       | bob1029 wrote:
       | Direct liquid cooling makes a shitload of sense from a purely
       | academic standpoint.
       | 
       | At what point in power density would it not even matter if the
       | datacenter was at meat locker temperatures? I feel like we are
       | getting pretty damn close.
       | 
       | The efficiency gains at scale must be really good. I can see why
       | this is not super popular though.
        
       | opwieurposiu wrote:
       | A lot of high power plasma processing equipment is water cooled.
       | RF and DC generators, matches, etc. Stuff that requires a coax
       | cable as thick as your arm. The switch from air to water cooling
       | happens around .5-1Kw, this is the same range they seem to be
       | targeting for datacenter stuff.
       | 
       | Aside from leaks, the building maintenance staff really needs to
       | stay on top of the cooling water chemistry. Cooling loops tend to
       | make slime and if you let it get out of control it clogs up
       | everything and becomes a real problem to clean.
        
       | jmcguckin wrote:
       | One place i worked used flourinert to cool the circuit cards of a
       | integrated circuit tester.
       | 
       | Each card has a 'cold plate' where the outside of the cold plate
       | has a brass tube brazed to the plate in a serpentine pattern
       | leading to two quick disconnect connectors that automatically
       | engage/disengage when the card in inserted or removed from the
       | card cage.
       | 
       | The other side of the cold plate (the 'inside') has spring loaded
       | fingers to pull the heat away from chips. We had some chips that
       | dissipated over 100W.
       | 
       | This worked great - you'd lose maybe 1 drop of fluid per card
       | insertion, etc. We used flourinert, but DI water, mineral oil or
       | water with ethylene glycol could be used as well.
        
       | Const-me wrote:
       | Technically, the best solution is distribute. Specifically,
       | compute stuff on user's own devices, as opposed to moving
       | everything to these centralized clouds controlled by just a few
       | large corporations.
       | 
       | Too bad that's unlikely to happen.
        
       | devwastaken wrote:
       | I'm curious why liquid cooling for computers still uses
       | compression fittings and other odd methods. Compression fittings
       | are widely out of favor due to their tendency to leak, and
       | nowadays everything is copper, pex, or metal+flared fittings. I
       | wonder if there's a PC running PEX-A for tubing.
       | 
       | Further thoughts:
       | 
       | Brake lines use flared fittings, with either metal tubing or
       | plastic tubing with metal ends. Uses a special bolt that allows
       | liquid through the pipe to enter the caliper, and is removable.
       | 
       | I would imagine something like that could work to make the lines
       | to the individual servers serviceable without relying on flaky
       | plastic "quick connects".
        
         | namibj wrote:
         | I'm about to get me proper industrial quick disconnects (the
         | hard part is the disconnecting, not the connecting, as
         | otherwise a simple valve on each end and a screwed fitting
         | would suffice) for my workstation, so that I can put a large
         | radiator outside of my room and still have an easy-to-carry
         | system when I need to be somewhere else and have a proper
         | computer. It's just no longer silent at that point.
         | 
         | These quick disconnects are polymer, but that's in large part
         | due to corrosion resistance. They are also rated to ~8 Bar and
         | also vacuum, if one would use the latter.
         | 
         | Also, for flexible tubing, compression fittings don't seem like
         | such a bad idea. Yes, don't use them for rigid pipes (PEX
         | counts there, for connecting purposes), but the only thing
         | better than squishing the hose into a seal-barb seems to be
         | welding the hose to the connector...
        
         | intpx wrote:
         | RGB-life liquidcooling != Data Center liquid cooling
         | 
         | They have precision dry break quick connects. They use crazy
         | jacketed hoses with PTFE liners and copolymer sheating,
         | sometimes with reinforcment layers. The coolant is pumping
         | through at an operating pressure of 10bar @ 200C. These
         | applications exceed the limits of potable water and hydronic
         | heating systems
        
           | [deleted]
        
           | namibj wrote:
           | For what reason would a datacenter operate 200C coolant?
        
             | bob1029 wrote:
             | The only reasonable thing I can come up with is we got an
             | extra 0 here. 20C/68F sounds like a more practical
             | temperature for keeping the computers alive.
        
           | KaiserPro wrote:
           | 10 bar to the rack that seems a bit high?
           | 
           | How does the coolant get to 200c, that'd imply some sort of
           | inline heatpump right?
        
         | lazide wrote:
         | Compression fittings are generally more convenient and cost
         | effective than Pex or copper in small volumes and with little
         | experience. The only downside as you note is leaks if someone
         | doesn't do them right (or as time passes), but that tends to be
         | more of problem at higher household service line pressures (60+
         | psi)
         | 
         | If it is a low pressure recirculation system, you can get by
         | with almost no tools and most people if they read instructions
         | at all probably won't mess it up bad enough to have a leak.
         | 
         | The brake line connectors could be interesting, but aren't
         | likely to work well stock - brakes are very low flow, high
         | pressure as they are 'dead ended' hydraulic systems used to
         | transfer force, not loops for cooling purposes. Also those
         | bolts can work loose, and then you have leaks. Brakes require
         | experienced technicians or people die, so folks working on
         | brakes tend to be the more qualified and experienced mechanics,
         | and they make sure to torque to spec, clean surfaces, do proper
         | prep, etc. which is not what you want to have to worry about
         | from an idiot proofing perspective.
        
           | heelix wrote:
           | Man, if only copper was easy. One of the gotchas is most
           | connectors for CPU, graphics cards, and chipsets tend to use
           | the G1/4" ends up having metric on the other side. 12mm or
           | 13mm. Most copper pipe is .5", which works out to about
           | 12.7mm. You have to be really picky with couplers if you want
           | to use copper. PTEG/Acrylic is less great for things that
           | would be banged around and a pain, compared to if you know
           | how to actually do copper.
        
             | namibj wrote:
             | Or you just use actual metric copper pipes in 12mm....
        
               | lazide wrote:
               | Good luck finding those easily around here!
        
       | titzer wrote:
       | Cool stuff. I remember seeing liquid cooling solutions that
       | immersed the entire system in some non-conductive fluid, like
       | mineral oil. Of course, that's a bit messy, but I wonder if all
       | components were designed to be immersed, whether it'd be feasible
       | to consider the entire server enclosure as the watertight unit,
       | e.g. in a rack, rather than hoses to individual servers.
        
         | toast0 wrote:
         | Immersing the rack as a unit means commiting to servicing the
         | rack as a unit.
         | 
         | Some organizations do that. Bring the rack up, do a burn in
         | test, then run it until enough bits are broken that it makes
         | sense to take the whole thing down to swap bits or until it's
         | obsolete enough to justify replacing the whole thing. But a lot
         | of organizations want to replace storage or ram or ?? as it
         | fails without turning off the whole rack.
         | 
         | Would bring more meaning to the words 'draining' a
         | server/rack/data center though.
         | 
         | Actually reading the article, they have immersion chambers
         | which look more or less like a rack rotated 90 to be
         | horizontal. Which means you can pull a rack mount server out
         | vertically to service it, but it also takes up a lot more
         | floorspace (at least 3x to my eye), which reduces density. If
         | you were OK with reduced density, you could leave your racks
         | 2/3rds empty or use 2U servers instead of 1U servers, etc.
         | Power and cooling requirements are already the bottleneck for
         | most datacenters rather than floorspace, and liquid cooling
         | doesn't really help a lot there (unless you can pump your
         | working fluid outdoors, but usually it's just dumping the heat
         | elsewhere in the room more effectively, sometimes with more
         | power for a pump than for fans).
        
         | PragmaticPulp wrote:
         | Submersion cooling systems are shown on page 3 of the article.
         | The page selector is at the bottom of the text. I like how they
         | have to have hoists to raise and lower the servers into the
         | bath because they're so heavy.
        
           | titzer wrote:
           | Cool, I should have read more of the article.
        
       | bastardoperator wrote:
       | Data centers have been using chilled water to cool air for a long
       | time. It would be interesting to see cooling delivered directly
       | to the CPU/GPU from a/the chiller.
        
         | sschueller wrote:
         | No thanks, the equinix DC I have dealt with has had so many
         | chiller outages I am glad that the fans were able to keep the
         | temp low enough to prevent damage.
         | 
         | If I lost all cooling the equipment would literally be toast.
        
           | wmf wrote:
           | Almost no server equipment will be damaged by loss of
           | cooling; it will shut down before damage occurs.
        
             | sschueller wrote:
             | Repeat overheating even with auto shutoff can result in
             | solder joints going bad and reducing the life span of hw.
             | Additionally not all components that are overheating will
             | cause on auto shutoff.
        
       | KaiserPro wrote:
       | > Data center liquid cooling is going to happen
       | 
       | I mean yeah, but I doubt its going to be mainstream anytime soon.
       | 
       | At the moment its cheaper to just use forced air, and yolo it.
       | Running at half density is expensive, but not as expensive as
       | backfilling everything with liquid cooling.
       | 
       | Also given that we've been able to run 2 socket blades at full
       | bore without liquid cooling kinda suggests its not actually
       | needed.
       | 
       | Having radiators on the front/back of the rack directly works
       | really well. We had it on our render farm. combine that with
       | enforced hot isle/cold isle and you can reduce the need for
       | aircon dramatically, without multiplying your leak risk by at
       | least 96 times.
       | 
       | The massive problem here is that its really difficult to hotswap
       | anything. Those cooling pipes need to be removed before you can
       | pull out the server. Unless they are self sealing (like hydrolic
       | lines) then you need to drain the loop first. That costs a
       | shitload of money at scale.
        
         | apex3stoker wrote:
         | >I doubt its going to be mainstream anytime soon.
         | 
         | I would like to have a quiet and powerful machine for deep
         | learning. The best one I found come from NVIDIA DGX station. It
         | uses liquid cooling and is <35dB acoustics. The problem is that
         | it is too expensive and, last I check, I think it requires
         | buying support contract from third-party.
         | 
         | If liquid cooling is what it takes to have a quiet powerful
         | machine, I hope it will be mainstream.
         | 
         | Source: https://www.nvidia.com/content/dam/en-
         | zz/Solutions/Data-Cent...
        
           | gambiting wrote:
           | Why does it need to be quiet though? Don't most of these live
           | in a datacentre with no humans around? I assume you will say
           | you want to keep it in your office or similar, but then I'll
           | just ask again - why exactly?
        
         | ksec wrote:
         | >The massive problem here is that its really difficult to
         | hotswap anything.
         | 
         | And this problem has been there since Day 1 ( For well over a
         | decade ). And no one seems to have solve it. It make sense if
         | you treat the whole Rack as a single entity with water cooling.
         | But for individual server I still dont understand how and why
         | liquid cooling could benefits.
        
           | sandworm101 wrote:
           | >> I still dont understand how and why liquid cooling could
           | benefits.
           | 
           | Because liquid cooling is only a marginal benefit for current
           | hardware, hardware designed to be air cooled. If liquid
           | cooling becomes a norm we should start seeing hardware
           | designed with the expectation of liquid cooling. That could
           | mean greater component density and greater power
           | concentration --> greater speeds. One wonders what CPUs would
           | be like if they were designed with the expectation of liquid
           | cooling, water within a millimetre from the heat source
           | rather than the metal heat spreaders that currently top most
           | chips.
           | 
           | How many fans are in a modern server rack? Liquid cooling
           | could theoretically replace all of those with one moving
           | part, one pump impeller.
        
             | meepmorp wrote:
             | > How many fans are in a modern server rack? Liquid cooling
             | could theoretically replace all of those with one moving
             | part, one pump impeller.
             | 
             | Or maybe more than one impeller, because at least with the
             | fans, cooling continues if there's a failure in one of
             | them.
        
               | sandworm101 wrote:
               | Well, perhaps coolant would be delivered to racks at a
               | particular psi/volume just as electricity is today
               | provided at a particular voltage and current. Then an
               | entire datacenter would be served by a handful of massive
               | pumps. Server racks might then have no moving parts,
               | which couldn't harm reliability.
        
           | mey wrote:
           | The problems that FAANG have aren't the problems most of us
           | have. Edit: That don't work for those companies. Different
           | levels of scale certainly.
           | 
           | https://xkcd.com/1737/
        
       | ChuckMcM wrote:
       | I cannot help but chuckle at how what is old is new again here.
       | In the 70's and early 80's all of IBM's mainframes supported
       | liquid cooling. Basically when a computer "uses" X kW of power it
       | really means that it generates that many kW of heat while it is
       | operating. Removing heat at scale has been a thing for a long
       | time.
       | 
       | And what was alluded to in the video is the thermal mass of 'air'
       | kind of sucks. So the old design of chilling air down to 67
       | degrees and filling a room with that air so that it can circulate
       | around electronics putting out prodigious amounts of heat, and
       | then collected and re-cooled, is not nearly as efficient as one
       | would like.
       | 
       | Cooling water, piping it to the heat exchanger in the back door
       | of the rack and then (unlike the video's idea) sucking air
       | through it first, and then pushing the cooled air over the
       | electronics to 're-heat' it, works better. Then you don't really
       | care what temperature the air in the data center itself is as
       | long as the heat exchanger can remove 'x' watts of heat from it
       | before it gets blown over the computers. Suck air in from the
       | floor (the coolest air) and blow it out the top (where it
       | continues on to the ceiling).
       | 
       | Still, that only doubles the power capacity of the racks (maybe
       | 2.5x if the heat exchanger is filled with actively chilled water)
       | 
       | Prior to heat exchanger doors people would have "cold" aisles and
       | "hot" aisles. The cold air from the CRAC units would come up from
       | the floor behind the servers, get sucked through them and
       | exhausted forward into the "hot" aisle. There is a whole little
       | mini industry of "cold air containment" which has stuff to build
       | doors/covers for the cold aisle so that all of that air is sucked
       | through servers.
        
       | swayvil wrote:
       | Why is that guy wearing a mask? Either servers are infectious or
       | wearing a mask is now just "expected".
       | 
       | Do any of you do a doubletake when you see people on tv without a
       | mask?
       | 
       | Have you noticed characters in cartoons wearing masks? Check out
       | the weather frog, sitting alone in the middle of a forest,
       | wearing a mask.
       | 
       | This how we become Morlocks.
        
       | 20100thibault wrote:
       | Liquid cooling also enables heat recovery and free cooling all
       | year long. Here's a project using liquid cooling to recover
       | energy from Data centers to heat greenhouses.
       | https://www.qscale.com/
        
       | alberth wrote:
       | What makes this time different?
       | 
       | I've literally heard this is coming to datacenter for 20 YEARS
       | and it hasn't yet.
       | 
       | Liquids like mineral oil, etc to be the cooling agent yet it
       | never gains measured adoption.
       | 
       | And with so much of servers now being centrally managed by just a
       | few major cloud providers (AWS, Azure, etc) - unless you can
       | break into those few accounts - how will this time be any
       | different than the past?
       | 
       | From 2003:
       | https://www.hitachi.com/New/cnews/E/2003/0217/index.html
        
         | kllrnohj wrote:
         | > Liquids like mineral oil, etc to be the cooling agent yet it
         | never gains measured adoption.
         | 
         | I've never seen a serious attempt to do mineral oil cooling
         | outside of funny gag setups. It was never really pitched as a
         | future of cooling. There's other attempts at other liquids for
         | submersion cooling, but that always seems like a bit of a
         | stretch.
         | 
         | Beyond that, liquid cooling _has_ taken over. That Hitachi
         | post, for example, seems to be about AIOs which are now very
         | common on desktops with the AIO market exploding over the last
         | ~5 years. Nearly every laptop also employs a form of  "liquid
         | cooling" these days with either heatpipes or vapor chambers.
         | 
         | As for "what makes this time different" for the datacenter,
         | well heat density continues to rise. >100 CPU cores per 2U rack
         | are trivial to achieve now, and more are readily plausible. GPU
         | accelerators are also more common than ever, and are pushing
         | staggering power draws (like the 8x 400W NVIDIA A100 in a
         | single 4U chasis the article talks about). You can keep
         | spending more power on fans, but there's diminishing returns
         | there not to mention the power consumption of the fans
         | themselves becomes non-trivial.
        
       | cyberge99 wrote:
       | I think datacenters will opt for more ARM architectures before
       | introducing liquid at scale. Things like Gravitron and Apple
       | Silicon are changing the landscape there.
        
         | sudosysgen wrote:
         | Graviton and Apple Silicon still don't offer significant
         | performance per watt improvements versus EPYC. I don't think it
         | will make or break the need for liquid cooling.
        
         | PragmaticPulp wrote:
         | The article is mostly about cooling high power, GPU-like
         | accelerator units that consume 400-600W or more.
         | 
         | Even with power efficient architectures, the push to scale up
         | core count and increase density will still drive toward more
         | liquid cooling.
        
         | atty wrote:
         | I'm pretty sure AMD offers perf/watt that is in the ballpark of
         | ARM chips, and I'm guessing Intel, if they ever get on a
         | similar process node again, will be able to get close.
         | 
         | None of that changes the need for accelerators though. Nvidia
         | et al want to make the biggest chips they can, and at some
         | point that means water cooling.
        
         | ksec wrote:
         | You still have a 280W CPU, instead of 64 Core you now have 128.
         | And if thermals permits they would like 128 x86 Core or 256 ARM
         | Core.
         | 
         | Samsung just announced their work of 7xxGB of DDR5 per stick.
         | With a future roadmap of 1TB per stick at a request of
         | hyperscaler. Along with 400W or 500W GPU.
         | 
         | And when you have many new packaging technology where each die
         | could be a 100W TDP you quickly run into all sort of thermals
         | limits. And there are all sort of HPC and niche that wants
         | super powerful Server.
        
       | jeffbee wrote:
       | It seems odd to discuss liquid cooling but spend the first part
       | of the article talking about AC PDUs and their issues. If you are
       | able to use liquid cooling in a data center, aren't you also
       | sophisticated enough for modern DC to point-of-load?
       | 
       | I can see why supermicro needs to pursue this direction, but it
       | seems inevitable that their business will get eaten up by OCP and
       | integration at the rack, row, and building level.
        
       | zamalek wrote:
       | > need to handle cooling at >1kW/U
       | 
       | I wonder if this waste heat could be used to power active/phase
       | change cooling.
        
         | icegreentea2 wrote:
         | The challenge is that it's really low grade heat (< 100C). DC
         | waste heat would probably find its best use in district heating
         | applications (though I did read about some cases still using a
         | heat pump to boost the waste heat stream even higher - still
         | for district heating though).
        