[HN Gopher] A collection of single egress buildings, illegal in ...
       ___________________________________________________________________
        
       A collection of single egress buildings, illegal in Canada
        
       Author : yeknoda
       Score  : 60 points
       Date   : 2023-01-09 16:14 UTC (6 hours ago)
        
 (HTM) web link (secondegress.ca)
 (TXT) w3m dump (secondegress.ca)
        
       | bearcobra wrote:
       | I'm currently remodeling my house and our contractor recommended
       | adding a fire suppression system as part of the project. I always
       | assumed that would be something I couldnt afford but the quote
       | was pretty reasonable (~2500) I wonder if these kinds of systems,
       | plus advances in other building materials have reduced the risk
       | profile to the point where multiple egress points are no longer
       | needed
        
         | xenadu02 wrote:
         | Any amount of water you can get onto a fire increases
         | survivability (both in time and number of locations). NFPA 13R
         | is a relatively recent addition to fire code that focuses on
         | making low-rise residential fire sprinklers much cheaper to
         | install and that shows in the price quote you got.
         | 
         | 13R allows use of existing plumbing connections. It doesn't
         | require a separate feed from the water main, nor does it
         | require a separate iron pipe network inside the structure. It
         | also doesn't require extensive equipment like some commercial
         | systems do (eg sensing when one sprinkler goes off and using
         | high-pressure to force the whole zone of sprinklers to go off).
         | 
         | > advances in other building materials
         | 
         | Definitely not. You'd think we would require a quick spray-down
         | of boric acid on wood stick construction right after framing.
         | Boric acid (or borax) is an insect repellant, smolder
         | suppressor, and fire retardant when used this way. It would -
         | at minimum - slow the spread of structure fires. It is also
         | dirt cheap. But nope... buildings themselves are just as
         | flammable today as they were 50 years ago. Survivability is
         | worse thanks to so much synthetic fabric and foam giving off
         | really toxic fumes and more or less no requirement to make
         | anything flame resistant.
         | 
         | ---
         | 
         | If you want to increase survivability in your own home:
         | 
         | 1. If you can afford it have sprinklers installed. In most US
         | states the cost is a lot less than you might think, well under
         | $10k. Usually under $5k. Insurance can't replace lives nor
         | keepsakes. Nor can it repair bodily injury. If you worry about
         | water damage I can promise you repairing it is far cheaper than
         | repairing smoke/fire damage.
         | 
         | 2. Have working smoke detectors. Get 10-year sealed lithium
         | ones. The day you install them set a reminder in you phone for
         | 10 years from now to replace them. Install them in the
         | recommended locations.
         | 
         | 3. Sleep with your door closed. If you need air, crack a
         | window. If your room doesn't circulate enough from a forced air
         | system shave a bit off the bottom of the door. Experiments show
         | even a cheap cardboard core door can provide 30 minutes of
         | protection from a raging house fire. It blocks most of the
         | smoke. It also greatly slows down heat transfer which reduces
         | flashover risk. I'm not joking - you can find videos on the web
         | where the hallway is a charred black hellscape but the
         | bedding/carpet in a bedroom behind a closed door isn't even
         | slightly blackened.
        
           | chromatin wrote:
           | Thanks for these reminders! #3 is especially important.
        
         | dieselgate wrote:
         | Just curious what the "fire suppression system" is in practice,
         | is it sprinklers or specific fire retardant materials (drywall,
         | shingles etc) used. Also wondering what geo location you are in
         | (in consideration of regional fire risks and codes).
         | 
         | Edit: would assume single/multiple egress points are tied to
         | the human capacity limit for the building but am not an
         | arch/civil engineer
        
       | henrikschroder wrote:
       | Wow, being European and used to single-stairwell multi-story
       | buildings, the North American obsession with fire escapes has
       | always seen weird, and it's super interesting that its
       | codification causes the economy of mid-rises to not work out,
       | which in turn causes the weird housing distribution of North
       | American cities. The "missing middle", that the site is talking
       | about.
        
         | vkou wrote:
         | Fire codes aren't the reason that you can't build in most of
         | North America.
         | 
         | NIMBYism, and the cultural obsession with low-density, single-
         | family homes only made possible by car-centric transportation
         | infrastructure is.
         | 
         | Which is also in no small part caused by a financial and tenant
         | rights system that pushes people towards home ownership,
         | instead of renting.
        
           | astrange wrote:
           | Part of the car-centric infrastructure is fire codes.
           | American towns have lots of fire departments which all refuse
           | to buy smaller European-style fire trucks, and all roads have
           | to be built to fit what they buy.
           | 
           | European buildings are also less likely to be made out of
           | wood, which is good if you care about fire safety that much.
        
             | vkou wrote:
             | > Part of the car-centric infrastructure is fire codes.
             | 
             | No, it's not. Cheap gas[0], giant freaking interstates, and
             | public transit systems (when they are even present) that
             | are very clearly built for the 'poors' are.
             | 
             | Another 3% to the per-square-foot-cost of building a multi-
             | tenant building aren't the reason that Houston has 12 and
             | 16-lane highways cutting right through the city, or why it
             | takes an hour to travel by bus in Stockton a distance that
             | you could travel in 10 minutes by car.
             | 
             | Fitting fire trucks is a problem for _local_ , last-mile
             | streets[1], not arterials, and availability of arterials
             | (and lack of availability of alternatives) are what plays a
             | large part in how people get around.
             | 
             | [0] Under $3.20/gallon in most of the country, compared to
             | over $7/gallon in most of Europe. Not to mention the
             | double-whammy of generally lower[2] European wages.
             | 
             | [1] Most American suburbs solve the width-of-last-mile-
             | street problem by simply... Not having sidewalks. It's not
             | like there's anywhere you can walk _to_ from them...
             | 
             | [2] Okay, okay, yes, Western European take-home incomes for
             | low-paying jobs tend to be higher than their American
             | counterparts.
        
         | orthoxerox wrote:
         | There's probably a fire escape somewhere that you haven't
         | noticed. When I lived in a 23-storey building it had a second
         | fire escape stairwell and a fire escape ladder outside next to
         | the garbage chutes. I now live in a 9-storey building and it
         | has a fire escape ladder bolted next to the balconies.
        
           | henrikschroder wrote:
           | > There's probably a fire escape somewhere that you haven't
           | noticed.
           | 
           | No.
        
         | [deleted]
        
         | [deleted]
        
         | synu wrote:
         | I think it comes from the houses being made out of wood instead
         | of brick. Or at least it seems likely comparing houses in the
         | Netherlands and US. The way houses burn is just totally
         | different.
        
           | rqtwteye wrote:
           | That's what I am thinking. It's hard to imagine a scenario
           | where the brick house I grew up in Germany could burn down
           | but my US house would probably burn completely once the wood
           | in the walls has caught fire.
        
           | henrikschroder wrote:
           | Yeah, that might be a big part of it. I was shocked to
           | discover how flimsy multi-story houses are constructed in
           | North America compared to what I'm used to.
           | 
           | Every single apartment I've lived in in Stockholm has had a
           | single stairwell, and it's not something I've ever thought
           | about because no-one thinks of it as an issue. But on the
           | other hand, those stairwells are always concrete and stone
           | and marble, and fire regulations forbid you from storing
           | _anything_ in the stairwells or outside your apartment.
           | 
           | Take my current Stockholm apartment, there's a four-storey
           | drop from the balcony to the ground and a single stairwell,
           | which would apparently horrify every North American.
           | 
           | But the walls are concrete. The walls between apartments are
           | concrete or drywall. There's four apartments per landing. The
           | apartment doors are made of steel. And the stairwell is empty
           | and marbled, so there's _nothing_ that can burn in the
           | stairwell, and it 's very difficult for fire to spread from
           | one apartment to the others. There's no sprinkler system, but
           | I think there's a fire extinguisher on each landing.
           | 
           | Not a problem.
        
             | oivey wrote:
             | If an apartment is on fire between yours and the stairwell
             | and that fire extends to the hallway, then you're dead,
             | right? If there was a second stairwell on the opposite side
             | then you'd still be able to escape.
             | 
             | I'm pretty sure sprinklers have been shown to massively
             | increase fire safety.
        
               | henrikschroder wrote:
               | > and that fire extends to the hallway, then you're dead,
               | right?
               | 
               | The point is that this can't happen for a number of
               | reasons. The landings in my building are quite small,
               | four doors and a stairwell, it's literally two meters
               | from my apartment door to the stairwell, there are no
               | long corridors. And there's nothing that can burn in the
               | stairwell, it's all concrete and stone and steel. And all
               | the apartment doors are steel as well.
               | 
               | The dangers of apartment fires are mitigated
               | _differently_ , so that there is no need for a second
               | stairwell or fire escape.
               | 
               | And this is something I didn't see on the site, and which
               | is probably where they're a bit wrong and misguided. Just
               | because actual fire statistics are better in Europe than
               | in North America despite allowing single stairwells, it
               | doesn't mean you can remove the requirement from the
               | Ontario building code and everything will be fine and
               | dandy. You have to add all the other things that mitigate
               | fire hazards.
        
             | colinb wrote:
             | (I think that) Flimsy ~= less likely to fall down in an
             | earthquake. When I moved from Ireland to California I moved
             | into a two storey (1940s?) apartment apparently constructed
             | from drinking straws and toilet paper. But... a few weeks
             | later the area was struck by a significant quake. Part of
             | the freeway fell down. I was woken from sleep by the
             | building swaying and creaking. But it didn't fall down.
             | 
             | Try your Stockholm apartment in that.
        
               | henrikschroder wrote:
               | This doesn't make sense.
               | 
               | The US can obviously build earthquake-proof concrete and
               | steel skyscrapers, just look at the entire SF downtown.
               | So if you can do that, why wouldn't you be able to build
               | earthquake-proof _midrise_ buildings out of concrete and
               | steel?
               | 
               | When I lived in SF I was woken one night by an
               | earthquake, the entire 42-story high-rise I was living in
               | was swaying back and forth, but obviously didn't
               | collapse.
               | 
               | Sure, I can see how a wooden construction is a _cheaper_
               | way to make buildings earthquake-proof, but does it
               | really cost that much to earthquake-proof a mid-rise? Or
               | is it not economically feasible to build mid-rises out of
               | anything but wood in the first place?
        
               | sgc wrote:
               | Well, because midrise buildings hit a horrible resonance
               | with the frequency of earthquakes and are the type of
               | building most at risk, and because those huge skyscrapers
               | have pendulum counterweights, wheels they roll on 100 ft
               | in the ground, and it just costs way too much to use that
               | tech in a smaller building.
        
             | sethhochberg wrote:
             | A lot of new construction in the urban US is similar - once
             | you reach a certain level of density.
             | 
             | I live in a row-style apartment building in NYC built
             | within the last decade, which is 6 floors, 2 apartments per
             | floor, steel frame with concrete floors. There is a single
             | interior stairwell, also all cinderblock. We have
             | restrictions on what can be stored in common space.
             | 
             | NYC categorizes this type of construction as "fireproof" -
             | which basically means that in case of fire, unless the fire
             | is in your unit, it is expected to be safer for you to
             | remain in your apartment and await evacuation than to enter
             | smoke-filled hallways. Any fire is expected to be
             | contained.
             | 
             | The city's other category of dwelling is "non-fireproof",
             | and non-fireproof buildings require multiple forms of
             | egress. You need multiple ways out because the fire is
             | expected to spread.
        
               | henrikschroder wrote:
               | > The city's other category of dwelling is "non-
               | fireproof", and non-fireproof buildings require multiple
               | forms of egress.
               | 
               | Cool!
               | 
               | That sounds perfectly reasonable to me, and since the
               | site is specifically about the building codes of Ontario,
               | arguing for adapting a building code similar to the one
               | you describe for NYC is probably a much better way of
               | making your case, rather than posting a bunch of artsy
               | floorplans from recent projects in various European
               | cities...
        
         | NickBusey wrote:
         | Yes, our obsession with not wanting to burn to death. So weird.
         | 
         | https://en.m.wikipedia.org/wiki/Iroquois_Theatre_fire
         | 
         | Or more recent and relevant, an apartment fire:
         | https://en.m.wikipedia.org/wiki/2022_Bronx_apartment_fire
        
           | petesergeant wrote:
           | Do more Western Europeans burn to death than Americans?
        
             | pessimizer wrote:
             | I feel this is something you can check yourself and bring
             | back to the thread instead of asking rhetorically, as if
             | it's obvious that they don't.
        
         | [deleted]
        
         | voz_ wrote:
         | Europe is behind on a lot of safety infrastructure compared to
         | the US. You frame it as obsession, but really it's just good
         | policy.
         | 
         | > which in turn causes the weird housing distribution of North
         | American cities.
         | 
         | This is a hilarious misunderstanding of the complex
         | intersection of class divides, race divides, gerrymandering,
         | history (white flight), nimbyism, and for-profit zoning that
         | has led to the current lack of mid-rise affordable housing.
        
           | boredumb wrote:
           | white flight is a pejorative, the correct term is reverse-
           | gentrification
        
             | astrange wrote:
             | This appears to be a dumb joke but the opposite of
             | gentrification is "disinvestment".
        
           | michaelt wrote:
           | _> You frame it as obsession, but really it 's just good
           | policy._
           | 
           | Well, there are alternative ways to reduce the risks
           | presented by a fire in the primary staircase trapping people
           | inside.
           | 
           | For example, good sprinkler coverage of the primary
           | staircase, strict rules prohibiting storing anything
           | flammable below the staircase or running electrical wiring
           | there, compartmentation so there's time for the fire brigade
           | to arrive before a fire can spread between homes, housing
           | options for vulnerable citizens so only able-bodied people
           | have to evacuate via the stairs, and so on.
           | 
           | Of course, many American buildings are made of wood, so it's
           | understandable why American fire codes look different to
           | European ones - and if I had to be in a burning building but
           | could choose the design, an American-style single storey
           | suburban home where every room has a window you can climb out
           | of at ground floor level is hard to beat!
        
           | JumpCrisscross wrote:
           | > _it 's just good policy_
           | 
           | Is there any empirical data on the safety benefits of a
           | second stairwell?
        
             | voz_ wrote:
             | In the spirit of curiosity - how would you go about
             | measuring that? A counterfactual is almost impossible.
             | 
             | That being said - when in doubt, I favor more regulation
             | for safety, not less.
        
               | JumpCrisscross wrote:
               | > _how would you go about measuring that?_
               | 
               | Death and injury frequencies. Anecdotes of preventable
               | deaths, _e.g._ where one stairwell was not enough versus
               | where a corridor separating two stairwells became,
               | itself, an obstacle. Drill simulations.
               | 
               | We should have have _some_ basis for the rule. (If we don
               | 't, I'd support scrapping it.)
        
               | jeffbee wrote:
               | You could measure it by people who perish in structure
               | fires, a metric on which America is far behind Europe.
        
               | rwmj wrote:
               | You'd need to weigh that against the costs and lost
               | opportunities. If no one can buy an affordable apartment
               | and overengineering is part of the cause, or if many die
               | because of a car-centric culture because you can't built
               | densely enough, that can be a problem.
        
               | frickinLasers wrote:
               | I'd wager most of the US deaths occur in single-family
               | homes--in basements (illegally housed), or even while
               | sleeping in rooms with plenty of opportunity for egress.
        
               | harywilke wrote:
               | This got me curious. Best i could find was the CTIF (The
               | International Association of Fire and Rescue Services)
               | [1] and their annual report [2].
               | 
               | Table 1.2 shows a breakdown of fire deaths per 100 fires.
               | US 0.3 France, Germany 0.1 Greece, UK, Belgium 0.2
               | Poland, Denmark, Slovakia 0.4
               | 
               | So it's a bit of a mixed bag. The reported average was
               | 0.5 (report didn't cover every country). Sadly Canada
               | wasn't in the table.
               | 
               | Japan at 3.8 was a bit of a surprise.
               | 
               | 1. https://ctif.org/world-fire-statistics 2. https://ctif
               | .org/sites/default/files/2022-08/CTIF_Report27_E...
        
           | jimbob45 wrote:
           | _white flight, nimbyism_
           | 
           | Is it truly unreasonable to want to move away from places
           | where crime is rising and cleanliness and living standards
           | are falling? Isn't it a bit unfair to ascribe that desire to
           | the level of whiteness of a person?
        
             | whatshisface wrote:
             | It's a historical fact that got named after its most
             | obvious feature. They _were_ white people.
        
             | pessimizer wrote:
             | Don't get triggered. Nobody is talking about you or calling
             | you a bad person.
        
             | mc32 wrote:
             | Agreed. If we went on calling bad things by the predominant
             | population which engages in negative practices, most people
             | would object.
        
           | thatfrenchguy wrote:
           | I mean, there's still more people who die in fires in the US
           | than in the EU, thanks mostly thanks to space heaters on
           | 120v/15A circuits and absolutely zero retrofit requirements
           | on anything (what do you mean I can have K&T and a Federal
           | Pacific Panel that does not trip on overcurrent in my house
           | with no GFCI/AFCI protection but every single new circuit I
           | add needs to have those?). The US/Canada have gone too far
           | into "new housing stock needs to be perfect" and not enough
           | into "existing housing stock needs to be retrofitted",
           | because not pissing off landlords and boomer homeowners is a
           | main policy goal.
        
             | sokoloff wrote:
             | The decision to not require retrofitting of existing,
             | undisturbed construction means that new code can evolve
             | more quickly to adopt new technologies or safer methods. If
             | every 15A and 20A residential outlet had to have AFCI
             | protection as of some specified date, I can tell you that
             | date would be sometime still in the future from now.
             | Requiring it only for new construction or new circuits
             | means it could be phased in starting in 1999.
        
               | thatfrenchguy wrote:
               | "Now for new construction and retrofit everyone in 10-15
               | years" would make much more sense. Especially for things
               | like GFCI/AFCI protection which is much more useful in
               | old circuits than new.
        
             | googlryas wrote:
             | A cursory search says 3k Americans die in house fires, and
             | 5k Europeans die in house fires per year, so probably EU
             | had more fire deaths per capita. But it's hard to tell
             | because EU doesn't have a FEMA equivalent collecting data
             | on residential fire deaths.
             | 
             | https://www.usfa.fema.gov/statistics/residential-fires/
             | 
             | https://www.europeanfiresafetyalliance.org/our-
             | focus/statist...
        
               | henrikschroder wrote:
               | Hang on, this article is explicitly about mid-rise
               | buildings and the fire safety of one vs two stairwells in
               | those, so you can't drag up statistics that show combined
               | data for all housing types. I'm assuming a large chunk of
               | those fire deaths are people dying because they
               | accidentally burned down their single-family single-story
               | building. That's completely irrelevant in this case so
               | you have to separate that out.
        
               | sokoloff wrote:
               | This sub thread got into the angle of general forced
               | retrofit of new code requirements, and claimed a general
               | loss of life from fires being higher in the US making
               | introduction of facts about fire deaths overall relevant
               | IMO.
        
             | happyopossum wrote:
             | > I mean, there's still more people who die in fires in the
             | US than in the EU
             | 
             | False - and it's not even close. Europe has almost a full
             | order of magnitude more death from residential fires than
             | the US - house fires caused 2,620 deaths over 5 years in
             | the US [0] vs ~5000/yr in Europe [1].
             | 
             | [0] https://www.thezebra.com/resources/research/house-fire-
             | stati... [1]
             | https://www.europeanfiresafetyalliance.org/our-
             | focus/statist...
        
               | comte7092 wrote:
               | >house fires caused 2,620 deaths over 5 years in the US
               | 
               | Your source says that was 2,620 per year further down in
               | the article:
               | 
               | >House fires cause an average of 2,620 civilian deaths
               | each year.
               | 
               | Given that the EU has a significantly higher population
               | than the US (~500 million, the EU data may or may not
               | have included the UK, vs ~330 million) the per capita
               | statistics end up fairly close.
        
           | henrikschroder wrote:
           | > Europe is behind on a lot of safety infrastructure compared
           | to the US.
           | 
           | That's a rather sweeping statement.
           | 
           | > and for-profit zoning that has led to the current lack of
           | mid-rise affordable housing.
           | 
           | Yes, it's a complicated issue with tons of causes, but what
           | this site is saying is that the requirement for a second
           | stairwell skews the economy of building mid-rises so much
           | that they become unfeasible for developers (In Ontario) even
           | if all the other factors were to be fixed. And so you're
           | stuck with either high-rises or single-story buildings.
        
       | barbazoo wrote:
       | This is the more interesting link outlining the actual problem:
       | 
       | https://secondegress.ca/A-Wicked-Problem
        
         | AlexTWithBeard wrote:
         | I still fail to understand: is slapping an escape ladder on the
         | side of the house THAT expensive?
        
       | hedora wrote:
       | So, the complaint is that they don't want to stick a fire door on
       | the back of new buildings, since it would undermine some
       | architectural design purity or something?
        
         | ripley12 wrote:
         | This is a snarky low-effort comment. Do better.
        
         | scrumper wrote:
         | The thesis isn't particularly clear but what I think they want
         | is a modification to Canadian building code so that structures
         | up to a certain size don't need a second egress. They want
         | that, I think, because that aspect of code makes it hard to
         | design housing that sits in the middle of the scale between
         | single family homes and high rises. That middle tier of housing
         | seems like it could be important if you consider what NIMBY-ism
         | and a shortage of housing is doing to some cities.
         | 
         | I couldn't find out out _why_ a second fire exit makes it hard
         | though. Maybe it's not the door, but the need for an extra
         | stairwell?
         | 
         | I'd hesitate to call it pretentious wank just because I don't
         | understand it, so let's just say that the site was clearly not
         | written for a lay audience.
        
           | monknomo wrote:
           | Requiring two egresses usually means that the building will
           | not have an apartment that spans the width of the building,
           | instead there will be a central hallway to connect every
           | apartment to two stairwells.
           | 
           | That central hallway seems small, but it eats a fairly
           | substantial percentage of the footprint space of the
           | building. (elevators and trashrooms are also examples of
           | things that eat a lot of footprint; limiting them for smaller
           | buildings is beneficial for floorplan efficiency)
           | 
           | And since people do not like bedrooms without windows, having
           | apartments that don't span the width of a building limits
           | possible floorplans, and drives the apartment design towards
           | studios and 1 bedrooms.
           | 
           | The buildings tend to become very wide in order to
           | accommodate enough apartments to make them worthwhile to
           | build, so they tend to use up a high percentage of the lot
           | they are sited on, which reduces greenspace and other
           | resident amennities.
        
             | nradov wrote:
             | In most areas, the building code explicitly requires a
             | window in every bedroom. This serves as an additional
             | emergency exit, either directly on the ground floor or with
             | assistance from firefighters on higher storeys.
        
               | bbojan wrote:
               | Ironically, in Toronto, not every bedroom is required to
               | have a window [1].
               | 
               | [1] BCC Ruling No. 14-03-1366: https://web.archive.org/we
               | b/20210422142050/http://www.mah.go...
        
           | henrikschroder wrote:
           | You have to go digging on that site a little bit to get to
           | the why:
           | 
           | "The building typology of five to six-storey apartment
           | buildings usually involves a single shared central stair,
           | accessed directly from the street with typically two to four
           | dwelling units per floor. However, because the Ontario
           | Building Code requires two means of egress, mid-rise
           | buildings in Toronto are designed with two exit stairs
           | connected by a common corridor. The result is that mid-rise
           | construction only proves feasible on larger sites where
           | around ten or more units can fit within a typical floor plan
           | to achieve an efficient floor area ratio. Zeidler explains
           | that "this appears to be a reasonable precaution for life
           | safety. However, the life safety of this single stair type in
           | Europe has been equal to, if not better than ours," due to
           | the fact that the single stair scheme is shared between fewer
           | units. By changing the code requirement for two exit stairs,
           | apartment buildings of midrise height could be designed
           | around a single common stair. For instance, a point-access
           | block, the dominant housing typology in dense urban contexts
           | like Berlin, Paris, or Barcelona, is currently not permitted
           | in Canada."
           | 
           | https://secondegress.ca/A-Wicked-Problem
        
           | mjmahone17 wrote:
           | A big chunk of why is the % of floor area that is used for
           | housing versus "support". Basically a single stair layout
           | gives you 90-95% floor efficiency, and a double stair is
           | closer to 80-85%. People don't rent common spaces like
           | stairs, so you can bring the value of a building up by ~10%
           | by allowing each apartment to have only a single exit
           | staircase. Also if a lot is small (like 20ft wide or less),
           | you have to compromise the design. For instance, instead of
           | having full-floor units that get cross ventilation (windows
           | at front and back), you may need to have duplex units that
           | take up 40% of the front or back (so only get one side of the
           | building).
        
           | RegnisGnaw wrote:
           | Its the second stairwell.
        
         | tlb wrote:
         | Most of the buildings on the page are multistory. A door on the
         | ground floor isn't a big deal, but above that they require fire
         | escape stairs, which are big and ugly and create a section with
         | poor views out the windows.
        
         | scotty79 wrote:
         | All examples seem to be about single stairs vs pair of stairs.
        
           | RegnisGnaw wrote:
           | Which is the key issue. The second set of stairs is needed
           | for the second egress.
        
         | jaclaz wrote:
         | Not really, they are saying that the requirement for a second
         | egress in multi-apartment buildings (which is not only a second
         | fire door, it is also a second stair, etc.) makes too
         | costly/complex mid size buildings.
         | 
         | The first image on this page exemplifies the issue:
         | 
         | https://secondegress.ca/A-Wicked-Problem
         | 
         | https://freight.cargo.site/t/original/i/9b6f13e0414b47f094ad...
        
           | eklitzke wrote:
           | I don't understand. I live in a three-story apartment
           | building in San Francisco that has about 20 units (ground
           | floor is retail space, the upper two floors have 10 apartment
           | units each). There's a single entrance and stairwell in my
           | building. However my building also has two fire escapes (one
           | of which is accessible via the hallway, I think the other
           | fire escape is only accessible by certain apartment units)
           | and an additional wooden staircase in the back that leads to
           | the garbage area. I don't know all the zoning laws, but this
           | is an extremely common layout in SF. My building, like many
           | many other buildings in the city, was built in 1906 after the
           | earthquake, and all of the building built in this time period
           | have a very similar style and layout.
        
             | bryanlarsen wrote:
             | According to the article, it's buildings with 2-4 units per
             | floor that are significantly impacted by this rule. At 10
             | per floor, your building is a lot larger than the ones the
             | article is talking about.
        
             | astrange wrote:
             | It's very common, especially in places like SF, for all the
             | old buildings and neighborhoods that people actually like
             | to be illegal to build if they were new.
             | 
             | Of course, in SF it's practically illegal to build anything
             | under any circumstances if any of your neighbors decide
             | they don't like it.
        
           | twblalock wrote:
           | That sounds fair on the surface, but we manage to build
           | multi-egress buildings all the time in other countries, and
           | if a single stairwell is the only egress a lot of people
           | could die in a fire. Some of these mod-sized buildings are
           | too tall to make jumping out of a window a realistic option.
           | So I'm not really sympathetic to this argument.
           | 
           | Unlike some building codes, this one is directly connected to
           | a life and death issue and we have seen what happens in fires
           | where people can't get out.
        
             | bombcar wrote:
             | Yeah, it seems to me that we can actually work out the
             | situations involved, and being on the sixth floor of a
             | building with only one fire egress seems undesirable.
             | 
             | Perhaps it can be compensated for with various "either two
             | egresses OR each bedroom must be equipped to be fire proof
             | for X minutes" or something, and bring back hook and ladder
             | trucks (arguably which are not used as much because
             | buildings now have multiple egresses when that tall).
        
               | pessimizer wrote:
               | > each bedroom must be equipped to be fire proof for X
               | minutes
               | 
               | This is the kind of absurdly complex regulation that
               | sounds simple, but is a lobbyist's dream. Two exits are
               | easy to know when you've implemented, and easy for
               | regulators to check if you've implemented. A "bedroom"
               | being "fire proof" for X minutes will involve 900 pages
               | of nonsense regulations from which lobbyists have
               | carefully removed anything that will affect their bottom
               | line.
               | 
               | "Each bedroom must be equipped to be fire proof for X
               | minutes" was the type of rule that caused the fire
               | brigades to tell people in Grenfell to stay in their
               | apartments, and even more importantly the type of rule
               | that allowed contractors to claim compliance to was
               | sufficient enough that they could use flammable, shit
               | cladding that was illegal in Europe and the US, and
               | install it incompetently (because if the units were
               | "fireproof," who could care?)
        
               | bombcar wrote:
               | Very good points - and Grenfell is an example as to why
               | these regulations exist; otherwise people would burn to
               | death in "missing middle" housing and nobody would really
               | care much.
        
               | nasmorn wrote:
               | I live in Vienna and almost all buildings are single
               | staircases with 4-8 floors. Almost all house fires are in
               | old housing stock. In new concrete apartment buildings it
               | is usually a single apartment that burns out. It is an
               | almost absurd fear compared to eg traffic related deaths.
        
             | henrikschroder wrote:
             | Except what this site says is that counter-intuitively,
             | this policy doesn't save lives, it's actually the opposite:
             | 
             | "Zeidler explains that "this appears to be a reasonable
             | precaution for life safety. However, the life safety of
             | this single stair type in Europe has been equal to, if not
             | better than ours," due to the fact that the single stair
             | scheme is shared between fewer units."
             | 
             | And that's the thing, _entire countries_ disagree on the
             | necessity of a second stairwell for fire safety, and there
             | 's data to back up the position.
             | 
             | But because a lot of people in North America have those
             | (unfounded) fears, the second stairwell is part of the
             | building code, and as a result an entire class of buildings
             | don't get built because the economics don't work out.
        
               | twblalock wrote:
               | > But because a lot of people in North America have those
               | (unfounded) fears, the second stairwell is part of the
               | building code, and as a result an entire class of
               | buildings don't get built because the economics don't
               | work out.
               | 
               | I don't believe the fears are unfounded, and frankly I
               | don't see why anyone should buy what this Zeidler guy is
               | selling -- if what he is saying is true, all it means is
               | that European buildings should also be changed to have
               | multiple egress options for every unit!
               | 
               | Seriously, would you be willing to live on the 6th floor
               | of a building where the only way out in a fire is a
               | single staircase? Don't look at statistics to decide
               | this: even if you would be safe most of the time, it only
               | takes one outlier incident to kill you, so why put
               | yourself in that situation?
        
               | WWLink wrote:
               | I'm siting here pondering how adding a second stairway to
               | a building makes it economically unfeasible. What kinda
               | crappy buildings are you making where the stairway is
               | that substantial to the cost of the construction?
               | 
               | And in low rise buildings, there's usually a LOT of
               | stairways lol. A typic suburban US apartment complex has
               | a half dozen buildings, and each one has maybe 12
               | apartments and like 4 stairways.
        
               | astrange wrote:
               | Adding a second stairway typically requires rearranging
               | the building to be double-loaded (having a central
               | hallway with apartments exclusively on either side),
               | which wastes much more space, only allows windows on one
               | side of the apartment, feels like you live in a hotel
               | etc.
               | 
               | https://www.treehugger.com/single-stair-buildings-united-
               | sta...
        
               | frickinLasers wrote:
               | What's wrong with fire escapes? I see plenty of space to
               | add those to a point access block.
        
             | squokko wrote:
             | How many fire deaths are worth how much housing?
             | Inaccessibility of housing is tied to economic destitution,
             | homelessness, and other things that directly cause deaths.
             | It's entirely possible for more quality-adjusted life years
             | to be lost in the path that causes less housing to be
             | built.
        
       ___________________________________________________________________
       (page generated 2023-01-09 23:03 UTC)