[HN Gopher] Continental Europe successfully synced with Ukraine ...
       ___________________________________________________________________
        
       Continental Europe successfully synced with Ukraine and Moldova
       power systems
        
       Author : _Microft
       Score  : 174 points
       Date   : 2022-03-16 13:36 UTC (9 hours ago)
        
 (HTM) web link (www.entsoe.eu)
 (TXT) w3m dump (www.entsoe.eu)
        
       | ISL wrote:
       | _" and the adoption of risks mitigation measures."_
       | 
       | i.e. We really need this yesterday. Stand back, let's see if it
       | works.
        
       | tpmx wrote:
       | Background article from a week ago:
       | 
       | https://www.wired.com/story/the-race-to-rescue-ukraines-powe...
       | 
       |  _The Race to Rescue Ukraine's Power Grid From Russia_
       | 
       |  _In late February, Ukraine began a long-planned 72-hour test to
       | unhook its electricity grid from Russia's. Then the invasion
       | started._
        
         | liketochill wrote:
         | Much better article. It says they have a 2000 MW transmission
         | line between Ukraine and Europe.
        
           | Hnrobert42 wrote:
           | I know almost nothing about this, so this is a genuine
           | question. Why do you say 2000 MW instead of 2 GW? Convention?
           | Is 2 GW incorrect?
        
             | GauntletWizard wrote:
             | They're equivalent. Neither is more correct. Megawatts are
             | a bit more understandable to the layperson, for the same
             | reason that "a million dollars" is more understandable than
             | "a billion dollars". A megawatt is about 1000 homes[1]. A
             | gigawatt is a city.
             | 
             | [1]https://www.eia.gov/tools/faqs/faq.php?id=97&t=3 A US
             | Household uses slightly more than a kilowatt on average,
             | though obviously peaks and troughs are well off that.
        
       | mantas wrote:
       | Looking forward to switching Latvia/Lithuania/Estonia from BRELL.
        
         | aivisol wrote:
         | This is long overdue. As well as unhooking from Russian gas.
        
           | mantas wrote:
           | Lithuania is already unhooked from Russian gas. LNG terminal
           | in Lithuania can supply enough gas for all 3 Baltic states
           | and there's a massive gas storage in Latvia. All 3 gas grids
           | are well interconnected as well.
           | 
           | Russian gas through pipe were cheaper than fully loading LNG
           | terminal though.
        
         | Hnrobert42 wrote:
         | I am curious. What effects will that have?
        
           | mantas wrote:
           | So far Baltics' grids frequency is stabilised by Russian
           | massive hydro plants. Technically Moscow can bring down
           | Baltics grids if they want to and try to hard enough. Baltics
           | could try to disconnect, but there's not enough stable power
           | generation to keep frequency stable permanently. Big part of
           | electricity is imported from Scandinavian hydros and they
           | can't be utilised for stabilising the frequency.
           | 
           | Another side effect - that means Kaliningrad would be
           | unhooked from Russian mainland grid. They already have enough
           | power generation on-site to keep the lights on, but I'm not
           | sure if they have the means to stabilise frequency and enough
           | redundancy if something bad happens. On top of that,
           | political question comes up if it would become it's own tiny
           | grid or become synchronised with continental europe grid too.
           | Major Russian navy base attached to NATO-controlled grid may
           | not sound cool for Russians :)
        
           | kolinko wrote:
           | Independence from Russia, ability to import/export
           | electricity from/tu EU
        
             | mantas wrote:
             | There're import/export links to Sweden, Poland and Finland
             | already. But they're connected through a converter rather
             | than directly.
        
         | pilsetnieks wrote:
         | Scheduled for 2025 but I do hope it gets accelerated.
        
           | mantas wrote:
           | It was already delayed several times because of EU fears of
           | Kaliningrad and Russia response. Hopefully now our
           | politicians have enough arguments to make it happen.
           | 
           | While at it, it may be good to stop the special permit for
           | visa-free train from Russian mainland to Kaliningrad.
        
             | earleybird wrote:
             | It might be a tactical distraction that is needed at this
             | point in time.
        
               | mantas wrote:
               | Military traffic is out of scope, so it'd be similar
               | inconvenience as air space closure. But every tiny bit
               | helps.
        
       | spywaregorilla wrote:
       | How secure is this? Is it actively supporting Kyiv? Eastern
       | Ukraine?
        
       | flavius29663 wrote:
       | This seems like a huge engineering challenge, imagine
       | synchronizing 40 million customers at 50 Hz
        
         | WJW wrote:
         | All those 40 million customers are already on a 50 Hz grid,
         | it's just that the phase of the Ukrainian grid might be
         | slightly different from the European grid. You can (with the
         | correct know-how, training and access to generator controls!)
         | fairly easily get one of the two to speed up or slow down by
         | 0.1 Hz or something like that, wait until the grids match phase
         | and then bring the frequencies back together. Now that they are
         | the same frequency and phase, you can connect the networks just
         | by flipping a switch and provided they were both in balance
         | before the procedure no current will flow initially. Afterwards
         | the two separate networks have effectively merged into one
         | bigger network.
         | 
         | It seems very complicated, but bringing generators and subgrids
         | into sync is something that network operators do all day long.
         | (Ship engineers too, since they can't rely on shore power for
         | obvious reasons! You can have some very "interesting" outages
         | if you forget to synchronize a newly started generator before
         | connecting to the rest of the ship electricity system.)
        
           | Knemejic wrote:
           | Is this actually how it is done? I would assume that the
           | complete ENTSO-E grid cannot be perfectly phase-synchronous
           | anyway, simply due to the physical dimension of the grid and
           | the speed of light.
           | 
           | I would have guessed that frequency-synchronicity is
           | sufficient for coupling two grids, and then you could use
           | something like a phase shifting transformer to control the
           | power flow?
        
             | 323 wrote:
             | Some country interconnections, in particular those to UK
             | and Nordic countries, have the ability to connect even
             | unmatched phases, by for example converting to and from DC
             | (AC -> DC -> AC).
        
               | lxgr wrote:
               | Austria and the Czech Republic (Czechoslovakia at the
               | time) used to have one of these too:
               | https://en.wikipedia.org/wiki/GK_D%C3%BCrnrohr
        
               | sebazzz wrote:
               | That ability to connect unmatched phases is secondary to
               | the primary function of those interconnects: over those
               | distances it is more efficient to transmit the power in
               | DC instead of AC. [0]
               | 
               | [0]: https://en.wikipedia.org/wiki/High-
               | voltage_direct_current#Ad...
        
               | jamincan wrote:
               | Sometimes connecting unsynchronized grids is the primary
               | reason. The Outaouais HVDC Intertie is only about 35km
               | long, but it allows the import and export of electricity
               | between Ontario and Quebec.
        
               | aerostable_slug wrote:
               | This was how the Tres Amigas Superstation was supposed to
               | work.
               | 
               | Unfortunately, ERCOT decided they didn't want to be
               | subject to the same regulations as the Eastern and
               | Western interconnects, so the project collapsed.
        
               | martin8412 wrote:
               | Even more fun is that Denmark despite its' very tiny size
               | is split in two when it comes to electricity. West
               | Denmark is connected with East Denmark through HVDC.
        
             | WJW wrote:
             | As far as I'm aware this is how grid operations are done in
             | the overwhelming majority of the world. You spin a
             | generator up to speed, match phases and close the switch to
             | connect it to the rest of the network. Due to how
             | electricity works, if any connected generator is slightly
             | out of phase with the rest that will generate currents
             | causing it to pulled back into phase in a closed feedback
             | loop. So while it is technically possible for a generator
             | to be out of phase with the network, it can never be
             | outside of phase for very long because literally all the
             | other generators on the network are pulling it back into
             | phase.
             | 
             | If the grids are particularly far from each other and/or
             | with differing frequencies, a DC high voltage line can be
             | used instead but that is certainly not the most used
             | method.
        
             | ars wrote:
             | I looked into this once, and they .... just don't worry
             | about it.
             | 
             | Each generator just matches whatever it sees. If you are
             | trying to match two other generators (like in a triangle,
             | and due to the speed of light it's impossible for all to be
             | perfectly in sync), then it matches to an average of the
             | two, and apparently that works.
        
             | numpad0 wrote:
             | Sounds like needs to be consistent within each subgraphs of
             | grids and synchronous at connection points
        
             | Armisael16 wrote:
             | You only need to match phase at the connection point, so
             | the phase of the grid in France doesn't really matter (as
             | long as ENTSO-E isn't destroying itself before you do
             | anything).
             | 
             | This does get much trickier if you have multiple connection
             | points and it is impossible to be synchronized at all of
             | them because the in-grid distance between the two points is
             | different on the two grids. Then you definitely do need
             | fancier tricks.
        
               | tremon wrote:
               | True, but you need to have a very large unbalanced grid
               | for that to occur: at the grid frequency (50 Hz), the
               | corresponding wavelength is 6000 kilometer. So assuming
               | that math is correct, you would need a path length
               | difference of 3000km between two transformers to get full
               | phase inversion between the paths.
               | 
               | That's more than twice the max diameter of the entire
               | European grid (Tunesia-Gibraltar-Turkey seems the longest
               | path). So as long as there's transformers every few
               | hundred kilometer, and multiple paths between most of the
               | connection points, the overall phase synchronization
               | should be adequate to not need those fancier tricks.
        
           | [deleted]
        
           | bckr wrote:
           | This sounds beautiful, like producing music where your
           | instruments are an entire continent's electrical grid.
        
             | aerostable_slug wrote:
             | Until you find your inner Hendrix and produce positive
             | feedback on transmission lines.
        
           | flavius29663 wrote:
           | I knew they were also on 50Hz, I was just thinking that if
           | they are on a different phase it could blow up or something.
           | But now that you mention some details, it doesn't seem that
           | big of a deal anymore, thanks! What happens if they were to
           | connect them while on opposite phases?
        
             | WJW wrote:
             | Well, if the generators and/or motors of each grid are not
             | in phase with each other then connecting the networks
             | together will cause electricity to flow in such a way that
             | the phase difference disappears. This will speed up the
             | generators that are "behind" and slow down the ones that
             | are "ahead" in terms of the weighted average phase. How big
             | this braking or accelerating force is depends on how much
             | electricity can flow and how "big" the networks are in
             | terms of the total rotational inertia of all connected
             | devices.
             | 
             | I once was on a ship where the engineering dept unadvisedly
             | connected a ~1.5 MW diesel generator to the network when it
             | was out of phase and that shook the entire 6000 ton ship.
             | We later calculated that the whole multi-ton rotor had
             | rotated about 60 extra degrees in under a tenth of a second
             | (in addition to already spinning at 50 Hz), so you can
             | imagine the forces involved with that.
             | 
             | In practice, there will be humongous circuit breakers that
             | trip to protect the equipment.
        
               | flavius29663 wrote:
               | So the result is either really bad...or worse than that:
               | 
               | - if the circuit breakers kick in, you might end up with
               | a huge nationwide blackout. Pretty hard to recover from
               | that - but at least you will recover directly in the new
               | grid.
               | 
               | - if they don't kick in, you get all the generators in
               | Ukraine + Moldova struggling immensely, possibly breaking
               | their encasings/bearings, a little less for Europe, since
               | they would have more mass to resist this spike.
        
         | liketochill wrote:
         | You only need to adjust one generator to change the frequency,
         | since Ukraine grid is in balance simply adding or removing
         | additional power will alter the frequency.
         | 
         | Controlling the voltage at the point of synchronization is
         | probably done with tap changers on transformers but would be
         | more complicated to ensure that power flows over the
         | transmission line once it is connected are as desired.
        
         | reincarnate0x14 wrote:
         | It's not as huge as all that, most of Europe is already
         | similarly synchronized and Ukrenergo was already running at 50
         | Hz. The longer term concern is communication and coordination
         | between the RTOs in Europe and Ukraine, as Ukraine must now
         | respond to grid conditions and act to maintain as spelled out
         | by complex and detailed operating procedures.
         | 
         | Actually syncing up is more of a case of putting in some high
         | resolution meters at the interconnect substation, or maybe some
         | phase shifting transformers, and adjusting the Ukrainian side's
         | frequency by a few micro-hertz an hour until the phase angles
         | are close enough by setting frequency targets at the largest
         | generators. Something similar happens all the time in wide area
         | grids when generators are brought back on line.
        
       ___________________________________________________________________