       | turdherder wrote:
       | Real life licensed and certified plumber here.
       | 
       | Regarding the threads on common pipe fittings here in Cali: NPT
       | threads are designed to be cut with a pitch and angle that are
       | self sealing.
       | 
       | Sealing compounds can assist in the lubrication of threads to
       | easily tighten them up but should not be absolutely necessary.
       | 
       | Imo it's an aid to assembly and disassembly and not always
       | necessary depending upon the application. And in some
       | applications it's forbidden
        
       | jasonhansel wrote:
       | Conveniently, of course, the US and Canada use NPT instead of
       | BSP, the worldwide standard. Even if an NPT fitting and a BSP
       | fitting are the same size, one won't screw into the other, since
       | the threads have different shapes and are at different angles.
        
         | djcapelis wrote:
         | This guy wrote a whole article outlining how bad and unusable
         | the British pipe standards are and you're surprised the two
         | (ish) continents that don't use them are actually pretty happy
         | with their standard and don't want the other?
         | 
         | NPT has some flaws and complexities but generally while it's
         | comprehensive conventions and practices mean that for specific
         | types of plumbing you'll need some specific standard fittings
         | and once you get used to them that's pretty much that. From
         | gases to liquids. None of this "whoa someone decided to use a
         | tapered one here" you don't get to chose what fitting you're
         | feeling like that day, we have building codes and if it's a
         | pipe in a wall carrying water than there's a convention (and
         | likely building code) that tells you your pipe, fitting, and
         | which way the threads should turn! (Generally in the broadest
         | strokes: Explosive gases are reverse threaded. Everything else
         | isn't.)
         | 
         | Anyway we've been saying no to bad British ideas since 1776.
         | Don't blame us outside the Americas the rest of you (and ISO)
         | fell for it.
        
       | dhosek wrote:
       | Of the three aspects of home maintenance that are most common1:
       | plumbing, electrical and carpentry, I feel most comfortable with
       | plumbing. It seems nicely discrete in that you're generally
       | putting together existing components without having to do much if
       | any measuring and cutting. That said, I'm moving into a new house
       | where I've got a handful of carpentry projects that will
       | definitely stretch my abilities in that arena.
       | 
       | [?]
       | 
       | 1. In my experience, I suppose, one could perhaps add
       | concrete/masonry and may be something with dirt?
        
       | agsamek wrote:
       | This article doesn't touch much about why plumbing is hard. I'm
       | from Poland so I'm not only IT but also a plumber ;)
       | 
       | Plumbing is hard because it is not forgiving. It's as binary as
       | IT except you can learn the outcome with some delay, once you
       | learnt about a damage caused by a leak. Either you do a pressure
       | tests right or repair can be expensive. And bugfixing is always
       | tricky.
       | 
       | Water also goes down whether you like it or not. Think about all
       | possible leaks inside the shower cabin. Or what is even more
       | impressive that under a pressure the water goes everywhere
       | possible.
       | 
       | Plumbing is similar to electrical engineering, except it usually
       | doesn't kill immidiately (though working with gas is tricky
       | anyway) but requires similar strict mental model to do right.
       | 
       | And when you see a plumber it seems like this person is just a
       | physical worker. So work status misconception must be leveled
       | with money...
        
         | PaulHoule wrote:
         | My complaint is that plumbers frequently do poor work for the
         | money.
         | 
         | We had some come and install an instant water heater and they
         | cut an ugly hole in the side of the house without much thought.
         | 
         | At one office I worked in they called Roto-Rooter (a non-union
         | franchise that is likely to wreck your pipes and require a call
         | to the union plumbers afterwards) who claimed that we'd flushed
         | a condom down the drain (very hard to believe) and wrecked the
         | pipes so we had to call the union plumber.
         | 
         | Another time the sink wasn't running so we called the union
         | plumbers, they unscrewed the aerator from the faucet, saw some
         | crud come out and the water run and left in triumph, sure of
         | their ability to outthink a group of mere computer nerds.
         | 
         | Us computer nerds were sitting at the faucet immediately after
         | that, running it and talking about it. The now aerator free
         | faucet clogged up again within 2 minutes of the plumbers
         | leaving.
        
           | nkrisc wrote:
           | > My complaint is that plumbers frequently do poor work for
           | the money.
           | 
           | Considering the quality of many expensive website and
           | software implementations I've been required to use throughout
           | the years at various jobs, this problem is not unique to
           | plumbers.
        
           | agsamek wrote:
           | > My complaint is that plumbers frequently do poor work for
           | the money.
           | 
           | Hehe - now you can feel like an IT customer. I think most
           | people feel the same about IT but the domain is just more
           | wide and prone to excuses.
        
             | pasquinelli wrote:
             | people feel that way about stuff they have to pay for,
             | generally.
        
               | PaulHoule wrote:
               | No, I've never felt that way about a union electrician or
               | generic handymen.
        
         | throw0101c wrote:
         | > _This article doesn 't touch much about why plumbing is hard.
         | I'm from Poland so I'm not only IT but also a plumber ;)_
         | 
         | I'm guessing that is a reference to Omid Djalili sketches about
         | Polish plumbers:
         | 
         | * https://www.youtube.com/watch?v=K85ZtXnMxbM
         | 
         | * https://www.youtube.com/watch?v=P8mjzu0Runo&t=1m
         | 
         | * https://www.youtube.com/watch?v=_FM9Ps6cW9U
         | 
         | * https://en.wikipedia.org/wiki/Omid_Djalili
        
           | lajosbacs wrote:
           | It's a stereotype across the whole Europe, even Poland takes
           | advantage of it https://en.wikipedia.org/wiki/Polish_plumber#
           | /media/File:Pol...
        
             | agsamek wrote:
             | Thanks for sharing. This was exactly what I was referring
             | to. Also youtube links from the UK are nice, shame you are
             | out of EU for the time being :)))
             | 
             | Anyway - I just added a valve regulation to our kitchen
             | floor heating this weekend, so it was not only joking :)
        
               | lajosbacs wrote:
               | I also found the UK vids amusing (am not a Pole) -- kind
               | of how to make fun of a stereotype in a positive way.
        
         | iancmceachern wrote:
         | Yes, and it's even less forgiving when it's a gas, or worse a
         | flammable gas, or 3000 psi hydraulic fluid.
        
         | georgeoliver wrote:
         | I had a funny experience a week ago. One night working on a
         | hobby web project it took me three or four hours to debug
         | something, I finally got to bed around midnight thinking "boy,
         | programming is hard".
         | 
         | The next day at work we had to find a broken heat wire in a
         | tiled bathroom floor, running 1000 volts through the wires to
         | try to fuse the broken wire, then heating the floor up and
         | searching with heat-sensitive paper overlays for the likely
         | broken spot, then breaking the tile with a hammer and digging
         | the wire out of the mortar bed. After we found it I thought,
         | "I'd rather hunt software bugs".
        
           | sokoloff wrote:
           | Does a thermal imaging camera not work for the finding task?
           | That seems like it would be faster, more certain, and less
           | aggravation all around.
        
             | georgeoliver wrote:
             | Good question, I don't know. The technician on site didn't
             | have one. I guessing the camera would be faster, but the
             | result image about the same. The nice thing about the paper
             | is you easily can check multiple spots at once, so it's
             | faster to divide down to the problem area.
        
           | CamperBob2 wrote:
           | Time-domain reflectometry. To Google it is to love it.
        
           | iancmceachern wrote:
           | I once had to jackhammer a 4 foot wide, 26 foot long, 4 foot
           | deep trench in my basement to replace the sanitary sewer in
           | my house. It was old terracotta pipe and had tree roots
           | growing into it and eventually blocked the flow. It was doing
           | that that helped me be so thankful to have an office job. I
           | also had to lug all the rubble upstairs in 5 gallon buckets.
        
       | swayvil wrote:
       | Given the choice, I love pex and those compression-bands that you
       | put on with the special pliers. Pex got flex.
       | 
       | For drains, pvc of course.
       | 
       | Given run-of-the-mill refurbby waterline junk with plain ol
       | copper, I like that brass kind of compression with the little
       | sleeve.
       | 
       | Don't trust sharkbite. Am a mediocre sweater.
       | 
       | For gas, threaded with that pipe goo works surprisingly well.
       | Haven't fucked it up yet.
       | 
       | I wonder if you can use pex with gas
        
         | ssl232 wrote:
         | You do your own gas work? I'm in the UK and I'm pretty sure you
         | basically cannot legally touch gas fittings unless you're a
         | qualified plumber.
        
         | iancmceachern wrote:
         | Agreed on the compression fittings over the sharkbite stuff.
        
       | PaulHoule wrote:
       | When I had to do some plumbing I found that everything was
       | undocumented. One source would tell you to refer to the
       | documentation published by the manufacturer of the fitting, which
       | is of course impossible to find.
        
       | jesusofnazarath wrote:
        
       | VLM wrote:
       | The story misses some points.
       | 
       | The first issue is pipes are used for a lot more than pressurized
       | drinking water, and for compressed gases there's various
       | standards so you don't accidentally connect your acetylene tank
       | to your argon regulator and vice versa. Depending on local
       | building codes, you have to work really hard in the USA to cross
       | connect your natgas to your water supply, etc. For a home
       | handyman this seems laughable but for giant construction projects
       | at industrial sites you will inevitably see insane stuff sooner
       | or later where roughed in water lines get accidentally connected
       | to compressed air and stuff like that. I personally saw a PVC
       | convenience pipe roughed in for ethernet cable get connected to
       | sewer vent.
       | 
       | The second issue, related to the above, is NPT relies on thread
       | deformation so the pros use pipe dope and the amateurs use teflon
       | tape that contaminates everything, so you technically "can" use
       | NPT for diesel or hydraulic but usually building codes and/or
       | OSHA prevent such nonsense. Also thread deformation means every
       | time you reuse a NPT its looser and leakier. Very slow leaking
       | threads are not an issue for compressed air, so black iron pipe
       | is common for industrial compressed air because who cares if
       | 0.01% leaks out, but for flammable contamination sensitive stuff
       | its a big issue. If 0.01% of your compressed air leaks out above
       | a food prep assembly line nobody cares but if 0.01% of your
       | hydraulic fluid leaks out into the food, then its a big food
       | safety mess. The point is that most of this technology is being
       | used outside its original use case, most NPT threads are not
       | holding back compressed air, but crazy people are trying to use
       | that tech to push natgas around or diesel or whatever and due to
       | "tradition" and "codes" we are stuck with it. So the argument
       | that NPT is shit so nobody should use it is pointless because its
       | "really intended for" compressed air and is great for that, super
       | cheap, easy to use, reliable enough, etc, so pointing out that
       | its not optimal for car brakes is both true and also not useful
       | "in practice".
       | 
       | Another comedy about threads: You can buy pipe dope to
       | professionally seal NPT threads for air, natgas, car brakes, and
       | water, but those pipe dopes are not the same, and you can cause
       | quite a bit of trouble if you use air dope on natgas for example.
        
       | thedanbob wrote:
       | I had a major plumbing problem some time ago (leak in the house's
       | main line) and paid a plumber way too much to dig a hole and fix
       | it. I of course wasn't about to pay him to fill the hole back up,
       | and while it was open I took a good look. That's when I
       | discovered PEX. PEX is wonderful: easy to work with, inexpensive,
       | simple to fix if you screw something up. I wish all plumbing was
       | PEX.
       | 
       | I briefly installed an NPT flow meter (that was probably actually
       | BSP) in the line. I can confirm that the PEX-to-NPT fittings
       | leaked until I used a whole roll of PTFE tape and a mountain
       | gorilla. Eventually the cheap flow meter started leaking from the
       | casing itself so I ripped it out and replaced it with beautiful
       | PEX.
        
         | iancmceachern wrote:
         | Pex is awesome, I replaced my entire house with it, I couldn't
         | have done it myself otherwise and had a great result.
        
         | toss1 wrote:
         | Can confirm - also started using PEX recently, and it is
         | fantastic - wouldn't go back for anything! Straightforward,
         | solid, more resistant to freezing (tho I still drain/blow out
         | the outside lines in winter). I've even had zero problems with
         | the PEX-copper fittings; I generally just attach straight onto
         | a cut pipe rather than an NPT fitting, so that may account for
         | my different experience.
         | 
         | I've run a few new lines in the house, and also new hose
         | faucets outside. Looking at using it for both vacuum and
         | compressed air lines in the shop.
        
           | VLM wrote:
           | There are two problems with PEX in the shop, one real one
           | joke.
           | 
           | The joke one is PVC + UV = shrapnel, and frankly given enough
           | time and vibration PVC doesn't need UV to shatter, so old
           | timers hearing you're using plastic in the shop will freak
           | out. (edited for those who don't get the joke: Pex will
           | definitely split or crack under UV but AFAIK never shatters,
           | so using PVC is a major OSHA violation but using unprotected
           | Pex is mostly safe although maybe economically unwise)
           | 
           | The real problem is the melting point is unimpressive and
           | you're like one lathe chip away from an air leak. Not
           | catastrophic but annoying. Murphy's law is air leaks only
           | happen when you don't have time to slap a new fitting on, or
           | when your collection of fittings is empty/missing and the
           | store closed five minutes ago.
        
             | toss1 wrote:
             | Thank you!! Very helpful tips, I appreciate it
        
               | scotty79 wrote:
               | There is a pex variant which consists of aluminium pipe
               | with plastic layers on the inside and outside. This
               | should combat low melting point of the plastic
        
             | beerandt wrote:
             | Locally, we also have problems with rodents chewing threw
             | unprotected pex. Probably because we rarely freeze, and
             | unprotected really means completely unprotected.
        
         | [deleted]
        
         | ssl232 wrote:
         | I've not done any major replumbing yet but I've been watching
         | Matt Risinger [1] on YouTube for a few months and have quickly
         | become a PEX fanboi. He's a home builder based in Texas and
         | uses PEX for basically every job. There are some videos on his
         | channel comparing different types of PEX and PEX against other
         | systems.
         | 
         | [1] https://www.youtube.com/@buildshow
        
         | latchkey wrote:
         | We started with welded joints, then moved to threaded (and
         | every variation in between of that). I kind of wonder if PEX
         | will be deprecated some day by something even better. We are
         | going to end up with yet another standard that PEX has to
         | interface with. Feels like an xkcd... https://xkcd.com/927/
        
         | jasonwatkinspdx wrote:
         | Came here to also plug PEX. A friend used it for his remodel,
         | did most of the work himself, and set everything up so all the
         | lines come down to a sort of "switchboard" panel in his
         | basement, so that as he did more remodeling work in the future
         | he could disconnect individual loops trivially. It just makes
         | so much sense and is so easy vs copper pipe.
         | 
         | Amusingly he told me one of the plumbers he did get a bid from
         | said something like "well all PEX does is save you time and
         | money" like it was a bad thing lol.
        
           | msrenee wrote:
           | It breaks down pretty quickly when exposed to light,
           | chlorine, and excessive heat. It's also very easy to damage.
           | A kid being an idiot or rats and mice gnawing on everything
           | like they do and you've got a heck of a leak that hopefully
           | is caught quickly.
           | 
           | Seems like there's lots of situations where it's a good
           | choice and lots of situations where it's not.
        
           | nemo44x wrote:
           | It's also super easy and affordable to run extra lines that
           | aren't being used for future use. For instance, it might be
           | you want to run a circulator across all your taps, but not
           | today.
           | 
           | You can in many cases snake it as well.
        
         | bilsbie wrote:
         | What's the one that leaks and you're supposed to replace?
        
           | schemescape wrote:
           | Probably polybutylene:
           | https://en.m.wikipedia.org/wiki/Polybutylene
        
           | tharkun__ wrote:
           | Kitec: http://kitecsettlement.com/
        
       | luxuryballs wrote:
       | I thought they were paid so much because plumbing is gross and
       | often just a huge pain.
        
         | iancmceachern wrote:
         | Exactly, I do the simple stuff myself and only call a plumber
         | when it involves crawling around in a spider infested crawl
         | space, working with poop, or similar things I am willing to oay
         | someone to do.
        
       | playingalong wrote:
       | What would you call this writing style (which I like a lot).
       | Ironic? Any more specific name?
        
         | mongol wrote:
         | Gonzo-inspired?
        
         | lelandfe wrote:
         | Disgruntled Brit? I read most of it in the tone of David
         | Mitchell: https://www.youtube.com/watch?v=Bz2-49q6DOI
        
         | OJFord wrote:
         | 'Annoying', personally.
         | 
         | Seriously though, sort of a monologue? Or I'd describe it (not
         | a single word) as spoken English taken to paper, in an oral
         | style, or something.
        
         | digitalsushi wrote:
         | conversational-familiar
        
       | hirundo wrote:
       | "When buying male fittings, it's best to always get tapered ones
       | so they fit in either."
       | 
       | I tried that with a shop compressed air system and got lot of
       | leaks, hissing, and the compressor turning on frequently. And I
       | never did get the system not to hiss somewhere, so I can
       | sympathize and ditto this rant. Even when using matching
       | fittings, with gobs of tape and/or dope, and enough force to
       | destroy multiple fittings, it leaks. I'd pay a plumber well to
       | teach me some of those mystic arts, if I could find one in my
       | plumber-free rural area.
        
         | loeg wrote:
         | Air hose standards are also annoying and differ from plumbing.
         | 
         | https://toolguyd.com/quick-guide-to-air-line-couplers-plugs/
        
           | katmannthree wrote:
           | The quick connect side yes, the threaded side is a standard
           | NPT (if you're in the US) which you treat the same way you
           | would any other NPT connection.
        
         | katmannthree wrote:
         | If you're talking about quick connects, they'll always leak a
         | bit.
         | 
         | The threaded fittings however are a different story. Assuming
         | you didn't use stainless steel on stainless steel fittings [0]:
         | 
         | * You can find the leaks by spraying soapy water on suspect
         | connections and looking for bubbles (wash off and dry with
         | clean water afterwards unless you want some serious corrosion).
         | You can also buy a jar of noncorrosive propylene glycol based
         | leak check fluid at your local hardware store for somewhere
         | around $10, which is a strictly better option although it's a
         | bit harder to clean off.
         | 
         | * Undo the connection and throw away every fitting you can
         | replace (you generally should not reuse NPT threaded
         | connections unless you know what you're doing). Clean all
         | fittings until they look brand new and with no visible debris
         | on/in the threads.
         | 
         | * Watch some videos [1] and remake the connection using the
         | proper amount of tape and sealant and appropriate torque [2].
         | Only tighten the fitting. If you loosen it even a bit during
         | the process, undo it completely. Clean both sides, reapply tape
         | and dope, and try again. Let the sealant set ~24h and retest.
         | 
         | [0]: Stainless steel pipe connections are a special case
         | because they tend to cold weld before they're fully tightened.
         | There are ways to mitigate that but the short answer is don't
         | use them if you don't already know how.
         | 
         | [1]: https://www.youtube.com/watch?v=whw9ApDJpJo
         | 
         | [2]: NPT connections really shouldn't be torqued (you instead
         | use turns from hand-tight for properly cut threads) but if
         | you're having trouble find a torque chart for your fitting
         | material (copper, brass, steel, etc) and follow that.
        
       | synecdoche wrote:
       | In one of the larger companies in Sweden in the third largest
       | city Malmo that sell to both other companies and consumers none
       | of the staff knew what I was talking about when I mentioned that
       | BSP and NPT are different. Neither people on the floor nor people
       | answering the phone. These were what appeared to be experienced
       | plumbers. It's amazing.
        
       | weare138 wrote:
       | That's funny. I literally just finished installing a new kitchen
       | sink and faucet at home. Holy crap was it a pain in the ass.
        
         | victor9000 wrote:
         | What was tricky about it? Having never done it, it seems
         | somewhat straight forward in my mind.
        
           | blincoln wrote:
           | Sinks are one of the few areas that I don't think one can get
           | out of using threaded connections on the supply lines
           | (haven't seen push-to-connect for that last leg yet). A lot
           | of them use NPT threads, and NPT is very easy to put together
           | in a way that will have a slow leak. Even a single drop every
           | few minutes can cause big problems if left unattended for
           | long enough. Also, a lot of the connections are in locations
           | that are a headache to reach, even with a basin wrench.
           | 
           | Getting a good seal on a sink drain can be a little tricky
           | the first time too.
        
             | sokoloff wrote:
             | The sink supply connections (usually from a shutoff valve)
             | are compression threads (a parallel/straight thread).
             | 
             | If the valve itself is threaded on, _that inlet_ might be
             | NPT (or might be compression), but the valve outlet will be
             | compression, which uses a tapered ferrule to provide the
             | seal and straight threads.
        
               | mindslight wrote:
               | The faucets I've seen are generally NPS where the supply
               | lines attach to the faucet, often with the retaining nuts
               | (or whatever they're called) using the same threads and
               | going on first.
               | 
               | To answer GGP's question, what's difficult about faucets
               | is getting up behind the sink, with your back straddling
               | the corner of the cabinet, reaching up with some sort of
               | basin wrench that inevitably won't grip those bespoke
               | retaining nuts well. Especially removing the old faucet
               | where the retaining nuts are a bit seized.
        
           | weare138 wrote:
           | The process itself is straight forward but I had to work in a
           | really tight space under the sink. That was really what made
           | it a pain in the ass. I had to lay on my back and cram myself
           | underneath the sink in the cabinet to reach everything plus
           | I'm a 6' tall goon so that definitely wasn't helping either.
           | You're just stuck in an awkward and uncomfortable position
           | most of the time.
        
             | ssl232 wrote:
             | Same experience installing a dishwasher. Inside a small
             | cavity accessible only by climbing over my new dishwasher
             | and avoiding the existing washing machine, crouching using
             | leg muscles I rarely ever use, with the only light coming
             | from a torch, on flooring made damp from dripping pipes
             | that I hadn't tightened enough, arms getting sore from
             | lifting them above my shoulders for extended periods, I
             | understood why plumbers get paid what they get paid.
        
       | throwawayacc4 wrote:
       | This article sucks. Lots of bad info from an inexperienced
       | plumber.
       | 
       | How the US military, nuclear power plants, and plumbers worth
       | their weight in salt do fittings: 3-4 times around the (male)
       | fitting with PTFE tape, then a light amount of pipe dope on top
       | of the PTFE tape.
       | 
       | Also, DO NOT buy the cheap PTFE tape as suggest. Buy the milspec
       | tape. Your big box store will have both and you'll know where
       | that money (a couple dollars at most) went.
        
         | CamperBob2 wrote:
         | _3-4 times around the (male) fitting with PTFE tape, then a
         | light amount of pipe dope on top of the PTFE tape._
         | 
         | That doesn't sound like a good idea at all. The whole idea
         | behind PTFE (aka Teflon) is that it reduces friction because
         | nothing, including pipe dope, sticks to it. What value does the
         | pipe dope add to a properly-wrapped fitting?
        
         | Severian wrote:
         | Milspec, lol. Doesn't that normally equal as cheap as they can
         | get away with?
         | 
         | There is a high-density thread sealing PTFE tape that works a
         | bit better than the el' cheapo generic white stuff (although
         | it's usually white too). Anything marked as such should be
         | sufficient unless you are working on an oil rig or nuclear
         | reactor.
         | 
         | EDIT: Unless the package has MIL-T-27730 on the tape, labeling
         | it milspec has no meaning.
        
           | kevin_thibedeau wrote:
           | > Milspec, lol. Doesn't that normally equal as cheap as they
           | can get away with?
           | 
           | It means a product meets stringent requirements that can't be
           | cheated on.
        
       | mildchalupa wrote:
       | The Teflon tape is only to be used as a friction modifier as NPT
       | and other tapered threads seal on the threads. Reduced friction
       | means that you can get enough load to deform the metal threads
       | and create a seal. Be careful to not add tape to the first 2
       | threads as small pieces of Teflon tape can break off and get
       | stuck into valves and things within appliances causing them to
       | leak. There is nothing wrong with pipe dope and I find it to be
       | superior though messy.
       | 
       | Annoyance for those in the states: Big box stores used to
       | advertise fittings as NPT (National pipe thread). NPT being an
       | ANSI spec. They seem to have switched to MIP and FIP for Male
       | Iron Pipe and Female Iron Pipe. These are NPT as well but with a
       | new name? Perhaps they are looking to avoid holding themselves to
       | the spec?
       | 
       | Lead content in brass drinking water rated piping and fittings
       | are being phazed out for obvious reasons. New low lead brass is
       | stronger and does not deform as easily as the older leaded brass
       | fittings. The result is that some fittings are now more difficult
       | to tighten untill leak free.
       | 
       | Pex and crimped copper fittings are not without there own issues.
       | Relying on an o-ring with a 30 year shelf life is problematic
       | when the pipe is behind drywall.
       | 
       | Perhaps one day we will get laser welded copper fittings.
        
         | loeg wrote:
         | I've seen FNPT and MNPT but not FIP/MIP.
        
         | frosted-flakes wrote:
         | Crimped PEX fittings do not use o-rings.
        
         | digitalsushi wrote:
         | it's really easy to go crazy at a box store and get boiler
         | fittings for a garden project. read the labels for lead
         | content!
        
         | imglorp wrote:
         | > Relying on an o-ring
         | 
         | Another category is Shark Bite, a simple push-on tech that is
         | almost homeowner proof. All you need for many jobs is a cutter,
         | some sandpaper, and the fitting: no pro tools, no torch. There
         | are tight joist spaces the new copper crimper won't fit and
         | overhead soldering is fraught, which you can sharkbite in 2
         | minutes.
         | 
         | Back to O-rings, I do wonder about the lifetime of the seals in
         | there though.
        
           | cf100clunk wrote:
           | If Shark Bite products are not available there is also the
           | Waterline Push-N-Connect line of similar products for
           | homeowners:
           | 
           | https://waterlineproducts.com/products/push-fit-fittings-
           | and...
           | 
           | There are other similar products from different companies.
        
           | belorn wrote:
           | Depend on size and material of the o-ring. A o-ring is a
           | flexible material that under pressure will bend in order to
           | fit a space. Under high pressure the material might intrude
           | out slowly, if you repeatably bend it it might snap, and as
           | with many flexible materials it may go brittle and crack if
           | exposed to changes in temperature or moisture.
        
       | jkqwzsoo wrote:
       | In case anyone from the US reads this, BSPP and BSPT fittings are
       | rare and incredibly frustrating here, as our NPT (National Pipe
       | Taper) threads are different and the selection of BSP(P/T)
       | fittings is extremely poor in comparison.
       | 
       | Also, I work with NPT fittings quite a lot:
       | 
       | > For what it's worth, I tightly wrap the tape 10 times round the
       | male thread and get an enraged mountain gorilla to tighten it up.
       | 
       | This is a WTF NO!!! for NPT and I'll assume a WTF NO!!! for BSPT
       | as well. You need about 1.5 wraps of PTFE tape to seal a fitting.
       | Any more is wasteful and asking for leaks (or damage, if you're
       | using plastic fittings). It helps if you use the correct tape
       | width for the fittings (1/4", 1/2", and 1" for me) and develop a
       | wrapping method that keeps the tape under tension at all time and
       | in such a direction that threading it into the fitting doesn't
       | unwrap the tape.
       | 
       | Also, in my experience, when someone inexperienced first learns
       | what pipe tape is, they try to apply it to everything. 20 wraps
       | around a tapered pipe? Wrap a Swagelok fitting? Try to make a
       | butt joint or an adapter for two pieces of plastic tubing? I've
       | seen it all.
        
         | PaulDavisThe1st wrote:
         | Pipe dope FTW.
        
           | jnellis wrote:
           | Indeed. If your threads are new you're not supposed to use
           | any teflon tape, you use pipe dope. Teflon tape is for worn
           | threads when you are out of pipe dope.
        
         | sokoloff wrote:
         | I use a minimum of 4 wraps and usually 5 or 6 wraps on black
         | pipe in the 3/4"-2" range. 2 wraps might be enough for nice
         | clean plastic or brass threads in the 1/2" or less range, but
         | larger steel fittings need more PTFE tape.
        
         | kortex wrote:
         | > You need about 1.5 wraps of PTFE tape to seal a fitting.
         | 
         | Not a pipe fitter, but I've done a lot of plumbing on a huge
         | variety of systems (sinks, drains, air lines, HPLCs and other
         | chemistry equipment, bioreactors, RO systems, potato cannons).
         | I have found through experience that the thick PTFE tape
         | (usually grey or yellow) is almost always superior to the thin
         | tape. I use 2-3 wraps of that and that seems to be ideal.
         | 
         | Thick tape is also a lot easier to remove than the thin PTFE if
         | you have to reinstall (you aren't supposed to re-use tape if
         | you unscrew it).
        
         | kennend3 wrote:
         | As someone who is NOT a pipe fitter but lived with one for many
         | years.. It was odd reading this and I'm glad someone like you
         | responded to correct things.
         | 
         | > For what it's worth, I tightly wrap the tape 10 times round
         | the male thread and get an enraged mountain gorilla to tighten
         | it up.
         | 
         | Again, not a pipe fitter but this just screams "WRONG". If
         | someone needs to use that much force to tighten it up, one can
         | only assume that the pipe is now so full of tape it simply
         | doesn't fit?
         | 
         | My roommate had a "unlimited BTU" gas fitter license (Canada
         | Class "A") and this for a living and preferred "pipe dope"
         | 
         | "Pipe dope is generally stronger seal than Teflon tape, which
         | is why plumbers and other professionals use it rather than tape
         | for seals that are permanent."
        
           | rsync wrote:
           | "My roommate had a "unlimited BTU" gas fitter license (Canada
           | Class "A") and this for a living and preferred "pipe dope""
           | 
           | I do this kind of thing _a lot_ as we own and maintain our
           | own water plant. My preferred sealant is the yellow PTFE tape
           | that is used for natural gas.
           | 
           | It is quite a bit thicker than the white tape, it sticks to
           | threads better and it is easier to work with, in terms of
           | manual dexterity.
           | 
           | I never use the white tape for anything.
           | 
           | I don't like pipe dope at all and I only use it for large
           | fittings that are going to be buried or inaccessible.
           | 
           | ALSO, helpful hint: If you are mixing plastic pipe (like
           | schedule 40/80) and metal pipe, always have metal female
           | couplings and plastic male couplings. A metal male going into
           | a plastic female is one tighten away from cracking the
           | plastic.
        
             | couchand wrote:
             | I've seen people suggest that white tape should only be
             | 1.5-2 but yellow should be 5 or more, do you have thoughts
             | on that? Is there a difference in usage or is it the same
             | overuse pattern on both?
        
             | amluto wrote:
             | > ALSO, helpful hint: If you are mixing plastic pipe (like
             | schedule 40/80) and metal pipe, always have metal female
             | couplings and plastic male couplings. A metal male going
             | into a plastic female is one tighten away from cracking the
             | plastic.
             | 
             | Or buy transition fittings or "special reinforced"
             | fittings. Or, if you trust them, use push-to-connect
             | fittings -- SharkBite, John Guest, ProLock, etc. (ProLock
             | appears to be a John Guest product that is also sold by
             | SharkBite.)
             | 
             | I've seen plenty of female plastic threaded fittings break
             | even when connected to male plastic threaded fittings.
             | They're just not that strong under circumferential tension.
        
         | balls187 wrote:
         | > Also, in my experience, when someone inexperienced first
         | learns what pipe tape is, they try to apply it to everything.
         | 
         | That's me. Whoops.
        
           | VLM wrote:
           | Tape causes massive contamination problems with fuel and
           | hydraulic systems.
           | 
           | Its not that the Teflon reacts with hyd oil, its that the
           | inevitably little tiny bits of stuff physically jam/ruin
           | seals and clog nozzles.
        
             | culopatin wrote:
             | But only if you put the tape over the edge. I usually leave
             | the first 2 threads uncovered, why would it fall into the
             | stream if you don't cover the tip of the thread with it?
        
               | kevin_thibedeau wrote:
               | When you open up the joint, bits are left behind in the
               | female half. Then they get pushed in when it's resealed.
        
               | VLM wrote:
               | The most installed/removed NPT thread will leak the most
               | thus have the most tape added and the scraping of
               | installation/removal will guarantee teflon contamination
               | of the system eventually.
               | 
               | You are also correct in that something installed one time
               | for the lifetime of the system, especially with some care
               | and attention to cleanliness, is almost certainly OK.
        
           | rdl wrote:
           | Ugh, I applied it to _PVC_ pipe, which made it leak, sigh.
        
             | [deleted]
        
             | VincentEvans wrote:
             | There's no problem applying it to a threaded connection in
             | PVC. Unless you mean that you've figured out a way to apply
             | to a fitting that's meant to be glued? In that case I
             | commend your abundant creativity.
        
               | rdl wrote:
               | My experience is that even one wrap of PTFE tape on
               | threaded PVC causes it to loosen and then leak, and it's
               | recommended by youtube/google to not use it. (Some say
               | sealant is ok).
        
         | hilbert42 wrote:
         | _" You need about 1.5 wraps of PTFE tape to seal a fitting. Any
         | more is wasteful and asking for leaks"_
         | 
         | I would have thought this obvious and it's essentially my
         | experience (and I'm definitely not a plumber). However, I've
         | found that more PTFE tape is needed on old or worn fittings or
         | on ones that have damaged or badly cut threads--or when mating
         | same sized pipes/fittings but each with different threads (yes,
         | that's a desperate brute-force move in an emergency but I've
         | had to force such matings on more than one occasion). In these
         | circumstances, I'll use two or three turns or more often by
         | trial and error--and this changes somewhat depending on whether
         | I'm using thinner white PTFE tape or the thicker pink one.
         | 
         | Of course--not being plumber--it often happens that when I
         | urgently need PTFE tape I cannot find it (it having been filed
         | in some obscure place that I've forgotten about--even though I
         | keep a reasonable stock of it), it's then I fall back to the
         | good old combination of Hessian/burlap jute-type rope (of which
         | there is always some lying around in my workshop) and linseed
         | oil based paint. It's messy and much less convenient
         | combination than PTFE tape but it still works wonderfully well.
         | Moreover, it's more tolerant of the amount applied as the
         | linseed oil actually binds to the pipe surface as opposed to
         | the more 'mechanical' bond of the PTFE.
        
           | SaintGhurka wrote:
           | "combination of Hessian/burlap jute-type rope (of which there
           | is always some lying around in my workshop) and linseed oil
           | based paint."
           | 
           | Could you explain that? How do you seal pipe fittings with
           | rope?
           | 
           | Edit: found an explanation. TIL that you can use the fibers
           | just like tape and wrap the threads.
        
             | hilbert42 wrote:
             | Perhaps if I'd used the proper name what I said may have
             | been clearer. The correct name is hemp rope or plumber's
             | rope but I don't often have that around (not being a
             | plumber) so I use the next best thing available Hessian
             | fabric or its rope equivalent).
             | 
             | Here are some photos:
             | https://www.bunnings.com.au/enduraseal-1m-plumbers-
             | hemp_p012...
             | 
             | https://waropes.com.au/twines/plumbers-hemp/
             | 
             | You wrap the hemp fibers around the threads that have been
             | brushed with linseed oil paint then apply a little more
             | paint to the hemp and then mate the couplings together.
             | This sealing technique has been around at least for several
             | hundred years if not longer.
        
             | throwaway294566 wrote:
             | You don't need oil, just rope works as well. Every DIY
             | store (at least over here) has loose manila fibre for that
             | purpose. Wrap into the thread, screw it together, done. The
             | not-so-nice problem: It might leak at first. The nice
             | feature: The fibres will soak up water (thats why oil is
             | actually counterproductive), swell up and make a tight fit
             | after half an hour or so. You can even readjust the angle
             | (other than with PTFE tape), it'll just drip for another
             | half hour.
        
               | hilbert42 wrote:
               | Right, there are multiple variations but they generally
               | work in skilled hands although I learned from plumbers
               | who always used oil (although using oil was always an
               | imperative with gas pipes). Using oil usually negates the
               | initial leaking whilst waiting for the hemp to dampen and
               | swell.
               | 
               |  _Edit: I agree that using oil is counterproductive with
               | water pipes--initially at least. I was taught by both
               | plumbers and my father (who wasn 't a plumber but a
               | mechanical engineer who worked on power station boilers)
               | that using oil is better in the long run as it prevents
               | the hemp from rotting and thus premature failure of the
               | seal. Moreover, using one oil-based method means that a
               | plumber cannot get confused and leave oil off gas
               | connections where it's essential.
               | 
               | (I'd add that when referring to oil I'm specifically
               | referring to linseed oil (even though I've seen some
               | plumbers inappropriately use engine oil) because it
               | slowly polymerizes and hardens even in the absence of
               | air. This adds to the seal's effectiveness and further
               | protects the hemp.)_
        
           | jcims wrote:
           | >Of course--not being plumber--it often happens that when I
           | urgently need PTFE tape I cannot find it
           | 
           | Ahh, young padawan, the way of the elder is to buy a roll
           | every time you have a project to do until you have achieved
           | saturation...where there is a lightly used roll of teflon
           | tape in every drawer and on every surface of your workshop
           | and garage.
        
             | sokoloff wrote:
             | I unlocked an uncommon DIY achievement last month: I
             | finished an entire 119 foot roll of PTFE tape.
        
               | jcims wrote:
               | That's beyond 'uncommon', you should get a trophy.
        
               | hilbert42 wrote:
               | One has to ask 'finished it doing what'.
        
               | bluGill wrote:
               | Some sort of mummy costume party i'm sure
        
             | andylynch wrote:
             | This is the way. It's also cheap enough that buying a dozen
             | rolls upfront is less effort!
        
             | semireg wrote:
             | I just bought 24x 6" stainless steel rulers because every
             | time I'd reach for one it'd be across the room at a
             | different desk. Now I can capture a dozen at a time in
             | their remote location for rehoming. Problem solved.
             | 
             | Also on my list of buy too many so I'm never left without:
             | sharpies, microfiber cloths, jumper cables, rice (carbs),
             | frozen sliced sourdough (fancy carbs), pocketable
             | protein/energy bars.
        
             | hilbert42 wrote:
             | Ha! I'm no longer a Padawan so, like you, I'm well
             | acquainted with the practice of spreading things around to
             | the point of saturation.
             | 
             | It's not only PTFE tape that I spread around in copious
             | quantities, other notables on the list are screwdrivers (of
             | various sizes and types), superglue tubes (they go off with
             | age anyway), propelling pencil leads, keys, USB and
             | computer cables, USB pen drives, computer mice, adhesive
             | tape, remote controls and any number of useful things.
             | 
             | The trouble is these supposedly inanimate objects come to
             | life in the middle of the night and conspire not to be
             | available when I most need them. Then the moment I've made
             | do by jerry-built means they suddenly reappear! ;-)
        
               | dtgriscom wrote:
               | When I was a kid, my mom's theory on pencil purchasing
               | was that if she bought enough, the house would be so
               | saturated that you could shake a curtain and a pencil
               | would fall out.
        
               | hilbert42 wrote:
               | Hum... Clearly, I'm not alone. That's at least some
               | comfort.
        
               | geerlingguy wrote:
               | Almost every night I pick up 3-5 pencils around the main
               | living area at our house. Somehow there are always dozens
               | of pencils around, but finding one with a working eraser
               | on the end is as rare as finding a unicorn.
        
               | devnullbrain wrote:
               | The mistake-making side is much larger than the mistake-
               | fixing side. This is a display of great, foolish
               | optimism.
        
             | mindslight wrote:
             | That's only the way of the middle-aged. If you do it with
             | just PTFE tape you'll be fine, but if you do it with all
             | similar sundries, then you'll be oversaturated and once
             | again won't be able to find anything without pawing through
             | piles.
        
               | hilbert42 wrote:
               | Right, see my reply to _jcims_ but that 's not all of
               | matter. One could suppose I'm going senile and perhaps
               | that's true but the fact is that I've been losing stuff
               | like this since before I was a teenager.
               | 
               | I've figured out the problem: my mind is thinking about
               | all sorts of seemingly important stuff all the time but
               | which in fact is mostly garbage, so my subconscious mind
               | handles what my conscious mind consideres as procedural
               | or unimportant. As my conscious and subconscious minds
               | aren't on speaking terms sufficient for my liking I often
               | end up with the problem of lost stuff.
               | 
               | If I consciously tell myself where I've put something
               | then I very rarely forget where it is. The trouble is I
               | don't remind myself to make note often enough.
        
               | mindslight wrote:
               | My own working model is one of complexity building up
               | over time. You can handle it fine as long as you don't
               | have many fields of endeavor, you have plenty of time to
               | periodically focus on them, keep the stuff organized, can
               | fully finish a project and button it up, etc. But then
               | things happen where you're forced to clear out your
               | mental cache, or even screw up your organization/storage
               | system for whatever, and it comes crashing down. Then all
               | the complexity you were managing gets in your way, and
               | the problem snowballs unless you regain some bandwidth
               | and take steps to mitigate the decay.
        
               | hilbert42 wrote:
               | Right, that makes sense. And my explanation is more
               | complex than I could detail in my comment.
               | 
               | I know I have too many diverse interests--fields of
               | endeavor to quote you--and the older I get the more of
               | them I accumulate. On the one hand having many interests
               | is very useful because it allows me to see and understand
               | common ideas or threads across quite disparate and
               | diverse subjects that otherwise would not have been
               | obvious but the matter of administration becomes a
               | significant problem. Often I've little time to deal with
               | prosaic matters so the mundane is often left to itself
               | (disorder accumulates).
               | 
               | That said, I'm instinctively an orderly and tidy person,
               | as I like to say _' there's a place for everything and
               | everything in its place'._ I hate mess and disorder but
               | that doesn't mean that I don't experience it--I do so
               | often for reasons that you mention. However, when
               | entropy/disorder around me reaches a certain
               | 'sensibility' threshold I'm triggered to have an almighty
               | cleanup much to the chagrin of others around who have a
               | more relaxed view of disorder.
               | 
               | Nevertheless, I'm not obsessive about it, sometimes I
               | amaze myself at the level of disorder I'll tolerate.
               | (Reordering things is boring and distracts me from my
               | interests despite the fact that I'm competent and
               | thorough about it. Essentially, the more preoccupied I am
               | with something the higher my toleration for mess and
               | disorder becomes).
        
               | Geezus-42 wrote:
               | Have you ever been diagnosed with ADD/ADHD?
        
               | TeMPOraL wrote:
               | Or you find yourself married and with children, and that
               | final step of regaining some bandwidth becomes
               | structurally impossible to achieve.
        
               | hilbert42 wrote:
               | It all adds up to what I call the 'overhead of living
               | problem'.
        
         | robk wrote:
         | This is more useful than Teflon tape I find
         | https://www.amazon.co.uk/Loctite-K97870-Henkel-Sealing-Multi...
        
         | aidos wrote:
         | I think there's cultural difference where the tongue in cheek
         | context has been lost a bit.
         | 
         | They probably use neither 10 full wraps, nor an enraged
         | mountain gorilla, but then I've seen stranger things in
         | plumbing.
        
           | fuzzfactor wrote:
           | The lowland gorilla comes to mind . . .
        
         | azalemeth wrote:
         | I particularly _hate_ the confusion that BSP and NPT cause.
         | They 're almost interchangeable (differing, iirc, probably on
         | the angle of flank) and will get about three turns in and then
         | leak or fail under pressure. In my world, this has led to
         | graduate students spraying liquid nitrogen around. It's clearly
         | the case that the two probably were supposed to be identical
         | but diverted due to manufacturing differences in the distant
         | past.
         | 
         | The standard advice I've been given when it comes to either
         | vacuum or cryo fittings is "cut anything American off it as
         | soon as it arrives and put DIN standard or KF kit on as soon as
         | possible". Standards are a pain and that xkcd about there being
         | too many of them is very, very true.
        
           | iancmceachern wrote:
           | Little nit pick. BSP is British.
        
         | mgarfias wrote:
         | A small quibble: the tape don't seal. It's a lubricant for the
         | threads wedging together to seal.
         | 
         | For a REALLY good primer on the subject, read Carrol Smith's
         | _Nuts, Bolts, Fasteners and Plumbing Handbook_ (aka Screw to
         | Win).
        
           | pengaru wrote:
           | > For a REALLY good primer on the subject, read Carrol
           | Smith's _Nuts, Bolts, Fasteners and Plumbing Handbook_ (aka
           | Screw to Win).
           | 
           | +1 for anything by Carrol Smith
           | 
           | Back in my gearhead days Engineer To Win was a near constant
           | fixture next to the toilet.
        
             | mgarfias wrote:
             | I had no idea he lived nearby when I was in HS (also
             | Gurney's shop was within biking distance, also didn't know
             | it).
             | 
             | If I could go back I'd blow off all the dumb shit I did and
             | go ask to push a broom all day just to hang around race
             | cars and learn.
        
           | johnwalkr wrote:
           | Such a great book. I'm a mechanical/aerospace engineer and
           | it's astounding how many in my field don't understand
           | fasteners and tend to oversize them. It's seen as
           | conservative but it can actually backfire.
        
           | kortex wrote:
           | > the tape don't seal.
           | 
           | No, the tape absolutely contributes to the seal. Sure, the
           | lubrication lets you thread more tightly without binding, but
           | that's not to say the tape isn't contributing to the seal. If
           | it didn't, you would still have a spiral leakage path. PTFE
           | tape is soft enough that it deforms and prevents the spiral
           | leakage path which can occur with any tapered threaded joint.
           | 
           | I've actually used PTFE tape in super high pressure
           | situations (>1000 psi) with straight (un-tapered) joints (you
           | aren't typically supposed to, but this was for an
           | experiment), and it indeed sealed.
           | 
           | > The tape also works as a deformable filler and thread
           | lubricant, helping to seal the joint without hardening or
           | making it more difficult to tighten
           | 
           | https://en.wikipedia.org/wiki/Thread_seal_tape
        
         | mannykannot wrote:
         | What do you think of the advice that it is acceptable to use a
         | tapered male thread in a straight female one? My guess is that
         | if you do that, you have at best one turn of the thread helix
         | holding them together and providing a seal (and perhaps you
         | would be trusting in nothing more than the tape jammed between
         | the threads if you used ten turns of it!)
        
           | [deleted]
        
           | johnwalkr wrote:
           | I don't think it's acceptable. Maybe works in pinch to get
           | through a weekend but I would always replace it with a proper
           | fitting. Plus if you damage the female threads or o-ring
           | seat, you've made a much worse problem for yourself.
        
         | berjin wrote:
         | If you want a really good seal you wrap the tape 1-2 overlaps
         | at the start of the thread and progressively make it thicker
         | and thicker so you have more overlaps (10x) at the base. I
         | guess it depends on the fittings but some run out of tapper and
         | you can't tighten it anymore without the hexagonal nut hitting
         | the adjacent fitting. This works well as you're building your
         | own tapper which is sort of acting as an o-ring.
         | 
         | Generally BSP male fittings are always tapped which is why they
         | don't mention it.
        
           | jakewins wrote:
           | Do you have a reference for this? Everything I've read is the
           | purpose of the tape is to reduce friction (hence PTFE), not
           | to actually seal. In other words, the seal comes from the
           | fittings connecting tightly, made possible by 2-3 wraps of
           | PTFE low friction tape.
        
             | XorNot wrote:
             | PTFE tape is meant to block the helical path around the
             | screw threads for leaks to propagate. For parallel threads
             | it's absolutely vital.
             | 
             | Taper threads are designed to crush together to achieve
             | something similar, but for what's available at the hardware
             | store I've always had problems.
        
         | [deleted]
        
       | Kaibeezy wrote:
       | All this plumbing talk got me remembering the time I redid a
       | bunch of the copper in a fixer-upper. Reading up on solder
       | joints, I got into the underlying metallurgy, and discovered
       | solder isn't "glue". You have to abrade it to remove the oxide,
       | quickly cover the raw copper with flux, and then let the boiling
       | flux draw the molten solder into the joint. It doesn't take much,
       | and you end up with a metal-metal-metal bond. Once I understood
       | the point, the joints were a breeze. Later, I had a pro plumber
       | in to deal with some iron pipe, noticed my copper work and was
       | impressed. Very satisfying.
        
         | Scoundreller wrote:
         | > and discovered solder isn't "glue".
         | 
         | I see you've never had the chance to observe some of my PCB
         | work!
        
           | rzzzt wrote:
           | "The bigger the glob, the better the job". Some solder joints
           | are structural.
        
         | scotty79 wrote:
         | I'm really not confident about copper pipes. Metals in solder
         | are very different electrochemically than copper. There might
         | be other electrically connected metals in the installation.
         | There might be some impurities grains in the copper.
         | 
         | I've seen videos of copper pipes developing pinhole leak from
         | corrision.
         | 
         | I always used aluPEX for doing the piping.
        
       | everyone wrote:
       | Programming is analogous to a trade like plumbing in many ways
       | imo.
       | 
       | * You both design and then build a thing.
       | 
       | * No one else knows how it works or cares until it stops working.
       | 
       | * Through work you build up your own set tools and methods that
       | you like and can apply to various jobs.
        
       | joshuaheard wrote:
       | I had to learn the arcane world of pipe fitting sizes working
       | with pneumatics for a scuba equipment project. It is extremely
       | confusing. Unfortunately, it can have fatal consequences. In a
       | recent story, a scuba store employee used the wrong size fitting
       | on a 3,000 psi scuba tank which shot out and killed them.
       | 
       | Seeing that American can't even adopt the metric system, I have
       | little hope for a clear international standard for pipe fittings.
        
         | noNothing wrote:
         | All Americans completely understand the metric system. We can
         | convert anything to anything in our heads. By the way, we all
         | speak a dozen foreign languages fluently, just choose not to.
         | It is because we are so humble that you do not know this.
        
       | mindslight wrote:
       | Cheap fittings from GENSYM sellers on Amazon/Ebay/Aliexpress will
       | have crappy threads, which will cause you endless pain. I'm
       | guessing this is what inspired the author's rant. I generally try
       | to buy fittings from suppliers that have an incentive to do some
       | quality control. If one thread in a joint isn't perfect you're
       | probably fine, but when both are terribly out of spec, it will
       | never seal.
       | 
       | I see the author used the word "spanner" so I assume they're
       | British which is why they have to earnestly deal with BSP. For
       | fellow Americans, don't get anything BSP/BSPP/BSPT unless you
       | have to (eg hydraulics commonly use BSPP/G-thread, and the bonded
       | rubber washer is not optional).
       | 
       | For pipe tape/dope, the important thing to know is their main
       | purpose is to reduce friction so you can tighten a joint further,
       | which deforms the threads more - packing the threads is a
       | secondary effect. I generally do dope, then 2-3 wraps of tape (in
       | the right direction, of course), then dope again. I generally use
       | the thicker blue tape, but thinner white should be the same with
       | a few more wraps. I learned this trick from an old timer at a
       | hardware store, and it has definitely helped on some recalcitrant
       | joints. I'd rather not find leaks after something is assembled,
       | so I just take the time and do it on most every joint now. (For
       | reference, I mostly deal with 1/4 - 1 inch NPT
       | brass/stainless/copper threads).
       | 
       | Also, not every type of connection takes dope/tape! For example,
       | while US showers generally have NPT-M coming out of the wall, the
       | showerhead generally has a rubber washer that makes the seal, and
       | thus does not need tape. Similarly with flare/compression
       | fittings.
       | 
       | Also, plumbers get paid a lot because it's generally heavily
       | regulated - water supply contamination is one of those things
       | we've refined over centuries and now take for granted. The
       | regulation means they get a middle class wage, which is
       | prohibitively expensive for other individuals to pay owing to
       | high taxes and other overhead. Imagine how much it would cost to
       | hire yourself as a software engineer for half a day.
        
       | jsz0 wrote:
       | I had to do some plumbing work a few years ago and quite enjoyed
       | solving the puzzle and completing the work myself. It did remind
       | me a lot of my day job in tech. No individual part of the job is
       | all that difficult but planning and executing everything
       | properly, and all the cryptic/arcane knowledge required, was very
       | similar. And just like when one of my networks or systems is down
       | the work had to be completed quickly to resolve the outage.
        
       | blincoln wrote:
       | I've helped out with some plumbing work in an older house, and
       | it's pretty fascinating to see the progression of technologies.
       | 
       | 100 years ago, most drain pipes in the US were massive cast-iron
       | pieces with no threads at all. They were mated together, then the
       | joint was filled with a compound called oakum. To really hold it
       | together, the plumber would pour molten lead on top of the oakum.
       | Just taking that stuff apart is a lot of work. I can't imagine
       | putting it together as well, especially for 40 hours a week.
       | 
       | I agree with the author's dismay about threaded fittings, but
       | 100% disagree about PTFE tape versus thread sealant. PTFE tape is
       | garbage. If you use thread sealer the way it's supposed to be
       | used (put on a decent amount, then thread the pieces together
       | with the "nudge and a grunt" technique instead of cranking down
       | on it with a huge amount of force), it will seal perfectly almost
       | every time, and any minor leaks can usually be fixed by
       | tightening the joint slightly. If that's not enough, just take it
       | apart and redo it. I've rarely had to try twice, and never three
       | times.
       | 
       | Not sure about British threaded pipe, but NPT threaded pipe
       | actually doesn't benefit from being tightened beyond a certain
       | point because of the way the threads are designed. I redid the
       | seals and some of the fittings[1] on all the antique hot water
       | radiators in a house because no contractor within a day's travel
       | would work on antique hydronic heating systems. Good quality
       | thread sealant, no garbagey PTFE tape, no leaks, even in constant
       | use.
       | 
       | That having been said, modern pipes and fittings make things dead
       | simple. PVC (or ABS, but PVC is nicer IMO) for drains, push-to-
       | connect fittings for water lines (I like PEX, but I know opinions
       | vary). No lead, no torches. Easy to cut with hand tools.
       | Lightweight. Anyone who's interested can probably do at least
       | basic work with modern pipes.
       | 
       | [1] https://youtube.com/watch?v=MeHiE-j1KuQ
        
         | Tijdreiziger wrote:
         | > To really hold it together, the plumber would pour molten
         | lead on top of the oakum.
         | 
         | This is pretty interesting, because plumbers are called 'lead-
         | pourers' (loodgieters) in Dutch, and I had always wondered why.
        
           | skeptical_dog wrote:
           | The english word, too, is derived from the Latin for lead:
           | plumbum.
        
             | jimnotgym wrote:
             | In fact _some_ plumbers still do lead work. Lead sheet roof
             | flashings are common in the UK. Roofers can beat it into
             | certain shapes, but if you need something more complex you
             | would get a plumber to weld it for you.
             | 
             | I learnt to lead-weld (with oxy acetylene) in the past and
             | found it very satisfying...
        
             | Scoundreller wrote:
             | It's not called Pb for nothing!
        
             | beerandt wrote:
             | Except the meaning is to plumb, as in to level, as in to
             | get water flowing downhill.
             | 
             | The lead refers to the (lead) plumb bob used to determine
             | the direction of vertical and therefore what's level.
        
               | robocat wrote:
               | https://etymology.en-academic.com/27822/plumber
               | 
               | https://etymology.en-academic.com/27820/plumb
               | 
               | It appears you are wrong, and the person you are replying
               | to was correct. Perhaps when baldly contradicting
               | someone, you could make some effort to back up your
               | opinion.
        
               | beerandt wrote:
               | The first 2 meanings of plumb from the site you link is:
               | 
               | https://etymology.en-academic.com/27820/plumb
               | 
               | plumb plumb {{11}}plumb (adj.) "perpendicular, vertical,"
               | mid-15c., from PLUMB (Cf. plumb) (n.). The notion of
               | "exact measurement" led to extended sense of "completely,
               | downright" (1748), sometimes spelled plump or plunk.
               | 
               | {{12}}plumb (n.) c.1300, "lead hung on a string to show
               | the vertical line," from O.Fr. _plombe, plomme "sounding
               | lead," from L.L. _plumba, originally plural of L. plumbum
               | "lead," the metal, of unknown origin, related to Gk.
               | molybdos "lead"
               | 
               | Neither have anything to do with pouring molten lead.
               | Only measuring the vertical.
               | 
               | The purpose of finding the vertical is to determine the
               | horizontal in installing sloped pipe.
        
               | robocat wrote:
               | I skimmed what appear to be reliable references, and they
               | all mention the Latin -> French -> English etymology for
               | plumber, and they do not reference "plumb" in the sense
               | you are using.
               | 
               | I suspect that plunging in and making a poor argument
               | doesn't reflect well upon you. I am happy to be
               | corrected, if you can provide a rock-solid reference: the
               | English language is a wonderful midden.
        
               | eesmith wrote:
               | Whilst "plumb" comes the Latin for "lead", so does
               | "plumber", and from a different and earlier path than
               | "plumb". Quoting https://www.etymonline.com/word/plumber#
               | etymonline_v_17491 :
               | 
               | > late 14c. (from c. 1100 as a surname), "a worker in any
               | sort of lead" (roofs, gutters, pipes), from Old French
               | plomier "lead-smelter" (Modern French plombier) and
               | directly from Latin plumbarius "worker in lead," noun use
               | of adjective meaning "pertaining to lead," from plumbum
               | "lead" (see plumb (n.)). The meaning focused 19c. on
               | "workman who installs pipes and fittings" as lead pipes
               | for conveying water and gas became the principal concern
               | of the trade.
               | 
               | We can read Vitruvius' description of chorobates at https
               | ://penelope.uchicago.edu/Thayer/E/Roman/Texts/Vitruvius..
               | . (Note that https://ethw.org/Roman_Aqueducts claims "the
               | credit given to this instrument by Vitruvius was out of
               | proportion to its real usefulness.")
               | 
               | > The chorobates is a rod about *twenty feet in length,
               | having two legs at its extremities of equal length and
               | dimensions, and fastened to the ends of the rod at right
               | angles with it; between the rod and the legs are cross
               | pieces fastened with tenons, whereon vertical lines are
               | correctly marked, through which correspondent plumb lines
               | hang down from the rod. When the rod is set, these will
               | coincide with the lines marked, and shew that the
               | instrument stands level.
               | 
               | The Latin for "plumb lines" is seen in "quae habent
               | lineas ad perpendiculum recte descriptas pendentiaque ex
               | regula perpendicula in singulis partibus" - Vitruvius
               | does not use a variation of "plumb" to describe those
               | verticals.
               | 
               | That usage, from the quoted etymology, wasn't created for
               | another 1,000+ years.
               | 
               | I could be wrong of course, but the evidence I've seen
               | doesn't support your claim at
               | https://news.ycombinator.com/item?id=33765351 .
        
           | manojlds wrote:
           | And plumbers are called plumbers in English because they work
           | in plumbings?
           | 
           | Same origin in English as well! (Plumbum = Lead)
        
           | [deleted]
        
         | blincoln wrote:
         | Just to be clear, I'm not trying to discount the skill and
         | knowledge of professional plumbers. It's an incredibly complex
         | field (especially since they need to be familiar with decades
         | of different pipe technology), and usually involves working in
         | filthy parts of the house no one else wants to go into. They
         | deserve every penny.
        
           | MomoXenosaga wrote:
           | Normally the market is supposed to correct these things but
           | sadly we've created a culture that looks down on physical
           | labour. Now there is a small group that can charge whatever
           | they want.
        
             | toast0 wrote:
             | They can't charge that much or people will do their own
             | plumbing. It's fussy, but most routine things aren't too
             | hard to do one step at a time. Sometimes you get a new
             | faucet with an internal leak though, experience might have
             | helped diagnose that without taking everything apart 20
             | times. Sometimes there's a big job like replacing a
             | lateral, which is yeah, time to hire a pro.
        
               | jimnotgym wrote:
               | In the UK gas work is regulated so only a registered
               | plumber can do it.
        
               | sacrosancty wrote:
        
             | bathtub365 wrote:
             | Is the market not supposed to reflect culture?
        
               | ElevenLathe wrote:
               | This is an outdated ideology. Now the market is meant to
               | define correctness. Deviation from the perfect wisdom of
               | the market is the only form of sin.
        
         | cmclaughlin wrote:
         | > I like PEX, but I know opinions vary
         | 
         | What's not to like about PEX?
        
           | johnmaguire wrote:
           | I believe it's less durable than alternatives.
        
             | Scoundreller wrote:
             | There's definitely a "right" way and a "wrong" way to do
             | it.
             | 
             | Having each fixture connection being a "home run" without
             | _any_ fittings between source and destination really
             | reduces a lot of vulnerabilities. Having a central manifold
             | that lets you easily turn off any tap is nice too.
             | 
             | A condo building I lived in did something wrong (I suspect)
             | either a bad batch of PEX, or more likely, a batch that sat
             | in the sun for a while, leading to multiple failures of hot
             | water return lines in few years that were a mystery to pin
             | down.
        
               | iancmceachern wrote:
               | Also using the compression fittings with a good crimping
               | tool, not the push to connect fittings IMO is more
               | durable and reliable.
        
               | frosted-flakes wrote:
               | Home run plumbing also means a _lot_ of pipes in the
               | walls, so you end up with 20x more pipes in the walls and
               | ceiling than is actually necessary, and 20+ valves, which
               | are often made of plastic instead of brass because
               | otherwise costs would balloon. In any case, the fittings
               | aren 't the weak point, the pipe is; a properly crimped
               | joint or expansion joint will never leak. And often it's
               | impossible to have no fittings on a run of pipe anyway.
               | 
               | In my opinion, traditional trunk and branch plumbing is
               | far more flexible and just as reliable. It also allows
               | for a hot water recirculation loop, which is impossible
               | with home-run plumbing.
        
             | bluGill wrote:
             | Actually pex is probably the most durable. Water is
             | corrosive and will slowly dissolve metal pipes .
             | 
             | Pex has zero UV resistance though, sp if exposed to sun at
             | all it is the least durable.
        
           | mindslight wrote:
           | Thinking about a system a half-step up from hose clamps
           | holding 100psi of pressure, which if it pulls apart will
           | rapidly release hundreds of gallons of water does not inspire
           | confidence. And since the house is already plumbed with
           | copper and I know how to sweat joints, I might as well
           | continue that.
           | 
           | I'm about to use PEX for the first time on my hydronic
           | heating system, which is only ~20psi and limited volume
           | (autofill valves are an anti-pattern). Maybe I'll fall in
           | love, who knows.
        
             | D13Fd wrote:
             | I haven't seen 100 psi in household applications
        
               | mindslight wrote:
               | My city water pressure was around there, with few ill
               | effects. I've since installed a pressure regular to drop
               | it to around 60psi. But I liked it better before,
               | especially on the silcocks.
               | 
               | It's not really the pressure that has me worried, but
               | rather the potential flow rate. I've dealt with a flooded
               | basement before, and I'd rather not do it again.
               | 
               | I don't see many people complaining that PEX fails by
               | completely pulling apart, but it's hard for my intuition
               | to accept that.
        
             | sokoloff wrote:
             | Be sure to read up on oxygen barrier vs permeable Pex. (You
             | probably already have, but if not, you almost certainly
             | want barrier Pex in a closed-loop system.)
        
             | blincoln wrote:
             | One of the things I like about it is that because it's
             | flexible, if you route it carefully you can avoid using
             | connectors in a lot of areas that rigid pipe would require
             | a joint. The way I saw it used, the only joints were in
             | areas like cleanout access and crawlspaces, so even if a
             | joint went bad, it wouldn't require opening up a wall to
             | fix. I'm not a pro, so maybe rigid pipe is supposed to only
             | have joints in accessible areas too, but that certainly
             | wasn't the case with the century-old plumbing I saw.
             | 
             | It's still relatively new compared to other pipe material,
             | so there may be some other surprises that crop up with long
             | term use, but I'm really impressed with its ease of
             | installation.
        
               | jimnotgym wrote:
               | One thing about plastic pipe is that it is susceptible to
               | rodent damage, unlike copper.
               | 
               | Seen it a few times.
        
         | TEP_Kim_Il_Sung wrote:
         | hemp fiber > PTFE tape
        
           | blincoln wrote:
           | For sure. Those oakum + lead joints were problem-free a
           | century after they were installed. How many of us can expect
           | that from the things we do at work?
           | 
           | The only reason some of that pipe needed to be replaced was
           | that it was fused (by rust) to mid-20th-century galvanized
           | pipe that had rusted completely shut.
        
             | dotancohen wrote:
             | Those lead joints were leaching lead into the water. If it
             | was a supply pipe, as opposed to a drain, then people were
             | ingesting that lead. It needed to be replaced whether it
             | was leaking or not.
        
               | blincoln wrote:
               | It was just the drain pipe system that was built that way
               | (at least in the house I helped out with). All of the
               | supply lines were galvanized steel, replaced with PEX.
        
               | jaggederest wrote:
               | The lead in those joints never touches liquid. It's a
               | sealant on the back of the oakum, which is what does the
               | actual water contacting.
               | 
               | Also, nearly all water supplies (municipal, at least) are
               | pH adjusted to be slightly basic, which causes lead to
               | form lead carbonates and oxides, which is (basically)
               | insoluble in cold water. Still good policy to replace
               | lead supply lines, but not a crisis unless you allow your
               | water quality to fluctuate (ala Flint or a number of
               | other US cities, sadly)
        
               | Scoundreller wrote:
               | More recently, beyond pH control, cities are doing
               | orthophosphte corrosion control. Nearly universal in UK
               | but hit and miss in other places.
               | 
               | https://www.haldimandcounty.ca/wp-
               | content/uploads/2018/07/Or...
               | 
               | A big source of lead can be recently sweated copper lines
               | (takes a while for the corrosion control to coat it), but
               | lead solder isn't _supposed_ to be in potable use
               | anymore. And old fixtures!
               | 
               | Even newer "lead-free" fixtures aren't 0% lead.
               | 
               | https://www.epa.gov/sdwa/questions-and-answers-about-
               | final-l...
        
               | jaggederest wrote:
               | Yes I've found it's very frustrating looking for
               | "genuinely zero lead" brass and bronze. Almost all scrap
               | has lead in it to some degree, and even new metal often
               | has a trace.
        
               | TEP_Kim_Il_Sung wrote:
               | Remove about 82% of lead from bronze using this one weird
               | trick!
               | 
               | https://www.researchgate.net/publication/250155103_Remova
               | l_o...
        
               | Scoundreller wrote:
               | I was hoping for something involving a particle
               | accelerator and making gold.
        
             | NegativeLatency wrote:
             | Generally the lead joints described above were only used
             | for waste plumbing where the max pressure is very very much
             | lower than the water supply pressure
        
         | baybal2 wrote:
        
         | blincoln wrote:
         | Also, I should mention that I've used PTFE tape without any
         | issues for air tool connections. It's just for plumbing - where
         | even a slow, tiny leak can cause massive damage - where I think
         | it's a terrible choice.
        
           | scotty79 wrote:
           | It's perfectly usable but you need to wrap a lot of it. If
           | you wrap so long that you can barely make out a thread
           | underneeth you can have a good seal lasting decades even if
           | you don't screw the thread in completely.
           | 
           | On steel pipes and fittings obviously. Plastic ones might
           | crack.
           | 
           | Also hemp fiber requires bit more practice and leverage but
           | it's really good.
        
       | naich wrote:
       | Having just completed a small project involving plumbing, this
       | post on my blog comes from the heart.
        
         | typhonic wrote:
         | There are plenty of technical comments here, but I have to say
         | I got a great laugh from this post. I have dealt with many of
         | the absurdities state side, so I can relate to your experience.
         | By the time I got to the words Windows XP Screensaver, I was
         | laughing so hard I couldn't read anymore. After finishing, I
         | bookmarked you. Looking forward to more. Thanks.
        
       | AlbertCory wrote:
       | I had a doctor once who was quitting his solo practice and taking
       | a regular job at a hospital, having become disillusioned with the
       | biz. He said his house was bought by a plumber, who was trading
       | up.
        
       | xyzelement wrote:
       | Why "someone" gets paid a lot was a discussion topics this
       | Thanksgiving. The answer is as always "law of supply and demand."
       | 
       | Want to make money? Learn to do something people really need but
       | not a lot of them can or want to do.
       | 
       | Perhaps pipe fitting is one of the "things" for plummers.
        
       | lisper wrote:
       | Best. Conclusion. Ever.
        
       | tehwebguy wrote:
       | Probably because you only call them when building or solving a
       | water or poop related emergency, so times when you _really_ need
       | a plumber.
       | 
       | Interesting read about the pipe fittings too though!
        
       | 1970-01-01 wrote:
       | They're paid so much because you need to pay twice for the bad
       | ones. My house's previous plumber threaded a copper line directly
       | into the stainless steel DHW tank. That wasn't a problem, until
       | it was.
        
         | amluto wrote:
         | I've never encountered a DHW tank made of stainless steel with
         | stainless steel fittings.
         | 
         | The error that _will_ destroy your pipes is to use anything
         | copper in the condensate plumbing of a condensing boiler. Use
         | PVC, CPVC or PEX (or stainless steel) with _plastic_ fittings
         | (PVC, CPVC, "engineered polymer", or John Guest ProLock or
         | similar). The high CO2 concentrations in the condensate will
         | rapidly corrode copper.
        
           | zbrozek wrote:
           | https://www.chiltrix.com/heat-exchanger-tanks/DHW80.pdf
        
       | bmalicoat wrote:
       | I was hoping this was going to be written by Leslie Claret.
       | 
       | https://www.lgclaret.com/
       | 
       | "Hey, let me walk you through our Donnelly nut spacing and crack
       | system rim-riding grip configuration. Using a field of half-C
       | sprats, and brass-fitted nickel slits, our bracketed caps and
       | splay-flexed brace columns vent dampers to dampening hatch depths
       | of one-half meter from the damper crown to the spurve plinths.
       | How? Well, we bolster twelve husked nuts to each girdle-jerry.
       | While flex tandems press a task apparatus of ten vertically
       | composited patch-hamplers. Then, pin flam-fastened pan traps at
       | both maiden-apexes of the jim-joist."
        
         | dtjohnnymonkey wrote:
         | This is what I came here looking for.
        
       | ok_computer wrote:
       | Bsp, Npt, goop (yuck!), and teflon tape are all inferior to
       | Swage. Cold weld and reuseable but it is a trade in itself to fit
       | and bend to place.
       | 
       | https://en.m.wikipedia.org/wiki/Compression_fitting
       | 
       | Working in labs on fluid and vacuum lines (<1in diameter) this is
       | the way.
       | 
       | If only it wouldn't cost as much as the house in fittings + tube
       | to hardpipe stainless fittings on our water supply lines.
       | 
       | I stayed in a hostel hotel in Munich, DE with hard piped bathroom
       | water lines. I was impressed and think they must have been in
       | service for 30-50 years.
        
       | walrus01 wrote:
       | Of other industrial interest re: pipes, sch40 and sch80 hot dip
       | galvanized pipes in various outer diameters are also a standard
       | item for telecom construction projects.
       | 
       | For when you want to have a pipe-to-pipe adapter to hang a radio
       | on a tower, or wall mount it on top of a building mechanical
       | penthouse or similar.
        
       | zabzonk wrote:
       | i got worried at this point:
       | 
       | "imagine putting a tapered male in a straight female"
        
       | csours wrote:
       | Because they are licensed, and the license requires the
       | equivalent of apprenticeship.
        
       | zackbloom wrote:
       | I would personally recommend trying TFE paste, rather than Teflon
       | tape. Easier to get a seal, less annoying to tighten.
        