       Why steam rises from San Francisco streets
        
       Author : kaycebasques
       Score  : 71 points
       Date   : 2023-04-23 15:08 UTC (7 hours ago)
        
 (HTM) web link (secretsanfrancisco.com)
 (TXT) w3m dump (secretsanfrancisco.com)
        
       | elcomet wrote:
       | This article actually never answers the question, why does this
       | steam network releases steam in the streets?
        
         | [deleted]
        
         | [deleted]
        
         | randyrand wrote:
         | bad pipes
        
           | mikeryan wrote:
           | Is this a guess?
           | 
           | I'd think there would be some sort of safety system for
           | venting pressure. Or even condensation around the hot pipes
           | (which seems to be why the same thing happens in New York
           | which also has a steam network)
           | 
           | All of the above could work too.
        
           | wongarsu wrote:
           | So what's up with maintenance? The leaks seem trivial to
           | locate and visibly waste both heat and water.
           | 
           | How is it more economical to have enough leaks that people
           | start talking about it instead of doing proper maintenance?
           | Especially since this situation seems fairly unique, I've
           | never seen this outside the US, and could only name San
           | Francisco and New York as places where this happens. So what
           | discourages maintenance in those places compared to
           | everywhere else?
        
             | sidewndr46 wrote:
             | As long as a service provider can pass those costs onto
             | customers and there is no alternative service, it can't be
             | economical to make repairs. You'd be expending capital to
             | decrease revenue.
        
               | wongarsu wrote:
               | But everyone is facing roughly the same forces here. You
               | either spend money on maintenance, or you lose money in
               | leaks. It's a tradeoff, but any place outside SF and NYC
               | seems to determine that the best place in that tradeoff
               | produces barely any leaks that a pedestrian would notice.
        
               | Scoundreller wrote:
               | Water distribution works the same way. Large systems lose
               | like 10% of their supply through leaks in the system but
               | just pump more through the system to make up for the
               | losses. Just like drug smugglers.
        
               | kevincox wrote:
               | This doesn't make sense. Price isn't set by the cost of
               | service. You could fix the leaks and still raise the
               | price to increase your profit margin.
        
               | zamnos wrote:
               | The energy market in California is highly regulated and
               | the prices consumers pay are fixed by the California
               | Public Utilities Commission (CPUC), and are designed to
               | cover the utility's costs, plus a "reasonable" profit.
        
             | toast0 wrote:
             | Steam leaks is a big indication that you've made it as the
             | downtown of a metropolis. I've witnessed it in Seattle,
             | pretty sure in Chicago and not sure about Milwaukee.
             | 
             | Doing proper maintenance requires opening the streets,
             | which is expensive and causes confusion and delay, so
             | there's some amount of acceptable leak before it's a good
             | idea to fix it. There's always a chance of finding unmapped
             | critical infrastructure when you dig, which adds more risk.
             | Plus, when you fix it, you lose the street cred.
        
               | wirrbel wrote:
               | I live in a town with teleheating, frankly I never saw it
               | steem. I would say the upkeep in the US of the
               | infrastructure is just bad.
               | 
               | This reminds me that in Paris you can pretty often see
               | water flowing on the street, it seems that the Paris
               | water supply has a tendency to leak that I just don't see
               | in other towns (but then, i am really walking for
               | kilometers through the city when visiting paris so maybe
               | I just have more opportunities to spot leaks).
        
               | Scoundreller wrote:
               | Paris regularly cleans its streets with the non-potable
               | water supply of its two-stream h2o distribution system.
               | Probably an antiquated practice back from when not
               | everyone had sewer connections and would dump their waste
               | pots on the road, but they still do it.
               | 
               | https://parisianfields.com/2012/03/11/a-most-unusual-
               | water-s...
        
         | greysteil wrote:
         | If it's the same as NYC then the steam you see is generally
         | from water evaporating off the outside of the pipes ( _not_
         | steam escaping from the pipes). The pipes are very hot, so any
         | outside water that touches them quickly turns to steam.
         | 
         | https://web.archive.org/web/20160811170408/http://www.coned....
        
           | jwr wrote:
           | That means the whole thing is incredibly wasteful. I always
           | wondered why nobody seems to care about the huge amounts of
           | energy being wasted in NYC in this way.
        
             | lukeschlather wrote:
             | There's an invisible component which is the efficiency of
             | the furnace used to create the heat. Suppose every building
             | uses a small furnace which is 30% efficient, then there's
             | no visible waste heat in the streets. On the other hand,
             | suppose a bunch of buildings use a single furnace which is
             | 50% efficient and pipe the heat with 10% waste from piping.
             | You're still substantially less wasteful to use the central
             | furnace. There's no such thing as a system that doesn't
             | generate waste, and the visibility or invisibility of the
             | waste doesn't tell you how wasteful the system is.
        
               | thaumasiotes wrote:
               | What does it mean for a heating furnace to be less than
               | 100% efficient? Efficiency is normally measured in terms
               | of how much waste heat you generate. If your goal is to
               | produce heat, it isn't possible to produce any waste
               | heat.
        
               | quesera wrote:
               | A lot heat is lost as exhaust into the air.
               | 
               | This can be a large portion, e.g. in older systems from
               | the days when fuel was cheap, and pollution wasn't a
               | topic.
               | 
               | Modern systems attempt to recover exhaust heat, and can
               | be 90-ish% efficient.
        
               | thaumasiotes wrote:
               | Releasing heat into the air is the entire point of the
               | building furnace. For the heat to get lost, it would have
               | to leave the building.
               | 
               | There's a more obvious argument that leaking steam into
               | the _streets_ is a waste of heat, but that still depends
               | on your goals. You might like having warmer streets.
        
               | quesera wrote:
               | > Releasing heat into the air is the entire point of the
               | building furnace
               | 
               | You're thinking of forced hot air systems, but these do
               | not vent combustion exhaust into living space. There are
               | fuel remnants and combustion byproducts in the exhaust
               | which would smell bad, and kill people.
               | 
               | Combustion exhaust, and all of the heat it contains, goes
               | up the chimney and is lost. The living space air is
               | heated by proximity to the combustion chamber, but
               | circulates in a separate closed loop.
               | 
               | Also, in a forced hot _water_ system, there is no air
               | circulation at all. 100% of the air involved is heated
               | and goes straight up the chimney.
               | 
               | Aside: Some people call FHW systems "boilers" instead of
               | "furnaces", but this seems to vary by region. Where I'm
               | from, "boilers" are steam systems only -- which seems
               | reasonable, since water is not _boiled_ in a FHW system.
        
             | tommoor wrote:
             | In NYC the steam is from co-generation facilities which
             | produce electricity first, so the steam is essentially
             | waste product to begin with - in most coal plants for
             | example you'd just have giant steam stacks to condense the
             | water again. But yes, it's all very normalized waste.
        
             | [deleted]
        
           | the_mitsuhiko wrote:
           | That however is not a natural "feature" of district heating.
           | Vienna uses it too and I have never seen steam leaks.
        
       | wolfgang42 wrote:
       | This post is basically a less-detailed blogspam of Cordia's
       | marketing page: https://cordiaenergy.com/our-networks/san-
       | francisco/
        
         | barbazoo wrote:
         | Thanks Google for making the internet shitty!
        
           | azinman2 wrote:
           | Curious - what would you do differently if you were google?
        
         | willcipriano wrote:
         | > plants produce steam and pipe it to approximately 180
         | customers for space heating, domestic hot water, air
         | conditioning
         | 
         | Had no idea you could make a steam powered air conditioner.
         | 
         | https://en.m.wikipedia.org/wiki/Steam_jet_cooling
        
           | sbierwagen wrote:
           | You can run a refrigerator off of any heat source: burning
           | propane, solar heat, etc
           | https://en.wikipedia.org/wiki/Absorption_refrigerator
        
       | bloomingeek wrote:
       | I'm about to retire from this very trade, so here's my 2 cents.
       | 
       | In my city the boilers run at 600psi.(Not near any salt water,
       | however if we decided to use it if we could, removing all the
       | impurities from the feed-water would be to expensive. At our psi
       | the feed-water must be clean and deaerated to protect the boiler
       | tubes.)
       | 
       | I'm a plant operator so I don't fix leaks in the field, these
       | steam leaks are just that, small leaks that develop in the steam
       | supply piping or the condensate return piping. (True, some lines
       | aren't insulated properly in the maintenance boxes, so you do get
       | some pulverized condensate.)
       | 
       | The steam generated from the main plant is used for all kinds of
       | applications. Heating of course, whether live steam or heating
       | water using a heat exchanger. Also it is used to power steam
       | turbine chillers to create chill water, which cools a significant
       | amount of office buildings and manufacturing plants. (These
       | chillers use refrigerant, usually 134a, to cool down the water
       | being pumped through them, which is then pumped to where the
       | cooling process is needed. Sometimes these pumps are steam
       | driven, but are usually electric motor driven. Water temp leaving
       | the chiller is usually 38 degrees, but may be around 42 by the
       | time it arrives to where it is used.)
       | 
       | My plant uses natural gas to create steam. Many electrical
       | generating power plants still use coal or nature gas to heat
       | treated water to create the steam to spin the turbines which spin
       | generators to create the electricity. (Sorry, I'm not a very good
       | writer.)
       | 
       | There are many other applications for steam boilers, and no
       | matter what they are, there's always the threat of leaks. The
       | cleaner the system, whether steam of water, the better the
       | chances of not corroding the piping. This is done by using
       | chemical treatments to destroy the oxygen or rust inhibiters.
        
         | schoen wrote:
         | > This is done by using chemical treatments to destroy the
         | oxygen
         | 
         | I couldn't help thinking of the fictional weapon used against
         | Godzilla:
         | 
         | https://godzilla.fandom.com/wiki/Oxygen_Destroyer
        
       | tedunangst wrote:
       | Because steam is warmer than the surrounding air, and thus rises.
       | 
       | Anyway, https://en.wikipedia.org/wiki/District_heating.
        
         | maxbond wrote:
         | I have a fun tangential story about when steam doesn't rise.
         | 
         | In college I would walk past a steam stack on campus every day,
         | because I could see it was always on the verge of making rings
         | (pretty much any cylinder with steam or smoke passing through
         | it or around it is, I've seen rings from incense, boiling rice
         | [the cylinder here is the column of steam bubbles], dropping
         | food coloring into water - if you look for them you start
         | finding them. The craziest example I've seen, which works much
         | like the food coloring, is an airplane contrail.). I thought if
         | I kept it up, one day the wind would blow in just right right
         | way and there would be a beautiful train of rings.
         | 
         | I never did see it. But on a hot day[1], I saw the steam settle
         | into the narrow alley next to the building. It formed into a
         | tiny roll cloud, about six feet long. I watch it stunned for
         | about fifteen seconds, and then it dispersed.
         | 
         | [1] I'm pretty sure it was a hot day, what I remember clearly
         | was that it was an unusual temperature. I surmise the air was
         | very warm and so the steam was denser than the air. But it may
         | have been a cold day and the steam cooled and then sank,
         | unfortunately I can't say for sure because I didn't write it
         | down.
        
         | fulafel wrote:
         | Other parts of the world with district heating don't leak
         | steam. Is it just because they use (liquid) water and not
         | steam?
         | 
         | The water is still plenty hot enough for steam to form in
         | leaks, so there's perhaps some factor that makes leaks more
         | tolerable in steam systems? Different corrosion concerns
         | perhaps, air leaking in is less corrosive?
        
           | tedunangst wrote:
           | I think it's an American thing. Our pipes are just that much
           | freer. New York and Philadelphia systems leak steam, too.
        
           | mangecoeur wrote:
           | Steam based systems are just obsolete, steam under pressure
           | leaks easily unless you do plenty of maintenance. Most
           | district heating systems use liquid water in a closed loop.
           | In fact most operators today are looking to further reduce
           | temperatures to reduce losses and improve efficiency. You
           | only let this much steam escape if you really dont care about
           | saving energy/money
        
             | bobthepanda wrote:
             | The issue is generally for these large historic systems,
             | the capital cost of replacement is larger than the savings.
             | Because the streets of New York had many utilities laid out
             | very early, there's poor mapping and everything underground
             | is haphazard, and disrupting somebody else's utility system
             | will get them to sue you.
        
           | wongarsu wrote:
           | Our smallish city has district heating with hot water, and no
           | steam rising from the streets.
        
       | [deleted]
        
       | arbuge wrote:
       | In NYC also:
       | https://www.bloomberg.com/news/articles/2015-10-23/why-steam...
        
       | ginko wrote:
       | >Critics of the system point out that the system produces heat,
       | but also wastes nearly 250,000 gallons of water per day,
       | according to a 2015 story by CBS Bay Area.
       | 
       | Any reason why they couldn't use ocean water?
        
         | throwaway173738 wrote:
         | Salt water ruins everything it comes in contact with.
        
           | Scoundreller wrote:
           | As someone that maintains two vehicles located in the rust
           | belt/salt belt, I concur.
        
         | PeterisP wrote:
         | Saltwater corrodes all the metal parts, and you simply can't
         | use it for a steam cycle as the salt would pile up as the water
         | turns to steam.
        
           | donalhunt wrote:
           | Google's datacenter in Hamina, Finland uses salt water for
           | one of the cooling loops. aiui it was not trivial to
           | incorporate the salt water loop (corrosion was an issue) but
           | they've made it work.
           | 
           | https://www.wired.com/2012/08/google-finland-data-center/
        
             | toast0 wrote:
             | Water in a datacenter cooling loop is almost certainly not
             | heated to the same temperatures as water in a (steam)
             | heating loop. Corrosion is temperature dependent.
        
               | ville wrote:
               | And on top of that, the Google datacenter in Hamina
               | doesn't use ocean water with 3.5% salinity, but water
               | from the Baltic sea, which in that part of the Gulf of
               | Finland only has roughly 0.3% salinity - a tenth of ocean
               | water.
        
               | Scoundreller wrote:
               | Sounds like less of a Baltic sea thing, but more of being
               | in a fjord or bay that's fed by fresh water keeping a lot
               | of the salty sea water out.
        
             | mikeryan wrote:
             | Building a system from the ground up to use saltwater is a
             | whole different ballgame then trying to retrofit an
             | existing legacy network though.
             | 
             | It would probably be cheaper to just convert to another
             | heat source all together.
        
             | justsomehnguy wrote:
             | Even without reading TFA it's surely not the loop what is
             | actually cooling the hardware.
        
             | jldugger wrote:
             | Google also has a 30 percent profit margin, even after
             | accounting for boondoggles like that.
        
             | Etrnl_President wrote:
             | You can get basalt-lined pipe, for chemical stability.
        
       | deepsun wrote:
       | Would be way more efficient if that was an power plant
       | (electricity generation), that just made use of its waste heat.
       | There were plenty of those in USSR, but I guess not everyone
       | likes a power plant in the neighborhood.
        
       | ElfinTrousers wrote:
       | tl;dr: leaky steam pipes in district heating in downtown SF. Same
       | reason you get it in NYC.
        
         | mokarma wrote:
         | Yup, we have it in Detroit too.
         | https://www.hourdetroit.com/community/whats-the-source-of-th...
        
           | ElfinTrousers wrote:
           | Not only is district heating energy-efficient, it's great for
           | setting a real film noir atmosphere.
        
       | grogenaut wrote:
       | One time walking past union square I saw smoke and flames coming
       | out of the cable car slot. There was just a cop watching it and
       | waving people around. Pretty sure just waiting on the repair
       | crew. Totes normal.
        
         | nharada wrote:
         | Meanwhile over in Chicago this is called "working as expected":
         | https://www.cnn.com/2019/01/30/us/chicago-train-tracks-fire-...
        
         | babyshake wrote:
         | It's tempting to make a joke about how in that neighborhood,
         | you're lucky if the worst thing you see is flames coming out of
         | the ground.
        