[HN Gopher] Homemade Heat Pump Manifesto (2009)
       ___________________________________________________________________
        
       Homemade Heat Pump Manifesto (2009)
        
       Author : walterbell
       Score  : 416 points
       Date   : 2022-09-24 05:02 UTC (17 hours ago)
        
 (HTM) web link (ecorenovator.org)
 (TXT) w3m dump (ecorenovator.org)
        
       | frankus wrote:
       | Slightly unrelated, but there's a proposal to use a shared
       | ownership/utility model for the borehole/trench component and
       | install it in e.g. the street: https://heet.org/energy-
       | shift/geomicrodistrict-feasibility-s...
        
         | kortex wrote:
         | Fascinating! I would have not expected that maintaining annual
         | thermal balance would be as big of an issue as it is.
        
       | sethammons wrote:
       | HN loves heat pumps; I'll never have one again - utter shite.
       | 
       | I lived in the mountains of Southern California. As part of an
       | FHA loan in buying my childhood house from my dad, we had to
       | "upgrade" from a swamp/evaporative cooler and wood burning stoves
       | and went with a heat pump. The unit and ducting just couldn't
       | keep up. It sighed out slightly warmer/cooler air and, when it
       | kicked on, it pushed outside-temp air into the house that, in
       | winter, would take the unit over an hour to bring the house back
       | to its starting temp, let alone warm it. It really sucks to be
       | cold and to have to get colder before a chance at warming up. It
       | was similarly lame at cooling, though it would keep the house
       | from sweltering if started before sunrise. Temp range outside:
       | 20-40s in winter, up to 90s with a couple of days in the 100s in
       | summer.
       | 
       | We went back to the wood burning stove and swamp cooler.
        
         | ricardobeat wrote:
         | Wait, why would the unit pull fresh outside air in? Shouldn't
         | the ratio of recirculation be adjustable?
        
           | sethammons wrote:
           | The venting was exterior to the house and was heavily
           | influenced by outside temp
        
             | timbit42 wrote:
             | I'm starting to wonder if you were scammed. That's not how
             | modern air-to-air heat pumps work.
        
         | [deleted]
        
         | Gravityloss wrote:
         | Something doesn't sound correct now. In an air heat pump, the
         | compressor and a heat exchanger are outside, only warm liquid
         | flows through a hose into the building where its heat is spread
         | out with a room unit. The system doesn't move air in or out.
        
           | sethammons wrote:
           | The heat pump we had installed did not have any liquid hosing
           | that I was aware of (maybe something internally in the unit?)
        
             | timbit42 wrote:
             | Whatever you had, it seems it wasn't like what are on the
             | market today. I don't think your experience is relevant
             | here.
        
         | xani_ wrote:
         | Sounds like fucked up install - why on earth it would get
         | colder when it activates ?
        
       | post_break wrote:
       | My new dryer is a heat pump. Uses less than half the energy my
       | previous one did. It does take longer to dry clothes, but it's
       | much gentler on the clothes so it's a perfect trade off for me.
       | I'd love to do a heat pump like this for the house but there is
       | so much oil pipeline around me and there's no way a truck with a
       | pile driver can reach my back yard.
        
         | dzhiurgis wrote:
         | Hot water cylinders can have heatpumps too!
         | 
         | Wish we found a solid way yo harvest heat from waste water. So
         | much energy is wasted on showers - similar to EV driving at
         | highway speeds.
        
           | bombcar wrote:
           | We do it. It's not yet economically worth it but I've seen
           | installs. I can't find it but I saw one that was designed to
           | let a massive shower run continuously with very little heat
           | loss - the water coming out the end of the drain was as cold
           | as the inlet water from the main.
           | 
           | https://en.m.wikipedia.org/wiki/Water_heat_recycling
        
           | throwaway4220 wrote:
           | https://en.m.wikipedia.org/wiki/Countercurrent_exchange A lot
           | of mammals do this including humans. Don't know if there's a
           | drop in plumbing shower solution.
        
           | theluketaylor wrote:
           | drain water heat recovery is already a thing. It's code for
           | new builds in British Columbia, Canada.
           | 
           | It's only expensive due to the amount of copper. The actual
           | install has no moving parts and is completely passive.
           | 
           | https://www.nrcan.gc.ca/energy/products/categories/water-
           | hea...
        
             | dzhiurgis wrote:
             | What efficiency are these? Brainstormed this a bit and
             | feels like shower cabins (pretty popular over NE Europe)
             | should have such system as standalone... As in - it
             | collects waste, collects heat and stores it for next
             | shower. Dunno how much energy a typical refrigerant can
             | store tho. Also great fit for Japanese-style smart baths
             | (press a button and water of desired temperature fills and
             | stays warm), tho they seem rare outside Japan.
        
               | theluketaylor wrote:
               | I think they can recover up to 60-70% of the heat in the
               | drain water. Not bad for totally passive. The installs I
               | have seen are on the main drain for the whole house and
               | located right next to the hot water heater. For it to
               | really work you need a hot water tank, but I have seen
               | some small tanks combined with tankless.
        
           | xani_ wrote:
           | If you already have water-water heat pump I'd imagine it
           | would be a heat exchanger away from recovering at least
           | _some_
        
       | walterbell wrote:
       | From the same forum, a 50+ page thread on DIY ventilation heat
       | exchangers, e.g. 4"x4"x24" window unit that moves heat from
       | exhaust airflow to fresh incoming airflow,
       | https://ecorenovator.org/forum/showthread.php?t=891&page=38#...
       | and a home-sized DIY HRV,
       | https://ecorenovator.org/forum/showpost.php?p=26861&postcoun...
       | 
       |  _> outside temperature is 10,0 degrees Celcius, inside T is 21,1
       | and incoming fresh breeze (top) at 19,0!!_
        
         | walterbell wrote:
         | More links via above thread.
         | 
         | 2016 pipe design with 3" metal duct inside 4" PVC pipe,
         | https://www.loudawson.com/17884/how-to-build-air-cross-flow-...
         | 
         | 2012 box design with aluminum foil on wood frames,
         | https://makezine.com/projects/heat-exchanger/
         | 
         | Elegant $100 commercial window HRV, discontinued (why?),
         | https://www.amazon.com/Bionaire-BAP336M-U-EverFresh-Exchange...
         | & https://ia904509.us.archive.org/29/items/manualzilla-
         | id-7067...
        
           | dzhiurgis wrote:
           | I keep thinking window air cons should integrate heat pump
           | and HRV. Such a simple solution for ton of problems.
        
           | sgc wrote:
           | One thing I noticed when reading on diy hrvs in the past, is
           | that many porjects are not taking into account air volume in
           | the two ducts, and the amount of nominal flow for the size
           | ducts compared to the ideal amount of air exchange. A 5 inch
           | duct inside a 7 inch duct is more or less the correct size
           | for many homes: about 50 cfm each direction. I do like the
           | fact that there is a ton of dead space in most attics, where
           | you can just drop a long, well insulated pipe hrv and be done
           | with it for a relatively low cost.
        
       | alexose wrote:
       | Note that this thread is still active 13 years later! The most
       | recent post is by the OP, and reads:
       | 
       | > I want to take a moment to recognize that the Homemade Heat
       | Pump Manifesto has gone beyond 2 million page views. I would like
       | to thank Daox and any other people who may have worked behind the
       | scene to make it possible.
       | 
       | > My initial goal was to make available the knowledge and
       | possibility that anybody with a few tools and gumption could
       | convert discarded air conditioners, and dehumidifiers into very
       | high efficiency heat ources, or cooling sources. Through the
       | years, we have received reports of success from many people,
       | living in many states, and countries.
       | 
       | > Another goal was to make zero money from this project, to give
       | it away and to encourage others to take it, share it, sell it.
       | 
       | > In the beginning I thought that maybe 200 people would find
       | this interesting. Obviously, I was wrong, gloriously wrong.
        
         | layer8 wrote:
         | And that is why traditional web forums and their
         | discoverability are great. This wouldn't work on Reddit or
         | Discord.
        
           | HenriTEL wrote:
           | What makes you think reddit is not discoverable?
        
             | kybernetyk wrote:
             | sometimes whole subreddits get deleted because of $reasons.
             | sometimes I get to a link and a message greets me: this
             | subreddit has been deleted because of no moderation.
        
               | ceejayoz wrote:
               | Whole forums go missing, too.
        
               | Scoundreller wrote:
               | Or the image boards that have all of the instructional
               | photos from 10y ago disappear, or go premium but the
               | original poster is MIA/dead.
               | 
               | Faaaack, I'm still maintaining this 17yo Toyota. I need
               | those brake change pictures!
        
               | layer8 wrote:
               | It's straightforward to have them archived on archive.org
               | though, because they are more akin to static web pages
               | than to a web app.
        
             | layer8 wrote:
             | What I mean regarding Reddit is that you couldn't have a
             | thread running for 13 years like that, which you could
             | easily follow (track up to which comment you've already
             | read) and conveniently browse like on a forum. Pagination
             | is important for that.
             | 
             | On web forums, a new comment on a thread automatically
             | bumps that thread up to the top of the thread list, which
             | means that even after a pause, existing threads gain
             | traction like if they were new threads. (Possibly even more
             | than new threads, due to the existing contents.) That way
             | it's easy to have a focused discussion for
             | weeks/months/years on a particular subtopic.
        
               | hutrdvnj wrote:
               | But the problem with that approach is that people tend to
               | revive zombie threads. I would estimate that <1% of
               | threads actually have any useful discussion after 10
               | years, the rest is bumping zombie threads.
        
               | layer8 wrote:
               | I'm not sure what qualifies as a zombie thread. If the
               | new comments are meaningful contributions to the topic,
               | it's perfectly fine to revive an old thread. It's
               | certainly better than to have new threads about the same
               | topic every few days or weeks, ignoring the previous
               | discussions.
               | 
               | In any case, I've never experienced reviving old threads
               | to be a significant issue, or to happen inappropriately
               | to any significant degree.
        
               | Tostino wrote:
               | Not my experience at all. I spent a whole lot of time on
               | the endless sphere forum (forum for building PEVs) when I
               | was in my teens and early 20s, and in my 30s now some of
               | the technical threads from back then are still relevant
               | and going strong. The discussion on there is light-years
               | better than Reddit and HN for anything related to power
               | electronics or EVs in general.
        
               | JeremyBanks wrote:
               | "Necro" or "zombie" threads aren't actually bad
        
               | cortic wrote:
               | I would just like to estimate that >99% of threads older
               | than 10 years have useful information and the potential
               | for useful discussion.
               | 
               | I realize that where i am enthusiastic about older
               | things, cars/bikes/tech/languages, you probably like new
               | stuff. I hope you realize that most of the zombie
               | revivalists agree with me. Most of the time we are
               | looking for a new solution to an old problem, which is
               | the definition of progress. Locking threads after 6
               | months (thanks Reddit) or berating someone who want to
               | revive an old topic, cripples progress.
        
               | soulofmischief wrote:
               | A simple visual indicator of the age of a post such as a
               | zombie emoji (or something less tacky) is all that is
               | needed to quickly disregard zombie posts you aren't
               | interested in. Forums are great but we definitely need a
               | UX overhaul incorporating the last 15 years of web UX
               | research.
        
               | layer8 wrote:
               | About UX, I agree insofar as web forums have worse
               | usability than Usenet clients had before. However, I
               | don't see how web UX has improved in the last 15 years,
               | in particular on the desktop, and in particular regarding
               | forum and messaging apps.
        
               | soulofmischief wrote:
               | Mainstream design has taken a total nosedive, but there's
               | still great UX research being done across multiple
               | domains, one big driver being games.
        
               | layer8 wrote:
               | It would be great to have a couple of blog posts about
               | that.
        
               | rsync wrote:
               | The ability to revive zombie threads is a _feature_.
        
             | sgt wrote:
             | IMHO a bit of the problem with Reddit is that it's so
             | extremely threaded. I can understand replying to an
             | individual message within a discussion topic, but the tree
             | growing to the right just makes it hard to find out what's
             | the "latest".
             | 
             | The great thing about old style forums is that you'll check
             | it once in a while and just go looking for the "latest"
             | message, almost like joining IRC after a few days. You can
             | go look at earlier messages but it's not always necessary.
             | 
             | Or am I wrong - can you make some sub-reddits work that way
             | ?
        
             | neither_color wrote:
             | On a ten year old reddit thread you'll find the top voted
             | answers and top voted replies to those answers but not a
             | sequential discussion for page after page.
        
             | slowmotiony wrote:
             | It's discoverable but you can't post comments in old
             | threads, after a few months they get "archived" and you
             | can't reply any more.
        
               | brazzy wrote:
               | This has changed. I just replied to a 5 year old post of
               | mine to confirm.
        
               | BolexNOLA wrote:
               | A Reddit thread is automatically archived due to
               | inactivity, forgot the exact duration. So in theory as
               | long as somebody is posting a comment on a thread every
               | few weeks (months?) it never archives unless the mods
               | manually do it. The problem with this is that adding
               | comments to a thread does nothing to make it more
               | visible. Traditional forms bump up all threads as long as
               | they have recent activity, which Reddit doesn't do.
               | 
               | The closest solution you could probably find would be for
               | the mods to pin the post to the top, but in my experience
               | most people just ignore pinned posts except in very
               | specific cases.
        
               | teraflop wrote:
               | That's not correct. On Reddit, thread archiving (on
               | subreddits that haven't opted to keep threads open
               | forever) is based on time elapsed since the thread was
               | posted, regardless of how much activity there's been.
               | IIRC the interval is 6 months.
        
               | BolexNOLA wrote:
               | Hmm it appears you're right. What I described used to be
               | the case but they changed it several years ago it looks
               | like.
               | 
               | https://www.reddit.com/r/changelog/comments/25kvjo/reddit
               | _ch...
        
               | ginja wrote:
               | I think it depends on the subreddit. E.g. this is
               | archived: https://old.reddit.com/r/Python/comments/hmoabi
               | /ive_designed...
        
             | xani_ wrote:
             | The thread would disappear from front page after days so
             | new people wouldn't come in and talk about it constantly
        
             | dna_polymerase wrote:
             | Reddit Threads are locked after a while aren't they?
             | 
             | Even if all of this would be in a Reddit thread I'd argue
             | the usability of their site has declined to a point where
             | using it for longer reading is unpleasant. (Login-Wall,
             | collapsed threads, slow JavaScript frontend)
             | 
             | So yeah discoverable yes, but nobody would use it like
             | that.
        
               | brazzy wrote:
               | > Reddit Threads are locked after a while aren't they?
               | 
               | Not anymore.
        
               | wholinator2 wrote:
               | What? I've seen more recent threads getting "archived"
               | (no one can comment or vote) earlier and earlier than
               | ever. It used to be that every thread was guaranteed to
               | stay communicable for at least a year, maybe 2. That was
               | enough for most things but still represented a
               | discontinuity in the transfer of knowledge as a new
               | thread would need to be made and gain traction and votes
               | and rarely (very rarely) the previous thread would be
               | linked to avoid just recycling the same points and never
               | making progress. That exceedingly rare linking now
               | basically never happens and threads get archived as early
               | as 6 months! I assume there's some variation as I believe
               | I may have seen threads that don't get locked so early
               | but it's a significant disruptor on the transfer of
               | knowledge. And with how bad reddit's searching is, unless
               | the previous thread is linked there's a tiny chance
               | you'll ever find it let alone even know it existed.
               | 
               | That format just promotes reposting and restating the
               | exact points that were popular 6 months ago. There have
               | been many times I have had something to contribute to a
               | discussion and have been rebuffed by the "This thread has
               | been archived" popup. Truly any thread more than a year
               | could not survive most current social conglomerates, I
               | understand the scaling issues but it does not make it
               | untrue.
        
               | brazzy wrote:
               | Yeah, independant of the auto-locking (which is
               | apparently opt-out per subreddit), old threads just don't
               | have any visibility to stay alive.
        
       | unixbane wrote:
       | Has anyone hacked furnaces yet? They have giant PCBs in them.
        
         | bombcar wrote:
         | Most furnaces are incredibly amazingly simple and the large PCB
         | is just for reliability and to support the transformers.
         | 
         | Many even now are (blower on/off) and (flame on/off). Only the
         | high end ones have variable blowers and flame heights.
         | 
         | I know this because before ours was replaced I had to jumper
         | past a bunch of the board to keep it running.
        
       | inferense wrote:
       | > Where did you learn to invent stuff like this?
       | 
       | Lots of reading, being willing to try something, welcoming
       | failure as also a learning moment.
        
       | voisin wrote:
       | Is there any way to combine a ground source heat pump with a
       | well?
        
         | bombcar wrote:
         | Some of them are basically multiple bidirectional wells (when
         | installed vertically in a colder climate) so drilling one more
         | for a wellhead is probably possible.
        
           | voisin wrote:
           | I've got wells on my property. Rather than drill more wells,
           | I am wondering if there's something that could be put in the
           | well to utilize the stable water temperature down below to
           | heat exchange? Seems like there would be a big market - lots
           | of people on wells are heating with oil or propane or
           | electricity at massive costs.
        
             | bombcar wrote:
             | It would depend on the well and the "heat availability"
             | (not a technical term) and how deep it was.
             | 
             | I suspect it could work but it'd be marginal enough as not
             | to be worth it compared to straight air heat pump or an
             | actual field (similarity could a heat field and a septic
             | field be installed at the same time ,,,)
        
               | voisin wrote:
               | I understood, perhaps incorrectly, that the ground below
               | the frost line is stable year round and if air source
               | heat pumps work more efficiently down to -10C, we know
               | the water isn't that cold (otherwise it would be ice), so
               | wondering if the efficiency threshold is the same for
               | ground source heat pumps?
        
               | bombcar wrote:
               | That's why the ground ones are dug vertically sometimes,
               | they can get to stable temperatures.
               | 
               | However, a well may be "just poking" into that territory
               | so you get the right temperature, but not enough surface
               | area to do much heating/cooling.
        
         | timbit42 wrote:
         | Absolutely but typically two wells, one to pull water from and
         | one to put the cooled water down. You also need a minimum
         | amount of water flow, depending on the unit and how much heat
         | your home needs.
         | 
         | They're considered better than air-to-air heat pumps which
         | become less efficient as the outside temperature goes down.
         | Ground source units remain efficient in cold weather as the
         | water in the well is below the frost line (only the top few
         | feet of the soil freezes). They cost four or five times more
         | than a typical air-to-air unit though so aren't as common.
        
           | xani_ wrote:
           | And technically also can be used for very efficient AC in
           | summer
        
       | usrusr wrote:
       | Reminds me of a surprising armchair heat macguyvering idea I've
       | had: if for some reason you are stuck with resistive heating, you
       | could use an old fridge as your resistive converter, with the
       | cold end _inside_ (cold end outside would be an actual heat pump,
       | but probably not a good one and very limited in placement, likely
       | losing more to the insulation downgrade from the placement): open
       | the door just enough to get the inside walls below condensation
       | of your current humidity level, collect the condensed water in a
       | way that it doesn 't just evaporate again but can be carried to
       | the sink.
       | 
       | Why? Slightly less air replacement required to fend off mold,
       | slightly more heat created, because the condensation is the
       | inverse of evaporative cooling. Haven't done the math but I think
       | it's safe to assume that the benefits would be tiny, but if, for
       | some reason, you were limited to resistive heating, doing it this
       | way would be slight ly less bad.
        
         | fsh wrote:
         | That's just a very ineffective dehumidifier.
        
         | sgc wrote:
         | Except you usually have a very dry environment when heating due
         | to the lack of moisture in the colder environmental air, and
         | need to add moisture to avoid falling out of healthy humidity
         | levels for human beings.
        
           | usrusr wrote:
           | Dry air is less unhealthy than moldy air.
        
             | sgc wrote:
             | We are talking about large amounts of moisture that need to
             | be added to the air when heating. There is 0 risk of mold
             | in that situation. Ideal humidity: General recommended
             | range: 40-60%; ideal/goldilocks humidity, 50%; mold
             | conducive conditions: 60%+; air when heating: often ~30%.
        
               | usrusr wrote:
               | Perhaps if the house leaks air like a sieve and you just
               | compensate by more heating watts (or if you use some
               | fancy heat recovery ventilation), but in a properly
               | closed shell, with considerable cold outside, your
               | primary problem is getting rid of all the humidity human
               | life produces without the water condensing on whatever
               | surface is coldest. I suspect that we are talking about
               | very different environments.
        
         | Gare wrote:
         | My humidifier uses about 3 liters of water per day for 40m2
         | apartment during winter, to keep the humidity at acceptable
         | 40%. Otherwise it's extremely dry inside.
        
       | JoelMcCracken wrote:
       | This is exactly why I keep coming back to this website
        
       | 0x53 wrote:
       | I have been doing a ton of research on building my own GSHP
       | lately and so this is a great resource!
       | 
       | However, what I have found in the process is that for well
       | insulated homes GSHP probably doesn't make sense.
       | 
       | Originally I was considering buying a kit from this site:
       | https://www.123zeroenergy.com/pricing/geo-thermal.html
       | 
       | But like it says on the page, because air source heat pumps have
       | been getting a lot better they no longer sell the kits. There are
       | a couple of individuals on YouTube who have used similar GSHP
       | kits and had good success. The main challenge is that you need to
       | dig 100ft of deep trenches per ton of cooling. Edit: should be
       | 300ft not 100
        
         | halbritt wrote:
         | > air source heat pumps have been getting a lot better
         | 
         | Mitsubishi, specifically, makes a heat pump with the marketing
         | vernacular, "H2i" or "hyper heat" which has reasonable
         | efficiency down to -13F/-25C.
        
           | hedora wrote:
           | That's not even the best one any more. Some other systems hit
           | -30C.
        
             | genewitch wrote:
             | The part with the compressor in it costs $12000-$15000
             | minimum just for the device, nevermind installation and the
             | rest, and that's for an equivalent to 3-6 ton systems
             | commonly installed.
             | 
             | My mini-split system worked fine down to about 10F, then it
             | was defrosting for 10 minutes after every 8 minutes of use
             | or so. I just turned on crypto miners on a few computers to
             | supplement. Laptop crypto mining is useful if you want to
             | keep your hands and wrists warm, hats, blankets, sweaters,
             | and some old 100+ watt light bulbs will also help.
             | 
             | All this is to say "you can just get a -30 degree capable
             | system" is out of reach for most people in the world. A
             | large swath of people geographically close to my house
             | still use window or wall HVAC units, rather than ducted
             | systems. I was the _only_ split ductless system my HVAC
             | installer had ever installed - they had to come fix their
             | install 4 times (four!) and eventually i contacted the
             | asurion purchase protection people and got refunded for the
             | cost of the HVAC system.
             | 
             | it works fine now, i told the HVAC installer to cut the
             | threaded connectors off everything and sweat all the copper
             | lines together, and it hasn't had an issue since.
             | 
             | it was always breaking in the late fall and early spring,
             | where it had to heat at night but cool during the day, it
             | would always break around 11AM. The pressure differentials
             | must have been an afterthought in the design, i guess.
        
         | cycomanic wrote:
         | We just build a house on the west coast of Sweden and we
         | initially considered both a ground or air heat pump.
         | Essentially our builder said with modern houses and heatpumps
         | going for the ground heat pump was really not worth it. Their
         | efficiency gain only becomes significant at outside
         | temperatures below 10 deg C and there were just not enough days
         | of such low temperature. Instead it is better to invest that
         | money into a solar installation.
        
           | dzhiurgis wrote:
           | Similar in Lithuania, where buildings are required to be
           | certified to A++ efficiency. Electric floor heating and air
           | to air heat pump (aka split system) is enough. Solar panels
           | are much better value. Cooling in summer is kinda becoming
           | much bigger issue.
           | 
           | For older building even replacing wood furnace with air to
           | water system is enough.
        
             | patd wrote:
             | Ground heat pumps provide free cooling in the summer for a
             | very limited amount of electricity as the ground will be at
             | 10-15C (depending on where you live) so you don't need to
             | use the compressor and just make the liquid flow to cool
             | down your house.
             | 
             | It also has the extra benefit of heating up your ground for
             | the winter period.
        
               | cycomanic wrote:
               | While that is in principle true, in practice there are
               | quite a few issues. Many heatpumps here are made to heat
               | the water for floor heating but don't transfer heat to
               | air indoors. So you would cool using your floor which
               | isn't very comfortable usually. More importantly because
               | of the above the heat pumps are build for only one
               | directional transfer. If one builds their own system it
               | might make sense to plan for it, but even then it's
               | unlikely that Sweden will become so hot that opening
               | windows will not cool off the house enough. If it comes
               | so far we likely have more pressing problems.
        
               | vel0city wrote:
               | It would be cool to have a valve to change between a
               | floor heat loop and an air heat exchanger for the inside
               | side of the system.
               | 
               | Of course this makes the system more complicated. More
               | complicated means more chances for failure and higher
               | costs for designing and installing.
        
               | patd wrote:
               | Some do wall heating or ceiling heating instead of floor
               | heating. Wall heating/cooling would probably not require
               | two systems.
        
               | patd wrote:
               | The ground heat pumps are not used in the opposite
               | direction, it doesn't cool down water to the floor but it
               | flows water at 10-15C into your floor. According to the
               | installers I've talked to here in Belgium, all the ground
               | heat pumps devices are capable of doing that.
               | 
               | While this might not be needed in Sweden, it's more
               | interesting further south. I live in Belgium and we had a
               | long heatwave this summer and they predict more of those
               | in the coming years. So cheap efficient cooling might
               | turn out useful here (even if nobody had AC systems 20
               | years ago)
        
           | froh wrote:
           | Goteborg is below 10degC November to March, five months
           | 
           | https://weatherspark.com/y/71566/Average-Weather-
           | in-G%C3%B6t...
           | 
           | in contrast sunshine duration and angle in Winter is frickin
           | low.
           | 
           | sure that guy wasn't trying to sell sth?
        
             | Scoundreller wrote:
             | Ground source is also just a lot more work, and often has a
             | large part of the job contracted out from your average HVAC
             | tech.
        
             | hedora wrote:
             | I assume they made a typo, and meant to write "under 10degC
             | below zero", Modern air source heat pumps are good to
             | -30degC; the old ones were OK to 0degC:
             | 
             | https://www.heatpumps.ca/articles/best-low-temperature-
             | heat-...
        
           | cassepipe wrote:
           | Not to say you were wrong since in making that choice but
           | with climate change days of extreme temperatures in both
           | directions will become ever more common so so you may have
           | considered it an investment into the future. Of course you
           | may have other problems by then (a reliable source of food
           | for example)
        
             | arinlen wrote:
             | > _(...) with climate change days of extreme temperatures
             | in both directions (...)_
             | 
             | This sort of take is unwise. It makes zero sense to invest
             | today in domestic systems with the expectation that at some
             | point in the future there will be extreme events a hand
             | full of times throughout the year. The benefit of shaving a
             | fraction of a percent from the baseline outweighs
             | multipercent gains of hypothetical extreme events that
             | happen a few times a year.
        
               | bombcar wrote:
               | And you can always add supplemental later.
               | 
               | When building spend as much as you can on the building
               | envelope (preventing air, vapor, water movement) and
               | insulation.
               | 
               | Those cannot be easily changed at all, but you can
               | relatively easily add another heating or cooling device.
               | 
               | And if you build above code minimums (you should!) be
               | sure to have someone knowledgeable calculate the actual
               | heating/cooling load. If you don't, the HVAC contractor
               | may assume code minimums and oversize the system.
               | 
               | Or get systems that are entirely variable.
               | 
               | And get every step inspected! Mid build blower door tests
               | are a great thing to do (right after the air seal
               | envelope is up).
        
               | arinlen wrote:
               | > _And you can always add supplemental later._
               | 
               | Great point.
               | 
               | Investments are made based on expected returns on
               | investment, and we're free to postpone them until they
               | make sense.
               | 
               | Spending money hoping to bank on the occurrence of
               | unexpected outcomes simply can't be justified.
        
               | hedora wrote:
               | > _Spending money hoping to bank on the occurrence of
               | unexpected outcomes simply can 't be justified._
               | 
               | I would have agreed a decade ago, but in the one year our
               | house has been standing, it has endured two 100 year
               | events (a heat wave and a rain/windstorm).
               | 
               | We overpaid about $1000 to go one size up on the
               | (variable) heat pump / AC and $10-20k to oversize +
               | harden the solar / battery.
               | 
               | It has been worth every penny at this point; the solar
               | kept the fridge, freezer and AC happy in > 100F heat
               | during a power outage. That's $500-1000 of food just for
               | the one event, and outages are increasing in frequency.
               | (Air conditioning was mostly unheard of in this area 20
               | years ago, since it didn't get hot enough to ever run
               | it.)
               | 
               | My big concern is that we're already eating into the
               | engineeeing tolerances for the wind rating on the house
               | itself.
               | 
               | I do agree that you should consider what can be upgraded
               | later, and put money towards things that are hard to
               | change (insulation, wind ratings, etc.)
        
               | genewitch wrote:
               | the "it doesn't get hot enough to need air conditioning"
               | argument was used to build out tons of apartment
               | complexes in the pacific northwest, say, around Tacoma
               | and Seattle. I lived in Tacoma in the mid-2000s for a
               | summer and it was miserable. And everyone i spoke to
               | about it said "yeah, that's the joke."
        
               | jagged-chisel wrote:
               | The same can be said for most insurance products. Whether
               | it's Worth it is subjective.
        
               | arinlen wrote:
               | > _The same can be said for most insurance products._
               | 
               | That's a terribly silly thing to say. Think about it for
               | a second, particularly how insurance premiums compare to
               | the cost of buying/rebuilding a new item.
        
               | hedora wrote:
               | Marge: I'm sure your insurance will cover the house.
               | 
               | Maude: Uh, well, no. Neddy doesn't believe in insurance.
               | He considers it a form of gambling.
        
           | fest wrote:
           | While I do agree that it was true a year ago, I wonder if it
           | holds true for current electricity prices?
           | 
           | My considerations for going with ground source heat pump
           | were:
           | 
           | * the maximum amount of solar that I could install is enough
           | for ground source heat pump, but is a bit short for air
           | source,
           | 
           | * what if the seasonal electricity prices get so extreme,
           | that the grid can't maintain 1:1 ratio for the net billing
           | system anymore?
           | 
           | * what if the global temperature swings become more extreme?
        
       | ianbooker wrote:
       | To aid the discussion: There are multiple kinds of heat pumps
       | used for homes, mainly air-to-water and water-to-water. Since the
       | post is 12 years old, the availability of air-to-water solutions
       | may be understated. At least in Europe it is now quite common to
       | find them in front of new homes. Placed and looks like an AC
       | unit, sounds like a laptop from 2005.
        
         | nicoburns wrote:
         | > sounds like a laptop from 2005
         | 
         | As someone who's never lived in a house with AC, is that
         | loud(er) or quiet(er) (than an AC unit)
        
           | bombcar wrote:
           | Quieter than a window air conditioner, a bit louder than
           | whole-home I suspect.
        
       | jhallenworld wrote:
       | The US Senate just approved an HFC ban. So which refrigerant
       | should be used in the heat pumps? Can we get HFC-free heat pumps
       | today?
       | 
       | See https://www.danby.com/blog/danbys-commitment-to-
       | remain-100-h...
       | 
       | http://hvacrfundamentals.blogspot.com/2019/06/appliances-wit...
       | 
       | Looks like r600a, iso-butane is already in use.
        
         | AvocadoPanic wrote:
         | r744
        
         | wongarsu wrote:
         | I would assume any refrigerant in use in air conditioning works
         | just fine, based on heat pumps being air conditioners ruining
         | in reverse
        
       | VLM wrote:
       | Does anyone have any financials on this?
       | 
       | I get that if your heart is set on having a heat pump you need a
       | heat pump, and that's the end of all financial consideration.
       | 
       | But how does, say, $10K of heat pump compare to $10K of
       | insulation and better windows/doors/roof, or $10K of solar panels
       | and cheap ultra-low-tech repairable all-electric HVAC, or $10K of
       | some other form of physical investment I'm not aware of?
        
         | hedora wrote:
         | Insulation almost always wins during initial construction.
         | 
         | Solar panels probably come in second because they create waste
         | energy that unlocks free EV charging, etc, etc (but you will
         | pay more than $10K for the system), so, thanks to sunk costs,
         | other stuff becomes "free".
         | 
         | Heat pumps are probably the cheapest big bang for the buck
         | upgrade for existing construction (especially if you have to
         | replace your HVAC anyway). Minisplits are often a big win for
         | retrofits of buildings without central air.
         | 
         | All of these things are dominated by labor costs, and we are in
         | the middle of a labor shortage. You are unlikely to find
         | realistic financials unless you get bids and compare with your
         | personal energy rates.
         | 
         | We didn't do any of that.
         | 
         | We just assumed energy prices would continue to explode over
         | time (we were right), and jumped off the inflation carousel by
         | putting in solar and all electric appliances.
         | 
         | Also, we can't get natural gas service, and propane costs 4x
         | per BTU more than natural gas around here. Most electrical
         | appliance upgrades are subsided by the government to make them
         | competitive with natural gas.
         | 
         | That made it a no brainer.
         | 
         | Since then, a bunch of indoor air pollution research showed
         | that natural gas causes asthma, etc, etc. Also, the war in
         | Ukraine started.
         | 
         | So, what are your health, future financial predictability, and
         | engineering economics braincells worth? For us, the answer was
         | "less than the installation cost of the system".
         | 
         | Also, after all they put us through, seeing a -$120 bill from
         | PG&E each month makes me irrationally unhappy. ;-)
        
         | ajross wrote:
         | A heat pump is 3x more efficient at heating than a resistive
         | electric heater, making it just about a wash with a gas furnace
         | in most markets in terms of sustained cost. The hardware is
         | more expensive, but not THAT much more expensive. When you
         | include installation costs and amortize over a 20 year system
         | life, the overhead is non-zero but quite low (10% or so). If
         | you guess that gas is going to be more expensive in the coming
         | decades where electricity is futureproof, it seems like a good
         | bet to me. Ask me in 20 years.
        
           | xani_ wrote:
           | I wonder how's the failure rate compared to oldchool types of
           | heating. The longest warranty I can find on the market is 10
           | years
        
         | fest wrote:
         | It really depends on your starting point.
         | 
         | If you have a perfectly serviceable means of heating that you
         | are happy with, then it's a straightforward cost analysis (cost
         | of consumables for the current heating method vs cost of
         | electricity for the heat pump).
         | 
         | I can only give an example that applies to my situation:
         | previously I burned ~2300l of diesel which cost around 2300EUR
         | for the previous heating season. So the yearly energy
         | consumption is about 24MWh (combustion heat of fuel multiplied
         | by efficiency of the furnace of ~94%). If I were to install air
         | source heat pump, it would require about 8-9.6MWh (COP =2.5-3)
         | of electricity per year (4000-4800EUR at the current fixed
         | price offering from my electricity supplier of ~500EUR/MWh).
         | 
         | If I were to install a ground source heat pump (COP of
         | 4.5-5.5), expected electricity consumption is between 4.3-5.3
         | MWh or ~2200-2600EUR/yr.
         | 
         | If I were to power the ground source heat pump using the
         | electricity generated by my solar panels (Latvia currently has
         | 1:1 net billing system, but there is a grid cost of ~50EUR/MWh)
         | the expected yearly heating cost is ~210-260EUR.
         | 
         | At the previous electricity cost of ~100EUR/MWh, air source
         | heat pumps for not-so-well insulated houses might be attractive
         | option- but not at the current prices in Europe.
         | 
         | When I did the calculations this spring, the break even time
         | for heat pump + solar installation was ~8 years (based on fuel
         | and electricity costs at that time).
         | 
         | Right now it's around 4 years (and I might even get ~40% of the
         | investment from a government clean energy incentive programme).
         | However, I have to operate under assumption that a crazy
         | dictator of a neighboring country doesn't decide to invade and
         | wipe my house off the Earth...
        
           | Slava_Propanei wrote:
        
       | nqzero wrote:
       | tangent: for a small air-to-air heat pump, what's the best
       | commercially available coefficient of performance (COP) for a
       | zero-delta-T ?
       | 
       | all the common ratings that i've found online refer to COP at a
       | non-zero delta-t over a ranges of conditions. to illustrate my
       | question, if you needed to pump heat from 70degF indoor air to
       | 70degF outdoor air with a 1-ton unit, what would be the best COP
       | you could achieve in 2022 ?
        
       | Roark66 wrote:
       | It is a very interesting thread, but reading 100+ pages of a
       | forum thread to find the details of the project is _hard_.
       | 
       | I would definitely like to read a detailed description of his
       | pump unit.
        
         | VBprogrammer wrote:
         | I've read it before and it's got some cracking info in there.
         | One of my favourite bits was him using propane as a purge gas
         | to get better quality brazed joints, though interestingly he
         | baulks at the idea of using propane as a refrigerant gas!
        
           | bagels wrote:
           | Sounds dangerous.
        
             | implements wrote:
             | It's a standard refrigerant gas for some settings:
             | 
             | https://www.agas.com/uk/products-and-
             | services/refrigerants/r...
        
               | theelous3 wrote:
               | No the brazing sounds dangerous. How does it not ignite??
               | Brazing is done with high heat open flame. Unless it's
               | just for back purging? But that sounds even more
               | dangerous - intentionally building up a propane resivoir
               | behind the braze.
        
               | bluGill wrote:
               | It would only ignite where you already want a flame so
               | who cares?
        
               | bagels wrote:
               | Where is the propane going when used as a purge? If it
               | stays in the pipe, you may create an explosive mixture.
               | If it doesn't stay in the pipe, you might create a
               | fireball in your face.
        
               | sidewndr46 wrote:
               | Propane is not an explosive. Environmental concerns
               | aside, millions of people burn propane each day all over
               | the world relatively safely, explosion isn't really the
               | leading concern.
               | 
               | You may be thinking of acetylene. But that isn't really
               | that dangerous in modern usage either.
        
               | bagels wrote:
               | Propane air mixtures can be explosive in the right
               | measure. Less energetic than acetylene of course.
               | 
               | It doesn't have to explode to burn you though. Where is
               | the purge gas escaping when used this way?
        
               | jonititan wrote:
               | Probably because you need sufficient oxygen for
               | combustion. The propane would only ignite where it comes
               | out and mixes. Once the flame travels into the purged
               | pipe it will probably die out for lack of oxygen.
               | 
               | Ticklish though I'm sure to do it properly and safely.
        
       | cyber_kinetist wrote:
       | Ah, the vive of people on the Internet talking for over a decade
       | on an old phpBB forum thread...
       | 
       | A bit off topic, but I really think the existing forum sites
       | aren't really that incompatible with "younger" people, and might
       | have a renaissance later on (looking at how they are using
       | Discord in a similar manner!) It's just that these old forum
       | sites have lots of UI clunkiness that deter people from browsing
       | or joining the site (older people who kind up grew up with phpBB
       | might be accustomed to these sorts of jank, but you shouldn't
       | expect someone who weren't in that era to be accustomed to it.)
        
         | VBprogrammer wrote:
         | I still use a couple of them for niche interests. The one thing
         | that annoys me is that they still make uploading photos a
         | chore. Usually you have to resize the image your self to get
         | under some pathetic size limit. It's enough that people tend
         | towards text when a picture or a drawing would be much better.
        
           | betwixthewires wrote:
           | When you're a guy running a long lived online community on a
           | $100 a year VPS you avoid storing media as mush as possible.
           | There's a reason photo bucket sites used to be so popular.
        
             | OJFord wrote:
             | Making it not 'a chore' though could mean a nice frontend
             | to upload to some such photobucket site and embed the
             | result.
             | 
             | Then you also avoid the annoying 'you must create an
             | account to view attachments'.
        
               | bombcar wrote:
               | Some of the forums have features to do that on upload -
               | you just have to configure it.
               | 
               | Sadly most of the admins for these type of fora are just
               | learning as they go.
        
       | lifeisstillgood wrote:
       | I understand that in a few years every new build in the UK must
       | have a GSHP (no gas boilers) and the goal is for every house to
       | have something like it.
       | 
       | I think this manifesto is a piece of genius - I think I shall be
       | studying :-)
        
         | Gordonjcp wrote:
         | I wonder if whoever thought that up has ever been to the UK?
        
           | helsinkiandrew wrote:
           | Its a UK government plan so yes, why do you ask?
        
             | Gordonjcp wrote:
             | Well, it doesn't sound like they know much about the
             | geography or geology of the UK, quite frankly.
             | 
             | How is every house builder going to afford a million quid
             | borehole?
        
               | helsinkiandrew wrote:
               | I think the UK is effectively banning gas boilers and its
               | upto the developer/consumer to choose an alternative - a
               | combination of CHP (local heating), GSHP, but most likely
               | air source heat pumps.
        
               | thombat wrote:
               | Ground source boreholes are mostly 10-15 metres deep, so
               | not wildly expensive, especially when part of a new
               | construction. You may be thinking of classic geothermal
               | bores? Drilling down to proper hot-rocks would be a much
               | costlier scheme in most of the UK.
        
               | dzhiurgis wrote:
               | Wonder if you could drill centralised borehole and then
               | use retrofit old gas lines to move compressed
               | refrigerant...
        
               | voisin wrote:
               | > Drilling down to proper hot-rocks would be a much
               | costlier scheme in most of the UK.
               | 
               | Is this something people do?
        
               | bombcar wrote:
               | Big buildings do. They often have to go down that deep
               | for foundation pillars anyway.
        
               | shh_labs wrote:
               | You don't need a borehole at all. Ours uses coils of pipe
               | that are about 1m deep.
        
               | Gordonjcp wrote:
               | So, not really suitable for most of the north-west then.
        
               | dabeeeenster wrote:
               | Almost all heat pumps in the UK being installed these
               | days are air-source.
        
               | Gordonjcp wrote:
               | Those work in hot dry countries. Lots of the UK - in
               | particular the north-west - is neither hot nor dry.
               | 
               | Up here you end up with the outdoor part freezing into a
               | block of ice.
        
               | diordiderot wrote:
               | Canadians have air source heat pumps with backups that
               | get used ~5-10 days a year...
        
               | d110af5ccf wrote:
               | I live in a similar climate and have never once had this
               | problem in the winter. Something is wrong if this is
               | happening to you.
        
               | g8oz wrote:
               | Incorrect. Try a quality brand like Mitsubishi or
               | Thermia.
        
               | [deleted]
        
               | n4r9 wrote:
               | I don't think the original claim is quite right. The UK
               | govt is banning new gas boiler installations after 2025,
               | but I believe there's a range of alternatives such as an
               | air or ground source heat pump, or a hydrogen boiler.
               | 
               | From what I've read through, replacing my boiler with a
               | gshp would cost in the tens of thousands, not a million
               | pounds.
        
               | bombcar wrote:
               | How would a hydrogen boiler work? Hydrogen trucks
               | deliverying? Is the UK piped for hydrogen? Electrolizing
               | water on site?
        
               | karottenreibe wrote:
               | I skimmed the plan and didn't find any requirement to use
               | a ground to water heat pump. Air to water devices are
               | mentioned several times as viable heat pumps for this
               | plan. These do not require boreholes.
        
           | [deleted]
        
         | PartyOperator wrote:
         | GSHPs are rare in the UK and likely to remain so. In practice
         | building regs will require most new homes to have heat pumps
         | but they'll almost all be air-source units. UK winters rarely
         | get very cold (typical minimum design temperatures are above
         | -5C in most of the country) so ASHPs work well all year.
        
           | tomatocracy wrote:
           | Even better would be to build out (in new build housing
           | estates at least) district heating. This is common in quite a
           | few other countries and it should work pretty well in the UK
           | too - it's always seemed odd to me that it isn't more common
           | here.
        
             | OJFord wrote:
             | I used to have it; it's a technically nice system when
             | working, but the problem is having no choice of provider,
             | no control when it goes wrong, etc.
             | 
             | Makes sense for flats (or dense area of many leasehold
             | houses, if that happens) where there's a management company
             | holding your throat anyway, but otherwise I can't see how
             | it works unless perhaps it was provided by the council
             | (similar disadvantages, just more trust/better outcomes
             | from complaints).
        
           | GordonS wrote:
           | Plus, don't GSHPs need quite a lot of land for the piping?
           | Houses in the UK are built on the smallest possible plots of
           | land :(
           | 
           | It's normal for temperatures in Scotland to dip below -5C
           | over winter - do ASHPs not work at those temps?
        
             | fest wrote:
             | For horizontal designs yes- the rule of thumb is the brine
             | coil area should be around 3x the heated area. However, the
             | vertical bores don't need much area, just expensive
             | drilling work.
        
           | lifeisstillgood wrote:
           | I think I can call myself fully corrected. I mistook GSHP for
           | all heat pumps and got confused
        
         | verisimi wrote:
         | I'd love to see the source for this info - do you have a link?
        
           | e2le wrote:
           | https://www.gov.uk/government/publications/heat-and-
           | building...
        
             | verisimi wrote:
             | Thank you!
        
         | baybal2 wrote:
        
         | melonrusk wrote:
         | New UK houses would all be cavity-wall so is there a reason the
         | inside of the exterior wall isn't being used as the source ?
        
       | ArchitectAnon wrote:
       | One note of caution, he describes removing the lath and plaster
       | and inserting eps insulation. It didn't mention if he did this,
       | he might have done, but it's important to have a continuous taped
       | vapour barrier on the warm side of the insulation to prevent
       | water vapour from passing through, condensing on the timber
       | structure and causing it to rot. Also ventilate the cold side of
       | the insulation or a least have a gap to form a capillary break
       | with the cold outside wall. I've seen a few badly done insulation
       | jobs in timber buildings that have needed floor joists and studs
       | cut out and replaced. It only takes about 15-20 years.
        
         | OJFord wrote:
         | Lath & plaster does not form a vapour barrier; deliberately not
         | in most cases (there was perhaps some crossover when more
         | moderm building techniques were still using lath and plaster) -
         | old houses need to 'breathe' as they say, moisture needs to be
         | allowed to move between inside and out. They can be warm & dry,
         | but the way to achieve it is (paradoxically) porous materials.
        
           | ArchitectAnon wrote:
           | Yes of course, but I was thinking more in terms of DIYers
           | jamming a lot of non-breathable eps into old houses. Probably
           | better to say consult someone who knows what they're talking
           | about before you internally insulate your old house.
        
             | bombcar wrote:
             | Yeah insulation that is a vapor barrier shouldn't replace
             | insulation that wasn't without considering the effects.
             | 
             | You can use something like rock wool (in batts or panels)
             | to get insulation that is still vapor permeable and water
             | resistant.
        
         | forgetfreeman wrote:
         | I'm glad someone addressed this as I cringed visibly when I got
         | to this part of the post. I'm very much hoping someone with
         | actual experience with controlling moisture stopped this person
         | before they completed this installation. If not, that house is
         | the residential equivalent of a dead man walking.
        
         | bombcar wrote:
         | Be careful with an impermeable vapor barrier especially if
         | adding one. It may work perfectly for keeping water out of the
         | wall cavity in winter, but become the condensation layer in
         | summer - on the wall side!
         | 
         | You can use smart vapor control layers (such as Intello) to
         | counteract this - but be sure you've discussed how the wall can
         | dry out if it gets wet.
         | 
         | And the worst of all is if you end up with two vapor barriers -
         | one on the inside and one on the outside - you'll end up with a
         | "dirty diaper" effect.
         | 
         | https://www.buildingscience.com/documents/digests/bsd-106-un...
        
           | ArchitectAnon wrote:
           | Good point, in a hot climate with air conditioning,
           | everything works in reverse in summer. My perspective is
           | Northern Europe; consult a local expert.
        
           | Freestyler_3 wrote:
           | What about one way barriers?
        
       | __turbobrew__ wrote:
       | I don't think the underwriter on my house insurance would be
       | happy with me hacking together a bunch of parts to create a
       | bootleg HVAC system.
       | 
       | The project is cool, but if the project caused a water leak or
       | fire you are probably screwed and wont get anything from the
       | house insurance.
        
       | diordiderot wrote:
       | I'm relatively young but this link feels like what hackernews is
       | supposed to be. An ugly forum post of someone hacking something
       | together
        
         | aaron695 wrote:
        
         | naasking wrote:
         | You could try: https://hackaday.com/
        
       | fest wrote:
       | I am currently installing a Thermia Calibra ground source heat
       | pump (installers are apparently too busy).
       | 
       | When I looked at the insides of the pump, the simplicity of
       | construction was surprising- I could readily understand whats
       | going on, as it consisted of off-the shelf parts made by other
       | companies- compressor, circulation pumps, VFD and heat
       | exchangers.
        
         | aivisol wrote:
         | I second to that. Just got same model installed few weeks ago
         | and was having exact same thoughts. However, now I start to
         | think that devil is in the details (as always). And it has ton
         | of details, which probably have cost thousands on people hours
         | to design, test and implement. Most are related to how to make
         | it work with maximum efficiency while consuming as little power
         | as possible, some are safety related, etc etc. And the build
         | quality is outstanding, it works flawlessly so far, no
         | complaints. Despite the steep price, one of the best
         | investments I have made recently.
        
           | fest wrote:
           | Yeah, I have travelled that road too often (hmm, looks
           | simple, I bet I can make it for half the cost- and a year
           | later I have spent way more even disregarding the cost of my
           | time and still only have a barely working thing) to know how
           | that would turn out :)
        
             | aivisol wrote:
             | I'm still catching myself doing that sometimes :)
        
               | fest wrote:
               | "That's OK, I learned a ton while doing this" :)
        
       | Nition wrote:
       | This is a wonderful thread, thanks for sharing it here.
       | 
       | > "The kicker is, that the smallest I have been able to find is
       | four ton (48,000 BTU/hr). So this means that in order to proceed
       | with the project, I'll have to build my own heat pump. In HVAC,
       | bigger is not better... just slightly smaller than big enough is
       | best, economically speaking."
       | 
       | Is he saying here that a heat pump that's too large for a space
       | is less efficient at heating, or is he just saying that a bigger
       | one costs more to buy?
       | 
       | If it's the former, can anyone here tell me why that is? It's
       | hard to Google since it gets mixed up with other info like "heat
       | pumps are less efficient at very low temperatures" etc.
       | 
       | I would have thought they'd end up the same. The only reason I
       | can think of is that a bigger one will maybe turn on and off more
       | often to maintain temperature than a small one that's on all the
       | time struggling to keep up.
       | 
       | Edit: Thanks all for the excellent responses.
        
         | moepstar wrote:
         | Not sure what the right terminology is, however, it's due to it
         | turning off, on, off, on again and again...
         | 
         | When it is slightly undersized, it'll run continously and also
         | prolonging compressor life...
         | 
         | Compare this to being able to drive continously at the same
         | speed vs. having to stop/start every 500m or so...
        
           | genewitch wrote:
           | duty cycle, i think.
        
         | zeckalpha wrote:
         | GSHP don't have as much issue with low temps as the below
         | ground temp is fairly stable year round.
        
           | fest wrote:
           | Brine temperature varies over the heating season by up to 10
           | deg C.
           | 
           | I really tried to verify the horizontal coil length and
           | installation depth recommended by installers from the first
           | principles, but I had to give up, as there were just too many
           | unknown inputs: the type of soil (thus, specific heat and
           | heat conduction), water content (which varies over the year),
           | received solar energy (shady/sunny).
        
         | boulos wrote:
         | The term of art is "short cycle". There's also the related
         | "turndown ratio" which is just minimum_output/maximum_output.
         | The discussion at [1] isn't bad, but [2] has a little diagram
         | showing the cycling (in this case as a benefit of variable-rate
         | inverters, but also as a warning).
         | 
         | [1] https://www.greenbuildingadvisor.com/question/what-is-
         | minisp...
         | 
         | [2] https://carbonswitch.com/heat-pump-sizing-guide/
        
         | ArchitectAnon wrote:
         | I think it takes a while for the juices to equalise and reach
         | equilibrium before it's running at max efficiency. You don't
         | want a duty cycle of say 15mins. You want say 1.5hrs. Something
         | like that. (Numbers very hand wavy this is not my field
         | directly) With an over designed system it stops and starts too
         | quickly and this invalidates the warranty on commercial
         | systems.
        
           | lazide wrote:
           | It also makes the environment itself uncomfortable in many
           | cases - excessively drying the air, or causing weird
           | moisture/condensation issues (as it won't fully cycle the air
           | in the house before stopping).
           | 
           | Essentially, you want your HVAC system to run for long enough
           | it's a gradual transition in temperatures inside and the
           | equipment can run for awhile each time it needs to run to
           | avoid the start/stop problems and let it 'settle in'.
        
           | fest wrote:
           | Modern heat pumps drive the VFD and circulation pumps as
           | needed (i.e. the pumps run slower when the heat demand is
           | low).
           | 
           | The main factor for good efficiency is low output
           | temperature- underfloor heating works at ~35 deg C, radiators
           | work at ~55 degC (because of smaller surface area).
           | 
           | I sized my heat pump based on historical data of heating oil
           | /diesel consumption- since I had the data of past two
           | winters, I could reliably determine the maximum continuous
           | heat requirements for my house.
        
         | rickboyce wrote:
         | I agree it's hard to find reliable information in this - ASHPs
         | and GSHPs are very hyped right now so a lot of the information
         | that comes up in searches is quite low level or low quality.
         | For example I've been told that a heat pump is at peak
         | efficiency when it is sized for a duty cycle of 50% but asking
         | why exactly this figure hasn't yielded good answers.
         | 
         | As I understand it, it comes down to a couple of things.
         | 
         | Heat pumps are much more efficient when providing lower
         | temperature flows, their efficiency drops off significantly
         | where the delta between the heat source (air or ground) and
         | their flow temperate is higher.
         | 
         | When an oversized heat pump cycles it is going to quickly reach
         | a higher temperate and shut off where as a correctly sized unit
         | will cycle for longer. So I guess simply it comes down to
         | having the heat pump operate in the most efficient range for
         | that property for longer vs. short spikes at temperature where
         | it is less efficient.
         | 
         | Most heat pumps have a variable speed motors so they can
         | modulate their output to match a desired flow temperature but
         | this only operates within a range relative to the size of the
         | unit. So if the unit isn't correctly sized for the required
         | heat output to be in its range then it has no choice but to
         | cycle inefficiently.
         | 
         | A couple of sources I found helpful:
         | 
         | https://assets.publishing.service.gov.uk/government/uploads/...
         | 
         | Most of the consumer advice is very low level - this Heat Geeks
         | site seems better that most, but it still lacks enough detail
         | for me to get into the numbers:
         | https://www.heatgeek.com/3-steps-to-maximise-your-heat-pump-...
        
           | d110af5ccf wrote:
           | I don't think it's the temperature delta in this case, at
           | least not between the room and outside. I suspect internal
           | equilibration of the unit when power cycled and also energy
           | transfer design capacity on the indoor side of the unit are
           | to blame.
           | 
           | > Most of the consumer advice is very low level - this Heat
           | Geeks site seems better that most, but it still lacks enough
           | detail for me to get into the numbers
           | 
           | You'll probably want an undergraduate physical chemistry
           | textbook for this.
        
           | Nition wrote:
           | Thanks. Yeah, especially difficult when you read multiple
           | different claims and none have a source. They probably heard
           | it themselves from someone else.
           | 
           | I'm quite curious because I _have_ an old-ish heat pump that
           | 's a little small for the space and I've been thinking of
           | getting a larger one. But if it'll be less efficient then
           | maybe I won't. The one I have does perfectly fine except on a
           | few of the coldest winter mornings.
        
             | TheSpiceIsLife wrote:
             | My 7kw unit can only possibly draw 900ish watt.
             | 
             | 800 watt for the refrigerant pump, and about 100 watt
             | combined for the two fans.
             | 
             | This means even when I'd like it a little warmer on the
             | coldest days, making the heat pump use more power isn't an
             | option.
             | 
             | A larger unit would have a bigger refrigerant pump and
             | larger fans. This would result in us inadvertently leaving
             | the unit on a higher heat setting more often.
             | 
             | Also, a larger unit will be turning a larger pump and
             | larger fans even when smaller would achieve the same
             | outcomes. Mechanic losses.
             | 
             | These two factors, human habit & mechanical losses, are, as
             | I understand it, why you're generally better off having
             | more small systems than one big system.
             | 
             | We have three split systems, in addition to the 7kW unit at
             | one end of the house, there are two 2.4kW units, one I'm
             | each of the bedrooms we use. When one or more units aren't
             | required they can be turned off. Another advantage of this
             | setup is that it's extremely unlikely all three systems
             | will breakdown simultaneously.
             | 
             | Another issue with the larger units is they tend to be
             | ducted, where the ducting is in a poorly insulated roof
             | space, so there's additional heat losses there, and
             | additional losses due to energy required to push air
             | through the ducts.
        
               | IgorPartola wrote:
               | Your first point is a bit silly: get a smart thermostat
               | and it'll take care of that for you.
               | 
               | Your second argument is silly: a larger pump will surely
               | take more energy to run but will run for less time. It'll
               | also wear out slower as it doesn't have to work as hard
               | unless you have drafts and it has to cycle on and off all
               | the time. Generally having more capacity is always a good
               | thing for mechanical things.
        
               | emj wrote:
               | It is explained like this in the thread.
               | 
               | > if you have a large compressor, you pay more for it
               | with every revolution the trick is to figure the maximum
               | BTUs or watts you will need, and design a little bit
               | smaller. Plan to use a supplimental energy source to fill
               | in during extreme conditions.
               | 
               | Worth noting the AC_Hacker paid $25 for the AC he used
               | for this.
        
               | taneq wrote:
               | Are you sure? Every ~7kW unit I've seen pulls about 2.6kW
               | electrical.
               | 
               | Agree that multiple smaller split systems is the way to
               | go though.
        
       | omgwtfbyobbq wrote:
       | Ecorenovator's great. Ecomodder has some pretty good stuff too.
        
       | namuol wrote:
       | I've heard that air source heat pumps can be very effective too,
       | and far simpler to install. I wonder if there's any discussion
       | about converting ordinary AC units into reversible units, which
       | supposedly is basically all an air source heat pump is.
        
         | ajross wrote:
         | Exterior heat pumps used in humid or below-freezing
         | environments need some kind of defrost mechanism, just like a
         | refrigerator. Otherwise your coils end up clogged with ice and
         | the system stops working. The compression cycle is indeed
         | symmetric, but the second order design constraints are quite
         | different.
        
           | theluketaylor wrote:
           | Modern setups are really good about managing frost buildup
           | and can be more efficient than resistive heat down to -20C.
           | Waste heat from the compressor is often used for the defrost.
        
       | haunter wrote:
       | I have zero knowledge about the topic but I wonder how NA
       | specific is this thing? As far as I'm aware houses built with
       | thin wood walls are more prevalent there, like in the original
       | example. I live in a similar aged house (maybe a bit older) in
       | Europe but we have 1 meter thick stone walls. We don't have AC or
       | ceiling fan but house always keeps cold in the summer and warm in
       | the winter. I like the topic but curious how would that work with
       | stone wall houses, especially like my example old style ones with
       | thick walls
        
         | bagels wrote:
         | One meter! Those are quite thick walls. Is it solid?
        
           | haunter wrote:
           | Yes of course. There is an outside insulation layer applied
           | some years ago but otherwise it is as built in the 19th
           | century
        
           | phinnaeus wrote:
           | Indeed, that seems absolutely insane. Like a castle that
           | would need to survive some sort of siege. Land is expensive
           | where I am and I cannot imagine wasting that much on such
           | insanely thick walls.
           | 
           | I want a picture. Walking through the front door must feel
           | like going through a tunnel.
        
             | ComodoHacker wrote:
             | It's not insane. I currently live in a house where some
             | older rooms have 0.9 meter adobe brick walls. These were
             | built in mid-XX century, when this was normal. Now we have
             | better materials and don't need that much width.
        
             | xani_ wrote:
             | My family house was expanded so it had a thick wall like
             | that between kitchen and the new part of the house. It was
             | so thick it barely got wifi thru
        
             | bombcar wrote:
             | I've seen some that are basically build as two concrete
             | block or brick walls, and the center are was filled with
             | rubble stone and dirt.
             | 
             | This is similar to an "earth house" and is very comfortable
             | where the average (or basement) temperature is comfortable.
             | The walls make an insane amount of thermal mass and the
             | temperature inside changes very slowly.
        
         | dzhiurgis wrote:
         | When you are building your most expensive purchase of lifetime
         | everyone needs to pragmatic and cheap. Each area have their own
         | climate, cost of materials, cost of labour, building code
         | (safety, efficiency, style) and tradition.
         | 
         | Europe spans 40 degrees of latitude - not listing yours is
         | dishonest.
        
         | mijamo wrote:
         | Stone walls are terrible for heat insolation. They have inertia
         | but no insolation. So they are good in the Mediterranean coast
         | where you want inertia in summer as some sort of natural
         | climate control to keep it cool during the day. But they are
         | terrible in winter when what you want is insolation to keep the
         | heat in during months. A 1m stone wall doesn't even insolate as
         | good than 5cm of dedicated insolation panels. It happens very
         | frequently now that old houses are renovated by adding
         | insolation to those old stone walls, but of course you lose the
         | charm of stone on one side of the wall. This is why you have
         | basically no stone houses in Scandinavia, because in winter it
         | would just be impossible to heat.
        
           | nawitus wrote:
           | Stone houses (in the modern times they're made from concrete
           | or brick, sometimes with insulation) exist in Scandinavia and
           | they have good insulating properties. A modern stone house is
           | even better than stick built houses when it comes to
           | insulation.
        
       | astrostl wrote:
       | I know two major things about heat pumps:
       | 
       | 1) their owners insist they are the greatest thing ever and
       | 
       | 2) nobody in the midwest seems to sell them (at any price)
       | 
       | I don't quite know how to reconcile those two things.
        
         | timbit42 wrote:
         | They are great if you are looking to use electricity to heat
         | because they are 3 to 4 times more efficient than resistive
         | heaters. It depends on the price of electricity and other heat
         | sources in your area.
         | 
         | If you live in the north where temperatures go below -15
         | Celsius, air-to-air units aren't as great because they lose
         | efficiency as it gets colder outside. My heat pump has a COP of
         | 3, meaning it can generate as much heat as a resistive heater
         | using 1/3 the electricity, but it shuts off at -15 Celsius
         | because below that point it is less efficient than resistive
         | heat. If your heat pump has a COP of 4, you might get to -25
         | Celsius before it is less efficient than a resistive heater.
         | 
         | Better, but more costly, heat pumps use in-ground water, either
         | from a pair of wells, or from a deep pond that won't freeze to
         | the bottom, or from many meters of water pipe buried deep
         | enough beneath your lawn to not freeze in the winter. Because
         | of the depth, they always have access to the earth's heat so
         | they don't lose efficiency in the winter.
         | 
         | The Technology Connections YT channel has a couple of good
         | videos about how them:
         | 
         | 1. https://www.youtube.com/watch?v=7J52mDjZzto
         | 
         | 2. https://www.youtube.com/watch?v=7zrx-b2sLUs
        
       ___________________________________________________________________
       (page generated 2022-09-24 23:01 UTC)