https://engineering.stackexchange.com/questions/50939/why-are-two-wires-used-in-railway-overhead-equipment Stack Exchange Network Stack Exchange network consists of 180 Q&A communities including Stack Overflow, the largest, most trusted online community for developers to learn, share their knowledge, and build their careers. Visit Stack Exchange [ ] Loading... 1. 0 2. +0 3. + Tour Start here for a quick overview of the site + Help Center Detailed answers to any questions you might have + Meta Discuss the workings and policies of this site + About Us Learn more about Stack Overflow the company + Business Learn more about our products 4. 5. current community + Engineering help chat + Engineering Meta your communities Sign up or log in to customize your list. more stack exchange communities company blog 6. 7. Log in 8. Sign up Engineering Stack Exchange is a question and answer site for professionals and students of engineering. It only takes a minute to sign up. Sign up to join this community [ano] Anybody can ask a question [ano] Anybody can answer [an] The best answers are voted up and rise to the top Engineering 1. Home 2. 1. Public 2. Questions 3. Tags 4. Users 5. Unanswered 3. Teams Stack Overflow for Teams - Start collaborating and sharing organizational knowledge. [teams-illo-free-si] Create a free Team Why Teams? 1. Teams 2. Create free Team Teams Q&A for work Connect and share knowledge within a single location that is structured and easy to search. Learn more Why are two wires used in railway overhead equipment? Ask Question Asked 2 days ago Modified yesterday Viewed 4k times 25 5 $\begingroup$ While watching the train videos, I came across these overhead wires. After searching on the internet, I found that both catenary and contact wires carry the same voltage and are connected by vertical wires called "droppers" at intermediate points (please refer to image 1 from this video. In the first image, it looks like the upper wire is supporting the lower wire, but in the second image from this video they look different. Why are two wires used if one wire is sufficient to carry current? railway overhead equipment-1 Railway Overhead equipment-2 mechanical-engineering electrical-engineering structural-engineering solid-mechanics power-transmission Share Improve this question Follow edited yesterday user avatar CommunityBot 1 asked 2 days ago user avatar mech_duckmech_duck 35133 silver badges44 bronze badges New contributor mech_duck is a new contributor to this site. Take care in asking for clarification, commenting, and answering. Check out our Code of Conduct. $\endgroup$ 4 * 3 $\begingroup$ I think the catenary wire holds up the contact wire. $\endgroup$ - user253751 2 days ago * $\begingroup$ Sounds like a variation on "Kelvin Connectors" in that the contact wire carries all the current, and the catenary wire is held at the same voltage to avoid high E-fields in the local structure. $\endgroup$ - Carl Witthoft 2 days ago * $\begingroup$ Both of your links seem to point to the same video, btw. The function of the catenary wire and the droppers is indeed to support the contact wire and in particular to keep it as straight as possible. In your second image there don't seem to be catenaries at all, maybe because they're not needed due to low speeds (as is the case with many tram systems) but it's difficult to tell based on the low-quality screenshot. $\endgroup$ - JohannesD 2 days ago * 1 $\begingroup$ What a fascinating question! +1 An interesting exercise will be to follow the catenary lines to their ends and see and enjoy the mechanical tensioning apparatus there which maintains constant tension despite thermal expansion and contraction of the wire throughout the day and year. $\endgroup$ - uhoh 2 days ago Add a comment | 3 Answers 3 Sorted by: Reset to default [Highest score (default) ] 65 $\begingroup$ Overhead line worker here. It's about speed. To answer your question, the purpose of the catenary wire is to get the contact wire to lay flat, so it isn't catenary itself. In your second photo, there is only the contact wire, so the contact wire will be somewhat catenary no matter how tightly you pull it. enter image description here Exaggerated considerably. Trolley wire is kept under 500-2000kg of tension. The problem is that a catenary curve is only smooth up to the anchor point, then it makes a fairly abrupt turn at the apex. From the pole or pantograph's perspective, it is actually this flipped over - because of the considerable up-force of the pole or pan. So the pan sees it as an inverse catenary, being dragged downward as it nears the anchor. enter image description here The zone of flex; the pole/pan is riding the top of this. So the pole/pan sees a nasty "knot" at each anchor where it's being forced downward to meet the anchor. Deflection force is abrupt and at maximum right before the anchor and minimum right after the anchor, so it's quite a jolt of vertical acceleration and jerk. I tried to illustrate just how hard the kink can be right near the anchor, but it doesn't show that well. But I've seen wire permanently bent this way on either side of an anchor. As you go faster, you increase wear and tear on the hardware, and increase wire breaks. Wire breaks are a nightmare to operations, as you might imagine. And mind you, arc fault detection is relatively new. The only thing that keeps the pantograph from "ski jumping" clear off the wire is its spring up-force. But that only works up to a certain speed. To go faster, we must get rid of that kink at the anchors. It would be ideal if the wire just hung flat. So, obviously, the catenary style of wiring. enter image description here I wasn't going to post an "entirely obvious" drawing of catenary overhead, but now I have a reason. The catenary wire is galvanized steel. The droppers are typically steel (there are plenty). The wire clamps are typically bronze. The contact wire is copper. Systems of this design are good for as fast as 200 kph/125 mph, depending on how well it's maintained. And it is compatible with trolley poles rather than pantographs - in fact, the North American "interurban railway" network of high speed lines was fully built out before pantographs entered the scene. The Chicago North Shore Line operated 100 mph/160 kph (when ICC inspectors weren't around) using poles on catenary. But you can see now, when a pole or pan passes along the wire, it still "hops up" but in a different manner altogether. enter image description here The pantograph or pole's uplist force creates a local rise in the wire as it passes, but it's very consistent; no stress hotspots. Note the droppers are made to rise up in a controlled way. The next evolution of speed requires abandoning the trolley pole (at least for regular trains). Up until this point, wire tension was set as a compromise to work well in the summer without deforming or breaking the wire in the winter. In order to go faster than this, we really need "winter tension" all year, and that means the line must be actively tensioned with counterweights. (so in the winter, the shrinking metal lifts the counterweights instead of breaking). This requires interrupted segments of trolley wire, which preclude use of trolley poles for any but maintenance equipment (which could stop and move the pole to the other wire). So why no catenary in photo 2? Because you're in "the twisty bits" there. Trains can't go all that fast, so catenary is not required. What about current? Why is the catenary wire energized? Plain and simple: because NOT energizing it would be a pain in the @$$, and make repairing the wire very dangerous. Wire line work (on sub-5000 volt lines) is done with the trolley energized, from car roofs or platforms made of insulating material. Workers on the platform are simply energized at trolley voltage, and that is fine. Ground is lethal to them, and nothing may ever be passed up except via an insulated rope. Trailing a wire down is folly. As such, these systems take care that everything near the trolley wire is on the "energized" side of the insulator, or attached to a wood pole. Does the catenary wire add to current ampacity? Sure, but it's just considered a bonus. Current is augmented by intentional feeder wire run parallel to the track, with bridging over to the trolley wire made every few poles depending on the voltage and draw. (due to the numerous droppers, tying to the catenary wire will suffice). Indeed, image 2 shows a feeder wire - the solitary wire up on the pole. I don't know if there is a ground feeder wire, it would be on the ground obviously, but heavy section welded rail doesn't need it so much with advanced signal systems that allow both rails to be grounded and continuous. That is a lot of steel, and it has to be there anyway. Image 2 also shows a 3-phase distribution line which feeds substations along the line. That suggests to me that this line is a DC voltage, generally the highest practical DC voltage is 3000V. (AC railroads use single-phase AC because they prefer 1 contact wire; distribution feeding a single-phase AC line is best single-phase, since phase conversion at every substation would suck). Typically, feeder wire is fat AA-1350 aluminum such as 1750 ACSR or larger. (ACSR has a cluster of steel wires in the center for carrying capacity). Sorry, that is 1750 kcmil (thousand circular mil). By contrast the contact wire is typically 4/0 (212 kcmil) or 250 or 300 kcmil and pure electrical copper. If I were king, and I'm not, the contact wire would be steel and the catenary wire would be ACSR (steel wires about the size of the current catenary wire) and would serve as feeder. The many droppers would assure adequate current. Copper gone; copper theft gone. What about keeping the trolley wire centered? Oh, you don't want that. First, a trolley pole doesn't care. Second, if you studiously keep the trolley wire dead center on track, your pantographs will get a deep groove in the middle. You want the wire to continuously skiff back and forth across the contact surface of the pantograph. This also makes alignment a whole lot easier, because you don't have to lol. Now if poles are in play, curves need to have typically a tilted catenary to keep the wire path relatively smooth. If you are pantograph only, no worries, just let it "polygon". What else about the second photo? I mentioned the contact wire, feeder and distribution wire - just by happenstance, way off in the distance is the national utility's power transmission lines up on the usual pylons. That's probably where the distribution wire gets its power. The 5th wire in play is crossing at an angle, and that is just to physically hold the contact wire in the air. It is crossing from a pole on the outside of the curve to a pole on the inside of the curve, which judging by the lump just barely visible, looks like it has a trolley wire hanger there. This is one of several ways of supporting trolley wires in curves. I mean you could do the whole shebang with wires simply zig-zagging between alternate poles; however in this case they are dancing around a bridge and creek at an oblique angle. You say "How is that cross-wire supporting the contact wire? The hanger wire between them has gone slack." Yes, because the contact wire is being pushed up by the train's pantograph. Share Improve this answer Follow edited yesterday user avatar Glorfindel 26611 gold badge22 silver badges99 bronze badges answered 2 days ago user avatar Harper - Reinstate UkraineHarper - Reinstate Ukraine 1,55066 silver badges1010 bronze badges $\endgroup$ 8 * 7 $\begingroup$ So that's what you do ;) ... Transmission line guys in helicopters get all the glory, but bonded, 12' off the ground? No thank you. $\endgroup$ - Mazura 2 days ago * 1 $\begingroup$ Mathematical fun fact: If the catenary wire has most of the mass of the system, it will trace a catenary, while if the contact line and droppers carry most of the mass, then the catenary wire will actually follow a parabola (in the mathematically ideal "extremely many droppers, entirely straight contact wire" scenario, of course). Since it's likely closer to 50-50 here (I have never seen these lines up-close, but the mass distribution doesn't look as lopsided as on, say, a suspension bridge, or a pure catenary with nothing below it), the catenary wire lies between a catenary and a parabola. $\endgroup$ - Arthur yesterday * 1 $\begingroup$ Is work really done on live wires? I've always seen workers ground the wires to the track (with thick clamps) while they are working on them so if the wires are accidentally turned on they are immediately shortened to ground. $\endgroup$ - Michael yesterday * 7 $\begingroup$ @Mazura Only half the time. I hear he spends the other half of the time reporting lost neutral faults in 240/120V split-phase wiring! $\endgroup$ - user253751 yesterday * 1 $\begingroup$ Created an account here just to +1 that, that was eye opening. I'm going to think of this every day on my commute. $\endgroup$ - Clumsy cat yesterday | Show 3 more comments 12 $\begingroup$ It isn't to do with current-carrying capacity; it is to maintain good contact between the current-carrying wire and the pantograph pickup on the locomotive, as it allows the contact wire to be relatively straight, with very little sag, so the pantograph doesn't have to make a lot of vertical movement. The faster the train, the harder it is to keep good contact; when that is lost, there will be arcing, which reduces the life of the pantograph. Share Improve this answer Follow edited 2 days ago answered 2 days ago user avatar jaybenjayben 34144 bronze badges $\endgroup$ 3 * $\begingroup$ That explains the existence of the support wire, but not why the wire and the droppers need to be conductive. $\ endgroup$ - Carl Witthoft 2 days ago * 8 $\begingroup$ @CarlWitthoft, the non-contact wires don't need to be conductive. They are just conductive coincidentally, as most metals are conductive, and they are physically attached to the real conductor in order to support its shape. The whole wirework, and their support brackets, are charged because it is simpler and more reliable to have a smaller number of insulator elements only on the stanchions which support the brackets, than to have an insulator between each drop wire and the conductor. $\endgroup$ - Steve 2 days ago * 1 $\begingroup$ The catenary wire is in parallel with the contact wire so it helps reduce voltage drop along the line too. I would think it makes contact wire replacement fairly straight-forward too. $\endgroup$ - Transistor 2 days ago Add a comment | 6 $\begingroup$ Why two wires: A wire hanged at two points sags (it forms a "catenary curve"). The pantograph can only handle a certain sag before losing contact and arcing. The acceptable sag depends on the train speed. Higher speed = less acceptable sag. One can tension the wire in order to decrease the sag, but the wire has limited mechanical properties (it is made of copper that worsens the problem). What else can we do? Use a second wire with better mechanical properties (steel) above the first one, allow it to sag however it wants at some moderate tension and use droppers to adjust the contact wire as straight as possible. Why the second wire is energized? There is a pretty much non-trivial part of this construct: the isolators. It is hard to create an isolator that is at the same time mechanically strong, electrically strong (25kV are no joke) and resistant to aging. The result: they are somewhat expensive, they have somewhat limited lifespan and they are heavy. They also leak some current (= power loses), especially in moist weather. They are also a point of failure. A single of them broken = power off, traffic stop, repair team dispatched. If you put them at every dropper, you will have 5x ... 10x of them with the corresponding increase of power loss, installation cost, weight (stronger poles and catenary) and maintenance downtime. Engineering conclusion: use the bare minimum of them, 2 per pole. Bonus point: the catenary wire carries some current (probably not much, because it is steel and the contact wire is copper). The catenary being energized also prevents (to an extent, but important in some places) sabotages and stealing. In regard to the second picture: It is still the catenary supporting the contact wire, but in a simpler setup for probably lower speeds and lower overall requirements. The catenary alternates between the left and right poles (at turns the poles are only at the outer side of the turn), supplying points to hang the contact wire over the rails. This second setup is made only with simple, straight poles and uses only a single isolator per pole. Share Improve this answer Follow edited 2 days ago answered 2 days ago user avatar fraxinusfraxinus 23111 silver badge33 bronze badges $\endgroup$ Add a comment | Your Answer mech_duck is a new contributor. Be nice, and check out our Code of Conduct. [ ] [ ] [ ] [ ] [ ] [ ] [ ] [ ] [ ] [ ] [ ] [ ] [ ] [ ] [ ] Thanks for contributing an answer to Engineering Stack Exchange! * Please be sure to answer the question. Provide details and share your research! But avoid ... * Asking for help, clarification, or responding to other answers. * Making statements based on opinion; back them up with references or personal experience. Use MathJax to format equations. MathJax reference. To learn more, see our tips on writing great answers. Draft saved Draft discarded [ ] Sign up or log in Sign up using Google Sign up using Facebook Sign up using Email and Password Submit Post as a guest Name [ ] Email Required, but never shown [ ] Post as a guest Name [ ] Email Required, but never shown [ ] Post Your Answer Discard By clicking "Post Your Answer", you agree to our terms of service, privacy policy and cookie policy Not the answer you're looking for? Browse other questions tagged mechanical-engineering electrical-engineering structural-engineering solid-mechanics power-transmission or ask your own question. The Overflow Blog * Software is adopted, not sold (Ep. 441) * An unfiltered look back at April Fools' 2022 Related 6 Why are turbo compound engines not more widely used? 0 Safely Measuring Voltage from Solar Panels in an Experimental Research Field 3 Why are both conductors in a High Voltage Direct Curent powerline isolated from ground? 1 Why do we have two different Elastic Modulus in Tension and Torsion? 0 Equations of condition: why are two moment equations around a hinge dependent? Hot Network Questions * Null conserved angular momentum * Making text larger without changing size of superscript? * If Earth had a smaller radius, but was rotating at the same speed, would its day be shorter? * How do I use Feeds Tamper to process multiple CSV columns into a single field? * Why does Emacs not load the init file when using sudo? * Swap lines in a file * How long before departure do I need to get to Lille Europe for a Eurostar to Brussels? * what's the purpose of /home/user/bin directory * "media: inaccessible or not found" error when attempting to control device volume via ADB * Does Gandalf ever say this in the book "The Hobbit", or is it made up for the movie? * What's the earliest point in human civilisation that anyone has time-travelled back to, in Star Trek? * Tricks for fitting a 7/16" bit into a 3/8" drill? * Why must we say Wo Ke Yi Cong Ni Na Er Jie Qian Ma ? instead of just Wo Ke Yi Cong Ni Jie Qian Ma ? * Does a compact contractible metric space have a point that is fixed by all isometries? * Are smartphone cells actually charged with 9V using QC and other techniques or does the smartphone always step down the voltage? * Why are there pairs of wind instruments in a symphonic orchestra? * How can farming be used to gain energy that powers a crystal? * Has any US state passed a law in a language other than English? * what is this design element called? * Criteria for Hausdorff * Is it safe to ride on wheels with rusted spoke eyelets? * Am I using the word "Hajimari" correctly in judo? * Prove that convergent integrals are equal * # ## ## ## ## ## ## ## ## ## # more hot questions Question feed Subscribe to RSS Question feed To subscribe to this RSS feed, copy and paste this URL into your RSS reader. [https://engineering.] * Engineering * Tour * Help * Chat * Contact * Feedback Company * Stack Overflow * Teams * Advertising * Collectives * Talent * About * Press * Legal * Privacy Policy * Terms of Service * Cookie Settings * Cookie Policy Stack Exchange Network * Technology * Culture & recreation * Life & arts * Science * Professional * Business * API * Data * Blog * Facebook * Twitter * LinkedIn * Instagram Site design / logo (c) 2022 Stack Exchange Inc; user contributions licensed under cc by-sa. rev 2022.5.13.42123 Your privacy By clicking "Accept all cookies", you agree Stack Exchange can store cookies on your device and disclose information in accordance with our Cookie Policy. Accept all cookies Customize settings