condition. Some appliances have a built-in fuse, but many
             | don't and that still doesn't offer the same level of
             | protection as a suitably-sized fuse in the plug.
        
               | PrimeMcFly wrote:
               | > The size is cumbersome, but folding plugs are available
               | for devices like phone chargers - the dummy earth pin is
               | retractable, so the overall size of the charger is
               | essentially the same as a US or EU charger.
               | 
               | How much does a folding plug fold? Look how minimal
               | this[0] is, I've never seen any UK plug anywhere close to
               | that size.
               | 
               | > I wouldn't
               | 
               | Any reason the fuse couldn't go in the socket instead?
               | 
               | [0] https://i0.wp.com/www.cablesgo.com/wp-
               | content/uploads/2018/0...
        
               | drcongo wrote:
               | > Any reason the fuse couldn't go in the socket instead?
               | 
               | Because changing the fuse in a socket just because you're
               | unplugging a lamp and plugging in a kettle would be very
               | stupid. With the fuse in the plug, you have the correct
               | fuse in every plug.
        
             | awhitby wrote:
             | For one thing, AU 2-prong plugs have a much more physically
             | secure connection than equivalent US plugs. The angled
             | prongs mean there's no rotational axis about which the plug
             | can fall out. Of course it also means the prongs can't
             | really fold away for storage.
        
       | hooch wrote:
       | How does ChatGPT come anywhere close in usefulness compared to
       | the breadth and fan-out of facts, opinion, supports and counter-
       | arguments offered by this format?
        
       | bloomingeek wrote:
       | "In some rare situations 220V might be more dangerous to touch."
       | 
       | Uh huh, here's an idea, go ahead and test that out for yourself!
        
         | Faaak wrote:
         | And with 30mA GFCIs, the risk is greatly diminished
        
       | temporallobe wrote:
       | I've lived in UK, Europe, and the US and I don't really see a
       | problem with either system. The 120V system is perfectly
       | sufficient for most cases, even refrigerators and other large
       | appliances. I suppose the one advantage a 220V system has is that
       | you can put a stove or dryer anywhere, and you can run certain
       | appliances, such as steamers and irons with way more power. On
       | the other hand I find the UK's plugs to be comically large
       | compared to the US's petite counterparts. Some European houses
       | even have a few 3-phase 380V outlets for heavy duty equipment,
       | which would be exceedingly rare in the US.
        
         | rekoil wrote:
         | > Some European houses even have a few 3-phase 380V outlets for
         | heavy duty equipment, which would be exceedingly rare in the
         | US.
         | 
         | My European 50m2 apartment has two.
        
       | sleepybrett wrote:
       | similar story to railroad gauges
        
       | SeanLuke wrote:
       | There were many factually correct, and even historically
       | interesting responses. But not a single response answered the
       | question.
        
         | wongarsu wrote:
         | I'm not sure there is a good answer, beyond "the US stuck with
         | Edison's 110V, Europe went with 230V because it's cheaper".
         | Both 110V and 230V are reasonable choices. And of course
         | technically the US primarily uses 230V split between two
         | phases. But Europe mostly uses 3-phase 400V, with each phase
         | delivering 230V (because phases are 120deg offset to each
         | other), so then we are just talking about 230V vs 400V, and two
         | vs three phases.
        
           | oblio wrote:
           | > Both 110V and 230V are reasonable choices.
           | 
           | Are they, though? With modern appliances, power requirements
           | are going up and 110V is struggling to keep up. One example
           | would be an induction hob.
           | 
           | I know that technically US homes can access 230V but they
           | aren't wired for that, probably 99% are wired just for 110V
           | except for maybe a few special lines.
        
             | wil421 wrote:
             | Laundry, stove, and ovens use 240V outlets (assuming no
             | gas). It's not very common but I know a few people with
             | wood working tools who have installed 240v outlets. Wood
             | framed houses make it easy to change wiring.
             | 
             | To change my gas stove/oven back to 240v induction would be
             | a 15 foot run of romex, a new outlet, and probably an
             | updated circuit breaker. Possible for a DIYer to do.
        
             | vel0city wrote:
             | Every US home I've lived in had 240V access in the kitchen
             | for appliances like electric ranges. They absolutely _are_
             | wired for that. Practically nobody 's house _only_ has
             | 120V.
        
               | gibspaulding wrote:
               | It sounds like you've always lived in relatively new/high
               | end houses then.
               | 
               | Older houses might have a dedicated 240 plug for the
               | dryer and the stove if they're not natural gass, but for
               | everything else there are plenty of homes full of
               | ungrounded 10 amp 120v circuits.
        
               | vel0city wrote:
               | My current house was built in '82. Is that a new house?
               | That's 41 years old at this point. Its a pretty average
               | single family suburban build for the time, not anything
               | especially fancy even for its day. Loads of houses we
               | looked at in the area were built in the 70s and 60s and
               | often had electric 240V appliances in the kitchen. That's
               | about 60 years old, is that a new? A single car garage
               | 1500sqft 3bdr house in a suburb sound like a high end
               | house?
               | 
               | And yeah, my house is full of 120V circuits, but once
               | again the house has 240V at the panel and could run 240V
               | anywhere in the house if needed. As you pointed out, they
               | probably do have a 240V plug for the dryer, ergo they've
               | got 240V service at the property, so they could wire the
               | kitchen if there's no wiring already. Once again,
               | practically nobody has _only_ 120V service at their home.
        
               | sbradford26 wrote:
               | Yeah the only situation I can think of only 120v being
               | available in a house is if it is a separate unit running
               | off a 120v sub panel from the main building. The other
               | option would be some off grid setups for like a tiny home
               | might only run 120v. That is mostly because anything that
               | would require 240v would be too power hungry to run off
               | of the solar system.
        
             | wongarsu wrote:
             | Interestingly enough, European oven/hob combos mostly run
             | on 400V 3-phase power. Same for many tankless water
             | heaters. That's certainly one advantage of 230V per phase.
             | It's probably also one factor in the decision to power
             | things by gas vs electric.
        
               | rootusrootus wrote:
               | But are they more powerful? AFAIK it's pretty common for
               | a European range to be in the 7000-10000 watt range.
               | That's also normal in the US on single phase 240V. And I
               | can go buy a 36000 watt tankless water heater from Home
               | Depot. I think it's a wash, either system can deliver
               | however much power you need.
               | 
               | The reason for gas in the US is because people like it.
               | It's been seen as upscale for decades to have a gas
               | cooktop. It also helps that gas water heaters don't
               | require electricity and work in an outage. Our
               | residential natural gas distribution network is extensive
               | and reliable, and it's pretty straightforward to use the
               | same appliances on propane for people out in the sticks.
        
               | vel0city wrote:
               | Depending on the market it can also be cheaper per BTU to
               | heat with gas than with electricity, at least resistive
               | heating. Heat pumps are starting to challenge that math,
               | but with higher upfront costs and more complexity as
               | tradeoffs.
        
             | michaelt wrote:
             | _> With modern appliances, power requirements are going up_
             | 
             | Things like lightbulbs and TVs and computers and
             | refrigerators are using less power than ever before.
             | 
             | Of course, if people are buying electric cars or replacing
             | gas furnaces with electric heat pumps, then you're right on
             | that side of things.
        
               | oblio wrote:
               | > Things like lightbulbs and TVs and computers and
               | refrigerators are using less power than ever before.
               | 
               | Are they, though?
               | 
               | Lightbulbs, sure, we won with LEDs.
               | 
               | But TVs, especially the huge, high brightness ones we
               | have nowadays? And with the extra computing needed?
               | 
               | Computers, same, I only see power usage going up. I mean
               | PCs, we're not comparing things with mainframes here :-)
               | 
               | Refrigerators: are they really more efficient?
               | 
               | Now add: heat pump, induction stove, electric oven, more
               | powerful AC, humidifiers/dehumidifiers, etc.
        
               | michaelt wrote:
               | Compared to the age of CRTs, modern TVs are much more
               | power efficient.
               | 
               | And compared to the age of the Pentium 4 with its 100W+
               | TDP, laptops now outsell desktop computers by a long way.
               | 
               | (I would agree that things like high-end gaming GPUs are
               | using more power than ever before - but they're also a
               | much smaller % of sales than ever before)
        
               | oblio wrote:
               | > Compared to the age of CRTs, modern TVs are much more
               | power efficient.
               | 
               | According to the internet a CRT TV used to use about
               | 100W, while a big LCD TV can use more.
               | 
               | Regarding desktops, don't forget that these days we have
               | many more electronic device in a home. Smart speakers,
               | home media devices, consoles, etc, etc. Electronics
               | probably use, in aggregate 5-10x what the old family PC
               | used to use, I'd imagine.
        
               | selectodude wrote:
               | A 32" Sony trinitron would pull down about 200W. An 85"
               | LCD will pull down about 150W.
        
               | bluGill wrote:
               | Though in the CRT days 19" was the most common size
               | (large did exist). I'm not sure what the most common size
               | TV is today, but it is bigger than that.
        
               | dontlaugh wrote:
               | Gaming PCs are actually getting close to the safe limits
               | for low voltage.
        
             | sbradford26 wrote:
             | Fundamentally the US just wires things differently. If a
             | house has an electric or induction hob(Cooktop) it will be
             | permanently wired for 240v. All your high power devices
             | such as HVAC, ovens, cooktops, and EV chargers have
             | dedicated lines at 240v for them. Every house in the US
             | other than some super niche scenarios has 240V. Yes largely
             | most everything is wired for 120V and only a few special
             | lines at 240v but that is because those are the only things
             | that really require more power.
        
               | ponector wrote:
               | While in Europe every regular socket has 230V but
               | induction has 400V with 5-wired connection. It is amazing
               | how fast it can boil water!
        
               | bluGill wrote:
               | Power = V*A. You can get any given power output out of
               | any voltage by following the formula. The number of wires
               | is not a factor at all. Number of wires and voltage is a
               | factor in cost of install of course, but nothing else.
        
               | sbradford26 wrote:
               | Yes European ones will run on higher voltage but largely
               | they are equally powerful.
               | 
               | US Version: https://www.bosch-
               | home.com/us/productslist/cooking-baking/co...
               | 
               | UK Version: https://www.bosch-home.co.uk/product-
               | list/cooking-baking/hob...
               | 
               | Largely they have the same power output. While the total
               | power available is actually higher for the US version at
               | 12kW versus 11.1 kW for the UK version. That is because
               | the US version needs to be on a 50 amp 240v circuit
               | versus the max 16 amp circuit for the UK version.
               | 
               | Even this Bosch one: https://www.bosch-
               | home.co.uk/product-list/cooking-baking/hob... Which
               | clearly calls out 400v 3 phase has a lower power output
               | at 7.4 kW.
               | 
               | The max output to a single pan/pot typically is going to
               | max out around 3.3-3.7 kW. I don't know the exact
               | reasoning behind that but I assume it might cause issues
               | with cookware if you go much higher than that.
        
           | [deleted]
        
           | johann8384 wrote:
           | US Power is typically 240v split-phase, a single phase, not
           | two phases. The transformer is 7200v to 240v. The Neutral
           | line to your house is center tapped on the transformer giving
           | you 120v from Hot to Neutral and 240v from Hot to Hot. I have
           | L14-30 and L5-30 outlets throughout my house and property for
           | example which lets me run higher voltage/amperage workloads
           | more easily. My workshop has an isolation transformer which
           | is 240v primary and 120v secondary. This allows me to run 80A
           | of 120v "stuff" in my workshop but it's a 40A 240v load from
           | the perspective of the main panel in the house.
        
         | JadeNB wrote:
         | Do you know the answer? (Of course your remark makes sense even
         | if you don't, but, if you do, then I'd love to know.)
        
         | antegamisou wrote:
         | Welcome to *.stackexchange.com
        
         | tyingq wrote:
         | The one explaining that Edison's DC system they were competing
         | with, in the US, was using ~100v DC. And the public
         | disinformation campaign characterizing AC as unsafe. Including
         | attacking anything higher than approximately 100v as unsafe.
         | That seemed like it answered the question to me.
        
         | refurb wrote:
         | "Edison's lamps were 100V" is in one of the answers.
        
           | Ekaros wrote:
           | And to me this seems most obvious answers. With possibility
           | that you had other resistive loads at that voltage already
           | sold. And people would be rather gross if they had to replace
           | them.
        
         | wiredfool wrote:
         | So, not only is the UK 230v, it's also wired in a ring (i.e.,
         | your circuit isn't a branch from your junction box, it's a full
         | loop). So, for a given power capacity, you can use much less
         | copper.
         | 
         | (from the wiki: https://en.wikipedia.org/wiki/Electrical_wiring
         | _in_the_Unite...)                 UK fixed wiring circuits,
         | unlike those found in almost all other countries, make
         | widespread use of ring circuit designs, as well as radial
         | circuit designs often seen in other countries. (This was one of
         | the recommendations of the Electrical Installations Committee,
         | convened in 1942 as part of the Post War Building Studies
         | programme, which in 1944 determined that the ring final circuit
         | offered a more efficient and lower cost method to support a
         | greater number of sockets.[6]) It continues to be the usual
         | wiring method for domestic and light commercial socket and
         | device wiring in the UK. Lighting circuits, which typically
         | have lower power requirements, are usually radially wired,
         | confusingly sometimes called "loop" wiring.
         | 
         | So, the why is: More power, less copper, and that's really
         | useful when you're resource constrained because someone has
         | declared war on you and is blockading your coast, or you're
         | recovering from that.
        
         | jqpabc123 wrote:
         | There is not one single all encompassing answer.
         | 
         | Safety was one significant concern. 230-240V is more likely to
         | stop a person's heart. 220 is available in most US homes for
         | specific cases where it is more practical.
         | 
         | Speaking from experience, I don't think it is uncommon for a
         | person to have been electrically shocked at some point in their
         | lives --- often when they were a child.
        
           | wongarsu wrote:
           | Maybe common in the US. Europe takes plug and outlet design
           | more serious (as a consequence of 230V), and while the UK
           | plug and continental Europe's Schuko plug are very different
           | both make it basically impossible to accidentally shock
           | yourself.
        
             | LinAGKar wrote:
             | Not impossible with the Schuko, it's still possible for
             | something to get caught in it and touch the pins when it's
             | partially inserted, that's happened to me. It's better when
             | only the tip of the pins are exposed, as on the UK plug and
             | the Europlug.
        
               | jqpabc123 wrote:
               | The plug is an issue but so is the socket.
               | 
               | What keeps a kid from sticking something metal into it?
        
               | james_a_craig wrote:
               | On UK plugs at least, there are shutters and you need to
               | insert something into the earth pin slot before they will
               | allow you to access the live/neutral pins. On better
               | sockets, the shutters then need simultaneous pressure on
               | both live/neutral to completely release. The actual
               | contacts in the socket are recessed too.
               | 
               | UK plugs and sockets are really, really, really safe.
               | Except to stand on.
        
               | kwhitefoot wrote:
               | Same on modern Schuko.
        
               | ovi256 wrote:
               | There is a hole cover plate that has to be pushed by
               | rounded plug pins to pivot and unlock the socket holes.
               | 
               | You can try pushing with something like a screwdriver (to
               | test for live) and it's hard to pivot the plate (feels
               | like it needs both pins to pivot), and a non round tool
               | snags on the plastic cover plate.
        
               | bluGill wrote:
               | In the US code requires shutters so you can't stick
               | anything into the socket other than the correct plug
               | (IIRC as of 2008?). Other responses are implying the UK
               | (and I assume EU) now require that too.
               | 
               | On the other end, in India I saw a power strip that would
               | accept EU, UK, or US plugs. I took one look and refused
               | to get close, but someone else plugged my laptop in and
               | it worked. (everything got 240 volts, which my laptop
               | power supply was fine with)
        
             | jandrewrogers wrote:
             | I've seen people shock themselves using the UK plugs with
             | casual handling more than once, it is definitely possible.
        
             | macrolime wrote:
             | I'm in Europe and I've been shocked a few times by 220V and
             | I know plenty of other who has too. It's usually not from
             | regular wall sockets, but wires with broken insulation or
             | working on things where parts of a circuit is uninsulated.
        
             | jqpabc123 wrote:
             | Plugs are only part of the safety issue.
             | 
             | Wire insulation deteriorates over time. Rodents like to
             | chew through it. Water can find it's way in through
             | plumbing or roof leaks. Higher voltage is more likely to
             | start a fire in these instances.
        
               | izacus wrote:
               | Are there any stats showing that Europe has more issues
               | with electricutions and electrical fires?
        
               | jqpabc123 wrote:
               | According to the European Fire Safety Alliance:
               | The total number of fires of electrical origin in the EU
               | is estimated to be 273,000 per year.
               | 
               | According to the US National Fire Protection Assocation:
               | Fire departments responded to an estimated average of
               | 46,700 home fires involving electrical failure or
               | malfunction each year in 2015-2019.
               | 
               | Stats aside, which do you think will cause a bigger
               | spark, 110 or 220?
               | 
               | https://www.europeanfiresafetyalliance.org/publications/w
               | hit...
               | 
               | https://www.nfpa.org/News-and-Research/Data-research-and-
               | too...
        
               | bluGill wrote:
               | Those numbers are not the same. EU is covering
               | everything, while US only home fires. And there is a
               | significant population difference in play as well.
        
       | jahnu wrote:
       | Even stranger than that, Japan has two grids, one at 50Hz and one
       | at 60Hz!
        
         | askvictor wrote:
         | ...which were completely isolated, until Fukushima led to power
         | shortages so they hurriedly linked /are linking the two with DC
         | interconnects.
        
       | hot_gril wrote:
       | Every comment in this thread is mentioning a different angle of
       | advantage/disadvantage between the two. I've given up on
       | determining the winner, but that's ok, I'm just learning a lot
       | about home power distribution.
        
         | mrguyorama wrote:
         | There is no winner. It's a simple API, with many correct
         | answers. The US ossified on it's system, and different European
         | countries did the same.
         | 
         | It's just a standard "Emacs vs VIM" flamewar.
        
           | hot_gril wrote:
           | Well if you compare it to emacs vs vim, that's making me
           | think there _is_ a correct answer.
        
             | bluGill wrote:
             | There is, but you are wrong... Hang on, let me go find my
             | old flame war cheat sheet I need to throw a few more
             | insults at you.
             | 
             | /s
        
           | rootusrootus wrote:
           | > The US ossified on it's system
           | 
           | Though it is crass, I'll say it. A silver lining to the
           | tremendous infrastructure damage caused by world wars in
           | Europe is that ossification was interrupted.
        
         | rootusrootus wrote:
         | > I've given up on determining the winner
         | 
         | That's because there is no winner. Nobody is doing something in
         | the US that is impossible in Europe, or vice versa. There are
         | upsides to both approaches, and different trade-offs, but
         | everyone is getting enough power.
        
         | darknavi wrote:
         | Tom Scott has a fun video not on voltage but on the merits of
         | the wall sockets them selves:
         | 
         | https://www.youtube.com/watch?v=UEfP1OKKz_Q
        
           | hot_gril wrote:
           | I don't normally like YouTube talking videos, but this one is
           | really good and to-the-point. Will say in response though, at
           | least 120V makes this less of a safety issue.
        
       | dim13 wrote:
       | Old joke: why USA use 110V and UdSSR 220V? Answer: because half
       | of it will be stollen in transition anyway.
        
       | noobermin wrote:
       | I moved from the US to Singapore which uses 230, and that coupled
       | with the humid environment makes things a lot less unsafe. That
       | plus old HDB electrical work isn't always the best. Getting
       | shocked and damaging electronics because a socket is lose is very
       | common here, and can be life threatening. I never had to worry
       | about this (at least as much). Floating ground here on the other
       | hand is device or even life threatening which is a real issue as
       | most chargers especially recent GaN ones do NOT have a ground
       | prong.
        
         | BeetleB wrote:
         | You should not get downvoted for this. The whole world isn't as
         | safe as Europe. I spent time in a country with 220V, and in
         | those days there was virtually nothing preventing you from
         | getting shocked (I know as I've been shocked). The prongs were
         | round, and you could easily touch the metal while inserting and
         | get a shock.
         | 
         | Another problem: Some of the plug/socket combinations were
         | fairly loose. It wasn't a tight fit. So if you're ironing, it
         | was not unusual for the plug to be partially out of the socket.
        
         | stephen_g wrote:
         | I'm really interested to hear more details about how this is
         | possible, because it's scary but fascinating!
         | 
         | Here in Australia we have 230V, and getting shocked is not at
         | all common - we have very strict electrical standards for both
         | installations and devices, residual current devices (GFCI
         | equilivalents) now required on every single circuit, everything
         | either has a proper ground or is double-insulated (unlike the
         | US sockets here without a ground pin are very uncommon because
         | you can't plug a lot of devices in to them) etc.
         | 
         | There was a possibility where you could pull the plug out very
         | slightly and slide something like a knife in between the plug
         | and socket and touch the active and neutral pins, so the
         | standards were changed many years ago now so compliant plugs
         | now have insulation on the live and neutral pins for the first
         | half of their length (see an example plug here - https://au.rs-
         | online.com/web/p/power-cords/0321168 ).
        
         | mytailorisrich wrote:
         | Getting shocked is a symptom of faulty electrics, not of using
         | 230V (even in a high humidity environment).
        
         | jraph wrote:
         | > that coupled with the humid environment makes things a lot
         | less unsafe
         | 
         | Safer? Why?
        
           | noobermin wrote:
           | When I am fly by night posting I do be using those double
           | negatives.
           | 
           | I meant less safe.
        
         | zuppy wrote:
         | this is not an issue in Europe. what kind of plugs do you use
         | in Singapore? the EU plug doesn't let you get shocked when
         | pulling the cord. i am willing to bet it's because of that, not
         | because of 220 vs 110. it has never been an issue in my life
         | and i don't get shocked ... ever.
         | 
         | edit: after a quick research i thing the reason is the socket:
         | https://www.everyworks.com/reasons-why-your-singapore-electr...
         | we don't use this, we have a small hole inside ours and it's
         | impossible to touch the live while the plug is connected
        
           | ketzu wrote:
           | Apparently they use british Type G plugs. ( https://en.wikipe
           | dia.org/wiki/AC_power_plugs_and_sockets#/me... )
        
             | zuppy wrote:
             | after a quick research, i think it's the socket not the
             | plug, it's easier to touch the live wire if the socket is
             | flat.
             | 
             | edit: can't reply to the child comments, maybe there's a
             | time limit, i'll answer here. i have no experience with the
             | british plugs, if you say it's impossible i believe you. i
             | don't understand, though, how does this happen to the
             | person from the top message.
        
               | the_mitsuhiko wrote:
               | Neither on British nor European Plugs can you touch a
               | live plug when only partially inserted.
        
               | Well_Keen wrote:
               | You absolutely can. I've personally be accidentally
               | shocked twice by pulling a firmly inserted plug out of a
               | socket, but it was my own fault. Get the plug partly
               | pulled out then readjust your hand to get more grip
               | around the side of the plug and in doing so accidentally
               | touch the non-insulated section of the live prong just as
               | it is in contact with the live terminal
        
               | jdietrich wrote:
               | If both the plug and socket are correctly made, it's
               | physically impossible - by the time the contacts on the
               | plug are exposed, they've disconnected from the contacts
               | in the socket. No matter how much you prod and poke, you
               | should only ever come into contact with an insulated
               | sleeve or a non-energised contact. Unfortunately there
               | are a lot of non-compliant plugs being sold by
               | disreputable online retailers.
               | 
               | It is possible to get a very mild shock from the plug
               | contacts if the input capacitors of the appliance haven't
               | fully discharged. This shouldn't happen with properly-
               | designed appliances, but it's very unlikely to be
               | dangerous if it does happen.
        
               | physicsguy wrote:
               | There's a long earth pin on the top of British plugs, the
               | socket doesn't open the holes to allow the other two pins
               | in until that's already inserted to the appropriate
               | depth. So you can't stick anything in to the socket and
               | touch a live wire.
        
               | circuit10 wrote:
               | If they use UK plugs it should be impossible to touch
               | that because there's a shutter that covers it until the
               | earth pin in put in
               | 
               | Here's a video by Tom Scott about why UK plugs are safer:
               | https://youtu.be/UEfP1OKKz_Q?si=f8UxqwhN4tmYxFMk
        
           | mnd999 wrote:
           | Should be the same for type G, the pins are shielded such
           | that it shouldn't be possible for them to have exposed metal
           | and be live at the same time.
        
       ___________________________________________________________________
       (page generated 2023-08-29 23:01 UTC)