[HN Gopher] Air-to-Air Heat Exchangers for Healthier Energy-Effi...
       ___________________________________________________________________
        
       Air-to-Air Heat Exchangers for Healthier Energy-Efficient Homes
        
       Author : MengerSponge
       Score  : 241 points
       Date   : 2023-02-04 08:26 UTC (14 hours ago)
        
 (HTM) web link (www.ndsu.edu)
 (TXT) w3m dump (www.ndsu.edu)
        
       | olivermuty wrote:
       | This required building code in all homes in Norway since 2017.
       | 
       | It is good when the building is designed to have the system
       | easily serviced, bad when the unit is in a hard to get loft.
       | 
       | You need to change filters at least once a year to keep your
       | indoor climate good.
       | 
       | I just bought an old house, sealing all the vents and installing
       | balanced ventilation with one of these is on my list for summer
       | of 2024. Adding 5cm of insulation (up to modern codes, from 10 to
       | 5cm of glass wool) to keep the house even less energy demanding
       | in winter.
        
         | wojciii wrote:
         | Same story in DK.
         | 
         | I live in a house with this tech in. Also with a heat pump
         | (ground version) and solar panels/battery to offset some of the
         | running cost of this system.
         | 
         | The house is uncomfortably warm during summer but ok during the
         | rest of the year. The air is not humid enough for my tastes.
         | 
         | The Danish company called Danfoss sells complete systems used
         | to heat and ventilate houses. There are other systems perhaps
         | better in terms of communication with others (control systems).
         | My main problem with Danfoss is that I'm unable to control
         | their products without mayor hacking. So I'm never going to buy
         | from them again.
        
           | jupp0r wrote:
           | You are unable to regulate the temperature of the heating in
           | your house?
        
             | drjasonharrison wrote:
             | Probably unable to enjoy as much cooling as possible given
             | existing insulation, unit size, etc.
             | 
             | Humans don't sense temperature or wetness. We sense thermal
             | energy flow. Two materials at the same temperature, one
             | highly heat conductive and another poor at conducting heat
             | will feel like they are are different temperatures. Eg, at
             | room temperature, water and wool.
        
               | dv_dt wrote:
               | People know if they step into a hot humid environment vs
               | a hot dry environment. Perhaps they're just sensing some
               | level of thermal energy flow at the skin and how fast
               | sweat cools, but I think you sinuses, sense of taste, and
               | lungs may also also add additional senses to
               | differentiate.
        
               | jannyfer wrote:
               | > "Humans don't sense ... wetness"
               | 
               | I read this elsewhere too and think it's worded
               | incorrectly. Maybe our _bodies_ don't have sensory
               | receptors for wetness, but humans can "sense" it by other
               | means (e.g. by observing change in friction, stickiness,
               | etc)
               | 
               | Our bodies don't have receptors for our spouse's
               | emotions, but I can "sense" when my spouse is in a bad
               | mood.
               | 
               | Or maybe my English is just bad and it's worded fine.
        
             | wojciii wrote:
             | The heatpump is not able to cool the house - per design. It
             | would need air conditioning.. which would be expensive.
             | 
             | The house is very well insolatated and therefore difficult
             | to keep cool during the warm months. We installed film
             | blocking some of the light on the HUGE windows which are
             | part of the problem.
             | 
             | So we are able to regulate the temperature but the house is
             | warmed up during hot days and not always cooled down enough
             | during the night.
        
               | [deleted]
        
         | spockz wrote:
         | How are you going to run the new ventilation shaft for balanced
         | ventilation? In most houses I know that would mean tearing
         | down/up a lot of walls and ceilings/floors. Or you have to run
         | them on the existing ceiling and those pipes are quite large.
        
           | HdS84 wrote:
           | We did this for our house built in 68.
           | 
           | Obviously it depends on the architecture but we where able to
           | place the central unit beneath the roof. All rooms on the
           | first floor are connected through the roof space. A central
           | column runs through the first floor and goes to the corridor
           | on the ground floor. From there we where able to connect all
           | rooms. The floor lost 15 cm height but it has 250 cm so it
           | did not matter much.
           | 
           | If you cannot do it you can run the pipes on the exterior
           | walls and insulate them with ,20 cm Styropor.
        
           | ericd wrote:
           | Usually HVAC heat exchangers pretty close to an exterior
           | wall, because the run to the exterior heat exchanger is
           | ideally not too long, so you can tap into the return plenum
           | there. But even if there's not, there's some flexibility in
           | where you tap in (though some places might be more ideal than
           | others).
           | 
           | For us, it was just a couple 6"holes in the cinderblocks of a
           | basement wall (at least 6 feet apart).
        
           | lnsru wrote:
           | Using old obsolete way oversized chimney. Enough place for
           | pipes and cables.
        
             | drjasonharrison wrote:
             | Laundry chutes too
        
         | kkfx wrote:
         | Hum, IME the cleaning cycle of both my old and new one is three
         | months, I generally try to flush them one time but no filter
         | last more than 6 month. Did you have some other filters in the
         | chain like an electrical one? No pine pollen etc around in
         | spring?
        
         | lnsru wrote:
         | I also bought an old house and going for 12 cm of Expanded
         | Polystyrene (EPS) insulation for outer walls in southern
         | Germany. Plus simple combined heat pump for mild weather in
         | living rooms and gas heating for real winter for whole house.
         | With all this setup I am going to install central ventilation
         | system for living rooms. It's really really nice to have fresh
         | air during the night. The morning in previous rental apartment
         | was always ugly with condensed moisture on all the windows.
        
           | Freak_NL wrote:
           | Why EPS and not PIR?
        
             | lnsru wrote:
             | EPS is like one third of PIR in EUR.
        
               | Freak_NL wrote:
               | But those costs are marginal in the bigger picture. With
               | only 12cm not going for PIR while you have the chance
               | seems just a waste of effort. It's not bad, but you're
               | really limiting the options you have for heating.
        
               | lnsru wrote:
               | Thanks, I will redo my calculations. PIR 0,026 W/mK. EPS
               | 0,035 W/mK. There is a nice difference.
        
           | stuaxo wrote:
           | I've been looking at spray cork.
           | 
           | You can have it applied indoors and skimmed at only about a
           | cm total or outdoors.
        
             | mikeyouse wrote:
             | No matter the substrate, there is almost no insulation
             | benefit to 1cm of material. It looks like cork has an R
             | value of ~4.0/inch so 1cm is roughly R-1.5? That's about
             | equivalent or a single pane of glass.
        
               | drjasonharrison wrote:
               | Sometimes you can only economically and aesthetically add
               | a bit until you get to the "tear it down and rebuild".
        
             | ericd wrote:
             | Spray... cork? Is that just glue+cork bits? Does it end up
             | airtight?
             | 
             | I've been pretty excited about steam expanded cork boards,
             | they apparently make for excellent (albeit expensive)
             | exterior cladding. Ditto granules for replacing attic
             | fiberglass, though the additional weight of a thick layer
             | seems like it might be a problem for ceiling drywall.
        
               | skybrian wrote:
               | Seems to be a paint/stucco alternative:
               | 
               | https://www.buildwithrise.com/stories/spray-cork-what-is-
               | it
        
           | tinco wrote:
           | EPS is a filler material for concrete structures and floating
           | installations that easily catch fire and has mediocre thermal
           | properties. Is it even allowed to use EPS on your walls?
           | 
           | PIR is the typical economical material used for that kind of
           | application. And 12cm is about the minimal thickness you'd
           | want for decent insulation.
        
             | lnsru wrote:
             | EPS will be plastered afterwards. I don't see any problem
             | having it between brick wall and plastered layer.
             | 
             | 12 cm is ok for an old house. More is not economically
             | viable.
        
           | stinos wrote:
           | Why do you choose a hybrid system and not just a heatpump? I
           | have the impression that unless your energy demand is still
           | fairly high or the heatpump rating is too low, houses are
           | doing fine with a heatpump and the high COP in mild weather
           | balances the lower COP in cold winters such that overall it's
           | still worth it.
        
             | pitaj wrote:
             | Moreover, why gas instead of electric backup?
        
               | letitbeirie wrote:
               | Depending on where the furnace is located, it can be
               | cheaper and have a lower carbon footprint.
               | 
               | In my area of the US for example, gas costs 32/C/therm,
               | which equates to 1.1/C/kWh.
               | 
               | Electricity on the other hand costs 6.4/C-10.9/C/kWh
               | (depending on time of day), and while a third of it comes
               | from renewables, another third of it comes from coal, so
               | it ends up being net worse for the environment than just
               | burning the gas.
        
               | jupp0r wrote:
               | How long will you operate this? Coal will be gone in a
               | few years.
        
               | philwelch wrote:
               | Even with gas it's more efficient to burn the gas for
               | heat yourself than for the power plant to burn the gas to
               | operate a turbine which you then use to generate
               | resistive heat.
        
               | kkfx wrote:
               | > Moreover, why gas instead of electric backup?
               | 
               | Hum, I do not know in you country but here in France the
               | maximum you can get from the grid is 36kW, 12kW per
               | phase, 3 phases. And while the electricity is still far
               | cheaper than in Germany if you try to heat a classic
               | badly insulated home (who have a typical 34-40kW gas
               | heating) with electricity you final bill will be a bit
               | astronomical....
        
               | djbusby wrote:
               | Maybe, like me, they've got existing gas heaters/boilers
               | installed.
               | 
               | When you get a heat-pump you need the backup for really
               | cold (-20c). So you just leave the existing one in for
               | that case.
        
               | [deleted]
        
             | hedora wrote:
             | It sounds like they are putting in minisplits, which are
             | great for retrofits. The cost of minisplits is roughly
             | linear in number of rooms.
        
             | davemp wrote:
             | afaik in many climates/older homes heatpumps can't supply
             | enough BTUs to heat a house in peak winter without being
             | massively oversized for the cooling load (which could cause
             | humidity problems).
        
         | jaclaz wrote:
         | >You need to change filters at least once a year to keep your
         | indoor climate good.
         | 
         | It really depends on the location and on the specific
         | machine/install, usually there is no need to change the filters
         | (they are normally washable) but they should be cleaned much
         | more often, like every 6 (or even 3) months.
        
         | mhb wrote:
         | How old? You can't put insulation around knob and tube wires
         | since they need air around them for cooling.
        
           | Freak_NL wrote:
           | If you are doing retrofit insulation, updating the electrical
           | stuff to modern standards is pretty much something you'll
           | have to do anyway.
        
             | germinalphrase wrote:
             | Presumably, you are entirely removing interior
             | plaster&lathe/drywall to access wall cavity (and replace
             | wires) rather than drill holes and blowing insulation?
        
               | drjasonharrison wrote:
               | You don't have to remove all of the lathe and plaster.
               | Blown in insulation after upgrading the electrical. Fish
               | poles and long cuts repaired afterwards.
        
               | Freak_NL wrote:
               | If you are upgrading the insulation from the inside
               | you'll have whatever is the inner wall out anyway, it's
               | pointless otherwise; if you're doing it from the outside
               | (possible with some roofs) it doesn't matter; and filling
               | the wall cavity is done from the outside too, unless you
               | have a really weird house no wiring goes there.
        
               | PaulDavisThe1st wrote:
               | > If you are upgrading the insulation from the inside
               | you'll have whatever is the inner wall out anyway
               | 
               | In Philadelphia in 1996, I had a company blow in
               | insulation to my wood-framed, plaster+wood-lathe covered
               | cavity walls without removing the inner walls. They
               | created a series of 4"/10cm holes at the top of each bay
               | and blew the insulation in that way.
               | 
               | ps. I later found out that this is a terrible idea for
               | vapor control reasons.
        
               | Freak_NL wrote:
               | Yeah, that's basically why just putting up new walls is
               | the long term solution. And as a bonus you can put in
               | some sweet CAT6 cabling and enough electrical sockets
               | while you're at it. :)
               | 
               | Another benefit: when you take out the inner walls in an
               | old house, you are going to find layers and layers of...
               | stuff. Like 2cm of styrofoam (insulation in a nineties
               | way) and a new layer of drywall on top of whatever
               | chipboard/grout/newspapers where put in in a distant past
               | (at least in my old house).
        
               | germinalphrase wrote:
               | Massive project though.
        
           | amluto wrote:
           | Sure you can, even in code-heavy places like California:
           | 
           | https://www.nachi.org/knob-and-tube.htm
           | 
           | In any case, if you overheat Romex and destroy the
           | insulation, you can create a line-to-ground-or-neutral arc or
           | short. If you overheat knob and tube and destroy the
           | insulation, you are quite unlikely to cause an actual problem
           | -- there's nothing nearby for it to short to.
           | 
           | Modern insulation tolerates rather higher temperature than
           | old insulation, and knob and tube has plenty of other
           | problems, but this isn't really one of them.
           | 
           | (If GCFIs on branch circuits or feeders were widely deployed,
           | even at higher thresholds than 5mA, and everyone used either
           | grounded metallic conduit or bundles of wire with a bare
           | ground in the middle (like Romex or NM-B), then insulation
           | failures would be quickly detected.)
        
             | mhb wrote:
             | Thanks. Good to know. But probably worth mentioning that,
             | even though you can insulate around knob and tube where
             | local jurisdictions allow it:
             | 
             | "K&T wiring is designed to dissipate heat into free air,
             | and insulation will disturb this process. Insulation around
             | K&T wires will cause heat to build up, and this creates a
             | fire hazard. The 2008 National Electrical Code (NEC)
             | requires that this wiring system not be covered by
             | insulation."
        
               | drjasonharrison wrote:
               | I wonder how often this actually is a problem, in that
               | the owner looks at knob and tube wiring and keeps it for
               | the heritage value. My parents were ripping it out in the
               | 1970s from a 1920s home. I know that heritage
               | designations often require using the original
               | construction techniques but do they prevent upgrades to
               | the electrical system?
               | 
               | "I'm sorry sir but your grandparents didn't have grounded
               | outlets so you can't install have them either."
        
               | mhb wrote:
               | The problem, at least in my case, is that my 1930 house
               | has k&t wiring and little/no insulation. The easiest way
               | to add insulation would be to blow it in through drilled
               | holes. This is a lot less involved than rewiring the
               | house.
               | 
               | I have no affection for the wiring - nostalgic or
               | otherwise.
               | 
               | And, yes, vapor issues.
        
           | drjasonharrison wrote:
           | Most home owners would either prioritize replacing/upgrading
           | knob and tube wiring because we like to have more outlets and
           | circuits than when knob and tube wiring was installed, or
           | because the building code or local permitting office would
           | require the upgrade. Same thing for aluminum wiring (1970s?),
           | GCFI, replacing fuses with breakers, etc.
        
         | oliwarner wrote:
         | 100mm? Not sure what your climate is but the recommendation in
         | the UK has been 270mm for two decades (based on 0.044W/m2K
         | fluff). It's a relatively cheap and easy upgrade.
        
           | lnsru wrote:
           | 270 mm for roof or walls? For roof yes, for walls I don't
           | know. I have no plan to create passive home from an old one.
        
           | Freak_NL wrote:
           | In an old house? Rarely. I've been able to fit 100mm of PIR
           | (Polyisocyanurate) under my roof (1920s Dutch terraced brick
           | house), and that is pushing it without eating too much into
           | your living space.
           | 
           | PIR is a great solution for space-constrained insulation
           | though: 0.022W/m2K, so 100mm gives you a thermal resistance
           | of 4.54m2K/W. It's the equivalent of 200mm of mineral wool
           | with a thermal insulance of 0.044W/m2K.
        
         | HyperSane wrote:
         | I really like the fresh air system were air from these is piped
         | to rooms in small diameter pipes.
        
       | pvillano wrote:
       | I've been meaning to do something like this for venting the fumes
       | of my resin printer in the winter. Glad the work has been done
       | for me
        
       | LarryMullins wrote:
       | The best method is to live someplace with a tolerable climate,
       | dress appropriately for the season (that means warm clothes in
       | winter!), and open your windows. I've run neither my furnace nor
       | my AC in years.
        
         | eternauta3k wrote:
         | What first-world country has good weather and is easy to
         | migrate to? Israel?
        
           | LarryMullins wrote:
           | Large swaths of America, and much of Europe. Most of the UK
           | has a climate similar to the climate where I live (PNW). It
           | sometimes drops below freezing where I live, but rarely much
           | longer for a day or so. Not long enough to necessitate
           | running the furnace to keep my pipes thawed.
           | 
           | Dressing appropriately for the season is the key. Most people
           | don't. From what I've seen, most people have a single set of
           | clothing they use in every season and jackets they use in
           | winter when outside. I wouldn't wear a jacket indoors either,
           | that would be weird, but my winter clothes are warm enough
           | that I don't need a jacket indoors in winter. That's what
           | sweaters, thick long-sleeve shirts, etc are for.
           | 
           | The payoffs for this lifestyle are two fold: I get to enjoy
           | fresh air whenever I want, without needing some moldy filter.
           | And my energy bill is virtually nil, which is good for the
           | environment.
        
       | _Microft wrote:
       | Ha, this is inspired by our comments in the CO_2 monitor thread,
       | right? I thought about finding something to post about heat
       | exchangers as well but was tending more towards the high-
       | power/industrial end of the spectrum but this one's a good one
       | too! :)
        
       | akozak wrote:
       | I've wanted an HRV/ERV system for a long time, but have been
       | wondering about best practices with the intakes. One in each
       | room? In the ceiling, if our furnace outputs are in the floor?
       | The new ducting network seems like the hardest part by far. (Plus
       | the house is 100 years old and super leaky anyway)
        
       | kkfx wrote:
       | Here in Europe these machines are called simply double-flux VMC,
       | mandatory in "new" home (where new vary since in some northern
       | countries are mandatory since a decade or so, while in the south
       | it's more a recent thing, depending on local climate).
       | 
       | They are VERY cheap in industrial terms, not so cheap for what
       | they are in end-buyers terms.
       | 
       | BUT really new buildings start to propose something better,
       | "thermodynamic VMC" who happen to be double flux ones as well but
       | instead of passively recovery the heat/cool they are active,
       | meaning a small heat pump between the two flux. It's far less
       | cheap in electricity bill (mine consume 10+kWh/day for 350 m3/h,
       | 12.360 ft3/h if this is the unit Imperial system use) but they
       | de-humidify extremely well.
       | 
       | IME those last + low inertia heating result in LESS expensive
       | heating/cooling than passive ones + same heating. At least in a
       | not so cold/not too hot place (typical winter minima -25, -15
       | this year, typical summer maxima +30-32).
        
       | throw0101c wrote:
       | These is more generally known as "heat recovery ventilation", HRV
       | (the term is first used about half-way down the article):
       | 
       | * https://en.wikipedia.org/wiki/Heat_recovery_ventilation
       | 
       | There are also energy recovery ventilators, ERV, which in
       | addition to tempering the temperature of incoming air, also
       | temper the humidity:
       | 
       | * https://en.wikipedia.org/wiki/Energy_recovery_ventilation
       | 
       | In the past HRVs were mostly used in colder climates, as the
       | humidity exchange would cause frosting of the exchange core, but
       | modern core membrane materials have improved in recent years, and
       | some units can operate frost-free down to -10C / 14F: colder than
       | that and you may need a have pre-heater running on the intake, or
       | the unit may have a defroster.
       | 
       | * https://www.broan-nutone.com/getmedia/d7230185-8067-4256-a1a...
       | 
       | Some units have defrost modes so that they can run even in -27C
       | (though it will probably be defrosting a lot):
       | 
       | * https://www.broan-nutone.com/getmedia/3ec22979-19c4-4f1e-94f...
        
         | oaiey wrote:
         | That defrosting feature is very expensive. Move triggered early
         | December for like 5 days. It runs at 1000W permanently. In our
         | lovely energy process this translate to 15EUR a day or 450EUR
         | if run for a full month.
         | 
         | Switched it off air exchange for dinner days until it got the
         | one degree weather where the dentist is not needed
        
           | Volundr wrote:
           | That's odd. I've got a heat pump, and it defrosts a couple
           | times an hour, but the defrost cycle only lasts a couple
           | minutes. Are you sure it's not malfunctioning?
        
         | h0l0cube wrote:
         | > In the past HRVs were mostly used in colder climates
         | 
         | Did you mean warmer climates? You went on to mention new
         | membrane tech and pre-heaters that can handle colder
         | temperatures.
        
           | throw0101c wrote:
           | >> _In the past HRVs were mostly used in colder climates_
           | 
           | > _Did you mean warmer climates?_
           | 
           | No: HRVs were in cold climates previously because HRV do not
           | deal with moisture, and so there was less frosting / icing up
           | of the membranes.
           | 
           | ERVs were more focused in warmer climates, because warmer
           | climates tend to have a lot of humidity, so if you had a
           | dehumidifier in (e.g.) Texas or Florida, and you exhausted
           | stale air, it would end up exhausting the conditioned drier
           | air and intake the outside humid air, which you would then
           | have to dehumidify again.
           | 
           | Of course ERVs are _also desirable_ in cold climates because
           | cold air is dry(er), so you 'd be drying out your house. So
           | now that is technically more easy, ERVs are also being used
           | in colder climates.
        
             | h0l0cube wrote:
             | Thank you for clarifying.
        
           | shkkmo wrote:
           | Those allow ERVs to operate at lower temperatures. HRVs don't
           | need a membrane that passes moisture through, they just need
           | a heat conductive surface.
        
             | h0l0cube wrote:
             | Got it, thanks! If I understand correctly, HRVs have always
             | been suitable for both warm and cold climates. Modern ERVs
             | are becoming more suitable for cold climates with frost
             | protection.
        
               | jaggederest wrote:
               | Not quite, HRVs are much less useful in a hot-humid
               | climate, because most of the energy actually goes to
               | condensing and removing the humidity, rather than the
               | temperature difference.
               | 
               | e.g. 25c -> 20c is only 5 kelvins different, but it might
               | have to go from 95% relative humidity to 50% relative
               | humidity at the same time.
               | 
               | So the bottom line for a long time has been, don't bother
               | with HRV in hot-humid climates because they only return
               | ~20% of the embodied energy of the conditioned air,
               | whereas in cold climates, 90%+ of the energy goes into
               | the e.g. 25 kelvins differential in the temperature of
               | the air, and the humidity is already low on incoming air
               | (desirable, since people produce humidity through sweat,
               | showers, cooking, and cleaning)
               | 
               | Now that ERVs are coping with much colder temperatures,
               | expect to see HRVs phase out except in extreme climates
               | like Alaska, Alberta and the upper midwest US.
               | 
               | I wouldn't expect to see either in very temperate
               | climates like San Diego - there's just not enough energy
               | payoff for the cost of installation. Better off just
               | opening the windows when it's only 2 kelvins different
               | inside and outside!
               | 
               | PS the other major difference between ERVs and HRVs is
               | that HRVs are more-or-less maintenance free for life,
               | since they're basically just stacked aluminum plates.
               | ERVs degrade in performance over time, being things like
               | moisture-permeable membranes, so that's a concern for
               | people interested in long term installation in remote
               | areas, for example, but most commercial/residential usage
               | isn't that worried about that.
        
               | throw0101c wrote:
               | > _Better off just opening the windows when it 's only 2
               | kelvins different inside and outside!_
               | 
               | Except for all the pollen, dust, and pollution that doing
               | so would also bring in. ERVs can cost as little as US$
               | 1000 for the units themselves:
               | 
               | * https://hvacdirect.com/residential-industrial-
               | commercial-fan...
               | 
               | If this is a retrofit, there can be challenges with
               | installation, but plumbing into existing force air ducts
               | is a common scenario.
        
               | jaggederest wrote:
               | Well, HRV/ERV have no built-in filtration in themselves,
               | so they're exactly comparable to throwing open the
               | window. If you run them before a filter, obviously
               | they're better, but they have no inherent advantages to
               | opening windows.
        
           | ericd wrote:
           | He's saying that you'd use an HRV instead of an ERV, because
           | the moisture exchange of the ERV would start frosting up in a
           | very cold climate. If that's not a concern, the humidity
           | conditioning the ERV does on the incoming air makes it
           | preferable.
        
         | stuaxo wrote:
         | Is this the same thing as MVHR ?
        
       | strife25 wrote:
       | Does anyone know of good building science websites? I'd love to
       | better understand best practices.
       | 
       | The only one I've found is https://inspectapedia.com
       | 
       | There's great stuff on YouTube too (e.g. Matt Risinger's
       | channel), but soooo much conflicting information.
        
         | losvedir wrote:
         | In another comment I mention how overwhelmed I am by all this
         | stuff, so maybe don't take it from me, but when I've been
         | searching for answers about stuff like best practices for
         | windows or replacing my furnace with a heat pump,
         | greenbuildingadvisor.com seems to come up a lot and seems
         | pretty good. That said, much of it is behind a paywall that's
         | quite expensive, and I've been waiting to save my free trial
         | for the optimal moment.
        
         | nerdbert wrote:
         | https://www.greenbuildingadvisor.com/
        
         | eternauta3k wrote:
         | https://constructionphysics.substack.com/
        
         | walterbell wrote:
         | DIY forum, https://ecorenovator.org/forum/
         | 
         | HVAC blog, https://www.energyvanguard.com/blog/
         | 
         | HVAC pro forum, https://hvac-talk.com/vbb/
         | 
         | Heating forum, https://forum.heatinghelp.com/
        
       | walterbell wrote:
       | Bionaire's elegant $100 commercial window HRV was discontinued,
       | there don't seem to be any alternatives at that price point,
       | https://www.amazon.com/Bionaire-BAP336M-U-EverFresh-Exchange....
       | Product manual might be useful for DIY:
       | https://ia904509.us.archive.org/29/items/manualzilla-id-7067...
       | 
       | Commercial ERV/HRV units start around $500,
       | https://www.greenbuildingadvisor.com/question/inexpensive-ef...
       | 
       | DIY counter-flow design with coroplast sheets,
       | https://ecorenovator.org/forum/showthread.php?t=891&page=38#...
        
         | Someone1234 wrote:
         | That Bionaire appears to have the air inlet and outlet within a
         | couple of inches of each other, that isn't going to do anything
         | except waste electricity. You're just recirculating indoor air.
         | 
         | Real ERV/HRVs have ducting ports in both sides, and installing
         | all the ducting and electrical is far more expensive than the
         | $500~1000 the unit itself costs. That's why they're uncommon:
         | Install is expensive and painful.
        
           | Bluestrike2 wrote:
           | The window unit linked at the top doesn't appear to do heat
           | recovery. Most of the decentralized single-room mechanical
           | ventilation heat-recovery (MVHR) units reverse their fans
           | every 60-70 seconds in order to operate their heat
           | exchangers, such as this example.[0] That period _should_ be
           | long enough for the exhausted air to disperse far enough away
           | outside that it won 't just be sucked back into the house,
           | unless the exterior exhaust is positioned in a really weird
           | spot outside where wind is minimal and the air can't
           | effectively disperse. Alternatively, they can also be paired
           | with another unit so that one exhausts air at the same time
           | the other brings in fresh air, allowing better airflow
           | across/within the room.
           | 
           | The problem with this approach is that once you start
           | ventilating multiple rooms with these small units (figure
           | $500 per room with a single unit, twice that if two), the
           | cost _rapidly_ approaches that of a centralized unit with
           | ducting. But if you 're just looking to ventilate a room or
           | two, they're likely a very cost-effective solution. I could
           | also see them being used on a first floor living room/kitchen
           | in conjunction with a centralized unit ventilating upstairs
           | bedrooms with the ducting run through an attic. That'd
           | probably be cheaper overall than trying to run an
           | intake/exhaust duct downstairs or installing units in each
           | room. Plus, each exterior penetration increases the
           | opportunity for uncontrolled air leakage and, most
           | importantly, water.
           | 
           | 0. https://www.bpcventilation.com/bsk-zephyr-single-room-
           | heat-r...
        
             | spxtr wrote:
             | The other problem with this approach is that it is limited
             | to 50% efficiency long-term. They claim "up to 90%", but it
             | is only 90% efficient immediately after switching
             | directions. The efficiency then drops to 0% before
             | switching modes again.
        
           | erikerikson wrote:
           | They make vents that exhaust in a spiral from the center and
           | intake from the sides so that the air flows are
           | perpendicular. Might look funny on that unit but could help
           | with that mixing problem.
        
           | walterbell wrote:
           | _> That Bionaire appears to have the air inlet and outlet
           | within a couple of inches of each other, that isn 't going to
           | do anything except waste electricity. You're just
           | recirculating indoor air._
           | 
           | Are you referring to the ports on the interior or exterior?
        
             | Someone1234 wrote:
             | Both are too close to each other.
        
               | walterbell wrote:
               | The unit is 26 in. wide for a use case (e.g. apartments)
               | where the HRV avoids leaving a window open for
               | simultaneous intake and exhaust. If the exterior wind
               | direction doesn't locate the exterior outlet downwind of
               | the intake, one could potentially install a short
               | exterior duct to add separation, as in step 13 of this
               | DIY HRV, https://www.loudawson.com/17884/how-to-build-
               | air-cross-flow-.... For the interior ports, 45-degree
               | angled vents can reduce overlap between the airflow
               | directions. Without the HRV, air would be moving in and
               | out of the same window anyway, without any structural
               | separation.
               | 
               | Amazon reviews for the Bionaire reported both energy
               | savings and air quality improvement, so it worked for
               | some people.
               | 
               | For homes, there are DIY full-sized HRVs, with custom
               | ducting, https://ecorenovator.org/forum/showpost.php?p=26
               | 861&postcoun...
        
           | D13Fd wrote:
           | This. Last quote I got was $5k to install a $700 unit.
        
         | amatix wrote:
         | The BluMartin FreshAir 100 and the Fresh-R series are both MVHR
         | units that fit into existing walls: there's a Fresh-R model
         | that goes into a window frame too.
        
         | hasbot wrote:
         | Here are detailed plans for a DIY HRV:
         | https://www.aivc.org/sites/default/files/airbase_2413.pdf
        
           | walterbell wrote:
           | Thanks. A coroplast design from 1985!
        
       | mnot wrote:
       | Installed one of these last year during a Reno, love it - no more
       | condensation, no mold, much fresher air.
        
         | danieldk wrote:
         | Same, our apartment complex has high-volume ventilation with
         | heat exchangers in every apartment (The Netherlands). Humidity
         | and mold has never been a problem and it's like continuously
         | ventilating your house without the cold air. We recently
         | replaced the gas heating and heat exchanger by an air-to-air
         | heat pump that also acts as the heat exchanger and regulates
         | the ventilation. Is a nice upgrade, because now the heat is
         | fully controlled by one unit.
        
           | alliao wrote:
           | wow, do you have any links on the product? sounds really good
        
           | simooooo wrote:
           | I still find my air feels cold for to it being moving air
        
       | leashless wrote:
       | I have an ambition to live in an insulated metal barn. They're
       | incredibly cheap compared to regular construction. I would then
       | construct smaller dwelling units inside of it, non load bearing,
       | which could be played around with much like legos. (It may help
       | to know I'm the designer of the hexayurt, a shelter technology
       | popular at Burning Man and eventually bound for the world's
       | refugee camps.)
       | 
       | Key to this plan is handling humidity. Metal buildings don't
       | breathe. Humidity condenses on the metal, turns into mould, then
       | you have real problems.
       | 
       | But with humidity sensors and A2A heat exchangers you wind up
       | with the best of both worlds. I think.
       | 
       | Let's say I'm not going to be building this before I've had real
       | analysis from a good hvac engineer or two.
       | 
       | https://www.kitbuildings.com/products/insulated-steel-buildi...
       | For a sense of prices.
        
         | amluto wrote:
         | Buildings don't need to breathe. They need some way to dry out,
         | because there is essentially no such thing as perfect
         | waterproofing.
         | 
         | I suspect the condensation problems in a barn like that are due
         | to insufficient insulation or insufficient control of air
         | movement. 50mm of polyisocyanurate is less than R10, which
         | doesn't come close to even the code minimums, and is totally
         | inadequate for a roof of a house anywhere remotely cold.
         | Separately, if it's cold, then the interior surface of the
         | metal will be cold, and any humid interior air making it to
         | that surface will condense. A real house would do something to
         | minimize that movement of warm interior air outward through the
         | insulation.
        
           | stuaxo wrote:
           | Co2 build up and indoor pollution is a thing.
        
             | newsclues wrote:
             | The building doesn't need to breath.
             | 
             | The building needs to have a supply of fresh air.
             | 
             | Both are true.
        
               | amluto wrote:
               | Indeed. You want fresh air (possibly filtered, heated,
               | cooled, humidified and/or dehumidified) to enter the
               | living space. This is not the same thing as air flowing
               | _through_ the walls, roof, etc.
        
         | aaronax wrote:
         | Put a vapor barrier inside of the insulation--this is very
         | typical in any cold climate construction. Then humidity inside
         | doesn't matter, because it never touches a cold surface.
        
           | rsync wrote:
           | ... but be careful when layering moisture barriers.
           | 
           | If you stack two moisture barriers with any void space or
           | (other material) in between, you can create a space that
           | moisture can enter ... but never escape.
        
         | throw0101c wrote:
         | > _Metal buildings don't breathe. Humidity condenses on the
         | metal, turns into mould, then you have real problems._
         | 
         | Neither do modern homes made out of timber and wood sheathing.
         | This is a good thing.
         | 
         | Humans need to breathe, not buildings. Buildings need to be
         | able to dry:
         | 
         | * https://www.energyvanguard.com/book-house-needs-breathe-
         | or-d...
         | 
         | * https://www.energyvanguard.com/blog/myth-a-house-needs-to-
         | br...
         | 
         | * https://www.greenbuildingadvisor.com/article/buildings-
         | dont-...
         | 
         | * https://www.youtube.com/watch?v=CIcrXut_EFA
        
           | PaulDavisThe1st wrote:
           | What lets them dry is mostly air movement, which some people
           | would calling "breathing".
           | 
           | The main difference between the "new" and the "old"
           | approaches to this is that the new one calls for much more
           | organized and controlled air movement, while the old one
           | tended to just rely on leakage, well, pretty much everywhere.
        
         | amelius wrote:
         | I guess cell phone reception would be an issue too.
        
           | paranoidrobot wrote:
           | Cell phone repeater tech isnt hugely expensive if you want to
           | do it.
           | 
           | More expensive the bigger the installation. Some carriers
           | offer basic units.
           | 
           | If your carrier supports wifi-calling then that can do most
           | of it if you have decent internet.
        
             | hedora wrote:
             | Lies, all lies!
             | 
             | We have metal siding, and get bitten by RF issues over and
             | over again. The back of the house is in a cell phone
             | shadow. The WiFi access point on the roof has all sorts of
             | unpredictable deadspots outside. The 900MHz weather station
             | display has to be placed within a 2" square spot indoors.
             | Also, the solar panels and batteries drop into "call
             | installer" mode a few times a week when their mesh network
             | collapses.
             | 
             | And so on. The internet of things will only make this worse
             | over time.
        
               | rsync wrote:
               | People who understand wireless technology use wires.
        
             | amelius wrote:
             | That sounds like a way to get locked in by a particular
             | carrier.
        
         | Retric wrote:
         | What makes barns cheap is the lack of glass windows,
         | insulation, plumbing, carpets, climate control, decks, etc.
         | 
         | Add that stuff back in and you are just building a house.
        
         | lnsru wrote:
         | I don't know where are you located. But I worked in insulated
         | containers in south Germany. The office was being built. It was
         | like sauna in summer and unpleasantly cold in winter. I guess
         | you would need 10 inches of insulation to have acceptable
         | result here.
        
           | stuaxo wrote:
           | There's a some research into thin internal wall insulation in
           | the UK, because our housing stock is old and small.
           | 
           | Spray cork seems to come out the winner.
           | 
           | https://www.gov.uk/government/publications/thin-internal-
           | wal...
        
             | PaulDavisThe1st wrote:
             | and for a very recent (last week) US perspective on cork
             | insulation (and siding), here's Matt Risinger (Build):
             | 
             | https://www.youtube.com/watch?v=iXY_f-bJDyA
        
         | fvdessen wrote:
         | You will live in the dark :/
        
         | defrost wrote:
         | There's a _lot_ of variations of prefab sheds, metal roofs, etc
         | in Australia.                   The vapour permeable sarking,
         | separated from the roof sheet by a drainage batten provides
         | drainage of any moisture or condensate forming below the roof
         | sheet.
         | 
         | https://dctech.com.au/products/dct-r01-1c/
         | 
         | is a common housing solution - that's a "runoff sheet"
         | immediately under the metal that allows vapor up to the metal
         | and then catches condensed water and runs it down to the sides
         | and out.
         | 
         | In a hot climate big wide roofs with a good pitch (and a
         | venting cap gap at the ridge line) can heat air under the metal
         | and use the rise of hot air (and out the ridge cap) to draw in
         | air through (say) watered hedges.
         | 
         | You might get some ideas browsing Aussie prefab shed solutions,
         | etc.
         | 
         | https://www.theshedcompany.com.au/barns/american-barns/
         | 
         | https://ams-group.com.au/
        
           | PaulDavisThe1st wrote:
           | > The vapour permeable sarking
           | 
           | I would have hoped that with fairly good knowledge of both UK
           | and US english construction terminology, AU english would
           | have nothing left to confuse me with. But ... no. "Sarking" ?
        
         | bitschubser_ wrote:
         | Actually, I'm wondering why not more houses are build out of a
         | metal-insulation sandwich contruction, one downside, no nails
         | on the outside walls (but this can also be solved with a
         | regular installation zone out of plywood, here is an example
         | from one who built his own home out of a metal sandwich
         | contruction: https://www.youtube.com/watch?v=brcGQZWbeLI
         | according to him it was really cheap (don't know how it
         | compares to wood framing with insulation)
         | 
         | wondering how prefacb metal sandwich construction compares to
         | prefab wood framing (which is quite common here in germany)
        
           | Retric wrote:
           | Wood beam construction is really fast, cheap, and easy to
           | insulate or modify.
           | 
           | People argue for all kinds of alternatives but the cost to
           | construct a wood frame is only around 5% the cost of the
           | home. Swapping to something else just doesn't buy you much
           | and most alternatives have significant downsides.
        
           | infecto wrote:
           | Barndominiums are really popular depending on where you live.
           | I see them all the time in the United States, really popular
           | for new construction custom home.
        
         | skeeter2020 wrote:
         | You wouldn't need to have exterior load bearing construction
         | inside, but I don't think that absolves all structural
         | concerns. What about services (HVAC, electricity, plumbing)?
         | What about interfacing with the outside world, i.e. windows?
        
         | infecto wrote:
         | With how popular barndominiums are these days I don't think
         | handling humidity is going to be that much of an issue. I have
         | even seen some more like you described where they build the
         | actual home on the interior of the metal structure instead of
         | adopting the metal structure as the homes walls.
        
         | dalbasal wrote:
         | Interesting, but I don't see the massive cost advantage.
         | 
         | $150k for a 150 m2 kit. That's before you have constructed the
         | outer shell _or_ the internal dwelling(s). What am I missing?
        
           | gog wrote:
           | The most expensive kit on the site (for me) is 50x15x7,3m
           | which comes out to 750 m2 and it is 2 stories high, so that
           | comes out to 1500 m2.
        
           | ilostmyshoes wrote:
           | Flexibility to change things without massive costs maybe?
        
             | lnsru wrote:
             | A drywall is then a solution. It can be build almost
             | anywhere and removed within hours again.
        
               | saalweachter wrote:
               | You basically want balloon framing, in spirit if not in
               | execution.
               | 
               | In old balloon framed houses you'll often find all the
               | interior walls are not structural -- they were often
               | built _after_ the sheet rock was put in on the exterior
               | walls and ceiling. That leaves you free to shift them
               | however you please without compromising the stability of
               | the house.
        
       | hasbot wrote:
       | From the article regarding maintenance:
       | 
       | - Clean or change the filters every one to three months
       | 
       | - At least once a year clean the heat exchanger core.
       | 
       | - In addition to the core, the fans should be cleaned at least
       | once a year.
       | 
       | There is a home efficiency YouTuber that mentioned recently that
       | his new home has 17 filters!
       | 
       | There's always plenty of house maintenance to do anyway, this is
       | just adding to it. I think Henry David Thoreau was onto
       | something.
        
       | losvedir wrote:
       | This makes me so overwhelmed. I own a house built in the 1950s
       | and I want to make it more energy efficient, but where do I
       | begin, and how do I change parts of it without causing other
       | problems.
       | 
       | Can I improve insulation without causing moisture and mold at the
       | boundary? Can I upgrade my furnace to a heatpump without first
       | improving insulation and air tightness? Which of the several ways
       | I've read about is the best to condition my crawl space? And now
       | I'm reading that I shouldn't seal up the drafts in my home
       | without one of these air exchangers? Etc etc
        
         | robohoe wrote:
         | Dealing with the same but a 1960s house. Make sure to air seal
         | and insulate it well. Most insulation contractors skip the air
         | sealing but that's very important!
        
         | hasbot wrote:
         | See if you can get an energy audit from your electric or gas
         | company.
         | 
         | You can definitely upgrade your furnace without first improving
         | insulation and air tightness. There are other conceptually
         | simple changes that will improve efficiency with low risk of
         | causing other problems (e.g. attic insulation, blown in wall
         | insulation, replacement windows). The energy audit will include
         | an analysis.
         | 
         | Home efficiency is pretty complex. Read up a lot before paying
         | for any changes. Even today, many new homes aren't built to be
         | airtight. There are air gaps everywhere. An HRV/ERV may help
         | reduce energy costs because air has to enter the house from
         | somewhere, but in older homes I'm not sure the slight benefits
         | one will gains will be worth the cost and extra complexity (an
         | HRV/ERV needs to be cleaned twice a year).
        
           | maxerickson wrote:
           | The audit should have some information about what is going to
           | be the most beneficial cost wise. Additional insulation is
           | often a pretty safe win (especially if it doesn't change the
           | moisture barrier).
           | 
           | Of course there can be other goals. I don't expect that
           | upgrading my 80% AFUE furnace would save me any money. High
           | efficiency furnaces cost more, break faster and it would
           | require more work to install one vs just replacing with an
           | 83% unit. But it would change how air moves in the house,
           | instead of drawing combustion air from the conditioned space,
           | a high efficiency furnace would pull it from outside, so it
           | would be easier to humidify the house to a more comfortable
           | level (a medium size wick humidifier doesn't keep the house
           | above 20% on colder days).
        
           | PaulDavisThe1st wrote:
           | Blown-in wall insulation is terrible in cold climates. With
           | no vapor barrier, any moisture from the living space will
           | condense once it hits the "cold zone", which is likely inside
           | the wall, and thus lead to rot (and mold) over time.
        
         | vegasje wrote:
         | I empathize with you, as I am in the same boat.
        
         | ganoushoreilly wrote:
         | A lot of the improvements would be built around any renovations
         | / remodels you want to undertake. One of our previous homes was
         | built in the 1900's. One of the things we did that were
         | immediately noticed were upgrading windows to double pane.
         | Again not feasible if you don't need the upgrade, but for us it
         | was a worthwhile investment. We also found that leaving doors
         | closed in various rooms was important to retaining heat. The
         | hallways would be cooler but it made it much easier to _spot_
         | warm parts of the home with a heater if absolutely necessary.
         | 
         | There may be a local company that can give you advice on things
         | you can do in a cost efficient, least headache manner. Whatever
         | you undertake though is probably going to be an expense, so
         | check with your local state / county and see if they have any
         | energy efficiency improvement programs. I just used one to
         | improve windows and attic / crawl space insulation in my
         | mother's home.
         | 
         | Good luck
        
           | hasbot wrote:
           | I've lived in two 50's houses where the windows were replaced
           | with double pane. Both window replacements were mediocre at
           | best. Replacement windows are a bit smaller than the original
           | windows so there is a gap between the house framing and the
           | window frame. In neither house did the installer do an
           | adequate job of sealing that gap. On one window, I could even
           | see daylight through the gap. I had to remove the inside trim
           | and spray in foam.
        
             | ganoushoreilly wrote:
             | That sucks, a poorly installed window definitely defeats
             | the benefits.
        
         | throw0101c wrote:
         | In a perfect world, you'd be able to build the perfect wall:
         | 
         | *
         | https://buildingscience.com/documents/insights/bsi-001-the-p...
         | 
         | What you should worry about in renovations may depend on which
         | climate zone you are in:
         | 
         | * https://www.ecohome.net/guides/3521/climate-zones-map-usa-
         | ca...
         | 
         | * https://basc.pnnl.gov/images/iecc-climate-zone-map
         | 
         | > _Can I improve insulation without causing moisture and mold
         | at the boundary? Can I upgrade my furnace to a heatpump without
         | first improving insulation and air tightness? Which of the
         | several ways I 've read about is the best to condition my crawl
         | space? And now I'm reading that I shouldn't seal up the drafts
         | in my home without one of these air exchangers? Etc etc_
         | 
         | If you're serious about this, then hiring a consultant /
         | company who specializes in this would be a first good step:
         | 
         | * https://www.youtube.com/@HomePerformance/videos
         | 
         | * https://www.youtube.com/watch?v=t-GIzX6bLeU
         | 
         | The money you pay upfront for a plan may save you cash down the
         | road to make sure you don't do things in the 'wrong' order or
         | buy incorrect equipment (type or size). The above two
         | presenters are a good start (and do remote consulting AFAICT),
         | but looking at ResNet-certified folks (in your area?) is a
         | broad good start.
         | 
         | Generally, for indoor air quality (IAQ), you want to go air
         | tightness (even without extra insulation) and then get a
         | ERV/HRV. If your current furnace/AC is working fine then
         | letting it run for a few more years won't harm anything, and
         | changing it won't help IAQ or comfort. For crawl spaces, making
         | it conditioned is a good start: insulation and a 10+ _mille_ (
         | "mill") poly tarp so stop moisture drive would be a good start.
         | 
         | P.S. If you think you have problems, I grew up a house from the
         | 1890s.
        
       | hasbot wrote:
       | Here are detailed plans for a DIY HRV:
       | https://www.aivc.org/sites/default/files/airbase_2413.pdf
        
       | simonebrunozzi wrote:
       | I am involved in a complex restoration project in Venice, Italy
       | (a side hobby); and I am trying to figure out what would be the
       | best option in regards to heat pump, potentially using geothermal
       | energy from underground.
       | 
       | In Venice you have the option to do air/water heat exchange,
       | using the water from the canals.
       | 
       | Any of you have any experience with something like that?
        
         | pifm_guy wrote:
         | Ask someone local.
         | 
         | What's available and rules vary really widely city to city.
         | 
         | What makes sense financially also depends on your building
         | construction, climate and fuel prices, which also depends a lot
         | on location.
        
           | simonebrunozzi wrote:
           | I was asking more about the technical aspects. Regulation,
           | etc I will need to deal with but it is pretty much sorted.
           | Thanks.
        
       | ClumsyPilot wrote:
       | I recently moved into an apartment with sucha ventillation
       | sustem, really pleased with it.
        
       | throwawaygo wrote:
       | [flagged]
        
         | MengerSponge wrote:
         | Every story on HN is also posted somewhere on Reddit, but the
         | discussion here is different.
         | 
         | I posted this because its germane to HN readers. Air quality
         | has major health and cognitive effects, and there are
         | substantial opportunities for technological innovations that
         | would dramatically improve our quality of life and work.
        
           | antisceptic wrote:
           | Let us not forget that it is squarely in the hacker spirit to
           | share heat with tech savvy, instead of scaling up a bad
           | solution!
        
           | throwawaygo wrote:
           | Uh huh.
        
       | jrockway wrote:
       | What kind of options do apartment dwellers have in this space?
       | I've been thinking of DIY-ing something like this (suck in air
       | from the window, heat it resistively in the rare event it's too
       | cold inside, pass it through a HEPA filter, pass it through a
       | humidifier, enjoy), but that is clunky and I'm wondering if
       | products actually exist that I could just buy instead.
       | 
       | (I own my apartment, but no HVAC system. Through-the-wall AC,
       | steam radiator heating.)
        