[HN Gopher] Cooling system leak led to Victorian Big Battery fire
       ___________________________________________________________________
        
       Cooling system leak led to Victorian Big Battery fire
        
       Author : bjowen
       Score  : 107 points
       Date   : 2021-09-28 10:06 UTC (12 hours ago)
        
 (HTM) web link (esv.vic.gov.au)
 (TXT) w3m dump (esv.vic.gov.au)
        
       | william2021 wrote:
       | Short circuit that led to a fire in an electronic component
        
       | bserge wrote:
       | Should've used metal flanges instead of plastic heh
        
       | spockz wrote:
       | > There were further contributory factors with the Megapack in
       | question being switched into an off-line service mode, resulting
       | in the protection systems being inactive.
       | 
       | A short in an offline device? That seems weird.
       | 
       | > A 24-hour delay in connecting the batteries to the supervisory
       | control and data acquisition (SCADA) system also meant there was
       | no active monitoring of the Megapack alarms.
       | 
       | So a new pack was installed and connected but not monitored? What
       | is the rationale behind that? Failures shouldn't happen to new
       | devices?
        
         | michaelt wrote:
         | _> So a new pack was installed and connected but not monitored?
         | What is the rationale behind that?_
         | 
         | Any time a house is built, there's some time between the
         | ceiling going up and the fire alarm installation being
         | completed.
         | 
         | Nothing wrong with that - if it's done properly and carefully.
        
         | jlg23 wrote:
         | Department #1 does the hardware setup, signs off their forms
         | and the next day department #2 integrates the new hardware into
         | monitoring?
        
       | tomalpha wrote:
       | An extract from the summary page suggests a few things went
       | wrong, but it seems like the fire was caused by liquid and
       | electricity mixing:
       | 
       | > ESV found a Megapack cooling system leak caused a short circuit
       | resulting in overheating that led to a fire in a nearby battery
       | compartment, which consequently damaged two Megapacks.
       | 
       | > There were further contributory factors with the Megapack in
       | question being switched into an off-line service mode, resulting
       | in the protection systems being inactive.
       | 
       | > A 24-hour delay in connecting the batteries to the supervisory
       | control and data acquisition (SCADA) system also meant there was
       | no active monitoring of the Megapack alarms.
        
         | [deleted]
        
         | sitkack wrote:
         | I would assume that each megapack would have zigbee for
         | telemetry which should be always transmitting, even if the pack
         | were in the off state.
         | 
         | And the cooling system should be continuously monitored for
         | faults. Not just inspected after filling.
        
           | WJW wrote:
           | That it's hardware instead of software doesn't mean it can't
           | be hacked together.
        
             | sitkack wrote:
             | Thermals are the number one aspect of battery engineering.
             | For something that is to run under load in the Victorian
             | heat, even more so.
             | 
             | This isn't some weekend hackathon contest, Tesla is
             | supposed to have the worlds best engineering.
             | 
             | https://en.wikipedia.org/wiki/Tesla_Megapack
        
               | WJW wrote:
               | Why would Tesla have the "worlds best" engineering? I
               | don't think I have ever seen anyone ever claim that
               | except for perhaps Tesla PR representatives. How would
               | you even measure "best" in such a field? Cheapest? Best
               | quality? Best value-for-money? Safest? Highest power
               | density?
        
           | aaron695 wrote:
           | There are 212 megapacks.
           | 
           | I would imagine this would be really fucking hard.
           | 
           | Most larger, more expensive engineering units don't have
           | this.
           | 
           | I'm open to the idea, if it exists or there are similar
           | setups then that would show it's possible.
           | 
           | Else I'd guess this is like creating Facebook in a weekend.
           | Easy to say. Regulations, security, false positives, unique
           | software.
        
         | smcleod wrote:
         | > "no active monitoring"
         | 
         | What the actual... how is something like this even allowed to
         | be operational without monitoring?
        
           | krisoft wrote:
           | It wasn't operational, it was being comissioned.
           | 
           | You folks are acting as if some huge crime against humanity
           | happened here. In reality nobody got hurt, the company who
           | messed up will pay to put it right. They already indicated
           | (in the linked report) that they learned from the incident
           | and changed multiple things in their systems and procedures
           | as a result.
        
             | wolrah wrote:
             | > It wasn't operational, it was being comissioned.
             | 
             | You're telling me that you don't see a problem with the
             | idea of starting up a bleeding edge system intended to
             | store incredible amounts of energy without the monitoring
             | systems connected?
             | 
             | In general if you don't have a way to monitor an
             | industrial-scale system you go in to your fail-safe state.
        
               | krisoft wrote:
               | > intended to store incredible amounts of energy
               | 
               | Each of these Megapacks can contain 1.5% of the energy
               | contained in a petrol station. :) Let's not get ahead of
               | ourselves, these are realy nice and big batteries. That
               | being said the energies stored in them are far from
               | incredible.
               | 
               | These boxes were by all accounts manufactured in Nevada.
               | They have been moved all the way to Victoria, lowered to
               | the ground and hooked to the site's wiring. They were not
               | "charged" yet. The next step as part of the comissioning
               | was to hook them up to the monitoring system before they
               | are checked out.
               | 
               | No matter when you hook them up to be monitored there is
               | a step just before it when they are not monitored yet.
               | 
               | > In general if you don't have a way to monitor an
               | industrial-scale system you go in to your fail-safe
               | state.
               | 
               | That is indeed a great idea. And if you read the report
               | you can see that after they hooked up each box they put
               | them manually into "maintenance" mode. This mode de-
               | energises all systems in the box. It totaly makes sense
               | that they thought this procedure is the correct one to
               | reach the fail-safe state you mention. Turns out they
               | were wrong. They learned this now and changed their
               | procedures.
        
             | nomercy400 wrote:
             | This. Lessons learned, improvements implemented.
        
             | throwaway0a5e wrote:
             | Nobody ever got internet virtue points by keeping their
             | cool. You gotta be Outraged(TM).
        
             | smcleod wrote:
             | It's a live (active) power source even if it's being
             | commissioned. I don't think it's a crime against humanity
             | but it sure created pollution and waste.
        
         | londons_explore wrote:
         | I am very surprised in this conclusion... Normally if you have
         | two high voltage wires being immersed in water, a large current
         | flows, vaporising the water, and then the current stops when
         | all the water has been evaporated.
         | 
         | For the current to flow for long enough to heat the battery
         | packs to cause a fire, there must have been a jet of water
         | flowing for a long period of time. And no fusible links between
         | that place and the battery.
         | 
         | It really seems like either very bad luck, or bad system
         | design, or both.
        
           | mannykannot wrote:
           | The article puts it this way: "ESV found a Megapack cooling
           | system leak caused a short circuit resulting in overheating
           | that led to a fire in a nearby battery compartment." Nothing
           | here implies that the damaging heat generation occurred at
           | the location of the short circuit. It could have been at any
           | point in the new current path created by the short circuit,
           | depending on its resistance and the share of the overload
           | current it carried.
        
           | michaelt wrote:
           | A cooling system for something that's on fire sounds like
           | exactly where there _should_ be a jet of water flowing for a
           | long period of time :)
        
           | algo_trader wrote:
           | Off topic: can we do a floating (mega-)mega-pack, and use
           | passive water cooling? This should help costs, efficiency AND
           | prolong life time
           | 
           | Of course issues with sweet vs salt water
        
             | londons_explore wrote:
             | Sure you can do it, but it won't be reliable or cost
             | effective.
             | 
             | Passive water cooling in natural water tends to lead to
             | seaweed and all kinds of sea creatures blocking up all heat
             | exchange surfaces.
             | 
             | In the case of a megapack, cooling isn't critical to safety
             | - as long as you're happy to stop using a battery when too
             | hot, it won't get hotter. The reason to cool is is so you
             | can keep using the battery.
        
         | Gepsens wrote:
         | offline monitoring is what caused tchernobyl, when will ppl
         | learn ?
        
           | nathancahill wrote:
           | Were you going for Chernobyl?
        
             | jjoonathan wrote:
             | Were you going for tche[?]rnob[?]y[?]l?
        
       | cube00 wrote:
       | _> Shorter connection times to the SCADA system to help alert
       | Tesla with specific alarms._
       | 
       | Interesting that even after installation Tesla are still involved
       | in operationally managing the megapacks.
        
         | toomuchtodo wrote:
         | Tesla's model is they both sell the Megapack system and then
         | orchestrate it over its lifetime using their Autobidder
         | platform. The owner is responsible for financing, integration
         | with on site generation, and working with the local grid
         | operator.
        
       | aetherspawn wrote:
       | > "A new battery module isolation loss alarm has been added."
       | 
       | This is the worst fault possible in an EV 101 scenario right here
       | (touch metal -> instant death), so I'm surprised that with all
       | Tesla's experience, they didn't consider an isolation leak as a
       | serious fault. And I'm surprised that they allow the battery
       | monitoring system to be disabled during servicing, especially the
       | IMD (insulation monitoring device).
        
         | londons_explore wrote:
         | I am constantly surprised how many systems have no isolation
         | when it would be easy and cheap to add.
         | 
         | For example, typical solar inverter systems don't have
         | isolation between the AC and DC sides. That means any chafed
         | wire can be deadly. They do at least have leakage detection,
         | but set at a 300mA level, which probably won't save your life.
         | 
         | Considering solar inverters already uses high frequency
         | switching inside the per-string MPPT boost converter, it would
         | have cost mere cents to put two windings on that inductor
         | rather than one and get isolation with no downside.
         | 
         | The cynic in me says manufacturers don't add safety features
         | not required by law, even if zero cost, because in the future
         | laws might be updated to require that safety feature,
         | preventing reuse of hardware already sold, which is good for
         | business.
        
           | Filligree wrote:
           | > For example, typical solar inverter systems don't have
           | isolation between the AC and DC sides. That means any chafed
           | wire can be deadly. They do at least have leakage detection,
           | but set at a 300mA level, which probably won't save your
           | life.
           | 
           | This is very yikes. I just installed such a system.
           | 
           | Do you know any way to test if that's a problem? And is it
           | possible to fix without opening the inverter?
        
             | londons_explore wrote:
             | It's normally set that high by design because the solar
             | panels have substantial capacitance to ground (they are
             | large flat conductors sat just a few cm off the ground
             | after all). The capacitance to ground wouldn't be an issue
             | if not for the fact the inverter is non-isolated. That
             | means current can flow to/from the grid to charge and
             | discharge that capacitor, which is indistinguishable from
             | AC leakage.
             | 
             | Some inverters will allow you to lower the leakage
             | threshold (usually with settings in a service menu), but
             | then you're limited to just attaching 3 or so panels or
             | getting false isolation trips.
        
               | Filligree wrote:
               | In my case the panels are, in fact, mounted on wooden
               | brackets a good 1.5 meters off the ground. On the other
               | hand, there's 20 m^2 of them.
        
           | Reason077 wrote:
           | Huh? 300 mA should barely give you a tingle unless you're
           | talking about some _very_ high voltages. What am I missing
           | here?
        
             | throwaway9870 wrote:
             | A basic knowledge of electricity. 100-200mA will kill you.
             | 
             | https://academic.oup.com/ptj/article-
             | abstract/46/9/968/46379...
             | 
             | I have heard people say "that can't be right, because a car
             | battery can source 100+ amps and touching those terminals
             | doesn't kill me!" The reason is because you have a high
             | enough impedance that 100mA doesn't flow from a 12V source
             | through your body.
        
               | Reason077 wrote:
               | Embarrassingly, I have managed to shock myself several
               | times during my life on 240V mains. Once quite recently
               | while working on a light fitting at a friend's flat and
               | not realising that someone had flipped the circuit back
               | on at the circuit breaker!
               | 
               | That shock was certainly quite unpleasant, but despite
               | touching my sweaty skin against live wires, it seems to
               | have been far from fatal.
               | 
               | Surely the dangerous situations are live-to-earth shocks,
               | which could potentially run across your whole body
               | (rather than just a hand or finger, as in my case). But
               | that's why we have RCD/GFCI protection, right? Those will
               | trip with tiny fault currents, certainly much less than
               | 300 mA.
               | 
               | Secondly, aren't "Type B" RCDs required on solar
               | inverters? Those will detect and trip on DC fault
               | currents as low as 30 mA, not 300!
        
               | nielsbot wrote:
               | you need "Lock Out Tag Out" lol
               | 
               | https://en.wikipedia.org/wiki/Lockout-tagout
        
               | james400 wrote:
               | "It's not the voltage that kills you, it's the amps!"
               | Wouldn't power (W) (or joules) be a better way to phrase
               | it? Because as you said, you can't have 100mA flowing
               | through your heart unless you ALSO have stiff enough
               | source to actually supply that current - which implies a
               | high compliance voltage, can't escape ohms law.
        
               | joncrocks wrote:
               | "It's the volts that jolt, but the mills (mA) that kills"
               | - The phrase a schoolteacher used when I was a lad.
        
               | jrockway wrote:
               | V = I * R
        
               | jhgb wrote:
               | The voltage across the heart will be rather bounded if
               | you fix the current at 100mA, though. Hearts will not
               | differ significantly from each other.
        
               | Johnny555 wrote:
               | Not really, whether it takes 50V with wet skin or 500V
               | with dry skin, it's the current that kills you, not the
               | watts
        
               | kortex wrote:
               | No, it's not the power, either, as low resistant paths
               | can be extremely dangerous (such as wet skin). Really,
               | it's a 2 dimensional space that makes for a less catchy
               | aphorism. "It's not the voltage that kills you, it's the
               | combination of voltage and conductivity".
               | 
               | Honestly I kinda hate that saying. It's like "it's not
               | the fall that kills you, it's the sudden decelleration on
               | impact." For most situations people encounter, it's high
               | voltage sources with more than enough power which are
               | dangerous.
        
               | jfrunyon wrote:
               | "The combination of voltage and conductivity" is ...
               | current, no?
        
               | jackweirdy wrote:
               | Here is medhi sadaghdar (electro boom) putting 11v at
               | 150A through his tongue
               | https://www.youtube.com/watch?v=XDf2nhfxVzg
        
               | aaronmdjones wrote:
               | GP mentioned impedance, not resistance. You won't feel
               | anything touching the 12/24V terminals in your car
               | because they're DC. Your skin has a high resistance, but
               | when faced with AC, has a low impedance. This makes AC
               | much more dangerous, as you conduct 120V AC much better
               | than 120V DC.
               | 
               | Even 50mA will likely kill you, as outlined on the "death
               | graph" as we electricians call it. This is independent of
               | voltage.
               | 
               | https://upload.wikimedia.org/wikipedia/commons/7/7f/IEC_T
               | S_6...
               | 
               | Blue is harmless and imperceptible, green is harmless,
               | yellow is harmful, red is fibrillation.
               | 
               | Edit: This illustrates why 30mA (or less) RCD protection
               | is common (and required) in various jurisdictions,
               | depending on the kind of circuits you're serving.
        
               | Reason077 wrote:
               | Right, and in particular, "Type B" RCD protection is
               | required for solar inverters in various jurisdictions.
               | These provide protection against DC fault currents.
        
               | jhgb wrote:
               | > This makes AC much more dangerous, as you conduct 120V
               | AC much better than 120V DC.
               | 
               | But at higher frequencies, you should experience the skin
               | effect, right?
        
             | chockablock wrote:
             | > A domestic power supply voltage (110 or 230 V), 50 or 60
             | Hz alternating current (AC) through the chest for a
             | fraction of a second may induce ventricular fibrillation at
             | currents as low as 30 milliamperes (mA).With direct current
             | (DC), 300 to 500 mA is required.
             | 
             | https://en.m.wikipedia.org/wiki/Electrical_injury
        
               | catmanjan wrote:
               | So you'd have to have a wire pressed against your chest
               | with your back on the ground... Unlikely but yes possible
               | hazard when working on solar panels
        
               | jfrunyon wrote:
               | Think about the path the electricity would have to follow
               | between, say, an arm and a leg, or even both arms.
        
               | rainbowzootsuit wrote:
               | These, and the GFCI outlets/breakers are calibrated
               | against injury for adults. The thresholds are lower for
               | children.
               | 
               | Mike Holt is an excellent instructor on the NEC and has
               | quite a few videos that speak about this topic.
               | 
               | https://m.youtube.com/user/MikeHoltNEC
        
           | shadowpho wrote:
           | I spent a bit working on various power supplies and sadly
           | isolation is non-trivial nor cheap. Adding isolation
           | (transformer vs inductor) requires changing control signals,
           | control mechanism, size. It costs far more then mere cents,
           | and loses some efficiency.
        
           | baybal2 wrote:
           | Aren't you are mistaking galvanic isolation with insulation?
        
             | aetherspawn wrote:
             | Galvanic isolation is useful because it means that you have
             | to touch 2 specific points on the affected unit
             | simultaneously to die, rather than 1 point. Galvanically
             | isolated systems can detect leaks on both the positive and
             | negative sides by using a dual channel IMD. Any insulation
             | issue is bad, but this method of detection can usually
             | detect it before it's able to instantly kill someone per-
             | se. Electric vehicles are an example of a galvanically
             | isolated system (from earth) with dual channel IMD, hence
             | you can have massive leaks such as 8-20mA before it becomes
             | a safety issue.
        
               | baybal2 wrote:
               | Yes..., but what difference it makes to this fire?
               | 
               | Are you working in EE?
        
               | aetherspawn wrote:
               | Galvanic isolation probably wouldn't have prevented this
               | fire, it sounds like the cells just shorted together.
               | They would have had to short over several cells, since a
               | non-trivial voltage is required to break down coolant, so
               | having maintenance contactors to break the pack up into
               | 20V or so segments may have prevented this fire.
               | 
               | Using a mineral oil type coolant that is not electrically
               | conductive (such as used in Tesla vehicles) would have
               | also helped to prevent this fire.
               | 
               | The batteries should be galvanically isolated from the
               | casing so that if liquid causes a current flow from any
               | point in the pack, then the maintenance contactors can be
               | opened and the opposite side current path for the leak is
               | interrupted. We can only assume that they are already
               | (galvanically isolated) since anything else would be
               | bizarre.
        
             | [deleted]
        
       | dhsysusbsjsi wrote:
       | Reading this it's a classic systems failure: multiple defensive
       | barriers gone wrong through poor safety planning. It's
       | reminiscent of the Victorian ESSO gas plant accident
       | https://en.wikipedia.org/wiki/Esso_Longford_gas_explosion
        
         | krisoft wrote:
         | In what way is it reminding you of that incident?
         | 
         | The paralels I can see:
         | 
         | - both involve energy installations.
         | 
         | - both happened in the same state.
         | 
         | The differences I can see:
         | 
         | - one involves a gas utility the other an electric one
         | 
         | - one has killed and hurt workers while the other did not
         | killed nor injured anyone.
         | 
         | - one happened after several years of operation, the other
         | happened during installation.
         | 
         | - one left the state without energy service for 20 days, the
         | other did not affect service at all.
         | 
         | Don't get me wrong. I love reading about how complex things go
         | wrong, one of my favourite pastimes. So I thank you for your
         | link. It just doesn't seem that similar to me. Not sure you
         | would be citing the same case for example have they not
         | happened in the same state.
         | 
         | If I have to choose a failure which the Big Battery fire
         | reminds me of I would rather choose the Florida International
         | University pedestrian bridge collapse. Why? It seems these
         | batteries had adequate safety functions and monitoring planned
         | in for their operation. Just these systems were not activated
         | during the installation in the right order. Similarly with the
         | bridge it seems they did calculations with the full bridge in
         | place, but nobody seems to have checked if the intermediate
         | steps during the construction will stay up too.
         | 
         | Another similarility (to my untrained eyes) is the aim to
         | install a system fast. The bridge project wanted to be a
         | flagship for accelerated bridge building, and the big selling
         | point of these Megapack installations is how fast they can be
         | comissioned. With the bridge project we know that this demand
         | for speediness was a contributing factor. Was it maybe also
         | with the Big Battery fire too?
        
           | throwaway0a5e wrote:
           | >In what way is it reminding you of that incident?
           | 
           | It's just in group signaling. "Hey this reminds me of
           | <vaguely related thing>" is a more polite way of saying "look
           | I know about X, I'm like you, gimme dat virtue points"
           | 
           | You see this on literally every virtue points (i.e. up-vote)
           | based form of social media that's big enough that any given
           | participant can blend in with the crowd.
           | 
           | The behavior is endemic these days you can't even post a
           | picture of a rotten and falling down deck on the internet
           | these days without some jerk derailing everything by dropping
           | a link to the wikipedia page on the hyatt regency and then
           | several more riding their coattails with quotes copied from
           | the page.
           | 
           | He probably doesn't even consciously realize he's doing it.
        
       | walrus01 wrote:
       | for people who might say 'oh, but these batteries are so
       | dangerous!'
       | 
       | How many cooling system leaks (radiator+water pump related
       | plumbing) result in vehicle engine fires per year?
       | 
       | I imagine the largest insurance companies have reasonably good
       | data on this as a cause of total-loss of a vehicle.
       | 
       | How many times have you seen in person, or seen a photo of a
       | burned out RV that somebody pushed too hard up a mountain pass
       | without keeping an eye on the engine temperature?
        
         | pengaru wrote:
         | Overheating ICEs blow head gaskets and warp cylinder heads,
         | they don't generally start fires.
         | 
         | Fuel leaks and/or exhaust system failures, especially on
         | turbocharged vehicles however...
        
         | driverdan wrote:
         | > How many cooling system leaks (radiator+water pump related
         | plumbing) result in vehicle engine fires per year?
         | 
         | Almost none. Overheating is highly unlikely to cause a fire.
         | Fuel leaks cause fires.
        
         | DoingIsLearning wrote:
         | Read the doc, this has nothing to do with lithium batteries as
         | a component. This was a System Requirements/Hazard Analysis
         | failure.
         | 
         | The fault lies square with Tesla. No amount of RV analogies can
         | dilute this.
        
           | walrus01 wrote:
           | The point was that plenty of other energy dense things with
           | radiator-based liquid cooling loops lack proper monitoring
           | systems.
           | 
           | Not excusing Tesla but the actual number of heat producing
           | things that catch on fire every year (in general) because of
           | cooling pump/cooling loop failure is quite a lot. In many
           | categories of equipment.
        
         | phaedrus wrote:
         | You have a gross misconception of the relative temperatures of
         | components in internal combustion engines, and you're using a
         | faulty conclusion based on the same misunderstanding as
         | supposed supporting evidence.
         | 
         | I assure you an RV or other gas/diesel vehicle does NOT
         | suddenly go "pop!" and produce an engine fire when the needle
         | reaches the right hand side of the temperature gauge.
         | 
         | The temperature gauge warns you when the coolant is at risk of
         | boiling; it's not a warning that the engine is about to
         | spontaneously combust.
        
           | walrus01 wrote:
           | right, that's why every burned out at the roadside RV I've
           | seen in my lifetime (probably more than a dozen now) was on
           | the upward slope of a high mountain pass, or at the peak...
           | 
           | one of the points I was trying to make is that people don't
           | maintain liquid cooling loops in general, and that's one of
           | the more common instances of it.
           | 
           | do you live somewhere flat?
           | 
           | go ask the towtruck drivers who work the coquihalla highway
           | in BC how many vehicle fires they see every year, and _where_
           | those vehicle fires occur.
        
       | nraynaud wrote:
       | how much would you ask to be paid to pressure test the coolant
       | system of a giant bomb in situ?
        
       | baybal2 wrote:
       | One advantage of LFP batteries is that they can survive much
       | higher temperatures without degradation.
       | 
       | If you can make battery packs air cooled, that's a big, big
       | weight saver.
        
       | userbinator wrote:
       | From the title I first thought this would be about a battery fire
       | that happened in the late 1800s.
        
         | bjowen wrote:
         | In a much cooler reality, it is, and it's the other Tesla.
        
       | RicoElectrico wrote:
       | So, they'll have to take note from their nuclear colleagues'
       | playbook? About passive safety.
        
         | cotillion wrote:
         | Well, the conclusions seem to suggest they have passive safety.
         | 
         | "The affected Megapacks failed safely despite total loss."
        
           | epistasis wrote:
           | I think that people understand the level of engineering and
           | technology that goes into batteries and their designs these
           | days. There's a ton of talent, a ton of continuous
           | innovation, it in the end it too often gets relegated to a
           | black box for energy in and energy out. Which is in some ways
           | a testament to the quality of the engineering.
        
         | karlkloss wrote:
         | Why? The factory didn't burn down, and there was no widespread
         | radioactive contamination.
         | 
         | It's a battery pack, not a stash of U235 above the critical
         | mass. Every recycling facility is more dangerous.
        
           | ashtonkem wrote:
           | Because fires are bad, and they can kill workers and shut
           | down facilities?
        